AAON F-060 User Manual

F1 Series
Indoor Air Handing Units
Installation, Operation
& Maintenance
QUALIFIED INSTALLER
Improper installation, adjustment, alteration, service or maintenance can cause property damage, personal injury or loss of life. Installation and service must be performed by a trained, qualified installer. A copy of this IOM should be kept with the unit.
These instructions are addressed primarily to the installer; however, useful maintenance information is included. This manual should be kept with the unit for future reference.
NOTICE
FOR YOUR SAFETY Do not store or use gasoline or other flammable vapors and liquids in the vicinity of this or any other appliance.
If the information in this manual is not followed exactly, a fire or explosion may result causing property damage, personal injury or loss of life.
Table of Contents
Safety .............................................................................................................................................. 6
F1 Base Model and Features Description ..................................................................................... 10
General Description ...................................................................................................................... 11
Codes and Ordinances ............................................................................................................... 11
Receiving Units ......................................................................................................................... 12
Before Beginning Installation ................................................................................................... 13
Storage ....................................................................................................................................... 13
Installation..................................................................................................................................... 14
General ...................................................................................................................................... 14
Service and Installation Clearance ............................................................................................ 14
Floor Mounted Units ................................................................................................................. 14
Suspended .................................................................................................................................. 14
Sealing ....................................................................................................................................... 15
Cooling Equipment ................................................................................................................... 15
Heating Equipment .................................................................................................................... 16
Field Wiring - MCA and MOP ................................................................................................. 16
Heat Pump ................................................................................................................................. 17
ECM Driven Fan ....................................................................................................................... 17
Reheat Coil Refrigerant Piping ................................................................................................. 18
Condensate Piping ..................................................................................................................... 20
Electrical .................................................................................................................................... 20
Thermostat ................................................................................................................................. 20
Filters ......................................................................................................................................... 20
Charging Refrigerant ................................................................................................................. 20
Evaporator Coil ......................................................................................................................... 22
Startup ........................................................................................................................................... 24
General ...................................................................................................................................... 24
Check-Out ................................................................................................................................. 24
Procedures ................................................................................................................................. 24
Electric Heat Section Procedures .............................................................................................. 25
Refrigerant Cooling Section Procedures ................................................................................... 25
Optional Equipment Procedures ................................................................................................ 25
Commissioning .......................................................................................................................... 26
Air Balancing ............................................................................................................................ 26
Water Balancing ........................................................................................................................ 26
Controls ..................................................................................................................................... 26
Operation and Maintenance .......................................................................................................... 26
General ...................................................................................................................................... 26
Maintenance Schedule ............................................................................................................... 26
Lubrication ................................................................................................................................ 27
Blower Assembly ...................................................................................................................... 27
Coils .......................................................................................................................................... 27
Heating ...................................................................................................................................... 27
Filters ......................................................................................................................................... 27
3
Refrigerant Piping ..................................................................................................................... 28
Determining Refrigerant Line Size ........................................................................................... 29
Equivalent Line Length ............................................................................................................. 29
Predetermined Line Sizes .......................................................................................................... 32
Refrigerant Piping Diagrams ........................................................................................................ 35
Thermostat Installation and Wiring .............................................................................................. 43
F1 Series Startup Form ................................................................................................................. 53
Maintenance Log .......................................................................................................................... 56
Literature Change History............................................................................................................. 57
R58420 · Rev. B · 120509
(ACP 29902)
Index of Table and Figures
Tables:
Table 1 - Electric Heat Minimum Circuit Ampacity .................................................................... 16
Table 2 - Electric Heat Maximum Overcurrent Protection ........................................................... 17
Table 3 - Factory Preset Air Flow................................................................................................. 17
Table 4 - Cooling Fan Speed Tap Settings ................................................................................... 17
Table 5 - Climate Settings ............................................................................................................. 18
Table 6 - Heating Fan Speed Tap Settings .................................................................................... 18
Table 7 - Acceptable Air-Cooled Refrigeration Circuit Values ................................................... 22
Table 8 - Predetermined Line Sizes for F1 and CB Series Matched Systems with Two Step R-
410A Scroll Compressors ............................................................................................................. 33
Figures:
Figure 1 - Typical Vertical and Horizontal Unit Installation Methods ......................................... 15
Figure 2 - Example Configuration of ECM Fan Taps .................................................................. 17
Figure 3 - Riser Height Versus Total Equivalent Line Length for R-410A Split System
Applications with Two Step Scroll Compressor CB-024 through CB-060 units. ........................ 34
Figure 4 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit above
Condensing Unit. .......................................................................................................................... 35
Figure 5 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit below
Condensing Unit ........................................................................................................................... 36
Figure 6 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit above
Condensing Unit with Optional Accumulator .............................................................................. 37
Figure 7 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit below
Condensing Unit with Optional Accumulator .............................................................................. 38
Figure 8 - Heat Pump Piping Diagram with Indoor Unit above Outdoor Unit............................. 39
Figure 9 - Heat Pump Piping Diagram with Outdoor Unit above Indoor Unit ............................. 40
Figure 10 - Heat Pump Piping Diagram with Modulating Hot Gas Reheat and Indoor Unit above
Outdoor Unit ................................................................................................................................. 41
Figure 11 - Heat Pump Piping with Modulating Hot Gas Reheat and Outdoor Unit above Indoor
Unit ............................................................................................................................................... 42
Figure 12 - 2 Stage Cooling with Electric Heat ............................................................................ 43
Figure 13 - 2 Stage Cooling with Heat Pump and Electric Heat .................................................. 44
Figure 14 - 2 Stage Cooling and Electric Heat with Hot Gas Reheat and Humidistat ................. 45
Figure 15 - Main Control Board for Units Equipped with Modulating Hot Gas Reheat .............. 46
Figure 16 - Field Wiring Connections for an F1 Series Air Handling Unit. ................................ 47
Figure 17 - 5kW Electric Heat ..................................................................................................... 48
Figure 18 - 10 kW Electric Heat .................................................................................................. 49
Figure 19 - 15 kW Electric Heat .................................................................................................. 50
Figure 20 - 20 kW Electric Heat ................................................................................................. 51
Figure 21 - 25 kW Electric Heat ................................................................................................. 52
5
Safety
NOTE - Notes are intended to clarify the unit installation, operation and maintenance.
CAUTION - Caution statements are given to prevent actions that may result in
equipment damage, property damage, or personal injury.
WARNING - Warning statements are given to prevent actions that could result in
equipment damage, property damage, personal injury or death.
DANGER - Danger statements are given to prevent actions that will result in equipment
damage, property damage, severe personal injury or death.
Attention should be paid to the following statements:
ELECTRIC SHOCK, FIRE OR EXPLOSION HAZARD
Failure to follow safety warnings exactly could result in dangerous operation, serious injury, death or property damage.
Improper servicing could result in dangerous operation, serious injury, death or property damage.
Before servicing, disconnect all
electrical power to the unit. More than one disconnect may be provided.
When servicing controls, label all
wires prior to disconnecting. Reconnect wires correctly.
Verify proper operation after
servicing. Secure all doors with key-lock or nut and bolt.
Electric shock hazard. Before servicing, disconnect all electrical power to the unit, including remote disconnects, to avoid shock hazard or injury from rotating parts. Follow proper Lockout-Tagout procedures.
FIRE, EXPLOSION OR CARBON MONOXIDE POISONING HAZARD
Failure to replace proper controls could result in fire, explosion or carbon monoxide poisoning. Failure to follow safety warnings exactly could result in serious injury, death or property damage. Do not store or use gasoline or other flammable vapors and liquids in the vicinity of this appliance.
6
During installation, testing, servicing and troubleshooting of the equipment it may be necessary to work with live electrical components. Only a qualified licensed electrician or individual properly trained in handling live electrical components shall perform these tasks.
Standard NFPA-70E, an OSHA regulation requiring an Arc Flash Boundary to be field established and marked for identification of where appropriate Personal Protective Equipment (PPE) be worn, should be followed.
GROUNDING REQUIRED
All field installed wiring must be completed by qualified personnel. Field installed wiring must comply with NEC/CEC, local and state electrical code requirements. Failure to follow code requirements could result in serious injury or death. Provide proper unit ground in accordance with these code requirements.
To prevent injury or death lifting equipment capacity shall exceed unit weight by an adequate safety factor. Always test-lift unit not more than 24 inches high to verify proper center of gravity lift point to avoid unit damage,
UNIT HANDLING
injury or death.
ROTATING COMPONENTS
Unit contains fans with moving parts that can cause serious injury. Do not open door containing fans until the power to the unit has been disconnected and fan wheel has stopped rotating.
Failure to properly drain and vent coils when not in use during freezing temperature may result in coil and equipment damage.
Rotation must be checked on all MOTORS AND COMPRESSORS of 3 phase units at startup by a qualified service technician. Scroll compressors are directional and can be damaged if rotated in the wrong direction. Compressor rotation must be checked using suction and discharge gauges. Fan motor rotation should be checked for proper operation. Alterations should only be made at the unit power connection
7
CAUTIO
CAUTIO
Do not use oxygen, acetylene or air in place of refrigerant and dry nitrogen for leak testing. A violent explosion may result causing injury or death.
WARNING
Always use a pressure regulator, valves and gauges to control incoming pressures when pressure testing a system. Excessive pressure may cause line ruptures, equipment damage or an explosion which may result in injury or death.
Do not work in a closed area where refrigerant or nitrogen gases may be leaking. A sufficient quantity of vapors may be present and cause injury or death.
Do not clean DX refrigerant coils with hot water or steam. The use of hot water or steam on refrigerant coils will cause high pressure inside the coil tubing and damage to the coil.
N
To prevent damage to the unit, do not use acidic chemical coil cleaners. Do not use alkaline chemical coil cleaners with a pH value greater than
8.5, after mixing, without first using an aluminum corrosion inhibitor in the cleaning solution.
N
Some chemical coil cleaning compounds are caustic or toxic. Use these substances only in accordance with the manufacturer’s usage instructions. Failure to follow instructions may result in equipment damage, injury or death.
Risk of injury from hot parts – Disconnect all power, close all isolation valves and allow equipment to cool before servicing equipment with heating coils. Hot water will circulated even after the power is off.
8
PVC (Polyvinyl Chloride) and CPVC (Chlorinated Polyvinyl Chloride) are vulnerable to attack by certain chemicals. Polyolester (POE) oils used with R-410A and other refrigerants, even in trace amounts, in a PVC or CPVC piping system will result in stress cracking of the piping and fittings and complete piping system failure.
1. The unit is for indoor use only. See
General Information section for more unit information.
2. Every unit has a unique equipment
nameplate with electrical, operational, and unit clearance specifications. Always refer to the unit nameplate for specific ratings unique to the model you have purchased.
3. READ THE ENTIRE INSTALLATION,
OPERATION AND MAINTENANCE MANUAL. OTHER IMPORTANT SAFETY PRECAUTIONS ARE PROVIDED THROUGHOUT THIS MANUAL.
4. Keep this manual and all literature
safeguarded near or on the unit.
9
F1
Series and
Generation
F1 Base Model and Features Description
A
-
Rev.
BASE MODEL
SERIES AND GENERATION
F1
REVISION
A = Design Sequence
UNIT SIZE
024 = 24 MBtu/h (2 ton) 036 = 36 MBtu/h (3 ton) 048 = 48 MBtu/h (4 ton) 060 = 60 MBtu/h (5 ton)
VOLTAGE
1 = 208-230V/1Φ/60Hz C = 115V/1Φ/60Hz
APPLICATION
V = Vertical Position (Up-flow) M = Multi-Position (Up-flow or Horizontal)
HEATING
0 = No Heat A = 5 kW B = 10 kW C = 15 kW D = 20 kW E = 25 kW G = Hot Water Heating H = Hot Water Heating - No Cooling
FEATURE 1: MOTORS
A = ECM - 1/2 hp B = ECM - 3/4 hp C = ECM - 1.0 hp
FEATURE 2: FILTERS
0 = Standard - 1” Fiberglass
060
-
Unit Size
1
-
Voltage App. Heat Mtrs Filters Cntls Blank Refri. Blank Cabinet Special
M
-
C
-
C 0 0 0 C 000 0 0
FEATURE 3: CONTROLS
0 = Standard - Terminal Block
FEATURE 4: BLANK
0 = Standard
FEATURE 5: REFRIGERATION
0 = Standard - Split System Air Conditioner C = Split System Heat Pump D = Split System Air Conditioner + Modulating Hot Gas Reheat F = Split System Heat Pump + Modulating Hot Gas Reheat
FEATURE 6: BLANK
0 = Standard
FEATURE 7: BLANK
0 = Standard
FEATURE 8: BLANK
0 = Standard
FEATURE 9: CABINET
0 = Standard - Embossed Galvanized Steel A = Painted Cabinet Exterior
FEATURE 10: SPECIAL
0 = Standard X = Special Price Authorization
10
General Description
F1 Series air handling units are designed for safe operation when installed, operated and maintained within design specifications and the instructions set forth in this manual. It is necessary to follow these instructions to avoid personal injury or damage to equipment or property during equipment installation, operation, start-up and maintenance.
Improper installation, adjustment, alteration, service or maintenance can cause property damage, personal injury or loss of life. Installation and service must be performed by a qualified installer. A copy of this IOM should be kept with the unit.
This equipment is protected by a standard limited warranty under the condition that initial startup and maintenance is performed according to the instructions set forth in this manual. This manual should be read in its entirety prior to installation and before performing any service or maintenance work.
These units must not be used as a “construction heater” at anytime during any phase of construction. Very low return air temperatures, harmful vapors, and misplacement of the filters will damage the unit and its efficiency.
Certification of Cooling Models
a. Certified for use with a residential
remote R-410A condensing unit with a two-step compressor.
b. Certified for indoor installation only
Certification of Cooling and Reheat Models
a. Certified for use with a residential
remote R-410A condensing unit with a two-step compressor and hot gas dehumidification capabilities.
b. Certified for indoor installation only
Certification of Electric Heat Models
a. Certified as an electric heating air
handling unit with a cooling coil.
b. Certified for indoor installation only.
Codes and Ordinances
F1 Series units have been tested and certified, by ETL, in accordance with UL Safety Standard 1995/CSA C22.2 No. 236.
System should be sized in accordance with the American Society of Heating, Refrigeration and Air Conditioning Engineers Handbook.
Installation of F1 Series units must conform to the ICC standards of the International Mechanical Code, the International Building Code, Installation of Air Conditioning and Ventilating Systems Standard, NFPA 90A, and local building, plumbing and waste water codes. All appliances must be electrically grounded in accordance with local codes, or in the absence of local codes, the current National Electric Code, ANSI/NFPA 70 or the current Canadian Electrical Code CSA C22.1.
Important: The United States Environmental Protection Agency (EPA) has issued various regulations regarding the introduction and disposal of refrigerants in
11
this unit. Failure to follow these regulations
CAUTIO
quip
may harm the environment and can lead to the imposition of substantial fines. Because regulations may vary due to passage of new laws, AAON suggests a certified technician perform any work done on this unit. Should you have any questions please contact the local office of the EPA.
WARNING
Do not, under any circumstances, connect ductwork to any other heat producing device such as fireplace insert, stove, etc. Unauthorized use of such devices may result in property damage, fire, carbon monoxide poisoning, explosion, personal injury or death.
It is the responsibility of the installing
contractor to comply with codes,
ordinances, local and municipal
building laws, and manufacturer’s
instruction. Personal injury and/or
equipment damage may result if
proper procedures are not followed.
The Clean Air Act of 1990 bans the
intentional venting of refrigerant as of
July 1, 1992. Approved methods of
recovery, recycling, or reclaiming
must be followed.
N
Always wear hand and eye protection when handling, installing, servicing, or maintaining equipment. Sharp edges, moving parts and fly debris may cause personal injury and care must be taken when working with
ment.
e
Any conflicting codes or regulations take precedence over the information in this manual. It is important that all installation and service work be performed by qualified professionals.
Receiving Units
All shipments are FOB from the factory. It is the responsibility of the receiving party to inspect the equipment upon arrival. Units should be inspected for damage that may have occurred in transit. Please do not refuse shipments!
Check the unit model number, specifications, electrical characteristics and accessories to determine if they are correct. In the event an incorrect unit is shipped, it must be returned to the supplier and must NOT be installed. The manufacturer assumes no responsibility for installation of incorrectly shipped units.
Do the following upon receipt:
1. Assure that freight carrier is in
compliance with Bill of Lading instructions.
2. Inspect delivery before signing Bill of
Lading.
If damage is found or items are missing:
1. Note on Bill of Lading immediately.
2. Call carrier immediately to file a freight
claim and to schedule an inspection.
3. Photograph damage if possible.
12
4. Do not move or discard damaged freight
packaging materials
5. After losses have been acknowledged by
the freight carrier, contact factory for a repair or replacement part quote.
6. With permission of freight carrier, order
parts and/or make repairs.
7. Stay in contact with freight carrier to
ensure payment of your claim.
Nameplate should be checked to ensure the correct model sizes and voltages have been received to match the job requirements.
If repairs must be made to damaged goods, then the factory should be notified before any repair action is taken in order to protect the warranty. Certain equipment alteration, repair, and manipulation of equipment without the manufacturer’s consent may void the product warranty. Contact the AAON Warranty Department for assistance with handling damaged goods, repairs, and freight claims: (903) 236-4403.
Note: Upon receipt check shipment for items that ship loose such as filters, thermostats and remote sensors. Consult order and shipment documentation to identify potential loose-shipped items. Loose-shipped items may have been placed inside unit cabinet for security.
Dependent upon the optional accessories that were ordered, this equipment may contain fragile components and delicate electronics. Although the unit is constructed of sturdy materials, avoid impacts and handling methods that may damage internal apparatus and structure of the unit. Take care not to apply destructive force to coils, coil and drain stub-outs, or other parts protruding beyond the extents of the unit casing. Always handle the unit by its exterior casing and never by any of the protruding parts.
Before Beginning Installation
Carefully read all instructions for the installation prior to installing unit. Make sure each step or procedure is understood and any special considerations are taken into account before starting installation. Assemble all tools, hardware and supplies needed to complete the installation.
Some items may need to be purchased locally. After deciding where to install unit, closely look the location over - both the inside and outside of home. Note any potential obstacles or problems that might be encountered as noted in this manual. Choose a more suitable location if necessary.
Storage
This equipment is not suitable for outdoor use or storage. Never place this equipment where it may be subjected to outdoor conditions such as rain, snow, humidity, extreme temperatures or corrosive chemicals.
If installation will not occur immediately following delivery, store equipment in a dry protected area away from construction traffic, and in the proper orientation as marked on the packaging with all internal packaging in place. Secure all loose-shipped items.
Keep equipment free from debris, and construction waste during installation. Foreign materials may adversely affect unit operation resulting in premature failures that will not be covered by the manufacturer’s warranty. Attach all service panels, and cover all exposed equipment when work is not being performed. Leave unit protected from other construction until start-up is to occur.
13
CAUTIO
This unit must be stored indoors if installation is not to occur immediately following delivery. Unprotected units could develop corrosion if left exposed to the environment. Damage resulting from improper storage will not be covered by the limited warranty.
N
Installation
AAON equipment has been designed for quick and easy installation.
General
F1 Series air handling units are designed as heating, cooling or combination units for indoor installation only. They are designed for R-410A refrigerant only. Flexible connectors are required on all duct connections to minimize air leaks.
Service and Installation Clearance
Before setting the air handling unit into place, caution must be taken to provide clearance for unit panels that must be accessible for periodic service. These areas contain the controls, safety devices, refrigerant piping, shut-off valves and filter access.
F1 series air handling units require a minimum of 36 inches of service clearance on the access panel side of the unit in order to ensure room for removal, replacement, or
service of coils and other components if necessary.
Note: An auxiliary (emergency) drain pan is recommended for all applications where there is a risk of water damage to surrounding structure or furnishings. Refer to local codes.
Floor Mounted Units
Make sure that the unit is level, and mounted on a field-supplied platform with a minimum height of 12” to allow for proper fall on the condensate line. Other installation provisions may be necessary according to job specifications. F1 series air handling units are designed for up flow and horizontal applications only.
Suspended
The F1 series multi-position air handling unit can be easily suspended for suspended horizontal installations. The air handling unit should be lifted into position, supporting the entire unit from the bottom throughout the lift. Suspend the air handling unit as shown in the following Figure 1. An auxiliary drain pan that covers the entire unit would be required for above ceiling installations.
The air handling unit must be installed level and care should be taken to prevent damage to the cabinet. Other installation provisions may be necessary according to job specifications and local code.
14
Figure 1 - Typical Vertical and Horizontal Unit Installation Methods
Sealing
It is very important to keep outside air from infiltrating the unit cabinet. Seal all piping penetrations with Armaflex, Permagum, or other suitable sealant. Also seal around drain connections, electrical connections, and other inlets where air may enter the cabinet. This is especially important when the unit is installed in an unconditioned area.
Cooling Equipment
Acceptable system design and installation will include consideration as follows:
Piping from the condensing unit to the indoor air handling unit is the responsibility of the installing contractor.
Only clean “ACR” tubing should be used.
Piping should conform to generally accepted practices and codes.
Care must be taken not to cross the circuits on reheat systems.
Once piped, the interconnecting piping and air handling unit MUST BE evacuated to 500 microns or less; leak checked and condenser shutoff valves opened to allow refrigerant flow to air handling unit. Charge unit with R-410A refrigerant to the recommended superheat/sub-cooling in the Charging Refrigerant section of this manual.
Make sure air handling unit thermal expansion valve bulb is mounted with good thermal contact on the suction line on a horizontal section, close to the evaporator but outside the cabinet in the 4 or 8 o’clock position and well insulated.
Lines should be fastened and supported according to local codes.
15
Heating Equipment
Hot Water Heating: Water supply lines must be insulated, properly fastened, drained and supported according to local code requirements.
Electric Heating:
Installing Electric Heat Strip into the Unit:
1. Remove front control panel(s) of the unit
2. Remove screws and panel covering heat
strip compartment
3. Open the heat strip kit and remove
assembly from package
4. Install strip heat into opening and secure
with 4 (four) screws
5. Install breaker assembly on bracket and
secure with breaker with 4 (four) screws
6. Make sure that breaker is in the OFF
position
7. Connect all control wires per wiring
diagram included in the unit
8. Pull and install power wires per wiring
diagram and MCA, MOP information herein and secure all wires firmly
9. Replace the front control panel(s) of the
unit
FIELD INSTALLED WIRES SHOULD BE SINGLE STRAND WIRES. USE OF ROMEX WIRES IS NOT ACCEPTABLE.
Heating is accomplished by passing electrical current through a specified amount of resistance heaters, which will produce the required heat. The indoor blower motor will energize at the same time as the heaters. Wiring to the air handling unit must be done in accordance with local electrical codes and/or standards. Check specified electrical rating and install with proper wire sizes. Also refer to wiring diagrams included with the unit for wire sizes and circuit breaker recommendations.
Field Wiring - MCA and MOP
Minimum Circuit Ampacity (MCA) and Maximum Overcurrent Protection (MOP) are necessary to correctly connect field wired equipment.
The calculations for the MCA and MOP are based on requirements of NFPA 70, the National Electrical Code (NEC) and CSA C22.1, the Canadian Electrical Code (CEC). The MCA is the minimum wire size needed to prevent the wiring from overheating during operating conditions for the life of the product. The MOP is the maximum allowable circuit breaker size that will properly disconnect power to the equipment under anticipated fault conditions.
In the following tables, locate the kW of the heater to be field installed, and then choose the corresponding MCA and MOP values to correctly size the wire gauge(s) and circuit breaker(s), respectively.
Table 1 - Electric Heat Minimum Circuit
Ampacity
230V 208V
kW kW MCA MCA MCA
5 3.75 26.0 10 7.50 52.1 15 11.25 52.1 26.0 20 15.00 52.1 52.1 25 18.75 52.1 52.1 26.0
Overcurrent protection less than that recommended on the unit's "Specification Sheet" could result in unnecessary fuse failure and service call. The manufacturer bears no responsibility for damage caused to the equipment as a result of not using the recommended size for the protective devices as listed on the unit's rating plate.
Line 1 Line 2 Line
3
16
Table 2 - Electric Heat Maximum
A
A
A
Overcurrent Protection
230V 208V Line 1 Line 2 Line
3
kW kW MOP MOP MOP
5 3.75 30 10 7.50 60 15 11.25 60 30 20 15.00 60 60 25 18.75 60 60 30
Heat Pump
For heat pump equipped split system configurations, the heat pump is the primary heat source during a call for heat. During operation at low ambient temperatures where the heat pump alone cannot satisfy the space temperature set point, electric resistance heat elements are activated. Below about 17°F, only the electric heat is operable; the heat pump is not active.
ECM Driven Fan
The Electrically Commutated Motor (ECM) has selectable fan speeds as determined by the configuration of four pins as shown in FIGURE 2.
----
B C
D
HEAT COOL ADJUST DELAY
- -
- -
- -
B C
D
- -
- -
- -
----
1
- -
+
- -
-
----
1
- -
----
B
- -
C
- -
D
- -
Figure 2 - Example Configuration of ECM
Fan Taps
Adjust the taps as desired for cooling, dehumidification, and heating according to the following instructions.
Cooling: Units are preprogrammed from the factory for a rated airflow rate of 400 cfm per ton as shown in Table 3.
Table 3 - Factory Preset Air Flow
Model Preset cfm
F1-060 2000 F1-048 1600 F1-036 1200 F1-024 800
* Maximum total static is 2.25” w.g.
The high speed for cooling may be selected by setting the COOL and ADJUST fan speed taps (shown in Figure 2). The setting combinations are shown in Table 4.
Note: On the ADJUST tap, both of the ‘1’ selections have the same effect on motor speed.
Table 4 - Cooling Fan Speed Tap Settings
F1-060/ F1-036/
F1-048 F1-024
(cfm) (cfm)
COOL
Tap
ADJUST
Tap
2000 1200 A 1 2000 1200 D 1
1840 1150 B + 1700 1020 A ­1700 1020 D ­1600 1000 B 1 1380 920 C + 1360 850 B ­1200 800 C 1 1020 680 C -
A signal from the thermostat, showing a need for dehumidification, will cause the unit to slow the fan speed in order to allow the air moving across the coil to get colder thereby better dehumidifying the air. Fist stage dehumidification has a low fan speed of 67% of the selected max speed. Second stage dehumidification has a fan speed of 45% of the selected max speed. NOTE: The Modulating Hot Gas Reheat option must be selected to have a second stage of dehumidification.
17
In this comfort cooling application of the ECM fan motor, heat and cool taps, A & D have the same effect on motor speed.
Humidity Control: Adjust the DELAY tap for humidity control that is suitable for the climate according to Table 5.
Table 5 - Climate Settings
CLIMATE DELAY Tap
Humid A Sub-humid/Dry B Semi-Arid C Arid/Hyper-Arid D
Heating: The fan speed for the heating cycle is selected by adjusting the HEAT tap (see FIGURE 2) according to TABLE 6.
Table 6 - Heating Fan Speed Tap Settings
F1-060/ F1-036/
HEAT Tap F1-048 F1-024
(cfm) (cfm)
1800 1000 A 1400 800 B 1200 600 C 1800 1000 D
ECM Fan Notes
1. Fan only = 50% of max speed
2. Dehumidifying speeds i) First stage dehumidification =
67% of max speed
ii) Second stage dehumidification =
45% of max speed
3. Green Light will blink once per every
100 CFM
4. Dehumidification terminal is BK. There
must be a constant voltage to this terminal, and when the voltage is
dropped then dehumidification mode will begin.
Fan wiring notes:
1. If only one stage of cooling is used then
jumper Y1 and Y2.
2. If unit is not heat pump capable then
jumper O and Y1.
3. If no humidistat is used then jumper BK
and R.
4. When only one stage of heat is used
jumper W1 and W2.
Reheat Coil Refrigerant Piping
The reheat coil is shipped already installed on the leaving air section of the air handling unit. A liquid receiver is shipped loose with the unit for field installation. (See Refrigerant Piping Section
to determine acceptable refrigerant line size.)
1. Run a hot gas line from the outdoor unit
and connect it to the inlet of the stub-out on the reheat coil. a. For vertical (up-flow) units. The
inlet connection is the left stub-out when facing the front of the unit. Connect the hot gas line from the outdoor unit to the left stub-out. Connect the check valve (shipped loose) to the right stub-out in a direction so that the refrigerant flow is leaving the right side of the coil. Be sure to not block access for
18
service of the air handling unit with the placement of the check valve.
b. For horizontal discharge units.
Connect the hot gas line from the outdoor unit to the upper stub-out connection of the reheat coil. Connect the check valve (shipped loose) to the lower stub-out in a direction so that the refrigerant is leaving the bottom side of the reheat coil. Be sure to not block access for service of the air handling unit with the placement of the check valve.
2. After installing the check valve, mount
the receiver (shipped loose). The receiver tank must be mounted horizontally for proper operation. The receiver may be mounted on the air handling unit or at a convenient location near the air handling unit. Be sure to not block access for service of the air handling unit with the placement of the receiver.
3. After mounting the receiver, run a liquid
line from the discharge of the check valve to the receiver tank through a tee connection. Run a liquid line from the condenser, through a check valve to the other side of the tee. Note check valve in
condenser liquid line is not used on heat pump models. (See Refrigerant Piping
Section to determine acceptable line size, location of components and to see a diagram depicting the finished line piping.)
4. After installing the receiver tank, run a
liquid line from the receiver outlet to the TXV. (See Refrigerant Piping Section to determine acceptable line size and to see a diagram depicting the finished line piping.)
5. After completing the reheat and liquid
lines, run a Suction line from the evaporator outlet to the outdoor unit shutoff valve (See Refrigerant Piping
Section to determine acceptable line size.)
6. After completing the refrigerant piping
installation, install the supply air temperature sensor (shipped loose) 18” from the leaving air outlet from the air handling unit.
7. After installing the supply air
temperature sensor, check that the reheat supply air temperature setpoint is correctly set on the control board. This temperature should be set to the desired space temperature when the unit is in cooling mode. If that temperature is unknown at the time of installation, set the setpoint to 72°F.
The reheat system provides for “neutral” (neither hot nor cold) air to the space so that the unit can dehumidify the air without over cooling or over heating the space. The desired leaving air temperature is set on the control board in the unit. The factory suggests a setpoint of 72°F for most applications; however, the setpoint is adjustable for more specific applications or differing comfort levels. The setpoint should be set for the desired temperature in the space during cooling mode. During dehumidification mode the cooling coil operates and the modulating valve in the reheat system meters the amount of hot refrigerant being directed to the reheat coil so that the cooled and dehumidified air is reheated, to the setpoint provided on the control board, to a room neutral temperature. This temperature setpoint and method of dehumidification allows for the home to be dehumidified even when there is not a need for cooling in the space.
Note: Systems with the modulating hot gas reheat option will require refrigerant to be field added because of the additional refrigerant components and piping associated with the system.
19
Condensate Piping
A drain trap must be connected to the drain pan at the unit. Condensate connections are provided on each side of the unit. Condensate piping should be installed according to local codes. The line should be the same pipe size as the drain nipple and should pitch downward toward the building drain.
All cooling coils must have drain pans equipped with “P” traps to avoid pulling air from outside the unit back through the drain line. All drain connection ports are sealed. Knock out only the connection port to be used. The trap should be located in warm ambient spaces. An additional drain pan may be installed under the air handling unit, and should include a separate drain line for overflow from the primary drain. An air break should be used with long runs of condensate lines.
Drain pans in any air conditioning equipment, even when they have a built-in slope to the drain, will have moisture present and will require periodic cleaning to prevent any build-up of algae or bacteria. Cleaning of the drain pans will also prevent any possible plugging of the drain lines, and overflow of the pan itself. Some means to clean out the “P” trap should be provided. Only qualified personnel should clean drain pans, drain lines, or the insides of equipment.
Electrical
Check the unit data plate to make sure it agrees with the power supply. Connect power to the unit according to the wiring diagram provided with the unit.
The power and control wiring may be brought in through the holes provided on the unit. Protect the branch circuit in accordance
with code requirements. If the control wires, are to run inside the same conduit, use 600­volt wire or as required by applicable codes.
The units must be electrically grounded in accordance with the National Electric Code, ANSI / UL 1995 when installed if an external source is utilized; in Canada use current C.S.A. Standard C22.2, No. 236, Canadian Electric Code Part 1.
Power wiring is to the unit terminal control board. The manufacturer has done all wiring beyond this point. Power can be applied to the unit after the control wiring is connected, and startup checks are complete.
Thermostat
Units without the neutral air dehumidification feature will operate with most common thermostats. Units with the neutral air dehumidification feature must use thermostats with a normally closed (NC) dehumidification option. The following stats have been approved for usage with the dehumidification feature.
Robertshaw Honeywell
9825i2
Filters
Open filter access bracket and slide correct filter in with arrow pointing towards the blower in the direction of airflow. Replacement filters are 20” x 20” x 1”.
Charging Refrigerant
The unit comes with full charge based on a 25-foot line set. Charging a system in the field must be based on determination of liquid sub-cooling and evaporator superheat. On a system with a thermostatic expansion valve, liquid sub-cooling is more representative of the charge than evaporator superheat but both measurements must be taken.
VisionPRO®IAQ
20
The Clean Air Act of 1990 bans the intentional venting of refrigerant as of July 1, 1992. Approved methods of recovery, recycling, or reclaiming must be followed.
Before Charging
The unit being charged must be at or near full load conditions before adjusting the charge.
Units equipped with hot gas reheat must have the hot gas reheat valves closed to get the proper charge.
Units equipped with hot gas reheat must be charged with the hot gas valve closed while the unit is in cooling mode.
After adding or removing charge the system must be allowed to stabilize, typically 10-15 minutes, before making any other adjustments.
The type of unit and options determine the ranges for liquid sub-cooling and evaporator superheat. Refer to Table 7 when determining the proper sub-cooling.
The vertical rise of the liquid line must be known in order to adjust the sub-cooling range for proper charge.
Checking Liquid Sub-cooling
1. Measure the temperature of the liquid
line as it leaves the condenser coil.
2. Read the gauge pressure reading of the
liquid line close to the point where the
temperature was taken. You must use liquid line pressure, as it will vary from discharge pressure due to condenser coil pressure drop.
3. Convert the pressure obtained in Step 2 to a saturated temperature using the appropriate refrigerant temperature-pressure chart.
4. Subtract the measured liquid line temperature in Step 1 from the saturated temperature in Step 3 to determine the liquid sub-cooling.
5. Compare calculated sub-cooling to TABLE 7 for the appropriate unit type and options.
Checking Evaporator Superheat
1. Measure the temperature of the suction line close to the compressor.
2. Read gauge pressure at the suction line
close to the compressor.
3. Convert the pressure obtained in Step 2 to a saturated temperature using the appropriate refrigerant temperature-pressure chart.
4. Subtract the saturated temperature in Step 3 from the measured suction line temperature in Step 1 to determine the evaporator superheat.
5. Compare calculated superheat to TABLE 7 for the appropriate unit type and options.
Adjusting Sub-cooling and Superheat Temperatures The system is overcharged if:
1. the sub-cooling temperature is too high and
2. the evaporator is fully loaded (low loads
on the evaporator result in increased sub­cooling) and
3. the evaporator superheat is within the temperature range as shown in TABLE 7 (high superheat results in increased sub­cooling)
21
Table 7 - Acceptable Air-Cooled
Refrigeration Circuit Values
Sub-cooling
with Hot
Gas Reheat
(°F)
Air-
Cooled
Condenser
Sub-
cooling
(°F)
12-18* 8-15** 15-22*
Superheat
(°F)
* Sub-cooling must be increased by 2°F per 20 feet of vertical liquid line rise for R­410A ** Superheat will increase with long suction line runs.
Correct an overcharged system by reducing the amount of refrigerant in the system to lower the sub-cooling.
Refrigerant overcharging leads to excess refrigerant in the condenser coils resulting in elevated compressor discharge pressure.
DO NOT OVERCHARGE!
The system is undercharged if:
1. The superheat is too high and
2. The sub-cooling is too low.
Correct an undercharged system by adding refrigerant to the system to reduce superheat and raise sub-cooling.
If the sub-cooling is correct and the superheat is too high, the TXV may need adjustment to correct the superheat.
Elevation Limitations
See Table 8 for rise and run limitations. All lengths listed are in equivalent feet. An equivalent foot of the line includes the
pressure drop of all valves, components, fittings and other pipes in the sections.
Evaporator Coil
Evaporator coils are shipped under high pressure. Use extreme care and follow the installation instructions provided with the evaporator coil to avoid personal injury.
The indoor coil is pressurized. The copper caps must be punctured to permit a gradual escape of the pressure prior to unsweating those caps. Immediately couple the tubing to the indoor unit to avoid exposing the coils to moisture. A properly sized filter drier is furnished in the condenser. When making solder connections, make sure dry nitrogen flows through the lines, when heating the copper, to prevent oxidization inside of the copper.
22
°F 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46
PSIG
78.3
80.0
81.8
83.6
85.4
87.2
89.1
91.0
92.9
94.9
96.8
98.8
100.9
102.9
105.0
107.1
109.2
111.4
113.6
115.8
118.1
120.3
122.7
125.0
127.4
129.8
132.2
Table 8 - R-410A Refrigerant Temperature-Pressure Chart
°F 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73
PSIG
134.7
137.2
139.7
142.2
144.8
147.4
150.1
152.8
155.5
158.2
161.0
163.8
166.7
169.6
172.5
175.4
178.4
181.5
184.5
187.6
190.7
193.9
197.1
200.4
203.6
207.0
210.3
°F 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99
100
PSIG
213.7
217.1
220.6
224.1
227.7
231.3
234.9
238.6
242.3
246.0
249.8
253.7
257.5
261.4
265.4
269.4
273.5
277.6
281.7
285.9
290.1
294.4
298.7
303.0
307.5
311.9
316.4
°F 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127
PSIG
321.0
325.6
330.2
334.9
339.6
344.4
349.3
354.2
359.1
364.1
369.1
374.2
379.4
384.6
389.9
395.2
400.5
405.9
411.4
416.9
422.5
428.2
433.9
439.6
445.4
451.3
457.3
°F 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150
PSIG
463.2
469.3
475.4
481.6
487.8
494.1
500.5
506.9
513.4
520.0
526.6
533.3
540.1
547.0
553.9
560.9
567.9
575.1
582.3
589.6
596.9
604.4
611.9
23
Startup
General
ONLY QUALIFIED, AUTHORIZED PERSONNEL SHOULD POWER ON, OR STARTUP THIS EQUIPMENT.
Before starting up the equipment, building construction should be complete, and start­up personnel should:
Have a working knowledge of general HVAC and mechanical commissioning procedures and practices.
Be familiar with unit functions, features, optional unit accessories, and all control sequences.
Have appropriate literature on hand for consultation.
Equipment operation during construction is not recommended. Construction site pollution can affect unit operation, and seriously degrade performance. Operation during construction will void all manufacturers’ warranties.
Before the structure is occupied, the installation, and/or startup personnel must take three essential steps:
1. Check-Out
2. Start-Up
3. Commissioning
Check-Out
Equipment should be thoroughly checked for loose wiring, a free spinning blower
wheel and well fitting access panels. Air handling units should not be operated without proper ductwork and access panels installed, except as required during start-up and air balancing.
1. Check all electrical connections to be
sure they are tight.
2. Open all access panels, and remove all
shipping screws, or restraints.
3. Clean out any debris that may be
present.
4. Check wheel alignment, and tightness of
fan drives.
5. Check bearing locking collars if
provided and fan wheel set screws for tightness.
6. Turn fan wheels to assure free rotation.
7. Ensure electrical supply matches the unit
nameplate.
8. Ensure condensate lines are correctly
connected.
9. Check local codes for any special
provisions.
10. Replace and/or close all access panels.
Procedures Note: Failure to adhere to the following
start-up procedures will void all manufacturer warranties.
Install gauges, voltmeter and ammeter before start-up. Observe refrigerant pressures during initial operation. Note, and determine the cause of any excessive sound or vibration. Follow start-up procedures outlined below to start each piece of equipment.
Note: Completed factory test sheets are in the equipment literature packet shipped inside the unit. Factory run-test readings recorded on the test sheets may be helpful to reference during start-up.
24
Do not alter factory wiring. Deviation from the supplied wiring diagram will void all warranties, and may result in equipment damage or personal injury. Contact the factory with wiring discrepancies.
Electric Heat Section Procedures
1. Perform final visual inspection.
Check all equipment ductwork and piping to verify that all work is complete. Improperly installed equipment or ductwork can affect readings.
2. Ensure that there is no construction
debris in the unit.
3. Check the unit for external damage.
4. Note all accessories installed.
5. Install a filter of the proper size and
type.
6. Check all terminal blocks, fuses, fuse
blocks, and contactors for correctness.
7. Check all high and low voltage
wiring connections for correctness, and tightness.
8. Check unit for correct incoming
voltage per the data plate.
9. Turn the power on.
10. Turn on the first stage of heating
Check amp draw of each element of each stage.
Ensure blower started with electric heat.
Check for temperature rise across heating section while all stages are on.
If temperature rise is within range, turn all heating calls off.
Check to see that fan stops.
Refrigerant Cooling Section Procedures
1. Perform final visual inspection. Check
all equipment, ductwork and piping to verify that all work is complete, and equipment is properly installed and mounted. Improperly installed equipment or ductwork can affect readings.
2. Perform condensing unit start-up checks
in addition to these air handling unit checks according to the unit manufacturer’s instructions.
3. Ensure that there is no construction
debris in the unit.
4. Check the unit for external damage.
5. Install filter of the proper size and type.
6. Ensure that drain P-trap is installed.
7. Check all terminal blocks, fuses, fuse
blocks, disconnect box, and contactors for correctness.
8. Check all high and low voltage wiring
connections for tightness. Check unit for correct incoming voltage per the data plate.
9. Check the security of the locking system
on all blower bearings.
10. Turn the power on.
11. Check and record ambient temperature.
12. Check for guaranteed off timers (GOT),
and/or time delay relays (TDR).
13. Start the first step cooling circuit, and
blower circuit.
Optional Equipment Procedures
If Modulating Hot Gas Reheat is equipped, additional installation steps are required.
1. Field installed piping is required.
2. The field supplied thermostat and humidistat must be wired to the reheat control as shown in the unit wiring diagram.
25
3. Verify that the condenser hot gas valve and reheat hot gas valve are wired as shown in the wiring diagram.
4. Verify that the Modulating Hot Gas Reheat system is working properly. Run for five minutes in the reheat mode and verify that the temperature of the supply air stream matches the reheat temperature set point.
Commissioning
Air Balancing
High performance systems commonly have complex air distribution and fan systems. Unqualified personnel should not attempt to adjust fan operation, or air circulation, as all systems have unique operating characteristics. Professional air balance specialists should be employed to establish actual operating conditions, and to configure the air delivery system for optimal performance.
Water Balancing
A hydronic specialist with a complete working knowledge of water systems, controls and operation must be employed to properly balance the entire system. Unqualified personnel should not attempt to manipulate temperatures, pressures, or flow rates, as all systems have unique operating characteristics, and improper balancing can result in undesirable noises and operation.
Controls
A variety of controls and electrical accessories may be provided with the equipment.
Identify the controls on each unit by consulting appropriate submittal or order documents, and operate according to the control manufacturer’s instructions. If you cannot locate installation, operation or maintenance information for the specific controls, then contact your sales
representative, or the control manufacturer for assistance.
Operation and Maintenance
General
Immediately following unit startup, the air conditioning system requires a maintenance schedule to assure continued successful operation. A maintenance program similar to the example given below should be scheduled for routine maintenance of this equipment in order to provide efficient and reliable operation for the owner.
Maintenance Schedule
One week after start-up: Check refrigerant charge. Evacuate and repair if leaking.
Check filters for cleanliness. Measure pressure loss if applicable. Replace if necessary.
Check cycling of compressors, fans and valves. Correct unusual cycling.
Monthly: Check cleanliness of filters, and replace if necessary.
Check cooling coil drain pan to assure proper drainage or correct.
Inspect evaporator and condenser coils. Clean if dirty or obstructed in any way.
Quarterly: Check operation of heating and cooling sections.
Check inlet and outlet air temperatures. Determine cause for abnormal changes.
26
Annually: Clean the condenser and evaporator coils with steam or a non-corrosive cleaner.
Clean the drain line, “P” trap and condensate pan. Check refrigerant pressures and temperatures every spring and correct unusual readings.
Check heating section every fall. Check all electrical connections for tightness and check heater elements for indications of overheating. Determine cause and replace elements if necessary.
Inspect and clean unit interior at the beginning of each heating and cooling season and as operating conditions require.
Lubrication
All original motors and bearings are furnished with factory lubrication. They require no lubrication.
Blower Assembly
F1 air handling units are equipped with highly efficient forward curved fans. The blower wheel should be inspected periodically and cleaned of dust and debris. Clean blower wheels reduce electrical use, maintain capacity and reduce stress on the unit.
To inspect and clean the blower, set thermostat to the “OFF” position. Turn the electrical power to the unit to the “OFF” position at the disconnect switch. Check set screw for tightness.
Coils
Coils should be inspected and cleaned annually to ensure there is no obstruction to airflow. Dirty evaporator coils will eventually freeze up, and often result in a time consuming and expensive service call.
Clean filters will help to prevent dirt from accumulating on the evaporator. The evaporator should be cleaned annually with a non-corrosive coil cleaning solution.
Heating
Electric: Set thermostat in the heat mode; call for heat to engage all electric heat strips. Verify that electric heat operates correctly.
Heat Pump: Set thermostat in the heat mode; call for heat to engage the three-way valve and turn the heat pump mode on. Verify that the heat pump operates correctly.
Hot Water: Set thermostat in the heat mode; call for hot water valve to open. Verify that hot water valve opens with call for heat.
Filters
Open filter access door. Slide filters away from unit and inspect. Replace dirty filters with 20” x 20” x 1” filters.
Ensure that the arrow points toward the blower in the direction of airflow. Filters should be checked every 30 days and replaced or cleaned as necessary.
Equipment should never be operation without filters.
Permanent type filters may be vacuumed and/or washed but should not be reinstalled until thoroughly dry. Most air filters are marked to indicate the direction of airflow, and this should be carefully noted when they are being installed.
27
Never flip a dirty filter to allow airflow in the opposite direction.
The blower and motor bearings are permanently lubricated and do not require additional lubrication. It is recommended that the owner have available at least one set of replacement fuses of the size supplied with the original equipment.
Important: Keep coils, fans and filters clean.
Service
In the event the unit is not functioning correctly and a service company is required, only a company with service technicians qualified and experienced in both heating and air conditioning should be permitted to service the systems in order to keep warranties in effect. The service tech may call the sales representative if assistance is required.
Note: Service technician must provide the model and serial number of the unit in all correspondence with AAON.
To order parts from the AAON parts store online go to www.aaonparts.com.
Refrigerant Piping
(See back of the manual for refrigerant piping diagrams.)
This section is for information only and is not intended to provide all details required by the designer or installer of the refrigerant piping between the condenser or condensing unit and the air handling unit. AAON is not responsible for interconnecting refrigerant piping. Consult ASHRAE Handbook – Refrigeration and ASME Standards.
General
Piping from the condensing unit to the air handling unit is the responsibility of the installing contractor.
Use only clean type “ACR” copper tubing that has been joined with high temperature brazing alloy.
The pipe sizes must be selected to meet the actual installation conditions and not simply based on the connection sizes at the evaporator and/or condensing unit.
Condensing units are provided with in-line shutoff valves on both the liquid and suction lines. These should remain closed until the system is ready for start-up after piping and vacuuming.
Piping should conform to generally accepted practices and codes.
Upon completion of piping connection, the interconnecting piping and air handling unit MUST BE evacuated to 500 microns or less; leak checked and charged with R-410A refrigerant.
28
Determining Refrigerant Line Size
Line sizes must be selected to meet actual installation conditions, not simply based on the connection sizes at the condensing unit or air handling unit.
The piping between the condenser and low side must assure:
1. Minimum pressure drop, and
2. Continuous oil return, and
3. Prevention of liquid refrigerant slugging,
or carryover
Minimizing the refrigerant line size is favorable from an economic perspective, reducing installation costs, and reducing the potential for leakage. However, as pipe diameters narrow, pressure-reducing frictional forces increase.
Excessive suction line pressure drop causes loss of compressor capacity and increased power usage resulting in reduced system efficiency. Excessive pressure drops in the liquid line can cause the liquid refrigerant to flash, resulting in faulty expansion valve operation and improper system performance. In order to operate efficiently and cost effectively, while avoiding malfunction, refrigeration systems must be designed to minimize both cost and pressure loss.
The pipe sizes must be selected to meet the actual installation conditions, and not simply based on the connection sizes at the evaporator and/or condensing unit.
Equivalent Line Length
All line lengths discussed in this manual, unless specifically stated otherwise, are Equivalent Line Lengths.
The frictional
pressure drop through valves, fittings and accessories is determined by establishing the equivalent length of straight pipe of the same diameter. Always use equivalent line lengths when calculating pressure drop. Special piping provisions must be taken when lines are run underground, up vertical risers, or in excessively long line runs.
Liquid Line Sizing
When sizing the liquid line, it is important to minimize the refrigerant charge to reduce installation costs and improve system reliability. This can be achieved by minimizing the liquid line diameter. However, reducing the pipe diameter will increase the velocity of the liquid refrigerant, which increases the frictional pressure drop in the liquid line, and causes other undesirable effects such as noise. Maintaining the pressure in the liquid line is critical to ensuring sufficient saturation temperature, avoiding flashing upstream of the TXV, and maintaining system efficiency. Pressure losses through the liquid line due to frictional contact, installed accessories and vertical risers are inevitable. Maintaining adequate sub-cooling at the condenser to overcome these losses is the only method to ensure that liquid refrigerant reaches the TXV.
Liquid refrigerant traveling upwards in a riser will lose head pressure. If the evaporator section is below the condenser, and the liquid line does not include risers, the gravitational force will increase the pressure of the liquid refrigerant. This will allow the refrigerant to withstand greater frictional losses without the occurrence of flashing prior to the TXV.
A moisture-indicating sight glass may be installed in the liquid line by special order to indicate the occurrence of premature flashing or moisture in the line. The sight
29
glass should not be used to determine if the
CAUTIO
system is properly charged. Use temperature and pressure measurements to determine liquid sub-cooling, not the sight glass.
Liquid Line Routing
Care should be taken with vertical risers. When the system is shut down, gravity will pull liquid down the vertical column, and back to the condenser when it is below the evaporator. This could potentially result in compressor flooding. A check valve can be installed in the liquid line where the liquid column rises above the condenser to prevent this. The liquid line is typically pitched along with the suction line, or hot gas line, in the direction of the compressor to minimize the complexity of the configuration.
Liquid Line Insulation
When the liquid line is routed through regions where temperature losses are expected, no insulation is required, as this may provide additional sub-cooling to the refrigerant. When routing the liquid line through high temperature areas, insulation of the line is appropriate to avoid loss of sub­cooling through heat gain.
Liquid Line Guidelines
In order to ensure liquid at the TXV, frictional losses must not exceed available sub-cooling. A commonly used guideline to consider is a system design with pressure losses due to friction through the line not to exceed a corresponding 1-2°F change in saturation temperature.
If the velocity of refrigerant in the liquid line is too great, it could cause excessive noise or piping erosion. The recommended maximum velocities for liquid lines are 100 fpm from the condenser to a receiver tank when used, to discourage fluid backup, and
300 fpm from receiver tank to the evaporator to minimize valve induced liquid hammer.
Liquid Line Accessories
The total length equivalent of pressure losses through valves, elbows and fittings must be considered when adding additional components in the field. It is a good practice to utilize the fewest elbows that will allow the mating units to be successfully joined.
Suction Line Sizing
The suction line is more critical than the liquid line from a design and construction standpoint. More care must be taken to ensure that adequate velocity is achieved to return oil to the compressor at minimum loading conditions. However, reducing the piping diameter to increase the velocity at minimal load can result in excessive pressure losses, capacity reduction, and noise at full load.
Suction Line Routing
Circuits with variable capacity scroll compressors require suction riser traps every 10 feet.
Pitch the suction line in the direction of flow (about 1 ft. per 100 ft of length) to maintain oil flow towards the compressor, and keep it from flooding back into the evaporator. Crankcase heaters are provided to keep any condensed refrigerant that collects in the compressor from causing damage or wear. Make sure to provide support to maintain suction line positioning, and insulate completely between the evaporator and condensing unit.
N
30
It is important to consider part load operation when sizing suction lines. At minimum capacity, refrigerant velocity may not be adequate to return oil up the vertical riser. Decreasing the diameter of the vertical riser will increase the velocity, but also the frictional loss.
A double suction riser can be applied in this situation. The double suction riser is designed to return oil at minimum load while not incurring excessive frictional losses at full load. The double suction riser consists of a small diameter riser in parallel with a larger diameter riser, and a trap at the base of the large riser. At minimum capacity, refrigerant velocity is not sufficient to carry oil up both risers, and it collects in the trap, effectively closing off the larger diameter riser, and diverting refrigerant up the small riser where velocity of the refrigerant is sufficient to maintain oil flow. At full load, the mass flow clears the trap of oil, and refrigerant is carried through both risers. The smaller diameter pipe should be sized to return oil at minimum load, while the larger diameter pipe should be sized so that flow through both pipes provides acceptable pressure drop at full load.
Suction Line Insulation
The entire suction line should be insulated. This prevents condensation from forming on the line, and reduces any potential loss in capacity associated with heat gain.
Suction Line Guidelines
For proper performance, suction line velocities less than a 4000 fpm maximum are recommended. The minimum velocity required to return oil is dependent on the pipe diameter; however, a general guideline of 1000 fpm minimum may be applied.
In a fashion similar to the liquid line, a common guideline to consider is a system
design with pressure losses due to friction through the line not to exceed a corresponding 1-2°F change in saturation temperature.
At points where small pipe size can be used to provide sufficient velocity to return oil in vertical risers at part loads, greater pressure losses are incurred at full loads. This can be compensated for by over sizing the horizontal runs and vertical drop sections. This will however require additional refrigerant charge.
If the job requirements specify suction accumulators, they must be separately purchased and installed.
Hot Gas Reheat
The AAON modulating hot gas reheat system diverts hot discharge gas from the condenser to the air handling unit through the hot gas line. Field piping between the
condensing unit and the air handling unit is required.
The line delivers the hot discharge gas to the reheat coil and/or the hot gas bypass valve, so it is sized as a discharge line.
Discharge lines should be sized to ensure adequate velocity of refrigerant to ensure oil return, avoid excessive noise associated with velocities that are too high, and to minimize efficiency losses associated with friction.
Pitch the hot gas line in the direction of flow for oil return.
When installing hot gas reheat risers, a drip leg must be provided at the lowest point in the system. The drip leg must be vertical, its diameter should be the same as the diameter of the riser, and it should be 1 foot long. Run a drip line, using 1/8 inch capillary tube, 10 feet in length, from the drip leg to the
31
suction line. Connect the drip line a minimum of 1-inch above the bottom of the drain leg.
Insulate the entire length of the hot gas line with a minimum 1-inch thick Armaflex insulation.
Hot Gas Reheat Guidelines
Maintain velocities below a maximum of 3500 fpm. A general minimum velocity guideline is 2000 fpm.
Predetermined Line Sizes
To aid in line sizing and selection, AAON has predetermined line sizes for the liquid and suction lines in comfort cooling applications.
In order to generate this information, the following cycle assumptions are made: Saturated suction temperature = 50°F, Saturated condensing temperature = 125°F, Sub-cooling = 10°F, Superheat = 15°F.
The liquid lines have been chosen to maintain velocities between 100 and 350 fpm. The suction line diameters are selected to limit velocities to a 4000 fpm maximum, while a minimum velocity restriction is imposed by the ability to entrain oil up vertical suction risers (ASHRAE Handbook
- Refrigeration).
Acceptable pressure loss criteria are applied to each of the lines: The total equivalent length of the liquid line available is determined such that 3°F of liquid sub­cooling remain at the TXV. This includes the pressure losses in horizontal and vertical sections, accessories, elbows, etc.
Recall that the available sub-cooling for the cycle is assumed as 10°F. To maintain at least 3°F sub-cooling as a factor of safety to avoid flashing at the TXV, we consider a
maximum pressure loss equivalent to a 7°F change in saturation temperature. Pressure losses in the suction line are not to exceed 2°F.
When to use predetermined line sizing
The line sizes presented are not the only acceptable pipe diameters, they are however appropriate for general comfort cooling applications, and satisfy common job requirements. Examine the conditions, assumptions, and constraints used in the generation of the predetermined pipe diameters to ensure that this method is applicable to a particular case. Do not assume that these line sizes are appropriate for every case. Consult ASHRAE Handbook – Refrigeration for generally accepted system practices.
How to use predetermined line sizing
First, read the previous section entitled (When to use predetermined line sizing) to decide if this method is applicable.
Next, consult Table 8 for pipe diameters.
Examine Figure 3 to determine the acceptable line dimensions associated with the pipe diameters determined in Table 8. The figure is shown as total available riser height versus total equivalent line length for the liquid line. This curve identifies a region of acceptable piping configuration when the predetermined line sizes are selected for any model in the table. A piping configuration above the curve falls outside the assumptions used to determine the line size and will result in a loss of sub­cooling, and additional pressure losses in the suction and hot gas bypass lines.
The total equivalent line length definition includes the height of vertical rise, pressure drop through elbows and accessories, and horizontal line length, so elbows,
32
accessories and vertical rise must be considered when determining horizontal length available from the total equivalent line length.
Figure 3 is presented in terms of the liquid line, but it assumes that the line lengths for the suction and hot gas bypass are similar, as these lines will commonly be routed together to minimize the space and cost required for split system installation.
Before using this table read the
When to Use Predetermined Line Sizes section. Do not assume that
these line sizes are appropriate for every case. Consult ASHRAE Handbook – Refrigeration for generally accepted system piping practices. The AAON Refrigerant Piping Calculator in Ecat32 can be used for job specific line sizing.
Table 8 - Predetermined Line Sizes for F1 and CB Series Matched Systems with Two Step R-
410A Scroll Compressors
Model
CB-024 3/8 inch 3/4 inch 3/8 inch 3/8 inch 3/4 inch 3/8 inch CB-036 3/8 inch 3/4 inch 3/8 inch 3/8 inch 3/4 inch 1/2 inch CB-048 3/8 inch 7/8 inch 1/2 inch 1/2 inch 7/8 inch 1/2 inch CB-060 3/8 inch 7/8 inch 1/2 inch 1/2 inch 7/8 inch 1/2 inch
Connection Sizes Predetermined Line Size
Liquid Suction Hot Gas Liquid Suction HGRH**
** Hot Gas Reheat line
33
Figure 3 - Riser Height Versus Total Equivalent Line Length for R-410A Split System
Applications with Two Step Scroll Compressor CB-024 through CB-060 units.
The region of acceptable riser height is the lighter area. Select the corresponding predetermined line size from Table 8 above.
Total Equivalent Line Length in this figure is limited to 160 equivalent feet.
34
Refrigerant Piping Diagrams
Figure 4 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit above
Condensing Unit.
35
Figure 5 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit below
Condensing Unit
36
Figure 6 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit above
Condensing Unit with Optional Accumulator
37
Figure 7 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit below
Condensing Unit with Optional Accumulator
38
Figure 8 - Heat Pump Piping Diagram with Indoor Unit above Outdoor Unit
39
40
Figure 9 - Heat Pump Piping Diagram with Outdoor Unit above Indoor Unit
Figure 10 - Heat Pump Piping Diagram with Modulating Hot Gas Reheat and Indoor Unit above
Outdoor Unit
41
Figure 11 - Heat Pump Piping with Modulating Hot Gas Reheat and Outdoor Unit above Indoor
Unit
42
Thermostat Installation and Wiring
Figure 12 - 2 Stage Cooling with Electric Heat
43
Figure 13 - 2 Stage Cooling with Heat Pump and Electric Heat
44
Figure 14 - 2 Stage Cooling and Electric Heat with Hot Gas Reheat and Humidistat
45
Figure 15 - Main Control Board for Units Equipped with Modulating Hot Gas Reheat
46
Figure 16 - Field Wiring Connections for an F1 Series Air Handling Unit.
Electric heating connections are made at LVTB3.
47
Figure 17 - 5kW Electric Heat
48
Figure 18 - 10 kW Electric Heat
49
Figure 19 - 15 kW Electric Heat
50
Figure 20 - 20 kW Electric Heat
51
Figure 21 - 25 kW Electric Heat
52
F1 Series Startup Form
Job Name:_______________________________________________
Date:______________
Address:______________________________________________________________________
______________________________________________________________________________
Model Number:_________________________________________________________________
Serial Number:_____________________________________________ Tag:_______________
Startup Contractor:______________________________________________________________
Address:______________________________________________________________________
_______________________________________________________ Phone:______________
Pre Startup Checklist
Installing contractor should verify the following items.
1. Is there any visible shipping damage? Yes No
2. Is the unit level? Yes No
3. Are the unit clearances adequate for service and operation? Yes No
4. Do all access doors open freely and are the handles operational? Yes No
5. Have all shipping braces been removed? Yes No
6. Have all electrical connections been tested for tightness? Yes No
7. Does the electrical service correspond to the unit nameplate? Yes No
8. On 208/230V units, has transformer tap been checked? Yes No
9. Has overcurrent protection been installed to match the unit nameplate
requirement? Yes No
10. Have all set screws on the fans been tightened? Yes No
11. Do all fans rotate freely? Yes No
12. Does the field water piping to the unit appear to be correct per design
parameters? Yes No
13. Is all copper tubing isolated so that it does not rub? Yes No
14. Are air filters installed with proper orientation? Yes No
15. Have condensate drain and p-trap been connected? Yes No
Ambient Temperature
Ambient Dry Bulb Temperature ________°F
Ambient Wet Bulb Temperature ________°F
53
Supply Fan Assembly
Alignment
Check Rotation
Nameplate Amps________
Number hp L1 L2 L3
1
Compressors/DX Cooling
Check Rotation
Number L1 L2 L3
1 - Full
Pressure
Head
PSIG
Suction
Pressure
PSIG
Crankcase
Heater
Amps
Capacity
2 ­Reduced Capacity
Refrigeration System 1 Full Capacity - Cooling Mode
Pressure
Saturated
Temperature
Line
Temperature
Sub-cooling Superheat
Discharge N/A N/A
Suction N/A
Liquid N/A
Refrigeration System 1 Reduced Capacity - Cooling Mode
Pressure
Saturated
Temperature
Line
Temperature
Sub-cooling Superheat
Discharge N/A N/A
Suction N/A
Liquid N/A
Refrigeration System 1 Full Capacity - Heating Mode (Heat Pump Only)
Pressure
Saturated
Temperature
Line
Temperature
Sub-cooling Superheat
Discharge N/A N/A
Suction N/A
Liquid N/A
Refrigeration System 1 Reduced Capacity - Heating Mode (Heat Pump Only)
Pressure
Saturated
Temperature
Line
Temperature
Sub-cooling Superheat
Discharge N/A N/A
Suction N/A
Liquid N/A
54
Unit Configuration
Water-Cooled Condenser Air-Cooled Condenser
No Water Leaks Condenser Safety Check
Water Flow ________ gpm
Water Inlet Temperature ________°F
Water Outlet Temperature ________°F
Water/Glycol System
1. Has the entire system been flushed and pressure checked? Yes No
2. Has the entire system been filled with fluid? Yes No
3. Has air been bled from the heat exchangers and piping? Yes No
4. Is the glycol the proper type and concentration (N/A if water)? Yes No
5. Is there a minimum load of 50% of the design load? Yes No
6. Has the water piping been insulated? Yes No
7. What is the freeze point of the glycol (N/A if water)? ______________________________
Air-Cooled Condenser
Alignment
Check Rotation
Nameplate Amps________
Number hp L1 L2 L3
1
Electric Heating
Stages__________ Limit Lockout Aux. Limit Lockout
Stage Amps Stage Amps
1 4 2 5 3 6
55
Maintenance Log
This log must be kept with the unit. It is the responsibility of the owner and/or maintenance/service contractor to document any service, repair or adjustments. AAON Service and Warranty Departments are available to advise and provide phone help for proper operation and replacement parts. The responsibility for proper startup, maintenance and servicing of the equipment falls to the owner and qualified licensed technician.
Entry Date Action Taken Name/Tel.
56
Literature Change History
November 2009
Update of the IOM formatting to match with other IOMs and adding some variable capacity scroll compressor information.
April 2009
Update of the IOM adding the F1 Series model number description.
June 2010
Revision of the IOM adding PVC and CPVC piping Caution.
April 2012
Update of the IOM adding the electronic startup form, adding the index of tables and figures, and updating the table of contents.
57
AAON
2425 South Yukon Ave.
Tulsa, OK 74107-2728
Phone: 918-583-2266
Fax: 918-583-6094
www.aaon.com
F1 Series
Installation, Operation &
Maintenance
R58420 · Rev. B · 120509
(ACP 29902)
It is the intent of AAON to provide accurate and current product information. However, in the interest of product improvement, AAON reserves the right to change pricing, specifications, and/or design of its product without notice, obligation, or liability.
Copyright © AAON, all rights reserved throughout the world.
AAON® and AAONAIRE® are registered trademarks of AAON, Inc., Tulsa, OK.