GE F60 Instruction Manual

GE
LISTED
52TL
IND.CONT. EQ.
E83849
Grid Solutions
F60
Feeder Protection System
Instruction Manual
Product version: 7.41x
GE publication code: 1601-0093-AE1 (GEK-130980)
1601-0093-AE1
Copyright © 2017 GE Multilin Inc. All rights reserved. F60 Feeder Protection System Instruction Manual for version 7.41x. F60, FlexLogic, FlexElement, FlexCurve, FlexAnalog, FlexInteger, FlexState, EnerVista,
CyberSentry, HardFiber, Multilin, and GE Multilin are trademarks or registered trademarks of GE Multilin Inc.
The contents of this manual are the property of GE Multilin Inc. This documentation is furnished on license and may not be reproduced in whole or in part without the permission of GE Multilin. The content of this manual is for informational use only and is subject to change without notice.
Part number: 1601-0093-AE1 (January 2017)
F60 Feeder Protection System
Table of contents
1 INTRODUCTION 1.1 Safety symbols and definitions.....................................................................1-1
1.1.1 General cautions and warnings ....................................................................................1-1
1.2 For further assistance .................................................................................... 1-2
2PRODUCT
DESCRIPTION
2.1 Product description......................................................................................... 2-1
2.1.1 Overview................................................................................................................................... 2-1
2.2 Security.............................................................................................................. 2-3
2.3 Order codes ...................................................................................................... 2-7
2.3.1 Order codes with enhanced CT/VT modules........................................................... 2-7
2.3.2 Order codes with process bus modules ..................................................................2-12
2.3.3 Replacement modules .....................................................................................................2-15
2.4 Signal processing...........................................................................................2-18
2.4.1 UR signal processing ........................................................................................................2-18
2.5 Specifications ................................................................................................. 2-20
2.5.1 Protection elements ..........................................................................................................2-20
2.5.2 User-programmable elements ....................................................................................2-26
2.5.3 Monitoring..............................................................................................................................2-27
2.5.4 Metering..................................................................................................................................2-28
2.5.5 Inputs .......................................................................................................................................2-29
2.5.6 Power supply........................................................................................................................2-31
2.5.7 Outputs....................................................................................................................................2-32
2.5.8 Communication protocols..............................................................................................2-34
2.5.9 Inter-relay communications..........................................................................................2-35
2.5.10 CyberSentry security.........................................................................................................2-36
2.5.11 Environmental......................................................................................................................2-36
2.5.12 Type tests...............................................................................................................................2-37
2.5.13 Production tests..................................................................................................................2-37
2.5.14 Approvals ...............................................................................................................................2-38
2.5.15 Maintenance.........................................................................................................................2-38
3 INSTALLATION 3.1 Unpack and inspect......................................................................................... 3-1
3.2 Panel cutouts.................................................................................................... 3-2
3.2.1 Horizontal units ..................................................................................................................... 3-2
3.2.2 Vertical units........................................................................................................................... 3-3
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL iii
TABLE OF CONTENTS
3.2.3 Rear terminal layout............................................................................................................3-8
3.3 Wiring ................................................................................................................3-9
3.3.1 Typical wiring..........................................................................................................................3-9
3.3.2 Dielectric strength ............................................................................................................. 3-10
3.3.3 Control power......................................................................................................................3-11
3.3.4 CT/VT modules ....................................................................................................................3-12
3.3.5 Process bus modules ....................................................................................................... 3-15
3.3.6 Contact inputs and outputs ..........................................................................................3-16
3.3.7 Transducer inputs and outputs...................................................................................3-23
3.3.8 RS232 faceplate port........................................................................................................ 3-25
3.3.9 CPU communication ports ............................................................................................ 3-26
3.3.10 IRIG-B....................................................................................................................................... 3-28
3.4 Direct input and output communications ................................................3-29
3.4.1 Description............................................................................................................................ 3-29
3.4.2 Fiber: LED and ELED transmitters...............................................................................3-32
3.4.3 Fiber laser transmitters...................................................................................................3-32
3.4.4 G.703 interface....................................................................................................................3-33
3.4.5 RS422 interface...................................................................................................................3-37
3.4.6 RS422 and fiber interface ..............................................................................................3-39
3.4.7 G.703 and fiber interface................................................................................................ 3-40
3.4.8 IEEE C37.94 interface .......................................................................................................3-40
3.4.9 C37.94SM interface...........................................................................................................3-43
3.5 Activate relay .................................................................................................3-46
3.6 Install software ..............................................................................................3-47
3.6.1 EnerVista communication overview ......................................................................... 3-47
3.6.2 System requirements.......................................................................................................3-48
3.6.3 Install software.................................................................................................................... 3-49
3.7 Add device to software.................................................................................3-50
3.7.1 Set IP address in UR..........................................................................................................3-50
3.7.2 Configure serial connection.......................................................................................... 3-56
3.7.3 Configure Ethernet connection ...................................................................................3-57
3.7.4 Configure modem connection..................................................................................... 3-59
3.7.5 Automatic discovery of UR devices...........................................................................3-59
3.8 Connect to the F60 ........................................................................................3-60
3.8.1 Connect to the F60 in EnerVista..................................................................................3-60
3.8.2 Use Quick Connect via the front panel RS232 port............................................3-61
3.8.3 Use Quick Connect via a rear Ethernet port..........................................................3-62
3.9 Set up CyberSentry and change default password.................................3-62
3.10 Import settings...............................................................................................3-63
4 INTERFACES 4.1 EnerVista software interface......................................................................... 4-1
4.1.1 Introduction .............................................................................................................................4-1
4.1.2 Settings files ............................................................................................................................4-1
4.1.3 Event viewing..........................................................................................................................4-2
4.1.4 File support ..............................................................................................................................4-3
4.1.5 EnerVista main window .....................................................................................................4-3
4.1.6 Protection summary window ..........................................................................................4-4
4.1.7 Settings templates................................................................................................................4-5
4.1.8 Secure and lock FlexLogic equations ..........................................................................4-9
4.1.9 Settings file traceability................................................................................................... 4-12
4.2 Front panel interface ....................................................................................4-15
4.2.1 Front panel display............................................................................................................ 4-15
4.2.2 Front panel keypad ........................................................................................................... 4-16
4.2.3 Menu navigation ................................................................................................................4-16
iv F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TABLE OF CONTENTS
4.2.4 Menu hierarchy ...................................................................................................................4-16
4.2.5 Changing settings ..............................................................................................................4-17
4.2.6 Faceplate................................................................................................................................4-19
4.2.7 LED indicators ......................................................................................................................4-20
4.2.8 Custom LED labeling.........................................................................................................4-24
4.2.9 Breaker control....................................................................................................................4-29
4.2.10 Change passwords............................................................................................................4-30
4.2.11 Invalid password entry ....................................................................................................4-31
4.3 Logic diagrams...............................................................................................4-32
4.4 FlexLogic design and monitoring using Engineer....................................4-33
4.4.1 Design logic...........................................................................................................................4-35
4.4.2 Send file to and from device .........................................................................................4-45
4.4.3 Monitor logic.........................................................................................................................4-46
4.4.4 View front panel and print labels................................................................................4-47
4.4.5 Generate connectivity report........................................................................................4-48
4.4.6 Preferences ...........................................................................................................................4-48
4.4.7 Toolbars ..................................................................................................................................4-52
5 SETTINGS 5.1 Settings menu .................................................................................................. 5-1
5.2 Overview ...........................................................................................................5-4
5.2.1 Introduction to elements .................................................................................................. 5-4
5.2.2 Introduction to AC sources .............................................................................................. 5-6
5.3 Product setup................................................................................................... 5-7
5.3.1 Security ..................................................................................................................................... 5-7
5.3.2 Display properties ..............................................................................................................5-26
5.3.3 Clear relay records.............................................................................................................5-28
5.3.4 Communications ................................................................................................................5-29
5.3.5 Modbus user map ..............................................................................................................5-95
5.3.6 Real-time clock....................................................................................................................5-95
5.3.7 Fault reports .........................................................................................................................5-99
5.3.8 Oscillography..................................................................................................................... 5-101
5.3.9 Data logger ........................................................................................................................5-103
5.3.10 Demand ...............................................................................................................................5-105
5.3.11 User-programmable LEDs ..........................................................................................5-106
5.3.12 User-programmable self-tests .................................................................................5-110
5.3.13 Control pushbuttons......................................................................................................5-110
5.3.14 User-programmable pushbuttons..........................................................................5-112
5.3.15 Flex state parameters ...................................................................................................5-117
5.3.16 User-definable displays................................................................................................ 5-118
5.3.17 Direct inputs and outputs............................................................................................5-120
5.3.18 Teleprotection...................................................................................................................5-126
5.3.19 Installation..........................................................................................................................5-127
5.4 Remote resources........................................................................................5-127
5.4.1 Remote resources configuration .............................................................................5-127
5.5 System setup................................................................................................5-129
5.5.1 AC inputs .............................................................................................................................5-129
5.5.2 Power system....................................................................................................................5-130
5.5.3 Signal sources...................................................................................................................5-131
5.5.4 Breakers...............................................................................................................................5-134
5.5.5 Disconnect switches ......................................................................................................5-138
5.5.6 FlexCurves........................................................................................................................... 5-141
5.5.7 Phasor Measurement Unit ..........................................................................................5-148
5.6 FlexLogic........................................................................................................5-168
5.6.1 FlexLogic operands ........................................................................................................ 5-168
5.6.2 FlexLogic rules ..................................................................................................................5-181
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL v
TABLE OF CONTENTS
5.6.3 FlexLogic evaluation...................................................................................................... 5-181
5.6.4 FlexLogic example..........................................................................................................5-182
5.6.5 FlexLogic equation editor............................................................................................ 5-187
5.6.6 FlexLogic timers...............................................................................................................5-187
5.6.7 FlexElements .....................................................................................................................5-187
5.6.8 Non-volatile latches.......................................................................................................5-191
5.7 Grouped elements .......................................................................................5-192
5.7.1 Overview ............................................................................................................................. 5-192
5.7.2 Setting group 1................................................................................................................. 5-192
5.7.3 Load encroachment ...................................................................................................... 5-193
5.7.4 Phase current ................................................................................................................... 5-195
5.7.5 Neutral current................................................................................................................. 5-207
5.7.6 Wattmetric ground fault.............................................................................................. 5-215
5.7.7 Ground current ................................................................................................................ 5-219
5.7.8 Negative sequence current........................................................................................ 5-226
5.7.9 Breaker failure (ANSI 50BF)......................................................................................... 5-232
5.7.10 Voltage elements ............................................................................................................ 5-241
5.7.11 Sensitive directional power (ANSI 32) .................................................................... 5-248
5.8 Control elements .........................................................................................5-251
5.8.1 Overview ............................................................................................................................. 5-251
5.8.2 Trip bus ................................................................................................................................ 5-251
5.8.3 Setting groups .................................................................................................................. 5-253
5.8.4 Selector switch................................................................................................................. 5-254
5.8.5 Underfrequency (ANSI 81U)........................................................................................ 5-261
5.8.6 Overfrequency (ANSI 81O) .......................................................................................... 5-262
5.8.7 Frequency rate of change (ANSI 81R)....................................................................5-263
5.8.8 Synchrocheck (ANSI 25) ............................................................................................... 5-265
5.8.9 Autoreclose (ANSI 79).................................................................................................... 5-270
5.8.10 Digital elements............................................................................................................... 5-276
5.8.11 Digital counters................................................................................................................5-279
5.9 Monitoring elements...................................................................................5-281
5.9.1 Cold load pickup.............................................................................................................. 5-309
5.9.2 Pilot schemes.................................................................................................................... 5-310
5.10 Inputs/outputs .............................................................................................5-315
5.10.1 Contact inputs.................................................................................................................. 5-315
5.10.2 Virtual inputs ..................................................................................................................... 5-317
5.10.3 Contact outputs............................................................................................................... 5-318
5.10.4 Virtual outputs.................................................................................................................. 5-322
5.10.5 Resetting .............................................................................................................................5-322
5.10.6 Direct inputs and outputs ........................................................................................... 5-322
5.10.7 Teleprotection................................................................................................................... 5-326
5.11 Transducer inputs/outputs........................................................................5-328
5.11.1 DCmA inputs...................................................................................................................... 5-328
5.11.2 RTD inputs .......................................................................................................................... 5-329
5.11.3 DCmA outputs .................................................................................................................. 5-330
5.12 Testing ...........................................................................................................5-334
5.12.1 Test mode function ........................................................................................................5-334
5.12.2 Test mode forcing........................................................................................................... 5-334
5.12.3 Phasor Measurement Unit test values.................................................................. 5-335
5.12.4 Force contact inputs ..................................................................................................... 5-336
5.12.5 Force contact outputs .................................................................................................. 5-336
6 ACTUAL VALUES 6.1 Actual Values menu.........................................................................................6-1
6.2 Front panel........................................................................................................ 6-3
vi F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TABLE OF CONTENTS
6.3 Status.................................................................................................................6-4
6.3.1 Contact inputs ....................................................................................................................... 6-4
6.3.2 Virtual inputs........................................................................................................................... 6-4
6.3.3 RxGOOSE boolean inputs.................................................................................................. 6-5
6.3.4 RxGOOSE DPS inputs ..........................................................................................................6-5
6.3.5 Teleprotection inputs.......................................................................................................... 6-5
6.3.6 Contact outputs ....................................................................................................................6-5
6.3.7 Virtual outputs ....................................................................................................................... 6-6
6.3.8 RxGOOSE status.................................................................................................................... 6-6
6.3.9 RxGOOSE statistics ..............................................................................................................6-6
6.3.10 Autoreclose ............................................................................................................................. 6-7
6.3.11 Digital counters ..................................................................................................................... 6-7
6.3.12 Selector switches.................................................................................................................. 6-7
6.3.13 Flex States................................................................................................................................ 6-7
6.3.14 Ethernet .................................................................................................................................... 6-8
6.3.15 Real time clock synchronizing........................................................................................ 6-8
6.3.16 Hi-Z status ............................................................................................................................... 6-9
6.3.17 Direct inputs............................................................................................................................6-9
6.3.18 Direct devices status ..........................................................................................................6-9
6.3.19 EGD protocol status ..........................................................................................................6-10
6.3.20 Teleprotection channel tests ........................................................................................6-10
6.3.21 Incipient fault detector ....................................................................................................6-11
6.3.22 Remaining connection status.......................................................................................6-11
6.3.23 Parallel Redundancy Protocol (PRP)...........................................................................6-11
6.3.24 TxGOOSE status ..................................................................................................................6-12
6.4 Metering .......................................................................................................... 6-13
6.4.1 Metering conventions.......................................................................................................6-13
6.4.2 Sources....................................................................................................................................6-17
6.4.3 Sensitive directional power ...........................................................................................6-23
6.4.4 Synchrocheck.......................................................................................................................6-23
6.4.5 Tracking frequency............................................................................................................6-24
6.4.6 Frequency rate of change..............................................................................................6-24
6.4.7 FlexElements.........................................................................................................................6-24
6.4.8 RxGOOSE analogs ..............................................................................................................6-25
6.4.9 Wattmetric ground fault .................................................................................................6-25
6.4.10 Phasor Measurement Unit .............................................................................................6-25
6.4.11 PMU aggregator..................................................................................................................6-26
6.4.12 Restricted ground fault....................................................................................................6-26
6.4.13 Transducer inputs and outputs ...................................................................................6-26
6.5 Records............................................................................................................6-27
6.5.1 Fault reports .........................................................................................................................6-27
6.5.2 Event records .......................................................................................................................6-28
6.5.3 Oscillography........................................................................................................................6-29
6.5.4 Data logger ...........................................................................................................................6-29
6.5.5 Phasor Measurement Unit records............................................................................6-29
6.5.6 Breaker maintenance.......................................................................................................6-30
6.5.7 Hi-Z records ..........................................................................................................................6-30
6.6 Product information......................................................................................6-31
6.6.1 Model information..............................................................................................................6-31
6.6.2 Firmware revisions ............................................................................................................6-32
7 COMMANDS AND
TARGETS
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL vii
7.1 Commands menu ............................................................................................7-1
7.1.1 Virtual inputs........................................................................................................................... 7-2
7.1.2 Clear records ..........................................................................................................................7-2
7.1.3 Set date and time................................................................................................................. 7-3
TABLE OF CONTENTS
7.1.4 Relay maintenance ..............................................................................................................7-3
7.1.5 Phasor Measurement Unit one-shot ...........................................................................7-4
7.1.6 Security......................................................................................................................................7-6
7.2 Targets menu ................................................................................................... 7-6
7.2.1 Target messages...................................................................................................................7-7
7.2.2 Relay self-tests .......................................................................................................................7-7
8 COMMISSIONING 8.1 Testing ...............................................................................................................8-1
8.1.1 Testing underfrequency and overfrequency elements.......................................8-1
9 THEORY OF
OPERATION
9.1 High-impedance (Hi-Z) fault detection ........................................................9-1
9.1.1 Description...............................................................................................................................9-1
9.1.2 Energy algorithm...................................................................................................................9-2
9.1.3 Randomness algorithm......................................................................................................9-2
9.1.4 Expert Arc Detector algorithm........................................................................................9-2
9.1.5 Spectral Analysis algorithm .............................................................................................9-3
9.1.6 Load Event Detector algorithm ......................................................................................9-3
9.1.7 Load Analysis algorithm ....................................................................................................9-3
9.1.8 Load Extraction algorithm................................................................................................9-3
9.1.9 Arc Burst Pattern Analysis algorithm...........................................................................9-4
9.1.10 Arcing Suspected algorithm ............................................................................................9-4
9.1.11 Overcurrent disturbance monitoring...........................................................................9-4
9.1.12 Hi-Z Even Harmonic Restraint algorithm...................................................................9-4
9.1.13 Hi-Z Voltage Supervision algorithm .............................................................................9-4
9.2 Fault locator ..................................................................................................... 9-4
9.2.1 Fault type determination...................................................................................................9-4
10 MAINTENANCE 10.1 Monitoring.......................................................................................................10-1
10.1.1 Devices with Site Targets ...............................................................................................10-1
10.1.2 Data with Modbus Analyzer..........................................................................................10-1
10.2 General maintenance ...................................................................................10-3
10.2.1 In-service maintenance..................................................................................................10-3
10.2.2 Out-of-service maintenance ........................................................................................10-3
10.2.3 Unscheduled maintenance (system interruption) ..............................................10-3
10.3 Retrieve files ...................................................................................................10-3
10.3.1 CyberSentry security event files..................................................................................10-4
10.4 Compare settings ..........................................................................................10-5
10.4.1 Compare against defaults .............................................................................................10-5
10.4.2 Compare two devices ......................................................................................................10-5
10.5 Back up and restore settings.......................................................................10-6
10.5.1 Back up settings ................................................................................................................. 10-6
10.5.2 Restore settings.................................................................................................................. 10-8
10.6 Upgrade software........................................................................................10-10
10.7 Upgrade firmware .......................................................................................10-11
10.8 Replace module............................................................................................10-12
10.9 Battery...........................................................................................................10-14
10.9.1 Replace battery for SH/SL power supply ............................................................. 10-14
10.9.2 Dispose of battery ..........................................................................................................10-15
10.10 Clear files and data after uninstall...........................................................10-18
10.11 Repairs...........................................................................................................10-19
10.12 Storage ..........................................................................................................10-19
10.13 Disposal.........................................................................................................10-20
viii F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TABLE OF CONTENTS
AFLEXANALOG
A.1 FlexAnalog items .............................................................................................A-1
OPERANDS
B RADIUS SERVER
B.1 RADIUS server configuration .........................................................................B-1
CONFIGURATION
C COMMAND LINE
C.1 Command line interface .................................................................................C-1
INTERFACE
D MISCELLANEOUS D.1 Warranty ...........................................................................................................D-1
D.2 Revision history ...............................................................................................D-1
ABBREVIATIONS
INDEX
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL ix
TABLE OF CONTENTS
x F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
F60 Feeder Protection System
Chapter 1: Introduction

Introduction

This chapter outlines safety and technical support information.

1.1 Safety symbols and definitions

Before attempting to install or use the device, review all safety indicators in this document to help prevent injury, equipment damage, or downtime.
The following safety and equipment symbols are used in this document.
Indicates a hazardous situation which, if not avoided, will result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in minor or moderate injury.
Indicates practices not related to personal injury.

1.1.1 General cautions and warnings

The following general safety precautions and warnings apply.
Ensure that all connections to the product are correct so as to avoid accidental risk of shock and/or fire, for example such as can arise from high voltage connected to low voltage terminals.
Follow the requirements of this manual, including adequate wiring size and type, terminal torque settings, voltage, current magnitudes applied, and adequate isolation/clearance in external wiring from high to low voltage circuits.
Use the device only for its intended purpose and application. Ensure that all ground paths are uncompromised for safety purposes during device operation and service. Ensure that the control power applied to the device, the AC current, and voltage input match the ratings specified on
the relay nameplate. Do not apply current or voltage in excess of the specified limits.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 1-1
1
FOR FURTHER ASSISTANCE CHAPTER 1: INTRODUCTION
Only qualified personnel are to operate the device. Such personnel must be thoroughly familiar with all safety cautions and warnings in this manual and with applicable country, regional, utility, and plant safety regulations.
Hazardous voltages can exist in the power supply and at the device connection to current transformers, voltage transformers, control, and test circuit terminals. Make sure all sources of such voltages are isolated prior to attempting work on the device.
Hazardous voltages can exist when opening the secondary circuits of live current transformers. Make sure that current transformer secondary circuits are shorted out before making or removing any connection to the current transformer (CT) input terminals of the device.
For tests with secondary test equipment, ensure that no other sources of voltages or currents are connected to such equipment and that trip and close commands to the circuit breakers or other switching apparatus are isolated, unless this is required by the test procedure and is specified by appropriate utility/plant procedure.
When the device is used to control primary equipment, such as circuit breakers, isolators, and other switching apparatus, all control circuits from the device to the primary equipment must be isolated while personnel are working on or around this primary equipment to prevent any inadvertent command from this device.
Use an external disconnect to isolate the mains voltage supply. Personal safety can be affected if the product is physically modified by the end user. Modifications to the product
outside of recommended wiring configuration, hardware, or programming boundaries is not recommended end-use practice. Product disassembly and repairs are not permitted. All service needs to be conducted by the factory.
LED transmitters are classified as IEC 60825-1 Accessible Emission Limit (AEL) Class 1M. Class 1M devices are considered safe to the unaided eye. Do not view directly with optical instruments.
This product is rated to Class A emissions levels and is to be used in Utility, Substation Industrial environments. Not to be used near electronic devices rated for Class B levels.

1.2 For further assistance

For product support, contact the information and call center as follows:
GE Grid Solutions 650 Markland Street Markham, Ontario Canada L6C 0M1 Worldwide telephone: +1 905 927 7070 Europe/Middle East/Africa telephone: +34 94 485 88 54 North America toll-free: 1 800 547 8629 Fax: +1 905 927 5098 Worldwide e-mail: multilin.tech@ge.com Europe e-mail: multilin.tech.euro@ge.com Website: http://www.gegridsolutions.com/multilin
When contacting GE by e-mail, optionally include a device information file, which is generated in the EnerVista software by clicking the Service Report button.
1-2 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 1: INTRODUCTION FOR FURTHER ASSISTANCE
Figure 1-1: Generate service report
1
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 1-3
1
FOR FURTHER ASSISTANCE CHAPTER 1: INTRODUCTION
1-4 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
F60 Feeder Protection System
Chapter 2: Product description

Product description

This chapter outlines the product, order codes, and specifications.

2.1 Product description

2.1.1 Overview

The F60 Feeder Protection System is part of the Universal Relay (UR) series of products. It is a microprocessor-based relay for feeder protection.
Overvoltage and undervoltage protection, overfrequency and underfrequency protection, breaker failure protection, directional current supervision, fault diagnostics, remote terminal unit (RTU), and programmable logic functions are provided. This relay also provides phase, neutral, ground and negative sequence, instantaneous and time overcurrent protection. The time overcurrent function provides multiple curve shapes or FlexCurves™ for optimum co-ordination. Automatic reclosing, synchrocheck, and line fault locator features are also provided. When equipped with a type 8Z current transformer/voltage transformer (CT/VT) module, an element for detecting high impedance faults is provided.
Voltage, current, and power metering are built in as standard features. Current parameters are available as total waveform root mean square (RMS) magnitude, or as fundamental frequency only RMS magnitude and angle (phasor).
Diagnostic features include an event recorder that stores 1024 time-tagged events. The internal clock used for time­tagging can be synchronized with an IRIG-B signal, using the Simple Network Time Protocol (SNTP) over the Ethernet port, or using the Precision Time Protocol (PTP). This precise time stamping allows the sequence of events to be determined throughout the system. Events can also be programmed (via FlexLogic™ equations) to trigger oscillography data capture that can be set to record the measured parameters before and after the event for viewing on a computer. These tools significantly reduce troubleshooting time and simplify report generation in the event of a system fault.
Several options are available for communication. A faceplate RS232 port can be used to connect to a computer to program settings and monitor actual values. The rear RS485 port allows independent access by operating and engineering staff. It can be connected to system computers with baud rates up to 115.2 kbps. All serial ports use the Modbus RTU protocol. The IEC 60870-5-103 protocol is supported on the RS485 interface. IEC 60870-5-103, DNP, and Modbus cannot be enabled simultaneously on this interface. Also only one of the DNP, IEC 60870-5-103, and IEC 60870-5-104 protocols can be enabled at any time on the relay. When the IEC 60870-5-103 protocol is chosen, the RS485 port has a fixed even parity and the baud rate can be either 9.6 kbps or 19.2 kbps. The 100Base-FX or 100Base-TX Ethernet interface provides fast, reliable communications in noisy environments. The Ethernet port supports IEC 61850, IEC 61850-90-5, Modbus/TCP, TFTP, and PTP (according to IEEE Std. 1588-2008 or IEC 61588), and it allows access to the relay via any standard web browser (F60 web pages). The IEC 60870-5-104 protocol is supported on the Ethernet port. The Ethernet port also supports the Parallel Redundancy Protocol (PRP) of IEC 62439-3 (clause 4, 2012) when purchased as an option.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-1
PRODUCT DESCRIPTION CHAPTER 2: PRODUCT DESCRIPTION
Secure Routable GOOSE (R-GOOSE) is supported with software options. Settings and actual values can be accessed from the front panel or EnerVista software. The F60 uses flash memory technology that allows field upgrading as new features are added. Firmware and software are
upgradable. The following single-line diagram illustrates the relay functionality using American National Standards Institute (ANSI)
device numbers.
2
Table 2-1: ANSI device numbers and functions supported
Device number Function Device number Function
25 Synchrocheck 51_2 Negative-sequence time overcurrent 27P Phase undervoltage 52 AC circuit breaker 27X Auxiliary undervoltage 59N Neutral overvoltage 32 Sensitive directional power 59P Phase overvoltage 32N Wattmetric zero-sequence directional 59X Auxiliary overvoltage 49 Thermal overload protection 59_2 Negative-sequence overvoltage 50BF/50NBF Breaker failure 67N Neutral directional overcurrent 50DD Disturbance detector 67P Phase directional overcurrent 50G Ground instantaneous overcurrent 67_2 Negative-sequence directional overcurrent 50N Neutral instantaneous overcurrent 79 Automatic recloser 50P Phase instantaneous overcurrent 81O Overfrequency 50_2 Negative-sequence instantaneous overcurrent 81R Rate of change frequency 51G Ground time overcurrent 81U Underfrequency 51N Neutral time overcurrent 87RGF Restricted ground fault 51P Phase time overcurrent
Figure 2-1: Single-line diagram
2-2 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SECURITY
Table 2-2: Other device functions
Function Function Function
Breaker arcing current (I Breaker control Event recorder Setting groups (6) Breaker flashover Fault detector and fault report Synchrophasor (PMU) Breaker restrike Fault locator Thermal overload protection Broken conductor detection FlexElements™ (8) Time synchronization over IRIG-B or IEEE
Cold load pickup FlexLogic equations Time synchronization over SNTP Contact inputs (up to 96) High impedance fault detection (Hi-Z) Transducer inputs and outputs Contact outputs (up to 64) IEC 60870-5-103 communications User-definable displays Control pushbuttons IEC 61850 communications User-programmable LEDs CT failure detector IEC 62351-9 data and communications
CyberSentry™ security Incipient cable fault detection User-programmable self-tests Data logger Load encroachment Virtual inputs (64) Demand Metering: current, voltage, power, PF,
Digital counters (8) Modbus user map VT fuse failure Digital elements (48) Non-volatile latches Direct inputs and outputs (32) Non-volatile selector switch Disconnect switches Oscillography
2
t) Ethernet Global Data Pilot schemes
1588
security
energy, frequency, harmonics, THD
User-programmable pushbuttons
Virtual outputs (96)
2

2.2 Security

The following security features are available:
Password security — Basic security present by default
EnerVista security — Role-based access to various EnerVista software screens and configuration elements. The feature is present by default in the EnerVista software.
CyberSentry security — Advanced security available using a software option. When purchased, the option is automatically enabled, and the default Password security and EnerVista security are disabled.

2.2.0.1 EnerVista security

The EnerVista security management system is a role-based access control (RBAC) system that allows an administrator to manage the privileges of multiple users. This allows for access control of UR devices by multiple personnel within a substation and conforms to the principles of RBAC as defined in ANSI INCITS 359-2004. The EnerVista security management system is disabled by default to allow the administrator direct access to the EnerVista software after installation. It is recommended that security be enabled before placing the device in service.
Basic password or enhanced CyberSentry security applies, depending on purchase.

2.2.0.2 Password security

Password security is a basic security feature present by default. Two levels of password security are provided: command and setting. Use of a password for each level controls whether
users can enter commands and/or change settings. The F60 supports password entry from a local or remote connection. Local access is defined as any access to settings or
commands via the faceplate interface. This includes both keypad entry and the through the faceplate RS232 port. Remote access is defined as any access to settings or commands via any rear communications port. This includes both Ethernet and RS485 connections. Any changes to the local or remote passwords enables this functionality.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-3
2
SECURITY CHAPTER 2: PRODUCT DESCRIPTION
When entering a settings or command password via EnerVista or any serial interface, the user must enter the corresponding connection password. If the connection is to the back of the F60, the remote password must be used. If the connection is to the RS232 port of the faceplate, the local password applies.
Password access events are logged in the Event Recorder.

2.2.0.3 CyberSentry security

CyberSentry embedded security is available using a software option (Level 1) that provide advanced security services. When the option is purchased, the basic password security is disabled automatically.
CyberSentry provides security through the following features:
An Authentication, Authorization, Accounting (AAA) Remote Authentication Dial-In User Service (RADIUS) client that is centrally managed, enables user attribution, provides accounting of all user activities, and uses secure standards­based strong cryptography for authentication and credential protection
A Role-Based Access Control (RBAC) system that provides a permission model that allows access to UR device operations and configurations based on specific roles and individual user accounts configured on the AAA server (that is, Administrator, Supervisor, Engineer, Operator, Observer roles)
Security event reporting through the Syslog protocol for supporting Security Information Event Management (SIEM) systems for centralized cybersecurity monitoring
Strong encryption of all access and configuration network messages between the EnerVista software and UR devices using the Secure Shell (SSH) protocol, the Advanced Encryption Standard (AES), and 128-bit keys in Galois Counter Mode (GCM) as specified in the U.S. National Security Agency Suite B extension for SSH and approved by the National Institute of Standards and Technology (NIST) FIPS-140-2 standards for cryptographic systems
CyberSentry user roles
CyberSentry user roles (Administrator, Engineer, Operator, Supervisor, Observer) limit the levels of access to various UR device functions. This means that the EnerVista software allows for access to functionality based on the user’s logged in role.
Example: Administrative functions can be segmented away from common operator functions, or engineering type access, all of which are defined by separate roles (see figure) so that access of UR devices by multiple personnel within a substation is allowed.
Figure 2-2: CyberSentry user roles
The table lists user roles and their corresponding capabilities.
Table 2-3: Permissions by user role for CyberSentry
Roles Administrator Engineer Operator Supervisor Observer
Complete access Complete access
except for CyberSentry Security
Device Definition R R R R R
2-4 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
Command menu
Authorizes writing
Default role
CHAPTER 2: PRODUCT DESCRIPTION SECURITY
Roles Administrator Engineer Operator Supervisor Observer
Settings |---------- Product Setup
|--------------- Security
(CyberSentry)
|--------------- Supervisory See table notes R R See table
|--------------- Display Properties RW RW R R R |--------------- Clear Relay Records
(settings) |--------------- Communications RW RW R R R |--------------- Modbus User Map RW RW R R R |--------------- Real Time Clock RW RW R R R |--------------- Oscillography RW RW R R R |--------------- Data Logger RW RW R R R |--------------- Demand RW RW R R R |--------------- User-Programmable
LEDs |--------------- User-Programmable
Self Tests |--------------- Control Pushbuttons RW RW R R R |--------------- User-Programmable
Pushbuttons |--------------- Flex state
Parameters |--------------- User-Definable
Displays |--------------- Direct I/O RW RW R R R |--------------- Teleprotection RW RW R R R |--------------- Installation RW RW R R R
|---------- System Setup RW RW R R R |---------- FlexLogic RW RW R R R |---------- Grouped Elements RW RW R R R |---------- Control Elements RW RW R R R |---------- Inputs / Outputs RW RW R R R
|--------------- Contact Inputs RW RW R R R |--------------- Contact Input
threshold |--------------- Virtual Inputs RW RW R R R |--------------- Contact Outputs RW RW R R R |--------------- Virtual Outputs RW RW R R R |--------------- Resetting RW RW R R R |--------------- Direct Inputs RW RW R R R |--------------- Direct Outputs RW RW R R R |--------------- Teleprotection RW RW R R R |--------------- Direct Analogs RW RW R R R |--------------- Direct Integers RW RW R R R
|---------- Transducer I/O RW RW R R R |---------- Testing RW RW R R R |---------- Front Panel Labels Designer NA NA NA NA NA
RW R R R R
R
notes
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-5
2
SECURITY CHAPTER 2: PRODUCT DESCRIPTION
Roles Administrator Engineer Operator Supervisor Observer
|---------- Protection Summary NA NA NA NA NA Commands RW RW RW R R |---------- Virtual Inputs RW RW RW R R |---------- Clear Records RW RW RW R R |---------- Set Date and Time RW RW RW R R User Displays R R R R R Targets R R R R R Actual Values R R R R R |---------- Front panel labels designer R R R R R |---------- Status R R R R R |---------- Metering R R R R R |---------- Transducer I/O R R R R R |---------- Records R R R R R |---------- Product Info R R R R R Maintenance RW RW R R R |---------- Modbus Analyzer NA NA NA NA NA |---------- Change front panel RW RW RW R R |---------- Update firmware Yes No No No No |---------- Retrieve file Yes No No No No
Table Notes: RW = read and write access R = read access Supervisor = RW (default), Administrator = R (default), Administrator = RW (only if Supervisor role is disabled) NA = the permission is not enforced by CyberSentry security
CyberSentry user authentication
The following types of authentication are supported by CyberSentry to access the UR device:
Device Authentication (local UR device authenticates)
Server Authentication (RADIUS server authenticates) The EnerVista software allows access to functionality that is determined by the user role, which comes either from the local
UR device or the RADIUS server. The EnerVista software has a device authentication option on the login screen for accessing the UR device. When the
"Device" button is selected, the UR uses its local authentication database and not the RADIUS server to authenticate the user. In this case, it uses its built-in roles (Administrator, Engineer, Supervisor, Observer, Operator, or Administrator and Supervisor when Device Authentication is disabled) as login names and the associated passwords are stored on the UR device. As such, when using the local accounts, access is not user-attributable.
In cases where user-attributable access is required especially to facilitate auditable processes for compliance reasons, use RADIUS authentication only.
When the "Server" Authentication Type option is selected, the UR uses the RADIUS server and not its local authentication database to authenticate the user.
No password or security information is displayed in plain text by the EnerVista software or UR device, nor is such information ever transmitted without cryptographic protection.
CyberSentry server authentication
The UR has been designed to direct automatically the authentication requests based on user names. In this respect, local account names on the UR are considered as reserved and not used on a RADIUS server.
2-6 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
The UR detects automatically whether an authentication request is to be handled remotely or locally. As there are five local accounts possible on the UR, if the user ID credential does not match one of the five local accounts, the UR forwards automatically the request to a RADIUS server when one is provided.
If a RADIUS server is provided, but is unreachable over the network, server authentication requests are denied. In this situation, use local UR accounts to gain access to the UR system.

2.3 Order codes

The order code is on the product label and indicates the product options applicable. The F60 is available as a 19-inch rack horizontal mount or reduced-size (¾) vertical unit. It consists of the following
modules: power supply, CPU, CT/VT, contact input and output, transducer input and output, and inter-relay communications. Module options are specified at the time of ordering.
The order codes shown here are subject to change without notice. See the web page for the product for the latest options. The order code depends on the mounting option (horizontal or vertical) and the type of CT/VT modules (enhanced
diagnostic CT/VT modules or HardFiber HardFiber Bricks.
The R-GOOSE protocol described in IEC 61850-8-1 is available through the IEC 61850 software option. If R-GOOSE security is required, the CyberSentry software option also must be purchased.

2.3.1 Order codes with enhanced CT/VT modules

Table 2-4: F60 order codes for horizontal units
BASE UNITF60|||||||||| |Base Unit CPU T | | | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
U | | | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | | | IEC 61850 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | | | CyberSentry Lvl 1 and phasor measurement unit (PMU) A7 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | | | IEEE 1588 B1 | | | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | | | PRP and IEC 61850 C4 | | | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | | | PRP and PMU C7 | | | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | | | IEEE 1588 and PRP E1 | | | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850
TM
process bus module). The process bus module provides an interface to
(SFP with RJ45)
(PMU)
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-7
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
MOUNT/ COATING FACEPLATE/ DISPLAY C | | | | | | | English display
G4 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | | | IEC 60870-5-103 J1 | | | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU Q7 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
H | | | | | | | | Horizontal (19” rack) - Standard A | | | | | | | | Horizontal (19” rack) - With harsh environmental coating
D|||||| |French display R|||||| |Russian display A | | | | | | | Chinese display P | | | | | | | English d isplay with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons W | | | | | | | Enhanced front panel with Turkish display Y | | | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons I | | | | | | | Enhanced front panel with German display J | | | | | | | Enhanced front panel with German display and user-programmable pushbuttons
61850-90-5
IEC 61850
61850-90-5
2-8 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
POWER SUPPLY (redundant supply must be same type as main supply)
ENHANCED DIAGNOSTICS CT/VT DSP (8L, 8M, 8N, 8R require DSP to be enhanced diagnostic)
CONTACT INPUTS/OUTPUTS XX XX XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
| | XX | XX | No DSP module (slots M and U only) 8L | 8L | | | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | | | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | | | Standard 8CT with enhanced diagnostics 8R | 8R | | | Sensitive Ground 8CT with enhanced diagnostics | | 8Z * | | | Hi-Z 4CT (required for high-impedance fault detection element)
4A 4A 4A 4A 4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4B 4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 4D 4D 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 6B 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 6C 6C 6C 6C 8 Form-C outputs 6D 6D 6D 6D 6D 16 Contact inputs 6E 6E 6E 6E 6E 4 Form-C outputs, 8 contact inputs 6F 6F 6F 6F 6F 8 Fast Form-C outputs 6G 6G 6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6H 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 6K 6K 6K 6K 4 Form-C and 4 Fast Form-C outputs 6L 6L 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 6M 6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 6N 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6P 6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 6R 6R 6R 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs 6S 6S 6S 6S 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 6T 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6U 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 6V 6V 6V 6V 2 Form-A outputs, 1 Form-C output, 1 Form-A latching output , 8 contact inputs 5A 5A 5A 5A 5A 4 DCmA inputs, 4 DCmA outputs 5C 5C 5C 5C 5C 8 RTD inputs 5D 5D 5D 5D 5D 4 RTD inputs, 4 DCmA outputs 5E 5E 5E 5E 5E 4 RTD inputs, 4 DCmA inputs 5F 5F 5F 5F 5F 8 DCmA inputs
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser
2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-9
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-5: F60 order codes for reduced-size vertical units
BASE UNIT F60 | | | | | | | | | Base Unit CPU T | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | IEC 61850 04 | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | CyberSentry Lvl 1 and phasor measurement unit (PMU) A7 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | IEEE 1588 B1 | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | PRP and IEC 61850 C4 | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | PRP and PMU C7 | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | IEEE 1588 and PRP E1 | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | IEC 60870-5-103 J1 | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU Q7 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
(SFP with RJ45)
(PMU)
61850-90-5
IEC 61850
61850-90-5
2-10 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
MOUNT/ COATING FACEPLATE/ DISPLAY F | | | | | English display
POWER SUPPLY ENHANCED DIAGNOSTICS CT/VT DSP (8L, 8M, 8N, 8R require DSP to be enhanced diagnostic)
CONTACT INPUTS/OUTPUTS XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital and transducer input/output modules; slot R is used for inter-relay communications modules.
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
V | | | | | | Vertical (3/4 rack) - Standard B | | | | | | Vertical (3/4 rack) - With harsh environmental coating
K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display L | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | Enhanced front panel with Chinese display and user-programmable pushbutt ons W | | | | | Enhanced front panel with Turkish display Y | | | | | Enhanced front panel with Turkish d isplay and user-programmable pushbuttons I | | | | | Enhanced front panel with German display J | | | | | Enhan ced front panel with German display and user-programmable pushbuttons
H | | | | 125 / 250 V AC/DC power supply L | | | | 24 to 48 V (DC only) power supply
XX | XX | No DSP module (slots M and U only) 8L | 8L | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | Standard 8CT with enhanced diagnostics 8R | 8R | Sensitive Ground 8CT with enhanced diagnostics | | 8Z * | Hi-Z 4CT (required for high-impedance fault detection element)
4A 4A 4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 6C 6C 8 Form-C outputs 6D 6D 6D 16 Contact inputs 6E 6E 6E 4 Form-C outputs, 8 contact inputs 6F 6F 6F 8 Fast Form-C outputs 6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 6K 6K 4 Form-C and 4 Fast Form-C outputs 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 6R 6R 2 Form-A (no monit oring) and 2 Form-C outputs, 8 contact inputs 6S 6S 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 6V 6V 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8
5A 5A 5A 4 DCmA inputs, 4 DCmA outputs (only one 5A module is allowed) 5C 5C 5C 8 RTD inputs 5D 5D 5D 4 RTD inputs, 4 DCmA outputs (only one 5D module is allowed) 5E 5E 5E 4 RTD inputs, 4 DCmA inputs 5F 5F 5F 8 DCmA inputs
contact inputs
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser
2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-11
2
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION

2.3.2 Order codes with process bus modules

Table 2-6: F60 order codes for horizontal units with process bus
BASE UNIT F60 | | | | | | | | | | | Base Unit CPU T | | | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
U | | | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | | | IEC 61850 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | | | IEEE 1588 B1 | | | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | | | PRP and IEC 61850 C4 | | | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | | | PRP and PMU C7 | | | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | | | IEEE 1588 and PRP E1 | | | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | | | IEC 60870-5-103 J1 | | | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU
(SFP with RJ45)
(PMU)
61850-90-5
IEC 61850
2-12 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
MOUNT/ COATING FACEPLATE/ DISPLAY C | | | | | | | English display
POWER SUPPLY (redundant supply must be same type as main supply)
PROCESS BUS MODULE | 81 | | | | Eight-port digital process bus module CONTACT INPUTS/OUTPUTS XX XX XX XX XX No Module
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
Q7 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
H | | | | | | | | Horizontal (19” rack) - Standard A | | | | | | | | Horizontal (19” rack) - With harsh environmental coating
D | | | | | | | French display R | | | | | | | Russian display A | | | | | | | Chinese display P | | | | | | | English display with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French d isplay and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbutt ons W | | | | | | | Enhanced front panel with Turkish display Y | | | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons I | | | | | | | Enhanced front panel with German display J | | | | | | | Enhanced front panel with German display and user-programmable pushbu ttons
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
4A 4A | 4 Solid-State (no monitoring) MOSFET outputs 4B 4B | 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C | 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D | 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L | 14 Form-A (no monitoring) Latching outputs 67 67 | 8 Form-A (no monitoring) outputs 6A 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 6C | 8 Form-C outputs 6D 6D | 16 Contact inputs 6E 6E | 4 Form-C outputs, 8 contact inputs 6F 6F | 8 Fast Form-C outputs 6G 6G | 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6H | 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 6K | 4 Form-C and 4 Fast Form-C outputs 6L 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 6N | 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6P | 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs 6S 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 6T | 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6U | 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 6V | 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8
61850-90-5
contact inputs 2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser 2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-13
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-7: F60 order codes for reduced-size vertical units with process bus
BASE UNIT F60 | | | | | | | | | Base Unit CPU T | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | IEC 61850 04 | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | IEEE 1588 B1 | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | PRP and IEC 61850 C4 | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | PRP and PMU C7 | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | IEEE 1588 and PRP E1 | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | IEC 60870-5-103 J1 | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU Q7 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
(SFP with RJ45)
(PMU)
61850-90-5
IEC 61850
61850-90-5
2-14 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
MOUNT/ COATING FACEPLATE/ DISPLAY F | | | | | English display
POWER SUPPLY PROCESS BUS MODULE | 81 | | Eight-port digital process bus module CONTACT INPUTS/OUTPUTS XX XX XX No Modu le
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital input/output modules; slot R is used for inter-relay communications modules.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
V | | | | | | Vertical (3/4 rack) - Standard B | | | | | | Vertical (3/4 rack) - With harsh environmental coating
D | | | | | French display R | | | | | Russian display A | | | | | Chinese display K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display L | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons W | | | | | Enhanced front panel with Turkish display Y | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons I | | | | | Enhanced front panel with German display J | | | | | Enhanced front panel with German display and user-programmable pushbuttons
H | | | | 125 / 250 V AC/DC power supply L | | | | 24 to 48 V (DC only) power supply
4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 16 Contact inputs with Auto-Bu rnishing (maximum of three modules within a case) 4L 14 Form-A (no monitoring) Latching outputs 67 8 Form-A (no monitoring) outputs 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 8 Form-C outputs 6D 16 Contact inputs 6E 4 Form-C outputs, 8 contact inputs 6F 8 Fast Form-C outputs 6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 4 Form-C and 4 Fast Form-C outputs 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8
contact inputs 2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser 2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2

2.3.3 Replacement modules

Replacement modules can be ordered separately. When ordering a replacement CPU module or faceplate, provide the serial number of your existing unit.
Not all replacement modules apply to the F60 relay. The modules specified in the order codes for the F60 are available as replacement modules for the F60.
The order codes shown here are subject to change without notice. See the web page for the product for the latest options.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-15
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-8: UR order codes for replacement modules, horizontal units
POWER SUPPLY redundant supply only available in horizontal units and must be same type as main supply CPU | T | RS485 with 3 100Base-FX Ethernet , multimode, SFP with LC
FACEP LATE/D ISPL AY | 3C | Horizontal faceplate with keypad and English display
CONTACT INPUTS AND OUTPUTS | 4A | 4 Solid-State (no monitoring) MOSFET outputs
CT/VT MODULES | 8L | Standard 4CT/4VT with enhanced diagnostics (not available for the C30) | 8N | Standard 8CT with enhanced diagnostics
INTER-RELAY COMMUNICATIONS | 2A | C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode
TRANSDUCER INPUTS/OUTPUTS | 5A | 4 DCmA inputs, 4 DCmA outputs (only one 5A module is allowed)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
UR - ** - *
| SH A | 125 / 300 V AC/DC | SL H | 24 to 48 V (DC only)
| U | RS485 with 1 100Base-TX Ethernet, SFP RJ-45 + 2 100Base-FX Ethernet , multimode, SFP with LC | V | RS485 with 3 100Base-TX Ethernet, SFP with RJ-45
| 3D | Horizontal faceplate with keypad and French display | 3R | Horizontal faceplate with keypad and Russian display | 3A | Horizontal faceplate with keypad and Chinese display | 3P | Horizontal faceplate with keypad, user-programmable pushbuttons, and English display | 3G | Horizontal faceplate with keypad, user-programmable pushbuttons, and French display | 3S | Horizontal faceplate with keypad, user-programmable pushbuttons, and Russian display | 3B | Horizontal faceplate with keypad, user-programmable pushbuttons, and Chinese display | 3K | Enhanced front panel with English display | 3M | Enhanced front panel with French display | 3Q | En hanced front panel with Russian display | 3U | Enhanced front panel with Chinese display | 3L | Enhanced front panel with English display and user-programmable pushbuttons | 3N | Enhanced front panel with French display and user-programmable pushbuttons | 3T | Enhanced front panel with Russian display a nd user-programmable pushbuttons | 3V | Enhanced front panel with Chinese display and user-programmable pushbuttons | 3I | Enhanced front panel with German display | 3J | Enhanced front panel with German display and user-programmable pushbuttons
| 4B | 4 Solid-State (voltage with optional current) MOSFET outputs | 4C | 4 Solid-State (current with optional voltage) MOSFET outputs | 4D | 16 Contact inputs with Auto-Burnishing | 4L | 14 Form-A (no monitoring) Latching outputs | 67 | 8 Form-A (no monitoring) outputs | 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs | 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs |6C|8 Form-C outputs | 6D | 16 Contact inputs | 6E | 4 Form-C outputs, 8 contact inputs |6F|8 Fast Form-C outputs | 6G | 4 Form-A (voltage with optional current) outputs, 8 contact inputs | 6H | 6 Form-A (voltage with optional current) outputs, 4 contact inputs | 6K | 4 Form-C and 4 Fast Form-C outputs | 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs | 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs | 6N | 4 Form-A (current with optional voltage) outputs, 8 contact inputs | 6P | 6 Form-A (current with optional voltage) outputs, 4 contact inputs | 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs | 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs | 6T | 4 Form-A (no monitoring) outputs, 8 contact inputs | 6U | 6 Form-A (no monitoring) outputs, 4 contact inputs | 6V | 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8 contact inputs
| 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics | 8R | Sensitive Ground 8CT with enhanced diagnostics | 8V | Standard 8VT with enhanced diagnostics (only one module supported) | 8Z | Hi-Z 4CT
| 2B | C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode | 2E | Bi-phase, single channel | 2F | Bi-phase, dual channel | 2G | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel | 2H | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels | 2I | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser | 2J | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser | 72 | 1550 nm, single-mode, Laser, 1 Channel | 73 | 1550 nm, single-mode, Laser, 2 Channel | 74 | Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser | 75 | Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser | 76 | IEEE C37.94, 820 nm, multimode, LED, 1 Channel | 77 | IEEE C37.94, 820 nm, multimode, LED, 2 Channels | 7A | 820 nm, multimode, LED, 1 Channel | 7B | 1300 nm, multimode, LED, 1 Channel | 7C | 1300 nm, single-mode, ELED, 1 Channel | 7D | 1300 nm, single-mode, Laser, 1 Channel | 7E | Channel 1 - G.703; Channel 2 - 820 nm, multimode | 7F | Channel 1 - G.703; Channel 2 - 1300 nm, multimode | 7G | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED | 7H | 820 nm, multimode, LED, 2 Channels | 7I | 1300 nm, multimode, LED, 2 Channels | 7J | 1300 nm, single-mode, ELED, 2 Channels | 7K | 1300 nm, single-mode, Laser, 2 Channels | 7L | Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED | 7M | Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED | 7N | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED | 7P | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser | 7Q | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser | 7R | G.703, 1 Channel | 7S | G.703, 2 Channels | 7T | RS422, 1 Channel | 7W | RS422, 2 Channels
| 5C | 8 RTD inputs | 5D | 4 RTD inputs, 4 DCmA outputs (only one 5D module is allowed) | 5E | 4 DCmA inputs, 4 RTD inputs | 5F | 8 DCmA inputs
2-16 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
Loading...