F60 Feeder Protection System
Table of contents
1 INTRODUCTION1.1Safety symbols and definitions.....................................................................1-1
1.1.1General cautions and warnings ....................................................................................1-1
1.2For further assistance .................................................................................... 1-2
B.1RADIUS server configuration .........................................................................B-1
CONFIGURATION
C COMMAND LINE
C.1Command line interface .................................................................................C-1
INTERFACE
D MISCELLANEOUSD.1 Warranty ...........................................................................................................D-1
D.2 Revision history ...............................................................................................D-1
ABBREVIATIONS
INDEX
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUALix
TABLE OF CONTENTS
xF60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
F60 Feeder Protection System
Chapter 1: Introduction
Introduction
This chapter outlines safety and technical support information.
1.1 Safety symbols and definitions
Before attempting to install or use the device, review all safety indicators in this document to help prevent injury,
equipment damage, or downtime.
The following safety and equipment symbols are used in this document.
Indicates a hazardous situation which, if not avoided, will result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in minor or moderate injury.
Indicates practices not related to personal injury.
1.1.1 General cautions and warnings
The following general safety precautions and warnings apply.
Ensure that all connections to the product are correct so as to avoid accidental risk of shock
and/or fire, for example such as can arise from high voltage connected to low voltage terminals.
Follow the requirements of this manual, including adequate wiring size and type, terminal torque settings, voltage,
current magnitudes applied, and adequate isolation/clearance in external wiring from high to low voltage circuits.
Use the device only for its intended purpose and application.
Ensure that all ground paths are uncompromised for safety purposes during device operation and service.
Ensure that the control power applied to the device, the AC current, and voltage input match the ratings specified on
the relay nameplate. Do not apply current or voltage in excess of the specified limits.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL1-1
1
FOR FURTHER ASSISTANCECHAPTER 1: INTRODUCTION
Only qualified personnel are to operate the device. Such personnel must be thoroughly familiar with all safety
cautions and warnings in this manual and with applicable country, regional, utility, and plant safety regulations.
Hazardous voltages can exist in the power supply and at the device connection to current transformers, voltage
transformers, control, and test circuit terminals. Make sure all sources of such voltages are isolated prior to
attempting work on the device.
Hazardous voltages can exist when opening the secondary circuits of live current transformers. Make sure that
current transformer secondary circuits are shorted out before making or removing any connection to the current
transformer (CT) input terminals of the device.
For tests with secondary test equipment, ensure that no other sources of voltages or currents are connected to such
equipment and that trip and close commands to the circuit breakers or other switching apparatus are isolated,
unless this is required by the test procedure and is specified by appropriate utility/plant procedure.
When the device is used to control primary equipment, such as circuit breakers, isolators, and other switching
apparatus, all control circuits from the device to the primary equipment must be isolated while personnel are working
on or around this primary equipment to prevent any inadvertent command from this device.
Use an external disconnect to isolate the mains voltage supply.
Personal safety can be affected if the product is physically modified by the end user. Modifications to the product
outside of recommended wiring configuration, hardware, or programming boundaries is not recommended end-use
practice. Product disassembly and repairs are not permitted. All service needs to be conducted by the factory.
LED transmitters are classified as IEC 60825-1 Accessible Emission Limit (AEL) Class 1M. Class 1M
devices are considered safe to the unaided eye. Do not view directly with optical instruments.
This product is rated to Class A emissions levels and is to be used in Utility, Substation Industrial
environments. Not to be used near electronic devices rated for Class B levels.
1.2 For further assistance
For product support, contact the information and call center as follows:
GE Grid Solutions
650 Markland Street
Markham, Ontario
Canada L6C 0M1
Worldwide telephone: +1 905 927 7070
Europe/Middle East/Africa telephone: +34 94 485 88 54
North America toll-free: 1 800 547 8629
Fax: +1 905 927 5098
Worldwide e-mail: multilin.tech@ge.com
Europe e-mail: multilin.tech.euro@ge.com
Website: http://www.gegridsolutions.com/multilin
When contacting GE by e-mail, optionally include a device information file, which is generated in the EnerVista software by
clicking the Service Report button.
1-2F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 1: INTRODUCTIONFOR FURTHER ASSISTANCE
Figure 1-1: Generate service report
1
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL1-3
1
FOR FURTHER ASSISTANCECHAPTER 1: INTRODUCTION
1-4F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
F60 Feeder Protection System
Chapter 2: Product description
Product description
This chapter outlines the product, order codes, and specifications.
2.1 Product description
2.1.1 Overview
The F60 Feeder Protection System is part of the Universal Relay (UR) series of products. It is a microprocessor-based relay
for feeder protection.
Overvoltage and undervoltage protection, overfrequency and underfrequency protection, breaker failure protection,
directional current supervision, fault diagnostics, remote terminal unit (RTU), and programmable logic functions are
provided. This relay also provides phase, neutral, ground and negative sequence, instantaneous and time overcurrent
protection. The time overcurrent function provides multiple curve shapes or FlexCurves™ for optimum co-ordination.
Automatic reclosing, synchrocheck, and line fault locator features are also provided. When equipped with a type 8Z current
transformer/voltage transformer (CT/VT) module, an element for detecting high impedance faults is provided.
Voltage, current, and power metering are built in as standard features. Current parameters are available as total
waveform root mean square (RMS) magnitude, or as fundamental frequency only RMS magnitude and angle (phasor).
Diagnostic features include an event recorder that stores 1024 time-tagged events. The internal clock used for timetagging can be synchronized with an IRIG-B signal, using the Simple Network Time Protocol (SNTP) over the Ethernet port,
or using the Precision Time Protocol (PTP). This precise time stamping allows the sequence of events to be determined
throughout the system. Events can also be programmed (via FlexLogic™ equations) to trigger oscillography data capture
that can be set to record the measured parameters before and after the event for viewing on a computer. These tools
significantly reduce troubleshooting time and simplify report generation in the event of a system fault.
Several options are available for communication. A faceplate RS232 port can be used to connect to a computer to
program settings and monitor actual values. The rear RS485 port allows independent access by operating and engineering
staff. It can be connected to system computers with baud rates up to 115.2 kbps. All serial ports use the Modbus RTU
protocol. The IEC 60870-5-103 protocol is supported on the RS485 interface. IEC 60870-5-103, DNP, and Modbus cannot be
enabled simultaneously on this interface. Also only one of the DNP, IEC 60870-5-103, and IEC 60870-5-104 protocols can
be enabled at any time on the relay. When the IEC 60870-5-103 protocol is chosen, the RS485 port has a fixed even parity
and the baud rate can be either 9.6 kbps or 19.2 kbps. The 100Base-FX or 100Base-TX Ethernet interface provides fast,
reliable communications in noisy environments. The Ethernet port supports IEC 61850, IEC 61850-90-5, Modbus/TCP, TFTP,
and PTP (according to IEEE Std. 1588-2008 or IEC 61588), and it allows access to the relay via any standard web browser
(F60 web pages). The IEC 60870-5-104 protocol is supported on the Ethernet port. The Ethernet port also supports the
Parallel Redundancy Protocol (PRP) of IEC 62439-3 (clause 4, 2012) when purchased as an option.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL2-1
PRODUCT DESCRIPTIONCHAPTER 2: PRODUCT DESCRIPTION
Secure Routable GOOSE (R-GOOSE) is supported with software options.
Settings and actual values can be accessed from the front panel or EnerVista software.
The F60 uses flash memory technology that allows field upgrading as new features are added. Firmware and software are
upgradable.
The following single-line diagram illustrates the relay functionality using American National Standards Institute (ANSI)
device numbers.
2
Table 2-1: ANSI device numbers and functions supported
Device numberFunctionDevice number Function
25Synchrocheck51_2Negative-sequence time overcurrent
27PPhase undervoltage52AC circuit breaker
27XAuxiliary undervoltage59NNeutral overvoltage
32Sensitive directional power59PPhase overvoltage
32NWattmetric zero-sequence directional59XAuxiliary overvoltage
49Thermal overload protection59_2Negative-sequence overvoltage
50BF/50NBFBreaker failure67NNeutral directional overcurrent
50DDDisturbance detector67PPhase directional overcurrent
50GGround instantaneous overcurrent67_2Negative-sequence directional overcurrent
50NNeutral instantaneous overcurrent79Automatic recloser
50PPhase instantaneous overcurrent81OOverfrequency
50_2Negative-sequence instantaneous overcurrent81RRate of change frequency
51GGround time overcurrent81UUnderfrequency
51NNeutral time overcurrent87RGFRestricted ground fault
51PPhase time overcurrent
Figure 2-1: Single-line diagram
2-2F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTIONSECURITY
Table 2-2: Other device functions
FunctionFunctionFunction
Breaker arcing current (I
Breaker controlEvent recorderSetting groups (6)
Breaker flashoverFault detector and fault reportSynchrophasor (PMU)
Breaker restrikeFault locatorThermal overload protection
Broken conductor detectionFlexElements™ (8)Time synchronization over IRIG-B or IEEE
Cold load pickupFlexLogic equationsTime synchronization over SNTP
Contact inputs (up to 96)High impedance fault detection (Hi-Z)Transducer inputs and outputs
Contact outputs (up to 64)IEC 60870-5-103 communicationsUser-definable displays
Control pushbuttonsIEC 61850 communicationsUser-programmable LEDs
CT failure detectorIEC 62351-9 data and communications
Digital counters (8)Modbus user mapVT fuse failure
Digital elements (48)Non-volatile latches
Direct inputs and outputs (32)Non-volatile selector switch
Disconnect switchesOscillography
2
t)Ethernet Global DataPilot schemes
1588
security
energy, frequency, harmonics, THD
User-programmable pushbuttons
Virtual outputs (96)
2
2.2 Security
The following security features are available:
•Password security — Basic security present by default
•EnerVista security — Role-based access to various EnerVista software screens and configuration elements. The
feature is present by default in the EnerVista software.
•CyberSentry security — Advanced security available using a software option. When purchased, the option is
automatically enabled, and the default Password security and EnerVista security are disabled.
2.2.0.1 EnerVista security
The EnerVista security management system is a role-based access control (RBAC) system that allows an administrator to
manage the privileges of multiple users. This allows for access control of UR devices by multiple personnel within a
substation and conforms to the principles of RBAC as defined in ANSI INCITS 359-2004. The EnerVista security
management system is disabled by default to allow the administrator direct access to the EnerVista software after
installation. It is recommended that security be enabled before placing the device in service.
Basic password or enhanced CyberSentry security applies, depending on purchase.
2.2.0.2 Password security
Password security is a basic security feature present by default.
Two levels of password security are provided: command and setting. Use of a password for each level controls whether
users can enter commands and/or change settings.
The F60 supports password entry from a local or remote connection. Local access is defined as any access to settings or
commands via the faceplate interface. This includes both keypad entry and the through the faceplate RS232 port. Remote
access is defined as any access to settings or commands via any rear communications port. This includes both Ethernet
and RS485 connections. Any changes to the local or remote passwords enables this functionality.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL2-3
2
SECURITYCHAPTER 2: PRODUCT DESCRIPTION
When entering a settings or command password via EnerVista or any serial interface, the user must enter the
corresponding connection password. If the connection is to the back of the F60, the remote password must be used. If the
connection is to the RS232 port of the faceplate, the local password applies.
Password access events are logged in the Event Recorder.
2.2.0.3 CyberSentry security
CyberSentry embedded security is available using a software option (Level 1) that provide advanced security services.
When the option is purchased, the basic password security is disabled automatically.
CyberSentry provides security through the following features:
•An Authentication, Authorization, Accounting (AAA) Remote Authentication Dial-In User Service (RADIUS) client that is
centrally managed, enables user attribution, provides accounting of all user activities, and uses secure standardsbased strong cryptography for authentication and credential protection
•A Role-Based Access Control (RBAC) system that provides a permission model that allows access to UR device
operations and configurations based on specific roles and individual user accounts configured on the AAA server (that
is, Administrator, Supervisor, Engineer, Operator, Observer roles)
•Security event reporting through the Syslog protocol for supporting Security Information Event Management (SIEM)
systems for centralized cybersecurity monitoring
•Strong encryption of all access and configuration network messages between the EnerVista software and UR devices
using the Secure Shell (SSH) protocol, the Advanced Encryption Standard (AES), and 128-bit keys in Galois Counter
Mode (GCM) as specified in the U.S. National Security Agency Suite B extension for SSH and approved by the National
Institute of Standards and Technology (NIST) FIPS-140-2 standards for cryptographic systems
CyberSentry user roles
CyberSentry user roles (Administrator, Engineer, Operator, Supervisor, Observer) limit the levels of access to various UR
device functions. This means that the EnerVista software allows for access to functionality based on the user’s logged in
role.
Example: Administrative functions can be segmented away from common operator functions, or engineering type access,
all of which are defined by separate roles (see figure) so that access of UR devices by multiple personnel within a
substation is allowed.
Figure 2-2: CyberSentry user roles
The table lists user roles and their corresponding capabilities.
Table 2-3: Permissions by user role for CyberSentry
|--------------- Display PropertiesRWRWRRR
|--------------- Clear Relay Records
(settings)
|--------------- CommunicationsRWRWRRR
|--------------- Modbus User MapRWRWRRR
|--------------- Real Time ClockRWRWRRR
|--------------- OscillographyRWRWRRR
|--------------- Data LoggerRWRWRRR
|--------------- DemandRWRWRRR
|--------------- User-Programmable
LEDs
|--------------- User-Programmable
Self Tests
|--------------- Control Pushbuttons RWRWRRR
|--------------- User-Programmable
Pushbuttons
|--------------- Flex state
Parameters
|--------------- User-Definable
Displays
|--------------- Direct I/ORWRWRRR
|--------------- TeleprotectionRWRWRRR
|--------------- InstallationRWRWRRR
|---------- System SetupRWRWRRR
|---------- FlexLogicRWRWRRR
|---------- Grouped ElementsRWRWRRR
|---------- Control ElementsRWRWRRR
|---------- Inputs / OutputsRWRWRRR
|---------- Protection SummaryNANANANANA
CommandsRWRWRWRR
|---------- Virtual InputsRWRWRWRR
|---------- Clear RecordsRWRWRWRR
|---------- Set Date and TimeRWRWRWRR
User DisplaysRRRRR
TargetsRRRRR
Actual ValuesRRRRR
|---------- Front panel labels designerRRRRR
|---------- StatusRRRRR
|---------- MeteringRRRRR
|---------- Transducer I/ORRRRR
|---------- RecordsRRRRR
|---------- Product InfoRRRRR
MaintenanceRWRWRRR
|---------- Modbus AnalyzerNANANANANA
|---------- Change front panelRWRWRWRR
|---------- Update firmwareYesNoNoNoNo
|---------- Retrieve fileYesNoNoNoNo
Table Notes:
RW = read and write access
R = read access
Supervisor = RW (default), Administrator = R (default), Administrator = RW (only if Supervisor role is disabled)
NA = the permission is not enforced by CyberSentry security
CyberSentry user authentication
The following types of authentication are supported by CyberSentry to access the UR device:
•Device Authentication (local UR device authenticates)
•Server Authentication (RADIUS server authenticates)
The EnerVista software allows access to functionality that is determined by the user role, which comes either from the local
UR device or the RADIUS server.
The EnerVista software has a device authentication option on the login screen for accessing the UR device. When the
"Device" button is selected, the UR uses its local authentication database and not the RADIUS server to authenticate the
user. In this case, it uses its built-in roles (Administrator, Engineer, Supervisor, Observer, Operator, or Administrator and
Supervisor when Device Authentication is disabled) as login names and the associated passwords are stored on the UR
device. As such, when using the local accounts, access is not user-attributable.
In cases where user-attributable access is required especially to facilitate auditable processes for compliance reasons, use
RADIUS authentication only.
When the "Server" Authentication Type option is selected, the UR uses the RADIUS server and not its local authentication
database to authenticate the user.
No password or security information is displayed in plain text by the EnerVista software or UR device, nor is such
information ever transmitted without cryptographic protection.
CyberSentry server authentication
The UR has been designed to direct automatically the authentication requests based on user names. In this respect, local
account names on the UR are considered as reserved and not used on a RADIUS server.
2-6F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTIONORDER CODES
The UR detects automatically whether an authentication request is to be handled remotely or locally. As there are five local
accounts possible on the UR, if the user ID credential does not match one of the five local accounts, the UR forwards
automatically the request to a RADIUS server when one is provided.
If a RADIUS server is provided, but is unreachable over the network, server authentication requests are denied. In this
situation, use local UR accounts to gain access to the UR system.
2.3 Order codes
The order code is on the product label and indicates the product options applicable.
The F60 is available as a 19-inch rack horizontal mount or reduced-size (¾) vertical unit. It consists of the following
modules: power supply, CPU, CT/VT, contact input and output, transducer input and output, and inter-relay
communications. Module options are specified at the time of ordering.
The order codes shown here are subject to change without notice. See the web page for the product for the latest options.
The order code depends on the mounting option (horizontal or vertical) and the type of CT/VT modules (enhanced
diagnostic CT/VT modules or HardFiber
HardFiber Bricks.
The R-GOOSE protocol described in IEC 61850-8-1 is available through the IEC 61850 software option. If R-GOOSE
security is required, the CyberSentry software option also must be purchased.
2.3.1 Order codes with enhanced CT/VT modules
Table 2-4: F60 order codes for horizontal units
BASE UNITF60|||||||||| |Base Unit
CPUT || | |||||||RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE00| | |||||||No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
U || | |||||||RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V || | |||||||RS485 and Three 10/100Base-TX (SFP with RJ45)
01| | |||||||Ethernet Global Data (EGD)
03| | |||||||IEC 61850
04| | |||||||Ethernet Global Data (EGD) and IEC 61850
06| | |||||||Phasor measurement unit (PMU)
07| | |||||||Phasor measurement unit (PMU) and IEC 61850
A0| | |||||||CyberSentry Lvl 1
A1| | |||||||CyberSentry Lvl 1 and Ethernet Global Data (EGD)
A3| | |||||||CyberSentry Lvl 1 and IEC 61850
A4| | |||||||CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
A6| | |||||||CyberSentry Lvl 1 and phasor measurement unit (PMU)
A7| | |||||||CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU)
B0| | |||||||IEEE 1588
B1| | |||||||IEEE 1588 and Ethernet Global Data (EGD)
B3| | |||||||IEEE 1588 and IEC 61850
B4| | |||||||IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD)
B6| | |||||||IEEE 1588 and phasor measurement unit (PMU)
B7| | |||||||IEEE 1588 and IEC 61850 and phasor measurement unit (PMU)
C0| | |||||||Parallel Redundancy Protocol (PRP)
C1| | |||||||PRP and Ethernet Global Data
C3| | |||||||PRP and IEC 61850
C4| | |||||||PRP, Ethernet Global Data, and IEC 61850
C6| | |||||||PRP and PMU
C7| | |||||||PRP, IEC 61850, and PMU
D0| | |||||||IEEE 1588 and CyberSentry Lvl 1
D1| | |||||||IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD)
D3| | |||||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850
D4| | |||||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
D6| | |||||||IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU)
D7| | |||||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0| | |||||||IEEE 1588 and PRP
E1| | |||||||IEEE 1588, PRP, and Ethernet Global Dada
E3| | |||||||IEEE 1588, PRP, and IEC 61850
E4| | |||||||IEEE 1588, PRP, Ethernet Global Data, and IEC 61850
E6| | |||||||IEEE 1588, PRP, and PMU
E7| | |||||||IEEE 1588, PRP, IEC 61850, and PMU
F0| | |||||||PRP and CyberSentry Lvl1
F1| | |||||||PRP, CyberSentry Lvl1, and Ethernet Global Data
F3| | |||||||PRP, CyberSentry Lvl 1, and IEC 61850
F4| | |||||||PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850
F6| | |||||||PRP, CyberSentry Lvl 1, and PMU
F7| | |||||||PRP, CyberSentry Lvl 1, IEC 61850, and PMU
G0| | |||||||IEEE 1588, PRP, and CyberSentry Lvl 1
G1| | |||||||IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data
G3| | |||||||IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850
TM
process bus module). The process bus module provides an interface to
(SFP with RJ45)
(PMU)
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL2-7
ORDER CODESCHAPTER 2: PRODUCT DESCRIPTION
2
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
H | |||||||Horizontal (19” rack) - Standard
A | |||||||Horizontal (19” rack) - With harsh environmental coating
D|||||| |French display
R|||||| |Russian display
A |||||||Chinese display
P |||||||English d isplay with 4 small and 12 large programmable pushbuttons
G |||||||French display with 4 small and 12 large programmable pushbuttons
S |||||||Russian display with 4 small and 12 large programmable pushbuttons
B |||||||Chinese display with 4 small and 12 large programmable pushbuttons
K |||||||Enhanced front panel with English display
M |||||||Enhanced front panel with French display
Q |||||||Enhanced front panel with Russian display
U |||||||Enhanced front panel with Chinese display
L |||||||Enhanced front panel with English display and user-programmable pushbuttons
N |||||||Enhanced front panel with French display and user-programmable pushbuttons
T |||||||Enhanced front panel with Russian display and user-programmable pushbuttons
V |||||||Enhanced front panel with Chinese display and user-programmable pushbuttons
W |||||||Enhanced front panel with Turkish display
Y |||||||Enhanced front panel with Turkish display and user-programmable pushbuttons
I |||||||Enhanced front panel with German display
J |||||||Enhanced front panel with German display and user-programmable pushbuttons
61850-90-5
IEC 61850
61850-90-5
2-8F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTIONORDER CODES
POWER SUPPLY
(redundant supply must
be same type as main supply)
ENHANCED DIAGNOSTICS CT/VT DSP
(8L, 8M, 8N, 8R require DSP to be
enhanced diagnostic)
CONTACT INPUTS/OUTPUTSXXXXXXXXXX No Module
TRANSDUCER
INPUTS/OUTPUTS
(select a maximum of 3 per unit)
INTER-RELAY
COMMUNICATIONS
(select a maximum of 1 per unit)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
H||||||125 / 250 V AC/DC power supply
H|||||SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply
L||||||24 to 48 V (DC only) power supply
L|||||SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
||XX|XX|No DSP module (slots M and U only)
8L|8L|||Standard 4CT/4VT with enhanced diagnostics
8M|8M|||Sensitive Ground 4CT/4VT with enhanced diagnostics
8N|8N|||Standard 8CT with enhanced diagnostics
8R|8R|||Sensitive Ground 8CT with enhanced diagnostics
||8Z *|||Hi-Z 4CT (required for high-impedance fault detection element)
4A4A4A4A4A 4 Solid-State (no monitoring) MOSFET outputs
4B4B4B4B4B 4 Solid-State (voltage with optional current) MOSFET outputs
4C4C4C4C4C 4 Solid-State (current with optional voltage) MOSFET outputs
4D4D4D4D4D 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case)
4L4L4L4L4L 14 Form-A (no monitoring) Latching outputs
6767676767 8 Form-A (no monitoring) outputs
6A6A6A6A6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs
6B6B6B6B6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs
6C6C6C6C6C 8 Form-C outputs
6D6D6D6D6D 16 Contact inputs
6E6E6E6E6E 4 Form-C outputs, 8 contact inputs
6F6F6F6F6F 8 Fast Form-C outputs
6G6G6G6G6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs
6H6H6H6H6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs
6K6K6K6K6K 4 Form-C and 4 Fast Form-C outputs
6L6L6L6L6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs
6M6M6M6M6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs
6N6N6N6N6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs
6P6P6P6P6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs
6R6R6R6R6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs
6S6S6S6S6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs
6T6T6T6T6T 4 Form-A (no monitoring) outputs, 8 contact inputs
6U6U6U6U6U 6 Form-A (no monitoring) outputs, 4 contact inputs
6V6V6V6V6V 2 Form-A outputs, 1 Form-C output, 1 Form-A latching output , 8 contact inputs
5A5A5A5A5A 4 DCmA inputs, 4 DCmA outputs
5C5C5C5C5C 8 RTD inputs
5D5D5D5D5D 4 RTD inputs, 4 DCmA outputs
5E5E5E5E5E 4 RTD inputs, 4 DCmA inputs
5F5F5F5F5F 8 DCmA inputs
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL2-9
ORDER CODESCHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-5: F60 order codes for reduced-size vertical units
BASE UNITF60| || | |||||Base Unit
CPUT || | |||||RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE00| | |||||No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U || | |||||RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V || | |||||RS485 and Three 10/100Base-TX (SFP with RJ45)
01| | |||||Ethernet Global Data (EGD)
03| | |||||IEC 61850
04| | |||||Ethernet Global Data (EGD) and IEC 61850
06| | |||||Phasor measurement unit (PMU)
07| | |||||Phasor measurement unit (PMU) and IEC 61850
A0| | |||||CyberSentry Lvl 1
A1| | |||||CyberSentry Lvl 1 and Ethernet Global Data (EGD)
A3| | |||||CyberSentry Lvl 1 and IEC 61850
A4| | |||||CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
A6| | |||||CyberSentry Lvl 1 and phasor measurement unit (PMU)
A7| | |||||CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU)
B0| | |||||IEEE 1588
B1| | |||||IEEE 1588 and Ethernet Global Data (EGD)
B3| | |||||IEEE 1588 and IEC 61850
B4| | |||||IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD)
B6| | |||||IEEE 1588 and phasor measurement unit (PMU)
B7| | |||||IEEE 1588 and IEC 61850 and phasor measurement unit (PMU)
C0| | |||||Parallel Redundancy Protocol (PRP)
C1| | |||||PRP and Ethernet Global Data
C3| | |||||PRP and IEC 61850
C4| | |||||PRP, Ethernet Global Data, and IEC 61850
C6| | |||||PRP and PMU
C7| | |||||PRP, IEC 61850, and PMU
D0| | |||||IEEE 1588 and CyberSentry Lvl 1
D1| | |||||IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD)
D3| | |||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850
D4| | |||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
D6| | |||||IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU)
D7| | |||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
POWER
SUPPLY
ENHANCED DIAGNOSTICS CT/VT DSP
(8L, 8M, 8N, 8R require DSP to be
enhanced diagnostic)
CONTACT INPUTS/OUTPUTSXXXXXX No Module
TRANSDUCER
INPUTS/OUTPUTS
(select a maximum of 3 per unit)
INTER-RELAY
COMMUNICATIONS
(select a maximum of 1 per unit)
For the last module, slot P is used for digital and transducer
input/output modules; slot R is used for inter-relay
communications modules.
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
V | |||||Vertical (3/4 rack) - Standard
B | |||||Vertical (3/4 rack) - With harsh environmental coating
K |||||Enhanced front panel with English display
M |||||Enhanced front panel with French display
Q |||||Enhanced front panel with Russian display
U |||||Enhanced front panel with Chinese display
L |||||Enhanced front panel with English display and user-programmable pushbuttons
N |||||Enhanced front panel with French display and user-programmable pushbuttons
T |||||Enhanced front panel with Russian display and user-programmable pushbuttons
V |||||Enhanced front panel with Chinese display and user-programmable pushbutt ons
W |||||Enhanced front panel with Turkish display
Y |||||Enhanced front panel with Turkish d isplay and user-programmable pushbuttons
I |||||Enhanced front panel with German display
J |||||Enhan ced front panel with German display and user-programmable pushbuttons
H||||125 / 250 V AC/DC power supply
L||||24 to 48 V (DC only) power supply
XX|XX|No DSP module (slots M and U only)
8L|8L|Standard 4CT/4VT with enhanced diagnostics
8M|8M|Sensitive Ground 4CT/4VT with enhanced diagnostics
8N|8N|Standard 8CT with enhanced diagnostics
8R|8R|Sensitive Ground 8CT with enhanced diagnostics
||8Z *|Hi-Z 4CT (required for high-impedance fault detection element)
4A4A4A 4 Solid-State (no monitoring) MOSFET outputs
4B4B4B 4 Solid-State (voltage with optional current) MOSFET outputs
4C4C4C 4 Solid-State (current with optional voltage) MOSFET outputs
4D4D4D 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case)
4L4L4L 14 Form-A (no monitoring) Latching outputs
676767 8 Form-A (no monitoring) outputs
6A6A6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs
6B6B6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs
6C6C6C 8 Form-C outputs
6D6D6D 16 Contact inputs
6E6E6E 4 Form-C outputs, 8 contact inputs
6F6F6F 8 Fast Form-C outputs
6G6G6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs
6H6H6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs
6K6K6K 4 Form-C and 4 Fast Form-C outputs
6L6L6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs
6M6M6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs
6N6N6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs
6P6P6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs
6R6R6R 2 Form-A (no monit oring) and 2 Form-C outputs, 8 contact inputs
6S6S6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs
6T6T6T 4 Form-A (no monitoring) outputs, 8 contact inputs
6U6U6U 6 Form-A (no monitoring) outputs, 4 contact inputs
6V6V6V 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL2-11
2
ORDER CODESCHAPTER 2: PRODUCT DESCRIPTION
2.3.2 Order codes with process bus modules
Table 2-6: F60 order codes for horizontal units with process bus
BASE UNITF60| || | |||||||Base Unit
CPUT || | |||||||RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE00| | |||||||No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
U || | |||||||RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V || | |||||||RS485 and Three 10/100Base-TX (SFP with RJ45)
01| | |||||||Ethernet Global Data (EGD)
03| | |||||||IEC 61850
04| | |||||||Ethernet Global Data (EGD) and IEC 61850
06| | |||||||Phasor measurement unit (PMU)
07| | |||||||Phasor measurement unit (PMU) and IEC 61850
A0| | |||||||CyberSentry Lvl 1
A1| | |||||||CyberSentry Lvl 1 and Ethernet Global Data (EGD)
A3| | |||||||CyberSentry Lvl 1 and IEC 61850
A4| | |||||||CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
A6| | |||||||CyberSentry Lvl 1 and phasor measurment unit (PMU)
A7| | |||||||CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU)
B0| | |||||||IEEE 1588
B1| | |||||||IEEE 1588 and Ethernet Global Data (EGD)
B3| | |||||||IEEE 1588 and IEC 61850
B4| | |||||||IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD)
B6| | |||||||IEEE 1588 and phasor measurement unit (PMU)
B7| | |||||||IEEE 1588 and IEC 61850 and phasor measurement unit (PMU)
C0| | |||||||Parallel Redundancy Protocol (PRP)
C1| | |||||||PRP and Ethernet Global Data
C3| | |||||||PRP and IEC 61850
C4| | |||||||PRP, Ethernet Global Data, and IEC 61850
C6| | |||||||PRP and PMU
C7| | |||||||PRP, IEC 61850, and PMU
D0| | |||||||IEEE 1588 and CyberSentry Lvl 1
D1| | |||||||IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD)
D3| | |||||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850
D4| | |||||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
D6| | |||||||IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU)
D7| | |||||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
H | |||||||Horizontal (19” rack) - Standard
A | |||||||Horizontal (19” rack) - With harsh environmental coating
D |||||||French display
R |||||||Russian display
A |||||||Chinese display
P |||||||English display with 4 small and 12 large programmable pushbuttons
G |||||||French display with 4 small and 12 large programmable pushbuttons
S |||||||Russian display with 4 small and 12 large programmable pushbuttons
B |||||||Chinese display with 4 small and 12 large programmable pushbuttons
K |||||||Enhanced front panel with English display
M |||||||Enhanced front panel with French display
Q |||||||Enhanced front panel with Russian display
U |||||||Enhanced front panel with Chinese display
L |||||||Enhanced front panel with English display and user-programmable pushbuttons
N |||||||Enhanced front panel with French d isplay and user-programmable pushbuttons
T |||||||Enhanced front panel with Russian display and user-programmable pushbuttons
V |||||||Enhanced front panel with Chinese display and user-programmable pushbutt ons
W |||||||Enhanced front panel with Turkish display
Y |||||||Enhanced front panel with Turkish display and user-programmable pushbuttons
I |||||||Enhanced front panel with German display
J |||||||Enhanced front panel with German display and user-programmable pushbu ttons
H||||||125 / 250 V AC/DC power supply
H|||||SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply
L||||||24 to 48 V (DC only) power supply
L|||||SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
4A4A|4 Solid-State (no monitoring) MOSFET outputs
4B4B|4 Solid-State (voltage with optional current) MOSFET outputs
4C4C|4 Solid-State (current with optional voltage) MOSFET outputs
4D4D|16 Contact inputs with Auto-Burnishing (maximum of three modules within a case)
4L4L|14 Form-A (no monitoring) Latching outputs
6767|8 Form-A (no monitoring) outputs
6A6A|2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs
6B6B|2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs
6C6C|8 Form-C outputs
6D6D|16 Contact inputs
6E6E|4 Form-C outputs, 8 contact inputs
6F6F|8 Fast Form-C outputs
6G6G|4 Form-A (voltage with optional current) outputs, 8 contact inputs
6H6H|6 Form-A (voltage with optional current) outputs, 4 contact inputs
6K6K|4 Form-C and 4 Fast Form-C outputs
6L6L|2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs
6M6M|2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs
6N6N|4 Form-A (current with optional voltage) outputs, 8 contact inputs
6P6P|6 Form-A (current with optional voltage) outputs, 4 contact inputs
6R6R|2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs
6S6S|2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs
6T6T|4 Form-A (no monitoring) outputs, 8 contact inputs
6U6U|6 Form-A (no monitoring) outputs, 4 contact inputs
6V6V|2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL2-13
ORDER CODESCHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-7: F60 order codes for reduced-size vertical units with process bus
BASE UNITF60| || | |||||Base Unit
CPUT || | |||||RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE00| | |||||No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U || | |||||RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V || | |||||RS485 and Three 10/100Base-TX (SFP with RJ45)
01| | |||||Ethernet Global Data (EGD)
03| | |||||IEC 61850
04| | |||||Ethernet Global Data (EGD) and IEC 61850
06| | |||||Phasor measurement unit (PMU)
07| | |||||Phasor measurement unit (PMU) and IEC 61850
A0| | |||||CyberSentry Lvl 1
A1| | |||||CyberSentry Lvl 1 and Ethernet Global Data (EGD)
A3| | |||||CyberSentry Lvl 1 and IEC 61850
A4| | |||||CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
A6| | |||||CyberSentry Lvl 1 and phasor measurment unit (PMU)
A7| | |||||CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU)
B0| | |||||IEEE 1588
B1| | |||||IEEE 1588 and Ethernet Global Data (EGD)
B3| | |||||IEEE 1588 and IEC 61850
B4| | |||||IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD)
B6| | |||||IEEE 1588 and phasor measurement unit (PMU)
B7| | |||||IEEE 1588 and IEC 61850 and phasor measurement unit (PMU)
C0| | |||||Parallel Redundancy Protocol (PRP)
C1| | |||||PRP and Ethernet Global Data
C3| | |||||PRP and IEC 61850
C4| | |||||PRP, Ethernet Global Data, and IEC 61850
C6| | |||||PRP and PMU
C7| | |||||PRP, IEC 61850, and PMU
D0| | |||||IEEE 1588 and CyberSentry Lvl 1
D1| | |||||IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD)
D3| | |||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850
D4| | |||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
D6| | |||||IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU)
D7| | |||||IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
POWER
SUPPLY
PROCESS BUS MODULE|81||Eight-port digital process bus module
CONTACT INPUTS/OUTPUTSXXXXXX No Modu le
INTER-RELAY
COMMUNICATIONS
(select a maximum of 1 per unit)
For the last module, slot P is used for digital
input/output modules; slot R is used for inter-relay
communications modules.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
V | |||||Vertical (3/4 rack) - Standard
B | |||||Vertical (3/4 rack) - With harsh environmental coating
D |||||French display
R |||||Russian display
A |||||Chinese display
K |||||Enhanced front panel with English display
M |||||Enhanced front panel with French display
Q |||||Enhanced front panel with Russian display
U |||||Enhanced front panel with Chinese display
L |||||Enhanced front panel with English display and user-programmable pushbuttons
N |||||Enhanced front panel with French display and user-programmable pushbuttons
T |||||Enhanced front panel with Russian display and user-programmable pushbuttons
V |||||Enhanced front panel with Chinese display and user-programmable pushbuttons
W |||||Enhanced front panel with Turkish display
Y |||||Enhanced front panel with Turkish display and user-programmable pushbuttons
I |||||Enhanced front panel with German display
J |||||Enhanced front panel with German display and user-programmable pushbuttons
H||||125 / 250 V AC/DC power supply
L||||24 to 48 V (DC only) power supply
4A 4 Solid-State (no monitoring) MOSFET outputs
4B 4 Solid-State (voltage with optional current) MOSFET outputs
4C 4 Solid-State (current with optional voltage) MOSFET outputs
4D 16 Contact inputs with Auto-Bu rnishing (maximum of three modules within a case)
4L 14 Form-A (no monitoring) Latching outputs
67 8 Form-A (no monitoring) outputs
6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs
6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs
6C 8 Form-C outputs
6D 16 Contact inputs
6E 4 Form-C outputs, 8 contact inputs
6F 8 Fast Form-C outputs
6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs
6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs
6K 4 Form-C and 4 Fast Form-C outputs
6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs
6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs
6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs
6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs
6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs
6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs
6T 4 Form-A (no monitoring) outputs, 8 contact inputs
6U 6 Form-A (no monitoring) outputs, 4 contact inputs
6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8
Replacement modules can be ordered separately. When ordering a replacement CPU module or faceplate, provide the
serial number of your existing unit.
Not all replacement modules apply to the F60 relay. The modules specified in the order codes for the F60 are available as
replacement modules for the F60.
The order codes shown here are subject to change without notice. See the web page for the product for the latest options.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL2-15
ORDER CODESCHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-8: UR order codes for replacement modules, horizontal units
POWER SUPPLY
redundant supply only available in horizontal
units and must be same type as main supply
CPU|T| RS485 with 3 100Base-FX Ethernet , multimode, SFP with LC
FACEP LATE/D ISPL AY|3C| Horizontal faceplate with keypad and English display
CONTACT INPUTS AND OUTPUTS|4A| 4 Solid-State (no monitoring) MOSFET outputs
CT/VT MODULES|8L| Standard 4CT/4VT with enhanced diagnostics
(not available for the C30)|8N| Standard 8CT with enhanced diagnostics
TRANSDUCER INPUTS/OUTPUTS|5A| 4 DCmA inputs, 4 DCmA outputs (only one 5A module is allowed)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
UR - ** - *
|SH A | 125 / 300 V AC/DC
|SL H | 24 to 48 V (DC only)
|U| RS485 with 1 100Base-TX Ethernet, SFP RJ-45 + 2 100Base-FX Ethernet , multimode, SFP with LC
|V| RS485 with 3 100Base-TX Ethernet, SFP with RJ-45
|3D| Horizontal faceplate with keypad and French display
|3R| Horizontal faceplate with keypad and Russian display
|3A| Horizontal faceplate with keypad and Chinese display
|3P| Horizontal faceplate with keypad, user-programmable pushbuttons, and English display
|3G| Horizontal faceplate with keypad, user-programmable pushbuttons, and French display
|3S| Horizontal faceplate with keypad, user-programmable pushbuttons, and Russian display
|3B| Horizontal faceplate with keypad, user-programmable pushbuttons, and Chinese display
|3K| Enhanced front panel with English display
|3M| Enhanced front panel with French display
|3Q| En hanced front panel with Russian display
|3U| Enhanced front panel with Chinese display
|3L| Enhanced front panel with English display and user-programmable pushbuttons
|3N| Enhanced front panel with French display and user-programmable pushbuttons
|3T| Enhanced front panel with Russian display a nd user-programmable pushbuttons
|3V| Enhanced front panel with Chinese display and user-programmable pushbuttons
|3I| Enhanced front panel with German display
|3J| Enhanced front panel with German display and user-programmable pushbuttons
|4B| 4 Solid-State (voltage with optional current) MOSFET outputs
|4C| 4 Solid-State (current with optional voltage) MOSFET outputs
|4D| 16 Contact inputs with Auto-Burnishing
|4L| 14 Form-A (no monitoring) Latching outputs
|67| 8 Form-A (no monitoring) outputs
|6A| 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs
|6B| 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs
|6C|8 Form-C outputs
|6D| 16 Contact inputs
|6E| 4 Form-C outputs, 8 contact inputs
|6F|8 Fast Form-C outputs
|6G| 4 Form-A (voltage with optional current) outputs, 8 contact inputs
|6H| 6 Form-A (voltage with optional current) outputs, 4 contact inputs
|6K| 4 Form-C and 4 Fast Form-C outputs
|6L| 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs
|6M| 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs
|6N| 4 Form-A (current with optional voltage) outputs, 8 contact inputs
|6P| 6 Form-A (current with optional voltage) outputs, 4 contact inputs
|6R| 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs
|6S| 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs
|6T| 4 Form-A (no monitoring) outputs, 8 contact inputs
|6U| 6 Form-A (no monitoring) outputs, 4 contact inputs
|6V| 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8 contact inputs
|8M| Sensitive Ground 4CT/4VT with enhanced diagnostics
|8R| Sensitive Ground 8CT with enhanced diagnostics
|8V| Standard 8VT with enhanced diagnostics (only one module supported)
|8Z| Hi-Z 4CT