GE F60 Instruction Manual

GE
LISTED
52TL
IND.CONT. EQ.
E83849
Grid Solutions
F60
Feeder Protection System
Instruction Manual
Product version: 7.41x
GE publication code: 1601-0093-AE1 (GEK-130980)
1601-0093-AE1
Copyright © 2017 GE Multilin Inc. All rights reserved. F60 Feeder Protection System Instruction Manual for version 7.41x. F60, FlexLogic, FlexElement, FlexCurve, FlexAnalog, FlexInteger, FlexState, EnerVista,
CyberSentry, HardFiber, Multilin, and GE Multilin are trademarks or registered trademarks of GE Multilin Inc.
The contents of this manual are the property of GE Multilin Inc. This documentation is furnished on license and may not be reproduced in whole or in part without the permission of GE Multilin. The content of this manual is for informational use only and is subject to change without notice.
Part number: 1601-0093-AE1 (January 2017)
F60 Feeder Protection System
Table of contents
1 INTRODUCTION 1.1 Safety symbols and definitions.....................................................................1-1
1.1.1 General cautions and warnings ....................................................................................1-1
1.2 For further assistance .................................................................................... 1-2
2PRODUCT
DESCRIPTION
2.1 Product description......................................................................................... 2-1
2.1.1 Overview................................................................................................................................... 2-1
2.2 Security.............................................................................................................. 2-3
2.3 Order codes ...................................................................................................... 2-7
2.3.1 Order codes with enhanced CT/VT modules........................................................... 2-7
2.3.2 Order codes with process bus modules ..................................................................2-12
2.3.3 Replacement modules .....................................................................................................2-15
2.4 Signal processing...........................................................................................2-18
2.4.1 UR signal processing ........................................................................................................2-18
2.5 Specifications ................................................................................................. 2-20
2.5.1 Protection elements ..........................................................................................................2-20
2.5.2 User-programmable elements ....................................................................................2-26
2.5.3 Monitoring..............................................................................................................................2-27
2.5.4 Metering..................................................................................................................................2-28
2.5.5 Inputs .......................................................................................................................................2-29
2.5.6 Power supply........................................................................................................................2-31
2.5.7 Outputs....................................................................................................................................2-32
2.5.8 Communication protocols..............................................................................................2-34
2.5.9 Inter-relay communications..........................................................................................2-35
2.5.10 CyberSentry security.........................................................................................................2-36
2.5.11 Environmental......................................................................................................................2-36
2.5.12 Type tests...............................................................................................................................2-37
2.5.13 Production tests..................................................................................................................2-37
2.5.14 Approvals ...............................................................................................................................2-38
2.5.15 Maintenance.........................................................................................................................2-38
3 INSTALLATION 3.1 Unpack and inspect......................................................................................... 3-1
3.2 Panel cutouts.................................................................................................... 3-2
3.2.1 Horizontal units ..................................................................................................................... 3-2
3.2.2 Vertical units........................................................................................................................... 3-3
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL iii
TABLE OF CONTENTS
3.2.3 Rear terminal layout............................................................................................................3-8
3.3 Wiring ................................................................................................................3-9
3.3.1 Typical wiring..........................................................................................................................3-9
3.3.2 Dielectric strength ............................................................................................................. 3-10
3.3.3 Control power......................................................................................................................3-11
3.3.4 CT/VT modules ....................................................................................................................3-12
3.3.5 Process bus modules ....................................................................................................... 3-15
3.3.6 Contact inputs and outputs ..........................................................................................3-16
3.3.7 Transducer inputs and outputs...................................................................................3-23
3.3.8 RS232 faceplate port........................................................................................................ 3-25
3.3.9 CPU communication ports ............................................................................................ 3-26
3.3.10 IRIG-B....................................................................................................................................... 3-28
3.4 Direct input and output communications ................................................3-29
3.4.1 Description............................................................................................................................ 3-29
3.4.2 Fiber: LED and ELED transmitters...............................................................................3-32
3.4.3 Fiber laser transmitters...................................................................................................3-32
3.4.4 G.703 interface....................................................................................................................3-33
3.4.5 RS422 interface...................................................................................................................3-37
3.4.6 RS422 and fiber interface ..............................................................................................3-39
3.4.7 G.703 and fiber interface................................................................................................ 3-40
3.4.8 IEEE C37.94 interface .......................................................................................................3-40
3.4.9 C37.94SM interface...........................................................................................................3-43
3.5 Activate relay .................................................................................................3-46
3.6 Install software ..............................................................................................3-47
3.6.1 EnerVista communication overview ......................................................................... 3-47
3.6.2 System requirements.......................................................................................................3-48
3.6.3 Install software.................................................................................................................... 3-49
3.7 Add device to software.................................................................................3-50
3.7.1 Set IP address in UR..........................................................................................................3-50
3.7.2 Configure serial connection.......................................................................................... 3-56
3.7.3 Configure Ethernet connection ...................................................................................3-57
3.7.4 Configure modem connection..................................................................................... 3-59
3.7.5 Automatic discovery of UR devices...........................................................................3-59
3.8 Connect to the F60 ........................................................................................3-60
3.8.1 Connect to the F60 in EnerVista..................................................................................3-60
3.8.2 Use Quick Connect via the front panel RS232 port............................................3-61
3.8.3 Use Quick Connect via a rear Ethernet port..........................................................3-62
3.9 Set up CyberSentry and change default password.................................3-62
3.10 Import settings...............................................................................................3-63
4 INTERFACES 4.1 EnerVista software interface......................................................................... 4-1
4.1.1 Introduction .............................................................................................................................4-1
4.1.2 Settings files ............................................................................................................................4-1
4.1.3 Event viewing..........................................................................................................................4-2
4.1.4 File support ..............................................................................................................................4-3
4.1.5 EnerVista main window .....................................................................................................4-3
4.1.6 Protection summary window ..........................................................................................4-4
4.1.7 Settings templates................................................................................................................4-5
4.1.8 Secure and lock FlexLogic equations ..........................................................................4-9
4.1.9 Settings file traceability................................................................................................... 4-12
4.2 Front panel interface ....................................................................................4-15
4.2.1 Front panel display............................................................................................................ 4-15
4.2.2 Front panel keypad ........................................................................................................... 4-16
4.2.3 Menu navigation ................................................................................................................4-16
iv F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TABLE OF CONTENTS
4.2.4 Menu hierarchy ...................................................................................................................4-16
4.2.5 Changing settings ..............................................................................................................4-17
4.2.6 Faceplate................................................................................................................................4-19
4.2.7 LED indicators ......................................................................................................................4-20
4.2.8 Custom LED labeling.........................................................................................................4-24
4.2.9 Breaker control....................................................................................................................4-29
4.2.10 Change passwords............................................................................................................4-30
4.2.11 Invalid password entry ....................................................................................................4-31
4.3 Logic diagrams...............................................................................................4-32
4.4 FlexLogic design and monitoring using Engineer....................................4-33
4.4.1 Design logic...........................................................................................................................4-35
4.4.2 Send file to and from device .........................................................................................4-45
4.4.3 Monitor logic.........................................................................................................................4-46
4.4.4 View front panel and print labels................................................................................4-47
4.4.5 Generate connectivity report........................................................................................4-48
4.4.6 Preferences ...........................................................................................................................4-48
4.4.7 Toolbars ..................................................................................................................................4-52
5 SETTINGS 5.1 Settings menu .................................................................................................. 5-1
5.2 Overview ...........................................................................................................5-4
5.2.1 Introduction to elements .................................................................................................. 5-4
5.2.2 Introduction to AC sources .............................................................................................. 5-6
5.3 Product setup................................................................................................... 5-7
5.3.1 Security ..................................................................................................................................... 5-7
5.3.2 Display properties ..............................................................................................................5-26
5.3.3 Clear relay records.............................................................................................................5-28
5.3.4 Communications ................................................................................................................5-29
5.3.5 Modbus user map ..............................................................................................................5-95
5.3.6 Real-time clock....................................................................................................................5-95
5.3.7 Fault reports .........................................................................................................................5-99
5.3.8 Oscillography..................................................................................................................... 5-101
5.3.9 Data logger ........................................................................................................................5-103
5.3.10 Demand ...............................................................................................................................5-105
5.3.11 User-programmable LEDs ..........................................................................................5-106
5.3.12 User-programmable self-tests .................................................................................5-110
5.3.13 Control pushbuttons......................................................................................................5-110
5.3.14 User-programmable pushbuttons..........................................................................5-112
5.3.15 Flex state parameters ...................................................................................................5-117
5.3.16 User-definable displays................................................................................................ 5-118
5.3.17 Direct inputs and outputs............................................................................................5-120
5.3.18 Teleprotection...................................................................................................................5-126
5.3.19 Installation..........................................................................................................................5-127
5.4 Remote resources........................................................................................5-127
5.4.1 Remote resources configuration .............................................................................5-127
5.5 System setup................................................................................................5-129
5.5.1 AC inputs .............................................................................................................................5-129
5.5.2 Power system....................................................................................................................5-130
5.5.3 Signal sources...................................................................................................................5-131
5.5.4 Breakers...............................................................................................................................5-134
5.5.5 Disconnect switches ......................................................................................................5-138
5.5.6 FlexCurves........................................................................................................................... 5-141
5.5.7 Phasor Measurement Unit ..........................................................................................5-148
5.6 FlexLogic........................................................................................................5-168
5.6.1 FlexLogic operands ........................................................................................................ 5-168
5.6.2 FlexLogic rules ..................................................................................................................5-181
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL v
TABLE OF CONTENTS
5.6.3 FlexLogic evaluation...................................................................................................... 5-181
5.6.4 FlexLogic example..........................................................................................................5-182
5.6.5 FlexLogic equation editor............................................................................................ 5-187
5.6.6 FlexLogic timers...............................................................................................................5-187
5.6.7 FlexElements .....................................................................................................................5-187
5.6.8 Non-volatile latches.......................................................................................................5-191
5.7 Grouped elements .......................................................................................5-192
5.7.1 Overview ............................................................................................................................. 5-192
5.7.2 Setting group 1................................................................................................................. 5-192
5.7.3 Load encroachment ...................................................................................................... 5-193
5.7.4 Phase current ................................................................................................................... 5-195
5.7.5 Neutral current................................................................................................................. 5-207
5.7.6 Wattmetric ground fault.............................................................................................. 5-215
5.7.7 Ground current ................................................................................................................ 5-219
5.7.8 Negative sequence current........................................................................................ 5-226
5.7.9 Breaker failure (ANSI 50BF)......................................................................................... 5-232
5.7.10 Voltage elements ............................................................................................................ 5-241
5.7.11 Sensitive directional power (ANSI 32) .................................................................... 5-248
5.8 Control elements .........................................................................................5-251
5.8.1 Overview ............................................................................................................................. 5-251
5.8.2 Trip bus ................................................................................................................................ 5-251
5.8.3 Setting groups .................................................................................................................. 5-253
5.8.4 Selector switch................................................................................................................. 5-254
5.8.5 Underfrequency (ANSI 81U)........................................................................................ 5-261
5.8.6 Overfrequency (ANSI 81O) .......................................................................................... 5-262
5.8.7 Frequency rate of change (ANSI 81R)....................................................................5-263
5.8.8 Synchrocheck (ANSI 25) ............................................................................................... 5-265
5.8.9 Autoreclose (ANSI 79).................................................................................................... 5-270
5.8.10 Digital elements............................................................................................................... 5-276
5.8.11 Digital counters................................................................................................................5-279
5.9 Monitoring elements...................................................................................5-281
5.9.1 Cold load pickup.............................................................................................................. 5-309
5.9.2 Pilot schemes.................................................................................................................... 5-310
5.10 Inputs/outputs .............................................................................................5-315
5.10.1 Contact inputs.................................................................................................................. 5-315
5.10.2 Virtual inputs ..................................................................................................................... 5-317
5.10.3 Contact outputs............................................................................................................... 5-318
5.10.4 Virtual outputs.................................................................................................................. 5-322
5.10.5 Resetting .............................................................................................................................5-322
5.10.6 Direct inputs and outputs ........................................................................................... 5-322
5.10.7 Teleprotection................................................................................................................... 5-326
5.11 Transducer inputs/outputs........................................................................5-328
5.11.1 DCmA inputs...................................................................................................................... 5-328
5.11.2 RTD inputs .......................................................................................................................... 5-329
5.11.3 DCmA outputs .................................................................................................................. 5-330
5.12 Testing ...........................................................................................................5-334
5.12.1 Test mode function ........................................................................................................5-334
5.12.2 Test mode forcing........................................................................................................... 5-334
5.12.3 Phasor Measurement Unit test values.................................................................. 5-335
5.12.4 Force contact inputs ..................................................................................................... 5-336
5.12.5 Force contact outputs .................................................................................................. 5-336
6 ACTUAL VALUES 6.1 Actual Values menu.........................................................................................6-1
6.2 Front panel........................................................................................................ 6-3
vi F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TABLE OF CONTENTS
6.3 Status.................................................................................................................6-4
6.3.1 Contact inputs ....................................................................................................................... 6-4
6.3.2 Virtual inputs........................................................................................................................... 6-4
6.3.3 RxGOOSE boolean inputs.................................................................................................. 6-5
6.3.4 RxGOOSE DPS inputs ..........................................................................................................6-5
6.3.5 Teleprotection inputs.......................................................................................................... 6-5
6.3.6 Contact outputs ....................................................................................................................6-5
6.3.7 Virtual outputs ....................................................................................................................... 6-6
6.3.8 RxGOOSE status.................................................................................................................... 6-6
6.3.9 RxGOOSE statistics ..............................................................................................................6-6
6.3.10 Autoreclose ............................................................................................................................. 6-7
6.3.11 Digital counters ..................................................................................................................... 6-7
6.3.12 Selector switches.................................................................................................................. 6-7
6.3.13 Flex States................................................................................................................................ 6-7
6.3.14 Ethernet .................................................................................................................................... 6-8
6.3.15 Real time clock synchronizing........................................................................................ 6-8
6.3.16 Hi-Z status ............................................................................................................................... 6-9
6.3.17 Direct inputs............................................................................................................................6-9
6.3.18 Direct devices status ..........................................................................................................6-9
6.3.19 EGD protocol status ..........................................................................................................6-10
6.3.20 Teleprotection channel tests ........................................................................................6-10
6.3.21 Incipient fault detector ....................................................................................................6-11
6.3.22 Remaining connection status.......................................................................................6-11
6.3.23 Parallel Redundancy Protocol (PRP)...........................................................................6-11
6.3.24 TxGOOSE status ..................................................................................................................6-12
6.4 Metering .......................................................................................................... 6-13
6.4.1 Metering conventions.......................................................................................................6-13
6.4.2 Sources....................................................................................................................................6-17
6.4.3 Sensitive directional power ...........................................................................................6-23
6.4.4 Synchrocheck.......................................................................................................................6-23
6.4.5 Tracking frequency............................................................................................................6-24
6.4.6 Frequency rate of change..............................................................................................6-24
6.4.7 FlexElements.........................................................................................................................6-24
6.4.8 RxGOOSE analogs ..............................................................................................................6-25
6.4.9 Wattmetric ground fault .................................................................................................6-25
6.4.10 Phasor Measurement Unit .............................................................................................6-25
6.4.11 PMU aggregator..................................................................................................................6-26
6.4.12 Restricted ground fault....................................................................................................6-26
6.4.13 Transducer inputs and outputs ...................................................................................6-26
6.5 Records............................................................................................................6-27
6.5.1 Fault reports .........................................................................................................................6-27
6.5.2 Event records .......................................................................................................................6-28
6.5.3 Oscillography........................................................................................................................6-29
6.5.4 Data logger ...........................................................................................................................6-29
6.5.5 Phasor Measurement Unit records............................................................................6-29
6.5.6 Breaker maintenance.......................................................................................................6-30
6.5.7 Hi-Z records ..........................................................................................................................6-30
6.6 Product information......................................................................................6-31
6.6.1 Model information..............................................................................................................6-31
6.6.2 Firmware revisions ............................................................................................................6-32
7 COMMANDS AND
TARGETS
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL vii
7.1 Commands menu ............................................................................................7-1
7.1.1 Virtual inputs........................................................................................................................... 7-2
7.1.2 Clear records ..........................................................................................................................7-2
7.1.3 Set date and time................................................................................................................. 7-3
TABLE OF CONTENTS
7.1.4 Relay maintenance ..............................................................................................................7-3
7.1.5 Phasor Measurement Unit one-shot ...........................................................................7-4
7.1.6 Security......................................................................................................................................7-6
7.2 Targets menu ................................................................................................... 7-6
7.2.1 Target messages...................................................................................................................7-7
7.2.2 Relay self-tests .......................................................................................................................7-7
8 COMMISSIONING 8.1 Testing ...............................................................................................................8-1
8.1.1 Testing underfrequency and overfrequency elements.......................................8-1
9 THEORY OF
OPERATION
9.1 High-impedance (Hi-Z) fault detection ........................................................9-1
9.1.1 Description...............................................................................................................................9-1
9.1.2 Energy algorithm...................................................................................................................9-2
9.1.3 Randomness algorithm......................................................................................................9-2
9.1.4 Expert Arc Detector algorithm........................................................................................9-2
9.1.5 Spectral Analysis algorithm .............................................................................................9-3
9.1.6 Load Event Detector algorithm ......................................................................................9-3
9.1.7 Load Analysis algorithm ....................................................................................................9-3
9.1.8 Load Extraction algorithm................................................................................................9-3
9.1.9 Arc Burst Pattern Analysis algorithm...........................................................................9-4
9.1.10 Arcing Suspected algorithm ............................................................................................9-4
9.1.11 Overcurrent disturbance monitoring...........................................................................9-4
9.1.12 Hi-Z Even Harmonic Restraint algorithm...................................................................9-4
9.1.13 Hi-Z Voltage Supervision algorithm .............................................................................9-4
9.2 Fault locator ..................................................................................................... 9-4
9.2.1 Fault type determination...................................................................................................9-4
10 MAINTENANCE 10.1 Monitoring.......................................................................................................10-1
10.1.1 Devices with Site Targets ...............................................................................................10-1
10.1.2 Data with Modbus Analyzer..........................................................................................10-1
10.2 General maintenance ...................................................................................10-3
10.2.1 In-service maintenance..................................................................................................10-3
10.2.2 Out-of-service maintenance ........................................................................................10-3
10.2.3 Unscheduled maintenance (system interruption) ..............................................10-3
10.3 Retrieve files ...................................................................................................10-3
10.3.1 CyberSentry security event files..................................................................................10-4
10.4 Compare settings ..........................................................................................10-5
10.4.1 Compare against defaults .............................................................................................10-5
10.4.2 Compare two devices ......................................................................................................10-5
10.5 Back up and restore settings.......................................................................10-6
10.5.1 Back up settings ................................................................................................................. 10-6
10.5.2 Restore settings.................................................................................................................. 10-8
10.6 Upgrade software........................................................................................10-10
10.7 Upgrade firmware .......................................................................................10-11
10.8 Replace module............................................................................................10-12
10.9 Battery...........................................................................................................10-14
10.9.1 Replace battery for SH/SL power supply ............................................................. 10-14
10.9.2 Dispose of battery ..........................................................................................................10-15
10.10 Clear files and data after uninstall...........................................................10-18
10.11 Repairs...........................................................................................................10-19
10.12 Storage ..........................................................................................................10-19
10.13 Disposal.........................................................................................................10-20
viii F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
TABLE OF CONTENTS
AFLEXANALOG
A.1 FlexAnalog items .............................................................................................A-1
OPERANDS
B RADIUS SERVER
B.1 RADIUS server configuration .........................................................................B-1
CONFIGURATION
C COMMAND LINE
C.1 Command line interface .................................................................................C-1
INTERFACE
D MISCELLANEOUS D.1 Warranty ...........................................................................................................D-1
D.2 Revision history ...............................................................................................D-1
ABBREVIATIONS
INDEX
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL ix
TABLE OF CONTENTS
x F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
F60 Feeder Protection System
Chapter 1: Introduction

Introduction

This chapter outlines safety and technical support information.

1.1 Safety symbols and definitions

Before attempting to install or use the device, review all safety indicators in this document to help prevent injury, equipment damage, or downtime.
The following safety and equipment symbols are used in this document.
Indicates a hazardous situation which, if not avoided, will result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in minor or moderate injury.
Indicates practices not related to personal injury.

1.1.1 General cautions and warnings

The following general safety precautions and warnings apply.
Ensure that all connections to the product are correct so as to avoid accidental risk of shock and/or fire, for example such as can arise from high voltage connected to low voltage terminals.
Follow the requirements of this manual, including adequate wiring size and type, terminal torque settings, voltage, current magnitudes applied, and adequate isolation/clearance in external wiring from high to low voltage circuits.
Use the device only for its intended purpose and application. Ensure that all ground paths are uncompromised for safety purposes during device operation and service. Ensure that the control power applied to the device, the AC current, and voltage input match the ratings specified on
the relay nameplate. Do not apply current or voltage in excess of the specified limits.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 1-1
1
FOR FURTHER ASSISTANCE CHAPTER 1: INTRODUCTION
Only qualified personnel are to operate the device. Such personnel must be thoroughly familiar with all safety cautions and warnings in this manual and with applicable country, regional, utility, and plant safety regulations.
Hazardous voltages can exist in the power supply and at the device connection to current transformers, voltage transformers, control, and test circuit terminals. Make sure all sources of such voltages are isolated prior to attempting work on the device.
Hazardous voltages can exist when opening the secondary circuits of live current transformers. Make sure that current transformer secondary circuits are shorted out before making or removing any connection to the current transformer (CT) input terminals of the device.
For tests with secondary test equipment, ensure that no other sources of voltages or currents are connected to such equipment and that trip and close commands to the circuit breakers or other switching apparatus are isolated, unless this is required by the test procedure and is specified by appropriate utility/plant procedure.
When the device is used to control primary equipment, such as circuit breakers, isolators, and other switching apparatus, all control circuits from the device to the primary equipment must be isolated while personnel are working on or around this primary equipment to prevent any inadvertent command from this device.
Use an external disconnect to isolate the mains voltage supply. Personal safety can be affected if the product is physically modified by the end user. Modifications to the product
outside of recommended wiring configuration, hardware, or programming boundaries is not recommended end-use practice. Product disassembly and repairs are not permitted. All service needs to be conducted by the factory.
LED transmitters are classified as IEC 60825-1 Accessible Emission Limit (AEL) Class 1M. Class 1M devices are considered safe to the unaided eye. Do not view directly with optical instruments.
This product is rated to Class A emissions levels and is to be used in Utility, Substation Industrial environments. Not to be used near electronic devices rated for Class B levels.

1.2 For further assistance

For product support, contact the information and call center as follows:
GE Grid Solutions 650 Markland Street Markham, Ontario Canada L6C 0M1 Worldwide telephone: +1 905 927 7070 Europe/Middle East/Africa telephone: +34 94 485 88 54 North America toll-free: 1 800 547 8629 Fax: +1 905 927 5098 Worldwide e-mail: multilin.tech@ge.com Europe e-mail: multilin.tech.euro@ge.com Website: http://www.gegridsolutions.com/multilin
When contacting GE by e-mail, optionally include a device information file, which is generated in the EnerVista software by clicking the Service Report button.
1-2 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 1: INTRODUCTION FOR FURTHER ASSISTANCE
Figure 1-1: Generate service report
1
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 1-3
1
FOR FURTHER ASSISTANCE CHAPTER 1: INTRODUCTION
1-4 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
F60 Feeder Protection System
Chapter 2: Product description

Product description

This chapter outlines the product, order codes, and specifications.

2.1 Product description

2.1.1 Overview

The F60 Feeder Protection System is part of the Universal Relay (UR) series of products. It is a microprocessor-based relay for feeder protection.
Overvoltage and undervoltage protection, overfrequency and underfrequency protection, breaker failure protection, directional current supervision, fault diagnostics, remote terminal unit (RTU), and programmable logic functions are provided. This relay also provides phase, neutral, ground and negative sequence, instantaneous and time overcurrent protection. The time overcurrent function provides multiple curve shapes or FlexCurves™ for optimum co-ordination. Automatic reclosing, synchrocheck, and line fault locator features are also provided. When equipped with a type 8Z current transformer/voltage transformer (CT/VT) module, an element for detecting high impedance faults is provided.
Voltage, current, and power metering are built in as standard features. Current parameters are available as total waveform root mean square (RMS) magnitude, or as fundamental frequency only RMS magnitude and angle (phasor).
Diagnostic features include an event recorder that stores 1024 time-tagged events. The internal clock used for time­tagging can be synchronized with an IRIG-B signal, using the Simple Network Time Protocol (SNTP) over the Ethernet port, or using the Precision Time Protocol (PTP). This precise time stamping allows the sequence of events to be determined throughout the system. Events can also be programmed (via FlexLogic™ equations) to trigger oscillography data capture that can be set to record the measured parameters before and after the event for viewing on a computer. These tools significantly reduce troubleshooting time and simplify report generation in the event of a system fault.
Several options are available for communication. A faceplate RS232 port can be used to connect to a computer to program settings and monitor actual values. The rear RS485 port allows independent access by operating and engineering staff. It can be connected to system computers with baud rates up to 115.2 kbps. All serial ports use the Modbus RTU protocol. The IEC 60870-5-103 protocol is supported on the RS485 interface. IEC 60870-5-103, DNP, and Modbus cannot be enabled simultaneously on this interface. Also only one of the DNP, IEC 60870-5-103, and IEC 60870-5-104 protocols can be enabled at any time on the relay. When the IEC 60870-5-103 protocol is chosen, the RS485 port has a fixed even parity and the baud rate can be either 9.6 kbps or 19.2 kbps. The 100Base-FX or 100Base-TX Ethernet interface provides fast, reliable communications in noisy environments. The Ethernet port supports IEC 61850, IEC 61850-90-5, Modbus/TCP, TFTP, and PTP (according to IEEE Std. 1588-2008 or IEC 61588), and it allows access to the relay via any standard web browser (F60 web pages). The IEC 60870-5-104 protocol is supported on the Ethernet port. The Ethernet port also supports the Parallel Redundancy Protocol (PRP) of IEC 62439-3 (clause 4, 2012) when purchased as an option.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-1
PRODUCT DESCRIPTION CHAPTER 2: PRODUCT DESCRIPTION
Secure Routable GOOSE (R-GOOSE) is supported with software options. Settings and actual values can be accessed from the front panel or EnerVista software. The F60 uses flash memory technology that allows field upgrading as new features are added. Firmware and software are
upgradable. The following single-line diagram illustrates the relay functionality using American National Standards Institute (ANSI)
device numbers.
2
Table 2-1: ANSI device numbers and functions supported
Device number Function Device number Function
25 Synchrocheck 51_2 Negative-sequence time overcurrent 27P Phase undervoltage 52 AC circuit breaker 27X Auxiliary undervoltage 59N Neutral overvoltage 32 Sensitive directional power 59P Phase overvoltage 32N Wattmetric zero-sequence directional 59X Auxiliary overvoltage 49 Thermal overload protection 59_2 Negative-sequence overvoltage 50BF/50NBF Breaker failure 67N Neutral directional overcurrent 50DD Disturbance detector 67P Phase directional overcurrent 50G Ground instantaneous overcurrent 67_2 Negative-sequence directional overcurrent 50N Neutral instantaneous overcurrent 79 Automatic recloser 50P Phase instantaneous overcurrent 81O Overfrequency 50_2 Negative-sequence instantaneous overcurrent 81R Rate of change frequency 51G Ground time overcurrent 81U Underfrequency 51N Neutral time overcurrent 87RGF Restricted ground fault 51P Phase time overcurrent
Figure 2-1: Single-line diagram
2-2 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SECURITY
Table 2-2: Other device functions
Function Function Function
Breaker arcing current (I Breaker control Event recorder Setting groups (6) Breaker flashover Fault detector and fault report Synchrophasor (PMU) Breaker restrike Fault locator Thermal overload protection Broken conductor detection FlexElements™ (8) Time synchronization over IRIG-B or IEEE
Cold load pickup FlexLogic equations Time synchronization over SNTP Contact inputs (up to 96) High impedance fault detection (Hi-Z) Transducer inputs and outputs Contact outputs (up to 64) IEC 60870-5-103 communications User-definable displays Control pushbuttons IEC 61850 communications User-programmable LEDs CT failure detector IEC 62351-9 data and communications
CyberSentry™ security Incipient cable fault detection User-programmable self-tests Data logger Load encroachment Virtual inputs (64) Demand Metering: current, voltage, power, PF,
Digital counters (8) Modbus user map VT fuse failure Digital elements (48) Non-volatile latches Direct inputs and outputs (32) Non-volatile selector switch Disconnect switches Oscillography
2
t) Ethernet Global Data Pilot schemes
1588
security
energy, frequency, harmonics, THD
User-programmable pushbuttons
Virtual outputs (96)
2

2.2 Security

The following security features are available:
Password security — Basic security present by default
EnerVista security — Role-based access to various EnerVista software screens and configuration elements. The feature is present by default in the EnerVista software.
CyberSentry security — Advanced security available using a software option. When purchased, the option is automatically enabled, and the default Password security and EnerVista security are disabled.

2.2.0.1 EnerVista security

The EnerVista security management system is a role-based access control (RBAC) system that allows an administrator to manage the privileges of multiple users. This allows for access control of UR devices by multiple personnel within a substation and conforms to the principles of RBAC as defined in ANSI INCITS 359-2004. The EnerVista security management system is disabled by default to allow the administrator direct access to the EnerVista software after installation. It is recommended that security be enabled before placing the device in service.
Basic password or enhanced CyberSentry security applies, depending on purchase.

2.2.0.2 Password security

Password security is a basic security feature present by default. Two levels of password security are provided: command and setting. Use of a password for each level controls whether
users can enter commands and/or change settings. The F60 supports password entry from a local or remote connection. Local access is defined as any access to settings or
commands via the faceplate interface. This includes both keypad entry and the through the faceplate RS232 port. Remote access is defined as any access to settings or commands via any rear communications port. This includes both Ethernet and RS485 connections. Any changes to the local or remote passwords enables this functionality.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-3
2
SECURITY CHAPTER 2: PRODUCT DESCRIPTION
When entering a settings or command password via EnerVista or any serial interface, the user must enter the corresponding connection password. If the connection is to the back of the F60, the remote password must be used. If the connection is to the RS232 port of the faceplate, the local password applies.
Password access events are logged in the Event Recorder.

2.2.0.3 CyberSentry security

CyberSentry embedded security is available using a software option (Level 1) that provide advanced security services. When the option is purchased, the basic password security is disabled automatically.
CyberSentry provides security through the following features:
An Authentication, Authorization, Accounting (AAA) Remote Authentication Dial-In User Service (RADIUS) client that is centrally managed, enables user attribution, provides accounting of all user activities, and uses secure standards­based strong cryptography for authentication and credential protection
A Role-Based Access Control (RBAC) system that provides a permission model that allows access to UR device operations and configurations based on specific roles and individual user accounts configured on the AAA server (that is, Administrator, Supervisor, Engineer, Operator, Observer roles)
Security event reporting through the Syslog protocol for supporting Security Information Event Management (SIEM) systems for centralized cybersecurity monitoring
Strong encryption of all access and configuration network messages between the EnerVista software and UR devices using the Secure Shell (SSH) protocol, the Advanced Encryption Standard (AES), and 128-bit keys in Galois Counter Mode (GCM) as specified in the U.S. National Security Agency Suite B extension for SSH and approved by the National Institute of Standards and Technology (NIST) FIPS-140-2 standards for cryptographic systems
CyberSentry user roles
CyberSentry user roles (Administrator, Engineer, Operator, Supervisor, Observer) limit the levels of access to various UR device functions. This means that the EnerVista software allows for access to functionality based on the user’s logged in role.
Example: Administrative functions can be segmented away from common operator functions, or engineering type access, all of which are defined by separate roles (see figure) so that access of UR devices by multiple personnel within a substation is allowed.
Figure 2-2: CyberSentry user roles
The table lists user roles and their corresponding capabilities.
Table 2-3: Permissions by user role for CyberSentry
Roles Administrator Engineer Operator Supervisor Observer
Complete access Complete access
except for CyberSentry Security
Device Definition R R R R R
2-4 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
Command menu
Authorizes writing
Default role
CHAPTER 2: PRODUCT DESCRIPTION SECURITY
Roles Administrator Engineer Operator Supervisor Observer
Settings |---------- Product Setup
|--------------- Security
(CyberSentry)
|--------------- Supervisory See table notes R R See table
|--------------- Display Properties RW RW R R R |--------------- Clear Relay Records
(settings) |--------------- Communications RW RW R R R |--------------- Modbus User Map RW RW R R R |--------------- Real Time Clock RW RW R R R |--------------- Oscillography RW RW R R R |--------------- Data Logger RW RW R R R |--------------- Demand RW RW R R R |--------------- User-Programmable
LEDs |--------------- User-Programmable
Self Tests |--------------- Control Pushbuttons RW RW R R R |--------------- User-Programmable
Pushbuttons |--------------- Flex state
Parameters |--------------- User-Definable
Displays |--------------- Direct I/O RW RW R R R |--------------- Teleprotection RW RW R R R |--------------- Installation RW RW R R R
|---------- System Setup RW RW R R R |---------- FlexLogic RW RW R R R |---------- Grouped Elements RW RW R R R |---------- Control Elements RW RW R R R |---------- Inputs / Outputs RW RW R R R
|--------------- Contact Inputs RW RW R R R |--------------- Contact Input
threshold |--------------- Virtual Inputs RW RW R R R |--------------- Contact Outputs RW RW R R R |--------------- Virtual Outputs RW RW R R R |--------------- Resetting RW RW R R R |--------------- Direct Inputs RW RW R R R |--------------- Direct Outputs RW RW R R R |--------------- Teleprotection RW RW R R R |--------------- Direct Analogs RW RW R R R |--------------- Direct Integers RW RW R R R
|---------- Transducer I/O RW RW R R R |---------- Testing RW RW R R R |---------- Front Panel Labels Designer NA NA NA NA NA
RW R R R R
R
notes
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
RW RW R R R
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-5
2
SECURITY CHAPTER 2: PRODUCT DESCRIPTION
Roles Administrator Engineer Operator Supervisor Observer
|---------- Protection Summary NA NA NA NA NA Commands RW RW RW R R |---------- Virtual Inputs RW RW RW R R |---------- Clear Records RW RW RW R R |---------- Set Date and Time RW RW RW R R User Displays R R R R R Targets R R R R R Actual Values R R R R R |---------- Front panel labels designer R R R R R |---------- Status R R R R R |---------- Metering R R R R R |---------- Transducer I/O R R R R R |---------- Records R R R R R |---------- Product Info R R R R R Maintenance RW RW R R R |---------- Modbus Analyzer NA NA NA NA NA |---------- Change front panel RW RW RW R R |---------- Update firmware Yes No No No No |---------- Retrieve file Yes No No No No
Table Notes: RW = read and write access R = read access Supervisor = RW (default), Administrator = R (default), Administrator = RW (only if Supervisor role is disabled) NA = the permission is not enforced by CyberSentry security
CyberSentry user authentication
The following types of authentication are supported by CyberSentry to access the UR device:
Device Authentication (local UR device authenticates)
Server Authentication (RADIUS server authenticates) The EnerVista software allows access to functionality that is determined by the user role, which comes either from the local
UR device or the RADIUS server. The EnerVista software has a device authentication option on the login screen for accessing the UR device. When the
"Device" button is selected, the UR uses its local authentication database and not the RADIUS server to authenticate the user. In this case, it uses its built-in roles (Administrator, Engineer, Supervisor, Observer, Operator, or Administrator and Supervisor when Device Authentication is disabled) as login names and the associated passwords are stored on the UR device. As such, when using the local accounts, access is not user-attributable.
In cases where user-attributable access is required especially to facilitate auditable processes for compliance reasons, use RADIUS authentication only.
When the "Server" Authentication Type option is selected, the UR uses the RADIUS server and not its local authentication database to authenticate the user.
No password or security information is displayed in plain text by the EnerVista software or UR device, nor is such information ever transmitted without cryptographic protection.
CyberSentry server authentication
The UR has been designed to direct automatically the authentication requests based on user names. In this respect, local account names on the UR are considered as reserved and not used on a RADIUS server.
2-6 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
The UR detects automatically whether an authentication request is to be handled remotely or locally. As there are five local accounts possible on the UR, if the user ID credential does not match one of the five local accounts, the UR forwards automatically the request to a RADIUS server when one is provided.
If a RADIUS server is provided, but is unreachable over the network, server authentication requests are denied. In this situation, use local UR accounts to gain access to the UR system.

2.3 Order codes

The order code is on the product label and indicates the product options applicable. The F60 is available as a 19-inch rack horizontal mount or reduced-size (¾) vertical unit. It consists of the following
modules: power supply, CPU, CT/VT, contact input and output, transducer input and output, and inter-relay communications. Module options are specified at the time of ordering.
The order codes shown here are subject to change without notice. See the web page for the product for the latest options. The order code depends on the mounting option (horizontal or vertical) and the type of CT/VT modules (enhanced
diagnostic CT/VT modules or HardFiber HardFiber Bricks.
The R-GOOSE protocol described in IEC 61850-8-1 is available through the IEC 61850 software option. If R-GOOSE security is required, the CyberSentry software option also must be purchased.

2.3.1 Order codes with enhanced CT/VT modules

Table 2-4: F60 order codes for horizontal units
BASE UNITF60|||||||||| |Base Unit CPU T | | | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
U | | | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | | | IEC 61850 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | | | CyberSentry Lvl 1 and phasor measurement unit (PMU) A7 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | | | IEEE 1588 B1 | | | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | | | PRP and IEC 61850 C4 | | | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | | | PRP and PMU C7 | | | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | | | IEEE 1588 and PRP E1 | | | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850
TM
process bus module). The process bus module provides an interface to
(SFP with RJ45)
(PMU)
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-7
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
MOUNT/ COATING FACEPLATE/ DISPLAY C | | | | | | | English display
G4 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | | | IEC 60870-5-103 J1 | | | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU Q7 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
H | | | | | | | | Horizontal (19” rack) - Standard A | | | | | | | | Horizontal (19” rack) - With harsh environmental coating
D|||||| |French display R|||||| |Russian display A | | | | | | | Chinese display P | | | | | | | English d isplay with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons W | | | | | | | Enhanced front panel with Turkish display Y | | | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons I | | | | | | | Enhanced front panel with German display J | | | | | | | Enhanced front panel with German display and user-programmable pushbuttons
61850-90-5
IEC 61850
61850-90-5
2-8 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
POWER SUPPLY (redundant supply must be same type as main supply)
ENHANCED DIAGNOSTICS CT/VT DSP (8L, 8M, 8N, 8R require DSP to be enhanced diagnostic)
CONTACT INPUTS/OUTPUTS XX XX XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
| | XX | XX | No DSP module (slots M and U only) 8L | 8L | | | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | | | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | | | Standard 8CT with enhanced diagnostics 8R | 8R | | | Sensitive Ground 8CT with enhanced diagnostics | | 8Z * | | | Hi-Z 4CT (required for high-impedance fault detection element)
4A 4A 4A 4A 4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4B 4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 4D 4D 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 6B 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 6C 6C 6C 6C 8 Form-C outputs 6D 6D 6D 6D 6D 16 Contact inputs 6E 6E 6E 6E 6E 4 Form-C outputs, 8 contact inputs 6F 6F 6F 6F 6F 8 Fast Form-C outputs 6G 6G 6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6H 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 6K 6K 6K 6K 4 Form-C and 4 Fast Form-C outputs 6L 6L 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 6M 6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 6N 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6P 6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 6R 6R 6R 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs 6S 6S 6S 6S 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 6T 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6U 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 6V 6V 6V 6V 2 Form-A outputs, 1 Form-C output, 1 Form-A latching output , 8 contact inputs 5A 5A 5A 5A 5A 4 DCmA inputs, 4 DCmA outputs 5C 5C 5C 5C 5C 8 RTD inputs 5D 5D 5D 5D 5D 4 RTD inputs, 4 DCmA outputs 5E 5E 5E 5E 5E 4 RTD inputs, 4 DCmA inputs 5F 5F 5F 5F 5F 8 DCmA inputs
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser
2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-9
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-5: F60 order codes for reduced-size vertical units
BASE UNIT F60 | | | | | | | | | Base Unit CPU T | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | IEC 61850 04 | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | CyberSentry Lvl 1 and phasor measurement unit (PMU) A7 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | IEEE 1588 B1 | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | PRP and IEC 61850 C4 | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | PRP and PMU C7 | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | IEEE 1588 and PRP E1 | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | IEC 60870-5-103 J1 | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU Q7 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
(SFP with RJ45)
(PMU)
61850-90-5
IEC 61850
61850-90-5
2-10 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
MOUNT/ COATING FACEPLATE/ DISPLAY F | | | | | English display
POWER SUPPLY ENHANCED DIAGNOSTICS CT/VT DSP (8L, 8M, 8N, 8R require DSP to be enhanced diagnostic)
CONTACT INPUTS/OUTPUTS XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital and transducer input/output modules; slot R is used for inter-relay communications modules.
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
V | | | | | | Vertical (3/4 rack) - Standard B | | | | | | Vertical (3/4 rack) - With harsh environmental coating
K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display L | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | Enhanced front panel with Chinese display and user-programmable pushbutt ons W | | | | | Enhanced front panel with Turkish display Y | | | | | Enhanced front panel with Turkish d isplay and user-programmable pushbuttons I | | | | | Enhanced front panel with German display J | | | | | Enhan ced front panel with German display and user-programmable pushbuttons
H | | | | 125 / 250 V AC/DC power supply L | | | | 24 to 48 V (DC only) power supply
XX | XX | No DSP module (slots M and U only) 8L | 8L | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | Standard 8CT with enhanced diagnostics 8R | 8R | Sensitive Ground 8CT with enhanced diagnostics | | 8Z * | Hi-Z 4CT (required for high-impedance fault detection element)
4A 4A 4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 6C 6C 8 Form-C outputs 6D 6D 6D 16 Contact inputs 6E 6E 6E 4 Form-C outputs, 8 contact inputs 6F 6F 6F 8 Fast Form-C outputs 6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 6K 6K 4 Form-C and 4 Fast Form-C outputs 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 6R 6R 2 Form-A (no monit oring) and 2 Form-C outputs, 8 contact inputs 6S 6S 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 6V 6V 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8
5A 5A 5A 4 DCmA inputs, 4 DCmA outputs (only one 5A module is allowed) 5C 5C 5C 8 RTD inputs 5D 5D 5D 4 RTD inputs, 4 DCmA outputs (only one 5D module is allowed) 5E 5E 5E 4 RTD inputs, 4 DCmA inputs 5F 5F 5F 8 DCmA inputs
contact inputs
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser
2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-11
2
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION

2.3.2 Order codes with process bus modules

Table 2-6: F60 order codes for horizontal units with process bus
BASE UNIT F60 | | | | | | | | | | | Base Unit CPU T | | | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
U | | | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | | | IEC 61850 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | | | IEEE 1588 B1 | | | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | | | PRP and IEC 61850 C4 | | | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | | | PRP and PMU C7 | | | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | | | IEEE 1588 and PRP E1 | | | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | | | IEC 60870-5-103 J1 | | | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU
(SFP with RJ45)
(PMU)
61850-90-5
IEC 61850
2-12 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
MOUNT/ COATING FACEPLATE/ DISPLAY C | | | | | | | English display
POWER SUPPLY (redundant supply must be same type as main supply)
PROCESS BUS MODULE | 81 | | | | Eight-port digital process bus module CONTACT INPUTS/OUTPUTS XX XX XX XX XX No Module
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
Q7 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
H | | | | | | | | Horizontal (19” rack) - Standard A | | | | | | | | Horizontal (19” rack) - With harsh environmental coating
D | | | | | | | French display R | | | | | | | Russian display A | | | | | | | Chinese display P | | | | | | | English display with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French d isplay and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbutt ons W | | | | | | | Enhanced front panel with Turkish display Y | | | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons I | | | | | | | Enhanced front panel with German display J | | | | | | | Enhanced front panel with German display and user-programmable pushbu ttons
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
4A 4A | 4 Solid-State (no monitoring) MOSFET outputs 4B 4B | 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C | 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D | 16 Contact inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L | 14 Form-A (no monitoring) Latching outputs 67 67 | 8 Form-A (no monitoring) outputs 6A 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 6C | 8 Form-C outputs 6D 6D | 16 Contact inputs 6E 6E | 4 Form-C outputs, 8 contact inputs 6F 6F | 8 Fast Form-C outputs 6G 6G | 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6H | 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 6K | 4 Form-C and 4 Fast Form-C outputs 6L 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 6N | 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6P | 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs 6S 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 6T | 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6U | 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 6V | 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8
61850-90-5
contact inputs 2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser 2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-13
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-7: F60 order codes for reduced-size vertical units with process bus
BASE UNIT F60 | | | | | | | | | Base Unit CPU T | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-TX
V | | | | | | | | RS485 and Three 10/100Base-TX (SFP with RJ45)
01 | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | IEC 61850 04 | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | IEEE 1588 B1 | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | PRP and IEC 61850 C4 | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | PRP and PMU C7 | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit
E0 | | | | | | | IEEE 1588 and PRP E1 | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | IEC 60870-5-103 J1 | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 K1 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU M0 | | | | | | | IEC 61850 + PMU + 61850-90-5 M7 | | | | | | | CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MD | | | | | | | IEEE 1588 + IEC 61850 + PMU + 61850-90-5 MJ | | | | | | | PRP + IEC 61850 + PMU + 61850-90-5 MP | | | | | | | IEEE 1588 + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 MV | | | | | | | IEEE 1588 + PRP + IEC 61850 + PMU + 61850-90-5 N1 | | | | | | | PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 N7 | | | | | | | IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU + 61850-90-5 ND | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NJ | | | | | | | IEEE 1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU + 61850-90-5 NP | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry UR Lvl 1 + IEC 61850 + PMU +
P0 | | | | | | | CyberSentry Lvl 2 P1 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data P3 | | | | | | | CyberSentry Lvl 2 + IEC 61850 P4 | | | | | | | CyberSentry Lvl 2 + Ethernet Global Data + IEC 61850 P6 | | | | | | | CyberSentry Lvl 2 + PMU P7 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU Q0 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 Q1 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data Q3 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 Q4 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + Ethernet Global Data +
Q6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + PMU Q7 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU R0 | | | | | | | CyberSentry Lvl 2 + IEC 61850 + PMU + 61850-90-5 R6 | | | | | | | IEC 60870-5-103 + IEEE 1588 + PRP + CyberSentry Lvl 2 + IEC 61850 + PMU +
(SFP with RJ45)
(PMU)
61850-90-5
IEC 61850
61850-90-5
2-14 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
MOUNT/ COATING FACEPLATE/ DISPLAY F | | | | | English display
POWER SUPPLY PROCESS BUS MODULE | 81 | | Eight-port digital process bus module CONTACT INPUTS/OUTPUTS XX XX XX No Modu le
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital input/output modules; slot R is used for inter-relay communications modules.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
V | | | | | | Vertical (3/4 rack) - Standard B | | | | | | Vertical (3/4 rack) - With harsh environmental coating
D | | | | | French display R | | | | | Russian display A | | | | | Chinese display K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display L | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons W | | | | | Enhanced front panel with Turkish display Y | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons I | | | | | Enhanced front panel with German display J | | | | | Enhanced front panel with German display and user-programmable pushbuttons
H | | | | 125 / 250 V AC/DC power supply L | | | | 24 to 48 V (DC only) power supply
4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 16 Contact inputs with Auto-Bu rnishing (maximum of three modules within a case) 4L 14 Form-A (no monitoring) Latching outputs 67 8 Form-A (no monitoring) outputs 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs 6C 8 Form-C outputs 6D 16 Contact inputs 6E 4 Form-C outputs, 8 contact inputs 6F 8 Fast Form-C outputs 6G 4 Form-A (voltage with optional current) outputs, 8 contact inputs 6H 6 Form-A (voltage with optional current) outputs, 4 contact inputs 6K 4 Form-C and 4 Fast Form-C outputs 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs 6N 4 Form-A (current with optional voltage) outputs, 8 contact inputs 6P 6 Form-A (current with optional voltage) outputs, 4 contact inputs 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs 6T 4 Form-A (no monitoring) outputs, 8 contact inputs 6U 6 Form-A (no monitoring) outputs, 4 contact inputs 6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8
contact inputs 2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode,
Laser 2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode,
Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels 7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2

2.3.3 Replacement modules

Replacement modules can be ordered separately. When ordering a replacement CPU module or faceplate, provide the serial number of your existing unit.
Not all replacement modules apply to the F60 relay. The modules specified in the order codes for the F60 are available as replacement modules for the F60.
The order codes shown here are subject to change without notice. See the web page for the product for the latest options.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-15
ORDER CODES CHAPTER 2: PRODUCT DESCRIPTION
2
Table 2-8: UR order codes for replacement modules, horizontal units
POWER SUPPLY redundant supply only available in horizontal units and must be same type as main supply CPU | T | RS485 with 3 100Base-FX Ethernet , multimode, SFP with LC
FACEP LATE/D ISPL AY | 3C | Horizontal faceplate with keypad and English display
CONTACT INPUTS AND OUTPUTS | 4A | 4 Solid-State (no monitoring) MOSFET outputs
CT/VT MODULES | 8L | Standard 4CT/4VT with enhanced diagnostics (not available for the C30) | 8N | Standard 8CT with enhanced diagnostics
INTER-RELAY COMMUNICATIONS | 2A | C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode
TRANSDUCER INPUTS/OUTPUTS | 5A | 4 DCmA inputs, 4 DCmA outputs (only one 5A module is allowed)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
UR - ** - *
| SH A | 125 / 300 V AC/DC | SL H | 24 to 48 V (DC only)
| U | RS485 with 1 100Base-TX Ethernet, SFP RJ-45 + 2 100Base-FX Ethernet , multimode, SFP with LC | V | RS485 with 3 100Base-TX Ethernet, SFP with RJ-45
| 3D | Horizontal faceplate with keypad and French display | 3R | Horizontal faceplate with keypad and Russian display | 3A | Horizontal faceplate with keypad and Chinese display | 3P | Horizontal faceplate with keypad, user-programmable pushbuttons, and English display | 3G | Horizontal faceplate with keypad, user-programmable pushbuttons, and French display | 3S | Horizontal faceplate with keypad, user-programmable pushbuttons, and Russian display | 3B | Horizontal faceplate with keypad, user-programmable pushbuttons, and Chinese display | 3K | Enhanced front panel with English display | 3M | Enhanced front panel with French display | 3Q | En hanced front panel with Russian display | 3U | Enhanced front panel with Chinese display | 3L | Enhanced front panel with English display and user-programmable pushbuttons | 3N | Enhanced front panel with French display and user-programmable pushbuttons | 3T | Enhanced front panel with Russian display a nd user-programmable pushbuttons | 3V | Enhanced front panel with Chinese display and user-programmable pushbuttons | 3I | Enhanced front panel with German display | 3J | Enhanced front panel with German display and user-programmable pushbuttons
| 4B | 4 Solid-State (voltage with optional current) MOSFET outputs | 4C | 4 Solid-State (current with optional voltage) MOSFET outputs | 4D | 16 Contact inputs with Auto-Burnishing | 4L | 14 Form-A (no monitoring) Latching outputs | 67 | 8 Form-A (no monitoring) outputs | 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs | 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs |6C|8 Form-C outputs | 6D | 16 Contact inputs | 6E | 4 Form-C outputs, 8 contact inputs |6F|8 Fast Form-C outputs | 6G | 4 Form-A (voltage with optional current) outputs, 8 contact inputs | 6H | 6 Form-A (voltage with optional current) outputs, 4 contact inputs | 6K | 4 Form-C and 4 Fast Form-C outputs | 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs | 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs | 6N | 4 Form-A (current with optional voltage) outputs, 8 contact inputs | 6P | 6 Form-A (current with optional voltage) outputs, 4 contact inputs | 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs | 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs | 6T | 4 Form-A (no monitoring) outputs, 8 contact inputs | 6U | 6 Form-A (no monitoring) outputs, 4 contact inputs | 6V | 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8 contact inputs
| 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics | 8R | Sensitive Ground 8CT with enhanced diagnostics | 8V | Standard 8VT with enhanced diagnostics (only one module supported) | 8Z | Hi-Z 4CT
| 2B | C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode | 2E | Bi-phase, single channel | 2F | Bi-phase, dual channel | 2G | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel | 2H | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels | 2I | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser | 2J | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser | 72 | 1550 nm, single-mode, Laser, 1 Channel | 73 | 1550 nm, single-mode, Laser, 2 Channel | 74 | Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser | 75 | Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser | 76 | IEEE C37.94, 820 nm, multimode, LED, 1 Channel | 77 | IEEE C37.94, 820 nm, multimode, LED, 2 Channels | 7A | 820 nm, multimode, LED, 1 Channel | 7B | 1300 nm, multimode, LED, 1 Channel | 7C | 1300 nm, single-mode, ELED, 1 Channel | 7D | 1300 nm, single-mode, Laser, 1 Channel | 7E | Channel 1 - G.703; Channel 2 - 820 nm, multimode | 7F | Channel 1 - G.703; Channel 2 - 1300 nm, multimode | 7G | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED | 7H | 820 nm, multimode, LED, 2 Channels | 7I | 1300 nm, multimode, LED, 2 Channels | 7J | 1300 nm, single-mode, ELED, 2 Channels | 7K | 1300 nm, single-mode, Laser, 2 Channels | 7L | Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED | 7M | Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED | 7N | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED | 7P | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser | 7Q | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser | 7R | G.703, 1 Channel | 7S | G.703, 2 Channels | 7T | RS422, 1 Channel | 7W | RS422, 2 Channels
| 5C | 8 RTD inputs | 5D | 4 RTD inputs, 4 DCmA outputs (only one 5D module is allowed) | 5E | 4 DCmA inputs, 4 RTD inputs | 5F | 8 DCmA inputs
2-16 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION ORDER CODES
Table 2-9: UR order codes for replacement modules, vertical units
POWER SUPPLY | SH B | 125 / 300 V AC/DC
CPU | T | RS485 with 3 100Base-FX Ethernet , multimode, SFP with LC
FACEP LATE/D ISPL AY | 3F | Vertical faceplate with keypad and English display
CONTACT INPUTS/OUTPUTS | 4A | 4 Solid-State (no monitoring) MOSFET outputs
CT/VT MODULES (not available for the C30)
INTER-RELAY COMMUNICATIONS | 2A | C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode
TRANSDUCER INPUTS/OUTPUTS | 5A | 4 DCmA inputs, 4 DCmA outputs (only one 5A module is allowed)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
UR - ** - *
| SL V | 24 to 48 V (DC only)
| U | RS485 with 1 100Base-TX Ethernet, SFP RJ-45 + 2 100Base-FX Ethernet , multimode, SFP with LC | V | RS485 with 3 100Base-TX Ethernet, SFP with RJ-45
| 3D | Vertical faceplate with keypad and French display | 3R | Vertica l faceplate with keypad and Russian display | 3A | Vertical faceplate with keypad and Chinese display | 3K | Enhanced front panel with English display | 3M | Enhanced front panel with French display | 3Q | En hanced front panel with Russian display | 3U | Enhanced front panel with Chinese display | 3L | Enhanced front panel with English display and user-programmable pushbuttons | 3N | Enhanced front panel with French display and user-programmable pushbuttons | 3T | Enhanced front panel with Russian display a nd user-programmable pushbuttons | 3V | Enhanced front panel with Chinese display and user-programmable pushbutt ons | 3I | Enhanced front panel with German display | 3J | Enhanced front panel with German display and user-programmable pushbuttons
| 4B | 4 Solid-State (voltage with optional current) MOSFET outputs | 4C | 4 Solid-State (current with optional voltage) MOSFET outputs | 4D | 16 Contact inputs with Auto-Burnishing | 4L | 14 Form-A (no monitoring) Latching outputs | 67 | 8 Form-A (no monitoring) outputs | 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs | 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs |6C|8 Form-C outputs | 6D | 16 Contact inputs | 6E | 4 Form-C outputs, 8 contact inputs |6F|8 Fast Form-C outputs | 6G | 4 Form-A (voltage with optional current) outputs, 8 contact inputs | 6H | 6 Form-A (voltage with optional current) outputs, 4 contact inputs | 6K | 4 Form-C and 4 Fast Form-C outputs | 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs | 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 contact inputs | 6N | 4 Form-A (current with optional voltage) outputs, 8 contact inputs | 6P | 6 Form-A (current with optional voltage) outputs, 4 contact inputs | 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs | 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs | 6T | 4 Form-A (no monitoring) outputs, 8 contact inputs | 6U | 6 Form-A (no monitoring) outputs, 4 contact inputs | 6V | 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8 contact inputs | 8L | Standard 4CT/4VT with enhanced diagnostics | 8N | Standard 8CT with enhanced diagnostics | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics | 8R | Sensitive Ground 8CT with enhanced diagnostics | 8V | Standard 8VT with enhanced diagnostics | 8Z * | HI-Z 4CT
| 2B | C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode | 2E | Bi-phase, single channel | 2F | Bi-phase, dual channel | 2G | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel | 2H | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels | 2I | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser | 2J | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser | 72 | 1550 nm, single-mode, Laser, 1 Channel | 73 | 1550 nm, single-mode, Laser, 2 Channel | 74 | Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser | 75 | Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser | 76 | IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel | 77 | IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels | 7A | 820 nm, multimode, LED, 1 Channel | 7B | 1300 nm, multimode, LED, 1 Channel | 7C | 1300 nm, single-mode, ELED, 1 Channel | 7D | 1300 nm, single-mode, Laser, 1 Channel | 7E | Channel 1 - G.703; Channel 2 - 820 nm, multimode | 7F | Channel 1 - G.703; Channel 2 - 1300 nm, multimode | 7G | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED | 7H | 820 nm, multimode, LED, 2 Channels | 7I | 1300 nm, multimode, LED, 2 Channels | 7J | 1300 nm, single-mode, ELED, 2 Channels | 7K | 1300 nm, single-mode, Laser, 2 Channels | 7L | Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED | 7M | Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED | 7N | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED | 7P | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser | 7Q | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser | 7R | G.703, 1 Channel | 7S | G.703, 2 Channels | 7T | RS422, 1 Channel | 7W | RS422, 2 Channels
| 5C | 8 RTD inputs | 5D | 4 RTD inputs, 4 DCmA outputs (only one 5D module is allowed) | 5E | 4 DCmA inputs, 4 RTD inputs | 5F | 8 DCmA inputs
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-17
2
SIGNAL PROCESSING CHAPTER 2: PRODUCT DESCRIPTION

2.4 Signal processing

2.4.1 UR signal processing

The UR series relays are microprocessor-based protective relays that are designed to measure power system conditions directly via CT and PT inputs and via other sources of information, such as analog inputs, communications inputs and contact inputs. The following figure shows the overall signal processing in URs.
An analog low pass anti-aliasing filter with a 3 dB corner frequency is set at 2.4 kHz and is used for current and voltage analog filtering as well as signal conditioning. The same filtering is applied for phase, ground currents, phase-to-phase (when applicable), and auxiliary voltages. The 2.4 kHz cut-off frequency applies to both 50 Hz and 60 Hz applications and fixed in the hardware, and thus is not dependent on the system nominal frequency setting.
Figure 2-3: UR signal processing
The UR samples its AC signals at 64 samples per cycle, that is, at 3840 Hz in 60 Hz systems, and 3200 Hz in 50 Hz systems. The sampling rate is dynamically adjusted to the actual system frequency by an accurate and fast frequency tracking system.
The A/D converter has the following ranges of AC signals:
2-18 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SIGNAL PROCESSING
Voltages:
Eq. 2-1
Currents:
Eq. 2-2
Current harmonics are estimated based on raw samples with the use of the full-cycle Fourier filter. Harmonics 2nd through 25th are estimated.
True RMS value for the current is calculated on a per-phase basis. The true RMS can be used for demand recording or as an input signal to Time Overcurrent function, if the latter is intended for thermal protection. The true RMS is calculated as per the widely accepted definition:
Eq. 2-3
RMS values include harmonics, inter-harmonics, DC components, and so on, along with fundamental frequency values. The true RMS value reflects thermal effects of the current and is used for the thermal related monitoring and protection functions.
Protection and control functions respond to phasors of the fundamental and/or harmonic frequency components (magnitudes and angles), with an exception for some functions that have an option for RMS or fundamental measurements, or some function responding to RMS only. This type of response is explained typically in each element's section in the instruction manual.
Currents are pre-filtered using a Finite Impulse Response (FIR) digital filter. The filter is designed to reject DC components and low-frequency distortions, without amplifying high-frequency noise. This filter is referred to as a modified MIMIC filter, which provides excellent filtering and overall balance between speed and accuracy of filtering. The filter is cascaded with the full-cycle Fourier filter for the current phasor estimation.
Voltages are pre-filtered using a patented Finite Impulse Response (FIR) digital filter. The filter has been optimized to reject voltage transformers specific distortions, such as Capacitive Voltage Transformer (CVT) noise and high-frequency oscillatory components. The filter is cascaded with the half-cycle Fourier filter for the voltage phasor estimation.
The URs measure power system frequency using the Clarke transformation by estimating the period of the waveform from two consecutive zero-crossings in the same direction (negative-to-positive). Voltage or current samples are pre-filtered using a Finite Impulse Response (FIR) digital filter to remove high frequency noise contained in the signal. The period is used after several security conditions are met, such as true RMS signal must be above 6% nominal for a certain time and others. If these security conditions are not met, the last valid measurement is used for a specific time after which the UR reverts to nominal system frequency.
Synchrophasors are calculated using a patented convolution integral algorithm. This algorithm allows use of the same time-stamped samples, which are used for protection and taken at the same sampling frequency. This allows URs to use one sampling clock for both protection algorithms and synchrophasors.
Synchrophasors on firmware versions 7.23 and up have been tested and certified to meet IEEE C.37.118-2011 and C.37.118.1a-2014 standards for both metering and protection classes with outputs available up to 60 synchrophasors per second for the metering class and 120 synchrophasors per second for the protection class. Synchrophasors measurement are also available via IEC 61850-90-5 protocol.
Contact inputs threshold is settable in the firmware with 17, 33, 84, 166 VDC settings available. Inputs are scanned every
0.5 ms and can be conditioned for the critical applications, using debounce time timer, settable from 0.0 ms to 16.0 ms. Contact inputs with auto-burnishing are available as well, when external contacts are exposed to the contamination in a harsh industrial environment.
All measured values are available in the UR metering section on the front panel and via communications protocols. Measured analog values and binary signals can be captured in COMTRADE format with sampling rates from 8 to 64 samples per power cycle. Analog values can be captured with Data Logger, allowing much slower rates extended over long period of time.
2
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-19
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
Other advanced UR order code options are available to support IEC 61850 Ed2.0 (including fast GOOSE, MMS server, 61850 services, ICD/CID/IID files, and so on), IEEE 1588 (IEEE C37.238 power profile) based time synchronization, CyberSentry (advanced cyber security), the Parallel Redundancy Protocol (PRP), IEC 60870-5-103, and so on.

2.5 Specifications

2
Specifications are subject to change without notice.

2.5.1 Protection elements

The operating times include the activation time of a trip rated form-A output contact unless otherwise indicated. FlexLogic operands of a given element are 4 ms faster. Take this into account when using FlexLogic to interconnect with other protection or control elements of the relay, building FlexLogic equations, or interfacing with other intelligent electronic devices (IEDs) or power system devices via communications or different output contacts. If not specified, the operate times given here are for a 60 Hz system at nominal system frequency. Operate times for a 50 Hz system are 1.2 times longer.
RESTRICTED GROUND FAULT
Pickup: 0.005 to 30.000 pu in steps of 0.001 Dropout: 97 to 98% of pickup Slope: 0 to 100% in steps of 1% Level accuracy:
0.1 to 2.0 x CT rating: ±0.5% of reading or ±1% of rated (whichever is greater)
>2.0 x CT rating ±1.5% of reading Pickup delay: 0 to 600.00 s in steps of 0.01 Dropout delay: 0 to 600.00 s in steps of 0.01 Operate time: <1 power system cycle
PHASE/NEUTRAL/GROUND TOC
Current: Phasor or RMS Pickup level: 0.020 to 30.000 pu in steps of 0.001 Dropout level: 97% to 98% of pickup Level accuracy:
0.1 to 2.0 × CT: ±0.5% of reading or ±0.4% of rated (whichever is greater)
> 2.0 × CT: ±1.5% of reading > 2.0 × CT rating Curve shapes: IEEE Moderately/Very/Extremely Inverse; IEC (and BS) A/B/C and Short Inverse; GE IAC Inverse,
Short/Very/ Extremely Inverse; I
curve) Curve multiplier: Time Dial = 0.00 to 600.00 in steps of 0.01 Reset type: Instantaneous/Timed (per IEEE) Curve timing accuracy at 1.03 to 20 x pickup:
±3.5% of operate time or ±½ cycle (whichever is greater) from pickup to operate Voltage restraint: Modifies pickup current for voltage in the range of 0.1 < V < 0.9 VT Nominal in a fixed linear rela-
tionship
2
t; FlexCurves™ (programmable); Definite Time (0.01 s base
PHASE/NEUTRAL/GROUND IOC
Pickup level: 0.020 to 30.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy:
0.1 to 2.0 × CT rating: ±0.5% of reading or ±0.4% of rated (whichever is greater) > 2.0 × CT rating: ±1.5% of reading
Overreach: <2% Pickup delay: 0.00 to 600.00 s in steps of 0.01 Reset delay: 0.00 to 600.00 s in steps of 0.01
2-20 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS
Operate time: <16 ms at 3 × pickup at 60 Hz (Phase/Ground IOC)
<20 ms at 3 × pickup at 60 Hz (Neutral IOC)
Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater)
NEGATIVE SEQUENCE TOC
Pickup level: 0.020 to 30.000 pu in steps of 0.001 Dropout level: 97% to 98% of pickup Level accuracy: ±0.5% of reading or ±0.4% of rated (whichever is greater)
from 0.1 to 2.0 x CT rating ±1.5% of reading > 2.0 x CT rating
Curve shapes: IEEE Moderately/Very/Extremely Inverse; IEC (and BS) A/B/C and Short Inverse; GE IAC Inverse,
Short/Very/ Extremely Inverse; I
curve) Curve multiplier (Time dial): 0.00 to 600.00 in steps of 0.01 Reset type: Instantaneous/Timed (per IEEE) and Linear Curve timing accuracy at 1.03 to 20 x pickup: ±3.5% of operate time or ±½ cycle (whichever is greater) from pickup to operate
2
t; FlexCurves™ (programmable); Definite Time (0.01 s base
NEGATIVE SEQUENCE IOC
Pickup level: 0.020 to 30.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: 0.1 to 2.0 × CT rating: ±0.5% of reading or ±0.4% of rated (whichever is greater); >2.0 × CT rating:
±1.5% of reading Overreach: <2% Pickup delay: 0.00 to 600.00 s in steps of 0.01 Reset delay: 0.00 to 600.00 s in steps of 0.01 Operate time: <20 ms at 3 × pickup at 60 Hz Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater)
2
PHASE DIRECTIONAL OVERCURRENT
Relay connection: 90° (quadrature) Quadrature voltage: ABC phase seq.: phase A (V
B (V
), phase C (VBA) Polarizing voltage threshold: 0.004 to 3.000 pu in steps of 0.001 Current sensitivity threshold: 0.05 pu Characteristic angle: 0 to 359 Angle accuracy: ±2° Operation time (FlexLogic operands):
Tripping (reverse load, forward fault): <12 ms, typically Blocking (forward load, reverse fault): <8 ms, typically
AC
° in steps of 1
), phase B (VCA), phase C (VAB); ACB phase seq.: phase A (VCB), phase
BC
NEUTRAL DIRECTIONAL OVERCURRENT
Directionality: Co-existing forward and reverse Polarizing: Voltage, Current, Dual, Dual-V, Dual-I Polarizing voltage: V_0 or VX Polarizing current: IG Operating current: I_0 Level sensing: 3 × (|I_0| – K × |I_1|), IG Restraint, K: 0.000 to 0.500 in steps of 0.001 Characteristic angle: –90 to 90° in steps of 1 Limit angle: 40 to 90° in steps of 1, independent for forward and reverse Angle accuracy: ±2° Offset impedance: 0.00 to 250.00 Ω in steps of 0.01 Pickup level: 0.002 to 30.000 pu in steps of 0.01 Dropout level: 97 to 98% Operation time: <16 ms at 3 × pickup at 60 Hz
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-21
2
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
NEGATIVE SEQUENCE DIRECTIONAL OC
Directionality: Co-existing forward and reverse Polarizing: Voltage Polarizing voltage: V_2 Operating current: I_2 Level sensing:
Zero-sequence: |I_0| – K × |I_1| Negative-sequence: |I_2| – K × |I_1|
Restraint, K: 0.000 to 0.500 in steps of 0.001 Characteristic angle: 0 to 90° in steps of 1 Limit angle: 40 to 90° in steps of 1, independent for forward and reverse Angle accuracy: ±2° Offset impedance: 0.00 to 250.00 Ω in steps of 0.01 Pickup level: 0.015 to 30.000 pu in steps of 0.01 Dropout level: 97 to 98% Operation time: <16 ms at 3 × pickup at 60 Hz
WATTMETRIC ZERO-SEQUENCE DIRECTIONAL
Measured power: zero-sequence Number of elements: 2 Characteristic angle: 0 to 360° in steps of 1 Minimum power: 0.001 to 1.200 pu in steps of 0.001 Pickup level accuracy: ±1% or ±0.0025 pu, whichever is greater Hysteresis: 3% or 0.001 pu, whichever is greater Pickup delay: definite time (0 to 600.00 s in steps of 0.01), inverse time, or FlexCurve Inverse time multiplier: 0.01 to 2.00 s in steps of 0.01 Curve timing accuracy: ±3.5% of operate time or ±1 cycle (whichever is greater) from pickup to operate Operate time: <30 ms at 60 Hz
SENSITIVE DIRECTIONAL POWER
Measured power: 3-phase, true RMS Number of stages: 2 Characteristic angle: 0 to 359° in steps of 1 Calibration angle: 0.00 to 0.95° in steps of 0.05 Minimum power: –1.200 to 1.200 pu in steps of 0.001 Pickup level accuracy: ±1% or ±0.001 pu, whichever is greater Hysteresis: 2% or 0.001 pu, whichever is greater Pickup delay: 0 to 600.00 s in steps of 0.01 Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater) Operate time: <50 ms
PHASE UNDERVOLTAGE
Voltage: Phasor only Pickup level: 0.004 to 3.000 pu in steps of 0.001 Dropout level: 102 to 103% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Curve shapes: GE IAV Inverse;
Definite T ime (0.1s base curve) Curve multiplier: Time dial = 0.00 to 600.00 in steps of 0.01 Curve timing accuracy at <0.90 x pickup:
±3.5% of operate time or ±1/2 cycle (whichever is greater) from pickup to operate Operate time: <30 ms at 0.9 pickup at 60 Hz for Definite Time mode
AUXILIARY UNDERVOLTAGE
Pickup level: 0.004 to 3.000 pu in steps of 0.001 Dropout level: 102 to 103% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V
2-22 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS
Curve shapes: GE IAV Inverse, Definite Time Curve multiplier: Time Dial = 0 to 600.00 in steps of 0.01 Curve timing accuracy at <0.90 x pickup:
±3.5% of operate time or ±1/2 cycle (whichever is greater) from pickup to operate
Operate time: <30 ms at 0.9 pickup at 60 Hz for Definite Time mode
PHASE OVERVOLTAGE
Voltage: Phasor only Pickup level: 0.004 to 3.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0.00 to 600.00 in steps of 0.01 s Operate time: <30 ms at 1.10 × pickup at 60 Hz Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater)
NEUTRAL OVERVOLTAGE
Pickup level: 0.004 to 3.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0.00 to 600.00 s in steps of 0.01 (definite time) or user-defined curve Reset delay: 0.00 to 600.00 s in steps of 0.01 Curve timing accuracy at >1.1 pickup: ±3.5% of operate time or ±1 cycle (whichever is greater) from pickup to operate Operate time: <30 ms at 1.10 pickup at 60 Hz
2
AUXILIARY OVERVOLTAGE
Pickup level: 0.004 to 3.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0 to 600.00 s in steps of 0.01 Reset delay: 0 to 600.00 s in steps of 0.01 Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater) Operate time: <30 ms at 1.10 × pickup at 60 Hz
NEGATIVE SEQUENCE OVERVOLTAGE
Pickup level: 0.004 to 1.250 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0 to 600.00 s in steps of 0.01 Reset delay: 0 to 600.00 s in steps of 0.01 Timer accuracy: ±3% of operate time or ±20 ms, whichever is greater Operate time: <30 ms at 1.10 × pickup at 60 Hz
UNDERFREQUENCY
Minimum signal: 0.10 to 1.25 pu in steps of 0.01 Pickup level: 20.00 to 65.00 Hz in steps of 0.01 Dropout level: pickup + 0.03 Hz Level accuracy: ±0.001 Hz Time delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater) Operate time: typically 4 cycles at 0.1 Hz/s change
typically 3.5 cycles at 0.3 Hz/s change typically 3 cycles at 0.5 Hz/s change
Typical times are average operate times including variables such as frequency change instance, test method, and so on, and can vary by ±0.5 cycles.
OVERFREQUENCY
Pickup level: 20.00 to 65.00 Hz in steps of 0.01
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-23
2
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
Dropout level: pickup – 0.03 Hz Level accuracy: ±0.001 Hz Time delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater) Operate time: typically 4 cycles at 0.1 Hz/s change
typically 3.5 cycles at 0.3 Hz/s change
typically 3 cycles at 0.5 Hz/s change Typical times are average operate times including variables such as frequency change instance, test method, and so on, and can vary by
±0.5 cycles.
RATE OF CHANGE OF FREQUENCY
df/dt trend: increasing, decreasing, bi-directional df/dt pickup level: 0.10 to 15.00 Hz/s in steps of 0.01 df/dt dropout level: 96% of pickup df/dt level accuracy: 80 mHz/s or 3.5%, whichever is greater Overvoltage supv.: 0.100 to 3.000 pu in steps of 0.001 Overcurrent supv.: 0.020 to 30.000 pu in steps of 0.001 Pickup delay: 0 to 65.535 s in steps of 0.001 Reset delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater) 95% settling time for df/dt: <24 cycles Operate time: typically 9.5 cycles at 2 × pickup
typically 8.5 cycles at 3 × pickup
typically 6.5 cycles at 5 × pickup Typical times are average operate times including variables such as frequency change instance, test method, and so on, and can vary by
±0.5 cycles.
BREAKER FAILURE
Mode: 1-pole, 3-pole Current supervision: phase, neutral current Current supv. pickup: 0.020 to 30.000 pu in steps of 0.001 Current supv. dropout: 97 to 98% of pickup Current supv. accuracy:
0.1 to 2.0 × CT rating: ±0.75% of reading or ±2% of rated (whichever is greater) above 2 × CT rating: ±2.5% of reading
BREAKER ARCING CURRENT
Principle: accumulates breaker duty (I2t) and measures fault duration Initiation: programmable per phase from any FlexLogic operand Compensation for auxiliary relays: 0 to 65.535 s in steps of 0.001 Alarm threshold: 0 to 50000 kA Fault duration accuracy: 0.25 of a power cycle Availability: 1 per CT bank with a minimum of 2
2
-cycle in steps of 1
BREAKER FLASHOVER
Operating quantity: phase current, voltage, and voltage difference Pickup level voltage: 0.004 to 1.500 pu in steps of 0.001 Dropout level voltage: 97 to 98% of pickup Pickup level current: 0.020 to 1.500 pu in steps of 0.001 Dropout level current: 97 to 98% of pickup Level accuracy: ±0.5% or ±0.1% of rated, whichever is greater Pickup delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±42 ms, whichever is greater Operate time: <42 ms at 1.10 × pickup at 60 Hz
BREAKER RESTRIKE
Principle: detection of high-frequency overcurrent condition ¼ cycle after breaker opens
2-24 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS
Availability: one per CT/VT module (not including 8Z modules) Pickup level: 0.1 to 2.00 pu in steps of 0.01 Reset delay: 0.000 to 65.535 s in steps of 0.001
INCIPIENT CABLE FAULT DETECTION
Principle: detection of ½ cycle or less overcurrent condition during normal load Availability: two per CT/VT module (not including 8Z modules) Pickup level: 0.1 to 10.00 pu in steps of 0.01 Reset delay: 0.000 to 65.535 s in steps of 0.001 Operating mode: number of counts, counts per time window
SYNCHROCHECK
Max voltage difference: 0 to 400000 V in steps of 1 Max angle difference: 0 to 100 Max freq. difference: 0.00 to 2.00 Hz in steps of 0.01 Hysteresis for max. freq. diff.: 0.00 to 0.10 Hz in steps of 0.01 Dead source function: None, LV1 & DV2, DV1 & LV2, DV1 or DV2, DV1 xor DV2, DV1 & DV2 (L = Live, D = Dead) S-CLS MAX dF: 0.10 to 2.00 Hz in steps of 0.01 S-CLS MIN dF: 0.00 to 1.00 Hz in steps of 0.01 V2 MAG CORR FACTOR: 0.10 to 10.00 in steps of 0.01 V2 ANGLE SHIFT: -180
° in steps of 1
° to +180° in steps of 1°
AUTORECLOSURE
Single breaker applications, 3-pole tripping schemes Up to four reclose attempts before lockout Independent dead time setting before each shot Possibility of changing protection settings after each shot with FlexLogic
2
PILOT-AIDED SCHEMES
Permissive Overreaching Transfer Trip (POTT) Directional Comparison Blocking Scheme
LOAD ENCROACHMENT
Responds to: Positive-sequence quantities Minimum voltage: 0.004 to 3.000 pu in steps of 0.001 Reach (sec. Ω): 0.02 to 250.00 Ω in steps of 0.01 Impedance accuracy: ±5% Angle: 5 to 50° in steps of 1 Angle accuracy: ±2° Pickup delay: 0 to 65.535 s in steps of 0.001 Reset delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle (whichever is greater) Operate time: <30 ms at 60 Hz
THERMAL OVERLOAD PROTECTION
Thermal overload curves: IEC 255-8 curve Base current: 0.20 to 3.00 pu in steps of 0.01 Overload (k) factor: 1.00 to 1.20 pu in steps of 0.05 Trip time constant: 0 to 1000 min. in steps of 1 Reset time constant: 0 to 1000 min. in steps of 1 Minimum reset time: 0 to 1000 min. in steps of 1 Timer accuracy (cold curve): ±100 ms or 2%, whichever is greater Timer accuracy (hot curve): ±500 ms or 2%, whichever is greater for I
<0.9 × k × Ib and I / (k × Ib) > 1.1
p
TRIP BUS (TRIP WITHOUT FLEXLOGIC)
Number of elements: 6 Number of inputs: 16
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-25
2
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
Operate time: <2 ms at 60 Hz Timer accuracy: ±3% or 10 ms, whichever is greater

2.5.2 User-programmable elements

FLEXLOGIC
Programming language: Reverse Polish Notation with graphical visualization (keypad programmable) Lines of code: 1024 Internal variables: 64 Supported operations: NOT, XOR, OR (2 to 16 inputs), AND (2 to 16 inputs), NOR (2 to 16 inputs), NAND (2 to 16 inputs),
latch (reset-dominant), edge detectors, timers Inputs: any logical variable, contact, or virtual input Number of timers: 32 Pickup delay: 0 to 60000 (ms, sec., min.) in steps of 1 Dropout delay: 0 to 60000 (ms, sec., min.) in steps of 1
FLEXCURVES™
Number: 4 (A through D) Reset points: 40 (0 through 1 of pickup) Operate points: 80 (1 through 20 of pickup) Time delay: 0 to 65535 ms in steps of 1
FLEX STATES
Number: up to 256 logical variables grouped under 16 Modbus addresses Programmability: any logical variable, contact , or virtual input
FLEXELEMENTS™
Number of elements: 8 Operating signal: any analog actual value, or two values in differential mode Operating signal mode: signed or absolute value Operating mode: level, delta Comparator direction: over, under Pickup Level: –90.000 to 90.000 pu in steps of 0.001 Hysteresis: 0.1 to 50.0% in steps of 0.1 Delta dt: 20 ms to 60 days Pickup and dropout delay: 0.000 to 65.535 s in steps of 0.001
NON-VOLATILE LATCHES
Type: set-dominant or reset-dominant Number: 16 (individually programmed) Output: stored in non-volatile memory Execution sequence: as input prior to protection, control, and FlexLogic
USER-PROGRAMMABLE LEDs
Number: 48 plus trip and alarm Programmability: from any logical variable, contact, or virtual input Reset mode: self-reset or latched
LED TEST
Initiation: from any contact input or user-programmable condition Number of tests: 3, interruptible at any time Duration of full test: approximately 3 minutes Test sequence 1: all LEDs on Test sequence 2: all LEDs off, one LED at a time on for 1 s Test sequence 3: all LEDs on, one LED at a time off for 1 s
2-26 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS
USER-DEFINABLE DISPLAYS
Number of displays: 16 Lines of display: 2 × 20 alphanumeric characters Parameters: up to 5, any Modbus register addresses Invoking and scrolling: keypad, or any user-programmable condition, including pushbuttons
CONTROL PUSHBUTTONS
Number of pushbuttons: 7 Operation: drive FlexLogic operands
USER-PROGRAMMABLE PUSHBUTTONS (OPTIONAL)
Number of pushbuttons: 12 (standard faceplate);
16 (enhanced faceplate) Mode: self-reset, latched Display message: 2 lines of 20 characters each Drop-out timer: 0.00 to 60.00 s in steps of 0.05 Autoreset timer: 0.2 to 600.0 s in steps of 0.1 Hold timer: 0.0 to 10.0 s in steps of 0.1
SELECTOR SWITCH
Number of elements: 2 Upper position limit: 1 to 7 in steps of 1 Selecting mode: time-out or acknowledge Time-out timer: 3.0 to 60.0 s in steps of 0.1 Control inputs: step-up and 3-bit Power-up mode: restore from non-volatile memory or synchronize to a 3-bit control input or synch/restore mode
2
DIGITAL ELEMENTS
Number of elements: 48 Operating signal: any FlexLogic operand Pickup delay: 0.000 to 999999.999 s in steps of 0.001 Dropout delay: 0.000 to 999999.999 s in steps of 0.001 Timing accuracy: ±3% or ±4 ms, whichever is greater

2.5.3 Monitoring

OSCILLOGRAPHY
Maximum records: 64 Sampling rate: 64 samples per power cycle Triggers: any element pickup, dropout, or operate; contact input change of state; contact output change
of state; FlexLogic equation Data: AC input channels; element state; contact input state; contact output state Data storage: in non-volatile memory
EVENT RECORDER
Capacity: 1024 events Time-tag: to 1 microsecond Triggers: any element pickup, dropout, or operate; contact input change of state; contact output change
of state; self-test events Data storage: in non-volatile memory
DATA LOGGER
Number of channels: 1 to 16 Parameters: any available analog actual value Sampling rate: 15 to 3600000 ms in steps of 1 Trigger: any FlexLogic operand Mode: continuous or triggered
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-27
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
Storage capacity: (NN is dependent on memory)
1-second rate:
01 channel for NN days
16 channels for NN days
60-minute rate:
01 channel for NN days 16 channels for NN days
2
FAULT LOCATOR
Number of independent fault locators: 1 per CT bank (to a maximum of 3) Method: single-ended Voltage source: wye-connected VTs, delta-connected VTs and neutral voltage, delta-connected VTs and zero-
sequence current (approximation) Maximum accuracy if: fault resistance is zero or fault currents from all line terminals are in phase Relay accuracy: ±1.5% (V > 10 V, I > 0.1 pu) Worst-case accuracy:
VT
+user data
%error
CT
+user data
%error
Z
Line%error
RELAY ACCURACY
+user data
+1.5%
%error
HI-Z
Detections: Arc Suspected, Arc Detected, Downed Conductor, Phase Identification
PHASOR MEASUREMENT UNIT
Output format: per IEEE C37.118 or IEC 61850-90-5 standard Number of channels: 14 synchrophasors, 8 analogs, 16 digitals TVE (total vector error): <1% Triggering: frequency, voltage, current, power, rate of change of frequency, user-defined Reporting rate: 1, 2, 5, 10, 12, 15, 20, 25, 30, 50, or 60 times per second for P and M class, and 100 or 120 times
per second for P class only Number of clients: one over TCP/IP port and one over UDP/IP per aggregator AC ranges: as indicated in appropriate specification sections Network reporting format: 16-bit integer (for IEEE C37.118) or 32-bit IEEE floating point numbers Network reporting style: rectangular (real and imaginary for IEEE C37.188) or polar (magnitude and angle) coordinates Post-filtering: none, 3-point, 5-point, 7-point Calibration: ±5° (angle) and ±5% (magnitude)

2.5.4 Metering

RMS CURRENT: PHASE, NEUTRAL, AND GROUND
Accuracy at
0.1 to 2.0 × CT rating: ±0.25% of reading or ±0.1% of rated (whichever is greater) > 2.0 × CT rating: ±1.0% of reading
RMS VOLTAGE
Accuracy: ±0.5% of reading from 10 to 208 V
REAL POWER (WATTS)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to 1.2 x VT rating:
±1.0% of reading at –1.0 PF < –0.8 and 0.8 < PF ≤ 10
REACTIVE POWER (VARS)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to 1.2 x VT rating:
±1.0% of reading at –0.2 PF 0.2
2-28 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS
APPARENT POWER (VA)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to 1.2 x VT rating:
±1.0% of reading
WATT-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading Range: ±0 to 1 × 10 Parameters: three-phase only Update rate: 50 ms
6
MWh
VAR-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading Range: ±0 to 1 × 10 Parameters: three-phase only Update rate: 50 ms
6
Mvarh
CURRENT HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, displayed as a % of f
THD: per phase, displayed as a % of f
Accuracy:
HARMONICS: 1. f
THD: 1. f1 > 0.4pu: (0.25% + 0.035% / harmonic) of reading or 0.20% of 100%, whichever is greater
> 0.4pu: (0.20% + 0.035% / harmonic) of reading or 0.15% of 100%, whichever is greater
1
2. f
< 0.4pu: as above plus %error of f
1
2. f
< 0.4pu: as above plus %error of f
1
1
1
1
(fundamental frequency phasor)
1
2
VOLTAGE HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, displayed as a % of f
THD: per phase, displayed as a % of f
Accuracy:
HARMONICS: 1. f
THD: 1. f1 > 0.4pu: (0.25% + 0.035% / harmonic) of reading or 0.20% of 100%, whichever is greater
> 0.4pu: (0.20% + 0.035% / harmonic) of reading or 0.15% of 100%, whichever is greater
1
2. f
< 0.4pu: as above plus %error of f
1
2. f
< 0.4pu: as above plus %error of f
1
1
1
1
(fundamental frequency phasor)
1
FREQUENCY
Accuracy at
V = 0.8 to 1.2 pu: ±0.001 Hz (when voltage signal is used for frequency measurement) I = 0.1 to 0.25 pu: ±0.005 Hz I > 0.25 pu: ±0.02 Hz (when current signal is used for frequency measurement)
DEMAND
Measurements: Phases A, B, and C present and maximum measured currents
3-Phase Power (P, Q, and S) present and maximum measured currents
Accuracy: ±2.0%

2.5.5 Inputs

AC CURRENT
CT rated primary: 1 to 50000 A CT rated secondary: 1 A or 5 A by connection Relay burden: < 0.2 VA at rated secondary Conversion range:
Standard CT: 0.02 to 46 × CT rating RMS symmetrical Sensitive Ground CT module: 0.002 to 4.6 × CT rating RMS symmetrical
HI-Z CT module: 0.002 to 4.6 × CT rating RMS symmetrical Current withstand: 20 ms at 250 times rated
1 sec at 100 times rated continuous 4xInom
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-29
2
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
Short circuit rating: 150000 RMS symmetrical amperes, 250 V maximum (primary current to external CT)
AC VOLTAGE
VT rated secondary: 50.0 to 240.0 V VT ratio: 1.00 to 24000.00 Relay burden: < 0.25 VA at 120 V Conversion range: 1 to 275 V Voltage withstand: continuous at 260 V to neutral
1 min/hr at 420 V to neutral
FREQUENCY
Nominal frequency setting: 25 to 60 Hz Sampling frequency: 64 samples per power cycle Tracking frequency range: 20 to 70 Hz
CONTACT INPUTS
Dry contacts: 1000 Ω maximum Wet contacts: 300 V DC maximum Selectable thresholds: 17 V, 33 V, 84 V, 166 V Tolerance: ±10% Contacts per common return: 4 Recognition time: < 1 ms Debounce time: 0.0 to 16.0 ms in steps of 0.5 Continuous current draw: 4 mA (when energized)
CONTACT INPUTS WITH AUTO-BURNISHING
Dry contacts: 1000 Ω maximum Wet contacts: 300 V DC maximum Selectable thresholds: 17 V, 33 V, 84 V, 166 V Tolerance: ±10% Contacts per common return: 2 Recognition time: < 1 ms Debounce time: 0.0 to 16.0 ms in steps of 0.5 Continuous current draw: 4 mA (when energized) Auto-burnish impulse current: 50 to 70 mA Duration of auto-burnish impulse: 25 to 50 ms
DCMA INPUTS
Current input (mA DC): 0 to –1, 0 to +1, –1 to +1, 0 to 5, 0 to 10, 0 to 20, 4 to 20 (programmable) Input impedance: 379 Ω ±10% Conversion range: –1 to + 20 mA DC Accuracy: ±0.2% of full scale Type: Passive
RTD INPUTS
Types (3-wire): 100 Ω Platinum, 100 and 120 Ω Nickel, 10 Ω Copper Sensing current: 5 mA Range: –50 to +250°C Accuracy: ±2°C Isolation: 36 V pk-pk
IRIG-B INPUT
IRIG formats accepted: B000…B007, B120…B127 IRIG control bits: IEEE Std C37.118.1-2011 Amplitude modulation: 1 to 10 V pk-pk DC shift: TTL–Compatible Input impedance: 50 kΩ Isolation: 2 kV
2-30 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS
DIRECT INPUTS
Input points: 32 Remote devices: 16 Default states on loss of comms.: On, Off, Latest/Off, Latest/On Ring configuration: Yes, No Data rate: 64 or 128 kbps CRC: 32-bit CRC alarm:
Responding to: Rate of messages failing the CRC Monitoring message count: 10 to 10000 in steps of 1 Alarm threshold: 1 to 1000 in steps of 1
Unreturned message alarm:
Responding to: Rate of unreturned messages in the ring configuration Monitoring message count: 10 to 10000 in steps of 1 Alarm threshold: 1 to 1000 in steps of 1
TELEPROTECTION
Input points: 16 Remote devices: 3 Default states on loss of comms.: On, Off, Latest/Off, Latest/On Ring configuration: No Data rate: 64 or 128 kbps CRC: 32-bit
2

2.5.6 Power supply

LOW RANGE
Nominal DC voltage: 24 to 48 V Minimum DC voltage: 20 V Maximum DC voltage: 75 V for SL power supply module Voltage loss hold-up: 200 ms duration at maximum load NOTE: Low range is DC only.
HIGH RANGE
Nominal DC voltage: 125 to 250 V Minimum DC voltage: 88 V Maximum DC voltage: 300 V Nominal AC voltage: 100 to 240 V at 50/60 Hz Minimum AC voltage: 88 V at 25 to 100 Hz Maximum AC voltage: 265 V at 25 to 100 Hz Voltage loss hold-up: 200 ms duration at maximum load
ALL RANGES
Volt withstand: 2 × Highest Nominal Voltage for 10 ms Power consumption: typical = 15 to 20 W/VA
maximum = 45 W/VA contact factory for exact order code consumption
INTERNAL FUSE
Ratings:
Low range power supply: 8 A / 250 V High range power supply: 4 A / 250 V
Interrupting capacity:
AC: 100 000 A RMS symmetrical DC: 10 000 A
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-31
2
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION

2.5.7 Outputs

FORM-A RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90 Carry continuous: 6 A Break (DC inductive, L/R = 40 ms):
Voltage Current
24 V 1 A 48 V 0.5 A 125 V 0.3 A 250 V 0.2 A
Operate time: < 4 ms Contact material: silver alloy
LATCHING RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90 Carry continuous: 6 A as per IEEE C37.90 Break (DC resistive as per IEC61810-1):
Voltage Current
24 V 6 A 48 V 1.6 A 125 V 0.4 A 250 V 0.2 A
Operate time: < 4 ms Contact material: silver alloy Control: separate operate and reset inputs Control mode: operate-dominant or reset-dominant
FORM-A VOLTAGE MONITOR
Applicable voltage: approx. 15 to 250 V DC Trickle current: approx. 1 to 2.5 mA
FORM-A CURRENT MONITOR
Threshold current: approx. 80 to 100 mA
FORM-C AND CRITICAL FAILURE RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90 Carry continuous: 8 A Break (DC inductive, L/R = 40 ms):
Voltage Current
24 V 1 A 48 V 0.5 A 125 V 0.3 A 250 V 0.2 A
Operate time: < 8 ms Contact material: silver alloy
FAST FORM-C RELAY
Make and carry: 0.1 A max. (resistive load)
2-32 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS
Minimum load impedance:
Input voltage Impedance
2 W Resistor 1 W Resistor
250 V DC 20 KΩ 50 KΩ 120 V DC 5 KΩ 2 KΩ 48 V DC 2 KΩ 2 KΩ 24 V DC 2 KΩ 2 KΩ Note: values for 24 V and 48 V are the same due to a
required 95% voltage drop across the load impedance.
Operate time: < 0.6 ms Internal Limiting Resistor: 100 Ω, 2 W
SOLID-STATE OUTPUT RELAY
Operate and release time: <100 µs Maximum voltage: 265 V DC Maximum leakage current in off state (excluding voltage monitor circuit current): 100 µA Maximum continuous current: 5 A at 45°C; 4 A at 65°C Make and carry:
for 0.2 s: 30 A as per ANSI C37.90 for 0.03 s: 300 A
Breaking capacity:
2
Specification UL 508 Utility application
Operations per interval
Break capability (0 to 250 V DC)
5000 operations, 1 second on, 9 seconds off
1000 operations
0.5 seconds on,
0.5 seconds off
3.2 A at L/R = 10 ms 10 A at L/R = 40 ms 10 A at L/R = 40 ms
1.6 A at L/R = 20 ms
0.8 A L/R =40ms
(autoreclose scheme)
5 operations
0.2 seconds on
0.2 seconds off within 1 minute
Industrial application
10000 operations
0.2 seconds on 30 seconds off
CONTROL POWER EXTERNAL OUTPUT (FOR DRY CONTACT INPUT)
Capacity: 100 mA DC at 48 V DC Isolation: ±300 Vpk
DIRECT OUTPUTS
Output points: 32
DCMA OUTPUTS
Range: –1 to 1 mA, 0 to 1 mA, 4 to 20 mA Max. load resistance: 12 kΩ for –1 to 1 mA range
12 kΩ for 0 to 1 mA range 600 Ω for 4 to 20 mA range
Accuracy: ±0.75% of full-scale for 0 to 1 mA range
±0.5% of full-scale for –1 to 1 mA range
±0.75% of full-scale for 0 to 20 mA range 99% Settling time to a step change: 100 ms Isolation: 1.5 kV Driving signal: any FlexAnalog quantity Upper and lower limit for the driving signal: –90 to 90 pu in steps of 0.001
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-33
2
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION

2.5.8 Communication protocols

IEC 61850
IEC 61850: Supports IEC 61850 Edition 2.0. See the UR Family Communications Guide and its conformance
statements.
RS232
Front port: 19.2 or 115.2 kbps, Modbus RTU
RS485
1 rear port: up to 115 kbps, Modbus RTU, DNP 3, IEC 60870-5-103 Typical distance: 1200 m Isolation: 2 kV, isolated together at 36 Vpk
FIBER ETHERNET PORT
Parameter Fiber type
100 Mb multimode
Wavelength 1310 nm Connector LC Transmit power –20 dBm Receiver sensitivity –30 dBm Power budget 10 dB Maximum input power –14 dBm Typical distance 2 km Full duplex yes Redundancy yes
ETHERNET (10/100 MB TWISTED PAIR)
Modes: 10 Mb, 10/100 Mb (auto-detect) Connector: RJ45
SIMPLE NETWORK TIME PROTOCOL (SNTP)
Clock synchronization error: <10 ms (typical)
PRECISION TIME PROTOCOL (PTP)
PTP IEEEStd1588 2008 (version 2) Power Profile (PP) per IEEEStandardPC37.238TM2011 Slave-only ordinary clock Peer delay measurement mechanism
PARALLEL REDUNDANCY PROTOCOL (PRP) (IEC 62439-3 CLAUSE 4, 2012)
Ethernet ports used: 2 and 3 Networks supported: 10/100 Mb Ethernet
OTHER
TFTP, SFTP, HTTP, IEC 60870-5-104, Ethernet Global Data (EGD), IEEE C37.118
2-34 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS

2.5.9 Inter-relay communications

SHIELDED TWISTED-PAIR INTERFACE OPTIONS
Interface type Typical distance
RS422 1200 m G.703 100 m
RS422 distance is based on transmitter power and does not take into consideration the clock source provided by the user.
LINK POWER BUDGET AND MAXIMUM OPTICAL INPUT POWER
The following specifications apply to filter interface modules manufactured from January 2012.
Emitter, fiber type Cable type Transmit power Received
820 nm, Multimode 62.5/125 μm -16 dBm -32 dBm 16 dBm -8 dBm
50/125 μm -20 dBm 12 dBm
1300 nm, Multimode 62.5/125 μm -16 dBm -32 dBm 16 dBm -8 dBm
50/125 μm -20 dBm 12 dBm
1300 nm, Single mode
1300 nm Laser, Single mode
1550 nm Laser, Single mode
The following specifications apply to filter interface modules implemented before January 2012.
Emitter, fiber type Transmit
820 nm LED, Multimode –20 dBm –30 dBm 10 dB –7.6 dBm 1300 nm LED, Multimode –21 dBm –30 dBm 9 dB –11 dBm 1300 nm ELED, Single mode –23 dBm –32 dBm 9 dB –14 dBm 1300 nm Laser, Single mode –1 dBm –30 dBm 29 dB –14 dBm 1550 nm Laser, Single mode +5 dBm –30 dBm 35 dB –14 dBm
9/125 μm -15 dBm -32 dBm 17 dBm -8 dBm
9/125 μm 0 dBm -34 dBm 34 dBm -8 dBm
9/125 μm 5 dBm -34 dBm 39 dBm -10 dBm
power
Received sensitivity
sensitivity
Power budget Maximum optical
Power budget Maximum
optical input power
input power
2
The power budgets are calculated from the manufacturer’s worst-case transmitter power and worst case receiver sensitivity.
The power budgets for the 1300 nm ELED are calculated from the manufacturer's transmitter power and receiver sensitivity at ambient temperature. At extreme temperatures these values deviate based on component tolerance. On average, the output power decreases as the temperature is increased by a factor of 1 dB / 5 °C.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-35
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
TYPICAL LINK DISTANCE
2
Emitter, fiber type Cable type Connector
820 nm LED, multimode
1300 nm LED, multimode
1300 nm ELED, single mode
1300 nm Laser, single mode
1550 nm Laser, single mode
62.5/125 μm ST 1.65 km 2 km 50/125 μm ST 1.65 km 2 km
62.5/125 μm ST 4 km 5 km 50/125 μm ST 4 km 5 km 9/125 μm ST 11.4 km 20 km
9/125 μm ST 64 km 65 km
9/125 μm ST 105 km 125 km
type
Typical distance Before
January 2012
From January 2012
Typical distances listed are based on the following assumptions for system loss. As actual losses vary from one installation to another, the distance covered by your system can vary.
CONNECTOR LOSSES (TOTAL OF BOTH ENDS)
ST connector: 0.7 dB (each)
FIBER LOSSES
820 nm multimode: 3 dB/km 1300 nm multimode: 1 dB/km 1300 nm single mode: 0.35 dB/km 1550 nm single mode: 0.25 dB/km Splice losses: one splice every 2 km at 0.05 dB loss per splice
SYSTEM MARGIN
3 dB additional loss added to calculations to compensate for all aging and other losses.
Compensated difference in transmitting and receiving (channel asymmetry) channel delays using GPS satellite clock: 10 ms

2.5.10 CyberSentry security

OPTIONS
Software options: Level 1

2.5.11 Environmental

AMBIENT TEMPERATURES
Storage temperature: –40 to 85°C Operating temperature: –40 to 60°C; the LCD contrast can be impaired at temperatures less than –20°C
HUMIDITY
Humidity: operating up to 95% (non-condensing) at 55°C (as per IEC60068-2-30 variant 1, 6 days)
OTHER
Altitude: 2000 m (maximum) Pollution degree: II Overvoltage category: II Ingress protection: IP20 front, IP10 back Noise: 0 dB
2-36 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 2: PRODUCT DESCRIPTION SPECIFICATIONS

2.5.12 Type tests

F60 TYPE TESTS
Test Reference standard Test level
Dielectric voltage withstand EN 60255-5 Impulse voltage withstand EN 60255-5 Damped oscillatory IEC 61000-4-18 / IEC 60255-22-1 2.5 kV CM, 1 kV DM Electrostatic discharge EN 61000-4-2 / IEC 60255-22-2 Level 3 RF immunity EN 61000-4-3 / IEC 60255-22-3 Level 3 Fast transient disturbance EN 61000-4-4 / IEC 60255-22-4 Class A and B Surge immunity EN 61000-4-5 / IEC 60255-22-5 Level 3 and 4 Conducted RF immunity EN 61000-4-6 / IEC 60255-22-6 Level 3 Power frequency immunity EN 61000-4-7 Voltage interruption and ripple DC IEC 60255-11 12% ripple, 200 ms interrupts Radiated and conducted emissions CISPR11 / CISPR22 / IEC 60255-25 Class A Sinusoidal vibration IEC 60255-21-1 Class 1 Shock and bump IEC 60255-21-2 Class 1 Seismic IEC 60255-21-3 Class 1 Power magnetic immunity IEC 61000-4-8 Level 5 Pulse magnetic immunity IEC 61000-4-9 Level 4 Damped magnetic immunity IEC 61000-4-10 Level 4 Voltage dip and interruption IEC 61000-4-11 0, 40, 70, 80% dips; 250 / 300 cycle interrupts Damped oscillatory IEC 61000-4-12 Conducted RF immunity, 0 to 150 kHz IEC 61000-4-16 Level 4 Voltage ripple IEC 61000-4-17 15% ripple Ingress protection IEC 60529 Cold IEC 60068-2-1 –40°C for 16 hours Hot IEC 60068-2-2 85°C for 16 hours Humidity IEC 60068-2-30 6 days, variant 1 Damped oscillatory IEEE/ANSI C37.90.1 2.5 kV, 1 MHz RF immunity IEEE/ANSI C37.90.2 20 V/m, 80 MHz to 1 GHz Safety UL 508 e83849 NKCR Safety UL C22.2-14 e83849 NKCR7 Safety UL 1053 e83849 NKCR Safety IEC 60255-27 Insulation: class 1, Pollution degree: 2, Over
1
1
1
/ IEC 60255-22-7 Class A and B
1
1
2.2 kV 5 kV
2.5 kV CM, 1 kV DM
IP20 front, IP10 back
voltage cat II
2
1 Not tested by third party.

2.5.13 Production tests

THERMAL
Products go through an environmental test based upon an Accepted Quality Level (AQL) sampling process.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 2-37
2
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION

2.5.14 Approvals

APPROVALS
Compliance Applicable council directive According to
CE Low voltage directive EN 60255-5
EMC directive EN 60255-26 / EN 50263
EN 61000-6-5
C-UL-US --- UL 508
UL 1053 C22.2 No. 14

2.5.15 Maintenance

MOUNTING
Attach mounting brackets using 20 inch-pounds (±2 inch-pounds) of torque.
CLEANING
Normally, cleaning is not required. When dust has accumulated on the faceplate display, wipe with a dry cloth.
To avoid deterioration of electrolytic capacitors, power up units that are stored in a de-energized state once per year, for one hour continuously.
2-38 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
F60 Feeder Protection System
Chapter 3: Installation

Installation

This chapter outlines installation of hardware and software. You unpack, check, mount, and wire the unit, then install the software and configure settings.

3.1 Unpack and inspect

Use this procedure to unpack and inspect the unit.
1. Open the relay package and check that the following items have been delivered:
–F60 – Mounting screws – GE EnerVista™ DVD (software and documentation) – F60 Instruction Manual (soft copy on DVD; printed copy if ordered) – UR Family Communications Guide (soft copy on DVD; printed copy if Instruction Manual ordered) –Certificate of Calibration –Test Report – EC Declaration of Conformity
2. Inspect the unit for physical damage.
3. View the rear nameplate and verify that the correct model has been delivered. The model number is at the top right.
4. For any issues, contact GE Grid Solutions as outlined in the For Further Assistance section in chapter 1.
5. Check that you have the latest copy of the F60 Instruction Manual and the UR Family Communications Guide, for the
applicable firmware version, at http://gegridsolutions.com/multilin/manuals/index.htm
The Instruction Manual outlines how to install, configure, and use the unit. The Communications Guide is for advanced use with communication protocols. The warranty is included at the end of this instruction manual and on the GE Digital Energy website.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-1
PANEL CUTOUTS CHAPTER 3: INSTALLATION

3.2 Panel cutouts

This section does not apply to the HardFiber Brick; see its instruction manual. Install the relay in an indoor environment within the environmental specifications. The relay complies with Pollution
Category II, which means installation in an office, laboratory, or testing environment.
The front panel can be switched in the EnerVista software between enhanced and standard panels under
Maintenance > Change Front Panel.

3.2.1 Horizontal units

3
The F60 is available as a 19-inch rack horizontal mount unit with a removable faceplate. The faceplate can be specified as either standard or enhanced at the time of ordering. The enhanced faceplate contains additional user-programmable pushbuttons and LED indicators.
The modular design allows the relay to be upgraded and repaired by qualified service personnel. The faceplate is hinged to allow access to the removable modules, and is itself removable to allow mounting on doors with limited rear depth.
The case dimensions are shown in the following figure, along with panel cutout details for panel mounting. When planning the location of your panel cutout, ensure that provision is made for the faceplate to swing open without interference to or from adjacent equipment.
The relay must be mounted such that the faceplate sits semi-flush with the panel or switchgear door, allowing the operator access to the keypad and the RS232 communications port. The relay is secured to the panel with the use of four screws supplied with the relay.
Figure 3-1: Horizontal dimensions (enhanced panel)
3-2 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION PANEL CUTOUTS
Figure 3-2: Horizontal mounting (enhanced panel)
Figure 3-3: Horizontal mounting and dimensions (standard panel)
3

3.2.2 Vertical units

The F60 is available as a reduced size (¾) vertical mount unit, with a removable faceplate. The faceplate can be specified as either standard or enhanced at the time of ordering. The enhanced faceplate contains additional user-programmable pushbuttons and LED indicators.
The modular design allows the relay to be upgraded and repaired by qualified service personnel. The faceplate is hinged to allow easy access to the removable modules, and is itself removable to allow mounting on doors with limited rear depth.
The case dimensions are shown in the following figure, along with panel cutout details for panel mounting. When planning the location of your panel cutout, ensure that provision is made for the faceplate to swing open without interference to or from adjacent equipment.
The relay must be mounted such that the faceplate sits semi-flush with the panel or switchgear door, allowing the operator access to the keypad and the RS232 communications port. The relay is secured to the panel with the use of four screws supplied with the relay.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-3
3
PANEL CUTOUTS CHAPTER 3: INSTALLATION
Figure 3-4: Vertical dimensions (enhanced panel)
3-4 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION PANEL CUTOUTS
Figure 3-5: Vertical and mounting dimensions (standard panel)
3
For side-mounting F60 devices with the enhanced front panel, see the following documents available on the UR DVD and the GE Grid Solutions website:
GEK-113180
GEK-113181
GEK-113182
Instruction Sheet
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-5
— UR-Series UR-V Side-Mounting Front Panel Assembly Instructions — Connecting a Remote UR-V Enhanced Front Panel to a Vertical UR Device Instruction Sheet — Connecting a Remote UR-V Enhanced Front Panel to a Vertically-Mounted Horizontal UR Device
3
PANEL CUTOUTS CHAPTER 3: INSTALLATION
For side-mounting F60 devices with the standard front panel, use the following figures.
Figure 3-6: Vertical side-mounting installation (standard panel)
3-6 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION PANEL CUTOUTS
Figure 3-7: Vertical side-mounting rear dimensions (standard panel)
3
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-7
3
PANEL CUTOUTS CHAPTER 3: INSTALLATION

3.2.3 Rear terminal layout

Do not touch any rear terminals while the relay is energized, else death or serious injury can result from electrical shock.
The small form-factor pluggable ports (SFPs) are pluggable transceivers. Do not use non-validated transceivers or install validated transceivers in the wrong Ethernet slot, else damage can occur.
The relay follows a convention with respect to terminal number assignments, which are three characters long and assigned by module slot position, row number, and column letter. Two-slot wide modules take their slot designation from the first slot position (nearest to CPU module), indicated by an arrow marker on the terminal block. The figure shows an example of rear terminal assignments.
Figure 3-8: Example of modules in F and H slots
3-8 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING

3.3 Wiring

3.3.1 Typical wiring

Figure 3-9: Typical wiring diagram (T module shown for CPU)
3
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-9
WIRING CHAPTER 3: INSTALLATION
832780A2.CDR
(Rear view)
1
Power Supply
9
CPU
8
CT/VT
6 Digital inputs/
outputs
8
CT
8
Digital inputs/ outputs
6
Digital inputs/ outputs
6
Digital inputs/ outputs
MODULE ARRANGEMENT
JU
MXLWKVBHTD
N
GS
PFR
CONTACTS SHOWN
WITH NO
CONTROL POWER
TYPICAL CONFIGURATION
THE AC SIGNAL PATH IS CONFIGURABLE
F60
FEEDER MANAGEMENT RELAY
AC or DC
DC
( DC ONLY )
F60 COMPUTER
1
TXD RXD RXD TXD
SGND SGND
1
8 3 2
20
7 6 4 5
22
25 PIN CONNECTOR
9 PIN
CONNECTOR
22 33 44 55 66 77 88 99
RS-232
(front)
DB-9
CRITICAL FAILURE
48 VDC
OUTPUT
CONTROL
POWER
HI LO
POWER SUPPLY
1
FILTER
SURGE
B3a
B1b
B8a
B6b
B8b
B6a
B3b
B1a B2b
B5b
GROUND BUS
No. 10AWG
minimum
MODULES MUST BE
GROUNDED IF
TERMINAL IS
PROVIDED
I
V
I
V
CONTACT INPUT H7a CONTACT INPUT H7c CONTACT INPUT H8a CONTACT INPUT H8c
COMMON H7b
DIGITAL INPUTS/OUTPUTS
6B
H1b
H2b
H3b
H4b
H5b
H6b
H1a
H2a
H3a
H4a
H5a
H6a
H1c
H2c
H3c
H4c
H5c
H6c
H1
H5
H2
H6
H3
H4
H8a
H7b
H7a
H8c
H7c
SURGE
H8b
6C
DIGITAL INPUTS/OUTPUTS
P1
P5
P2
P6
P3
P7
P4
P8
P7a
P1a
P2b
P7c
P1c
P7b
P1b
P8c
P8b
P2c
P8a
P2a
P4a
P5b
P4c
P6b
P3b
P3a
P6a
P4b
P5c
P5a
P3c
P6c
M7c
M8c
M8b
M8a
M5c
M5b
M5a
M7b
M7a
M3c
M4b
M4a
M4c
M1c
M2b
M2a
M6b
M6a
M6c
M2c
M1b
M1a
M3b
M3a
CURRENT INPUTS NOT USED
8Z
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
CONNECTION
AS REQUIRED
OPEN DELTA
VT CONNECTION (ABC)
A
B
C
POSITIVE WATTS
(5 Amp CT)
52
8F / 8L / 8G / 8M
F8c
F8a
F7c
F5a
F5c
F6a
F7a
F6c
VX
VA
VB
VC
VOLTAGE INPUTS
VX
VA
VB
VC
F1c
F3c
F3b
CURRENT INPUTS
F2c
F4c
F1a
F4b
F4a
F1b
F2a
F3a
F2b
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
F5a
F5c
F6a
F7a
F7c
F6c
VA
VB
VC
VOLTAGE INPUTS
VA
VB
VC
* Optional
D1a D2a
D4b
D3a
D4a
IRIG-B
Input
COM
2
RS485 COM 2
ALTERNATE
NORMAL
com
CPU T
100BaseFX
Tx2
Rx2
Tx1
Rx1
BNC
Fibre Optic
*
Ground at
Remote
Device
Shielded
twisted pairs
Co-axial
Co-axial *
Co-axial * - For IRIG-B Input only use one terminal as input
This diagram is based on the following order code:
F60-T00-HCH-F8F-H6B-M8Z-P6C-UXX-WXX
This diagram provides an example of how the device is wired, not specifically how to wire the device. Please refer to the Instruction Manual for additional details on wiring based on various configurations.
100BaseFX
100BaseFX
Tx3
Rx3
3

3.3.2 Dielectric strength

Dielectric strength is the maximum electric strength that can be sustained without breakdown. It is measured in volts. The table shows the dielectric strength of the UR-series module hardware.
3-10 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
Figure 3-10: Typical wiring diagram with high-impedance detection (T module shown for CPU)
CHAPTER 3: INSTALLATION WIRING
Table 3-1: Dielectric strength of UR series modules
Module type Module function Terminals Dielectric strength
From To
1 Power supply High (+); Low (+); (–) Chassis 2000 V AC for 1 minute 1 Power supply 48 V DC (+) and (–) Chassis 2000 V AC for 1 minute 1 Power supply Relay terminals Chassis 2000 V AC for 1 minute 2 Reserved N/A N/A N/A 3 Reserved N/A N/A N/A 4 Digital contact inputs/
outputs 5 Analog inputs/outputs All except 8b Chassis < 50 V DC 6 Digital contact inputs/
outputs 7 G.703 All except 2b, 3a, 7b, 8a Chassis 2000 V AC for 1 minute
RS422 All except 6a, 7b, 8a Chassis < 50 V DC 8 CT/VT All Chassis 2000 V AC for 1 minute 9 CPU All Chassis 2000 V AC for 1 minute
All Chassis 2000 V AC for 1 minute
All Chassis 2000 V AC for 1 minute
Filter networks and transient protection clamps are used in the hardware to prevent damage caused by high peak voltage transients, radio frequency interference (RFI), and electromagnetic interference (EMI). These protective components can be damaged by application of the ANSI/IEEE C37.90 specified test voltage for a period longer than the specified minute.
3

3.3.3 Control power

Control power supplied to the relay must be connected to the matching power supply range of the relay. If voltage is applied to the wrong terminals, damage can occur.
The F60, like almost all electronic relays, contains electrolytic capacitors. These capacitors are well­known to deteriorate over time if voltage is not applied periodically. Deterioration can be avoided by powering up the relay at least once a year.
The power supply module can be ordered for two possible voltage ranges, and the F60 can be ordered with or without a redundant power supply module option. Each range has a dedicated input connection for proper operation. The ranges are as follows (see the Specifications section of chapter 2 for details):
Low (LO) range — 24 to 48 V (DC only) nominal
High (HI) range — 125 to 250 V nominal The power supply module provides power to the relay and supplies power for dry contact input connections. The power supply module provides 48 V DC power for dry contact input connections and a critical failure relay (see the
Typical Wiring Diagram earlier). The critical failure relay is a form-C device that is energized once control power is applied and the relay has successfully booted up with no critical self-test failures. If on-going self-test diagnostic checks detect a critical failure (see the Self-Test Errors section in chapter 7) or control power is lost, the relay de-energizes.
For high-reliability systems, the F60 has a redundant option in which two F60 power supplies are placed in parallel on the bus. If one of the power supplies becomes faulted, the second power supply assumes the full load of the relay without any interruptions. Each power supply has a green LED on the front of the module to indicate that it is functional. The critical fail relay of the module also indicates a faulted power supply.
An LED on the front of the control power module shows the status of the power supply, as outlined in the table.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-11
3
WIRING CHAPTER 3: INSTALLATION
Table 3-2: Power supply LED on front panel
LED indication Power supply
Continuous on OK On/off cycling Failure Off Failure or no power
Figure 3-11: Control power connection

3.3.4 CT/VT modules

The CT and VT inputs are analog current transformer and voltage transformer signals used to monitor AC power lines. The UR-series relays support 1 A and 5 A CTs.
A CT/VT module can have current or voltage inputs on channels 1 through 4 inclusive, or channels 5 through 8 inclusive. Channels 1 and 5 are intended for connection to phase A, and are labeled as such in the relay. Likewise, channels 2 and 6 are intended for connection to phase B, and channels 3 and 7 are intended for connection to phase C.
Channels 4 and 8 are intended for connection to a single-phase source. For voltage inputs, these channels are labeled as auxiliary voltage (VX). For current inputs, these channels are intended for connection to a CT between system neutral and ground, and are labelled as ground current (IG).
Verify that the connection made to the relay terminals for nominal current of 1 A or 5 A matches the secondary rating of the connected CTs. Unmatched CTs can result in equipment damage or inadequate protection.
To connect the module, size 12 American Wire Gauge (AWG) is used commonly; the maximum size is 10 AWG. CT/VT modules can be ordered with a standard ground current input that is the same as the phase current input. Each AC
current input has an isolating transformer and an automatic shorting mechanism that shorts the input when the module is withdrawn from the chassis. There are no internal ground connections on the current inputs. Current transformers with 1 to 50000 A primaries and 1 A or 5 A secondaries can be used.
CT/VT modules with a sensitive ground input are also available. The ground CT input of the sensitive ground modules is 10 times more sensitive than the ground CT input of standard CT/VT modules. However, the phase CT inputs and phase VT inputs are the same as those of regular CT/VT modules.
These modules have enhanced diagnostics that can automatically detect CT/VT hardware failure and take the relay out of service.
CT connections for both ABC and ACB phase rotations are identical, as shown in the Typical Wiring Diagram.
3-12 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
The exact placement of a zero-sequence core balance CT to detect ground fault current is shown as follows. Twisted-pair cabling on the zero-sequence CT is recommended.
Figure 3-12: Zero-sequence core balance CT installation
3
The phase voltage channels are used for most metering and protection purposes. The auxiliary voltage channel is used as input for the synchrocheck and volts-per-hertz features, which are optional features available for some UR models.
Substitute the tilde “~” symbol with the slot position of the module in the following figure.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-13
3
WIRING CHAPTER 3: INSTALLATION
Figure 3-13: CT/VT module wiring
A relay configured for high impedance fault detection element includes two CT/VT modules: one type 8F, 8G, 8H, or 8J module and one type 8Z module. For correct operation of the high impedance fault detection element, the ground current terminals of the two CT modules must be connected to a ground current source, either a zero-sequence CT (see the Typical wiring diagram with high impedance fault detection earlier in this chapter) or, if a zero-sequence CT is not available, to the neutral conductor of the phase CTs (see diagram below).
3-14 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
Figure 3-14: Typical 8Z module wiring with phase CTs
3

3.3.5 Process bus modules

The F60 can be ordered with a process bus interface module. The module interfaces with the HardFiber Process Bus System, or HardFiber Brick, allowing bidirectional IEC 61850 fiber optic communications with up to eight HardFiber Bricks. The HardFiber system integrates seamlessly with the existing UR-series applications, including protection functions, FlexLogic, metering, and communications.
This process bus system offers the following benefits:
Reduces labor associated with design, installation, and testing of protection and control applications using the UR by reducing the number of individual copper terminations
Integrates seamlessly with existing UR applications, since the IEC 61850 process bus interface module replaces the traditional CT/VT modules
Communicates using open standard IEC 61850 messaging
For details on the HardFiber system, see its Instruction Manual.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-15
3
WIRING CHAPTER 3: INSTALLATION

3.3.6 Contact inputs and outputs

Every contact input/output module has 24 terminal connections. They are arranged as three terminals per row, with eight rows in total. A given row of three terminals can be used for the outputs of one relay. For example, for form-C relay outputs, the terminals connect to the normally open (NO), normally closed (NC), and common contacts of the relay. For a form-A output, there are options of using current or voltage detection for feature supervision, depending on the module ordered. The terminal configuration for contact inputs is different for the two applications.
The contact inputs are grouped with a common return. The input/output modules have two versions of grouping: four inputs per common return and two inputs per common return. When a contact input/output module is ordered, four inputs per common is used. If the inputs must be isolated per row, then two inputs per common return are selected (4D module).
The tables and diagrams on the following pages illustrate the module types (6A and so on) and contact arrangements that can be ordered for the relay. Since an entire row is used for a single contact output, the name is assigned using the module slot position and row number. However, since there are two contact inputs per row, these names are assigned by module slot position, row number, and column position.
Some form-A / solid-state relay outputs include circuits to monitor the DC voltage across the output contact when it is open, and the DC current through the output contact when it is closed. Each of the monitors contains a level detector whose output is set to logic “On = 1” when the current in the circuit is above the threshold setting. The voltage monitor is set to “On = 1” when there is a voltage across open contact (the detector allows a current of about 1 to 2.5 mA), and the current monitor is set to “On = 1” when the current flowing through the closed contact exceeds about 80 to 100 mA. The voltage monitor is intended to check the health of the overall trip circuit, and the current monitor can be used to seal-in the output contact until an external contact has interrupted current flow. If enabled, the current monitoring can be used as a seal-in signal to ensure that the form-A contact does not attempt to break the energized inductive coil circuit and weld the output contacts.
Block diagrams are shown as follows for form-A and solid-state relay outputs with optional voltage monitor, optional current monitor, and with no monitoring. The actual values shown for contact output 1 are the same for all contact outputs. Form-A contact output with or without a current or voltage monitoring option is not polarity sensitive. The polarity shown in the figure is required for solid-state contact output connection.
Figure 3-15: Form-A and solid-state contact outputs with voltage and current monitoring
3-16 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
The operation of voltage and current monitors is reflected with the corresponding FlexLogic operands (CONT OP # VON, CONT
OP # VOFF, and CONT OP # ION) that can be used in protection, control, and alarm logic. The typical application of the voltage
monitor is breaker trip circuit integrity monitoring; a typical application of the current monitor is seal-in of the control command.
See the Digital Elements section of chapter 5 for an example of how form-A and solid-state relay contacts can be applied for breaker trip circuit integrity monitoring.
Consider relay contacts unsafe to touch when the unit is energized. Death or serious injury can result from touching live relay contacts.
USE OF FORM-A AND SOLID-STATE RELAY OUTPUTS IN HIGH-IMPEDANCE CIRCUITS For form-A and solid-state relay output contacts internally equipped with a voltage measuring circuit across the
contact, the circuit has an impedance that can cause a problem when used in conjunction with external high-input impedance monitoring equipment such as modern relay test set trigger circuits. These monitoring circuits can continue to read the form-A contact as being closed after it has closed and subsequently opened, when measured as an impedance.
The solution is to use the voltage measuring trigger input of the relay test set, and connect the form-A contact through a voltage-dropping resistor to a DC voltage source. If the 48 V DC output of the power supply is used as a source, a 500 , 10 W resistor is appropriate. In this configuration, the voltage across either the form-A contact or the resistor can be used to monitor the state of the output.
3
Where a tilde “~” symbol appears, substitute the slot position of the module. Where a number sign “#” appears, substitute the contact number.
When current monitoring is used to seal-in the form-A and solid-state relay contact outputs, give the FlexLogic operand driving the contact output a reset delay of 10 ms to prevent damage of the output contact (in situations when the element initiating the contact output is bouncing, at values in the region of the pickup value).
Table 3-3: Contact input and output module assignments
~6A module ~6B module ~6C module ~6D module Terminal
assignment
~1 Form-A ~1 Form-A ~1 Form-C ~1a, ~1c 2 Inputs ~2 Form-A ~2 Form-A ~2 Form-C ~2a, ~2c 2 Inputs ~3 Form-C ~3 Form-C ~3 Form-C ~3a, ~3c 2 Inputs ~4 Form-C ~4 Form-C ~4 Form-C ~4a, ~4c 2 Inputs ~5a, ~5c 2 Inputs ~5 Form-C ~5 Form-C ~5a, ~5c 2 Inputs ~6a, ~6c 2 Inputs ~6 Form-C ~6 Form-C ~6a, ~6c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7 Form-C ~7a, ~7c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8 Form-C ~8a, ~8c 2 Inputs
~6E module ~6F module ~6G module ~6H module Terminal
assignment ~1Form-C~1Fast Form-C~1 Form-A ~1 Form-A ~2Form-C~2Fast Form-C~2 Form-A ~2 Form-A ~3Form-C~3Fast Form-C~3 Form-A ~3 Form-A ~4Form-C~4Fast Form-C~4 Form-A ~4 Form-A
Output or input
Output or input
Terminal assignment
Terminal assignment
Output or input
Output Terminal
Terminal assignment
assignment
Output Terminal
Output or input
assignment
Terminal assignment
Output
Output or input
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-17
3
WIRING CHAPTER 3: INSTALLATION
~6E module ~6F module ~6G module ~6H module Terminal
assignment ~5a, ~5c 2 Inputs ~5Fast Form-C~5a, ~5c 2 Inputs ~5 Form-A ~6a, ~6c 2 Inputs ~6Fast Form-C~6a, ~6c 2 Inputs ~6 Form-A ~7a, ~7c 2 Inputs ~7Fast Form-C~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~8a, ~8c 2 Inputs ~8Fast Form-C~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
~6K module ~6L module ~6M module ~6N module Terminal
assignment
~1 Form-C ~1Form-A~1Form-A~1Form-A ~2 Form-C ~2Form-A~2Form-A~2Form-A ~3 Form-C ~3Form-C~3Form-C~3Form-A ~4 Form-C ~4Form-C~4Form-C~4Form-A ~5 Fast Form-C ~5a, ~5c 2 Inputs ~5Form-C~5a, ~ ~6 Fast Form-C ~6a, ~6c 2 Inputs ~6Form-C~6a, ~6c 2 Inputs ~7 Fast Form-C ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~8 Fast Form-C ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
Output or input
Output Terminal
Terminal assignment
assignment
Output Terminal
Output or input
assignment
Terminal assignment
Output or input
Output or input
Terminal assignment
Terminal assignment
5c 2 Inputs
Output or input
Output or input
~6P module ~6R module ~6S module ~6T module Terminal
assignment
~1 Form-A ~1Form-A~1Form-A~1Form-A ~2 Form-A ~2Form-A~2Form-A~2Form-A ~3 Form-A ~3Form-C~3Form-C~3Form-A ~4 Form-A ~4Form-C~4Form-C~4Form-A ~5 Form-A ~5a, ~5c 2 Inputs ~5Form-C~5a, ~5c 2 Inputs ~6 Form-A ~6a, ~6c 2 Inputs ~6Form-C
~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
~6U module ~6v module ~67 module ~4A module Terminal
assignment
~1 Form-A ~1 Form-A ~1Form-A~1 Not Used ~2 Form-A ~2 Form-A ~2Form-A~2 Solid-State ~3 Form-A ~3 Form-C ~3Form-A~3 Not Used ~4 Form-A ~4 2 Outputs ~4Form-A~4 Solid-State ~5 Form-A ~5a, ~5c 2 Inputs ~5Form-A~5 Not Used ~6 Form-A ~6a, ~6c 2 Inputs ~6Form-A~6 Solid-State
~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7Form-A~7 Not Used ~
8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8Form-A~8 Solid-State
Output or input
Output or input
Terminal assignment
Terminal assignment
Output or input
Output or input
Terminal assignment
Terminal assignment
Output or input
Output Terminal
Terminal assignment
~6a, ~6c 2 Inputs
assignment
Output or input
Output
3-18 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
~4B module ~4C module ~4D module ~4L module Terminal
assignment ~1Not Used~1 Not Used ~1a, ~1c 2 Inputs ~1 2 Outputs ~2 Solid-State ~2 Solid-State ~2a, ~2c 2 Inputs ~2 2 Outputs ~3Not Used~3 Not Used ~3a, ~3c 2 Inputs ~3 2 Outputs ~4 Solid-State ~4 Solid-State ~4a, ~4c 2 Inputs ~4 2 Outputs ~5Not Used~5 Not Used ~5a, ~5c 2 Inputs ~5 2 Outputs ~6 Solid-State ~6 Solid-State ~6a, ~6c 2 Inputs ~6 2 Outputs ~7Not Used~7 Not Used ~7a, ~7c 2 Inputs ~72 Outputs ~8 Solid-State ~8 Solid-State ~8a, ~8c 2 Inputs ~8 Not Used
Output Terminal
assignment
Output Terminal
assignment
Output Terminal
assignment
Output
3
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-19
3
WIRING CHAPTER 3: INSTALLATION
Figure 3-16: Contact input and output module wiring (Sheet 1 of 2)
3-20 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
Figure 3-17: Contact input and output module wiring (Sheet 2 of 2)
3
For proper functionality, observe the polarity shown in the figures for all contact input and output connections.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-21
3
WIRING CHAPTER 3: INSTALLATION
3.3.6.1 Contact inputs
A dry contact has one side connected to terminal B3b. This is the positive 48 V DC voltage rail supplied by the power supply module. The other side of the dry contact is connected to the required contact input terminal. Each contact input group has its own common (negative) terminal that must be connected to the DC negative terminal (B3a) of the power supply module. When a dry contact closes, a current of 1 to 3 mA flows through the associated circuit.
A wet contact has one side connected to the positive terminal of an external DC power supply. The other side of this contact is connected to the required contact input terminal. If a wet contact is used, then the negative side of the external source must be connected to the relay common (negative) terminal of each contact group. The maximum external source voltage for this arrangement is 300 V DC.
The voltage threshold at which each group of four contact inputs detects a closed contact input is programmable as 17 V DC for 24 V sources, 33 V DC for 48 V sources, 84 V DC for 110 to 125 V sources, and 166 V DC for 250 V sources.
Figure 3-18: Dry and wet contact input connections
Where a tilde “~” symbol appears, substitute the slot position of the module.
There is no provision in the relay to detect a DC ground fault on 48 V DC control power external output. We recommend using an external DC supply.
3.3.6.2 Use of contact inputs with auto-burnishing
The contact inputs sense a change of the state of the external device contact based on the measured current. When external devices are located in a harsh industrial environment (either outdoor or indoor), their contacts can be exposed to various types of contamination. Normally, there is a thin film of insulating sulfidation, oxidation, or contaminates on the surface of the contacts, sometimes making it difficult or impossible to detect a change of the state. This film must be removed to establish circuit continuity — an impulse of higher than normal current can accomplish this.
The contact inputs with auto-burnish create a high current impulse when the threshold is reached to burn off this oxidation layer as a maintenance to the contacts. Afterwards the contact input current is reduced to a steady-state current. The impulse has a five-second delay after a contact input changes state.
3-22 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
Figure 3-19: Current through contact inputs with auto-burnishing
Regular contact inputs limit current to less than 3 mA to reduce station battery burden. In contrast, contact inputs with auto-burnishing allow currents up to 50 to 70 mA at the first instance when the change of state was sensed. Then, within 25 to 50 ms, this current is slowly reduced to 3 mA as indicated. The 50 to 70 mA peak current burns any film on the contacts, allowing for proper sensing of state changes. If the external device contact is bouncing, the auto-burnishing starts when external device contact bouncing is over.
Another important difference between the auto-burnishing input module and the regular input modules is that only two contact inputs have common ground, as opposed to four contact inputs sharing one common ground (see the Contact Input and Output Module Wiring diagrams). This is beneficial when connecting contact inputs to separate voltage sources. Consequently, the threshold voltage setting is also defined per group of two contact inputs.
The auto-burnish feature can be disabled or enabled using the DIP switches found on each daughter card. There is a DIP switch for each contact, for a total of 16 inputs.
Figure 3-20: Auto-burnish DIP switches
3
The auto-burnish circuitry has an internal fuse for safety purposes. During regular maintenance, check the auto-burnish functionality using an oscilloscope.

3.3.7 Transducer inputs and outputs

Transducer input modules can receive input signals from external DCmA output transducers (DCmA In) or resistance temperature detectors (RTDs). Hardware and software are provided to receive signals from these external transducers and convert these signals into a digital format for use as required.
Transducer output modules provide DC current outputs in several standard DCmA ranges. Software is provided to configure virtually any analog quantity used in the relay to drive the analog outputs.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-23
3
WIRING CHAPTER 3: INSTALLATION
Every transducer input/output module has a total of 24 terminal connections. These connections are arranged as three terminals per row with a total of eight rows. A given row can be used for either inputs or outputs, with terminals in column "a" having positive polarity and terminals in column "c" having negative polarity. Since an entire row is used for a single input/output channel, the name of the channel is assigned using the module slot position and row number.
Each module also requires that a connection from an external ground bus be made to terminal 8b. The current outputs require a twisted-pair shielded cable, where the shield is grounded at one end only. The following figure illustrates the transducer module types (5A, 5C, 5D, 5E, and 5F) and channel arrangements that can be ordered for the relay.
Where a tilde “~” symbol appears, substitute the slot position of the module.
Figure 3-21: Transducer input/output module wiring
The following figure show how to connect RTDs.
3-24 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
Figure 3-22: RTD connections
3

3.3.8 RS232 faceplate port

A nine-pin RS232C serial port is located on the faceplate for programming with a computer. All that is required to use this interface is a computer running the EnerVista UR Setup software provided with the relay. Cabling for the RS232 port is shown in the following figure for both 9-pin and 25-pin connectors.
The baud rate for this port can be set, with a default of 115200 bps.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-25
3
WIRING CHAPTER 3: INSTALLATION
Figure 3-23: RS232 faceplate port connection

3.3.9 CPU communication ports

3.3.9.1 Overview
In addition to the faceplate RS232 port , there is a rear RS485 communication port. The CPU modules do not require a surge ground connection.
3-26 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION WIRING
Figure 3-24: CPU module communications wiring
3
3.3.9.2 RS485 port
RS485 data transmission and reception are accomplished over a single twisted-pair wire with transmit and receive data alternating over the same two wires. Through the use of the port, continuous monitoring and control from a remote computer, SCADA system, or Power Line Carrier (PLC) is possible.
To minimize errors from noise, the use of shielded twisted-pair wire is recommended. Correct polarity must be observed. For instance, the relays must be connected with all RS485 “+” terminals connected together, and all RS485 “–” terminals connected together. Though data is transmitted over a two-wire twisted pair, all RS485 devices require a shared reference, or common voltage. This common voltage is implied to be a power supply common. Some systems allow the shield (drain wire) to be used as common wire and to connect directly to the F60 COM terminal (#3); others function correctly only if the common wire is connected to the F60 COM terminal, but insulated from the shield.
To avoid loop currents, ground the shield at only one point. If other system considerations require the shield to be grounded at more than one point, install resistors (typically 100 ohms) between the shield and ground at each grounding point. Each relay needs to be daisy-chained to the next one in the link. A maximum of 32 relays can be connected in this manner without exceeding driver capability. For larger systems, additional serial channels must be added. It is also possible to use commercially available repeaters to have more than 32 relays on a single channel. Avoid star or stub connections entirely.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-27
3
WIRING CHAPTER 3: INSTALLATION
Lightning strikes and ground surge currents can cause large momentary voltage differences between remote ends of the communication link. For this reason, surge protection devices are provided internally at both communication ports. An isolated power supply with an optocoupled data interface also acts to reduce noise coupling. To ensure maximum reliability, ensure that all equipment has similar transient protection devices installed.
Terminate both ends of the RS485 circuit with an impedance as shown in the figure.
Figure 3-25: RS485 serial connection
3.3.9.3 100Base-FX fiber optic ports
The fiber optic communication ports allow for fast and efficient communications between relays at 100 Mbps. Optical fiber can be connected to the relay supporting a wavelength of 1310 nm in multimode.
Ensure that the dust covers are installed when the fiber is not in use. Dirty or scratched connectors can lead to high losses on a fiber link.

3.3.10 IRIG-B

IRIG-B is a standard time code format that allows stamping of events to be synchronized among connected devices. The IRIG-B code allows time accuracies of up to 100 ns. Using the IRIG-B input, the F60 operates an internal oscillator with 1 µs resolution and accuracy. The IRIG time code formats are serial, pulse width-modulated codes that can be either DC level shifted or amplitude modulated (AM). The GE MultiSync 100 1588 GPS Clock as well as third-party equipment are available for generating the IRIG-B signal; this equipment can use a global positioning system (GPS) satellite system to obtain the time reference so that devices at different geographic locations can be synchronized.
3-28 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
Figure 3-26: Options for the IRIG-B connection
3
Using an amplitude-modulated receiver causes errors up to 1 ms in event time stamping.

3.4 Direct input and output communications

3.4.1 Description

The direct inputs and outputs feature makes use of the type 7 series of communications modules and allows direct messaging between UR devices. The communications modules are outlined in the table later in this section.
The communications channels are normally connected in a ring configuration, as shown in the following figure. The transmitter of one module is connected to the receiver of the next module. The transmitter of this second module is then connected to the receiver of the next module in the ring. This is continued to form a communications ring. The figure illustrates a ring of four UR-series relays with the following connections: UR1-Tx to UR2-Rx, UR2-Tx to UR3-Rx, UR3-Tx to UR4-Rx, and UR4-Tx to UR1-Rx. A maximum of 16 URs can be connected in a single ring.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-29
3
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION
Figure 3-27: Direct input and output single-channel connection
IRC modules with protocol C37.94 and G.703 are designed for back-to-back communication connections, so the ring configuration shown in the previous figure does not apply. To establish inter-relay communication in more than two URs, you need to have two channel IRC module and enable DIRECT I/O CHANNEL CROSSOVER function in all relays, as shown in the next figure. This configuration can be expanded to 16 URs, and this configuration does not provide redundancy ring since both channels are made into single ring by the channel crossover function. As per the figure Typical Pin Interconnection between Two G.703 Interfaces later in this chapter, the clock is supplied typically by multiplexer (MUX) and all URs are in Loop Timing Mode. If there is no MUX, then UR1 and UR3 can be in Internal Timing Mode and UR2 and UR4 can be in Loop Timing Mode. That is, connected channels must have opposite timing modes.
Figure 3-28: Ring configuration for C37.94 module (concept also applies to G.703)
The interconnection for dual-channel type 7 communications modules is shown as follows. Two-channel modules allow for a redundant ring configuration. That is, two rings can be created to provide an additional independent data path. The required connections are: UR1-Tx1 to UR2-Rx1, UR2-Tx1 to UR3-Rx1, UR3-Tx1 to UR4-Rx1, and UR4-Tx1 to UR1-Rx1 for the first ring; and UR1-Tx2 to UR4-Rx2, UR4-Tx2 to UR3-Rx2, UR3-Tx2 to UR2-Rx2, and UR2-Tx2 to UR1-Rx2 for the second ring.
3-30 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
Figure 3-29: Direct input and output dual-channel connection
3
The following diagram shows the connection for three UR-series relays using two independent communication channels. UR1 and UR3 have single type 7 communication modules; UR2 has a dual-channel module. The two communication channels can be of different types, depending on the type 7 modules used. To allow the direct input and output data to cross-over from channel 1 to channel 2 on UR2, set the forces UR2 to forward messages received on Rx1 out Tx2, and messages received on Rx2 out Tx1.
Figure 3-30: Direct input and output single/dual channel combination connection
The inter-relay communications modules are available with several interfaces and some are outlined here in more detail. Those that apply depend on options purchased. The options are outlined in the Inter-Relay Communications section of the Order Code tables in Chapter 2. All of the fiber modules use ST type connectors.
DIRECT I/O CHANNEL CROSSOVER setting to “Enabled” on UR2. This
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-31
3
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION

3.4.2 Fiber: LED and ELED transmitters

The following figure shows the configuration for the 7A, 7B, 7C, 7H, 7I, and 7J fiber-only modules.
Figure 3-31: LED and ELED fiber modules

3.4.3 Fiber laser transmitters

The following figure shows the configuration for the 72, 73, 7D, and 7K fiber-laser modules.
Figure 3-32: 7x Laser fiber modules
The following figure shows configuration for the 2I and 2J fiber-laser modules.
3-32 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
Figure 3-33: 2I and 2J laser fiber modules
Observing any fiber transmitter output can injure the eye.
3
When using a laser Interface, attenuators can be necessary to ensure that you do not exceed the maximum optical input power to the receiver.

3.4.4 G.703 interface

3.4.4.1 Description
The following figure shows the 64K ITU G.703 co-directional interface configuration. The G.703 module is fixed at 64 kbps. The
applicable to this module. AWG 24 twisted shielded pair is recommended for external connections, with the shield grounded only at one end.
Connecting the shield to pin X1a or X6a grounds the shield since these pins are connected internally to ground. Thus, if pin X1a or X6a is used to ground the shield at one end, do not ground the shield at the other end. This interface module is protected by surge suppression devices.
SETTINGS PRODUCT SETUP  DIRECT I/O DIRECT I/O DATA RATE setting is not
Figure 3-34: G.703 interface configuration
The following figure shows the typical pin interconnection between two G.703 interfaces. For the actual physical arrangement of these pins, see the Rear Terminal Layout section earlier in this chapter. All pin interconnections are to be maintained for a connection to a multiplexer.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-33
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION
Figure 3-35: Typical pin interconnection between two G.703 interfaces
3
Pin nomenclature differs from one manufacturer to another. It is not uncommon to see pinouts numbered TxA, TxB, RxA, and RxB. In such cases, assume that “A” is equivalent to “+” and “B” is equivalent to “–.”
3.4.4.2 G.703 selection switch procedures
1. With the power to the relay off, remove the G.703 module (7R or 7S) as follows. Record the original location of the module to help ensure that the same or replacement module is inserted into the correct slot.
2. Simultaneously pull the ejector/inserter clips located at the top and at the bottom of each module in order to release the module for removal. (For more information on accessing modules, see the Maintenance chapter.)
3. Remove the module cover screw.
4. Remove the top cover by sliding it towards the rear and then lift it upwards.
5. Set the timing selection switches (channels 1 and 2) to the required timing modes.
6. Replace the top cover and the cover screw.
7. Re-insert the G.703 module. Take care to ensure that the correct module type is inserted into the correct slot position. The ejector/inserter clips located at the top and bottom of each module must be in the disengaged position as the module is inserted smoothly into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module is inserted fully.
3-34 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
Figure 3-36: G.703 timing selection switch setting
3
Table 3-4: G.703 timing selections
Switches Function
S1 OFF octet timing disabled
S5 and S6 S5 = OFF and S6 = OFF loop timing mode
ON octet timing 8 kHz
S5 = ON and S6 = OFF internal timing mode S5 = OFF and S6 = ON minimum remote loopback mode S5 = ON and S6 = ON dual loopback mode
3.4.4.3 G.703 octet timing
If octet timing is enabled (ON), this 8 kHz signal is asserted during the violation of bit 8 (LSB) necessary for connecting to higher order systems. When F60s are connected back-to-back, octet timing is disabled (OFF).
3.4.4.4 G.703 timing modes
There are two timing modes for the G.703 module: internal timing mode and loop timing mode (default).
Internal Timing Mode — The system clock is generated internally. Therefore, set the G.703 timing selection to internal
timing mode for back-to-back (UR-to-UR) connections. For back-to-back connections, set octet timing (S1 = OFF) and timing mode to internal timing (S5 = ON and S6 = OFF).
Loop Timing Mode — The system clock is derived from the received line signal. Therefore, set the G.703 timing
selection to loop timing mode for connections to higher order systems. For connection to a higher order system (UR­to-multiplexer, factory defaults), set to octet timing (S1 = ON) and set timing mode to loop timing (S5 = OFF and S6 = OFF).
The switch settings for the internal and loop timing modes are shown.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-35
3
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION
Figure 3-37: Switches
3.4.4.5 G.703 test modes
In minimum remote loopback mode, the multiplexer is enabled to return the data from the external interface without any processing to assist in diagnosing G.703 line-side problems irrespective of clock rate. Data enters from the G.703 inputs, passes through the data stabilization latch that also restores the proper signal polarity, passes through the multiplexer and then returns to the transmitter. The differential received data is processed and passed to the G.703 transmitter module after which point the data is discarded. The G.703 receiver module is fully functional and continues to process data and passes it to the differential Manchester transmitter module. Since timing is returned as it is received, the timing source is expected to be from the G.703 line side of the interface.
Figure 3-38: G.703 minimum remote loopback mode
In dual loopback mode, the multiplexers are active and the functions of the circuit are divided into two with each receiver/ transmitter pair linked together to deconstruct and then reconstruct their respective signals. Differential Manchester data enters the Differential Manchester receiver module and then is returned to the differential Manchester transmitter module. Likewise, G.703 data enters the G.703 receiver module and is passed through to the G.703 transmitter module to be returned as G.703 data. Because of the complete split in the communications path and because, in each case, the clocks are extracted and reconstructed with the outgoing data, in this mode there must be two independent sources of timing. One source lies on the G.703 line side of the interface while the other lies on the differential Manchester side of the interface.
Figure 3-39: G.703 dual loopback mode
3-36 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS

3.4.5 RS422 interface

3.4.5.1 Description
There are two RS422 inter-relay communications modules available: single-channel RS422 (module 7T) and dual-channel RS422 (module 7W). The modules can be configured to run at 64 kbps or 128 kbps. AWG 20-24 twisted shielded pair cable is recommended for external connections. These modules are protected by optically-isolated surge suppression devices.
The shield pins (6a and 7b) are connected internally to the ground pin (8a). Proper shield termination is as follows:
Site 1 — Terminate shield to pins 6a or 7b or both
Site 2 — Terminate shield to COM pin 2b Match the clock terminating impedance with the impedance of the line.
Figure 3-40: RS422 interface connections
3
The following figure shows the typical pin interconnection between two single-channel RS422 interfaces installed in slot W. All pin interconnections are to be maintained for a connection to a multiplexer.
Figure 3-41: Typical pin interconnect between two RS422 interfaces
3.4.5.2 Two-channel application via multiplexers
The RS422 interface can be used for single-channel or two-channel applications over SONET/SDH or multiplexed systems. When used in single-channel applications, the RS422 interface links to higher-order systems in a typical way, observing transmit (Tx), receive (Rx), and send timing (ST) connections. However, when used in two-channel applications, certain criteria must be followed since there is one clock input for the two RS422 channels. The system functions correctly when the following connections are observed and your data module has a terminal timing feature. Terminal timing is a common feature to most synchronous data units that allows the module to accept timing from an external source. Using the terminal timing feature, two-channel applications can be achieved if these connections are followed: the send timing outputs from the multiplexer (data module 1) connects to the clock inputs of the UR RS422 interface in the usual way. In
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-37
3
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION
addition, the send timing outputs of data module 1 are also paralleled to the terminal timing inputs of data module 2. By using this configuration, the timing for both data modules and both UR RS422 channels are derived from a single clock source. As a result, data sampling for both of the UR RS422 channels is synchronized via the send timing leads on data module 1, shown as follows. If the terminal timing feature is not available or this type of connection is not wanted, the G.703 interface is a viable option that does not impose timing restrictions.
Figure 3-42: Timing configuration for RS422 two-channel, three-terminal application
Data module 1 provides timing to the F60 RS422 interface via the ST(A) and ST(B) outputs. Data module 1 also provides timing to data module 2 TT(A) and TT(B) inputs via the ST(A) and AT(B) outputs. The data module pin numbers have been omitted in the figure because they vary by manufacturer.
3.4.5.3 Transmit timing
The RS422 interface accepts one clock input for transmit timing. It is important that the rising edge of the 64 kHz transmit timing clock of the multiplexer interface is sampling the data in the center of the transmit data window. Therefore, it is important to confirm clock and data transitions to ensure proper system operation. For example, the following figure shows the positive edge of the Tx clock in the center of the Tx data bit.
3-38 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
Figure 3-43: Clock and data transitions
3
3.4.5.4 Receive timing
The RS422 interface utilizes NRZI-MARK modulation code and therefore does not rely on an Rx clock to recapture data. NRZI-MARK is an edge-type, invertible, self-clocking code.
To recover the Rx clock from the data-stream, an integrated digital phase lock loop (DPLL) circuit is utilized. The DPLL is driven by an internal clock, which is 16-times over-sampled, and uses this clock along with the data-stream to generate a data clock that can be used as the serial communication controller (SCC) receive clock.

3.4.6 RS422 and fiber interface

The following figure shows the combined RS422 plus fiberoptic interface configuration at 64 K baud. The 7L, 7M, 7N, 7P, and 74 modules are used in two-terminal with a redundant channel or three-terminal configurations where channel 1 is employed via the RS422 interface (possibly with a multiplexer) and channel 2 via direct fiber.
AWG 20-24 twisted shielded pair is recommended for external RS422 connections and ground the shield only at one end. For the direct fiber channel, address power budget issues properly.
When using a laser interface, attenuators can be necessary to ensure that you do not exceed maximum optical input power to the receiver.
Figure 3-44: RS422 and fiber interface connection
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-39
3
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION
The connections shown in the figure are for multiplexers configured as data communications equipment (DCE) units.

3.4.7 G.703 and fiber interface

The following figure shows the combined G.703 plus fiberoptic interface configuration at 64 kbps. The 7E, 7F, 7G, 7Q, and 75 modules are used in configurations where channel 1 is employed via the G.703 interface (possibly with a multiplexer) and channel 2 via direct fiber. AWG 24 twisted shielded pair is recommended for external G.703 connections connecting the shield to pin 1a at one end only. For the direct fiber channel, address power budget issues properly. See previous sections for details on the G.703 and fiber interfaces.
When using a laser interface, attenuators can be necessary to ensure that you do not exceed the maximum optical input power to the receiver.
Figure 3-45: G.703 and fiber interface connection

3.4.8 IEEE C37.94 interface

The UR-series IEEE C37.94 communication modules (module types 2G, 2H, 2I, 2J, 76, and 77) are designed to interface with IEEE C37.94 compliant digital multiplexers or an IEEE C37.94 compliant interface converter for use with direct input and output applications. The IEEE C37.94 standard defines a point-to-point optical link for synchronous data between a multiplexer and a teleprotection device. This data is typically 64 kbps, but the standard provides for speeds up to 64n kbps, where n = 1, 2,…, 12. The UR-series C37.94 communication modules are either 64 kbps (with n fixed at 1) for 128 kbps (with n fixed at 2). The frame is a valid International Telecommunications Union (ITU-T) recommended G.704 pattern from the standpoint of framing and data rate. The frame is 256 bits and is repeated at a frame rate of 8000 Hz, with a resultant bit rate of 2048 kbps.
The specifications for the module are as follows:
IEEE standard — C37.94 for 1 × 128 kbps optical fiber interface (for 2G and 2H modules) or C37.94 for 2 × 64 kbps optical fiber interface (for 76 and 77 modules)
Fiber optic cable type — 50 nm or 62.5 μm core diameter optical fiber
Fiber optic mode — multimode
Fiber optic cable length — up to 2 km
Fiber optic connector — type ST
Wavelength — 820 ±40 nm
Connection — as per all fiber optic connections, a Tx to Rx connection is required
The UR-series C37.94 communication module can be connected directly to any compliant digital multiplexer that supports the IEEE C37.94 standard. The figure shows the concept.
3-40 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
Figure 3-46: IEEE C37.94 connection to compliant digital multiplexer
The UR-series C37.94 communication module can be connected to the electrical interface (G.703, RS422, or X.21) of a non­compliant digital multiplexer via an optical-to-electrical interface converter that supports the IEEE C37.94 standard. The following figure shows the concept.
Figure 3-47: IEEE C37.94 connection to non-compliant digital multiplexer
In 2008, GE Grid Solutions released revised modules 76 and 77 for C37.94 communication to enable multi-ended fault location functionality with firmware 5.60 release and higher. All modules 76 and 77 shipped since the change support this feature and are fully backward compatible with firmware releases below 5.60. For customers using firmware release 5.60 and higher, the module can be identified with "Rev D" printed on the module and is to be used on all ends of F60 communication for two and three terminal applications. Failure to use it at all ends results in intermittent communication alarms. For customers using firmware revisions below 5.60, it is not required to match the revision of the modules installed.
The UR-series C37.94 communication module has six switches to set the clock configuration. The following figure shows the functions of these control switches.
Figure 3-48: Switches
3
For the internal timing mode, the system clock is generated internally. Therefore, set the timing switch selection to internal timing for relay 1 and loop timed for relay 2. There must be only one timing source configured.
For the looped timing mode, the system clock is derived from the received line signal. Therefore, set the timing selection to loop timing mode for connections to higher order systems.
The IEEE C37.94 communications module cover removal procedure is as follows:
1. With power to the relay off, remove the IEEE C37.94 module (type 2G, 2H, 2I, 2J, 76, or 77 module) as follows. Record
the original location of the module to help ensure that the same or replacement module is inserted into the correct slot.
2. Simultaneously pull the ejector/inserter clips located at the top and bottom of each module in order to release the
module for removal.
3. Remove the module cover screw.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-41
3
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION
4. Remove the top cover by sliding it towards the rear and then lift it upwards.
5. Set the timing selection switches (channels 1 and 2) to the required timing modes (see description earlier).
6. Replace the top cover and the cover screw.
7. Re-insert the IEEE C37.94 module. Take care to ensure that the correct module type is inserted into the correct slot position. The ejector/inserter clips located at the top and at the bottom of each module must be in the disengaged position as the module is inserted smoothly into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module is inserted fully.
Figure 3-49: IEEE C37.94 timing selection switch setting
Modules shipped since January 2012 have status LEDs that indicate the status of the DIP switches, as shown in the following figure.
3-42 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
Figure 3-50: Status LEDs
3
The clock configuration LED status is as follows:
Flashing green — loop timing mode while receiving a valid data packet
Flashing yellow — internal mode while receiving a valid data packet
Solid red — (switch to) internal timing mode while not receiving a valid data packet The link/activity LED status is as follows:
Flashing green — FPGA is receiving a valid data packet
Solid yellow — FPGA is receiving a "yellow bit" and remains yellow for each "yellow bit"
Solid red — FPGA is not receiving a valid packet or the packet received is invalid

3.4.9 C37.94SM interface

The UR-series C37.94SM communication modules (2A and 2B) are designed to interface with modified IEEE C37.94 compliant digital multiplexers or IEEE C37.94 compliant interface converters that have been converted from 820 nm multi­mode fiber optics to 1300 nm ELED single-mode fiber optics. The IEEE C37.94 standard defines a point-to-point optical link for synchronous data between a multiplexer and a teleprotection device. This data is typically 64 kbps, but the standard provides for speeds up to 64n kbps, where n = 1, 2,…, 12. The UR-series C37.94SM communication module is 64 kbps only with n fixed at 1. The frame is a valid International Telecommunications Union (ITU-T) recommended G.704 pattern from the standpoint of framing and data rate. The frame is 256 bits and is repeated at a frame rate of 8000 Hz, with a resultant bit rate of 2048 kbps.
The specifications for the module are as follows:
Emulated IEEE standard — Emulates C37.94 for 1 × 64 kbps optical fiber interface (modules set to n = 1 or 64 kbps)
Fiber optic cable type — 9/125 μm core diameter optical fiber
Fiber optic mode — Single-mode, ELED compatible with HP HFBR-1315T transmitter and HP HFBR-2316T receiver
Fiber optic cable length — Up to 11.4 km
Fiber optic connector — Type ST
Wavelength — 1300 ±40 nm
Connection — As per all fiber optic connections, a Tx to Rx connection is required
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-43
3
DIRECT INPUT AND OUTPUT COMMUNICATIONS CHAPTER 3: INSTALLATION
The UR-series C37.94SM communication module can be connected directly to any compliant digital multiplexer that supports C37.94SM, as shown.
It also can be connected directly to any other UR-series relay with a C37.94SM module, as shown.
In 2008, GE Grid Solutions released revised modules 2A and 2B for C37.94SM communication to enable multi-ended fault location functionality with firmware 5.60 release and higher. All modules 2A and 2B shipped since the change support this feature and are fully backward compatible with firmware releases below 5.60. For customers using firmware release 5.60 and higher, the module can be identified with "Rev D" printed on the module and is to be used on all ends of F60 communication for two and three terminal applications. Failure to use it at all ends results in intermittent communication alarms. For customers using firmware revisions below 5.60, it is not required to match the revision of the modules installed.
The UR-series C37.94SM communication module has six switches that are used to set the clock configuration. The following figure shows the functions of these control switches.
Figure 3-51: Switches
For the internal timing mode, the system clock is generated internally. Therefore, set the timing switch selection to internal timing for relay 1 and loop timed for relay 2. There must be only one timing source configured.
For the looped timing mode, the system clock is derived from the received line signal. Therefore, set the timing selection to loop timing mode for connections to higher-order systems.
The C37.94SM communications module cover removal procedure is as follows:
1. With power to the relay off, remove the C37.94SM module (module 2A or 2B) as follows. Record the original location of the module to help ensure that the same or replacement module is inserted into the correct slot.
2. Simultaneously pull the ejector/inserter clips located at the top and at the bottom of each module in order to release the module for removal.
3. Remove the module cover screw.
4. Remove the top cover by sliding it towards the rear and then lift it upwards.
5. Set the timing selection switches (channels 1 and 2) to the required timing modes (see description earlier).
3-44 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION DIRECT INPUT AND OUTPUT COMMUNICATIONS
6. Replace the top cover and the cover screw.
7. Re-insert the C37.94SM module. Take care to ensure that the correct module type is inserted into the correct slot
position. The ejector/inserter clips located at the top and at the bottom of each module must be in the disengaged position as the module is inserted smoothly into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module is inserted fully.
Figure 3-52: C37.94SM timing selection switch setting
3
Modules shipped since January 2012 have status LEDs that indicate the status of the DIP switches, as shown in the following figure.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-45
3
ACTIVATE RELAY CHAPTER 3: INSTALLATION
Figure 3-53: Status LEDs
The clock configuration LED status is as follows:
Flashing green — loop timing mode while receiving a valid data packet
Flashing yellow — internal mode while receiving a valid data packet
Solid red — (switch to) internal timing mode while not receiving a valid data packet
The link/activity LED status is as follows:
Flashing green — FPGA is receiving a valid data packet
Solid yellow — FPGA is receiving a "yellow bit" and remains yellow for each "yellow bit"
Solid red — FPGA is not receiving a valid packet or the packet received is invalid

3.5 Activate relay

The relay is in the default “Not Programmed” state when it leaves the factory. When powered up successfully, the "Trouble" LED is on and the "In Service" LED is off. The relay in the “Not Programmed” state blocks signaling of any output relay. These conditions remain until the relay is explicitly put in the “Programmed” state.
RELAY SETTINGS: Not Programmed
The relay can be activated on the front panel or in the EnerVista software. To activate the relay using the front panel:
1. Press the
2. Press the
3. Press the
4. Press the
MENU key until the SETTINGS header flashes momentarily and the PRODUCT SETUP message displays. MESSAGE right arrow until the SECURITY message displays. MESSAGE down arrow until the INSTALLATION message displays. MESSAGE right arrow until the RELAY SETTINGS: Not Programmed message displays.
When the relay is powered up, the "Trouble LED" is on, the "In Service" LED is off, and this message displays, indicating that the relay is in the "Not Programmed" state and is safeguarding (output relays blocked) against the installation of a relay whose settings have not been entered. This message remains until the relay is explicitly put in the "Programmed" state.
3-46 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CHAPTER 3: INSTALLATION INSTALL SOFTWARE
SETTINGS
 SETTINGS  PRODUCT SETUP
SECURITY
DISPLAY PROPERTIES
INSTALLATION
5. After the RELAY SETTINGS: Not Programmed message displays, press a VALUE key to change the selection to
"Programmed."
6. Press the
RELAY SETTINGS: Not Programmed
7. When the "NEW SETTING HAS BEEN STORED" message appears, the relay is in "Programmed" state and the "In Service"
LED turns on.
To activate the relay using EnerVista software:
1. Navigate to Settings > Product Setup > Installation and change the Relay Settings field to "Programmed."
2. Save the change.
ENTER key to save the change.
RELAY SETTINGS: Programmed
RELAY SETTINGS:
Not Programmed
NEW SETTING HAS BEEN STORED

3.6 Install software

3.6.1 EnerVista communication overview

3
The EnerVista UR Setup software communicates to the relay via the faceplate RS232 port or the rear panel RS485 / Ethernet ports.
To communicate via the faceplate RS232 port, use a standard straight-through serial cable. Connect the DB-9 male end to the relay and the DB-9 or DB-25 female end to the computer COM2 port as described in the CPU Communication Ports section earlier in this chapter.
F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 3-47
3
INSTALL SOFTWARE CHAPTER 3: INSTALLATION
Figure 3-54: Relay communication options
To communicate through the F60 rear RS485 port from a computer RS232 port, the GE Grid Solutions RS232/RS485 converter box is required. This device (catalog number F485) connects to the computer using a straight-through serial cable. A shielded twisted-pair (20, 22, or 24 AWG) connects the F485 converter to the F60 rear communications port. The converter terminals (+, –, GND) are connected to the F60 communication module (+, –, COM) terminals. See the CPU Communication Ports section in chapter 3 for details. The line is terminated with an R-C network (that is, 120 Ω, 1 nF) as described in this chapter.

3.6.2 System requirements

The relay front panel or the EnerVista UR Setup software can be used to communicate with the relay. The software interface is the preferred method to edit settings and view actual values because the computer monitor can display more information.
The minimum system requirements for the EnerVista software are as follows:
Intel Pentium processor (dual core)
Microsoft Windows 7 with Service Pack 1 (32-bit or 64-bit) or Windows Server 2008 Release 2 with Service Pack 1 (64­bit)
1 GB free hard drive space
•2 GB RAM
1280 x 800 display screen
3-48 F60 FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
Loading...