AAON F-060 User Manual

F1 Series
Indoor Air Handing Units
Installation, Operation
& Maintenance
QUALIFIED INSTALLER
Improper installation, adjustment, alteration, service or maintenance can cause property damage, personal injury or loss of life. Installation and service must be performed by a trained, qualified installer. A copy of this IOM should be kept with the unit.
These instructions are addressed primarily to the installer; however, useful maintenance information is included. This manual should be kept with the unit for future reference.
NOTICE
FOR YOUR SAFETY Do not store or use gasoline or other flammable vapors and liquids in the vicinity of this or any other appliance.
If the information in this manual is not followed exactly, a fire or explosion may result causing property damage, personal injury or loss of life.
Table of Contents
Safety .............................................................................................................................................. 6
F1 Base Model and Features Description ..................................................................................... 10
General Description ...................................................................................................................... 11
Codes and Ordinances ............................................................................................................... 11
Receiving Units ......................................................................................................................... 12
Before Beginning Installation ................................................................................................... 13
Storage ....................................................................................................................................... 13
Installation..................................................................................................................................... 14
General ...................................................................................................................................... 14
Service and Installation Clearance ............................................................................................ 14
Floor Mounted Units ................................................................................................................. 14
Suspended .................................................................................................................................. 14
Sealing ....................................................................................................................................... 15
Cooling Equipment ................................................................................................................... 15
Heating Equipment .................................................................................................................... 16
Field Wiring - MCA and MOP ................................................................................................. 16
Heat Pump ................................................................................................................................. 17
ECM Driven Fan ....................................................................................................................... 17
Reheat Coil Refrigerant Piping ................................................................................................. 18
Condensate Piping ..................................................................................................................... 20
Electrical .................................................................................................................................... 20
Thermostat ................................................................................................................................. 20
Filters ......................................................................................................................................... 20
Charging Refrigerant ................................................................................................................. 20
Evaporator Coil ......................................................................................................................... 22
Startup ........................................................................................................................................... 24
General ...................................................................................................................................... 24
Check-Out ................................................................................................................................. 24
Procedures ................................................................................................................................. 24
Electric Heat Section Procedures .............................................................................................. 25
Refrigerant Cooling Section Procedures ................................................................................... 25
Optional Equipment Procedures ................................................................................................ 25
Commissioning .......................................................................................................................... 26
Air Balancing ............................................................................................................................ 26
Water Balancing ........................................................................................................................ 26
Controls ..................................................................................................................................... 26
Operation and Maintenance .......................................................................................................... 26
General ...................................................................................................................................... 26
Maintenance Schedule ............................................................................................................... 26
Lubrication ................................................................................................................................ 27
Blower Assembly ...................................................................................................................... 27
Coils .......................................................................................................................................... 27
Heating ...................................................................................................................................... 27
Filters ......................................................................................................................................... 27
3
Refrigerant Piping ..................................................................................................................... 28
Determining Refrigerant Line Size ........................................................................................... 29
Equivalent Line Length ............................................................................................................. 29
Predetermined Line Sizes .......................................................................................................... 32
Refrigerant Piping Diagrams ........................................................................................................ 35
Thermostat Installation and Wiring .............................................................................................. 43
F1 Series Startup Form ................................................................................................................. 53
Maintenance Log .......................................................................................................................... 56
Literature Change History............................................................................................................. 57
R58420 · Rev. B · 120509
(ACP 29902)
Index of Table and Figures
Tables:
Table 1 - Electric Heat Minimum Circuit Ampacity .................................................................... 16
Table 2 - Electric Heat Maximum Overcurrent Protection ........................................................... 17
Table 3 - Factory Preset Air Flow................................................................................................. 17
Table 4 - Cooling Fan Speed Tap Settings ................................................................................... 17
Table 5 - Climate Settings ............................................................................................................. 18
Table 6 - Heating Fan Speed Tap Settings .................................................................................... 18
Table 7 - Acceptable Air-Cooled Refrigeration Circuit Values ................................................... 22
Table 8 - Predetermined Line Sizes for F1 and CB Series Matched Systems with Two Step R-
410A Scroll Compressors ............................................................................................................. 33
Figures:
Figure 1 - Typical Vertical and Horizontal Unit Installation Methods ......................................... 15
Figure 2 - Example Configuration of ECM Fan Taps .................................................................. 17
Figure 3 - Riser Height Versus Total Equivalent Line Length for R-410A Split System
Applications with Two Step Scroll Compressor CB-024 through CB-060 units. ........................ 34
Figure 4 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit above
Condensing Unit. .......................................................................................................................... 35
Figure 5 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit below
Condensing Unit ........................................................................................................................... 36
Figure 6 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit above
Condensing Unit with Optional Accumulator .............................................................................. 37
Figure 7 - Modulating Hot Gas Reheat Piping Diagram with Air Handling Unit below
Condensing Unit with Optional Accumulator .............................................................................. 38
Figure 8 - Heat Pump Piping Diagram with Indoor Unit above Outdoor Unit............................. 39
Figure 9 - Heat Pump Piping Diagram with Outdoor Unit above Indoor Unit ............................. 40
Figure 10 - Heat Pump Piping Diagram with Modulating Hot Gas Reheat and Indoor Unit above
Outdoor Unit ................................................................................................................................. 41
Figure 11 - Heat Pump Piping with Modulating Hot Gas Reheat and Outdoor Unit above Indoor
Unit ............................................................................................................................................... 42
Figure 12 - 2 Stage Cooling with Electric Heat ............................................................................ 43
Figure 13 - 2 Stage Cooling with Heat Pump and Electric Heat .................................................. 44
Figure 14 - 2 Stage Cooling and Electric Heat with Hot Gas Reheat and Humidistat ................. 45
Figure 15 - Main Control Board for Units Equipped with Modulating Hot Gas Reheat .............. 46
Figure 16 - Field Wiring Connections for an F1 Series Air Handling Unit. ................................ 47
Figure 17 - 5kW Electric Heat ..................................................................................................... 48
Figure 18 - 10 kW Electric Heat .................................................................................................. 49
Figure 19 - 15 kW Electric Heat .................................................................................................. 50
Figure 20 - 20 kW Electric Heat ................................................................................................. 51
Figure 21 - 25 kW Electric Heat ................................................................................................. 52
5
Safety
NOTE - Notes are intended to clarify the unit installation, operation and maintenance.
CAUTION - Caution statements are given to prevent actions that may result in
equipment damage, property damage, or personal injury.
WARNING - Warning statements are given to prevent actions that could result in
equipment damage, property damage, personal injury or death.
DANGER - Danger statements are given to prevent actions that will result in equipment
damage, property damage, severe personal injury or death.
Attention should be paid to the following statements:
ELECTRIC SHOCK, FIRE OR EXPLOSION HAZARD
Failure to follow safety warnings exactly could result in dangerous operation, serious injury, death or property damage.
Improper servicing could result in dangerous operation, serious injury, death or property damage.
Before servicing, disconnect all
electrical power to the unit. More than one disconnect may be provided.
When servicing controls, label all
wires prior to disconnecting. Reconnect wires correctly.
Verify proper operation after
servicing. Secure all doors with key-lock or nut and bolt.
Electric shock hazard. Before servicing, disconnect all electrical power to the unit, including remote disconnects, to avoid shock hazard or injury from rotating parts. Follow proper Lockout-Tagout procedures.
FIRE, EXPLOSION OR CARBON MONOXIDE POISONING HAZARD
Failure to replace proper controls could result in fire, explosion or carbon monoxide poisoning. Failure to follow safety warnings exactly could result in serious injury, death or property damage. Do not store or use gasoline or other flammable vapors and liquids in the vicinity of this appliance.
6
During installation, testing, servicing and troubleshooting of the equipment it may be necessary to work with live electrical components. Only a qualified licensed electrician or individual properly trained in handling live electrical components shall perform these tasks.
Standard NFPA-70E, an OSHA regulation requiring an Arc Flash Boundary to be field established and marked for identification of where appropriate Personal Protective Equipment (PPE) be worn, should be followed.
GROUNDING REQUIRED
All field installed wiring must be completed by qualified personnel. Field installed wiring must comply with NEC/CEC, local and state electrical code requirements. Failure to follow code requirements could result in serious injury or death. Provide proper unit ground in accordance with these code requirements.
To prevent injury or death lifting equipment capacity shall exceed unit weight by an adequate safety factor. Always test-lift unit not more than 24 inches high to verify proper center of gravity lift point to avoid unit damage,
UNIT HANDLING
injury or death.
ROTATING COMPONENTS
Unit contains fans with moving parts that can cause serious injury. Do not open door containing fans until the power to the unit has been disconnected and fan wheel has stopped rotating.
Failure to properly drain and vent coils when not in use during freezing temperature may result in coil and equipment damage.
Rotation must be checked on all MOTORS AND COMPRESSORS of 3 phase units at startup by a qualified service technician. Scroll compressors are directional and can be damaged if rotated in the wrong direction. Compressor rotation must be checked using suction and discharge gauges. Fan motor rotation should be checked for proper operation. Alterations should only be made at the unit power connection
7
CAUTIO
CAUTIO
Do not use oxygen, acetylene or air in place of refrigerant and dry nitrogen for leak testing. A violent explosion may result causing injury or death.
WARNING
Always use a pressure regulator, valves and gauges to control incoming pressures when pressure testing a system. Excessive pressure may cause line ruptures, equipment damage or an explosion which may result in injury or death.
Do not work in a closed area where refrigerant or nitrogen gases may be leaking. A sufficient quantity of vapors may be present and cause injury or death.
Do not clean DX refrigerant coils with hot water or steam. The use of hot water or steam on refrigerant coils will cause high pressure inside the coil tubing and damage to the coil.
N
To prevent damage to the unit, do not use acidic chemical coil cleaners. Do not use alkaline chemical coil cleaners with a pH value greater than
8.5, after mixing, without first using an aluminum corrosion inhibitor in the cleaning solution.
N
Some chemical coil cleaning compounds are caustic or toxic. Use these substances only in accordance with the manufacturer’s usage instructions. Failure to follow instructions may result in equipment damage, injury or death.
Risk of injury from hot parts – Disconnect all power, close all isolation valves and allow equipment to cool before servicing equipment with heating coils. Hot water will circulated even after the power is off.
8
PVC (Polyvinyl Chloride) and CPVC (Chlorinated Polyvinyl Chloride) are vulnerable to attack by certain chemicals. Polyolester (POE) oils used with R-410A and other refrigerants, even in trace amounts, in a PVC or CPVC piping system will result in stress cracking of the piping and fittings and complete piping system failure.
1. The unit is for indoor use only. See
General Information section for more unit information.
2. Every unit has a unique equipment
nameplate with electrical, operational, and unit clearance specifications. Always refer to the unit nameplate for specific ratings unique to the model you have purchased.
3. READ THE ENTIRE INSTALLATION,
OPERATION AND MAINTENANCE MANUAL. OTHER IMPORTANT SAFETY PRECAUTIONS ARE PROVIDED THROUGHOUT THIS MANUAL.
4. Keep this manual and all literature
safeguarded near or on the unit.
9
F1
Series and
Generation
F1 Base Model and Features Description
A
-
Rev.
BASE MODEL
SERIES AND GENERATION
F1
REVISION
A = Design Sequence
UNIT SIZE
024 = 24 MBtu/h (2 ton) 036 = 36 MBtu/h (3 ton) 048 = 48 MBtu/h (4 ton) 060 = 60 MBtu/h (5 ton)
VOLTAGE
1 = 208-230V/1Φ/60Hz C = 115V/1Φ/60Hz
APPLICATION
V = Vertical Position (Up-flow) M = Multi-Position (Up-flow or Horizontal)
HEATING
0 = No Heat A = 5 kW B = 10 kW C = 15 kW D = 20 kW E = 25 kW G = Hot Water Heating H = Hot Water Heating - No Cooling
FEATURE 1: MOTORS
A = ECM - 1/2 hp B = ECM - 3/4 hp C = ECM - 1.0 hp
FEATURE 2: FILTERS
0 = Standard - 1” Fiberglass
060
-
Unit Size
1
-
Voltage App. Heat Mtrs Filters Cntls Blank Refri. Blank Cabinet Special
M
-
C
-
C 0 0 0 C 000 0 0
FEATURE 3: CONTROLS
0 = Standard - Terminal Block
FEATURE 4: BLANK
0 = Standard
FEATURE 5: REFRIGERATION
0 = Standard - Split System Air Conditioner C = Split System Heat Pump D = Split System Air Conditioner + Modulating Hot Gas Reheat F = Split System Heat Pump + Modulating Hot Gas Reheat
FEATURE 6: BLANK
0 = Standard
FEATURE 7: BLANK
0 = Standard
FEATURE 8: BLANK
0 = Standard
FEATURE 9: CABINET
0 = Standard - Embossed Galvanized Steel A = Painted Cabinet Exterior
FEATURE 10: SPECIAL
0 = Standard X = Special Price Authorization
10
General Description
F1 Series air handling units are designed for safe operation when installed, operated and maintained within design specifications and the instructions set forth in this manual. It is necessary to follow these instructions to avoid personal injury or damage to equipment or property during equipment installation, operation, start-up and maintenance.
Improper installation, adjustment, alteration, service or maintenance can cause property damage, personal injury or loss of life. Installation and service must be performed by a qualified installer. A copy of this IOM should be kept with the unit.
This equipment is protected by a standard limited warranty under the condition that initial startup and maintenance is performed according to the instructions set forth in this manual. This manual should be read in its entirety prior to installation and before performing any service or maintenance work.
These units must not be used as a “construction heater” at anytime during any phase of construction. Very low return air temperatures, harmful vapors, and misplacement of the filters will damage the unit and its efficiency.
Certification of Cooling Models
a. Certified for use with a residential
remote R-410A condensing unit with a two-step compressor.
b. Certified for indoor installation only
Certification of Cooling and Reheat Models
a. Certified for use with a residential
remote R-410A condensing unit with a two-step compressor and hot gas dehumidification capabilities.
b. Certified for indoor installation only
Certification of Electric Heat Models
a. Certified as an electric heating air
handling unit with a cooling coil.
b. Certified for indoor installation only.
Codes and Ordinances
F1 Series units have been tested and certified, by ETL, in accordance with UL Safety Standard 1995/CSA C22.2 No. 236.
System should be sized in accordance with the American Society of Heating, Refrigeration and Air Conditioning Engineers Handbook.
Installation of F1 Series units must conform to the ICC standards of the International Mechanical Code, the International Building Code, Installation of Air Conditioning and Ventilating Systems Standard, NFPA 90A, and local building, plumbing and waste water codes. All appliances must be electrically grounded in accordance with local codes, or in the absence of local codes, the current National Electric Code, ANSI/NFPA 70 or the current Canadian Electrical Code CSA C22.1.
Important: The United States Environmental Protection Agency (EPA) has issued various regulations regarding the introduction and disposal of refrigerants in
11
this unit. Failure to follow these regulations
CAUTIO
quip
may harm the environment and can lead to the imposition of substantial fines. Because regulations may vary due to passage of new laws, AAON suggests a certified technician perform any work done on this unit. Should you have any questions please contact the local office of the EPA.
WARNING
Do not, under any circumstances, connect ductwork to any other heat producing device such as fireplace insert, stove, etc. Unauthorized use of such devices may result in property damage, fire, carbon monoxide poisoning, explosion, personal injury or death.
It is the responsibility of the installing
contractor to comply with codes,
ordinances, local and municipal
building laws, and manufacturer’s
instruction. Personal injury and/or
equipment damage may result if
proper procedures are not followed.
The Clean Air Act of 1990 bans the
intentional venting of refrigerant as of
July 1, 1992. Approved methods of
recovery, recycling, or reclaiming
must be followed.
N
Always wear hand and eye protection when handling, installing, servicing, or maintaining equipment. Sharp edges, moving parts and fly debris may cause personal injury and care must be taken when working with
ment.
e
Any conflicting codes or regulations take precedence over the information in this manual. It is important that all installation and service work be performed by qualified professionals.
Receiving Units
All shipments are FOB from the factory. It is the responsibility of the receiving party to inspect the equipment upon arrival. Units should be inspected for damage that may have occurred in transit. Please do not refuse shipments!
Check the unit model number, specifications, electrical characteristics and accessories to determine if they are correct. In the event an incorrect unit is shipped, it must be returned to the supplier and must NOT be installed. The manufacturer assumes no responsibility for installation of incorrectly shipped units.
Do the following upon receipt:
1. Assure that freight carrier is in
compliance with Bill of Lading instructions.
2. Inspect delivery before signing Bill of
Lading.
If damage is found or items are missing:
1. Note on Bill of Lading immediately.
2. Call carrier immediately to file a freight
claim and to schedule an inspection.
3. Photograph damage if possible.
12
4. Do not move or discard damaged freight
packaging materials
5. After losses have been acknowledged by
the freight carrier, contact factory for a repair or replacement part quote.
6. With permission of freight carrier, order
parts and/or make repairs.
7. Stay in contact with freight carrier to
ensure payment of your claim.
Nameplate should be checked to ensure the correct model sizes and voltages have been received to match the job requirements.
If repairs must be made to damaged goods, then the factory should be notified before any repair action is taken in order to protect the warranty. Certain equipment alteration, repair, and manipulation of equipment without the manufacturer’s consent may void the product warranty. Contact the AAON Warranty Department for assistance with handling damaged goods, repairs, and freight claims: (903) 236-4403.
Note: Upon receipt check shipment for items that ship loose such as filters, thermostats and remote sensors. Consult order and shipment documentation to identify potential loose-shipped items. Loose-shipped items may have been placed inside unit cabinet for security.
Dependent upon the optional accessories that were ordered, this equipment may contain fragile components and delicate electronics. Although the unit is constructed of sturdy materials, avoid impacts and handling methods that may damage internal apparatus and structure of the unit. Take care not to apply destructive force to coils, coil and drain stub-outs, or other parts protruding beyond the extents of the unit casing. Always handle the unit by its exterior casing and never by any of the protruding parts.
Before Beginning Installation
Carefully read all instructions for the installation prior to installing unit. Make sure each step or procedure is understood and any special considerations are taken into account before starting installation. Assemble all tools, hardware and supplies needed to complete the installation.
Some items may need to be purchased locally. After deciding where to install unit, closely look the location over - both the inside and outside of home. Note any potential obstacles or problems that might be encountered as noted in this manual. Choose a more suitable location if necessary.
Storage
This equipment is not suitable for outdoor use or storage. Never place this equipment where it may be subjected to outdoor conditions such as rain, snow, humidity, extreme temperatures or corrosive chemicals.
If installation will not occur immediately following delivery, store equipment in a dry protected area away from construction traffic, and in the proper orientation as marked on the packaging with all internal packaging in place. Secure all loose-shipped items.
Keep equipment free from debris, and construction waste during installation. Foreign materials may adversely affect unit operation resulting in premature failures that will not be covered by the manufacturer’s warranty. Attach all service panels, and cover all exposed equipment when work is not being performed. Leave unit protected from other construction until start-up is to occur.
13
CAUTIO
This unit must be stored indoors if installation is not to occur immediately following delivery. Unprotected units could develop corrosion if left exposed to the environment. Damage resulting from improper storage will not be covered by the limited warranty.
N
Installation
AAON equipment has been designed for quick and easy installation.
General
F1 Series air handling units are designed as heating, cooling or combination units for indoor installation only. They are designed for R-410A refrigerant only. Flexible connectors are required on all duct connections to minimize air leaks.
Service and Installation Clearance
Before setting the air handling unit into place, caution must be taken to provide clearance for unit panels that must be accessible for periodic service. These areas contain the controls, safety devices, refrigerant piping, shut-off valves and filter access.
F1 series air handling units require a minimum of 36 inches of service clearance on the access panel side of the unit in order to ensure room for removal, replacement, or
service of coils and other components if necessary.
Note: An auxiliary (emergency) drain pan is recommended for all applications where there is a risk of water damage to surrounding structure or furnishings. Refer to local codes.
Floor Mounted Units
Make sure that the unit is level, and mounted on a field-supplied platform with a minimum height of 12” to allow for proper fall on the condensate line. Other installation provisions may be necessary according to job specifications. F1 series air handling units are designed for up flow and horizontal applications only.
Suspended
The F1 series multi-position air handling unit can be easily suspended for suspended horizontal installations. The air handling unit should be lifted into position, supporting the entire unit from the bottom throughout the lift. Suspend the air handling unit as shown in the following Figure 1. An auxiliary drain pan that covers the entire unit would be required for above ceiling installations.
The air handling unit must be installed level and care should be taken to prevent damage to the cabinet. Other installation provisions may be necessary according to job specifications and local code.
14
Figure 1 - Typical Vertical and Horizontal Unit Installation Methods
Sealing
It is very important to keep outside air from infiltrating the unit cabinet. Seal all piping penetrations with Armaflex, Permagum, or other suitable sealant. Also seal around drain connections, electrical connections, and other inlets where air may enter the cabinet. This is especially important when the unit is installed in an unconditioned area.
Cooling Equipment
Acceptable system design and installation will include consideration as follows:
Piping from the condensing unit to the indoor air handling unit is the responsibility of the installing contractor.
Only clean “ACR” tubing should be used.
Piping should conform to generally accepted practices and codes.
Care must be taken not to cross the circuits on reheat systems.
Once piped, the interconnecting piping and air handling unit MUST BE evacuated to 500 microns or less; leak checked and condenser shutoff valves opened to allow refrigerant flow to air handling unit. Charge unit with R-410A refrigerant to the recommended superheat/sub-cooling in the Charging Refrigerant section of this manual.
Make sure air handling unit thermal expansion valve bulb is mounted with good thermal contact on the suction line on a horizontal section, close to the evaporator but outside the cabinet in the 4 or 8 o’clock position and well insulated.
Lines should be fastened and supported according to local codes.
15
Heating Equipment
Hot Water Heating: Water supply lines must be insulated, properly fastened, drained and supported according to local code requirements.
Electric Heating:
Installing Electric Heat Strip into the Unit:
1. Remove front control panel(s) of the unit
2. Remove screws and panel covering heat
strip compartment
3. Open the heat strip kit and remove
assembly from package
4. Install strip heat into opening and secure
with 4 (four) screws
5. Install breaker assembly on bracket and
secure with breaker with 4 (four) screws
6. Make sure that breaker is in the OFF
position
7. Connect all control wires per wiring
diagram included in the unit
8. Pull and install power wires per wiring
diagram and MCA, MOP information herein and secure all wires firmly
9. Replace the front control panel(s) of the
unit
FIELD INSTALLED WIRES SHOULD BE SINGLE STRAND WIRES. USE OF ROMEX WIRES IS NOT ACCEPTABLE.
Heating is accomplished by passing electrical current through a specified amount of resistance heaters, which will produce the required heat. The indoor blower motor will energize at the same time as the heaters. Wiring to the air handling unit must be done in accordance with local electrical codes and/or standards. Check specified electrical rating and install with proper wire sizes. Also refer to wiring diagrams included with the unit for wire sizes and circuit breaker recommendations.
Field Wiring - MCA and MOP
Minimum Circuit Ampacity (MCA) and Maximum Overcurrent Protection (MOP) are necessary to correctly connect field wired equipment.
The calculations for the MCA and MOP are based on requirements of NFPA 70, the National Electrical Code (NEC) and CSA C22.1, the Canadian Electrical Code (CEC). The MCA is the minimum wire size needed to prevent the wiring from overheating during operating conditions for the life of the product. The MOP is the maximum allowable circuit breaker size that will properly disconnect power to the equipment under anticipated fault conditions.
In the following tables, locate the kW of the heater to be field installed, and then choose the corresponding MCA and MOP values to correctly size the wire gauge(s) and circuit breaker(s), respectively.
Table 1 - Electric Heat Minimum Circuit
Ampacity
230V 208V
kW kW MCA MCA MCA
5 3.75 26.0 10 7.50 52.1 15 11.25 52.1 26.0 20 15.00 52.1 52.1 25 18.75 52.1 52.1 26.0
Overcurrent protection less than that recommended on the unit's "Specification Sheet" could result in unnecessary fuse failure and service call. The manufacturer bears no responsibility for damage caused to the equipment as a result of not using the recommended size for the protective devices as listed on the unit's rating plate.
Line 1 Line 2 Line
3
16
Table 2 - Electric Heat Maximum
A
A
A
Overcurrent Protection
230V 208V Line 1 Line 2 Line
3
kW kW MOP MOP MOP
5 3.75 30 10 7.50 60 15 11.25 60 30 20 15.00 60 60 25 18.75 60 60 30
Heat Pump
For heat pump equipped split system configurations, the heat pump is the primary heat source during a call for heat. During operation at low ambient temperatures where the heat pump alone cannot satisfy the space temperature set point, electric resistance heat elements are activated. Below about 17°F, only the electric heat is operable; the heat pump is not active.
ECM Driven Fan
The Electrically Commutated Motor (ECM) has selectable fan speeds as determined by the configuration of four pins as shown in FIGURE 2.
----
B C
D
HEAT COOL ADJUST DELAY
- -
- -
- -
B C
D
- -
- -
- -
----
1
- -
+
- -
-
----
1
- -
----
B
- -
C
- -
D
- -
Figure 2 - Example Configuration of ECM
Fan Taps
Adjust the taps as desired for cooling, dehumidification, and heating according to the following instructions.
Cooling: Units are preprogrammed from the factory for a rated airflow rate of 400 cfm per ton as shown in Table 3.
Table 3 - Factory Preset Air Flow
Model Preset cfm
F1-060 2000 F1-048 1600 F1-036 1200 F1-024 800
* Maximum total static is 2.25” w.g.
The high speed for cooling may be selected by setting the COOL and ADJUST fan speed taps (shown in Figure 2). The setting combinations are shown in Table 4.
Note: On the ADJUST tap, both of the ‘1’ selections have the same effect on motor speed.
Table 4 - Cooling Fan Speed Tap Settings
F1-060/ F1-036/
F1-048 F1-024
(cfm) (cfm)
COOL
Tap
ADJUST
Tap
2000 1200 A 1 2000 1200 D 1
1840 1150 B + 1700 1020 A ­1700 1020 D ­1600 1000 B 1 1380 920 C + 1360 850 B ­1200 800 C 1 1020 680 C -
A signal from the thermostat, showing a need for dehumidification, will cause the unit to slow the fan speed in order to allow the air moving across the coil to get colder thereby better dehumidifying the air. Fist stage dehumidification has a low fan speed of 67% of the selected max speed. Second stage dehumidification has a fan speed of 45% of the selected max speed. NOTE: The Modulating Hot Gas Reheat option must be selected to have a second stage of dehumidification.
17
In this comfort cooling application of the ECM fan motor, heat and cool taps, A & D have the same effect on motor speed.
Humidity Control: Adjust the DELAY tap for humidity control that is suitable for the climate according to Table 5.
Table 5 - Climate Settings
CLIMATE DELAY Tap
Humid A Sub-humid/Dry B Semi-Arid C Arid/Hyper-Arid D
Heating: The fan speed for the heating cycle is selected by adjusting the HEAT tap (see FIGURE 2) according to TABLE 6.
Table 6 - Heating Fan Speed Tap Settings
F1-060/ F1-036/
HEAT Tap F1-048 F1-024
(cfm) (cfm)
1800 1000 A 1400 800 B 1200 600 C 1800 1000 D
ECM Fan Notes
1. Fan only = 50% of max speed
2. Dehumidifying speeds i) First stage dehumidification =
67% of max speed
ii) Second stage dehumidification =
45% of max speed
3. Green Light will blink once per every
100 CFM
4. Dehumidification terminal is BK. There
must be a constant voltage to this terminal, and when the voltage is
dropped then dehumidification mode will begin.
Fan wiring notes:
1. If only one stage of cooling is used then
jumper Y1 and Y2.
2. If unit is not heat pump capable then
jumper O and Y1.
3. If no humidistat is used then jumper BK
and R.
4. When only one stage of heat is used
jumper W1 and W2.
Reheat Coil Refrigerant Piping
The reheat coil is shipped already installed on the leaving air section of the air handling unit. A liquid receiver is shipped loose with the unit for field installation. (See Refrigerant Piping Section
to determine acceptable refrigerant line size.)
1. Run a hot gas line from the outdoor unit
and connect it to the inlet of the stub-out on the reheat coil. a. For vertical (up-flow) units. The
inlet connection is the left stub-out when facing the front of the unit. Connect the hot gas line from the outdoor unit to the left stub-out. Connect the check valve (shipped loose) to the right stub-out in a direction so that the refrigerant flow is leaving the right side of the coil. Be sure to not block access for
18
Loading...