1.0 bar
Standard setting
0.2 bar
90°
Initial settings
Installation and
Operation
Pneumatic Positioner F10
CCW Direct
CW Reverse
Accredited by the Dutch Council for Certification
DOC.6.41.EI 10.98
Page 2
F 10 Pneumatic Positioner
Where to Find Information
Page Product Description 1 Operating Principle 2 Installation, Rotary Actuators
- Mechanical 3
-Pneumatic, Double Acting 3
-Pneumatic, Single Acting 4
-Air Supply Requirement 4
Installation, Linear Actuators
-Mechanical installation 5
-Pneumatic installation 6
Calibration
-Initial Settings 7
-Cam Changes 7
-Zero Adjustment 8
-Range Adjustment 8
Trouble Shooting 9
General Specification:
Metric Imperial
Hysteresis : 0.6% Linearity : 1.0% Air Flow : 210 Nl/min (at 6 bar) : (7.4 SCFM at 87 psi) Air Consumption : 15 Nl/min (at 6 bar) : (0.6 SCFM at 87 psi) Min. volume actuator : 0.1 Nl : 6.1 in Temperature : -20° to +80° C : (-4° to +176°F) Enclosure : IP54 (option IP65) : NEMA 3 (option NEMA 4) Mounting : VDI/VDE 3845 or
IEC 534/6 Air Entry : G 1/4" : (1/4" NPT) Air Supply : 1.4 to 8.6 bar : (21 to 125 psi). Input Signal
- Standard : 0.2 to 1.0 bar : (3 to 15 psi).
- Adjustable : 0.2 to 0.6 bar : (3 to 9 psi).
: 0.6 to 1.0 bar : (9 to 15 psi).
3
Media : Non-lubricated instrument air, filtered at 25 micron.
: Dew point should be 10°C (18°F) below enviromental temperatur. : Air quality class 3-2-3 accord. to ISO 8573-1.
Page 3
Product Description
The F10 positioner provides the means for a pneu­matic actuator to be positioned to any point between full open and full closed position. This allows accu­rate setting of rotary and linear control valves as well as a wide range of dampers and similar de­vices. The actuator’s movement is controlled in proportion to a 0.2 to 1 bar (3-15 psi) incoming pressure signal.
The Posiflex F10 positioner provides:
-A single model covers both single acting and double acting actuators.
- External Zero Adjustment.
- High accuracy due to “high gain” amplification.
-Four Position Cam for Linear Actuators provides for linear, quick opening, equal per­centage and split range characteristics.
- Three Position Cam for Rotary Actuators provides for linear, quick opening and equal percentage characteristics. A special cam for rotary actuator provides for split range.
- Direct or Reverse Acting.
F 10 positioners are available for both rotary and linear applications and because of the standard­ized mounting interface (VDI/VDE 3845 or IEC 534/
6), installation is simple and trouble free. Mounting kits are available for most actuator types.
The purely Pneumatic mode of operation means that F10 positioners may be used in explosion hazardous areas without any additional protection being necessary.
A wide range of modular control options are avail­able: These cover the addition of gauges, indicat­ing switches, position transmitters, etc.
F10
Pneumatic POSITIONER
Open
Closed
1.
Page 4
Operating Principles
The Posiflex F10 Pneumatic Positioner is a high gain, motion balance instrument, suitable for use with a wide variety of single acting and double acting rotary and linear actuators.
Referring to the diagram below: The positioner is shown in a mid position with INSTRUMENT and SUPPLY air connected. The flapper and nozzle (5) maintains the instrument in it’s “balanced” state with just enough pilot air pressure being applied to the spool valve for it to hold the actuator in it’s “set” position.
When the actuator is required to move to a new “more open” position, the INSTRUMENT pressure signal is increased accordingly. This closes the air gap at the nozzle (5) causing an amplified pressure
1. Balance assembly.
2. Pneumatic valve block.
3. Actuator.
4. Mechanical feedback.
5. Flapper and nozzle.
6. Cam.
Output
increase at the spool valve end, this in turn dis­places the spool and allowing an increasing air pressure at the “open” side of the actuator and exhausting air from the “close” side. When the actuator moves position it rotates the cam (6) in a CCW (counter clockwise) direction and in doing so it progressively opens the air gap at the nozzle (5). On reaching the new set point the pilot pressure is reduced to the “balanced” state and again locks the actuator in new set position.
Similarly a decreasing INSTRUMENT pressure will cause a CW (clockwise) positioner movement.
The operation for single acting actuators is the same except that the unused pneumatic connection OUTPUT 2 is plugged off.
2
5
Supply
Close
3
1
Open
4
Instrument
6
2.
Page 5
Mechanical installation - Rotary actuators
The positioner is mounted on to the top surface of the pneumatic actuator using an appropriate mounting kit.
The positioner’s mounting configuration is to the VDE/ VDI 3845 standard, if the actuator is to the same standard, a standard NAMUR mounting kit can be used, otherwise a special mounting kit will have to be obtained.
Assuming the installation will use the standard NAMUR mounting kit, proceed as follows:
1. Fix the bracket to the top surface of the actuator using the 4 screws provided.
2. Check that the spring clip is securely in place on the bottom of the positioner shaft.
3. Locate the positioner in place on top of the bracket, making sure that the 4 mm. tongue locates properly into it’s slot in the actuator spindle and the centring screw is in position.
4. Fix the positioner to the bracket using the 4 screws provided.
Installation Rotary Actuators
Mechanical Installation
Pneumatic Connections - Double acting
This assumes a standard (direct acting) installation with an increasing signal to open the valve in a CCW (counter clockwise) direction.
Before connecting any air supply make sure that the air available is clean dry instrument air filtered to at least 25 microns - see page 4.
1. Connect an appropriate piece of air tubing between the port 1. on the positioner to the “A” port on the actuator. (The “A” port is the one that when air is applied to it, rotates the actuator in a counter clock­wise direction).
2. Connect an appropriate piece of air tubing between the port 2. on the positioner to the “B” port on the actuator. (The “B” port is the one that when air is applied to it, rotates the actuator in a clockwise direction).
3. Connect an air supply to the positioner port Marked “Supply”.
4. If the positioner is required to meet enclosure rating IP54, be sure that the "Exhaust" port is connected with elements which prevent the input of water and give no pressure rising inside the housing because of throttling of exhaust flow (no sintered filters, but a piece of tube or a special IP65 Exhaust plug with diaphragm
Supply
Instrument
Exhaust
1
A
2
B
Pneumatic connections
Double acting
5. Connect the instrument air to the port marked "INSTR".
Note: For a reverse acting assembly, both the air
connections and the cam plate must be reversed - see page 7.
3.
Page 6
Installation Rotary Actuators
Pneumatic Connections - Single acting
This assumes a standard installation, direct acting with an increasing signal to open the valve in a CCW (counterclockwise) direction.
Before connecting any air supply make sure that the air available is clean dry instrument air filtered to at least 25 microns - see below.
1. Connect an appropriate piece of air tubing between the port 1. on the positioner to the “A” port on the actuator. (The “A” port is the one that, when air is applied to it, rotates the actua­tor in a counter clockwise direction).
2. Connect an air supply to the positioner port marked “Supply”.
3. The unused positioner port 2, should be plugged using the pipe plug supplied with your positioner. Connect port "Exhaust" with elements, which guarantee IP54.
4. If the positioner is required to meet enclosure rating IP54, be sure that the "Exhaust" port is connected with elements which prevent the input of water and give no pressure rising inside the housing because of throttling of exhaust flow (no sintered filters, but a piece of tube or a special IP65 Exhaust plug with diaphragm.
5. Connect the instrument air to the port marked "INSTR".
Supply Exhaust
1
A
Instrument
2
Pneumatic Connections
Single acting
Note: For a reverse acting assembly, use the
same procedure but remember that a re­verse acting actuator must be used - see page 7.
Air Supply Requirements CAUTION: Pressure in excess of 8.6 bar (125 psi)
will cause damage to the Positioner. Positioner supply air must be clean, dry and oil free.
The air should be filtered to at least 25 microns (as defined in the Instrument Society of America standard ISA S7.3 specifications). The filter should be installed as close to the positioner as possible to ensure maximum efficiency.
4.
Page 7
Mechanical Installation - Linear Actuators
The mountings for linear positioners will vary dependent on the type of control valve.
The simplest assembly is where the control valve yoke is to the standard IEC 534-6 and has type “C” (Pillar) yoke design. A standard mounting kit is available for this and will provide a suitable mounting for most valves in this category.
Installation - Linear Actuators
7 6
3
Typical installation for a direct acting assembly. (Increas­ing signal opens the valve with a rising spindle).
1. Fix the bracket (1) to the positioner base, using the four bolts provided.
2. Move the valve spindle into a mid-stroke position.
3. Fix the lever (2) to the valve connection block (3) using the two M6 bolts. The carrier bolt (5) should be posi­tioned loosely in the lever (2).
4. Assemble the slider on the feed back lever (7). Use assembly "a" (below) for strokes 60 to 100 mm. or assembly "b" for strokes 10 to 40 mm.
5. Locate the positioner, together with the bracket (1) on the left-hand pillar using the "U"-bolt clamps (4). (Use the right-hand pillar for reversacting assemblies). pass the carrier bolt (5) through the feedback lever slot, taking care to keep the anti-backlash spring (6) in it's correct position.
2
4
1
5
Linear mounting
Slider installation for 100 mm. stroke
6. Slide the positioner up or down the pillar until the lever (2) and the feedback lever (7) are parallel. Fix in posi­tion.
7. Adjust the linkage to the correct stroke by moving the slider until the appropriate position on the feedback lever is indicated. Then tighten the carrier bolt (5).
8. Let the actuator make a full stroke and check that the linkage moves freely within the bracket.
9. Move the actuator to it's "zero" position. Turn the positioner shaft counterclockwise (CCW) to the end of stroke. Fasten the feedback lever to the positioner shaft.
5.
Installation mark for 60 and 100 mm. stroke
a) Lever for 60 to 100 mm. Stroke
Installation mark for 10 and 16 mm. stroke
Installation mark for 20 and 40 mm. stroke
Slider installation for 25 mm. stroke
b) Lever for 10 to 40 mm. Stroke
Page 8
Installation - Linear Actuators
Pneumatic Connections - Double acting
Assuming a standard installation, direct acting with an increasing signal to open the valve (rising spindle).
Before connecting any air supply make sure that the air available is clean dry instrument air filtered to at least 25 microns.
1. Connect an appropriate piece of air tubing between the port 1. on the positioner to the “A” port on the actuator. (The “A” port is the one that, when air is applied to it, opens the valve).
2. Connect an appropriate piece of air tubing between the port 2. on the positioner to the “B” port on the actuator. (The “B” port is the one that when air is applied to it, closes the valve).
3. Connect an air supply to the positioner port marked “S”.
4. If the positioner is required to meet enclosure rating IP54, be sure that the "Exhaust" port is connected with elements which prevent the input of water and give no pressure rising inside the housing because of throttling of exhaust flow (no sintered filters, but a piece of tube or a special IP65 Exhaust plug with diaphragm
5. Connect port "Instrument" with pneumatic input signal.
Double acting
Note: For a reverse acting assembly, both the air
connections and the cam must be reversed ­see page 7.
Pneumatic Connections - Single acting
Assuming a standard installation, with direct acting an increasing signal to open the valve (rising spindle).
Before connecting any air supply make sure that the air available is clean dry instrument air filtered to at least 25 microns.
1. Connect an appropriate piece of air tubing between the port 1. on the positioner to the “A” port on the actuator. (The “A” port is the one that when air is applied to it, opens the valve).
2. Connect an air supply to the positioner port marked “S”.
3. If the positioner is required to meet enclosure rating IP54, be sure that the "Exhaust" port is connected with elements which prevent the input of water and give no pressure rising inside the housing because of throttling of exhaust flow (no sintered filters, but a piece of tube or a special IP65 Exhaust plug with diaphragm
Single acting
4. Connect port "Instrument" with pneumatic input signal.
Note: For a reverse acting assembly, both the air
connections and the cam must be reversed ­see page 7.
6.
Page 9
Initial Settings
Cam Segment
Rotary actuator
Linear actuator
40° CCW
40° CW
lin
=%
QO
SR
Calibration - Initial Settings - Cam Changes
The factory settings provide the positioner with an initial range of settings that will allow the operation of position­ers on most applications.
Signal Input - 0.2 to 1.0. bar. (3-15 psi). Range - 0% to 100% Control Function - Linear. Action - Direct Acting.
(Opening on increasing Signal in CCW-direction).
The F10 positioner is provided with the following features for making changes to the initial settings:
Zero By the external zero adjustment screw. Range By the internal range adjustment ring. Range Spring The standard range spring is suitable for
normal operation and split ranging.
Cam Segment Six segments are provided for the rotary
positioner and eight segments for the linear positioner (see table).
Cam Changes
Remove the cover and indicator from the positioner exposing the Cam. The Cam is double sided: CCW for direct acting, CW for reverse acting.
If the actuator is fully clockwise and the actuator is to rotate CCW on instrument signal increase, the Cam should be on the “CCW” side and the start marking should be in line with the Cam Follower Bearing. If the actuator is fully counterclockwise and the actuator is to rotate CW on instrument signal increase, the Cam should be on the “CW” side and the start marking should be in line with the Cam Follower Bearing.
If the cam is not in the correct position, change as fol­lows:
1.0 bar
0.2 bar 0
Standard setting
CCW Direct
CW Reverse
Initial settings
90° CCW 90° CW
lin lin lin =% =% =% QO QO QO
* * SR
lin = linear =% = equal percentage QO = Quick Opening SR = Split Range * = Special cam split range
90°
2
1
1. Remove the cam nut (1).
2. Re-install the cam plate in the correct position, taking
3. Replace the cam nut and fix it.
4. Replace the indicator disk, taking care that it in the
care that the correct segment is adjacent to the cam follower (2).
correct position.
7.
Top view of cam
Rotary actuator
Cam 90°
Linear actuator
Cam 40° (49°)
Page 10
Calibration - Zero and Range
Before making any adjustments positioner should be properly mounted, the cam should be in the correct sector on the correct side as determined from the cam markings.
Zero Adjustment
The zero adjustment is carried out externally, this is located at the right hand side of the positioner casing and is accessed by means of a removable plug.
1. Remove the access plug (1).
2. Adjust the instrument signal to its minimum value (0.2 bar for a 0.2-1.0 bar range), (3 psi for a 3-15 psi range).
3. Rotate the Zero adjusting screw (2) until the actuator just begins to move. Turning the adjust­ing nut clockwise raises the start value.
4. After adjustment, replace the access plug (1).
Range Adjustment
Remove the cover from the positioner exposing the knurled range adjuster ring, this is located at the righthand side of the assembly.
The factory set range is so that a 0.2 to 1.0 bar (3­15 psi) instrument pressure produces a full stroke movement. This may be changed by resetting the full stroke position (max. opening) at the 1.0 bar (max. instrument) pressure. To adjust the range carry out the following:
1. Increase the instrument signal to its maximum value (1.0 bar for a 0.2 to 1.0 bar range), (15 psi for a 3-15 psi range).
2. If the actuator does not reach its final position, rotate the knurled adjusting ring (3) in CCW­direction until the full stroke position is reached.
3. Turning the range screw cw reduces the range; ccw increases the range.
4. After range adjustment, reset the zero position and adjust it if necessary.
3
2
1
8.
Page 11
Troubleshooting
If it is suspected that the positioner is not operat­ing correctly, check the following :
1. Is the Cam in the proper orientation for your application ? (See page 5).
2 Is the positioner properly mounted ? (See page
3).
3. Is the coupling or NAMUR shaft in proper alignment with the Positioner Cam shaft and actuator ?
4. Is the positioner piped correctly ? (See page 3 and 4).
5. Make sure supply pressure exceeds minimum pressure required to move the actuator.
6. Is there instrument and output pressure at the Positioner ? (If the Positioner is equipped with a Gauge Block, check the instrument and output pressure readings. If the positioner is not equipped with a Gauge Block, connect gauges to the instrument and output ports and note readings.)
7. Is the actuator working properly ? (Disconnect the supply pressure from the Positioner and connect the supply pressure to the actuator. Does the actuator move full stroke ?)
Maintenance
If additional help is needed, contact your local El­o-matic office or representative, (see back page).
9.
Page 12
INTERNATIONAL BENELUX UNITED KINGDOM
EL-O- MATI C B.V. EL-O- MATI C Benelux EL-O- MATIC Ltd. P. O . Bo x 223 P. O . Bo x 223 16/1 7 Beedi ng Cl ose 7550 AE Hengelo (O) 7550 AE Hengelo (O) Southern Cross Trading Estate Asvel dweg 19 Asvel dweg 11 Bognor Regis 7556 BR Hengelo (O) 7556 BT Hengelo (O) West Sussex, PO 22 9TS Holland Holland Tel. +44 1243 830 3 63 Tel. +31 74 256 10 10 Tel. +31 74 256 10 20 Fax. +44 1243 830 843 Fax. +31 74 291 09 38 Fax. +31 74 243 86 90
FRANCE GERMANY U.S.A.
EL-O- MATI C France EL -O- MATI C GmbH. EL-O- MATIC U.S.A. Inc. Z.A. Créapole 1 Postfach 460234 . 47856 Willich 1 35 Engl ish Street 32 R ue de Tour nenfi ls Si eme nsr ing 112 . 4 7877 W i ll ich Hackensack NJ 0 7601 91540 Mennecy Tel. +49 2154 499660 Tel. +1 201 489 5550 Tel. +33 1 69 900 734 Fax. +49 2154 427669 Fax. +1 201 489 9171 Fax. +3 3 1 69 900 709
VENEZUELA INDIA SINGAPORE
EL-O- MATI C INTERNAT IO NAL EL-O- MATIC I ndia Pv t Ltd. EL-O -MATIC Valve Actuators Av. Princ ipal Los Ruices 296 /A/1/5, St. Patrick ’s T own Fa r East Pte L td. Edif. stemo piso 1 Ofc. 1A Near Railway Crossing 28 Third Lok Yang Road Caracas Had apsar In dustrial Estate Si ngapor e 628016 Venezuela Pune 411 013 Tel. +65 26 24 515 Tel. +58 2 237 77 51 Tel. +91 212 672916 Fax. +65 2680028 / 770 80 80 Fax. +5 8 2 238 9023 Fax. +9 1 212 674465
SOUTH AFRICA AUSTRALIA / NEW ZEALAND
EL-O-MATI C (Pty) Ltd. EL-O-MATIC Austral-Asia Teknipark, 62 Lower Germiston Road 329 Brighton Road, Brighton 5048 Heriotd ale, Jo hannesburg P. O . Bo x 12 P.O. Box 40348 Glenelg 5045 Cleveland 2022 South Australia Tel. +27 11 626 2880/1/2 Tel. +61 8 377 2744 Fax. +2 7 11 626 2905 Fax. +6 1 8 377 2576
Loading...