Mitsubishi Electronics FR-A800, F800 User Manual

INVERTER FR-A800/F800
Safety Stop Function Instruction Manual

CONTENTS

1. GENERAL DESCRIPTION ............................................ 2
2. INSTALLATION AND WIRING...................................... 3
3. EXAMPLE OF SAFETY SYSTEM CONFIGURATION .... 7
4. TEST AND CHECKING FAILURE ............................... 10

Compliance with the EU Machinery Directive – Functional Safety

WARNING
Any misuse of safety function could lead to personal injury or death, property damage, or economic
loss. To ensure that the system complies fully with requirement of safety, make a system-level risk assessment. Mitsubishi Electric Co. cannot assume responsibility for any system to comply with safety directive.
CAUTION
The information of this manual is merely a guide for proper installation.Mitsubishi Electric Co. cannot assume responsibility for the compliance or the noncompliance to
any code, national, local or otherwise for the proper installation of this equipment.
A hazard of personal injury and/or equipment damage exists if codes are ignored during installation.
WARNING
To avoid an electric shock hazard, verify that the voltage on the bus capacitors has discharged
before performing any work on the drive. Measure the DC bus voltage at the P(+) and N(-) terminals or test points (refer to your drive’s User Manual for locations and discharging time). The voltage must be zero.
WARNING
The safety stop function do not isolate electrically between drive and motor. To avoid an electric
shock hazard, disconnect/isolate power to the drive and verify to ensure that the voltage is zero before performing any work on the motor (refer to your drive’s User Manual for discharging time).
1

1 GENERAL DESCRIPTION

Features
Mitsubishi FR-A800/F800 safety stop function prevents a drive from supplying rotational energy to motors. Dual
safety channels ‘S1’ and ‘S2’ cut off the gate-drive power for IGBT to turn off.
RESET
Emergency stop button
SO
SOC
PC
24VDC
SIC
SD
Safety relay module
/ Safety programmable controller
S2
S1
Fuse
+24V
CPU
Logic
FR-A800/F800
Gate
ASIC
Driver
Gate
Driver
G G
R/L1 S/L2 T/L3
IGBTs
U
V
M
W
Fig.1 FR-A800/F800 safety stop function diagram
WARNING
Disconnecting the power to the gate driver by the safety stop function does not isolate electrically
between drive and motor. To avoid an electric shock hazard, disconnect power to the drive and verify that the main circuit capacitor voltage is zero (across P and N terminals) before performing any work on the motor (refer to your drive’s User Manual for discharging time).
Standards
Mitsubishi FR-A800/F800 safety stop function meets the following directives and categories.
ISO13849-1:2008 Category 3/PLd
IEC62061:2005 / IEC61800-5-2:2007 / IEC61508 SIL2
IEC60204-1:2010 / IEC61800-5-2:2007 Stop category 0
WARNING
The misuse of safety function leads to personal injury or death, property damage, or economic loss.
To ensure that the system complies fully with requirement of safety, make a system-level risk assessment. Mitsubishi Electric Co. cannot assume responsibility for any system to comply with safety directive.
2
GENERAL DESCRIPTION

2 INSTALLATION AND WIRING

CAUTION
The following information is merely a guide for proper installation.Mitsubishi Electric Co. cannot assume responsibility for the compliance or the noncompliance to
any code, national, local or otherwise for the proper installation of this equipment.
A hazard of personal injury and/or equipment damage exists if codes are ignored during installation.
CAUTION
Ensure the safety relay unit and the FR-A800/F800 unit is mounted closely in enclosure meeting IP54
and all interconnection wiring is short and protected against open and short circuit faults. Refer ISO/ IEC13849-2.
Installation
Mitsubishi FR-A800/F800 safety stop function should be used under following condition and environment.
Table.1 The condition and environment for using safety stop function
Item Condition
Surrounding air temperature
Storage temperature -20ºC to +65ºC
Ambient humidity
Vibration
Altitude Maximum 2500 above sea level
Atmosphere Indoors (free from corrosive gas, flammable gas, oil mist, dust and dirt)
Over voltage category III or less
Pollution degree II or less
Mounting Wall mounting / vertical orientation
LD, ND, HD
SLD -10ºC to +40ºC (non-freezing)
 -10ºC to +50ºC (non-freezing)

With circuit board coating (conforming to IEC60721-3-3 3C2/3S2): 95% RH or less (non-condensing), Without circuit board coating: 90% RH or less (non-condensing)
2
5.9m/s
or less at 10 to 55Hz (directions of X, Y, Z axes)

 The ND and HD ratings can be selected only for the FR-A800.  Temperature applicable for a short time, e.g. in transit.  For the installation at an altitude above 1,000 m (3280.80 feet) up to 2,500 m (8202 feet), derate the rated current 3% per 500
m (1640.40 feet).
INSTALLATION AND WIRING
3
CAUTION
In order to meet safety stop, an approved safety relay unit to ISO13849-1 safety category 3 or better
shall be used in conjunction with FR-A800/F800 as shown in example. In addition, all other components with in the safety stop loop shall be ‘safety approved’ types.
WARNING
To avoid an electric shock hazard, insert the magnetic contactor (MC) between power source and
drive.
Open the contact of MC and keep away from drive for discharging time (refer to your drive’s User
Manual for information) before performing any work on the drive. And verify that the voltage on the bus capacitors has discharged before Measuring the DC bus voltage at the P(+) and N(-) terminals or test points (refer to your drive’s User Manual for locations). The voltage must be zero.
CAUTION
To avoid systematic faults, a test even for faulty demands of the safety function has to be performed
in order to check the correct function of the monitor signal. This test shall be carried out at system installation, any software changes, parameterization changes, and/or at least once per year. Refer to ‘4. Test and checking failure’.
Wiring
The safety related terminals are described in Table.2 and Table.3
Table.2 The safety related terminals
Term i nal
symbol
For input of safety stop channel 1.
S1
S2
SIC Common terminal for S1 terminal and S2 terminal.
SO
SOC Common terminal for SO terminal.
S1-SIC is OFF: In safety stop mode. ON: Non safety stop mode.
For input of safety stop channel 2. S2-SIC is OFF: In safety stop mode. ON: Non safety stop mode.
As output for failure detection and alarm. SO terminal type is ‘Open collector output’. SO-SOC is OFF: Detect failure or alarm. ON: No failure detected.
Note: This terminal cannot be used to output safety outputs in a
safety system. This terminal can be used for alarm or to prevent restart only, no other safety function.
 Specifications for conforming safety standards.  ON: The transistor is conducted. OFF: The transistor is not conducted.
Description  Rating 
Input resistance: 4.7k Input current : 4 to 6 mADC (In case of 24VDC input)
Load: 24VDC/0.1A max. Voltage drop: 3.4V max. (In case of ‘ON’ state)
4
INSTALLATION AND WIRING
Table.3 Truth table of safety related signals
Error definition Operation panel indication
Option fault. E.OPT
Communication option fault E.OP1
Parameter storage device fault E.PE
Retry count excess E.RET
Parameter storage device fault E.PE2
Operation panel power supply short circuit/ RS-485 terminals power supply short circuit
E.CTE
24 VDC power fault E.P24
Safety circuit fault E.SAF
Overspeed occurrence E.OS
CPU fault
E.CPU
E.5 to E.7
Internal circuit fault E.13
Error definition Operation panel indication
Input
power
Internal
safety circuit status
Input terminal , 
S1 S2 SO E.SAF  SA 
Output
terminal
Inverter running status
OFF OFF Output shutoff (Safe state)
 Drive enabled
 Output shutoff (Safe state) Displayed Displayed  Output shutoff (Safe state) Displayed Displayed
 Output shutoff (Safe state)
ON
Normal ON ON ON
Normal ON OFF OFF Normal OFF ON OFF
Normal OFF OFF ON
Fault ON ON OFF Output shutoff (Safe state) Displayed
Fault ON OFF OFF Output shutoff (Safe state) Displayed Displayed Fault OFF ON OFF Output shutoff (Safe state) Displayed Displayed Fault OFF OFF OFF Output shutoff (Safe state) Displayed Displayed
 ON: The transistor is conducted. OFF: The transistor is not conducted.  When not using the safety stop function, short across terminals S1 and PC, S2 and PC, and SIC and SD to use the inverter.
(In the initial status, terminals S1 and PC, S2 and PC, and SIC and SD are respectively shorted with shorting wires.)
 If any of the protective functions shown in the following table is activated, the terminal SO turns OFF.
Operation panel
indication
Not displayed
Not displayed
Not displayed
Not displayed
Not displayed
Displayed
Not displayed

 If the internal safety circuit is operated normally, the terminal SO remains ON until E.SAF is displayed, and the terminal SO
turns OFF when E.SAF is displayed.
 SA is displayed when the terminals S1 and S2 are identified as OFF due to the internal safety circuit failure.  If another fault occurs at the same time as E.SAF, the other fault can be displayed.  If another warning occurs at the same time as SA, the other warning can be displayed.
NOTE
• The response time from safety stop signal input to drive shutoff (safe state) is faster than 8ms.
• Hold the ON or OFF status for 2ms or longer to input signal to terminal S1 or S2. Signal input shorter than 2ms is not recognized.
INSTALLATION AND WIRING
5
Wire and ferrule specification
Table.4 Wire and ferrule specification
Wire size (mm2)
Ferrule with insulation collar  Crimping tool name 
0.3 / 0.5 AI 0,5-10WH
0.75 AI 0,75-10GY
1AI 1-10RD
CRIMPFOX 6
1.25 / 1.5 AI1,5-10BK
0.75 (combined 2 wire) AI TWIN 2 X 0,75-10GY
 Ferrules and tools are distributed by Phoenix Contact.
Jumper cable
The jumper cable between S1,S2 and PC terminal between SIC and SD terminal has been installed in the factory
as shown in Fig.2.
2 5 4 1 F/C
AM
5 10E 10 SE SE SU
+24
SD SD S1 S2 PC A1 B1 C1 A2 B2 C2SICSo
SOC
RUN
IPF OL FU PC RL RM RH RT AU SD SD CSSTP
MRS RES
STF STR
JOG
Terminal block of FR-A800/F800
Fig.2. Short wire
Before connecting safety input wire to S1,S2 and SIC terminal, remove this jumper cable.
6
INSTALLATION AND WIRING
3 EXAMPLE OF SAFETY SYSTEM
S 2
FR-A800/F800
SO
R/L1 S/L2
T/L3
IGBTs
SOC
RESET
+24V
X0
X1
24G
XS0
XS1
Z10
Z00
Z20
Z11
Z01 Z21
24V DC
S a f e t y r e l a y module
M E L S E C Q S 9 0 S R 2 S N-Q
STF
START
STOP
Emergency stop button
G
PC
*1
Fuse
ASIC
Gate
Drive r
G
Gate
CPU
SD
U
V
W
M
STOP
COM0
COM1
Internal
Safety Circuit
24V DC
Drive r
CONFIGURATION
FR-A800/F800 configuration example
Logic
S 1
K1
K 2
SIC
NOTE
CAUTION
To prevent restart in case of recovering from input power loss of drive, 3-wired connection for
START/STOP control is recommended. In case of 2-wire connection and using latching type switch to short between STF and SD/PC for starting, ensure the compliance with safety requirement for the restarting when the drive recover from input power loss.
+24V
 If the control logic is SINK logic, the common terminal is terminal SD.
Fig.3 Safety system example with FR-A800/F800
• When starting up the system’s operation, press the RESET switch to reset the safety stop function first,
then turn ON the START switch to run the motor.
• In the above configuration, after reset of emergency stop button, drive will be in safe-state until RESET
switch is pressed.

EXAMPLE OF SAFETY SYSTEM CONFIGURATION

7
Multiple inverter configuration example
NOTE
RESET
SO
SOC
R/L1 S/L2
T/L3
Logic
Emergency stop button
24V DC
COM0
X1
Internal
Safety
Circuit
COM1
X0
+24V
24G
S a f e t y r e l a y module
M E L S E C Q S 9 0 S R 2 S N-Q
XS0
K1
K 2
XS1
Z00
Z10
Z11
Z01 Z21
24V DC
Z20
SO
SOC
SIC
SD
PC
S 2
S 1
CPU
ASIC
Gate
Drive r
G
Gate
Drive r
IGBTs
G
+24V
Fuse
FR-A800/F800
W
U
V
M
R/L1 S/L2
T/L3
Logic
CPU
ASIC
Gate
Drive r
Gate Drive r
IGBTs
S 2
S 1
SIC
SD
PC
G
+24V
Fuse
FR-A800/F800
G
W
U
V
M
Fig.4 When using multiple safety stop function inverters (FR-A800/F800)
• Some models cannot be used together because their control logics are different. Refer to the SAFETY
STOP FUNCTION MANUAL of each model.
8
EXAMPLE OF SAFETY SYSTEM CONFIGURATION
Safety controller configuration example
WS0-C PU0
24VDC
X1
X2
FLEXBUS+
FLEXBUS+
I8
I7
I6
I5
I4
24V 0V
WS0-X TIO
Q4
Q3
Q2
Q1
I1
I2 I3
WS0-CPU0
A1(24V)
A2(0V)
A2(0V)
Application
FLEXBUS+
FLEXBUS+
I8
I7
I6
I5
I4
24V 0V
WS0-XTIO
I1 I2
I3
A1(24V)
RESET
MITSUBISHI safety controller MELSEC-WS series CPU module WS0-CPU0 Safety I/O combined module WS0-XTIO
Emergency stop button
Application
R/L1 S/L2 T/L3
UV W
M
SO
SOC
S1
S2
G G
FR-A800/F800
SIC
SD
PC
Gate
Driver
Gate
Driver
IGBTs
Fuse
CPU
+24V
Logic
ASIC
Fig.5 Safety system example with FR-A800/F800
NOTE
• When starting up the system’s operation, press the RESET switch to reset the safety stop function first.
• In the above configuration, after reset of emergency stop button, drive will be in safe-state until RESET
switch is pressed.
EXAMPLE OF SAFETY SYSTEM CONFIGURATION
9

4 TEST AND CHECKING FAILURE

NOTE
Error definition Operation panel indication
Option fault. E.OPT
Communication option fault E.OP1
Parameter storage device fault E.PE
Retry count excess E.RET
Parameter storage device fault E.PE2
Operation panel power supply short circuit/ RS-485 terminals power supply short circuit
E.CTE
24 VDC power fault E.P24
Safety circuit fault E.SAF
Overspeed occurrence E.OS
CPU fault
E.CPU
E.5 to E.7
Internal circuit fault E.13
Error definition Operation panel indication
CAUTION
To avoid systematic faults, a test even for faulty demands of the safety function has to be performed
in order to check the correct function of the monitor signal. This test shall be carried out at system installation, any software changes, parameterization changes, and/or at least once per year.
I/O status and failure
FR-A800/F800 safety related I/O status obeys the following truth table.
Table.5 Truth table of safety related signals
Input
power
Internal
safety circuit status
Input terminal , 
S1 S2 SO E.SAF  SA 
OFF OFF Output shutoff (Safe state)
Normal ON ON ON
Normal ON OFF OFF Normal OFF ON OFF
ON
Normal OFF OFF ON
Fault ON ON OFF Output shutoff (Safe state) Displayed
Fault ON OFF OFF Output shutoff (Safe state) Displayed Displayed Fault OFF ON OFF Output shutoff (Safe state) Displayed Displayed Fault OFF OFF OFF Output shutoff (Safe state) Displayed Displayed
 ON: The transistor is conducted. OFF: The transistor is not conducted.  When not using the safety stop function, short across terminals S1 and PC, S2 and PC, and SIC and SD to use the inverter.
(In the initial status, terminals S1 and PC, S2 and PC, and SIC and SD are respectively shorted with shorting wires.)
 If any of the protective functions shown in the following table is activated, the terminal SO turns OFF.
Output
terminal
Inverter running status
Operation panel
indication
Not displayed
 Drive enabled
 Output shutoff (Safe state) Displayed Displayed  Output shutoff (Safe state) Displayed Displayed
 Output shutoff (Safe state)
Not displayed
Not displayed
Not displayed
Not displayed
Displayed
Not displayed

 If the internal safety circuit is operated normally, the terminal SO remains ON until E.SAF is displayed, and the terminal SO
turns OFF when E.SAF is displayed.
 SA is displayed when the terminals S1 and S2 are identified as OFF due to the internal safety circuit failure.  If another fault occurs at the same time as E.SAF, the other fault can be displayed.  If another warning occurs at the same time as SA, the other warning can be displayed.
• The response time from safety stop signal input to drive shutoff (safe state) is faster than 8ms.
• Hold the ON or OFF status for 2ms or longer to input signal to terminal S1 or S2. Signal input shorter than 2ms is not recognized.
10
TEST AND CHECKING FAILURE
Diagnostic
If the failure detected, FR-A800/F800 output alarm signal and indicate ‘E.SAF’ at the display.
In case of FR-A800/F800 output the alarm, please take following action.
1) Check the S1-SIC and S2-SIC input signal logic is the same. If these are different logic, collect the input signal
and reset the FR-A800/F800.
2) Disconnect the wire from S1, S2, SIC terminal, then reset or power-off and on. If the ‘SA’ letter is flashed up at
display, there is failure in system except FR-A800/F800. But, still ‘E.SAF’ is displayed and alarm output, there
is malfunction on FR-A800/F800.
Self diagnostic test
FR-A800/F800 does the self-diagnostic test on the power-ON.
If FR-A800/F800 output alarm (SA, E.SAF) at power-up, please take the action described in ‘Diagnostic’ at
above.
Test procedure for functionality
As depicted ‘CAUTION’ in above, the test for the functionality is important.
Please do the test following procedure.
1) Please make each state of S1-SIC and S2-SIC depicted at Table.5.
2) If there is any different state from Table.5, FR-A800/F800 has some malfunction.
3) If there is no different state from Table.5, check the systematic performance, such as, press the emergency
switch, press the start/restart button at the failure detected (SO-SOC opened), and so on.
4) Finally clear the error record of the FR-A800/F800 (see the user manual how to clear the error record).

5 SAFETY PARAMETERS OF FR-A800/F800

The safety parameters of FR-A800/F800 are depicted as follows.
Table.6 Safety parameters of FR-A800/F800
Parameter Value
PFDAVG
PFHD
PL d
MTTF
D 670 years
AVG 60%
DC
5.16x10
5.89x10
-4
-9
SAFETY PARAMETERS OF FR-A800/F800
11

REVISIONS

Modification
Print Date Manual Number Revision
Apr. 2013 BCN-A23228-001(E) First edition
Jun. 2013 BCN-A23228-001-A(E)
Jul. 2014 BCN-A23228-001-B(E) Compatibility with the FR-F800 series
Multiple inverter configuration example
12
BCN-A23228-001-B(E)
HEADQUARTERS EUROPEAN REPRESENTATIVES EUROPEAN REPRESENTATIVES
z
MITSUBISHI ELECTRIC EUROPE EUROPE B.V. German Branch Gothaer Straße 8
D-40880 Ratingen
Phone: +49 (0) 21 02 / 486-0 Hotline: +49 2102 1805 000-765 /-766 Fax: +49 (0) 21 02 / 4 86-1 12 0 e mail: megfa-mail@meg.mee.com www.mitsubishi-automation.com
MITSUBISHI ELECTRIC FRANCE FRANCE 25, Boulevard des Bouvets
F-92741 Nanterre Cedex
Phone: +33 1 55 68 55 68 Fax: +33 1 49 01 07 25 e mail: factory.automation@fra.mee.com
MITSUBISHI ELECTRIC ITALY EUROPE B.V. Italian Branch C.D. Colleoni-P. Perseo lng. 2 Via Paracelso 12
I-20041 Agrate Brianza (Ml)
Phone: +39 (0) 39 / 60 53 1 Fax: +39 (0) 39 / 60 53 312 e mail: factory.automation@it.mee.com
MITSUBISHI ELECTRIC SPAIN EUROPE B.V. Pol. lnd. Can Magi-C. Calle Joan Buscallá, 2-4 AC 420
E-08190 Sant Cugat del Vallés
Phone: +34 (9) 3 / 565 31 31 Fax: +34 (9) 3 / 589 29 48
MITSUBISHI ELECTRIC UK EUROPE B.V. UK Branch Travellers Lane
Hatfield, Hertfordshire, AL10 8 XB
Phone: +44 (0) 1707 / 27 61 00 Fax: +44 (0) 1707 / 27 86 95
MITSUBISHI ELECTRIC JAPAN CORPORATION Tokyo Bldg. 2-7-3 Marunouchi Chiyoda-Ku
Tokyo 100-8310
Phone: +81 (0) 3 / 32 18 31 76 Fax: +81 (0) 3 / 32 18 24 22
MITSUBISHI ELECTRIC USA AUTOMATION 500 Corporate Woods Parkway
Vernon Hills, Illinois 60061
Phone: +1 (0) 847 / 478 21 00 Fax: +1 (0) 847 / 478 03 27
GEVA AUSTRIA Wiener Straße 89
A-2500 Baden
Phone: +43 (0) 2252 / 85 55 20 Fax: +43 (0) 2252 / 488 60 e mail: office@geva.co.at
Getronics b.v. BELGIUM Control Systems Pontbeeklaan 43
B-1731 Asse-Zellik
Phone: +32 (0) 2 / 4 67 17 51 Fax: +32 (0) 2 / 4 67 17 45 e mail: infoautomation@getronics.com
TELECON CO. BULGARlA 4, A. Ljapchev Blvd.
BG-1756 Sofia
Phone: +359 92 / 97 44 05 8 Fax: +359 92 / 97 44 06 1 e mail: ——
AutoCont CZECHIA Control Systems s.r.o. Nemocnicni 12
CZ-70200 Ostrava 2
Phone: +420 (0) 69 / 615 21 11 Fax: +420 (0) 69 / 615 21 12 e mail: ——
louis poulsen DENMARK industri & automation Geminivej 32
DK-2670 Greve
Phone: +45 (0) 43 / 95 95 95 Fax: +45 (0) 43 / 95 95 91 e mail: lpia@lpmail.com
UTU Elektrotehnika AS ESTONIA Pärnu mnt. 160i
EE-10621 Tallinn
Phone: +372 6 / 51 72 80 Fax: +372 6 / 51 72 88 e mail: utu@utu.ee
URHO TUOMINEN OY FINLAND Hevoshaankatu 3
FIN-28600 Pori
Phone: +358 (0) 2 / 55 08 00 Fax: +358 (0) 2 / 55 088 41 e mall: ——
UTECO A.B.E.E. GREECE 5, Mavrogenous Str.
GR-18542 Piraeus
Phone: +30 (0) 1 / 42 10 050 Fax: +30 (0) 1 / 42 12 033 e mall: uteco@uteco.gr
MITSUBISHI ELECTRIC IRELAND EUROPE B.V.-Irish Branch Westgate Business Park Ballymount
IRL-Dublin 24
Phone: +353 (0) 1 / 419 88 00 Fax: +353 (0) 1 / 419 88 90 e mail: sales.info@meuk.mee.com
ALFATRADE LTD. MALTA 99 Paola Hill
Paola PLA 08
Phone: +356 / 697816 Fax: +356 / 697817 e mail: paul.licari@alfatrx.com
Getronics bv NETHERLANDS Control Systems Donauweg 10
NL-1043 AJ-Amsterdam
Phone: +31 (0) 20 / 586 15 92 Fax: +31 (0) 20 / 586 19 27 e mail: infoautomation@getronics.com
Beijer Electronics AS NORWAY Teglverksveien 1
N-3002 Drammen
Phone: +47 (0) 32 / 24 30 00 Fax: +47 (0) 32 / 84 85 77 e mall: ——
MPL Technology SP.Z.o.o POLAND ul.Wroclawska 53
PL-30-011 Kraków
Phone: +48 (0) 12 / 632 28 85 Fax: +48 (0) 12 / 632 47 82 e mail: krakow@mpl.com.pl
Sirius Trading&Services srl ROMANIA Bd. Ghica nr. 112, BI. 41
RO-72335 Bucaresti 2
Phone: +40 (0) 1 / 210 55 11 Fax: +40 (0) 1 / 210 55 11 e mail: sirius_t_s@fx.ro
ACP AUTOCOMP a.s. SLOVAKIA Chalupkova 7
SK-81109 Bratislava
Phone: +421 (0) 7 592 22 54 Fax: +421 (0) 7 592 22 48 e mall: ——
lNEA d.o.o. SLOVENlA Ljubljanska 80
SI-1230 Dom ale
Phone: +386 (0) 17 21 80 00 Fax: +386 (0) 17 24 16 72 e mail: inea@inea.si
EUROPEAN REPRESENTATIVES
Beijer Electronics AB SWEDEN Box 426
S-20123 Malmö
Phone: +46 (0) 40 / 35 86 00 Fax: +46 (0) 40 / 93 23 02 e mall: ——
ECONOTEC AG SWITZERLAND Postfach 282
CH-8309 Nürensdorf
Phone: +41 (0) 1 / 838 48 11 Fax: +41 (0) 1 / 838 48 12 e mall: ——
GTS TURKEY Darülaceze Cad. No. 43A KAT: 2
TR-80270 Okmeydani-Istanbul
Phone: +90 (0) 212 / 320 1640 Fax: +90 (0) 212 / 320 1649 e mall: ——
EURASIAN REPRESENTATIVES
MITSUBISHI ELECTRIC RUSSIA EUROPE B.V. 12/1 Goncharnaya St, suite 3C
RUS-109240 Moskow
Phone: +7 (0) 95 / 915-8624/02 Fax: +7 (0) 95 / 915-8603 e mall: ——
STC Drive Technique RUSSIA Poslannikov per., 9, str. 1
RUS-107005 Moskow
Phone: +7 (0) 95 / 786 21 00 Fax: +7 (0) 95 / 786 21 01 e mall: ——
JV-CSC Automation UKRAINE 15, M. Raskovoyi St., Floor 10, Office 1010
U-02002 Kiev
Phone: +380 (4) 4 / 238 83 16 Fax: +380 (4) 4 / 238 83 17 e-Mail: mkl@csc-a.kiev.ua
MIDDLE EAST REPRESENTATIVE
SHERF Motion Techn. LTD ISRAEL Rehov Hamerkava 19
IL-58851 Holon
Phone: +972 (0) 3 / 559 54 62 Fax: +972 (0) 3 / 556 01 82 e mall: ——
HEAD OFFICE: TOKYO BUILDING 2-7-3, MARUNOUCHI, CHIYODA-KU, TOKYO 100-8310, JAPAN
BCN-A23228-001-B(E)(1407)MEE Printed in Japan Specifications subject to change without notice.
Loading...