ION F-16 User Manual

F-16
LINE INTERACTIVE UPS
UPS USER MANUAL
1KVA/1.5KVA/2KVA/3KVA
ION F-16
INSTRUCTIONS
SAVE THESE INSTRUCTIONS
This user manual contains important instructions for the
I
ON F-16 1000VA / 1500VA/ 2000VA / 3000VA series which
should be followed for the installation and maintenance of
the UPS and batteries. Please read all safety and operating
instructions before operating the UPS. Adhere to all
warnings on the unit and in this manual and follow all
operating and user instructions.
CONTENTS
1. Introduction ············································································································ 1
2. Safety Warning ······································································································· 2
2.1 Description of Commonly Used Symbols ····························································· 3
3. Installation ·············································································································· 4
3.1 Inspection of Unit ······························································································· 4
3.2 Unpacking the Cabinet ······················································································· 4
3.3 UPS Setup ········································································································· 4
3.4 EBM Installation (Optional) ················································································· 9
3.5 UPS Initial Startup ···························································································· 15
4. Operation ·············································································································· 16
4.1 Display Panel ··································································································· 16
4.2 Operating Mode ······························································································· 20
4.3 Configuring Load Segment ··············································································· 20
4.4 Configuring UPS for EBM Numbers ·································································· 21
4.5 Configuring Green Function ·············································································· 21
5. Communication Port····························································································· 22
5.1 RS-232 and USB Communication Ports ···························································· 22
5.2 Emergency Power Off (EPO) ············································································ 22
5.3 Network Management Card (Optional) ······························································ 23
6. UPS Maintenance ································································································· 24
6.1 UPS and Battery Care ······················································································ 24
6.2 Storing the UPS and Batteries ·········································································· 24
6.3 Time to Replace Batteries················································································· 24
6.4 Replacing UPS Internal Batteries ······································································ 25
6.5 Testing New Batteries ······················································································· 27
6.6 Recycling the Used Battery:·············································································· 27
7. Specification ········································································································· 28
7.1 Specification ···································································································· 28
7.2 Rear Panels ····································································································· 30
8. Trouble Shooting ·································································································· 33
8.1 Audible Alarm Trouble Shooting ········································································ 33
8.2 General Trouble Shooting ················································································· 33
9. Software Installation ····························································································· 34
1
1. Introduction
This ION F-16 line-interactive series is compact and pure sine wave UPS and designed for essential applications and environments, such as desktops, servers, workstations, and other networking equipment. These models are available in the output ratings of 1000VA, 1500VA, 2000VA and 3000VA. The series protects your sensitive electronic equipment against power problems including power sags, spike, brownouts, line noise and blackouts.
The series is convertible to rack and tower forms. It can be placed either in Rack 2U or Tower form. The front panel of the ION F-16 UPS includes LCD display and four control buttons which allow users to monitor, configure and control the unit. The LCD includes a graphical bar, two status indications and four alarm indications. A control button on the front panel allows users to silence the AC fail alarm and initiate the UPS self-test sequence. The UPS case for 1000VA ~ 3000VA is made of metal. This series is powered from the AC mains and supply AC outputs via receptacles on the rear panel. Communication and control of the UPS is available through serial or USB ports located on the rear panel. The serial port supports communications directly with a server.
Features:
Microprocessor control guarantees high reliability
High frequency design
Built-in boost and buck AVR Easy battery replacement design Selectable input and output range Cold start capability Built-in Dry contact/RS-232/USB communication port SNMP allows for web-based remote or monitoring management Enable to extend runtime with scalable external battery module(EBM) Overload, short-circuit, and overheat protection Rack/Tower 2 in 1 Design 19 inches rack mount available for all models
2
2. Safety Warning
DANGER:
This ION UPS contains high voltage. All repairs and service should be performed by authorised service personnel only. There are no user serviceable parts inside the UPS.
WARNING:
This ION UPS contains its own energy source (batteries).The UPS output may
carry live voltage even when the UPS is not connected to an AC supply.
To reduce the risk of fire or electric shock, install this UPS in a temperature and
humidity controlled, indoor environment, free of conductive contaminants.(Ambient :0-40°C)
To reduce the risk of fire, connect to a circuit breaker provided with 20 amperes
maximum branch circuit over-current protection.
To comply with international standards and wiring regulations, the sum of the
leakage currents of the UPS and the connected loads must not exceed 3.5mA.
The socket outlet that supplies the UPS should be installed close to this unit
and be easily accessible.
Protective earthing connections - a disconnection of a protective earth should
be made at a point furthest away from the UPS, maintaining the dedicated line in order to secure equipotential connection.
The UPS and EBMs connected in a series should be installed close to each
other so that the operators cannot touch the interconnecting wire which is basic insulated from primary circuit.
CAUTION:
Batteries may present a risk of electrical shock or burnt from high short-circuit
current. Observe proper precautions. Servicing should be performed by qualified service personnel experienced with batteries and required precautions. Keep unauthorised personnel away from batteries.
Proper disposal of batteries is required. You should refer to your requirements
in your jurisdiction for disposal.
3
Never dispose of batteries by incineration. Batteries may explode when
exposed to flame.
Following figure shows the basic internal circuit configuration of the ION UPS
2.1 Description of Commonly Used Symbols
Some or all of the following notations in this manual may appear in your a
pplication process. All UPS users should be familiar with and understand
these notations.
Table1. Description of Commonly Used Symbols
S
ymbol Description
Alert you to pay special attention
Caution of high voltage
Alternating current source (AC)
Direct current source(DC)
Protective ground
Recycle
Keep UPS in a clear area
4
3. Installation
3.1 Inspection of Unit
Inspect the UPS upon receiving. If the UPS appears to be damaged from shipment, keep the box and packing material in its original form from the carrier and notify the carrier and dealer immediately.
3.2 Unpacking the Cabinet
To unpack the system:
1. Open the outer carton and remove the accessories packaged with the cabinet.
2. Carefully lift the cabinet out of the outer carton and set it on a flat, stable surface.
3. Discard or recycle the packaging in a responsible manner, or store it for future use.
3.3 UPS Setup
All model series are designed for tower and rack deployment and can be installed into a 19 inch equipment rack. Please follow the instruction for Tower Setup and Rack-Mount Setup.
Tower setup
This series of ION UPS can be placed horizontally and vertically. For a tower configuration, stands have been provided to stabilise the UPS when it is positioned vertically. The UPS stand must be attached to the bottom of the tower.
5
Use the following procedure to install ION UPS in its stands.
1. Slide the UPS down vertically and put the two stands at the end of the tower.
2. Place the UPS down between the two stands carefully
.
6
3. Pull out the LCD box and rotate it in a clockwise direction to 90 degrees and then push it back in the front panel.
7
Rack-mount setup
The series can be installed in 19 inch racks. Both the UPS and external battery enclosure need 2U of available rack space.
Use the following procedure to install the UPS in a rack.
1. Align the mounting ears with screw holes on the side of the UPS and tighten the screw.
2. Assemble the rack rails with the rack-mounting.
8
3. Slide the UPS into the rack rail and lock it in the rack enclosure.
4
. Tighten the screw, and the load can then be connected.
9
3.4 EBM Installation (Optional)
Connecting the EBM in Tower form:
1. Slide the UPS and EBM down vertically and place the two UPS stands with the extended part at the end of the tower.
2. Tighten the screw on the metal sheet to stabilise
3. Connect the Earth line from UPS (port A) to EBM (p
ort B)
B
A
10
4. Take off the front panel, and connect the battery terminal (A) from UPS to EBM terminal (B) as shown below. Users should remove the small gate (C) on side of the front panel to allow the outlet wire of the EBM to pass through the gate and then reassemble the front panel.
Connecting the EBM in a rack form
1. Using the same method as assembling UPS in a rack form, assemble EBM into the rack-mounting on the above or below the UPS.
B
A
C
11
2. Connect the earth line from UPS (port A) to EBM (port B)
3. Take off the LCD box, and unscrew the internal screw
s.
A
B
Unscrew
Unscrew
12
4. Take off the front panel, and connect the battery terminal (A) from UPS to EBM terminal (B) shown as below. Users need to remove the small gate (C) on side of the front panel to allow the outlet wire of the EBM to pass through the gate and then reassemble front panel.
5
. After installing the UPS into the rack, the load can then be connected.
Please make sure the load equipment is turned off before plugging all loads into the output receptacle.
Connecting Multiple EBMs
1000VA / 1500VA / 2000VA and 3000VA UPS include external battery ports allowing users to connect multiple EBMs in order to provide additional backup time. Follow the procedure to install multiple EBMs below.
B
A
C
13
Connecting multiple EBMs in Tower form
1. Connect Earth line between UPS and the first EBM, then connect the Earth Line between the first EBM and the second EBM.
2. Take off the front panel, and connect the battery terminal (A) from UPS to EBM terminal (B) shown as below, then connect the battery terminal (D) from the first EBM to the battery terminal (E) from the second EBM. Users need to remove the small gate (C) on side of the front panel to allow the outlet wire of the EBM to pass through the gate and then reassemble front panel.
B
C
A
D
E
14
Connecting Multiple EBMs in rack form
1. Connect Earth line between UPS and the first EBM, then connect the Earth Line between the first EBM and the second EBM.
2. Take off the front panel, and connect the battery te
rminal (A) from UPS to EBM terminal (B) shown as below, then connect the battery terminal (D) from the first EBM to the battery terminal (E) from the second EBM. Remove the small gate (C) on side of the front panel to allow the outlet wire of the EBM to pass through the gate and then reassemble the front panel.
Note:
Three or more EBMs can be connected to the UPS in the same way as shown
above.
E
B
C
A
D
15
3.5 UPS Initial Start-up
To start up the ION UPS:
1. Verify that the internal batteries are connected. If optional EBMs are installed, verify that the EBMs are connected to the UPS.
2. Plug the equipment to be protected onto the UPS, but do not turn on protected equipment.
3. Plug in the UPS input power cord. The UPS front panel display illuminates and UPS status display shows “STbY”
4. Press and hold the button for at least 3 seconds. The UPS status display then changes to “NORM”
6. Check the UPS display for active alarms or notices. Resolve any active alarms before continuing. See “Troubleshooting”
8. If optional EBMs are installed, see “Configuring UPS for EBM numbers” on page 21 to set the number of installed EBMs.
9. To change any other factory-set defaults, see “Operation”
Note: At initial start-up, the UPS sets system frequency according to input line frequency.
16
4. Operation
4.1 Display Panel
This ION UPS has a four-button graphical LCD with dual colour backlight. Standard back-light is used to light up the display with black text and a blue background. When the UPS has a critical alarm, the backlight changes the background to red. See Figure below:
C
ontrol Buttons functions:
There are four buttons on the control panel.
ON/OFF
UPS Test /Alarm Silence
Select
Enter
17
The following table describes the functions of the LCD control buttons.
Table2. Description of control button
Control
Button
Switch Function
ON/OFF
--To turn on/off the UPS
Press and hold the button for at least 3 seconds.
--To release the UPS from faulty mode
Cut off input power and then press and hold the button for at least 2 seconds to shut down the
UPS.
UPS Test Alarm Silence
--To perform basic function test
Press and hold the button for 3 seconds.
--To perform Battery life test
Press and hold the button for 10 seconds.
-- To disable alarm buzzer
Press the button for one second.
Select
Press the Select button to select the settings value one by one
Enter
-- Enter settings mode
Press and hold the button for 3 seconds.
-- Enter settings item
Press and hold the Enter button for 1 second, the UPS allows users to configure the settings, and the settings string will flash.
-- Confirm settings
Press and hold the Enter button for 1 second.
-- Exit Settings mode
Press and hold the Enter button for 3 seconds or button for 0.5 second.
Note: Ensure the battery is fully charged during line mode when conducting functional tests.
Note: The events for which the alarm buzzer cannot be disabled are: Low Battery, Fan Failed, Fan Fault Time Out, and Overheat.
Note: You can disable the alarm buzzer when it’s sounding, but the alarm will still sound when a new alarm event is encountered.
18
LCD display functions:
The following table describes the functions of the LCD display.
Table3. Description of LCD display function
No. Description Function
Input frequency and voltage
Indicates the value of input frequency and voltage
Input plug indicator
Light is on when the UPS has input power.
Output frequency and voltage
Indicates the value of output frequency and voltage
Output plug indicator
The UPS has two groups of outlets. The output plug indicator will be lit when there is output power.
UPS status/user setting display String
Strings indicate the UPS status (see Table 4) Strings indicate user setting options (see Table 5)
Warning indication Light is on when the UPS has failure or alarm.
Settings
Light is on when the UPS is on settings mode.
Battery volume level display
Indicates the amount of battery volume remaining. Each battery volume level bar indicates a 20% of total battery volume
Load capacity level display
Indicates the percentage of UPS load capacity being used by the protected equipment. Each LCD level bar indicates 20% of the total UPS output capacity.
19
UPS Status Display String Description:
The following table shows the description of the LCD display string:
Table4. UPS Status Display String
LCD Display String
Description
STbY UPS is on Standby mode
IPVL Input voltage is too low
IPVH Input voltage is too high
IPFL Input frequency is too low
IPFH Input frequency is too high
NORM UPS is working on Line mode
AVR UPS is working on AVR mode bATT UPS is working on Battery mode TEST UPS is working on battery life/function test mode
OPVH Battery mode, the output is too high
OPVL Battery mode, the output is too low OPST Output short OVLD Overload
bATH Battery voltage is too high
bATL Battery voltage is too low
OVTP Internal temperature is too high
FNLK Fan is locked
bTWK Batteries are weak
User Setting String Description:
The following table shows the options that can be changed by user.
Table5. User Setting String
OPV Output voltage mode select
[220]= 220V [230]= 230V [240]= 240V
AVR Input type select
[000]= Normal range mode [001]= Wide range mode [002]= Generator mode
EbM
External battery module (EBM)
0~9 is the number of external battery module
TEST Auto self-test
[000]=Disable [001]=Enable
20
AR Automatic restart
[000]=Disable [001]=Enable
GF Green function
[000]=Disable [001]=Enable
bZ Buzzer control
[000]=Disable [001]=Enable
LS1 Load segment 1
[000]=Turn off [001]=Turn on
LS2 Load segment 2
[000]=Turn off [001]=Turn on
4.2 Operating Mode
Normal range mode: Under Input mode, the UPS accepts AC input voltage
range for +/-20%.
Generator mode: Under generator mode, the low frequency transfer point can
go as low as 40Hz and as high as 70Hz before being transferred to battery mode.
Wide range mode: Under Input settings mode, the UPS accepts AC input
voltage range for -30% ~ +20%.
Battery mode
When the UPS is operating during a power outage, the alarm beeps once every four seconds and the LCD display shows “bATT” to indicate the UPS is working on battery mode.
If battery volume becomes low while in Battery mode, the alarm beeps once every second and the LCD display string shows “bATL”.
Standby mode
When the UPS is turned off and remains plugged into a power outlet, the UPS is on Standby mode. The LCD display string shows “STbY” to indicate that power is not available to your equipment. The battery recharges when necessary.
4.3 Configuring Load Segment
Load segments are sets of receptacles that can be controlled through the display. Each UPS has two configurable load segments. See “Rear Panels” on page 30 for load segment for each UPS model.
Note: This configuring can be operated when UPS is power on.
To configure the load segment through the display:
1. Enter settings mode: Press and hold the Enter button
for 3 seconds. The
UPS will then transfer to setting mode.
2. Select settings items: Press the Select button
to select the setting items
show as Table 5.
21
3. Enter settings item: When the LCD display “LS1” or “LS2”, press the enter button for 1 second to enter the setting item and the settings string will
flash.
4. Select setting value: Press the Select button to select the settings value. Select the value [001] or [000] to set the desired load segment ON or OFF.
5. Confirm settings: Press and hold the Enter button for 1 second, the UPS will return to current setting item.
6. Exit Settings mode: Press and hold the Enter button for 3 seconds or button
for 0.5 second to exit setting mode.
4.4 Configuring UPS for EBM Numbers
To ensure the LCD displays the correct battery volume, configure the UPS for the correct number of EBMs:
1. Enter settings mode: Press for 3 seconds to enter setting mode.
2. Select settings items: Press to select setting items as “EbM”.
3. Enter settings item: Press for 1 second to enter the setting item.
4. Select setting value: Press the Select button to select the number of EBM according to your UPS configuration.
5. Confirm settings: Press and hold the Enter button
for 1 second, the UPS
will return to current setting item.
6. Exit Settings mode: Press and hold the Enter button for 3 seconds or button for 0.5 second to exit setting mode.
4.5 Configuring Green Function
The Green Function is for when an insignificant load amount is detected, which will shut the UPS output down automatically on battery mode.
The green function is disabled on default mode but the user can configure Green Function through the display:
1. Enter settings mode: Press for 3 seconds to enter setting mode.
2. Select settings items: Press to select setting items as “GF”.
3. Enter settings item: Press for 1 second to enter the setting item.
4. Select setting value: Press the Select button to select “001”.
5. Confirm settings: Press and hold the Enter button for 1 second, the UPS will then return to current setting item.
6. Exit Settings mode: Press and hold the Enter button for 3 seconds or button for 0.5 second to exit setting mode.
22
5. Communication Port
5.1 RS-232 and USB Communication Ports
To establish communication between the UPS and a computer, connect your computer to one of the UPS communication ports using an appropriate communication cable.
When the communication cable is installed, power management software will exchange data with the UPS. The software checks the UPS for detailed information on the status of the power environment. If a power emergency occurs, the software initiates the saving of all data and commences an orderly shutdown of equipment.
The cable pins for the RS-232 communication port are identified here, and the pin functions are described in Table 6.
Table6. DB9 Female (RS232 +dry contact)
PIN #
Description
I/O Function Explanation
1 BATLOW Output Battery low 2 RXD input RXD 3 TXD Output TXD 4 DTR Input N/A 5 Common -- Common (tied to chassis) 6 DTR Input N/A 7 RING Output Ring 8 LNFAIL1 Output Line fail
RS232 Communication Port
5.2 Emergency Power Off (EPO)
EPO is used to shut down the load from a distance. This feature can be used for shutting down the load on Emergency.
Warning:
This circuit must be separated from hazardous voltage circuits by reinforced insulation.
23
Caution:
The EPO must not be connected to any utility connected circuits. Reinforced insulation to the utility is required. The EPO Switch must have a minimum rating of 24Vdc and 20mA and a dedicated latching-type switch not tied into any other circuit. The EPO signal must remain active for at least 20 minutes for proper operation
EPO Connections
Wire Function Terminal Wire Size Rating Suggested Wire Size EPO 4-0.32mm2(12-22AWG) 0.82mm2(18AWG)
Note: Leave the EPO connector installed in the EPO port on the UPS even if the EPO function is not needed.
EPO Connector
5.3 Network Management Card (Optional)
Network Management Card allows the UPS to communicate in a variety of networking environments and with different types of devices. The series UPS has one available communication slot for Webpower or other optional cards to achieve remote management of the UPS through internet/ intranet. Please contact your local dealer for further information.
24
6. UPS Maintenance
6.1 UPS and Battery Care
For the best preventive maintenance, keep the area around the UPS clean and dust-free. If the atmosphere is dusty, clean the outside of the system with a vacuum cleaner. For long battery life, keep the UPS at an ambient temperature of 25°C (77°F)
6.2 Storing the UPS and Batteries
If you intend to store the UPS for a long period, recharge the battery every 6 months by connecting the UPS to utility power. The batteries charge to 90% capacity in approximately 4 hours. However, it is recommended that the batteries charge for 48 hours after long-term storage.
6.3 Time to Replace Batteries
When LCD backlight turns to red, the screen displays “bTWK” and there is a continuous sounding, the battery may need to be replaced. Check the battery connection or contact your local dealer to order a new battery.
WARNING:
Turn off the UPS and disconnect the utility power cord from the wall outlet. Servicing should be performed by qualified service personnel experienced
with batteries and required precautions. Keep unauthorised personnel away from batteries
Batteries can present a risk of electrical shock or burns from high short
circuit current. The following precautions should be observed:
1. Remove watches, rings, or other metal objects.
2. Use tools with insulated handles.
3. Do not lay tools or metal parts on top of batteries.
4. Wear rubber gloves and boots.
5. Disconnect the charging source prior to connecting or disconnecting battery terminal.
When replacing batteries, replace with the same type and number of
batteries or battery packs. Contact your service representative to order new batteries.
Do not incinerate batteries. Batteries may explode when exposed to flame.
Proper disposal of batteries is required. Refer to regulations in your
jurisdiction for disposal requirements.
Do not open or mutilate the battery as this may release toxic electrolyte
25
which is harmful to skin and eyes.
Note: If you are not qualified service personnel, do not attempt to open the battery cabin. Contact your local dealer or distributor immediately.
6.4 Replacing UPS Internal Batteries
Follow the steps and Charts as below to replace batteries:
1. Take off the LCD box, and remove the screws.
2. Slide and Pull the front panel leftward and then take it off.
3. Disconnect the cable from the UPS and battery pack.
26
4. Remove the right inner battery bracket.
5. Pull the battery pack out onto flat area.
6. Install new battery pack into UPS.
7. Screw up the battery bracket and reconnect the battery cable A and B
8. Re-install the front panel back to UPS.
27
6.5 Testing New Batteries
For a battery test:
Check that the batteries are fully charged. The UPS is in Normal mode with no active alarms. Do not take on/off the load.
To test batteries:
1. Connect the UPS to utility power for at least 48 hours to charge the batteries.
2. Press and hold the button 10 seconds to start the battery test. The status
display string shows “TEST”
6.6 Recycling the Used Battery:
Warning:
Never incinerate batteries in a fire as they may explode. Do not open or mutilate the batteries as this may release toxic electrolyte
which is harmful to the skins and eyes. A battery may present a risk of electrical shock and high short circuit current.
Recycle the used battery properly; do not discard the UPS, battery pack or batteries via garbage collection. Please follow your laws and regulations in your jurisdiction; contact your local recycling waste management centre for information on how to dispose the used UPS, battery pack and batteries properly.
28
7. Specification
7.1 Specification
Table7. Electrical Specification
Model
1000
1000S
1500
1500S
2000
2000S
3000
3000S
Capacity Watt 900W 1350W 1800W 2700W
Input
Input voltage range 161-276VAC
Frequency range
50/60Hz ±5Hz for Normal Mode
40-70Hz for Generator Mode
Output
Voltage 220/230/240VAC
Voltage Regulation (Batt. Mode)
±5%
Frequency 50Hz or 60Hz
Waveform Pure sinewave
Overload rating
Line Mode
110% -0%, +8%: shutdown after 3 minutes.
150% -0%, +10%: shutdown after about 200ms
Battery Mode
110% ± 6%; shutdown after 30 seconds.
120 % ± 6 %; Shutdown after about 100ms
Internal battery
Battery Type
12V/9AH
Backup Time (at full load)
6 3 6 3
Recharge Time
4 hours to
90% after
discharged
4 hours to
90% after
discharged
4 hours to
90% after
discharged
4 hours to
90% after
discharged
External battery module(EBM)
Battery Type
Depend on the Capacity of External Batteries
Backup Time (at full load) Recharge Time
Interface
RS-232
Optional
Dry-Contact
Optional
USB
Optional
SNMP
Optional
EPO
Optional
29
Table8. Indicators and Audible alarm
Indicator
AC Mode NORM---normal mode
Backup Mode Show “bATT” and sounding every 4 seconds
Load/Battery Level LCD showing
UPS Fault LCD show red screen and “ **** ”
Overload LCD show red screen and “ OVLD ”
Low Battery LCD show red screen and “ bTLW ”
Audible alarm
Backup Mode Sounding every 4 seconds
Low Battery Sounding every second
UPS Fault Continuously sounding
Overload Sounding every second
Battery Replacement Sounding every second
Table9. Operating Environment
Temperature 0 to 40°C
Humidity 20%-80% relative humidity (non-condensing)
Altitude
1500m
Storage Temperature
-15° to 45° C
Table10. Dimensions and weights
Model 1000 1000S 1500 1500S 2000 2000S 3000 3000S
UPS
Case
Net weight (kg) 19.3 10 17.8 10 30.8 16 27.8 16
Dimension (mm)
(W x H x D)
438X86.5x436 438X86.5x608
EBM
Case
Dimension (mm)
(W x H x D)
438X86.5x436
438X86.5x608
Net weight (kg) 23.5 39.3
30
7.2 Rear Panels
The UPS rear panel description table and pictures are shown as below:
1000VA &1500VA Standard & Super charger model rear panel
87651
2 431
NETWORK/TELEPHONEPROTECTION
INPUT 220-240 V~
INTERF ACE OPTION
EPO
USBRS232
OUTIN
LS2 OUT PUT
25KV~ 10A
LS1 OUT PUT
25KV~ 10A
No.
Function
(
1000VA &1500VA
)
1 AC Output 2 Modem/Network Surge Protection 3 SNMP Port 4 AC Input 5 RS232 / Dry-Contact Communication Port 6 USB Port 7 EPO 8 Earth Line Port
No.
Function(
2K/3KVA Standard &
Supper charger model)
1 AC Output 2 Modem/Network Surge Protection 3 SNMP Port 4 Fan 5 AC Input 6 RS232 / Dry-Contact Communication Port 7 USB Port 8 EPO 9 Earth Line Port
31
2000VA Standard model rear panel
2000VA Super charger model rear panel
3000VA Standard & Supper charger model rear panel
L
S
1
O
U
T
P
U
T
2
5
K
V
~
1
0
A
L
S
2
O
U
T
P
U
T
2
5
K
V
~
1
0
A
1
4
1
3
7
5
6
8 9
2
I
N
O
U
T
N
E
T
W
O
R
K
/
T
E
L
E
P
H
O
N
E
P
R
O
T
E
C
T
I
O
N
INTERFACE OPTION
EPO
USBRS232
I
N
P
U
T
2
2
0
-
2
4
0
V
~
L
S
1
O
U
T
P
U
T
2
5
K
V
~
1
0
A
L
S
2
O
U
T
P
U
T
2
5
K
V
~
1
0
A
1
4
1
3
7
5
6 8 9
2
I
N
O
U
T
N
E
T
W
O
R
K
/
T
E
L
E
P
H
O
N
E
P
R
O
T
E
C
T
I
O
N
INTERFACE OPTION
EPO
USBRS232
I
N
P
U
T
2
2
0
-
2
4
0
V
~
L
S
1
O
U
T
P
U
T
2
5
K
V
~
1
0
A
L
S
2
O
U
T
P
U
T
2
5
K
V
~
1
0
A
1
~
1 4
1
3
7
5
6
8 9
2
2
5
K
V
1
6
A
I
N
O
U
T
N
E
T
W
O
R
K
/
T
E
L
E
P
H
O
N
E
P
R
O
T
E
C
T
I
O
N
INTERFACE OPTION
EPO
USBRS232
I
N
P
U
T
2
2
0
-
2
4
0
V
~
32
The EBM rear panel description table and picture are shown as below:
36V &72V EBM rear panel
1
1
No.
Function(
36V &72V
EBM
)
1 Earth Line Port
33
8. Trouble Shooting
8.1 Audible Alarm Trouble Shooting
Indication
Cause
Solution
Sounding every 4 seconds
The UPS is on battery mode
Check input voltage
Sounding every Second and “bATL” on screen
The battery voltage is low
Save your work and turn off your equipment
Sounding every second and “OVLD” on screen
Output overload
Check load level indicator and remove some load
Continuously sounding and red display
The UPS fails Please contact your local dealer
8.2 General Trouble Shooting
Problem
Cause
Solution
The UPS can't be turned on when power switch is pressed
Internal fuse may be broken
Please contact your local dealer
UPS is on and no power to load
Output Jumpers is not connected correctly
Check output Jumpers
No power on output receptacle
Check if the LS1 and LS2 are set up from "001 to 000".
Backup time is short
Battery is empty
Re-charge the battery at least 24 hours
Battery aging Replace Battery
Continuously sounding
and display turn to red
The UPS fails Please contact your local dealer
Buttons does not work
The setting mode is not a right path
please see right configuring method
Button is Broken Please contact your local dealer
34
9. Software Installation
Winpower is UPS monitoring software, featuring user-friendly interface to monitor and control of your UPS. This software provides power protection for your computer system during a power failure. With this software, users can monitor their UPS status on their LAN. Furthermore, a UPS can provide security protection for more than one computer on the same LAN at the same time, shutting down system in security, saving application data and shutting down the UPS if power fails.
I
nstallation procedure:
1. Go to the website: http://www.ups-software-download.
com/index.htm
2. Select your operating system and follow the instructions on the website to download the software.
3. When downloading the required files from the internet, enter the serial No: 511C1-01220-0100-478DF2A to install the software.
When your computer restarts, the Winpower software wil
l appear as a green plug
icon located in the system tray, near the clock.
Loading...