F35 Multiple Feeder Protection
System
UR Series Instruction Manual
F35 Revision: 5.8x
Manual P/N: 1601-0106-V2 (GEK-113550A)
Copyright © 2017 GE Multilin Inc.
650 Markland Street
Markham, Ontario
Canada L6C 0M1
Tel: +1 905 927 7070 Fax: +1 905 927 5098
Internet: http://www.GEGridSolutions.com
*1601-0106-V2*
GE Multilin's Quality Management
System is registered to
ISO9001:2008
QMI # 005094
UL # A3775

Addendum

ADDENDUM
This addendum contains information that relates to the F35 Multiple Feeder Protection System, version 5.8x. This addendum lists a number of information items that appear in the instruction manual GEK-113550A (revision V2) but are not included in the current F35 operations.
The following functions and items are not yet available with the current version of the F35 relay:
•N/A.
Version 4.0x and higher releases of the F35 relay includes new hardware (CPU and CT/VT modules).
• The new CPU modules are specified with the following order codes: 9E, 9G, 9H, 9J, 9K, 9L, 9M, 9N, 9P, 9R, and 9S.
• The new CT/VT modules are specified with the following order codes: 8F, 8G, 8H, 8J 8L, 8M, 8N, 8R.
The following table maps the relationship between the old CPU and CT/VT modules to the newer versions:
MODULE OLD NEW DESCRIPTION
CPU 9A 9E RS485 and RS485 (Modbus RTU, DNP)
9C 9G RS485 and 10Base-F (Ethernet, Modbus TCP/IP, DNP)
9D 9H RS485 and redundant 10Base-F (Ethernet, Modbus TCP/IP, DNP)
--- 9J RS485 and multi-mode ST 100Base-FX
--- 9K RS485 and multi-mode ST redundant 100Base-FX
--- 9L RS485 and single mode SC 100Base-FX
--- 9M RS485 and single mode SC redundant 100Base-FX
--- 9N RS485 and 10/100Base-T
--- 9P RS485 and single mode ST 100Base-FX
--- 9R RS485 and single mode ST redundant 100Base-FX
--- 9S RS485 and six-port managed Ethernet switch
CT/VT 8A 8F Standard 4CT/4VT
8B 8G Sensitive ground 4CT/4VT
8C 8H Standard 8CT
8D 8J Sensitive ground 8CT
-- 8L Standard 4CT/4VT with enhanced diagnostics
-- 8M Sensitive ground 4CT/4VT with enhanced diagnostics
-- 8N Standard 8CT with enhanced diagnostics
-- 8R Sensitive ground 8CT with enhanced diagnostics
The new CT/VT modules can only be used with the new CPUs (9E, 9G, 9H, 9J, 9K, 9L, 9M, 9N, 9P, 9R, and 9S), and the old CT/VT modules can only be used with the old CPU modules (9A, 9C, 9D). To prevent any hardware mis­matches, the new CPU and CT/VT modules have blue labels and a warning sticker stating “Attn.: Ensure CPU and DSP module label colors are the same!”. In the event that there is a mismatch between the CPU and CT/VT module, the relay will not function and a
DSP ERROR or HARDWARE MISMATCH error will be displayed.
All other input/output modules are compatible with the new hardware.
With respect to the firmware, firmware versions 4.0x and higher are only compatible with the new CPU and CT/VT mod­ules. Previous versions of the firmware (3.4x and earlier) are only compatible with the older CPU and CT/VT modules.

Table of Contents

TABLE OF CONTENTS
1. GETTING STARTED 1.1 IMPORTANT PROCEDURES
1.1.1 CAUTIONS AND WARNINGS ........................................................................... 1-1
1.1.2 INSPECTION CHECKLIST ................................................................................ 1-2
1.2 UR OVERVIEW
1.2.1 INTRODUCTION TO THE UR ........................................................................... 1-3
1.2.2 HARDWARE ARCHITECTURE......................................................................... 1-4
1.2.3 SOFTWARE ARCHITECTURE.......................................................................... 1-5
1.2.4 IMPORTANT CONCEPTS ................................................................................. 1-5
1.3 ENERVISTA UR SETUP SOFTWARE
1.3.1 PC REQUIREMENTS ........................................................................................ 1-6
1.3.2 INSTALLATION.................................................................................................. 1-6
1.3.3 CONFIGURING THE F35 FOR SOFTWARE ACCESS .................................... 1-7
1.3.4 USING THE QUICK CONNECT FEATURE..................................................... 1-10
1.3.5 CONNECTING TO THE F35 RELAY............................................................... 1-16
1.4 UR HARDWARE
1.4.1 MOUNTING AND WIRING............................................................................... 1-17
1.4.2 COMMUNICATIONS........................................................................................ 1-17
1.4.3 FACEPLATE DISPLAY.................................................................................... 1-17
1.5 USING THE RELAY
1.5.1 FACEPLATE KEYPAD..................................................................................... 1-18
1.5.2 MENU NAVIGATION ....................................................................................... 1-18
1.5.3 MENU HIERARCHY ........................................................................................ 1-18
1.5.4 RELAY ACTIVATION....................................................................................... 1-18
1.5.5 RELAY PASSWORDS..................................................................................... 1-19
1.5.6 FLEXLOGIC™ CUSTOMIZATION................................................................... 1-19
1.5.7 COMMISSIONING ........................................................................................... 1-20
2. PRODUCT DESCRIPTION 2.1 INTRODUCTION
2.1.1 OVERVIEW........................................................................................................ 2-1
2.1.2 ORDERING........................................................................................................ 2-2
2.1.3 REPLACEMENT MODULES ............................................................................. 2-6
2.2 SPECIFICATIONS
2.2.1 PROTECTION ELEMENTS ............................................................................... 2-9
2.2.2 USER-PROGRAMMABLE ELEMENTS........................................................... 2-10
2.2.3 MONITORING.................................................................................................. 2-11
2.2.4 METERING ...................................................................................................... 2-12
2.2.5 INPUTS ............................................................................................................2-13
2.2.6 POWER SUPPLY ............................................................................................ 2-14
2.2.7 OUTPUTS ........................................................................................................2-14
2.2.8 COMMUNICATIONS........................................................................................ 2-16
2.2.9 INTER-RELAY COMMUNICATIONS............................................................... 2-17
2.2.10 ENVIRONMENTAL .......................................................................................... 2-18
2.2.11 TYPE TESTS ................................................................................................... 2-19
2.2.12 PRODUCTION TESTS .................................................................................... 2-19
2.2.13 APPROVALS ................................................................................................... 2-20
2.2.14 MAINTENANCE ............................................................................................... 2-20
3. HARDWARE 3.1 DESCRIPTION
3.1.1 PANEL CUTOUT ............................................................................................... 3-1
3.1.2 MODULE WITHDRAWAL AND INSERTION ..................................................... 3-6
3.1.3 REAR TERMINAL LAYOUT............................................................................... 3-8
3.2 WIRING
3.2.1 TYPICAL WIRING............................................................................................ 3-10
3.2.2 DIELECTRIC STRENGTH ............................................................................... 3-11
3.2.3 CONTROL POWER ......................................................................................... 3-11
3.2.4 CT/VT MODULES ............................................................................................ 3-12
3.2.5 PROCESS BUS MODULES ............................................................................ 3-14
3.2.6 CONTACT INPUTS AND OUTPUTS............................................................... 3-14
GE Multilin F35 Multiple Feeder Protection System v
TABLE OF CONTENTS
3.2.7 TRANSDUCER INPUTS/OUTPUTS.................................................................3-26
3.2.8 RS232 FACEPLATE PORT..............................................................................3-27
3.2.9 CPU COMMUNICATION PORTS.....................................................................3-27
3.2.10 IRIG-B ...............................................................................................................3-31
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
3.3.1 DESCRIPTION .................................................................................................3-32
3.3.2 FIBER: LED AND ELED TRANSMITTERS ......................................................3-35
3.3.3 FIBER-LASER TRANSMITTERS .....................................................................3-35
3.3.4 G.703 INTERFACE...........................................................................................3-36
3.3.5 RS422 INTERFACE .........................................................................................3-39
3.3.6 RS422 AND FIBER INTERFACE .....................................................................3-41
3.3.7 G.703 AND FIBER INTERFACE ......................................................................3-41
3.3.8 IEEE C37.94 INTERFACE................................................................................3-42
3.3.9 C37.94SM INTERFACE ...................................................................................3-45
3.4 MANAGED ETHERNET SWITCH MODULES
3.4.1 OVERVIEW ......................................................................................................3-48
3.4.2 MANAGED ETHERNET SWITCH MODULE HARDWARE..............................3-48
3.4.3 MANAGED SWITCH LED INDICATORS .........................................................3-49
3.4.4 CONFIGURING THE MANAGED ETHERNET SWITCH MODULE.................3-49
3.4.5 UPLOADING F35 SWITCH MODULE FIRMWARE .........................................3-52
3.4.6 ETHERNET SWITCH SELF-TEST ERRORS...................................................3-54
4. HUMAN INTERFACES 4.1 ENERVISTA UR SETUP SOFTWARE INTERFACE
4.1.1 INTRODUCTION ................................................................................................4-1
4.1.2 CREATING A SITE LIST ....................................................................................4-1
4.1.3 ENERVISTA UR SETUP OVERVIEW................................................................4-1
4.1.4 ENERVISTA UR SETUP MAIN WINDOW..........................................................4-3
4.2 EXTENDED ENERVISTA UR SETUP FEATURES
4.2.1 SETTINGS TEMPLATES ...................................................................................4-4
4.2.2 SECURING AND LOCKING FLEXLOGIC™ EQUATIONS ................................4-8
4.2.3 SETTINGS FILE TRACEABILITY.....................................................................4-10
4.3 FACEPLATE INTERFACE
4.3.1 FACEPLATE.....................................................................................................4-13
4.3.2 LED INDICATORS............................................................................................4-14
4.3.3 CUSTOM LABELING OF LEDS .......................................................................4-17
4.3.4 DISPLAY...........................................................................................................4-23
4.3.5 KEYPAD ...........................................................................................................4-23
4.3.6 BREAKER CONTROL ......................................................................................4-23
4.3.7 MENUS.............................................................................................................4-24
4.3.8 CHANGING SETTINGS ...................................................................................4-26
5. SETTINGS 5.1 OVERVIEW
5.1.1 SETTINGS MAIN MENU ....................................................................................5-1
5.1.2 INTRODUCTION TO ELEMENTS......................................................................5-4
5.1.3 INTRODUCTION TO AC SOURCES..................................................................5-5
5.2 PRODUCT SETUP
5.2.1 SECURITY..........................................................................................................5-8
5.2.2 DISPLAY PROPERTIES ..................................................................................5-12
5.2.3 CLEAR RELAY RECORDS ..............................................................................5-14
5.2.4 COMMUNICATIONS ........................................................................................5-15
5.2.5 MODBUS USER MAP ......................................................................................5-37
5.2.6 REAL TIME CLOCK .........................................................................................5-38
5.2.7 FAULT REPORTS ............................................................................................5-39
5.2.8 OSCILLOGRAPHY ...........................................................................................5-41
5.2.9 DATA LOGGER................................................................................................5-43
5.2.10 DEMAND ..........................................................................................................5-45
5.2.11 USER-PROGRAMMABLE LEDS .....................................................................5-46
5.2.12 USER-PROGRAMMABLE SELF TESTS .........................................................5-49
5.2.13 CONTROL PUSHBUTTONS ............................................................................5-50
vi F35 Multiple Feeder Protection System GE Multilin
TABLE OF CONTENTS
5.2.14 USER-PROGRAMMABLE PUSHBUTTONS ...................................................5-51
5.2.15 FLEX STATE PARAMETERS..........................................................................5-56
5.2.16 USER-DEFINABLE DISPLAYS .......................................................................5-57
5.2.17 DIRECT INPUTS/OUTPUTS ........................................................................... 5-59
5.2.18 TELEPROTECTION......................................................................................... 5-67
5.2.19 INSTALLATION................................................................................................ 5-67
5.3 REMOTE RESOURCES
5.3.1 REMOTE RESOURCES CONFIGURATION ................................................... 5-69
5.4 SYSTEM SETUP
5.4.1 AC INPUTS ......................................................................................................5-70
5.4.2 POWER SYSTEM............................................................................................ 5-71
5.4.3 SIGNAL SOURCES ......................................................................................... 5-72
5.4.4 BREAKERS......................................................................................................5-75
5.4.5 DISCONNECT SWITCHES .............................................................................5-79
5.4.6 FLEXCURVES™..............................................................................................5-82
5.5 FLEXLOGIC™
5.5.1 INTRODUCTION TO FLEXLOGIC™............................................................... 5-89
5.5.2 FLEXLOGIC™ RULES .................................................................................... 5-98
5.5.3 FLEXLOGIC™ EVALUATION.......................................................................... 5-98
5.5.4 FLEXLOGIC™ EXAMPLE ............................................................................... 5-99
5.5.5 FLEXLOGIC™ EQUATION EDITOR ............................................................. 5-103
5.5.6 FLEXLOGIC™ TIMERS................................................................................. 5-103
5.5.7 FLEXELEMENTS™ ....................................................................................... 5-105
5.5.8 NON-VOLATILE LATCHES ........................................................................... 5-109
5.6 GROUPED ELEMENTS
5.6.1 OVERVIEW.................................................................................................... 5-110
5.6.2 SETTING GROUP .........................................................................................5-110
5.6.3 PHASE CURRENT ........................................................................................ 5-110
5.6.4 NEUTRAL CURRENT.................................................................................... 5-119
5.6.5 GROUND CURRENT..................................................................................... 5-121
5.6.6 NEGATIVE SEQUENCE CURRENT ............................................................. 5-123
5.6.7 VOLTAGE ELEMENTS.................................................................................. 5-126
5.7 CONTROL ELEMENTS
5.7.1 OVERVIEW.................................................................................................... 5-132
5.7.2 TRIP BUS.......................................................................................................5-132
5.7.3 SETTING GROUPS ....................................................................................... 5-134
5.7.4 SELECTOR SWITCH..................................................................................... 5-135
5.7.5 UNDERFREQUENCY.................................................................................... 5-141
5.7.6 AUTORECLOSE ............................................................................................ 5-142
5.7.7 DIGITAL ELEMENTS..................................................................................... 5-148
5.7.8 DIGITAL COUNTERS .................................................................................... 5-151
5.7.9 8-BIT SWITCHES .......................................................................................... 5-153
5.7.10 MONITORING ELEMENTS ........................................................................... 5-155
5.7.11 PID REGULATOR.......................................................................................... 5-161
5.8 INPUTS AND OUTPUTS
5.8.1 CONTACT INPUTS........................................................................................ 5-164
5.8.2 VIRTUAL INPUTS.......................................................................................... 5-166
5.8.3 CONTACT OUTPUTS.................................................................................... 5-167
5.8.4 VIRTUAL OUTPUTS...................................................................................... 5-169
5.8.5 REMOTE DEVICES....................................................................................... 5-170
5.8.6 REMOTE INPUTS.......................................................................................... 5-171
5.8.7 REMOTE DOUBLE-POINT STATUS INPUTS .............................................. 5-172
5.8.8 REMOTE OUTPUTS...................................................................................... 5-172
5.8.9 RESETTING...................................................................................................5-173
5.8.10 DIRECT INPUTS AND OUTPUTS ................................................................. 5-174
5.8.11 TELEPROTECTION INPUTS AND OUTPUTS.............................................. 5-177
5.8.12 IEC 61850 GOOSE ANALOGS...................................................................... 5-179
5.8.13 IEC 61850 GOOSE INTEGERS.....................................................................5-180
5.9 TRANSDUCER INPUTS AND OUTPUTS
5.9.1 DCMA INPUTS .............................................................................................. 5-181
5.9.2 RTD INPUTS.................................................................................................. 5-182
5.9.3 DCMA OUTPUTS .......................................................................................... 5-184
GE Multilin F35 Multiple Feeder Protection System vii
TABLE OF CONTENTS
5.10 TESTING
5.10.1 TEST MODE ...................................................................................................5-187
5.10.2 FORCE CONTACT INPUTS...........................................................................5-188
5.10.3 FORCE CONTACT OUTPUTS.......................................................................5-189
6. ACTUAL VALUES 6.1 OVERVIEW
6.1.1 ACTUAL VALUES MAIN MENU.........................................................................6-1
6.2 STATUS
6.2.1 CONTACT INPUTS ............................................................................................6-3
6.2.2 VIRTUAL INPUTS ..............................................................................................6-3
6.2.3 REMOTE INPUTS ..............................................................................................6-3
6.2.4 REMOTE DOUBLE-POINT STATUS INPUTS...................................................6-4
6.2.5 TELEPROTECTION INPUTS .............................................................................6-4
6.2.6 CONTACT OUTPUTS ........................................................................................6-4
6.2.7 VIRTUAL OUTPUTS ..........................................................................................6-5
6.2.8 AUTORECLOSE.................................................................................................6-5
6.2.9 REMOTE DEVICES............................................................................................6-5
6.2.10 DIGITAL COUNTERS.........................................................................................6-6
6.2.11 SELECTOR SWITCHES ....................................................................................6-6
6.2.12 FLEX STATES....................................................................................................6-6
6.2.13 ETHERNET ........................................................................................................6-7
6.2.14 DIRECT INPUTS ................................................................................................6-7
6.2.15 DIRECT DEVICES STATUS ..............................................................................6-8
6.2.16 IEC 61850 GOOSE INTEGERS .........................................................................6-8
6.2.17 EGD PROTOCOL STATUS................................................................................6-8
6.2.18 TELEPROTECTION CHANNEL TESTS.............................................................6-9
6.2.19 INCIPIENT FAULT DETECTOR.........................................................................6-9
6.2.20 ETHERNET SWITCH .......................................................................................6-10
6.3 METERING
6.3.1 METERING CONVENTIONS ...........................................................................6-11
6.3.2 SOURCES ........................................................................................................6-14
6.3.3 TRACKING FREQUENCY................................................................................6-19
6.3.4 FLEXELEMENTS™..........................................................................................6-20
6.3.5 IEC 61580 GOOSE ANALOG VALUES ...........................................................6-20
6.3.6 TRANSDUCER INPUTS/OUTPUTS.................................................................6-21
6.4 RECORDS
6.4.1 FAULT REPORTS ............................................................................................6-22
6.4.2 EVENT RECORDS...........................................................................................6-22
6.4.3 OSCILLOGRAPHY ...........................................................................................6-23
6.4.4 DATA LOGGER................................................................................................6-23
6.4.5 BREAKER MAINTENANCE .............................................................................6-24
6.5 PRODUCT INFORMATION
6.5.1 MODEL INFORMATION...................................................................................6-25
6.5.2 FIRMWARE REVISIONS..................................................................................6-25
7. COMMANDS AND TARGETS
7.1 COMMANDS
7.1.1 COMMANDS MENU...........................................................................................7-1
7.1.2 VIRTUAL INPUTS ..............................................................................................7-1
7.1.3 CLEAR RECORDS.............................................................................................7-2
7.1.4 SET DATE AND TIME ........................................................................................7-2
7.1.5 RELAY MAINTENANCE.....................................................................................7-3
7.2 TARGETS
7.2.1 TARGETS MENU ...............................................................................................7-4
7.2.2 TARGET MESSAGES ........................................................................................7-4
7.2.3 RELAY SELF-TESTS .........................................................................................7-4
viii F35 Multiple Feeder Protection System GE Multilin
TABLE OF CONTENTS
8. SECURITY 8.1 PASSWORD SECURITY
8.1.1 OVERVIEW........................................................................................................ 8-1
8.1.2 PASSWORD SECURITY MENU ....................................................................... 8-2
8.1.3 LOCAL PASSWORDS....................................................................................... 8-2
8.1.4 REMOTE PASSWORDS ................................................................................... 8-3
8.1.5 ACCESS SUPERVISION................................................................................... 8-3
8.1.6 DUAL PERMISSION SECURITY ACCESS....................................................... 8-4
8.2 SETTINGS SECURITY
8.2.1 SETTINGS TEMPLATES................................................................................... 8-6
8.2.2 SECURING AND LOCKING FLEXLOGIC™ EQUATIONS ............................. 8-10
8.2.3 SETTINGS FILE TRACEABILITY.................................................................... 8-12
8.3 ENERVISTA SECURITY MANAGEMENT SYSTEM
8.3.1 OVERVIEW...................................................................................................... 8-15
8.3.2 ENABLING THE SECURITY MANAGEMENT SYSTEM................................. 8-15
8.3.3 ADDING A NEW USER ................................................................................... 8-15
8.3.4 MODIFYING USER PRIVILEGES ................................................................... 8-16
9. THEORY OF OPERATION 9.1 FAULT LOCATOR
9.1.1 FAULT TYPE DETERMINATION....................................................................... 9-1
10. COMMISSIONING 10.1 TESTING
10.1.1 TESTING UNDERFREQUENCY ELEMENTS ................................................. 10-1
A. FLEXANALOG AND
FLEXINTEGER PARAMETERS
B. MODBUS
COMMUNICATIONS
A.1 PARAMETER LISTS
A.1.1 FLEXANALOG ITEMS .......................................................................................A-1
A.1.2 FLEXINTEGER ITEMS ....................................................................................A-16
B.1 MODBUS RTU PROTOCOL
B.1.1 INTRODUCTION................................................................................................B-1
B.1.2 PHYSICAL LAYER.............................................................................................B-1
B.1.3 DATA LINK LAYER............................................................................................B-1
B.1.4 CRC-16 ALGORITHM........................................................................................B-2
B.2 MODBUS FUNCTION CODES
B.2.1 SUPPORTED FUNCTION CODES ...................................................................B-3
B.2.2 READ ACTUAL VALUES OR SETTINGS (FUNCTION CODE 03/04H) ...........B-3
B.2.3 EXECUTE OPERATION (FUNCTION CODE 05H) ...........................................B-4
B.2.4 STORE SINGLE SETTING (FUNCTION CODE 06H).......................................B-4
B.2.5 STORE MULTIPLE SETTINGS (FUNCTION CODE 10H) ................................B-5
B.2.6 EXCEPTION RESPONSES...............................................................................B-5
B.3 FILE TRANSFERS
B.3.1 OBTAINING RELAY FILES VIA MODBUS........................................................B-6
B.3.2 MODBUS PASSWORD OPERATION ...............................................................B-7
B.4 MEMORY MAPPING
B.4.1 MODBUS MEMORY MAP .................................................................................B-8
B.4.2 DATA FORMATS .............................................................................................B-65
C. IEC 61850
COMMUNICATIONS
C.1 OVERVIEW
C.1.1 INTRODUCTION................................................................................................C-1
C.1.2 COMMUNICATION PROFILES .........................................................................C-1
GE Multilin F35 Multiple Feeder Protection System ix
TABLE OF CONTENTS
C.2 SERVER DATA ORGANIZATION
C.2.1 OVERVIEW .......................................................................................................C-2
C.2.2 GGIO1: DIGITAL STATUS VALUES.................................................................C-2
C.2.3 GGIO2: DIGITAL CONTROL VALUES..............................................................C-2
C.2.4 GGIO3: DIGITAL STATUS AND ANALOG VALUES FROM RECEIVED GOOSE
DATAC-2
C.2.5 GGIO4: GENERIC ANALOG MEASURED VALUES.........................................C-2
C.2.6 MMXU: ANALOG MEASURED VALUES ..........................................................C-3
C.2.7 PROTECTION AND OTHER LOGICAL NODES............................................... C-3
C.3 SERVER FEATURES AND CONFIGURATION
C.3.1 BUFFERED/UNBUFFERED REPORTING........................................................C-5
C.3.2 FILE TRANSFER...............................................................................................C-5
C.3.3 TIMESTAMPS AND SCANNING....................................................................... C-5
C.3.4 LOGICAL DEVICE NAME .................................................................................C-5
C.3.5 LOCATION ........................................................................................................C-5
C.3.6 LOGICAL NODE NAME PREFIXES..................................................................C-6
C.3.7 CONNECTION TIMING.....................................................................................C-6
C.3.8 NON-IEC 61850 DATA...................................................................................... C-6
C.3.9 COMMUNICATION SOFTWARE UTILITIES.....................................................C-6
C.4 GENERIC SUBSTATION EVENT SERVICES: GSSE AND GOOSE
C.4.1 OVERVIEW .......................................................................................................C-7
C.4.2 GSSE CONFIGURATION..................................................................................C-7
C.4.3 FIXED GOOSE.................................................................................................. C-7
C.4.4 CONFIGURABLE GOOSE ................................................................................ C-7
C.4.5 ETHERNET MAC ADDRESS FOR GSSE/GOOSE ..........................................C-9
C.4.6 GSSE ID AND GOOSE ID SETTINGS............................................................C-10
C.5 IEC 61850 IMPLEMENTATION VIA ENERVISTA UR SETUP
C.5.1 OVERVIEW .....................................................................................................C-11
C.5.2 CONFIGURING IEC 61850 SETTINGS .......................................................... C-12
C.5.3 ABOUT ICD FILES ..........................................................................................C-13
C.5.4 CREATING AN ICD FILE WITH ENERVISTA UR SETUP.............................. C-17
C.5.5 ABOUT SCD FILES.........................................................................................C-17
C.5.6 IMPORTING AN SCD FILE WITH ENERVISTA UR SETUP........................... C-20
C.6 ACSI CONFORMANCE
C.6.1 ACSI BASIC CONFORMANCE STATEMENT ................................................ C-22
C.6.2 ACSI MODELS CONFORMANCE STATEMENT............................................C-22
C.6.3 ACSI SERVICES CONFORMANCE STATEMENT .........................................C-23
C.7 LOGICAL NODES
C.7.1 LOGICAL NODES TABLE ............................................................................... C-26
D. IEC 60870-5-104 COMMS. D.1 IEC 60870-5-104 PROTOCOL
D.1.1 INTEROPERABILITY DOCUMENT...................................................................D-1
D.1.2 POINTS LIST.....................................................................................................D-9
E. DNP COMMUNICATIONS E.1 DEVICE PROFILE DOCUMENT
E.1.1 DNP V3.00 DEVICE PROFILE .......................................................................... E-1
E.1.2 IMPLEMENTATION TABLE .............................................................................. E-4
E.2 DNP POINT LISTS
E.2.1 BINARY INPUT POINTS ................................................................................... E-8
E.2.2 BINARY AND CONTROL RELAY OUTPUT...................................................... E-9
E.2.3 COUNTERS..................................................................................................... E-10
E.2.4 ANALOG INPUTS............................................................................................ E-11
F. MISCELLANEOUS F.1 CHANGE NOTES
F.1.1 REVISION HISTORY......................................................................................... F-1
F.1.2 CHANGES TO THE MANUAL ........................................................................... F-2
x F35 Multiple Feeder Protection System GE Multilin
TABLE OF CONTENTS
F.2 ABBREVIATIONS
F.2.1 STANDARD ABBREVIATIONS ......................................................................... F-8
F.3 WARRANTY
F.3.1 GE MULTILIN WARRANTY ............................................................................. F-10
INDEX
GE Multilin F35 Multiple Feeder Protection System xi
TABLE OF CONTENTS
xii F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.1 IMPORTANT PROCEDURES
DANGER
WARNING
CAUTION
NOTICE
DANGER
1 GETTING STARTED 1.1IMPORTANT PROCEDURES
Please read this chapter to help guide you through the initial setup of your new relay.

1.1.1 CAUTIONS AND WARNINGS

Before attempting to install or use the device, review all safety indicators in this document to help prevent injury, equipment damage, or downtime.
The following safety and equipment symbols are used in this document.
Indicates a hazardous situation which, if not avoided, will result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in minor or moderate injury.
Indicates practices not related to personal injury.
a) GENERAL CAUTIONS AND WARNINGS
The following general safety precautions and warnings apply.
Ensure that all connections to the product are correct so as to avoid accidental risk of shock and/or fire, for example such as can arise from high voltage connected to low voltage termi­nals.
Follow the requirements of this manual, including adequate wiring size and type, terminal torque settings, voltage, current magnitudes applied, and adequate isolation/clearance in external wiring from high to low voltage circuits.
Use the device only for its intended purpose and application.
Ensure that all ground paths are uncompromised for safety purposes during device operation and service.
Ensure that the control power applied to the device, the AC current, and voltage input match the ratings specified on the relay nameplate. Do not apply current or voltage in excess of the specified limits.
Only qualified personnel are to operate the device. Such personnel must be thoroughly familiar with all safety cau­tions and warnings in this manual and with applicable country, regional, utility, and plant safety regulations.
Hazardous voltages can exist in the power supply and at the device connection to current transformers, voltage transformers, control, and test circuit terminals. Make sure all sources of such voltages are isolated prior to attempting work on the device.
Hazardous voltages can exist when opening the secondary circuits of live current transformers. Make sure that current transformer secondary circuits are shorted out before making or removing any connection to the current transformer (CT) input terminals of the device.
For tests with secondary test equipment, ensure that no other sources of voltages or currents are connected to such equipment and that trip and close commands to the circuit breakers or other switching apparatus are iso­lated, unless this is required by the test procedure and is specified by appropriate utility/plant procedure.
When the device is used to control primary equipment, such as circuit breakers, isolators, and other switching apparatus, all control circuits from the device to the primary equipment must be isolated while personnel are working on or around this primary equipment to prevent any inadvertent command from this device.
Use an external disconnect to isolate the mains voltage supply.
Personal safety can be affected if the product is physically modified by the end user. Modifications to the product outside of recommended wiring configuration, hardware, or programming boundaries is not recommended end­use practice. Product disassembly and repairs are not permitted. All service needs to be conducted by the factory.
This product is rated to Class A emissions levels and is to be used in Utility, Substation Industrial environments. Not to be used near electronic devices rated for Class B levels.
1
GE Multilin F35 Multiple Feeder Protection System 1-1
1.1 IMPORTANT PROCEDURES 1 GETTING STARTED
CAUTION
®
®
Technical Support: Tel: (905) 294-6222 Fax: (905) 201-2098
http://www.GEmultilin.com
Model: Mods: Wiring Diagram: Inst. Manual: Serial Number: Firmware: Mfg. Date:
F35E00HCHF8AH6AM6BP8BX7A 000 832767A3 GEK-113271 MAZB98000029 D 2005/01/05
Control Power: Contact Inputs: Contact Outputs:
88-300V DC @ 35W / 77-265V AC @ 35VA 300V DC Max 10mA Standard Pilot Duty / 250V AC 7.5A 360V A Resistive / 125V DC Break 4A @ L/R = 40mS / 300W
RATINGS:
F35
GE Multilin
Made in Canada
- M A A B 9 7 0 0 0 0 9 9 -
Multiple Feeder Management Relay
®
832772A1.CDR
NOTE
LED transmitters are classified as IEC 60825-1 Accessible Emission Limit (AEL) Class 1M. Class 1M devices are considered safe to the unaided eye. Do not view directly with optical
1
instruments.

1.1.2 INSPECTION CHECKLIST

1. Open the relay packaging and inspect the unit for physical damage.
2. View the rear nameplate and verify that the correct model has been ordered.
Figure 1–1: REAR NAMEPLATE (EXAMPLE)
3. Ensure that the following items are included:
• Instruction manual.
• GE EnerVista CD (includes the EnerVista UR Setup software and manuals in PDF format).
• Mounting screws.
For product information, instruction manual updates, and the latest software updates, please visit the GE Grid Solutions website.
If there is any noticeable physical damage, or any of the contents listed are missing, contact GE Multilin immedi­ately.
GE MULTILIN CONTACT INFORMATION AND CALL CENTER FOR PRODUCT SUPPORT:
TELEPHONE: Worldwide +1 905 927 7070
Europe/Middle East/Africa +34 94 485 88 54 North America toll-free 1 800 547 8629
FAX: +1 905 927 5098 E-MAIL: Worldwide multilin.tech@ge.com
Europe multilin.tech.euro@ge.com
HOME PAGE: http://www.gegridsolutions.com/multilin
1-2 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.2 UR OVERVIEW

1.2UR OVERVIEW 1.2.1 INTRODUCTION TO THE UR

Historically, substation protection, control, and metering functions were performed with electromechanical equipment. This first generation of equipment was gradually replaced by analog electronic equipment, most of which emulated the single­function approach of their electromechanical precursors. Both of these technologies required expensive cabling and auxil­iary equipment to produce functioning systems.
Recently, digital electronic equipment has begun to provide protection, control, and metering functions. Initially, this equip­ment was either single function or had very limited multi-function capability, and did not significantly reduce the cabling and auxiliary equipment required. However, recent digital relays have become quite multi-functional, reducing cabling and aux­iliaries significantly. These devices also transfer data to central control facilities and Human Machine Interfaces using elec­tronic communications. The functions performed by these products have become so broad that many users now prefer the term IED (Intelligent Electronic Device).
It is obvious to station designers that the amount of cabling and auxiliary equipment installed in stations can be even further reduced, to 20% to 70% of the levels common in 1990, to achieve large cost reductions. This requires placing even more functions within the IEDs.
Users of power equipment are also interested in reducing cost by improving power quality and personnel productivity, and as always, in increasing system reliability and efficiency. These objectives are realized through software which is used to perform functions at both the station and supervisory levels. The use of these systems is growing rapidly.
High speed communications are required to meet the data transfer rates required by modern automatic control and moni­toring systems. In the near future, very high speed communications will be required to perform protection signaling with a performance target response time for a command signal between two IEDs, from transmission to reception, of less than 3 milliseconds. This has been established by the IEC 61850 standard.
IEDs with the capabilities outlined above will also provide significantly more power system data than is presently available, enhance operations and maintenance, and permit the use of adaptive system configuration for protection and control sys­tems. This new generation of equipment must also be easily incorporated into automation systems, at both the station and enterprise levels. The GE Multilin Universal Relay (UR) has been developed to meet these goals.
1
GE Multilin F35 Multiple Feeder Protection System 1-3
1.2 UR OVERVIEW 1 GETTING STARTED
827822A2.CDR
Input Elements
LAN
Programming
Device
Operator Interface
Contact Inputs Contact Outputs
Virtual Inputs
Virtual Outputs
Analog Inputs
Analog Outputs
CT Inputs
VT Inputs
Input
Status
Table
Output
Status
Table
Pickup Dropout Operate
Protective Elements
Logic Gates
Remote Outputs
-DNA
-USER
CPU Module Output Elements
Remote Inputs
Direct Inputs
Direct Outputs

1.2.2 HARDWARE ARCHITECTURE

1
a) UR BASIC DESIGN
The UR is a digital-based device containing a central processing unit (CPU) that handles multiple types of input and output signals. The UR can communicate over a local area network (LAN) with an operator interface, a programming device, or another UR device.
Figure 1–2: UR CONCEPT BLOCK DIAGRAM
The CPU module contains firmware that provides protection elements in the form of logic algorithms, as well as program­mable logic gates, timers, and latches for control features.
Input elements accept a variety of analog or digital signals from the field. The UR isolates and converts these signals into logic signals used by the relay.
Output elements convert and isolate the logic signals generated by the relay into digital or analog signals that can be used to control field devices.
b) UR SIGNAL TYPES
The contact inputs and outputs are digital signals associated with connections to hard-wired contacts. Both ‘wet’ and ‘dry’ contacts are supported.
The virtual inputs and outputs are digital signals associated with UR-series internal logic signals. Virtual inputs include signals generated by the local user interface. The virtual outputs are outputs of FlexLogic™ equations used to customize the device. Virtual outputs can also serve as virtual inputs to FlexLogic™ equations.
The analog inputs and outputs are signals that are associated with transducers, such as Resistance Temperature Detec- tors (RTDs).
The CT and VT inputs refer to analog current transformer and voltage transformer signals used to monitor AC power lines. The UR-series relays support 1 A and 5 A CTs.
The remote inputs and outputs provide a means of sharing digital point state information between remote UR-series devices. The remote outputs interface to the remote inputs of other UR-series devices. Remote outputs are FlexLogic™ operands inserted into IEC 61850 GSSE and GOOSE messages.
The direct inputs and outputs provide a means of sharing digital point states between a number of UR-series IEDs over a dedicated fiber (single or multimode), RS422, or G.703 interface. No switching equipment is required as the IEDs are con­nected directly in a ring or redundant (dual) ring configuration. This feature is optimized for speed and intended for pilot­aided schemes, distributed logic applications, or the extension of the input/output capabilities of a single relay chassis.
1-4 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.2 UR OVERVIEW
827823A1.CDR
PKP DPO OP
Protective Elements
Protection elements
serviced by sub-scan
Read Inputs
Solve Logic
Set Outputs
c) UR SCAN OPERATION
The UR-series devices operate in a cyclic scan fashion. The device reads the inputs into an input status table, solves the logic program (FlexLogic™ equation), and then sets each output to the appropriate state in an output status table. Any resulting task execution is priority interrupt-driven.
Figure 1–3: UR-SERIES SCAN OPERATION
1

1.2.3 SOFTWARE ARCHITECTURE

The firmware (software embedded in the relay) is designed in functional modules which can be installed in any relay as required. This is achieved with object-oriented design and programming (OOD/OOP) techniques.
Object-oriented techniques involve the use of objects and classes. An object is defined as “a logical entity that contains both data and code that manipulates that data”. A class is the generalized form of similar objects. By using this concept, one can create a protection class with the protection elements as objects of the class, such as time overcurrent, instanta­neous overcurrent, current differential, undervoltage, overvoltage, underfrequency, and distance. These objects represent completely self-contained software modules. The same object-class concept can be used for metering, input/output control, hmi, communications, or any functional entity in the system.
Employing OOD/OOP in the software architecture of the F35 achieves the same features as the hardware architecture: modularity, scalability, and flexibility. The application software for any UR-series device (for example, feeder protection, transformer protection, distance protection) is constructed by combining objects from the various functionality classes. This results in a common look and feel across the entire family of UR-series platform-based applications.

1.2.4 IMPORTANT CONCEPTS

As described above, the architecture of the UR-series relays differ from previous devices. To achieve a general understand­ing of this device, some sections of Chapter 5 are quite helpful. The most important functions of the relay are contained in “elements”. A description of the UR-series elements can be found in the Introduction to elements section in chapter 5. Examples of simple elements, and some of the organization of this manual, can be found in the Control elements section of chapter 5. An explanation of the use of inputs from CTs and VTs is in the Introduction to AC sources section in chapter 5. A description of how digital signals are used and routed within the relay is contained in the Introduction to FlexLogic™ section in chapter 5.
GE Multilin F35 Multiple Feeder Protection System 1-5
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED

1.3ENERVISTA UR SETUP SOFTWARE 1.3.1 PC REQUIREMENTS

1
The faceplate keypad and display or the EnerVista UR Setup software interface can be used to communicate with the relay. The EnerVista UR Setup software interface is the preferred method to edit settings and view actual values because the PC monitor can display more information in a simple comprehensible format.
The following minimum requirements must be met for the EnerVista UR Setup software to properly operate on a PC.
Pentium class or higher processor (Pentium II 300 MHz or higher recommended)
Windows 95, 98, 98SE, ME, NT 4.0 (Service Pack 4 or higher), 2000, XP
Internet Explorer 4.0 or higher
128 MB of RAM (256 MB recommended)
200 MB of available space on system drive and 200 MB of available space on installation drive
Video capable of displaying 800 x 600 or higher in high-color mode (16-bit color)
RS232 and/or Ethernet port for communications to the relay
The following qualified modems have been tested to be compliant with the F35 and the EnerVista UR Setup software.
US Robotics external 56K FaxModem 5686
US Robotics external Sportster 56K X2
PCTEL 2304WT V.92 MDC internal modem

1.3.2 INSTALLATION

After ensuring the minimum requirements for using EnerVista UR Setup are met (see previous section), use the following procedure to install the EnerVista UR Setup from the enclosed GE EnerVista CD.
1. Insert the GE EnerVista CD into your CD-ROM drive.
2. Click the Install Now button and follow the installation instructions to install the no-charge EnerVista software.
3. When installation is complete, start the EnerVista Launchpad application.
4. Click the IED Setup section of the Launch Pad window.
5. In the EnerVista Launch Pad window, click the Add Product button and select the “F35 Multiple Feeder Protection System” from the Install Software window as shown below. Select the “Web” option to ensure the most recent software
1-6 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
release, or select “CD” if you do not have a web connection, then click the Add Now button to list software items for the F35.
6. EnerVista Launchpad will obtain the software from the Web or CD and automatically start the installation program.
7. Select the complete path, including the new directory name, where the EnerVista UR Setup will be installed.
8. Click on Next to begin the installation. The files will be installed in the directory indicated and the installation program
will automatically create icons and add EnerVista UR Setup to the Windows start menu.
9. Click Finish to end the installation. The UR-series device will be added to the list of installed IEDs in the EnerVista
Launchpad window, as shown below.
1

1.3.3 CONFIGURING THE F35 FOR SOFTWARE ACCESS

a) OVERVIEW
The user can connect remotely to the F35 through the rear RS485 port or the rear Ethernet port with a PC running the EnerVista UR Setup software. The F35 can also be accessed locally with a laptop computer through the front panel RS232 port or the rear Ethernet port using the Quick Connect feature.
GE Multilin F35 Multiple Feeder Protection System 1-7
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
To configure the F35 for remote access via the rear RS485 port(s), refer to the Configuring Serial Communications
1
section.
To configure the F35 for remote access via the rear Ethernet port, refer to the Configuring Ethernet Communications section. An Ethernet module must be specified at the time of ordering.
To configure the F35 for local access with a laptop through either the front RS232 port or rear Ethernet port, refer to the Using the Quick Connect Feature section. An Ethernet module must be specified at the time of ordering for Ethernet communications.
b) CONFIGURING SERIAL COMMUNICATIONS
Before starting, verify that the serial cable is properly connected to the RS485 terminals on the back of the device. The faceplate RS232 port is intended for local use and is not described in this section; see the Using the Quick Connect Feature section for details on configuring the RS232 port.
A GE Multilin F485 converter (or compatible RS232-to-RS485 converter) is will be required. Refer to the F485 instruction manual for additional details.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE EnerVista CD or online from http://www.gegridsolutions.com/multilin
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
3. Click the Device Setup button to open the Device Setup window and click the Add Site button to define a new site.
4. Enter the desired site name in the “Site Name” field. If desired, a short description of site can also be entered along with the display order of devices defined for the site. In this example, we will use “Location 1” as the site name. Click the OK button when complete.
5. The new site will appear in the upper-left list in the EnerVista UR Setup window. Click the Device Setup button then select the new site to re-open the Device Setup window.
6. Click the Add Device button to define the new device.
7. Enter the desired name in the “Device Name” field and a description (optional) of the site.
8. Select “Serial” from the Interface drop-down list. This will display a number of interface parameters that must be entered for proper serial communications.
). See the Software Installation section for installation details.
Figure 1–4: CONFIGURING SERIAL COMMUNICATIONS
1-8 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
9. Enter the relay slave address, COM port, baud rate, and parity settings from the SETTINGS PRODUCT SETUP  COM-
MUNICATIONS  SERIAL PORTS menu in their respective fields.
10. Click the Read Order Code button to connect to the F35 device and upload the order code. If an communications error
occurs, ensure that the EnerVista UR Setup serial communications values entered in the previous step correspond to the relay setting values.
11. Click “OK” when the relay order code has been received. The new device will be added to the Site List window (or
Online window) located in the top left corner of the main EnerVista UR Setup window.
The Site Device has now been configured for RS232 communications. Proceed to the Connecting to the F35 section to begin communications.
c) CONFIGURING ETHERNET COMMUNICATIONS
Before starting, verify that the Ethernet network cable is properly connected to the Ethernet port on the back of the relay. To setup the relay for Ethernet communications, it will be necessary to define a Site, then add the relay as a Device at that site.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE EnerVista CD or
online from http://www.gegridsolutions.com/multilin
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
3. Click the Device Setup button to open the Device Setup window, then click the Add Site button to define a new site.
4. Enter the desired site name in the “Site Name” field. If desired, a short description of site can also be entered along
with the display order of devices defined for the site. In this example, we will use “Location 2” as the site name. Click the OK button when complete.
5. The new site will appear in the upper-left list in the EnerVista UR Setup window. Click the Device Setup button then
select the new site to re-open the Device Setup window.
6. Click the Add Device button to define the new device.
7. Enter the desired name in the “Device Name” field and a description (optional) of the site.
8. Select “Ethernet” from the Interface drop-down list. This will display a number of interface parameters that must be
entered for proper Ethernet functionality.
). See the Software Installation section for installation details.
1
Figure 1–5: CONFIGURING ETHERNET COMMUNICATIONS
GE Multilin F35 Multiple Feeder Protection System 1-9
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
9. Enter the relay IP address specified in the SETTINGS PRODUCT SETUP  COMMUNICATIONS  NETWORK IP
1
ADDRESS) in the “IP Address” field.
10. Enter the relay slave address and Modbus port address values from the respective settings in the SETTINGS PROD-
UCT SETUP  COMMUNICATIONS  MODBUS PROTOCOL menu.
11. Click the Read Order Code button to connect to the F35 device and upload the order code. If an communications error occurs, ensure that the three EnerVista UR Setup values entered in the previous steps correspond to the relay setting values.
12. Click OK when the relay order code has been received. The new device will be added to the Site List window (or Online window) located in the top left corner of the main EnerVista UR Setup window.
The Site Device has now been configured for Ethernet communications. Proceed to the Connecting to the F35 section to begin communications.

1.3.4 USING THE QUICK CONNECT FEATURE

a) USING QUICK CONNECT VIA THE FRONT PANEL RS232 PORT
Before starting, verify that the serial cable is properly connected from the laptop computer to the front panel RS232 port with a straight-through 9-pin to 9-pin RS232 cable.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE EnerVista CD or online from http://www.gegridsolutions.com/multilin
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
3. Click the Quick Connect button to open the Quick Connect dialog box.
). See the Software Installation section for installation details.
4. Select the Serial interface and the correct COM Port, then click Connect.
5. The EnerVista UR Setup software will create a site named “Quick Connect” with a corresponding device also named “Quick Connect” and display them on the upper-left corner of the screen. Expand the sections to view data directly from the F35 device.
Each time the EnerVista UR Setup software is initialized, click the Quick Connect button to establish direct communica­tions to the F35. This ensures that configuration of the EnerVista UR Setup software matches the F35 model number.
b) USING QUICK CONNECT VIA THE REAR ETHERNET PORTS
To use the Quick Connect feature to access the F35 from a laptop through Ethernet, first assign an IP address to the relay from the front panel keyboard.
1. Press the MENU key until the SETTINGS menu is displayed.
2. Navigate to the
3. Enter an IP address of “1.1.1.1” and select the ENTER key to save the value.
4. In the same menu, select the
5. Enter a subnet IP address of “255.0.0.0” and press the ENTER key to save the value.
SETTINGS PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting.
SUBNET IP MASK setting.
1-10 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
842799A1.CDR
END 1 END 2 Pin Wire color Diagram Pin Wire color Diagram
1 White/orange 1 White/green 2 Orange 2 Green
3 White/green 3 White/orange 4 Blue 4 Blue 5 White/blue 5 White/blue 6 Green 6 Orange 7 White/brown 7 White/brown 8 Brown 8 Brown
1
2
3
4
5
6
7
8
Next, use an Ethernet cross-over cable to connect the laptop to the rear Ethernet port. The pinout for an Ethernet cross­over cable is shown below.
Figure 1–6: ETHERNET CROSS-OVER CABLE PIN LAYOUT
Now, assign the laptop computer an IP address compatible with the relay’s IP address.
1. From the Windows desktop, right-click the My Network Places icon and select Properties to open the network con-
nections window.
1
2. Right-click the Local Area Connection icon and select Properties.
GE Multilin F35 Multiple Feeder Protection System 1-11
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
3. Select the Internet Protocol (TCP/IP) item from the list provided and click the Properties button.
1
4. Click on the “Use the following IP address” box.
5. Enter an IP address with the first three numbers the same as the IP address of the F35 relay and the last number dif­ferent (in this example, 1.1.1.2).
6. Enter a subnet mask equal to the one set in the F35 (in this example, 255.0.0.0).
7. Click OK to save the values.
Before continuing, it will be necessary to test the Ethernet connection.
1. Open a Windows console window by selecting Start > Run from the Windows Start menu and typing “cmd”.
2. Type the following command:
C:\WINNT>ping 1.1.1.1
3. If the connection is successful, the system will return four replies as follows:
Pinging 1.1.1.1 with 32 bytes of data:
Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 4, Lost = 0 (0% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
4. Note that the values for time and TTL will vary depending on local network configuration.
If the following sequence of messages appears when entering the
C:\WINNT>ping 1.1.1.1 command:
1-12 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
Pinging 1.1.1.1 with 32 bytes of data:
Request timed out. Request timed out. Request timed out. Request timed out.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
Verify the physical connection between the F35 and the laptop computer, and double-check the programmed IP address in
PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting, then repeat step 2 in the above procedure.
the
If the following sequence of messages appears when entering the
Pinging 1.1.1.1 with 32 bytes of data:
Hardware error. Hardware error. Hardware error. Hardware error.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
C:\WINNT>ping 1.1.1.1 command:
Verify the physical connection between the F35 and the laptop computer, and double-check the programmed IP address in
PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting, then repeat step 2 in the above procedure.
the
If the following sequence of messages appears when entering the
Pinging 1.1.1.1 with 32 bytes of data:
Destination host unreachable. Destination host unreachable. Destination host unreachable. Destination host unreachable.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
C:\WINNT>ping 1.1.1.1 command:
Verify the IP address is programmed in the local PC by entering the ipconfig command in the command window.
C:\WINNT>ipconfig
Windows 2000 IP Configuration
Ethernet adapter <F4FE223E-5EB6-4BFB-9E34-1BD7BE7F59FF>:
Connection-specific DNS suffix. . :
IP Address. . . . . . . . . . . . : 0.0.0.0
Subnet Mask . . . . . . . . . . . : 0.0.0.0
Default Gateway . . . . . . . . . :
Ethernet adapter Local Area Connection:
Connection-specific DNS suffix . :
IP Address. . . . . . . . . . . . : 1.1.1.2
Subnet Mask . . . . . . . . . . . : 255.0.0.0
Default Gateway . . . . . . . . . :
C:\WINNT>
It may be necessary to restart the laptop for the change in IP address to take effect (Windows 98 or NT).
1
GE Multilin F35 Multiple Feeder Protection System 1-13
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
Before using the Quick Connect feature through the Ethernet port, it is necessary to disable any configured proxy settings in Internet Explorer.
1
1. Start the Internet Explorer software.
2. Select the Tools > Internet Options menu item and click on Connections tab.
3. Click on the LAN Settings button to open the following window.
4. Ensure that the “Use a proxy server for your LAN” box is not checked.
If this computer is used to connect to the Internet, re-enable any proxy server settings after the laptop has been discon­nected from the F35 relay.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE enerVista CD or online from http://www.gegridsolutions.com/multilin). See the Software Installation section for installation details.
2. Start the Internet Explorer software.
3. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
4. Click the Quick Connect button to open the Quick Connect dialog box.
5. Select the Ethernet interface and enter the IP address assigned to the F35, then click Connect.
6. The EnerVista UR Setup software will create a site named “Quick Connect” with a corresponding device also named “Quick Connect” and display them on the upper-left corner of the screen. Expand the sections to view data directly from the F35 device.
Each time the EnerVista UR Setup software is initialized, click the Quick Connect button to establish direct communica­tions to the F35. This ensures that configuration of the EnerVista UR Setup software matches the F35 model number.
When direct communications with the F35 via Ethernet is complete, make the following changes:
1. From the Windows desktop, right-click the My Network Places icon and select Properties to open the network con­nections window.
2. Right-click the Local Area Connection icon and select the Properties item.
3. Select the Internet Protocol (TCP/IP) item from the list provided and click the Properties button.
1-14 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
4. Set the computer to “Obtain a relay address automatically” as shown below.
If this computer is used to connect to the Internet, re-enable any proxy server settings after the laptop has been discon­nected from the F35 relay.
AUTOMATIC DISCOVERY OF ETHERNET DEVICES
The EnerVista UR Setup software can automatically discover and communicate to all UR-series IEDs located on an Ether­net network.
Using the Quick Connect feature, a single click of the mouse will trigger the software to automatically detect any UR-series relays located on the network. The EnerVista UR Setup software will then proceed to configure all settings and order code options in the Device Setup menu, for the purpose of communicating to multiple relays. This feature allows the user to identify and interrogate, in seconds, all UR-series devices in a particular location.
1
GE Multilin F35 Multiple Feeder Protection System 1-15
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
842743A3.CDR
Communications status indicators:
Green = OK Red = No communications UR icon = report is open
Quick action hot links
Expand the site list by double-clicking or selecting the +/– box.
NOTE
1
1. Open the Display Properties window through the Site List tree as shown below:

1.3.5 CONNECTING TO THE F35 RELAY

2. The Display Properties window will open with a status indicator on the lower left of the EnerVista UR Setup window.
3. If the status indicator is red, verify that the Ethernet network cable is properly connected to the Ethernet port on the back of the relay and that the relay has been properly setup for communications (steps A and B earlier).
If a relay icon appears in place of the status indicator, than a report (such as an oscillography or event record) is open. Close the report to re-display the green status indicator.
4. The Display Properties settings can now be edited, printed, or changed according to user specifications.
See chapter 4 in this manual and the EnerVista UR Setup Help File for more information about the using the EnerV­ista UR Setup software interface.
QUICK ACTION HOT LINKS
The EnerVista UR Setup software has several new quick action buttons that provide users with instant access to several functions that are often performed when using F35 relays. From the online window, users can select which relay to interro­gate from a pull-down window, then click on the button for the action they wish to perform. The following quick action func­tions are available:
View the F35 event record.
View the last recorded oscillography record.
View the status of all F35 inputs and outputs.
View all of the F35 metering values.
View the F35 protection summary.
1-16 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.4 UR HARDWARE

1.4UR HARDWARE 1.4.1 MOUNTING AND WIRING

Please refer to Chapter 3: Hardware for detailed mounting and wiring instructions. Review all WARNINGS and CAUTIONS carefully.

1.4.2 COMMUNICATIONS

The EnerVista UR Setup software communicates to the relay via the faceplate RS232 port or the rear panel RS485 / Ether­net ports. To communicate via the faceplate RS232 port, a standard straight-through serial cable is used. The DB-9 male end is connected to the relay and the DB-9 or DB-25 female end is connected to the PC COM1 or COM2 port as described in the CPU communications ports section of chapter 3.
1
Figure 1–7: RELAY COMMUNICATIONS OPTIONS
To communicate through the F35 rear RS485 port from a PC RS232 port, the GE Multilin RS232/RS485 converter box is required. This device (catalog number F485) connects to the computer using a “straight-through” serial cable. A shielded twisted-pair (20, 22, or 24 AWG) connects the F485 converter to the F35 rear communications port. The converter termi­nals (+, –, GND) are connected to the F35 communication module (+, –, COM) terminals. Refer to the CPU communica- tions ports section in chapter 3 for option details. The line should be terminated with an R-C network (that is, 120 Ω, 1 nF) as described in the chapter 3.

1.4.3 FACEPLATE DISPLAY

All messages are displayed on a 2 × 20 backlit liquid crystal display (LCD) to make them visible under poor lighting condi­tions. Messages are descriptive and should not require the aid of an instruction manual for deciphering. While the keypad and display are not actively being used, the display will default to user-defined messages. Any high priority event driven message will automatically override the default message and appear on the display.
GE Multilin F35 Multiple Feeder Protection System 1-17
1.5 USING THE RELAY 1 GETTING STARTED

1.5USING THE RELAY 1.5.1 FACEPLATE KEYPAD

1
Display messages are organized into pages under the following headings: actual values, settings, commands, and targets. The MENU key navigates through these pages. Each heading page is broken down further into logical subgroups.
The MESSAGE keys navigate through the subgroups. The VALUE keys scroll increment or decrement numerical setting values when in programming mode. These keys also scroll through alphanumeric values in the text edit mode. Alterna­tively, values may also be entered with the numeric keypad.
The decimal key initiates and advance to the next character in text edit mode or enters a decimal point. The HELP key may be pressed at any time for context sensitive help messages. The ENTER key stores altered setting values.

1.5.2 MENU NAVIGATION

Press the MENU key to select the desired header display page (top-level menu). The header title appears momentarily fol­lowed by a header display page menu item. Each press of the MENU key advances through the following main heading pages:
Actual values.
Settings.
Commands.
Targets.
User displays (when enabled).

1.5.3 MENU HIERARCHY

The setting and actual value messages are arranged hierarchically. The header display pages are indicated by double scroll bar characters (), while sub-header pages are indicated by single scroll bar characters (). The header display pages represent the highest level of the hierarchy and the sub-header display pages fall below this level. The MESSAGE UP and DOWN keys move within a group of headers, sub-headers, setting values, or actual values. Continually pressing the MESSAGE RIGHT key from a header display displays specific information for the header category. Conversely, contin­ually pressing the MESSAGE LEFT key from a setting value or actual value display returns to the header display.
HIGHEST LEVEL LOWEST LEVEL (SETTING VALUE)
 SETTINGS  PRODUCT SETUP
 SETTINGS  SYSTEM SETUP
The relay is defaulted to the “Not Programmed” state when it leaves the factory. This safeguards against the installation of a relay whose settings have not been entered. When powered up successfully, the Trouble LED will be on and the In Ser­vice LED off. The relay in the “Not Programmed” state will block signaling of any output relay. These conditions will remain until the relay is explicitly put in the “Programmed” state.
Select the menu message
RELAY SETTINGS: Not Programmed
SETTINGS PRODUCT SETUP  INSTALLATION RELAY SETTINGS
PASSWORD SECURITY
ACCESS LEVEL: Restricted

1.5.4 RELAY ACTIVATION

1-18 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.5 USING THE RELAY
NOTE
To put the relay in the “Programmed” state, press either of the VALUE keys once and then press ENTER. The faceplate Trouble LED will turn off and the In Service LED will turn on. The settings for the relay can be programmed manually (refer to Chapter 5) via the faceplate keypad or remotely (refer to the EnerVista UR Setup help file) via the EnerVista UR Setup software interface.

1.5.5 RELAY PASSWORDS

It is recommended that passwords be set up for each security level and assigned to specific personnel. There are two user password security access levels, COMMAND and SETTING:
1. COMMAND
The COMMAND access level restricts the user from making any settings changes, but allows the user to perform the fol­lowing operations:
change state of virtual inputs
clear event records
clear oscillography records
operate user-programmable pushbuttons
2. SETTING
The SETTING access level allows the user to make any changes to any of the setting values.
See the Changing Settings section in Chapter 4 for complete instructions on setting up security level passwords.
1

1.5.6 FLEXLOGIC™ CUSTOMIZATION

FlexLogic™ equation editing is required for setting up user-defined logic for customizing the relay operations. See the Flex­Logic™ section in Chapter 5 for additional details.
GE Multilin F35 Multiple Feeder Protection System 1-19
1.5 USING THE RELAY 1 GETTING STARTED

1.5.7 COMMISSIONING

1
The F35 requires a minimum amount of maintenance when it is commissioned into service. Since the F35 is a microproces­sor-based relay, its characteristics do not change over time. As such, no further functional tests are required.
Furthermore, the F35 performs a number of continual self-tests and takes the necessary action in case of any major errors (see the Relay Self-tests section in chapter 7 for details). However, it is recommended that F35 maintenance be scheduled with other system maintenance. This maintenance may involve the in-service, out-of-service, or unscheduled maintenance.
In-service maintenance:
1. Visual verification of the analog values integrity such as voltage and current (in comparison to other devices on the cor­responding system).
2. Visual verification of active alarms, relay display messages, and LED indications.
3. LED test.
4. Visual inspection for any damage, corrosion, dust, or loose wires.
5. Event recorder file download with further events analysis.
Out-of-service maintenance:
1. Check wiring connections for firmness.
2. Analog values (currents, voltages, RTDs, analog inputs) injection test and metering accuracy verification. Calibrated test equipment is required.
3. Protection elements setting verification (analog values injection or visual verification of setting file entries against relay settings schedule).
4. Contact inputs and outputs verification. This test can be conducted by direct change of state forcing or as part of the system functional testing.
5. Visual inspection for any damage, corrosion, or dust.
6. Event recorder file download with further events analysis.
7. LED Test and pushbutton continuity check.
Unscheduled maintenance such as during a disturbance causing system interruption:
1. View the event recorder and oscillography or fault report for correct operation of inputs, outputs, and elements.
If it is concluded that the relay or one of its modules is of concern, contact GE Multilin for prompt service.
1-20 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION

2 PRODUCT DESCRIPTION 2.1INTRODUCTION 2.1.1 OVERVIEW

The F35 Multiple Feeder Protection System is a microprocessor based relay designed for the protection of up to five feed­ers with busbar voltage measurement or up to six feeders without busbar voltage.
Overcurrent and undervoltage protection, breaker recloser, underfrequency, fault diagnostics, and RTU functions are pro­vided. The F35 provides phase, neutral/ground, instantaneous and time overcurrent protection. The time overcurrent func­tion provides multiple curve shapes or FlexCurve™ for optimum co-ordination.
Voltage, current, and power metering is built into the relay as a standard feature. Current parameters are available as total waveform RMS magnitude, or as fundamental frequency only RMS magnitude and angle (phasor). Voltage harmonics and THD metering are also included with the relay.
Diagnostic features include a sequence of records capable of storing 1024 time-tagged events. The internal clock used for time-tagging can be synchronized with an IRIG-B signal or via the SNTP protocol over the Ethernet port. This precise time stamping allows the sequence of events to be determined throughout the system. Events can also be programmed (via FlexLogic™ equations) to trigger oscillography data capture which may be set to record the measured parameters before and after the event for viewing on a personal computer (PC). These tools significantly reduce troubleshooting time and sim­plify report generation in the event of a system fault.
A faceplate RS232 port may be used to connect to a PC for the programming of settings and the monitoring of actual val­ues. A variety of communications modules are available. Two rear RS485 ports allow independent access by operating and engineering staff. All serial ports use the Modbus
®
RTU protocol. The RS485 ports may be connected to system computers with baud rates up to 115.2 kbps. The RS232 port has a fixed baud rate of 19.2 kbps. Optional communications modules include a 10Base-F Ethernet interface which can be used to provide fast, reliable communications in noisy environments. Another option provides two 10Base-F fiber optic ports for redundancy. The Ethernet port supports IEC 61850, Modbus TCP, and TFTP protocols, and allows access to the relay via any standard web browser (F35 web pages). The IEC 60870­5-104 protocol is supported on the Ethernet port. DNP 3.0 and IEC 60870-5-104 cannot be enabled at the same time.
The F35 IEDs use flash memory technology which allows field upgrading as new features are added. The following Single line diagram illustrates the relay functionality using ANSI (American National Standards Institute) device numbers.
2
®
/
Table 2–1: ANSI DEVICE NUMBERS AND FUNCTIONS
DEVICE NUMBER
27P Phase undervoltage 51N (up to 6) Neutral time overcurrent
27X Auxiliary undervoltage 51P (up to 6) Phase time overcurrent
50DD Disturbance detector 51_2 (2) Negative-sequence time overcurrent
50G (up to 12) Ground instantaneous overcurrent 52 AC circuit breaker
50N (up to 12) Neutral instantaneous overcurrent 59N Neutral overvoltage
50P (up to 12) Phase instantaneous overcurrent 59X Auxiliary overvoltage
50_2 (2) Negative-sequence instantaneous overcurrent 79 (up to 6) Autoreclose
51G (up to 6) Ground time overcurrent 81 (up to 6) Underfrequency
FUNCTION DEVICE
NUMBER
FUNCTION
GE Multilin F35 Multiple Feeder Protection System 2-1
2.1 INTRODUCTION 2 PRODUCT DESCRIPTION
$&'5

* *
6DPHIXQFWLRQVDVEUHDNHU
)RUEUHDNHU
3 B 1 1
8
1 ;
3;
0HWHULQJ

)0XOWLSOH)HHGHU3URWHFWLRQ6\VWHP
0RQLWRULQJ
&/26(
75,3

7UDQVGXFHU
LQSXWV
)OH[(OHPHQWV
70
3 B
NOTE
2
Table 2–2: OTHER DEVICE FUNCTIONS
FUNCTION FUNCTION FUNCTION
Breaker arcing current (I
Breaker control Event recorder Setting groups (6)
Contact inputs (up to 96) Fault detector and fault report Teleprotection inputs and outputs
Contact outputs (up to 64) FlexElements™ (16) Time synchronization over SNTP
Control pushbuttons FlexLogic™ equations Transducer inputs and outputs
Data logger IEC 61850 communications (optional) User-definable displays
Demand Incipient cable fault detection User-programmable LEDs
Digital counters (8) Metering: current, voltage, power, energy,
Digital elements (48) User-programmable self-tests
Direct inputs and outputs (32) Modbus user map Virtual inputs (64)
Disconnect switches Non-volatile latches Virtual outputs (96)
DNP 3.0 or IEC 60870-5-104 comms. Non-volatile selector switch
2
t) Ethernet Global Data protocol (optional) Oscillography
Figure 2–1: SINGLE LINE DIAGRAM
User-programmable pushbuttons
frequency, harmonics, THD

2.1.2 ORDERING

a) OVERVIEW
The F35 is available as a 19-inch rack horizontal mount or reduced-size (¾) vertical unit and consists of the following mod­ules: power supply, CPU, CT/VT, digital input and output, transducer input and output, and inter-relay communications. Each of these modules can be supplied in a number of configurations specified at the time of ordering. The information required to completely specify the relay is provided in the following tables (see chapter 3 for full details of relay modules).
Order codes are subject to change without notice. See the web page for the product for the latest ordering options.
The order code structure is dependent on the mounting option (horizontal or vertical) and the type of CT/VT modules (regu­lar CT/VT modules or the HardFiber modules). The order code options are described in the following sub-sections.
2-2 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION
b) ORDER CODES WITH TRADITIONAL CTS AND VTS
The order codes for the horizontal mount units with traditional CTs and VTs are shown below.
Table 2–3: F35 ORDER CODES (HORIZONTAL UNITS)
BASE UNIT F35 | | | | | | | | | | | Base Unit CPU E | | | | | | | | | | RS485 and RS485
SOFTWARE 00 | | | | | | | | | No Software Options
MOUNT/COATING H | | | | | | | | Horizontal (19” rack)
FACEPLATE/ DISPLAY C | | | | | | | English display
POWER SUPPLY (redundant supply must be same type as main supply)
CT/VT MODULES 8F | 8F | 8F | Standard 4CT/4VT
DIGITAL INPUTS/OUTPUTS XX XX XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
F35 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
J | | | | | | | | | | RS485, multi -mode ST 100Base-FX, and 10/100Base-T K | | | | | | | | | | RS485, multi-mode ST redundant 100Base- FX, and 10/100Base-T N | | | | | | | | | | RS485 and 1 0/100Base-T S | | | | | | | | | | RS485 and six-port managed Ethernet switch ( four 100Base-FX and two 100Base-T)
01 | | | | | | | | | Ethernet Global Data (EGD); not available for Type E CPUs 03 | | | | | | | | | IEC 61850; not available for Type E CPUs 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850; not available for Type E CPUs
A | | | | | | | | Horizontal (19” rack) with harsh environmental coating
D | | | | | | | French display R | | | | | | | Russian display A | | | | | | | Chinese display P | | | | | | | English display with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with r edundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) w ith redundant 24 to 48 V DC power supply
8G | 8G | 8G | Sensitive Ground 4CT/4VT 8H | 8H | 8H | Standard 8CT 8J | 8J | 8J | Sensitive Ground 8CT 8L | 8L | 8L | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | 8N | Standard 8CT with enhanced diagnostics 8R | 8R | 8R | Sensitive Ground 8CT with enhanced dia gnostics 8V | | | | | Standard 8VT with enhanced diagnostics (only one module supported)
4A 4A 4A 4A 4A 4 Solid-State (no monitoring) MOSFET out puts 4B 4B 4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET out puts 4C 4C 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 4D 4D 16 digital inputs with Auto-Burnishing 4L 4L 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs 6B 6B 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs 6C 6C 6C 6C 6C 8 Form-C outputs 6D 6D 6D 6D 6D 16 digital inputs 6E 6E 6E 6E 6E 4 Form-C outputs, 8 digi tal inputs 6F 6F 6F 6F 6F 8 Fast Form-C out puts 6G 6G 6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 digital inputs 6H 6H 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 6K 6K 6K 6K 4 Form-C and 4 F ast Form-C outputs 6L 6L 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 6M 6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 6N 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6P 6P 6P 6P 6 Form-A (curr ent with optional voltage) outputs, 4 digital inputs 6R 6R 6R 6R 6R 2 Form-A (no monitoring) and 2 Form-C o utputs, 8 digital inputs 6S 6S 6S 6S 6S 2 Form-A (no monit oring) and 4 Form-C outputs, 4 digital inputs 6T 6T 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 digital inputs 6U 6U 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 6V 6V 6V 6V 2 Form-A outputs, 1 For m-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs 5A 5A 5A 5A 5A 4 dcmA inputs, 4 dcmA out puts (only one 5A or 5D module is allowed) 5C 5C 5C 5C 5C 8 RTD inputs 5D 5D 5D 5D 5D 4 RTD inputs, 4 dcmA outputs (only one 5A or 5D module is allowed) 5E 5E 5E 5E 5E 4 RTD inputs, 4 dcmA inputs 5F 5F 5F 5F 5F 8 dcmA inputs
2A 2A C37.94SM, 130 0nm single-mode, ELED, 1 channel single-mode 2B 2B C37.94SM, 130 0nm single-mode, ELED, 2 channel single-mode 2E 2E Bi-ph ase, single channel 2F 2F Bi-phase, dual channel 2G 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels
| 2S Six-port managed Ethernet switch with high voltage power supply (110 to 250 V DC / 100 to 240 V AC )
| 2T Six-port managed Ethernet switch with low voltage power supply (48 V DC) 72 72 1550 nm, single-mode, LASER, 1 Channel 73 73 1550 nm, single-mode, LASER, 2 Channel 74 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, LASER 75 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode LASER 76 76 IEE E C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 77 IEE E C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 7A 820 nm, multi-mode, LED, 1 Channel 7B 7B 1300 nm, multi-mode, LED, 1 Channel 7C 7C 1300 nm, single-mode, ELED, 1 Channel 7D 7D 1300 nm, single-mode, LASER, 1 Channel 7E 7E Channel 1 - G.703; Channel 2 - 820 nm, multi-mode 7F 7F Channel 1 - G.703; Channel 2 - 1300 nm, multi-mode 7G 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 7H 820 nm, multi-mode, LED, 2 Channels
7I 7I 1300 nm, multi-mode, LED, 2 Channels 7J 7J 1300 nm, single-mode, ELED, 2 Channels 7K 7K 1300 nm, single-mode, LASER, 2 Channels 7L 7L Channel 1 - RS422; Channel 2 - 820 nm, multi-mode, LED 7M 7M Channel 1 - RS422; Channel 2 - 1300 nm, multi-mode, LED 7N 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, EL ED 7P 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, LASER 7Q 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode LASER 7R 7R G.703, 1 Channel 7S 7S G.703, 2 Channels 7T 7T RS422, 1 Channel 7W 7W RS422, 2 Channels
2
GE Multilin F35 Multiple Feeder Protection System 2-3
2.1 INTRODUCTION 2 PRODUCT DESCRIPTION
The order codes for the reduced size vertical mount units with traditional CTs and VTs are shown below.
Table 2–4: F35 ORDER CODES (REDUCED SIZE VERTICAL UNITS)
BASE UNIT F35 | | | | | | | | | Base Unit CPU E | | | | | | | | RS485 and RS485
SOFTWARE 00 | | | | | | | No Software Options
MOUNT/COATING V | | | | | | Vertical (3/4 rack)
2
FACEPLATE/ DISPLAY F | | | | | English display
POWER SUPPLY H | | | | 125 / 250 V AC/DC power supply
CT/VT MODULES 8F | 8F | Standard 4CT/4VT
DIGITAL INPUTS/OUTPUTS XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital and transducer input/output modules; slot R is used for inter-relay communications modules.
F35 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
J | | | | | | | | RS485, multi-mode ST 100Base-FX, and 10/100Base-T K | | | | | | | | RS485, mult i-mode ST redundant 100Base-FX, and 10/100Base-T N | | | | | | | | RS485 and 10/100Base-T
01 | | | | | | | Ethernet Global Data (EGD); not available for Type E CPUs 03 | | | | | | | IEC 61850; not available for Type E CPUs 04 | | | | | | | Ethernet Global Data (EGD) and IEC 61850; not available for Type E CPUs
B | | | | | | Vertical (3/4 rack) with harsh environmental coating
D | | | | | French display R | | | | | Russian display A | | | | | Chinese display K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display L | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons
L | | | | 24 to 48 V (DC only) power supply
8G | 8G | Sensitive Ground 4CT/4VT 8H | 8H | Standard 8CT 8J | 8J | Sensitive Ground 8CT 8L | 8L | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | Standard 8CT with enhanced diagnostics 8R | 8R | Sensitive Ground 8CT with enhanced diagnostics 8V | | | Standard 8VT with enhanced diagnostics (only one module supported)
4A 4A 4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 16 digital inputs with Auto-Burnishing 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs 6C 6C 6C 8 Form-C outputs 6D 6D 6D 16 digital inputs 6E 6E 6E 4 Form-C outputs, 8 digital inputs 6F 6F 6F 8 Fast Form-C outputs 6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 digital inputs 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 6K 6K 4 Form-C and 4 Fast Form-C outputs 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 6M 6M 2 For m-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 digital inputs 6R 6R 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs 6S 6S 6S 2 Form-A (no monitoring) and 4 For m-C outputs, 4 digital inputs 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 digital inputs 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 6V 6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs 5A 5A 5A 4 dcmA inputs, 4 dcmA outputs (only one 5A or 5D module is allowe d) 5C 5C 5C 8 RTD inputs 5D 5D 5D 4 RTD inputs, 4 dcmA outputs (only one 5A or 5D module is allowed) 5E 5E 5E 4 RTD inputs, 4 dcmA inputs 5F 5F 5F 8 dcmA inputs
2A C37.94SM, 1300nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 72 1550 nm, single-mode, LASER, 1 Channel 73 1550 nm, single-mode, LASER, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 n m, single-mode, LASER 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode LASER 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multi-mode, LED, 1 Channel 7B 1300 nm, multi-mode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, LASER, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multi-mode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multi-mode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multi-mode, LED, 2 Channels
7I 1300 nm, multi-mode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, LASER, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multi- mode, LED 7M Channel 1 - RS422; Channel 2 - 1300 n m, multi-mode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, LASER 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode LASER 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2-4 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION
c) ORDER CODES WITH PROCESS BUS MODULES
The order codes for the horizontal mount units with the process bus module are shown below.
Table 2–5: F35 ORDER CODES (HORIZONTAL UNITS WITH PROCESS BUS)
BASE UNIT F35 | | | | | | | | | | | Base Unit CPU E | | | | | | | | | | RS485 and RS485
SOFTWARE 00 | | | | | | | | | No Software Options
MOUNT/COATING H | | | | | | | | Hor izontal (19” rack)
FACEPLATE/ DISPLAY C | | | | | | | English display
POWER SUPPLY (redundant supply must be same type as main supply)
PROCESS BUS MODULE | 81 | | | | Eight-port digital process bus module DIGITAL INPUTS/OUTPUTS XX XX XX XX XX No Module
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
F35 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
J | | | | | | | | | | RS485, multi -mode ST 100Base-FX, and 10/100Base-T K | | | | | | | | | | RS485, multi-mode ST redundant 100Base- FX, and 10/100Base-T N | | | | | | | | | | RS485 and 10/100Ba se-T
01 | | | | | | | | | Ethernet Global Data (EGD); not available for Type E CPUs 03 | | | | | | | | | IEC 61850; not available for Type E CPUs 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850; not available for Type E CPUs
A | | | | | | | | Horizontal (19” rack) with harsh environmental coating
D | | | | | | | French display R | | | | | | | Russian display A | | | | | | | Chinese display P | | | | | | | English display with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with r edundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) w ith redundant 24 to 48 V DC power supply
4A 4A | 4 Solid-State (no monitoring) MOSFET outputs 4B 4B | 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C | 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D | 16 digital inputs with Auto-Burnishing 4L 4L | 14 Form-A (no monitoring) Latching outputs 67 67 | 8 Form-A (no monitoring) outputs 6A 6A | 2 Form-A (voltage with optional current) and 2 Form- C outputs, 8 digital inputs 6B 6B | 2 Form-A (voltage with optional current) and 4 Form- C outputs, 4 digital inputs 6C 6C | 8 Form-C outputs 6D 6D | 16 digital inputs 6E 6E | 4 Form-C outputs, 8 digital inputs 6F 6F | 8 Fast Form-C outputs 6G 6G | 4 Form-A (voltage with optiona l current) outputs, 8 digital inputs 6H 6H | 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 6K | 4 Form-C and 4 Fast Form-C outputs 6L 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 6N | 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6P | 6 Form-A (current with optional voltage) outputs, 4 digital inputs 6R 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs 6S 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs 6T 6T | 4 Form-A (no monit oring) outputs, 8 digital inputs 6U 6U | 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 6V | 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs
2A 2A C37.94SM, 130 0nm single-mode, ELED, 1 channel single-mode 2B 2B C37.94SM, 130 0nm single-mode, ELED, 2 channel single-mode 2E 2E Bi-ph ase, single channel 2F 2F Bi-phase, dual channel 2G 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 72 72 1550 nm, single-mode, LASER, 1 Channel 73 73 1550 nm, single-mode, LASER, 2 Channel 74 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, LASER 75 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode LASER 76 76 IEE E C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 77 IEE E C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 7A 820 nm, multi-mode, LED, 1 Channel 7B 7B 1300 nm, multi-mode, LED, 1 Channel 7C 7C 1300 nm, single-mode, ELED, 1 Channel 7D 7D 1300 nm, single-mode, LASER, 1 Channel 7E 7E Channel 1 - G.703; Channel 2 - 820 nm, multi-mode 7F 7F Channel 1 - G.703; Channel 2 - 1300 nm, multi-mode 7G 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 7H 820 nm, multi-mode, LED, 2 Channels
7I 7I 1300 nm, multi-mode, LED, 2 Channels 7J 7J 1300 nm, single-mode, ELED, 2 Channels 7K 7K 1300 nm, single-mode, LASER, 2 Channels 7L 7L Channel 1 - RS422; Channel 2 - 820 nm, multi-mode, LED 7M 7M Channel 1 - RS422; Channel 2 - 1300 nm, multi-mode, LED 7N 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, EL ED 7P 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, LASER 7Q 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode LASER 7R 7R G.703, 1 Channel 7S 7S G.703, 2 Channels 7T 7T RS422, 1 Channel 7W 7W RS422, 2 Channels
2
The order codes for the reduced size vertical mount units with the process bus module are shown below.
Table 2–6: F35 ORDER CODES (REDUCED SIZE VERTICAL UNITS WITH PROCESS BUS)
BASE UNIT F35 | | | | | | | | | Base Unit CPU E | | | | | | | | RS485 and RS485
SOFTWARE 00 | | | | | | | No Software Options
MOUNT/COATING V | | | | | | Vertical (3/4 rack)
FACEPLATE/ DISPLAY F | | | | | English display
F35 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
J | | | | | | | | RS485, multi-mode ST 100Base-FX, and 10/100Base-T K | | | | | | | | RS485, mult i-mode ST redundant 100Base-FX, and 10/100Base-T N | | | | | | | | RS485 and 10/100Base-T
01 | | | | | | | Ethernet Global Data (EGD); not available for Type E CPUs 03 | | | | | | | IEC 61850; not available for Type E CPUs 04 | | | | | | | Ethernet Global Data (EGD) and IEC 61850; not available for Type E CPUs
B | | | | | | Vertical (3/4 rack) with harsh environmental coating
D | | | | | French display R | | | | | Russian display A | | | | | Chinese display K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display
GE Multilin F35 Multiple Feeder Protection System 2-5
2.1 INTRODUCTION 2 PRODUCT DESCRIPTION
NOTE
Table 2–6: F35 ORDER CODES (REDUCED SIZE VERTICAL UNITS WITH PROCESS BUS)
L | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons
POWER SUPPLY H | | | | 125 / 250 V AC/DC power supply
CT/VT MODULES | 81 | | Eight-port digital process bus module DIGITAL INPUTS/OUTPUTS XX XX XX No Module
2
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital and transducer input/output modules; slot R is used for inter-relay communications modules.
V | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons
L | | | | 24 to 48 V (DC only) power supply
4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 16 digital inputs with Auto-Burnishing 4L 14 Form-A (no monitoring) Latching out puts 67 8 Form-A (no monitoring) outputs 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs 6C 8 Form-C outputs 6D 16 digital inputs 6E 4 Form-C outputs, 8 digital inputs 6F 8 Fast Form-C outputs 6G 4 Form-A (voltage wit h optional current) outputs, 8 digital inputs 6H 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 4 Form-C and 4 Fast Form-C outputs 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6 Form-A (current with optional voltage) outputs, 4 digital inputs 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs 6T 4 Form-A (no monitoring) outputs, 8 digital inputs 6U 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 dig ital inputs 2A C37.94SM, 1300nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels 72 1550 nm, single-mode, LASER, 1 Channel 73 1550 nm, single-mode, LASER, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 n m, single-mode, LASER 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode LASER 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multi-mode, LED, 1 Channel 7B 1300 nm, multi-mode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, LASER, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multi-mode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multi-mode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multi-mode, LED, 2 Channels
7I 1300 nm, multi-mode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, LASER, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multi- mode, LED 7M Channel 1 - RS422; Channel 2 - 1300 n m, multi-mode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, LASER 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode LASER 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels

2.1.3 REPLACEMENT MODULES

Replacement modules can be ordered separately as shown below. When ordering a replacement CPU module or face­plate, please provide the serial number of your existing unit.
Not all replacement modules may be applicable to the F35 relay. Only the modules specified in the order codes are available as replacement modules.
Replacement module codes are subject to change without notice. See the web page for the product for the latest ordering options.
2-6 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION
The replacement module order codes for the horizontal mount units are shown below.
Table 2–7: ORDER CODES FOR REPLACEMENT MODULES, HORIZONTAL UNITS
POWER SUPPLY redundant supply only available in horizontal units and must be same type as main supply, for example must swap both power supplies when switching from RH to SH CPU | 9E | RS485 and RS485 (Modbu s RTU, DNP 3.0)
FACEPLATE/DISPLAY | 3C | Horizontal faceplate with keypad and English display
DIGITAL INPUTS AND OUTPUTS | 4A | 4 Solid-State (no monitoring) MOSFET outputs
CT/VT MODULES (NOT AVAILABLE FOR THE C30)
INTER-RELAY COMMUNICATIONS | 2A | C37.94SM, 1300nm single-mode, ELED, 1 channel single-mode
TRANSDUCER INPUTS/OUTPUTS
UR - ** - *
| SH A 125 / 300 V AC/DC
| SL H 24 to 48 V (DC only)
| 9J | RS485, multi-mode S T 100Base-FX (Ethernet, Modbus TCP/IP, DNP 3.0), and 10/100Base-T | 9K | RS485, multi-mode ST redundant 100Base-FX (Ethernet, Modbus TCP/IP, DNP 3.0), and 10/100Base-T | 9N | RS485 and 10/100Base-T | 9S | RS485 and six-port managed Ethernet switch (four 100Base-FX and two 100Base-T)
| 3D | Horizontal faceplate with keypad and French display | 3R | Horizontal faceplate with keypad and Russian display | 3A | Horizontal faceplate with keypad and Chinese display | 3P | Horizontal faceplate with keypad, user-p rogrammable pushbuttons, and English display | 3G | Horizontal faceplate with keypad, user-programmable pushbuttons, and French display | 3S | Horizontal faceplate with keypad, user-programmable pushbuttons, and Russian display | 3B | Horizontal faceplate with keypad, user-p rogrammable pushbuttons, and Chinese display | 3K | Enhanced front panel with English display | 3M | Enhanced front panel with French display | 3Q | Enhanced front panel with Russian display | 3U | Enhanced front panel with Chinese display | 3L | Enhanced front panel with English display and user-programmable pushbuttons | 3N | Enhanced front panel with French display and user-programmable pushbuttons | 3T | Enhanced front panel with Russian display and user-programmable pushbuttons | 3V | Enhanced front panel wit h Chinese display and user-programmable pushbuttons
| 4B | 4 Solid-State (voltage with optional current) MOSFET outputs | 4C | 4 Solid-State (current with optional voltage) MOSFET outputs | 4D | 16 digital inputs with Auto-Burnishi ng | 4L | 14 Form-A (no monitoring) Latching outputs | 67 | 8 Form-A (no monitoring) outputs | 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs | 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs | 6C | 8 Form-C outputs | 6D | 16 digital inputs | 6E | 4 Form-C outputs, 8 digital inputs | 6F | 8 Fast Form-C outputs | 6G | 4 Form-A (voltage with optional current) outputs, 8 digital inputs | 6H | 6 Form-A (voltage with opt ional current) outputs, 4 digital inputs | 6K | 4 Form-C and 4 Fast Form-C outputs | 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digi tal inputs | 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs | 6N | 4 Form-A (curr ent with optional voltage) outputs, 8 digital inputs | 6P | 6 Form-A (current with optional voltage) outputs, 4 digital inputs | 6R | 2 Form-A (no moni toring) and 2 Form-C outputs, 8 digital inputs | 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs | 6T | 4 Form-A (no monitoring) outputs, 8 digital inputs | 6U | 6 Form-A (no moni toring) outputs, 4 digital inputs | 6V | 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs
| 8F | Standard 4CT/4VT
| 8G | Sensitive Ground 4CT/4VT | 8H | Standard 8CT | 8J | Sensitive Ground 8CT | 8L | Standard 4CT/4VT with enhanced diagnostics | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics | 8N | Standard 8CT with enhanced diagnostics | 8R | Sensitive Ground 8CT with enhanced diagnostics
| 2B | C37.94SM, 1300nm single-mode, ELED, 2 channel single-mode | 2E | Bi-phase, single channel | 2F | Bi-phase, dual channel | 2G | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel | 2H | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels | 2S | Six-port managed Ethernet switch with high voltage power supply (110 to 250 V DC / 100 to 240 V AC) | 2T | Six-port managed Ethernet switch with low voltage power supply (48 V DC) | 72 | 1550 nm, single-mode, LASER, 1 Channel | 73 | 1550 nm, single-mode, LASER, 2 Channel | 74 | Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, LASER | 75 | Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode LASER | 76 | IEEE C37.94, 820 nm, multimode, LED, 1 Channel | 77 | IEEE C37.94, 820 nm, multimode, LED, 2 Channels | 7A | 820 nm, multi-mode, LED, 1 Channel | 7B | 1300 nm, multi-mode, LED, 1 Channel | 7C | 1300 nm, single-mode, EL ED, 1 Channel | 7D | 1300 nm, single-mode, LA SER, 1 Channel | 7E | Channel 1 - G.703; Channel 2 - 820 nm, multi-mode | 7F | Channel 1 - G.703; Channel 2 - 1300 nm, multi-mode | 7G | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED | 7H | 820 nm, multi-mode, LED, 2 Channels | 7I | 1300 nm, multi-mode, LED, 2 Channels | 7J | 1300 nm, single- mode, ELED, 2 Channels | 7K | 1300 nm, single-mode, LASER, 2 Channels | 7L | Channel 1 - RS422; Channel 2 - 820 nm, multi-mode, LED | 7M | Channel 1 - RS422; Channel 2 - 1300 nm, multi-mode, LED | 7N | Channel 1 - RS422; Chann el 2 - 1300 nm, single-mode, ELED | 7P | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, LASER | 7Q | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode LASER | 7R | G.703, 1 Channel | 7S | G.703, 2 Channels | 7T | RS422, 1 Channel | 7W | RS422, 2 Channels | 5A | 4 dcmA inputs, 4 dcmA outputs (only one 5A or 5D module is allowed) | 5C | 8 RTD inputs | 5D | 4 RTD inputs, 4 dcmA outputs (only one 5A or 5D module is allowed) | 5E | 4 dcmA inputs, 4 RTD inputs | 5F | 8 dcmA inputs
2
GE Multilin F35 Multiple Feeder Protection System 2-7
2.1 INTRODUCTION 2 PRODUCT DESCRIPTION
The replacement module order codes for the reduced-size vertical mount units are shown below.
Table 2–8: ORDER CODES FOR REPLACEMENT MODULES, VERTICAL UNITS
POWER SUPPLY | SH B 125 / 300 V AC/DC
CPU | 9E | RS485 and RS485 (Modbu s RTU, DNP 3.0)
FACEPLATE/DISPLAY | 3F | Vertical faceplate with keypad and English display
2
DIGITAL INPUTS/OUTPUTS
CT/VT MODULES (NOT AVAILABLE FOR THE C30)
INTER-RELAY COMMUNICATIONS | 2A | C37.94SM, 1300nm single-mode, ELED, 1 channel single-mode
TRANSDUCER INPUTS/OUTPUTS
UR - ** - *
| SL | 24 to 48 V (DC only)
| 9J | RS485, multi-mode S T 100Base-FX (Ethernet, Modbus TCP/IP, DNP 3.0), and 10/100Base-T | 9K | RS485, multi-mode ST redundant 100Base-FX (Ethernet, Modbus TCP/IP, DNP 3.0), and 10/100Base-T | 9N | RS485 and 10/100Base-T
| 3D | Vertical faceplate with keypad and French display | 3R | Vertical faceplate with keypad and Russian display | 3K | Vertical faceplate with keypad and Chinese display | 3K | Enhanced front panel with English display | 3M | Enhanced front panel with French display | 3Q | Enhanced front panel with Russian display | 3U | Enhanced front panel with Chinese display | 3L | Enhanced front panel with English display and user-programmable pushbuttons | 3N | Enhanced front panel with French display and user-programmable pushbuttons | 3T | Enhanced front panel with Russian display and user-programmable pushbuttons | 3V | Enhanced front panel wit h Chinese display and user-programmable pushbuttons | 4A | 4 Solid-State (no monitoring) MOSFET outputs | 4B | 4 Solid-State (voltage with optional current) MOSFET outputs | 4C | 4 Solid-State (current with optional voltage) MOSFET outputs | 4D | 16 digital inputs with Auto-Burnishi ng | 4L | 14 Form-A (no monitoring) Latching outputs | 67 | 8 Form-A (no monitoring) outputs | 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs | 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs | 6C | 8 Form-C outputs | 6D | 16 digital inputs | 6E | 4 Form-C outputs, 8 digital inputs | 6F | 8 Fast Form-C outputs | 6G | 4 Form-A (voltage with optional current) outputs, 8 digital inputs | 6H | 6 Form-A (voltage with opt ional current) outputs, 4 digital inputs | 6K | 4 Form-C and 4 Fast Form-C outputs | 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digi tal inputs | 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs | 6N | 4 Form-A (curr ent with optional voltage) outputs, 8 digital inputs | 6P | 6 Form-A (current with optional voltage) outputs, 4 digital inputs | 6R | 2 Form-A (no moni toring) and 2 Form-C outputs, 8 digital inputs | 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs | 6T | 4 Form-A (no monitoring) outputs, 8 digital inputs | 6U | 6 Form-A (no moni toring) outputs, 4 digital inputs | 6V | 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs
| 8F | Standard 4CT/4VT
| 8G | Sensitive Ground 4CT/4VT | 8H | Standard 8CT | 8J | Sensitive Ground 8CT | 8L | Standard 4CT/4VT with enhanced diagnostics | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics | 8N | Standard 8CT with enhanced diagnostics | 8R | Sensitive Ground 8CT with enhanced diagnostics
| 2B | C37.94SM, 1300nm single-mode, ELED, 2 channel single-mode | 2E | Bi-phase, single channel | 2F | Bi-phase, dual channel | 2G | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel | 2H | IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels | 72 | 1550 nm, single-mode, LASER, 1 Channel | 73 | 1550 nm, single-mode, LASER, 2 Channel | 74 | Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, LASER | 75 | Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode LASER | 76 | IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel | 77 | IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels | 7A | 820 nm, multi-mode, LED, 1 Channel | 7B | 1300 nm, multi-mode, LED, 1 Channel | 7C | 1300 nm, single-mode, EL ED, 1 Channel | 7D | 1300 nm, single-mode, LA SER, 1 Channel | 7E | Channel 1 - G.703; Channel 2 - 820 nm, multi-mode | 7F | Channel 1 - G.703; Channel 2 - 1300 nm, multi-mode | 7G | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED | 7H | 820 nm, multi-mode, LED, 2 Channels | 7I | 1300 nm, multi-mode, LED, 2 Channels | 7J | 1300 nm, single- mode, ELED, 2 Channels | 7K | 1300 nm, single-mode, LASER, 2 Channels | 7L | Channel 1 - RS422; Channel 2 - 820 nm, multi-mode, LED | 7M | Channel 1 - RS422; Channel 2 - 1300 nm, multi-mode, LED | 7N | Channel 1 - RS422; Chann el 2 - 1300 nm, single-mode, ELED | 7P | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, LASER | 7Q | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode LASER | 7R | G.703, 1 Channel | 7S | G.703, 2 Channels | 7T | RS422, 1 Channel | 7W | RS422, 2 Channels | 5A | 4 dcmA inputs, 4 dcmA outputs (only one 5A or 5D module is allowed) | 5C | 8 RTD inputs | 5D | 4 RTD inputs, 4 dcmA outputs (only one 5A or 5D module is allowed) | 5E | 4 dcmA inputs, 4 RTD inputs | 5F | 8 dcmA inputs
2-8 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.2 SPECIFICATIONS
NOTE
2.2SPECIFICATIONSSPECIFICATIONS ARE SUBJECT TO CHANGE WITHOUT NOTICE

2.2.1 PROTECTION ELEMENTS

The operating times below include the activation time of a trip rated form-A output contact unless otherwise indi­cated. FlexLogic™ operands of a given element are 4 ms faster. This should be taken into account when using FlexLogic™ to interconnect with other protection or control elements of the relay, building FlexLogic™ equations, or interfacing with other IEDs or power system devices via communications or different output contacts.
PHASE/NEUTRAL/GROUND TOC
Current: Phasor or RMS
Pickup level: 0.000 to 30.000 pu in steps of 0.001
Dropout level: 97% to 98% of pickup
Level accuracy:
for 0.1 to 2.0 × CT: ±0.5% of reading or ±0.4% of rated
for > 2.0 × CT: ±1.5% of reading > 2.0 × CT rating
Curve shapes: IEEE Moderately/Very/Extremely
Curve multiplier: Time Dial = 0.00 to 600.00 in steps of
Reset type: Instantaneous/Timed (per IEEE) Timing accuracy: Operate at > 1.03 × actual pickup
(whichever is greater)
Inverse; IEC (and BS) A/B/C and Short Inverse; GE IAC Inverse, Short/Very/ Extremely Inverse; I (programmable); Definite Time (0.01 s base curve)
0.01
±3.5% of operate time or ±½ cycle (whichever is greater)
2
t; FlexCurves™
PHASE/NEUTRAL/GROUND IOC
Pickup level: 0.000 to 30.000 pu in steps of 0.001
Dropout level: 97 to 98% of pickup
Level accuracy:
0.1 to 2.0 × CT rating: ±0.5% of reading or ±0.4% of rated
(whichever is greater)
> 2.0 × CT rating ±1.5% of reading
Overreach: <2%
Pickup delay: 0.00 to 600.00 s in steps of 0.01
Reset delay: 0.00 to 600.00 s in steps of 0.01 Operate time: <16 ms at 3 × pickup at 60 Hz
(Phase/Ground IOC) <20 ms at 3 × pickup at 60 Hz (Neutral IOC)
Timing accuracy: Operate at 1.5 × pickup
±3% or ±4 ms (whichever is greater)
NEGATIVE SEQUENCE TOC
Pickup level: 0.000 to 30.000 pu in steps of 0.001
Dropout level: 97% to 98% of pickup
Level accuracy: ±0.5% of reading or ±0.4% of rated
Curve shapes: IEEE Moderately/Very/Extremely
Curve multiplier (Time dial): 0.00 to 600.00 in steps of 0.01
Reset type: Instantaneous/Timed (per IEEE) and Lin-
Timing accuracy: Operate at > 1.03 × actual pickup
(whichever is greater) from 0.1 to 2.0 x CT rating ±1.5% of reading > 2.0 x CT rating
Inverse; IEC (and BS) A/B/C and Short Inverse; GE IAC Inverse, Short/Very/ Extremely Inverse; I (programmable); Definite Time (0.01 s base curve)
ear
±3.5% of operate time or ±½ cycle (whichever is greater)
2
t; FlexCurves™
NEGATIVE SEQUENCE IOC
Pickup level: 0.000 to 30.000 pu in steps of 0.001
Dropout level: 97 to 98% of pickup Level accuracy: 0.1 to 2.0 × CT rating: ±0.5% of reading
Overreach: < 2%
Pickup delay: 0.00 to 600.00 s in steps of 0.01
Reset delay: 0.00 to 600.00 s in steps of 0.01 Operate time: < 20 ms at 3 × pickup at 60 Hz Timing accuracy: Operate at 1.5 × pickup
or ±0.4% of rated (whichever is greater); > 2.0 × CT rating: ±1.5% of reading
±3% or ±4 ms (whichever is greater)
PHASE UNDERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001
Dropout level: 102 to 103% of pickup
Level accuracy: ±0.5% of reading from 10 to 208 V
Curve shapes: GE IAV Inverse;
Definite Time (0.1s base curve)
Curve multiplier: Time dial = 0.00 to 600.00 in steps of
Timing accuracy: Operate at < 0.90 × pickup
Operate time: <30 ms at 0.9 pickup at 60 Hz for Defi-
0.01
±3.5% of operate time or ±4 ms (which­ever is greater)
nite Time mode
2
GE Multilin F35 Multiple Feeder Protection System 2-9
2.2 SPECIFICATIONS 2 PRODUCT DESCRIPTION
AUXILIARY UNDERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001
Dropout level: 102 to 103% of pickup
Level accuracy: ±0.5% of reading from 10 to 208 V
Curve shapes: GE IAV Inverse, Definite Time
Curve multiplier: Time Dial = 0 to 600.00 in steps of 0.01
Timing accuracy: ±3% of operate time or ±4 ms
2
Operate time: <30 ms at 0.9 pickup at 60 Hz for Defi-
(whichever is greater)
nite Time mode
NEUTRAL OVERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001
Dropout level: 97 to 98% of pickup
Level accuracy: ±0.5% of reading from 10 to 208 V
Pickup delay: 0.00 to 600.00 s in steps of 0.01 (definite
Reset delay: 0.00 to 600.00 s in steps of 0.01
Timing accuracy: ±3% or ±20 ms (whichever is greater) Operate time: < 30 ms at 1.10 × pickup at 60 Hz
time) or user-defined curve
AUXILIARY OVERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001
Dropout level: 97 to 98% of pickup
Level accuracy: ±0.5% of reading from 10 to 208 V
Pickup delay: 0 to 600.00 s in steps of 0.01
Reset delay: 0 to 600.00 s in steps of 0.01
Timing accuracy: ±3% of operate time or ±4 ms
(whichever is greater)
Operate time: < 30 ms at 1.10 × pickup at 60 Hz
UNDERFREQUENCY
Minimum signal: 0.10 to 1.25 pu in steps of 0.01
Pickup level: 20.00 to 65.00 Hz in steps of 0.01
Dropout level: pickup + 0.03 Hz
Level accuracy: ±0.001 Hz
Time delay: 0 to 65.535 s in steps of 0.001
Timer accuracy: ±3% or 4 ms, whichever is greater
Operate time: typically 4 cycles at 0.1 Hz/s change
typically 3.5 cycles at 0.3 Hz/s change typically 3 cycles at 0.5 Hz/s change
Typical times are average operate times including variables such as frequency change instance, test method, etc., and may vary by ±0.5 cycles.
BREAKER ARCING CURRENT
Principle: accumulates breaker duty (I2t) and mea-
sures fault duration
Initiation: programmable per phase from any Flex-
Logic™ operand
Compensation for auxiliary relays: 0 to 65.535 s in steps of 0.001
Alarm threshold: 0 to 50000 kA2-cycle in steps of 1
Fault duration accuracy: 0.25 of a power cycle
Availability: 1 per CT bank with a minimum of 2
INCIPIENT CABLE FAULT DETECTION
Principle: detection of ½ cycle or less overcurrent
condition during normal load
Availability: two per CT/VT module (not including 8Z
modules)
Pickup level: 0.1 to 10.00 pu in steps of 0.01
Reset delay: 0.000 to 65.535 s in steps of 0.001
Operating mode: number of counts, counts per time win-
dow
AUTORECLOSURE
Single breaker applications, 3-pole tripping schemes
Up to 4 reclose attempts before lockout
Independent dead time setting before each shot
Possibility of changing protection settings after each shot with
FlexLogic™
TRIP BUS (TRIP WITHOUT FLEXLOGIC™)
Number of elements: 6
Number of inputs: 16
Operate time: <2 ms at 60 Hz
Time accuracy: ±3% or 10 ms, whichever is greater

2.2.2 USER-PROGRAMMABLE ELEMENTS

FLEXLOGIC™
Programming language: Reverse Polish Notation with graphical
visualization (keypad programmable)
Lines of code: 512
Internal variables: 64
Supported operations: NOT, XOR, OR (2 to 16 inputs), AND (2
to 16 inputs), NOR (2 to 16 inputs), NAND (2 to 16 inputs), latch (reset-domi­nant), edge detectors, timers
Inputs: any logical variable, contact, or virtual
input
Number of timers: 32
Pickup delay: 0 to 60000 (ms, sec., min.) in steps of 1
Dropout delay: 0 to 60000 (ms, sec., min.) in steps of 1
FLEXCURVES™
Number: 4 (A through D)
Reset points: 40 (0 through 1 of pickup)
Operate points: 80 (1 through 20 of pickup)
Time delay: 0 to 65535 ms in steps of 1
2-10 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.2 SPECIFICATIONS
FLEX STATES
Number: up to 256 logical variables grouped
under 16 Modbus addresses
Programmability: any logical variable, contact, or virtual
input
FLEXELEMENTS™
Number of elements: 16
Operating signal: any analog actual value, or two values in
differential mode
Operating signal mode: signed or absolute value
Operating mode: level, delta
Comparator direction: over, under
Pickup Level: –90.000 to 90.000 pu in steps of 0.001
Hysteresis: 0.1 to 50.0% in steps of 0.1
Delta dt: 20 ms to 60 days
Pickup & dropout delay: 0.000 to 65.535 s in steps of 0.001
NON-VOLATILE LATCHES
Type: set-dominant or reset-dominant
Number: 16 (individually programmed)
Output: stored in non-volatile memory
Execution sequence: as input prior to protection, control, and
FlexLogic™
USER-PROGRAMMABLE LEDs
Number: 48 plus trip and alarm
Programmability: from any logical variable, contact, or vir-
tual input
Reset mode: self-reset or latched
LED TEST
Initiation: from any digital input or user-program-
mable condition
Number of tests: 3, interruptible at any time
Duration of full test: approximately 3 minutes
Test sequence 1: all LEDs on
Test sequence 2: all LEDs off, one LED at a time on for 1 s
Test sequence 3: all LEDs on, one LED at a time off for 1 s
USER-DEFINABLE DISPLAYS
Number of displays: 16 Lines of display: 2 × 20 alphanumeric characters
Parameters: up to 5, any Modbus register addresses
Invoking and scrolling: keypad, or any user-programmable con-
dition, including pushbuttons
CONTROL PUSHBUTTONS
Number of pushbuttons: 7
Operation: drive FlexLogic™ operands
USER-PROGRAMMABLE PUSHBUTTONS (OPTIONAL)
Number of pushbuttons: 12 on standard front panel
16 on enhanced horizontal front panel 6 on enhanced vertical front panel
Mode: self-reset, latched
Display message: 2 lines of 20 characters each
Drop-out timer: 0.00 to 60.00 s in steps of 0.05
Autoreset timer: 0.2 to 600.0 s in steps of 0.1
Hold timer: 0.0 to 10.0 s in steps of 0.1
SELECTOR SWITCH
Number of elements: 2
Upper position limit: 1 to 7 in steps of 1
Selecting mode: time-out or acknowledge
Time-out timer: 3.0 to 60.0 s in steps of 0.1
Control inputs: step-up and 3-bit
Power-up mode: restore from non-volatile memory or syn-
chronize to a 3-bit control input or synch/ restore mode
8-BIT SWITCH
Number of elements: 6
Input signals: two 8-bit integers via FlexLogic™ oper-
ands
Control signal: any FlexLogic™ operand
Response time: < 8 ms at 60 Hz, < 10 ms at 50 Hz
DIGITAL ELEMENTS
Number of elements: 48
Operating signal: any FlexLogic™ operand
Pickup delay: 0.000 to 999999.999 s in steps of 0.001
Dropout delay: 0.000 to 999999.999 s in steps of 0.001
Timing accuracy: ±3% or ±4 ms, whichever is greater
2

2.2.3 MONITORING

OSCILLOGRAPHY
Maximum records: 64
Sampling rate: 64 samples per power cycle
Triggers: any element pickup, dropout, or operate;
digital input change of state; digital out­put change of state; FlexLogic™ equa­tion
Data: AC input channels; element state; digital
input state; digital output state
Data storage: in non-volatile memory
EVENT RECORDER
Capacity: 1024 events
Time-tag: to 1 microsecond
Triggers: any element pickup, dropout, or operate;
digital input change of state; digital out­put change of state; self-test events
Data storage: in non-volatile memory
GE Multilin F35 Multiple Feeder Protection System 2-11
2.2 SPECIFICATIONS 2 PRODUCT DESCRIPTION
DATA LOGGER
Number of channels: 1 to 16
Parameters: any available analog actual value
Sampling rate: 15 to 3600000 ms in steps of 1
Trigger: any FlexLogic™ operand
Mode: continuous or triggered
Storage capacity: (NN is dependent on memory)
2
1-second rate:
01 channel for NN days
16 channels for NN days
60-minute rate:
01 channel for NN days 16 channels for NN days
RMS CURRENT: PHASE, NEUTRAL, AND GROUND
Accuracy at
0.1 to 2.0 × CT rating: ±0.25% of reading or ±0.1% of rated
> 2.0 × CT rating: ±1.0% of reading
(whichever is greater)
RMS VOLTAGE
Accuracy: ±0.5% of reading from 10 to 208 V
REAL POWER (WATTS)
Accuracy: ±1.0% of reading at
–0.8 < PF –1.0 and 0.8 < PF ≤ 1.0
REACTIVE POWER (VARS)
Accuracy: ±1.0% of reading at –0.2 PF 0.2
APPARENT POWER (VA)
Accuracy: ±1.0% of reading
WATT-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading Range: ±0 to 1 × 10
Parameters: three-phase only
Update rate: 50 ms
6
MWh
VAR-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading Range: ±0 to 1 × 10
Parameters: three-phase only
Update rate: 50 ms
6
Mvarh
FAULT LOCATOR
Number of independent fault locators: 1 per CT bank (to a maxi-
mum of 5)
Method: single-ended
Voltage source: wye-connected VTs, delta-connected
Maximum accuracy if: fault resistance is zero or fault currents
Relay accuracy: ±1.5% (V > 10 V, I > 0.1 pu)
Worst-case accuracy:
+ user data
VT
%error
+ user data
CT
%error
Z
Line%error
METHOD
RELAY ACCURACY
+ user data
+ see chapter 8
%error
VTs and neutral voltage, delta-connected VTs and zero-sequence current (approxi­mation)
from all line terminals are in phase
+ (1.5%)
%error

2.2.4 METERING

VOLTAGE HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, dis-
played as a % of f quency phasor) THD: per phase, displayed as a % of f
Accuracy:
HARMONICS: 1. f
THD: 1. f1 > 0.4pu: (0.25% + 0.035% / harmonic) of
> 0.4pu: (0.20% + 0.035% / harmonic) of
1
reading or 0.15% of 100%, whichever is greater
2. f
< 0.4pu: as above plus %error of f
1
reading or 0.20% of 100%, whichever is greater
2. f
< 0.4pu: as above plus %error of f
1
(fundamental fre-
1
1
1
FREQUENCY
Accuracy at
V = 0.8 to 1.2 pu: ±0.001 Hz (when voltage signal is used
I = 0.1 to 0.25 pu: ±0.005 Hz I > 0.25 pu: ±0.001 Hz (when current signal is used
for frequency measurement)
for frequency measurement)
DEMAND
Measurements: Phases A, B, and C present and maxi-
Accuracy: ±2.0%
mum measured currents 3-Phase Power (P, Q, and S) present and maximum measured currents
1
2-12 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.2 SPECIFICATIONS

2.2.5 INPUTS

AC CURRENT
CT rated primary: 1 to 50000 A
CT rated secondary: 1 A or 5 A by connection
Nominal frequency: 20 to 65 Hz
Relay burden: < 0.2 VA at rated secondary
Conversion range:
Standard CT: 0.02 to 46 × CT rating RMS symmetrical Sensitive Ground CT module:
0.002 to 4.6 × CT rating RMS symmetrical
Current withstand: 20 ms at 250 times rated
1 sec. at 100 times rated continuous at 3 times rated
Short circuit rating: 150000 RMS symmetrical amperes, 250
V maximum (primary current to external CT)
AC VOLTAGE
VT rated secondary: 50.0 to 240.0 V
VT ratio: 1.00 to 24000.00
Nominal frequency: 20 to 65 Hz
Relay burden: < 0.25 VA at 120 V
Conversion range: 1 to 275 V
Voltage withstand: continuous at 260 V to neutral
1 min./hr at 420 V to neutral
CONTACT INPUTS
Dry contacts: 1000 Ω maximum
Wet contacts: 300 V DC maximum
Selectable thresholds: 17 V, 33 V, 84 V, 166 V
Tolerance: ±10%
Contacts per common return: 4
Recognition time: < 1 ms
Debounce time: 0.0 to 16.0 ms in steps of 0.5
Continuous current draw:3 mA (when energized)
CONTACT INPUTS WITH AUTO-BURNISHING
Dry contacts: 1000 Ω maximum
Wet contacts: 300 V DC maximum
Selectable thresholds: 17 V, 33 V, 84 V, 166 V
Tolerance: ±10%
Contacts per common return: 2
Recognition time: < 1 ms
Debounce time: 0.0 to 16.0 ms in steps of 0.5
Continuous current draw:3 mA (when energized)
Auto-burnish impulse current: 50 to 70 mA
Duration of auto-burnish impulse: 25 to 50 ms
DCMA INPUTS
Current input (mA DC): 0 to –1, 0 to +1, –1 to +1, 0 to 5, 0 to 10,
0 to 20, 4 to 20 (programmable)
Input impedance: 379 Ω ±10%
Conversion range: –1 to + 20 mA DC
Accuracy: ±0.2% of full scale
Type: Passive
RTD INPUTS
Types (3-wire): 100 Ω Platinum, 100 & 120 Ω Nickel, 10
Ω Copper
Sensing current: 5 mA
Range: –50 to +250°C
Accuracy: ±2°C
Isolation: 36 V pk-pk
IRIG-B INPUT
Amplitude modulation: 1 to 10 V pk-pk
DC shift: TTL Input impedance: 22 kΩ
Isolation: 2 kV
REMOTE INPUTS (IEC 61850 GSSE/GOOSE)
Number of input points: 32, configured from 64 incoming bit pairs
Number of remote devices: 16
Default states on loss of comms.: On, Off, Latest/Off, Latest/On
Number of remote DPS inputs: 5
DIRECT INPUTS
Number of input points: 32
No. of remote devices: 16
Default states on loss of comms.: On, Off, Latest/Off, Latest/On
Ring configuration: Yes, No
Data rate: 64 or 128 kbps
CRC: 32-bit
CRC alarm:
Responding to: Rate of messages failing the CRC Monitoring message count: 10 to 10000 in steps of 1 Alarm threshold: 1 to 1000 in steps of 1
Unreturned message alarm:
Responding to: Rate of unreturned messages in the ring
configuration Monitoring message count: 10 to 10000 in steps of 1 Alarm threshold: 1 to 1000 in steps of 1
TELEPROTECTION
Number of input points: 16
No. of remote devices: 3
Default states on loss of comms.: On, Off, Latest/Off, Latest/On
Ring configuration: No
Data rate: 64 or 128 kbps
CRC: 32-bit
2
GE Multilin F35 Multiple Feeder Protection System 2-13
2.2 SPECIFICATIONS 2 PRODUCT DESCRIPTION

2.2.6 POWER SUPPLY

LOW RANGE
Nominal DC voltage: 24 to 48 V
Minimum DC voltage: 20 V
Maximum DC voltage: 60 V for RL power supply module (obso-
lete), 75 V for SL power supply module
Voltage loss hold-up: 20 ms duration at nominal
2
NOTE: Low range is DC only.
HIGH RANGE
Nominal DC voltage: 125 to 250 V
Minimum DC voltage: 88 V
Maximum DC voltage: 300 V
Nominal AC voltage: 100 to 240 V at 50/60 Hz
Minimum AC voltage: 88 V at 25 to 100 Hz
Maximum AC voltage: 265 V at 25 to 100 Hz
Voltage loss hold-up: 200 ms duration at nominal
FORM-A RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90
Carry continuous: 6 A
Break (DC inductive, L/R = 40 ms):
VOLTAGE CURRENT
24 V 1 A
48 V 0.5 A
125 V 0.3 A
250 V 0.2 A
Operate time: < 4 ms
Contact material: silver alloy
LATCHING RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90
Carry continuous: 6 A
Break at L/R of 40 ms: 0.25 A DC max.
Operate time: < 4 ms
Contact material: silver alloy
Control: separate operate and reset inputs
Control mode: operate-dominant or reset-dominant
FORM-A VOLTAGE MONITOR
Applicable voltage: approx. 15 to 250 V DC
Trickle current: approx. 1 to 2.5 mA
FORM-A CURRENT MONITOR
Threshold current: approx. 80 to 100 mA
ALL RANGES
Volt withstand: 2 × Highest Nominal Voltage for 10 ms
Power consumption: typical = 15 to 20 W/VA
maximum = 50 W/VA contact factory for exact order code con­sumption
INTERNAL FUSE
RATINGS
Low range power supply: 8 A / 250 V High range power supply: 4 A / 250 V
INTERRUPTING CAPACITY
AC: 100 000 A RMS symmetrical DC: 10 000 A

2.2.7 OUTPUTS

FORM-C AND CRITICAL FAILURE RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90
Carry continuous: 8 A
Break (DC inductive, L/R = 40 ms):
VOLTAGE CURRENT
24 V 1 A
48 V 0.5 A
125 V 0.3 A
250 V 0.2 A
Operate time: < 8 ms
Contact material: silver alloy
FAST FORM-C RELAY
Make and carry: 0.1 A max. (resistive load)
Minimum load impedance:
INPUT
VOLTAGE
250 V DC 20 KΩ 50 KΩ 120 V DC 5 KΩ 2 KΩ
48 V DC 2 KΩ 2 KΩ 24 V DC 2 KΩ 2 KΩ
Note: values for 24 V and 48 V are the same due to a required 95% voltage drop across the load impedance.
Operate time: < 0.6 ms Internal Limiting Resistor: 100 Ω, 2 W
2 W RESISTOR 1 W RESISTOR
IMPEDANCE
2-14 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.2 SPECIFICATIONS
SOLID-STATE OUTPUT RELAY
Operate and release time: <100 µs
Maximum voltage: 265 V DC
Maximum leakage current in off state
(excluding voltage monitor circuit current): 100 µA
Maximum continuous current: 5 A at 45°C; 4 A at 65°C
Make and carry:
for 0.2 s: 30 A as per ANSI C37.90 for 0.03 s 300 A
Breaking capacity:
Operations/ interval
Break capability (0 to 250 V DC)
UL508 Utility
5000 ops /
1s-On, 9s-Off
1000 ops /
0.5 s-On, 0.5 s-Off
3.2 A
L/R = 10 ms
1.6 A
L/R = 20 ms
0.8 A
L/R = 40 ms
application
(autoreclose
scheme)
5ops/
0.2 s-On,
0.2 s-Off within 1
minute
10 A
L/R = 40 ms
application
10000 ops /
L/R = 40 ms
IRIG-B OUTPUT
Amplitude: 10 V peak-peak RS485 level
Maximum load: 100 ohms
Time delay: 1 ms for AM input
40 μs for DC-shift input
Isolation: 2 kV
CONTROL POWER EXTERNAL OUTPUT (FOR DRY CONTACT INPUT)
Capacity: 100 mA DC at 48 V DC
Isolation: ±300 Vpk
REMOTE OUTPUTS (IEC 61850 GSSE/GOOSE)
Standard output points: 32
User output points: 32
Industrial
0.2 s-On, 30 s-Off
10 A
DIRECT OUTPUTS
Output points: 32
DCMA OUTPUTS
Range: –1 to 1 mA, 0 to 1 mA, 4 to 20 mA Max. load resistance: 12 kΩ for –1 to 1 mA range
12 kΩ for 0 to 1 mA range 600 Ω for 4 to 20 mA range
Accuracy: ±0.75% of full-scale for 0 to 1 mA range
±0.5% of full-scale for –1 to 1 mA range ±0.75% of full-scale for 0 to 20 mA range
99% Settling time to a step change: 100 ms
Isolation: 1.5 kV
Driving signal: any FlexAnalog quantity
Upper and lower limit for the driving signal: –90 to 90 pu in steps of
0.001
ETHERNET SWITCH (HIGH VOLTAGE, TYPE 2S)
Nominal DC voltage: 110 to 240 V DC
Minimum DC voltage: 88 V DC
Maximum DC voltage: 300 V DC
Input Current: 0.9 A DC maximum
Nominal AC voltage: 100 to 240 V AC, 0.26 to 0.16 A/26 to 39
VA at 50/60 Hz
Minimum AC voltage: 85 V AC, 0.31 A/22 VA at 50/60 Hz
Maximum AC voltage: 265 V AC, 0.16 A/42 VA at 50/60 Hz
Internal fuse: 3 A / 350 V AC, Ceramic, Axial SLO
BLO; Manufacturer: Conquer; Part number: SCD-A 003
ETHERNET SWITCH (LOW VOLTAGE, TYPE 2T)
Nominal voltage: 48 V DC, 0.31 A/15 W
Minimum voltage: 30 V DC, 0.43 A/16 W
Maximum voltage: 60 V DC
Internal fuse: 5 A / 350 V AC, Ceramic, Axial SLO
BLO; Manufacturer: Conquer; Part number: SCD-A 005
2
GE Multilin F35 Multiple Feeder Protection System 2-15
2.2 SPECIFICATIONS 2 PRODUCT DESCRIPTION
OPB P
TMIN()PRMIN()
=
Total insertion loss number of connectors 0.5 dB×=
2 0.5 dB×= 1.0 dB=
OPB
WORST
OPB 1 dB (LED aging) total insertion loss=
10dB 1 dB 1dB 8dB=
Maximum fiber length
OPB
WORST
(in dB)
cable loss (in dB/km)
-------------------------------------------------------
=
8 dB
2.8 dB/km
---------------------------
= 2.8 km=

2.2.8 COMMUNICATIONS

RS232
Front port: 19.2 kbps, Modbus® RTU
RS485
1 or 2 rear ports: Up to 115 kbps, Modbus® RTU, isolated
Typical distance: 1200 m
2
Isolation: 2 kV
together at 36 Vpk
ETHERNET (FIBER)
PARAMETER FIBER TYPE
10MB MULTI-
MODE
Wavelength 820 nm 1310 nm 1310 nm
Connector ST ST SC
Transmit power –20 dBm –20 dBm –15 dBm
Receiver sensitivity –30 dBm –30 dBm –30 dBm
Power budget 10 dB 10 dB 15 dB
Maximum input power
Typical distance 1.65 km 2 km 15 km
Duplex full/half full/half full/half
Redundancy yes yes yes
–7.6 dBm –14 dBm –7 dBm
100MB MULTI-
MODE
The UR-2S and UR-2T only support 100 Mb multimode
ETHERNET (10/100 MB TWISTED PAIR)
Modes: 10 MB, 10/100 MB (auto-detect)
Connector: RJ45
SNTP clock synchronization error: <10 ms (typical)
100MB SINGLE-
MODE
ETHERNET SWITCH FIBER OPTIC PORTS
Maximum fiber segment length calculation:
The maximum fiber segment length between two adjacent switches or between a switch and a device is calculated as fol­lows. First, calculate the optical power budget (OPB) of each device using the manufacturer’s data sheets.
where OPB = optical power budget, P and P
= receiver sensitivity.
R
The worst case optical power budget (OPB lated by taking the lower of the two calculated power budgets, sub­tracting 1 dB for LED aging, and then subtracting the total insertion loss. The total insertion loss is calculated by multiplying the num­ber of connectors in each single fiber path by 0.5 dB. For example, with a single fiber cable between the two devices, there will be a minimum of two connections in either transmit or receive fiber paths for a total insertion loss of 1db for either direction:
The worst-case optical power budget between two type 2T or 2S modules using a single fiber cable is:
To calculate the maximum fiber length, divide the worst-case opti­cal power budget by the cable attenuation per unit distance speci­fied in the manufacturer data sheets. For example, typical attenuation for 62.5/125 μm glass fiber optic cable is approxi- mately 2.8 dB per km. In our example, this would result in the fol­lowing maximum fiber length:
= transmitter output power,
T
) is then calcu-
WORST
2-16 F35 Multiple Feeder Protection System GE Multilin
The customer must use the attenuation specified within the manu­facturer data sheets for accurate calculation of the maximum fiber length.
ETHERNET SWITCH 10/100BASE-T PORTS
Connector type: RJ45
MAXIMUM 10 MBPS ETHERNET SEGMENT LENGTHS
Unshielded twisted pair: 100 m (328 ft.)
Shielded twisted pair: 150 m (492 ft.)
MAXIMUM STANDARD FAST ETHERNET SEGMENT LENGTHS
10Base-T (CAT 3, 4, 5 UTP): 100 m (328 ft.)
100Base-TX (CAT 5 UTP):100 m (328 ft.)
Shielded twisted pair: 150 m (492 ft.)
2 PRODUCT DESCRIPTION 2.2 SPECIFICATIONS
NOTE
NOTE
NOTE

2.2.9 INTER-RELAY COMMUNICATIONS

SHIELDED TWISTED-PAIR INTERFACE OPTIONS
INTERFACE TYPE TYPICAL DISTANCE
RS422 1200 m
G.703 100 m
RS422 distance is based on transmitter power and does not take into consideration the clock source provided by the user.
LINK POWER BUDGET AND MAXIMUM OPTICAL INPUT POWER
The following specifications apply to C37.94 modules implemented since January 2012.
EMITTER, FIBER TYPE
820 nm, Multimode -16 dBm -32 dBm 16 dBm -8 dBm Coupled into 62.5/125 μm multi-mode fiber
1300 nm, Multimode
1300 nm, Single mode
1300 nm Laser, Single mode
1550 nm Laser, Single mode
TRANSMIT POWER
-20 dBm 12 dBm Coupled into 50/125 μm multi-mode fiber
-16 dBm -32 dBm 16 dBm -8 dBm Coupled into 62.5/125 μm multi-mode fiber
-20 dBm 12 dBm Coupled into 50/125 μm multi-mode fiber
-15 dBm -32 dBm 17 dBm -8 dBm Coupled into 9/125 μm single-mode fiber
0 dBm -34 dBm 34 dBm -8 dBm Coupled into 9/125 μm single-mode fiber
5 dBm -34 dBm 39 dBm -10 dBm Coupled into 9/125 μm single-mode fiber
RECEIVED SENSITIVITY
POWER BUDGET
MAXIMUM OPTICAL INPUT POWER
NOTE
The following specifications apply to C37.94 modules implemented before January 2012.
EMITTER, FIBER TYPE
820 nm LED, Multimode
1300 nm LED, Multimode
1300 nm ELED, Single mode
1300 nm Laser, Single mode
1550 nm Laser, Single mode
TRANSMIT POWER
–20 dBm –30 dBm 10 dB –7.6 dBm
–21 dBm –30 dBm 9 dB –11 dBm
–23 dBm –32 dBm 9 dB –14 dBm
–1 dBm –30 dBm 29 dB –14 dBm
+5 dBm –30 dBm 35 dB –14 dBm
RECEIVED SENSITIVITY
POWER BUDGET
MAX. OPTICAL INPUT POWER
2
These power budgets are calculated from the manu­facturer’s worst-case transmitter power and worst case receiver sensitivity.
The power budgets for the 1300 nm ELED are calcu­lated from the manufacturer's transmitter power and receiver sensitivity at ambient temperature. At extreme temperatures these values deviate based on component tolerance. On average, the output power decreases as the temperature is increased by a factor 1dB / 5°C.
GE Multilin F35 Multiple Feeder Protection System 2-17
2.2 SPECIFICATIONS 2 PRODUCT DESCRIPTION
NOTE
TYPICAL LINK DISTANCE
EMITTER TYPE CABLE
820 nm LED, multimode
1300 nm LED, multimode
1300 nm ELED,
2
single mode
1300 nm Laser, single mode
1550 nm Laser, single-mode
Typical distances listed are based on the follow­ing assumptions for system loss. As actual losses will vary from one installation to another, the dis­tance covered by your system may vary.
CONNECTOR LOSSES (TOTAL OF BOTH ENDS)
ST connector 2 dB
FIBER LOSSES
820 nm multimode 3 dB/km
1300 nm multimode 1 dB/km
1300 nm singlemode 0.35 dB/km
1550 nm singlemode 0.25 dB/km
Splice losses: One splice every 2 km,
SYSTEM MARGIN
3 dB additional loss added to calculations to compensate for all other losses.
TYPE
62.5/125 μmST 1.65 km
62.5/125 μm ST 3.8 km
9/125 μmST11.4 km
9/125 μm ST 64 km
9/125 μm ST 105 km
at 0.05 dB loss per splice.
CONNECTOR
TYPE
TYPICAL
DISTANCE
Compensated difference in transmitting and receiving (channel asymmetry) channel delays using GPS satellite clock: 10 ms
AMBIENT TEMPERATURES
Storage temperature: –40 to 85°C
Operating temperature: –40 to 60°C; the LCD contrast may be
impaired at temperatures less than – 20°C
HUMIDITY
Humidity: operating up to 95% (non-condensing) at
55°C (as per IEC60068-2-30 variant 1, 6days).

2.2.10 ENVIRONMENTAL

OTHER
Altitude: 2000 m (maximum)
Pollution degree: II
Overvoltage category: II
Ingress protection: IP20 front, IP10 back
2-18 F35 Multiple Feeder Protection System GE Multilin
2 PRODUCT DESCRIPTION 2.2 SPECIFICATIONS

2.2.11 TYPE TESTS

F35 TYPE TESTS
TEST REFERENCE STANDARD TEST LEVEL
Dielectric voltage withstand EN60255-5 2.3 kV
Impulse voltage withstand EN60255-5 5 kV
Damped oscillatory IEC61000-4-18 / IEC60255-22-1 2.5 kV CM, 1 kV DM
Electrostatic discharge EN61000-4-2 / IEC60255-22-2 Level 3
RF immunity EN61000-4-3 / IEC60255-22-3 Level 3
Fast transient disturbance EN61000-4-4 / IEC60255-22-4 Class A and B
Surge immunity EN61000-4-5 / IEC60255-22-5 Level 3 and 4
Conducted RF immunity EN61000-4-6 / IEC60255-22-6 Level 3
Power frequency immunity EN61000-4-7 / IEC60255-22-7 Class A and B
Voltage interruption and ripple DC IEC60255-11 12% ripple, 200 ms interrupts
Radiated and conducted emissions CISPR11 / CISPR22 / IEC60255-25 Class A
Sinusoidal vibration IEC60255-21-1 Class 1
Shock and bump IEC60255-21-2 Class 1
Seismic IEC60255-21-3 Class 1
Power magnetic immunity IEC61000-4-8 Level 5
Pulse magnetic immunity IEC61000-4-9 Level 4
Damped magnetic immunity IEC61000-4-10 Level 4
Voltage dip and interruption IEC61000-4-11 0, 40, 70, 80% dips; 250 / 300 cycle interrupts
Damped oscillatory IEC61000-4-12 2.5 kV CM, 1 kV DM
Conducted RF immunity, 0 to 150 kHz IEC61000-4-16 Level 4
Voltage ripple IEC61000-4-17 15% ripple
Ingress protection IEC60529 IP20 front, IP10 back
Cold IEC60068-2-1 –40°C for 16 hours
Hot IEC60068-2-2 85°C for 16 hours
Humidity IEC60068-2-30 6 days, variant 1
Damped oscillatory IEEE/ANSI C37.90.1 2.5 kV, 1 MHz
RF immunity IEEE/ANSI C37.90.2 20 V/m, 80 MHz to 1 GHz
Safety UL508 e83849 NKCR
Safety UL C22.2-14 e83849 NKCR7
Safety UL1053 e83849 NKCR
2

2.2.12 PRODUCTION TESTS

THERMAL
Products go through an environmental test based upon an
Accepted Quality Level (AQL) sampling process.
GE Multilin F35 Multiple Feeder Protection System 2-19
2.2 SPECIFICATIONS 2 PRODUCT DESCRIPTION
NOTE
APPROVALS
2
COMPLIANCE APPLICABLE
CE compliance Low voltage directive EN60255-5
North America --- UL508
COUNCIL DIRECTIVE
EMC directive EN60255-26 / EN50263
--- UL1053
--- C22.2 No. 14
ACCORDING TO
EN61000-6-5

2.2.14 MAINTENANCE

MOUNTING
Attach mounting brackets using 20 inch-pounds (±2 inch-pounds) of torque.
CLEANING
Normally, cleaning is not required; but for situations where dust has accumulated on the faceplate display, a dry cloth can be used.
Units that are stored in a de-energized state should be powered up once per year, for one hour continuously, to avoid deterioration of electrolytic capacitors.

2.2.13 APPROVALS

2-20 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.1 DESCRIPTION
17.56”
[446,02 mm]
9.687”
[246,05 mm]
11.016”
[279,81 mm]
7.460”
[189,48 mm]
6.960” [176,78 mm]
19.040”
[483,62 mm]
6.995”
[177,67 mm]
842807A1.CDR

3 HARDWARE 3.1DESCRIPTION 3.1.1 PANEL CUTOUT

a) HORIZONTAL UNITS
The F35 Multiple Feeder Protection System is available as a 19-inch rack horizontal mount unit with a removable faceplate. The faceplate can be specified as either standard or enhanced at the time of ordering. The enhanced faceplate contains additional user-programmable pushbuttons and LED indicators.
The modular design allows the relay to be easily upgraded or repaired by a qualified service person. The faceplate is hinged to allow easy access to the removable modules, and is itself removable to allow mounting on doors with limited rear depth. There is also a removable dust cover that fits over the faceplate, which must be removed when attempting to access the keypad or RS232 communications port.
The case dimensions are shown below, along with panel cutout details for panel mounting. When planning the location of your panel cutout, ensure that provision is made for the faceplate to swing open without interference to or from adjacent equipment.
The relay must be mounted such that the faceplate sits semi-flush with the panel or switchgear door, allowing the operator access to the keypad and the RS232 communications port. The relay is secured to the panel with the use of four screws supplied with the relay.
3
Figure 3–1: F35 HORIZONTAL DIMENSIONS (ENHANCED PANEL)
GE Multilin F35 Multiple Feeder Protection System 3-1
3
18.370”
[466,60 mm]
842808A2.CDR
0.280” [7,11 mm] Typ. x 4
4.000”
[101,60 mm]
17.750”
[450,85 mm]
CUT-OUT
7.13”
[181.1 mm]
3.1 DESCRIPTION 3 HARDWARE
Figure 3–2: F35 HORIZONTAL MOUNTING (ENHANCED PANEL)
Figure 3–3: F35 HORIZONTAL MOUNTING AND DIMENSIONS (STANDARD PANEL)
b) VERTICAL UNITS
The F35 Multiple Feeder Protection System is available as a reduced size (¾) vertical mount unit, with a removable face­plate. The faceplate can be specified as either standard or enhanced at the time of ordering. The enhanced faceplate con­tains additional user-programmable pushbuttons and LED indicators.
The modular design allows the relay to be easily upgraded or repaired by a qualified service person. The faceplate is hinged to allow easy access to the removable modules, and is itself removable to allow mounting on doors with limited rear depth. There is also a removable dust cover that fits over the faceplate, which must be removed when attempting to access the keypad or RS232 communications port.
The case dimensions are shown below, along with panel cutout details for panel mounting. When planning the location of your panel cutout, ensure that provision is made for the faceplate to swing open without interference to or from adjacent equipment.
3-2 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.1 DESCRIPTION
14.025”
7.482”
15.000”
4.000”
9.780”
11.015”
1.329”
13.560”
843809A1.CDR
The relay must be mounted such that the faceplate sits semi-flush with the panel or switchgear door, allowing the operator access to the keypad and the RS232 communications port. The relay is secured to the panel with the use of four screws supplied with the relay.
3
Figure 3–4: F35 VERTICAL DIMENSIONS (ENHANCED PANEL)
GE Multilin F35 Multiple Feeder Protection System 3-3
3
e
URSERIESURSERIES
3.1 DESCRIPTION 3 HARDWARE
Figure 3–5: F35 VERTICAL MOUNTING AND DIMENSIONS (STANDARD PANEL)
For details on side mounting F35 devices with the enhanced front panel, refer to the following documents available online from the GE Grid Solutions website.
GEK-113180: UR-series UR-V side-mounting front panel assembly instructions.
GEK-113181: Connecting the side-mounted UR-V enhanced front panel to a vertical UR-series device.
GEK-113182: Connecting the side-mounted UR-V enhanced front panel to a vertically-mounted horizontal UR-series device.
For details on side mounting F35 devices with the standard front panel, refer to the figures below.
3-4 F35 Multiple Feeder Protection System GE Multilin
PANEL
UR 19"
MOUNTING
BRACKET
UR-V FRONT BEZEL
ASSEMBLY
#6x1/2" PAN PHILIPS
HEAD
BLACK OXIDE
PLASTITE SCREW
#10-3/8" PAN PHILIPS HEAD
ZINC
P/N: 1410-0006
4 PLACES TO MOUNT THE
BRACKETS
STEP 3
MOUNT FRONT BEZEL TO
PANEL
STEP 2
MOUNT BRACKETS TO
PANEL
#10-32 NYLOCK
NUT
P/N: 1422-1032
4 PLACES
#8-3/8" PAN PHILIPS HEAD
BLACK OXIDE SCREW
P/N: 1408-0306
8 PLACES TO MOUNT THE UNIT
#8 LOCKWASHER
EXTERNAL TOOTH
P/N: 1435-0002
8 PLACES TO MOUNT
STEP 4
ASSEMBLE UR-V UNIT
TO MOUNTING BRACKETS
UR-V UNIT
STEP 1 - CREATE THE HOLES AND CUT-OUT INTO THE PANEL
AS PER DRAWING 843753.
PLUG THE DISPLAY CABLE INTO
THE FRONT BEZEL
BEFORE MOUNTING THE
UNIT ON THE PANEL
DISPLAY CABLE
GROUND CABLE
ATTACH CABLE TO
FRONT BEZEL
BEFORE MOUNTING
FRONT BEZEL ON
THE
PANEL
SIDE MOUNT COVER
P/N: 1004-0018
#8-3/8"
PAN PHILIPS HEAD
BLACK OXIDE
SCREW
843757A2.cdr
3 HARDWARE 3.1 DESCRIPTION
3
Figure 3–6: F35 VERTICAL SIDE MOUNTING INSTALLATION (STANDARD PANEL)
GE Multilin F35 Multiple Feeder Protection System 3-5
3
CUT-OUT
1.33" (33.9)
2.83" (71.9)
6.66"
(169.2)
12.20" (309.9)
0.159" DIA. (6 PLACES) (4.0)
0.213" DIA. (5.4) (4 PLACES) SEE HOLES MARKED 'X'
INCHES
(MILLIMETERS)
5.33"
(135.4)
PANEL SHOWN FOR REFERENCE ONLY (VIEWED FROM FRONT)
'X''X'
'X''X'
1.00" (25.4)
1.00" (25.4)
10.05 (255.3)
"
0.04 (1.0)
"
0.68" (17.3)
5.27
(133.8)
"
843753A3.cdr
WARNING
3.1 DESCRIPTION 3 HARDWARE
Figure 3–7: F35 VERTICAL SIDE MOUNTING REAR DIMENSIONS (STANDARD PANEL)

3.1.2 MODULE WITHDRAWAL AND INSERTION

Module withdrawal and insertion may only be performed when control power has been removed from the unit. Inserting an incorrect module type into a slot may result in personal injury, damage to the unit or connected equipment, or undesired operation!
Proper electrostatic discharge protection (for example, a static strap) must be used when coming in contact with modules while the relay is energized!
The relay, being modular in design, allows for the withdrawal and insertion of modules. Modules must only be replaced with like modules in their original factory configured slots.
The enhanced faceplate can be opened to the left, once the thumb screw has been removed, as shown below. This allows for easy accessibility of the modules for withdrawal. The new wide-angle hinge assembly in the enhanced front panel opens completely and allows easy access to all modules in the F35.
3-6 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.1 DESCRIPTION
842812A1.CDR
NOTE
Figure 3–8: UR MODULE WITHDRAWAL AND INSERTION (ENHANCED FACEPLATE)
The standard faceplate can be opened to the left, once the sliding latch on the right side has been pushed up, as shown below. This allows for easy accessibility of the modules for withdrawal.
Figure 3–9: UR MODULE WITHDRAWAL AND INSERTION (STANDARD FACEPLATE)
To properly remove a module, the ejector/inserter clips, located at the top and bottom of each module, must be pulled simultaneously. Before performing this action, control power must be removed from the relay. Record the original loca­tion of the module to ensure that the same or replacement module is inserted into the correct slot. While modules with cur­rent input provide automatic shorting of external CT circuits, for CT/VT modules it is recommended to short/isolate external circuits accordingly for maximum safety.
To properly insert a module, ensure that the correct module type is inserted into the correct slot position. The ejector/ inserter clips located at the top and at the bottom of each module must be in the disengaged position as the module is smoothly inserted into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module will be fully inserted.
All CPU modules except the 9E are equipped with 10/100Base-T or 100Base-F Ethernet connectors. These con­nectors must be individually disconnected from the module before it can be removed from the chassis.
3
GE Multilin F35 Multiple Feeder Protection System 3-7
3
NOTE
XWV U TS PNM L KJ H DGF BR
8
4
7
3
6
2
5
1
b
8
4
7
3
6
2
5
1
a
abc abc abc abc
4
3
2
1
b
4
3
2
1
a
IN
OUT
Tx1
Tx2
Rx2
Rx1
CH1
Tx
CH2
Rx
CH1
CH2
®
®
Technical Support: Tel: (905) 294-6222 Fax: (905) 201-2098
Model: Mods: Wiring Diagram: Inst. Manual: Serial Number: Firmware: Mfg. Date:
F35D00HCHF8AH6AM6BP8BX7A 000 ZZZZZZ D MAZB98000029 D 1999/01/05
Control Power: Contact Inputs: Contact Outputs:
88-300V DC @ 35W / 77-265V AC @ 35VA 300V DC Max 10mA Standard Pilot Duty / 250V AC 7.5A 360V A Resistive / 125V DC Break 4A @ L/R = 40mS / 300W
RATINGS:
F35
Multiple Feeder Management Relay
Made in Canada
- M A A B 9 7 0 0 0 0 9 9 -
http://www.GEIndustrial.com/Multilin
GE Multilin
Optional Ethernet
switch
Optional
direct
input/output
module
CPU module
(Ethernet not
available when
ordered with
Ethernet switch)
Optional
contact
input/output
module
CT/VT
module
Power supply
module
Tx1
Tx2
Rx1
Rx2
Tx1
Tx2
832766A3.CDR
Optional CT/VT or
contact
input/output
module
Optional
contact
input/output
module
WARNING
3.1 DESCRIPTION 3 HARDWARE
The 4.0x release of the F35 relay includes new hardware modules.The new CPU modules are specified with codes 9E and higher. The new CT/VT modules are specified with the codes 8F and higher.
The new CT/VT modules can only be used with new CPUs; similarly, old CT/VT modules can only be used with old CPUs. To prevent hardware mismatches, the new modules have blue labels and a warning sticker stating “Attn.: Ensure CPU and DSP module label colors are the same!”. In the event that there is a mismatch between the CPU and CT/VT module, the relay will not function and a
DSP ERROR or HARDWARE MISMATCH error will be dis-
played.
All other input and output modules are compatible with the new hardware. Firmware versions 4.0x and higher are only compatible with the new hardware modules. Previous versions of the firmware (3.4x and earlier) are only com­patible with the older hardware modules.

3.1.3 REAR TERMINAL LAYOUT

The relay follows a convention with respect to terminal number assignments which are three characters long assigned in order by module slot position, row number, and column letter. Two-slot wide modules take their slot designation from the first slot position (nearest to CPU module) which is indicated by an arrow marker on the terminal block. See the following figure for an example of rear terminal assignments.
3-8 F35 Multiple Feeder Protection System GE Multilin
Do not touch any rear terminals while the relay is energized!
Figure 3–10: REAR TERMINAL VIEW
3 HARDWARE 3.1 DESCRIPTION
Figure 3–11: EXAMPLE OF MODULES IN F AND H SLOTS
The torque used to connect the terminal blocks to the back of the relay chassis (screws a, b, c shown) is 9 inch-pounds. For the connections to the terminal blocks (rows 1 to 8), use a minimum of 17 inch-pounds. During manufacturing, the power supply and CPU modules are installed in slots B and D of the chassis with 13 inch-pounds of torque on the screws at the top and bottom of the modules.
3
GE Multilin F35 Multiple Feeder Protection System 3-9
3.2 WIRING 3 HARDWARE
832767A4.CDR
(Rear View)
1
Power Supply
9
CPU8CT6Inputs/
outputs
8
CT
8
CT/VT6Inputs/
outputs
6
Inputs/ outputs
MODULE ARRANGEMENT
JU
MXLWKVBHTD
N
GSP FR
CONTACTSSHOWN
WITH NO
CONTROL POWER
TYPICAL CONFIGURATION
THE AC SIGNAL PATHIS CONFIGURABLE
POSITIVE WATTS
F35
MULTIPLEFEEDER MANAGEMENT RELAY
AC or DC
DC
( DCONLY)
UR COMPUTER
1
TXD RXD RXD TXD
SGND SGND
1
8 3 2
20
7 6 4 5
22
25 PIN CONNECTOR
9PIN
CONNECTOR
22 33 44 55 66 77 88 99
RS-232
(front)
DB-9
CRITICAL FAILURE
48 VDC OUTPUT
CONTROL
POWER
HI LO
POWER SUPPLY
1
FILTER
SURGE
B3a
B1b
B8a
B6b
B8b
B6a
B3b
B1a B2b
B5b
P1a
P2b
P1c
P1b
P2c
P2a
P4a
P4c
P3b
P3a
P4b
P3c
CONTACTINPUT P5a
CONTACTINPUT P7a
CONTACTINPUT P5c
CONTACTINPUT P7c
CONTACTINPUT P6a
CONTACTINPUT P8a
CONTACTINPUT P6c
CONTACTINPUT P8c
COMMON P5b
COMMON P7b
SURGE
P6a
P8a
P5b
P7b
P8b
P5a
P7a
P6c
P8c
P5c
P7c
P1
P2
P3
P4
I
V
I
V
I
V
I
V
DIGITALINPUTS/OUTPUTS
6G
H1a
H2b
H1c
H1b
H2c
H2a
H4a
H4c
H3b
H3a
H4b
H3c
CONTACTINPUT H5a
CONTACTINPUT H7a
CONTACTINPUT H5c
CONTACTINPUT H7c
CONTACTINPUT H6a
CONTACTINPUT H8a
CONTACTINPUT H6c
CONTACTINPUT H8c
COMMON H5b
COMMON H7b
SURGE
H6a
H8a
H5b
H7b
H8b
H5a
H7a
H6c
H8c
H5c
H7c
H1
H2
H3
H4
I
V
I
V
I
V
I
V
DIGITALINPUTS/OUTPUTS
6G
W1a
W2b
W1c
W1b
W2c
W2a
W4a
W4c
W3b
W3a
W4b
W3c
CONTACTINPUT W5a
CONTACTINPUT W7a
CONTACTINPUT W5c
CONTACTINPUT W7c
CONTACTINPUT W6a
CONTACTINPUT W8a
CONTACTINPUT W6c
CONTACTINPUT W8c
COMMON W5b
COMMON W7b
SURGE
W6a
W8a
W5b
W7b
W8b
W5a
W7a
W6c
W8c
W5c
W7c
W1
W2
W3
W4
I
V
I
V
I
V
I
V
DIGITALINPUTS/OUTPUTS
6G
U1c
U4a
U3c
U5a
U5c
U7c
CIRCUIT U
CURRENT INPUTS
U6a
U7a
U6c
U2c
VA
VB
VC
U4c
U1a
U4b
U1b
U2a
U3a
U2b
U3b
CIRCUIT U
VOLTAGEINPUTS
8F /8G
VA
VB
VC
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
F7c
F8c
F8b
F8a
F5c
F5a
F5b
F7b
F3c
F4b
F4a
F4c
F1c
F6a
F2b
F7a
F2a
F6b
F6c
F2c
F1a
F1b
F3a
F3b
CIRCUIT U
CIRCUIT U
CURRENT INPUTS
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
CURRENT INPUTS
8H /8J
IC
IA
M7c
M8c
M8b
M8a
M5c
M5a
M5b
M7b
M3c
M4b
M4a
M4c
M1c
M6a
M2b
M7a
M2a
M6b
M6c
M2c
M1a
M1b
M3a
M3b
CIRCUIT U
CIRCUIT U
CURRENT INPUTS
8H /8J
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
A
B
C
1
2
3
4
5
GROUND BUS
No.10AWG
Minimum
MODULES MUSTBE
GROUNDED IF
TERMINAL IS
PROVIDED
TC
TC
2
1
VOLTAGESUPERVISION
VOLTAGEAND
CURRENT SUPERVISION
CONNECTION
AS REQUIRED
U8c
U8a
VX
VX
OPEN DELTA(ABC)
VT CONNECTION
CBA
U5a
U5c
U7c
U6a
U7a
U6c
VA
VB
VC
VOLTAGEINPUTS
VA
VB
VC
D1a D2a
D4b
D3a
D4a
IRIG-B Input
IRIG-B
Output
COM
1
RS485
COM 2
ALTERNATE
NORMAL
com
CPU
9H
10BaseT
10BaseFL
10BaseFL
Tx2
Rx2
Tx1
Rx1
BNC
BNC
Fibre Optic
*
Groundat
Remote
Device
Shielded
twistedpairs
Co-axial
Co-axial
Co-axial*
Co-axial * - For IRIG-B Input
only use one terminal as input
This diagram is based on the following order code:
This diagram provides an example of how the device is wired, not specifically how to wire the device. Please refer to the Instruction Manual for additional details on wiring based on various configurations.
F35-H00-HCH-F8H-H6G-M8H-P6G-U8F-W6G
GE Consumer & Industrial
Multilin

3.2WIRING 3.2.1 TYPICAL WIRING

3
3-10 F35 Multiple Feeder Protection System GE Multilin
Figure 3–12: TYPICAL WIRING DIAGRAM
3 HARDWARE 3.2 WIRING
NOTICE
NOTE

3.2.2 DIELECTRIC STRENGTH

The dielectric strength of the UR-series module hardware is shown in the following table.
Table 3–1: DIELECTRIC STRENGTH OF UR-SERIES MODULE HARDWARE
MODULE
TYPE
1 Power supply High (+); Low (+); (–) Chassis 2000 V AC for 1 minute
1 Power supply 48 V DC (+) and (–) Chassis 2000 V AC for 1 minute
1 Power supply Relay terminals Chassis 2000 V AC for 1 minute
2 Reserved N/A N/A N/A
3 Reserved N/A N/A N/A
4 Digital inputs/outputs All Chassis 2000 V AC for 1 minute
5 Analog inputs/outputs All except 8b Chassis < 50 V DC
6 Digital inputs/outputs All Chassis 2000 V AC for 1 minute
7
8 CT/VT All Chassis 2000 V AC for 1 minute
9 CPU All Chassis 2000 V AC for 1 minute
MODULE FUNCTION TERMINALS DIELECTRIC STRENGTH
FROM TO
G.703 All except 2b, 3a, 7b, 8a Chassis 2000 V AC for 1 minute
RS422 All except 6a, 7b, 8a Chassis < 50 V DC
(AC)
Filter networks and transient protection clamps are used in the hardware to prevent damage caused by high peak voltage transients, radio frequency interference (RFI), and electromagnetic interference (EMI). These protective components can be damaged by application of the ANSI/IEEE C37.90 specified test voltage for a period longer than the specified one min­ute.
3

3.2.3 CONTROL POWER

Control power supplied to the relay must be connected to the matching power supply range of the relay. If the voltage is applied to the wrong terminals, damage may occur.
The F35 relay, like almost all electronic relays, contains electrolytic capacitors. These capacitors are well known to be subject to deterioration over time if voltage is not applied periodically. Deterioration can be avoided by powering the relays up once a year.
The power supply module can be ordered for two possible voltage ranges, with or without a redundant power option. Each range has a dedicated input connection for proper operation. The ranges are as shown below (see the Technical specifica- tions section of chapter 2 for additional details):
Low (LO) range: 24 to 48 V (DC only) nominal.
High (HI) range: 125 to 250 V nominal.
The power supply module provides power to the relay and supplies power for dry contact input connections.
The power supply module provides 48 V DC power for dry contact input connections and a critical failure relay (see the Typical wiring diagram earlier). The critical failure relay is a form-C device that will be energized once control power is applied and the relay has successfully booted up with no critical self-test failures. If on-going self-test diagnostic checks detect a critical failure (see the Self-test errors section in chapter 7) or control power is lost, the relay will de-energize.
For high reliability systems, the F35 has a redundant option in which two F35 power supplies are placed in parallel on the bus. If one of the power supplies become faulted, the second power supply will assume the full load of the relay without any interruptions. Each power supply has a green LED on the front of the module to indicate it is functional. The critical fail relay of the module will also indicate a faulted power supply.
GE Multilin F35 Multiple Feeder Protection System 3-11
3.2 WIRING 3 HARDWARE
AC or DC
NOTE: 14 gauge stranded wire with suitable disconnect devices is recommended.
Heavy copper conductor
or braided wire
Switchgear
ground bus
UR-series
protection system
FILTER
SURGE
+
LOW
+
HIGH
B8b B8a B6a B6b B5b
CONTROL
POWER
827759AA.CDR
+
OPTIONAL
ETHERNET SWITCH
AC or DC
GND
NOTE
NOTICE
An LED on the front of the control power module shows the status of the power supply:
LED INDICATION POWER SUPPLY
CONTINUOUS ON OK
ON / OFF CYCLING Failure
OFF Failure
3
Figure 3–13: CONTROL POWER CONNECTION
When using an SH/SL power supply module or a F35 with the HardFiber system, before powering off the F35, save data in the compact flash memory using Commands > Relay Maintenance > Save Non-Volatile Data. When not saved or the relay loses power, up to the last two minutes of data is not saved to the compact flash memory.

3.2.4 CT/VT MODULES

A CT/VT module may have voltage inputs on channels 1 through 4 inclusive, or channels 5 through 8 inclusive. Channels 1 and 5 are intended for connection to phase A, and are labeled as such in the relay. Likewise, channels 2 and 6 are intended for connection to phase B, and channels 3 and 7 are intended for connection to phase C.
Channels 4 and 8 are intended for connection to a single-phase source. For voltage inputs, these channel are labelled as auxiliary voltage (VX). For current inputs, these channels are intended for connection to a CT between system neutral and ground, and are labelled as ground current (IG).
Verify that the connection made to the relay nominal current of 1 A or 5 A matches the secondary rating of the connected CTs. Unmatched CTs may result in equipment damage or inadequate pro­tection.
CT/VT modules may be ordered with a standard ground current input that is the same as the phase current input. Each AC current input has an isolating transformer and an automatic shorting mechanism that shorts the input when the module is withdrawn from the chassis. There are no internal ground connections on the current inputs. Current transformers with 1 to 50000 A primaries and 1 A or 5 A secondaries may be used.
CT/VT modules with a sensitive ground input are also available. The ground CT input of the sensitive ground modules is ten times more sensitive than the ground CT input of standard CT/VT modules. However, the phase CT inputs and phase VT inputs are the same as those of regular CT/VT modules.
The above modules are available with enhanced diagnostics. These modules can automatically detect CT/VT hardware failure and take the relay out of service.
CT connections for both ABC and ACB phase rotations are identical as shown in the Typical wiring diagram.
3-12 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
Ground connection to neutral must be on the source side
UNSHIELDED CABLE
LOAD
ABCN G
Ground outside CT
Source
LOAD
SHIELDED CABLE
996630A5
AB C
Source
To ground; must be on load side
Stress cone
shields
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
1a
1b
1c
2a
2b
2c
3a
4a
5a
6a
7a
8a
3b
4b
5c
6c
7c
8c
3c
4c
Current inputs
8F, 8G, 8L , and 8M modules (4 CTs and 4 VTs)
Voltage inputs
VA
VB
VC
VX
VA
VB
VC
VX
IA
IC
IB
IG
IA5
IC5
IB5
IG5
IA1
IC1
IB1
IG1
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
1a
5a
1b
5b
1c
5c
2a
6a
2b
6b
2c
6c
3a
7a
4a
8a
3b
7b
4b
8b
3c
7c
4c
8c
Current inputs
842766A3.CDR
IA
IA
IC
IC
IB
IB
IG
IG
IA5
IA5
IC5
IC5
IB5
IB5
IG5
IG5
IA1
IA1
IC1
IC1
IB1
IB1
IG1
IG1
8H, 8J, 8N, and 8R modules (8 CTs)
The exact placement of a zero-sequence core balance CT to detect ground fault current is shown below. Twisted-pair cabling on the zero-sequence CT is recommended.
Figure 3–14: ZERO-SEQUENCE CORE BALANCE CT INSTALLATION
The phase voltage channels are used for most metering and protection purposes. The auxiliary voltage channel is used as input for the synchrocheck and volts-per-hertz features.
Substitute the tilde “~” symbol with the slot position of the module in the following figure.
3
Figure 3–15: CT/VT MODULE WIRING
GE Multilin F35 Multiple Feeder Protection System 3-13
3.2 WIRING 3 HARDWARE

3.2.5 PROCESS BUS MODULES

The F35 can be ordered with a process bus interface module. This module is designed to interface with the GE Multilin HardFiber system, allowing bi-directional IEC 61850 fiber optic communications with up to eight HardFiber merging units, known as Bricks. The HardFiber system has been designed to integrate seamlessly with the existing UR-series applica­tions, including protection functions, FlexLogic™, metering, and communications.
The IEC 61850 process bus system offers the following benefits.
Drastically reduces labor associated with design, installation, and testing of protection and control applications using the F35 by reducing the number of individual copper terminations.
Integrates seamlessly with existing F35 applications, since the IEC 61850 process bus interface module replaces the traditional CT/VT modules.
Communicates using open standard IEC 61850 messaging.
3
For additional details on the HardFiber system, refer to GE publication GEK-113500: HardFiber System Instruction Manual.

3.2.6 CONTACT INPUTS AND OUTPUTS

Every contact input/output module has 24 terminal connections. They are arranged as three terminals per row, with eight rows in total. A given row of three terminals may be used for the outputs of one relay. For example, for form-C relay outputs, the terminals connect to the normally open (NO), normally closed (NC), and common contacts of the relay. For a form-A output, there are options of using current or voltage detection for feature supervision, depending on the module ordered. The terminal configuration for contact inputs is different for the two applications.
The contact inputs are grouped with a common return. The F35 has two versions of grouping: four inputs per common return and two inputs per common return. When a contact input/output module is ordered, four inputs per common is used. The four inputs per common allows for high-density inputs in combination with outputs, with a compromise of four inputs sharing one common. If the inputs must be isolated per row, then two inputs per common return should be selected (4D module).
The tables and diagrams on the following pages illustrate the module types (6A, etc.) and contact arrangements that may be ordered for the relay. Since an entire row is used for a single contact output, the name is assigned using the module slot position and row number. However, since there are two contact inputs per row, these names are assigned by module slot position, row number, and column position.
Some form-A / solid-state relay outputs include circuits to monitor the DC voltage across the output contact when it is open, and the DC current through the output contact when it is closed. Each of the monitors contains a level detector whose out­put is set to logic “On = 1” when the current in the circuit is above the threshold setting. The voltage monitor is set to “On = 1” when the current is above about 1 to 2.5 mA, and the current monitor is set to “On = 1” when the current exceeds about 80 to 100 mA. The voltage monitor is intended to check the health of the overall trip circuit, and the current monitor can be used to seal-in the output contact until an external contact has interrupted current flow.
Block diagrams are shown below for form-A and solid-state relay outputs with optional voltage monitor, optional current monitor, and with no monitoring. The actual values shown for contact output 1 are the same for all contact outputs.
3-14 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
/RDG
,
aD
aE
aF
,I,GFP$ RWKHUZLVH
 &RQW2S
&RQW2S
 ´92
 ´92IIµ
9
$&'5
D9ROWDJHZLWKRSWLRQDO FXUUHQWPRQLWRULQJ
9ROWDJHPRQLWRULQJRQO\
/RDG
,
9
%RWKYROWDJHDQGFXUUHQWPRQLWRULQJ
,I,GFP$ &RQW2S
&RQW2S
 ´,2
RWKHUZLVH ´,2IIµ
,I,GFP$ RWKHUZLVH
 &RQW2S
&RQW2S
 ´92
 ´92IIµ
/RDG
,
9
E&XUUHQWZLWKRSWLRQDO YROWDJHPRQLWRULQJ
&XUUHQWPRQLWRULQJRQO\ %RWKYROWDJHDQGFXUUHQWPRQLWRULQJ
H[WHUQDOMXPSHUDELVUHTXLUHG
,I,GFP$ &RQW2S
&RQW2S
´,2Qµ
RWKHUZLVH ´,2IIµ
/RDG
9
,I,GFP$ &RQW2S
&RQW2S
´,2
RWKHUZLVH ´,2IIµ
,I,GFP$ RWKHUZLVH
 &RQW2S
&RQW2S
 ´92
´92IIµ
/RDG
F1RPRQLWRULQJ
aD
aE
aF
aD
aE
aF
aD
aE
aF
aD
aE
aF
,
WARNING
NOTE
NOTE
3
Figure 3–16: FORM-A AND SOLID-STATE CONTACT OUTPUTS WITH VOLTAGE AND CURRENT MONITORING
The operation of voltage and current monitors is reflected with the corresponding FlexLogic™ operands (CONT OP # VON,
CONT OP # VOFF, and CONT OP # ION) which can be used in protection, control, and alarm logic. The typical application of
the voltage monitor is breaker trip circuit integrity monitoring; a typical application of the current monitor is seal-in of the control command.
Refer to the Digital elements section of chapter 5 for an example of how form-A and solid-state relay contacts can be applied for breaker trip circuit integrity monitoring.
Relay contacts must be considered unsafe to touch when the unit is energized! If the relay contacts need to be used for low voltage accessible applications, it is the customer’s respon­sibility to ensure proper insulation levels!
USE OF FORM-A AND SOLID-STATE RELAY OUTPUTS IN HIGH IMPEDANCE CIRCUITS
For form-A and solid-state relay output contacts internally equipped with a voltage measuring cIrcuit across the contact, the circuit has an impedance that can cause a problem when used in conjunction with external high input impedance monitoring equipment such as modern relay test set trigger circuits. These monitoring circuits may con­tinue to read the form-A contact as being closed after it has closed and subsequently opened, when measured as an impedance.
The solution to this problem is to use the voltage measuring trigger input of the relay test set, and connect the form­A contact through a voltage-dropping resistor to a DC voltage source. If the 48 V DC output of the power supply is used as a source, a 500 Ω, 10 W resistor is appropriate. In this configuration, the voltage across either the form-A contact or the resistor can be used to monitor the state of the output.
Wherever a tilde “~” symbol appears, substitute with the slot position of the module; wherever a number sign “#” appears, substitute the contact number
GE Multilin F35 Multiple Feeder Protection System 3-15
3.2 WIRING 3 HARDWARE
NOTICE
When current monitoring is used to seal-in the form-A and solid-state relay contact outputs, the Flex­Logic™ operand driving the contact output should be given a reset delay of 10 ms to prevent dam­age of the output contact (in situations when the element initiating the contact output is bouncing, at values in the region of the pickup value).
Table 3–2: CONTACT INPUT AND OUTPUT MODULE ASSIGNMENTS
~6A MODULE ~6B MODULE ~6C MODULE ~6D MODULE
3
TERMINAL
ASSIGNMENT
~1 Form-A ~1 Form-A ~1 Form-C ~1a, ~1c 2 Inputs
~2 Form-A ~2 Form-A ~2 Form-C ~2a, ~2c 2 Inputs
~3 Form-C ~3 Form-C ~3 Form-C ~3a, ~3c 2 Inputs
~4 Form-C ~4 Form-C ~4 Form-C ~4a, ~4c 2 Inputs
~5a, ~5c 2 Inputs ~5 Form-C ~5 Form-C ~5a, ~5c 2 Inputs
~6a, ~6c 2 Inputs ~6 Form-C ~6 Form-C ~6a, ~6c 2 Inputs
~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7 Form-C ~7a, ~7c 2 Inputs
~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8 Form-C ~8a, ~8c 2 Inputs
TERMINAL
ASSIGNMENT
~1Form-C ~1 Fast Form-C ~1Form-A ~1Form-A
~2Form-C ~2 Fast Form-C ~2Form-A ~2Form-A
~3Form-C ~3 Fast Form-C ~3Form-A ~3Form-A
~4Form-C ~4 Fast Form-C ~4Form-A ~4Form-A
~5a, ~5c 2 Inputs ~5 Fast Form-C ~5a, ~5c 2 Inputs ~5 Form-A
~6a, ~6c 2 Inputs ~6 Fast Form-C ~6a, ~6c 2 Inputs ~6 Form-A
~7a, ~7c 2 Inputs ~7 Fast Form-C ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs
~8a, ~8c 2 Inputs ~8 Fast Form-C ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
OUTPUT OR
INPUT
~6E MODULE ~6F MODULE ~6G MODULE ~6H MODULE
OUTPUT OR
INPUT
TER MINA L
ASSIGNMENT
TER MINA L
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT TERMINAL
TERMINAL
ASSIGNMENT
ASSIGNMENT
OUTPUT TERMINAL
OUTPUT OR
INPUT
ASSIGNMENT
TER MINA L
ASSIGNMENT
OUTPUT
OUTPUT OR
INPUT
~6K MODULE ~6L MODULE ~6M MODULE ~6N MODULE
TERMINAL
ASSIGNMENT
~1 Form-C ~1Form-A ~1Form-A ~1Form-A
~2 Form-C ~2Form-A ~2Form-A ~2Form-A
~3 Form-C ~3Form-C ~3Form-C ~3Form-A
~4 Form-C ~4Form-C ~4Form-C ~4Form-A
~5 Fast Form-C ~5a, ~5c 2 Inputs ~5Form-C ~5a, ~5c 2 Inputs
~6 Fast Form-C ~6a, ~6c 2 Inputs ~6Form-C
~7 Fast Form-C ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs
~8 Fast Form-C ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
OUTPUT TERMINAL
ASSIGNMENT
OUTPUT OR
INPUT
TERMINAL
ASSIGNMENT
OUTPUT OR
INPUT
TER MINA L
ASSIGNMENT
~6a, ~6c 2 Inputs
OUTPUT OR
INPUT
3-16 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
~6P MODULE ~6R MODULE ~6S MODULE ~6T MODULE
TERMINAL
ASSIGNMENT
~1 Form-A ~1Form-A ~1Form-A ~1Form-A
~2 Form-A ~2Form-A ~2Form-A ~2Form-A
~3 Form-A ~3Form-C ~3Form-C ~3Form-A
~4 Form-A ~4Form-C ~4Form-C ~4Form-A
~5 Form-A ~5a, ~5c 2 Inputs ~5Form-C ~5a, ~5c 2 Inputs
~6 Form-A ~6a, ~6c 2 Inputs ~6Form-C ~6a, ~6c 2 Inputs
~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs
~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
TERMINAL
ASSIGNMENT
~1 Form-A ~1 Form-A ~1Form-A ~1Not Used
~2 Form-A ~2 Form-A ~2Form-A ~2 Solid-State
~3 Form-A ~3 Form-C ~3Form-A ~3Not Used
~4 Form-A ~4 2 Outputs ~4Form-A ~4 Solid-State
~5 Form-A ~5a, ~5c 2 Inputs ~5Form-A ~5Not Used
~6 Form-A ~6a, ~6c 2 Inputs ~6Form-A ~6 Solid-State
~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7Form-A ~7Not Used
~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8Form-A ~8 Solid-State
OUTPUT OR
INPUT
~6U MODULE ~6V MODULE ~67 MODULE ~4A MODULE
OUTPUT OR
INPUT
TER MINA L
ASSIGNMENT
TER MINA L
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT OR
INPUT
TERMINAL
ASSIGNMENT
TERMINAL
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT TERMINAL
TER MINA L
ASSIGNMENT
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT
3
~4B MODULE ~4C MODULE ~4D MODULE ~4L MODULE
TERMINAL
ASSIGNMENT
~1Not Used ~1 Not Used ~1a, ~1c 2 Inputs ~1 2 Outputs
~2 Solid-State ~2 Solid-State ~2a, ~2c 2 Inputs ~2 2 Outputs
~3Not Used ~3 Not Used ~3a, ~3c 2 Inputs ~3 2 Outputs
~4 Solid-State ~4 Solid-State ~4a, ~4c 2 Inputs ~4 2 Outputs
~5Not Used ~5 Not Used ~5a, ~5c 2 Inputs ~5 2 Outputs
~6 Solid-State ~6 Solid-State ~6a, ~6c 2 Inputs ~6 2 Outputs
~7Not Used ~7 Not Used ~7a, ~7c 2 Inputs ~72 Outputs
~8 Solid-State ~8 Solid-State ~8a, ~8c 2 Inputs ~8Not Used
OUTPUT TERMINAL
ASSIGNMENT
OUTPUT TERMINAL
ASSIGNMENT
OUTPUT TERMINAL
ASSIGNMENT
OUTPUT
GE Multilin F35 Multiple Feeder Protection System 3-17
3
3.2 WIRING 3 HARDWARE
Figure 3–17: CONTACT INPUT AND OUTPUT MODULE WIRING (1 of 2)
3-18 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
DIGITAL I/O
6K
1b
2b
3b
4b
5b
7b
6b
8b
1a
2a
3a
4a
5a
7a
6a
8a
1c
2c
3c
4c
5c
7c
6c
8c
1
5
7
2
6
8
3
4
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
I
V
I
V
I
V
I
V
DIGITAL I/O
6P
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
DIGITAL I/O
6U
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
DIGITAL I/O
6M
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
DIGITAL I/O
6S
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
I
V
I
V
DIGITAL I/O
6N
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
DIGITAL I/O
6T
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
DIGITAL I/O
6L
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
DIGITAL I/O
6R
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
842763A2.CDR
NOTICE
3
Figure 3–18: CONTACT INPUT AND OUTPUT MODULE WIRING (2 of 2)
Observe correct polarity for all contact input and solid state output connections for proper functional­ity.
GE Multilin F35 Multiple Feeder Protection System 3-19
3.2 WIRING 3 HARDWARE
827741A4.CDR
CRITICAL
FAILURE
1bB B B B B B B B B B
1a
2b
3a -
3b +
-
5b HI+
6b LO+
6a
8a
8b
48 VDC
OUTPUT
CONTROL
POWER
SURGE
FILTER
POWER SUPPLY 1
24-250V
(Wet)(Dry)
7a
DIGITAL I/O 6B
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~7c
8a
8c
7b
+
-
8b
+ +
+
CONTACT IN 7a
CONTACT IN 7c
CONTACT IN 8a
CONTACT IN 8c
COMMON 7b
SURGE
7a
DIGITAL I/O 6B
7c 8a 8c 7b
+
-
8b
+ +
+
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
NOTE
NOTE
CONTACT INPUTS:
A dry contact has one side connected to terminal B3b. This is the positive 48 V DC voltage rail supplied by the power sup­ply module. The other side of the dry contact is connected to the required contact input terminal. Each contact input group has its own common (negative) terminal which must be connected to the DC negative terminal (B3a) of the power supply module. When a dry contact closes, a current of 1 to 3 mA will flow through the associated circuit.
A wet contact has one side connected to the positive terminal of an external DC power supply. The other side of this contact is connected to the required contact input terminal. If a wet contact is used, then the negative side of the external source must be connected to the relay common (negative) terminal of each contact group. The maximum external source voltage for this arrangement is 300 V DC.
The voltage threshold at which each group of four contact inputs will detect a closed contact input is programmable as 17 V DC for 24 V sources, 33 V DC for 48 V sources, 84 V DC for 110 to 125 V sources, and 166 V DC for 250 V sources.
3
Figure 3–19: DRY AND WET CONTACT INPUT CONNECTIONS
Wherever a tilde “~” symbol appears, substitute with the slot position of the module.
Contact outputs may be ordered as form-a or form-C. The form-A contacts may be connected for external circuit supervi­sion. These contacts are provided with voltage and current monitoring circuits used to detect the loss of DC voltage in the circuit, and the presence of DC current flowing through the contacts when the form-A contact closes. If enabled, the current monitoring can be used as a seal-in signal to ensure that the form-A contact does not attempt to break the energized induc­tive coil circuit and weld the output contacts.
GENERAL APPLICATION CONSIDERATIONS:
There is no provision in the relay to detect a DC ground fault on 48 V DC control power external output. We recom­mend using an external DC supply.
Contacts outputs of protective relays, auxiliary contacts from breakers, disconnectors and other devices, are generally con­nected to contacts inputs of protective relays. In some situations, the contact outputs of some protective relays can have high impedance connected across it. When such a contact output is connected across a F35 contact input, it can spuriously operate the F35 input even when the output is open, if there is a substantial distributed capacitance (represented by C1) present in the wiring between the output and the F35 input and the debounce time setting in the F35 relay is low enough. This false assertion of the contact input, when there is inadvertent ground present at the DC positive terminal, can be pre­vented by inserting a resistor across the F35 input.
3-20 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
The following figure shows a typical DC circuit, with battery ground detection, of contact input. The contact output has par­allel impedance across it (represented by R1).
Figure 3–20: TYPICAL CONTACT INPUT DC CIRCUIT
The presence of the impedance path (R1) across the contact output allows the stray (distributed) capacitance C1 to charge as shown, thus developing a voltage across the contact input enough to momentarily operate the input while the capaci­tance discharges in the presence of DC ground on the positive terminal of the battery.
The duration of the discharge depends on the value of the distributed capacitance, the initial voltage of the distributed capacitance, and the input impedance of the contact input. If the duration is greater than the debounce time setting, then the contact input operates.
The application example that follows describes how to mitigate this problem by connecting a resistor across the contact input, as shown in the next figure, or by adjusting the debounce time setting to a value greater than the discharge time to prevent spurious operation of the contact input only if the voltage (with output open) across the contact input due to trickle current is less than the threshold voltage. This operation of contact inputs also can be prevented by using the Auto-Burnish contact inputs or contact inputs with active impedance.
3
Figure 3–21: CONTACT INPUT CONNECTED TO A CONTACT OUTPUT WITH RESISTOR (R2) ACROSS THE INPUT
GE Multilin F35 Multiple Feeder Protection System 3-21
3.2 WIRING 3 HARDWARE
APPLICATION EXAMPLE:
This example is for illustrative purposes only and the calculations present the worst-case scenario. In practice, the value of debounce time can be lower.
Contact input ON state impedance used in the calculation of the discharge period is based on the following table.
Table 3–3: DISCHARGE PERIOD
BATTERY VOLTAGE (V) INPUT IMPEDANCE (KΩ)
130 50
250 97
Debounce time setting = 2 ms
Assume a stray capacitance of 0.1 μF.
3
Assume an initial voltage across the stray capacitance "Vinitial" = 19 V (Vthreshold - 65 V), where Vthreshold = 84 V. The initial voltage Vinitial depends on values of impedance of R1 and contact inputs when the contact input is OFF (non-acti­vated state).
Therefore, discharge time constant (τ) =50 k *0.1 μF = 5 ms.
Discharge period t is calculated from the following equation:
Vthreshold = (Vbatt - VInitial) *e^ (-t/τ)
84 = -149 *e^ (t/0.005) (EQ 3.1)
T = -0.005 * ln (84/149) = 0.0029 s
Therefore, in this example the contact inputs operate.
To prevent this operation, the debounce time must be increased to 4 ms (set debounce time as per the following table) or insert a resistor less than or equal to "R" as calculated later.
Table 3–4: TYPICAL DEBOUNCE TIME SETTING
STRAY CAPACITANCE (μF) BATTERY VOLTAGE (V) DEBOUNCE TIME (MS)
0.05 130 2
0.1 130 4
0.2 130 6
0.05 250 3
0.1 250 6
0.2 250 11
The value of this resistor "R" is calculated as follows:
1. Determine the minimum voltage (V threshold) required to turn on the input. This is determined by direct measurement or referenced in the input specifications.
2. Calculate the resistance necessary to limit the voltage to 1/3 V threshold (when the contact is OFF, the non-activated state) as follows:
R = (Vthreshold / 3) / (2 mA) (EQ 3.2)
The 2 mA current is used in case the contact input is connected across the GE Form A contact output with voltage monitoring. Otherwise use the amperage of the active circuit connected to the contact input when its contact output is open and the voltage across the contact input is third trigger threshold to calculate the resistor value.
3. When the contact is ON (operate state), the battery voltage appears across the resistor. The wattage rating of the resistor is then:
PR = 1.3 * (Vbatt) ^2 / R Watts (EQ 3.3)
4. Applying the following equation to our example:
R = 84 V / 3*(1 / 2 mA) = 14 k
PR = 1.57 Watts (EQ 3.4)
3-22 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
842749A1.CDR
50 to 70 mA
3 mA
25 to 50 ms
current
time
5. Calculating the voltage across the contact input with the Burden Resistor, Voltage across the contact Input:
Vresistor = 2 mA * 14 Kohm = 28 V
Vresistor < contact input threshold (84 V) (EQ 3.5)
In conclusion, in this example, the contact input does NOT operate falsely with the Burden Resistor across its input AND when a battery ground is present.
USE OF CONTACT INPUTS WITH AUTO-BURNISHING:
The contact inputs sense a change of the state of the external device contact based on the measured current. When exter­nal devices are located in a harsh industrial environment (either outdoor or indoor), their contacts can be exposed to vari­ous types of contamination. Normally, there is a thin film of insulating sulfidation, oxidation, or contaminates on the surface of the contacts, sometimes making it difficult or impossible to detect a change of the state. This film must be removed to establish circuit continuity – an impulse of higher than normal current can accomplish this.
The contact inputs with auto-burnish create a high current impulse when the threshold is reached to burn off this oxidation layer as a maintenance to the contacts. Afterwards the contact input current is reduced to a steady-state current. The impulse will have a 5 second delay after a contact input changes state.
3
Figure 3–22: CURRENT THROUGH CONTACT INPUTS WITH AUTO-BURNISHING
Regular contact inputs limit current to less than 3 mA to reduce station battery burden. In contrast, contact inputs with auto­burnishing allow currents up to 50 to 70 mA at the first instance when the change of state was sensed. Then, within 25 to 50 ms, this current is slowly reduced to 3 mA as indicated above. The 50 to 70 mA peak current burns any film on the con­tacts, allowing for proper sensing of state changes. If the external device contact is bouncing, the auto-burnishing starts when external device contact bouncing is over.
Another important difference between the auto-burnishing input module and the regular input modules is that only two con­tact inputs have common ground, as opposed to four contact inputs sharing one common ground (refer to the Contact Input and Output Module Wiring diagrams). This is beneficial when connecting contact inputs to separate voltage sources. Con­sequently, the threshold voltage setting is also defined per group of two contact inputs.
GE Multilin F35 Multiple Feeder Protection System 3-23
3.2 WIRING 3 HARDWARE
CONTACT INPUT 1 AUTO-BURNISH = OFF
= OFFCONTACT INPUT 2 AUTO-BURNISH
CONTACT INPUT 1 AUTO-BURNISH CONTACT INPUT 2 AUTO-BURNISH
= ON = OFF
CONTACT INPUT 1 AUTO-BURNISH CONTACT INPUT 2 AUTO-BURNISH
= OFF = ON
CONTACT INPUT 1 AUTO-BURNISH CONTACT INPUT 2 AUTO-BURNISH
= ON = ON
842751A1.CDR
NOTE
The auto-burnish feature can be disabled or enabled using the DIP switches found on each daughter card. There is a DIP switch for each contact, for a total of 16 inputs.
3
Figure 3–23: AUTO-BURNISH DIP SWITCHES
The auto-burnish circuitry has an internal fuse for safety purposes. During regular maintenance, the auto-burnish functionality can be checked using an oscilloscope.
USE OF CONTACT INPUTS WITH ACTIVE IMPEDANCE:
Contact inputs susceptible to parasitic capacitance caused by long cable runs affected by switching surges from external circuits can result in inadvertent activation of contact inputs with the external contact open. In this case, GE recommends using the digital I/O module with active impedance circuit.
Active impedance contact input can tolerate external cable capacitance of up to 0.2 µF, without entering the ON state for more than 2 ms. The contact input debounce time can still be set above 2 ms for added security to prevent contact input activations cause by external transient ON states.
An active impedance contact input is normally in Low impedance mode during OFF contact state (non-activated condition). During Low impedance state contact input impedance is maintained at 10 K Ohms impedance to allow fast discharge of the stray capacitance of the long cables.
When the contact input voltage exceeds the set threshold, active impedance maintains 10 K Ohms impedance value. If voltage starts rapidly decreasing, this indicates that stray capacitance is being discharged through the contact input. If, however, voltage stabilizes above the set threshold, the input impedance is switched to High impedance mode of 100 K Ohms. This value reduces the input current to <3 mA, and contact input switched to the ON state (operated state).
The figure shows the active impedance contact input V-I characteristic. Different thresholds with their corresponding char­acteristics are shown by color. The contact input is in the ON (operated) state if the input voltage is to the right of the col­ored threshold band (+/-10% tolerance), and the contact input is in the OFF (non-activated) state when input voltage is to the left of the band. A contact input is in LOW state during non-operated system condition, and actively switches to HIGH state upon detection of input voltage above the settable threshold.
3-24 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
3
Figure 3–24: ACTIVE IMPEDANCE CONTACT INPUT V-I CHARACTERISTIC
GE Multilin F35 Multiple Feeder Protection System 3-25
3.2 WIRING 3 HARDWARE
NOTE

3.2.7 TRANSDUCER INPUTS/OUTPUTS

Transducer input modules can receive input signals from external dcmA output transducers (dcmA In) or resistance tem­perature detectors (RTD). Hardware and software is provided to receive signals from these external transducers and con­vert these signals into a digital format for use as required.
Transducer output modules provide DC current outputs in several standard dcmA ranges. Software is provided to configure virtually any analog quantity used in the relay to drive the analog outputs.
Every transducer input/output module has a total of 24 terminal connections. These connections are arranged as three ter­minals per row with a total of eight rows. A given row may be used for either inputs or outputs, with terminals in column "a" having positive polarity and terminals in column "c" having negative polarity. Since an entire row is used for a single input/ output channel, the name of the channel is assigned using the module slot position and row number.
Each module also requires that a connection from an external ground bus be made to terminal 8b. The current outputs require a twisted-pair shielded cable, where the shield is grounded at one end only. The figure below illustrates the trans-
3
ducer module types (5A, 5C, 5D, 5E, and 5F) and channel arrangements that may be ordered for the relay.
Wherever a tilde “~” symbol appears, substitute with the slot position of the module.
Figure 3–25: TRANSDUCER INPUT/OUTPUT MODULE WIRING
3-26 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
NOTE
NOTE
NOTE

3.2.8 RS232 FACEPLATE PORT

A 9-pin RS232C serial port is located on the F35 faceplate for programming with a personal computer. All that is required to use this interface is a personal computer running the EnerVista UR Setup software provided with the relay. Cabling for the RS232 port is shown in the following figure for both 9-pin and 25-pin connectors.
The baud rate for this port is fixed at 19200 bps.
3
Figure 3–26: RS232 FACEPLATE PORT CONNECTION

3.2.9 CPU COMMUNICATION PORTS

a) OPTIONS
In addition to the faceplate RS232 port, the F35 provides two additional communication ports or a managed six-port Ether­net switch, depending on the installed CPU module.
The CPU modules do not require a surge ground connection.
Modules 9G, 9H, 9L, and 9M are no longer available.
Table 3–5: CPU MODULE COMMUNICATIONS
CPU TYPE COM1 COM2
9E RS485 RS485
9G 10Base-F or 10Base-T RS485
9H Redundant 10Base-F or 10Base-T RS485
9J 100Base-FX or 10/100Base-T RS485
9K Redundant 100Base-FX or 10/100Base-T RS485
9L 100Base-FX RS485
9M Redundant 100Base-FX RS485
9N 10/100Base-T RS485
9S Six-port managed Ethernet switch RS485
For the 9G/9H CPU, the 10Base-T port can only be used when the CH1 10Base-F fiber has been removed. The 10Base-T Ethernet cable and the CH1 10Base-F fiber cable cannot both be installed at the same time.
For the 9J/9K CPU, the 10/100Base-T port has the lowest priority and is only active if both CH1 and CH2 fiber links are down. Installation of the 10/100Base-T Ethernet cable at the same time as the CH1 and/or CH2 100Base-F fiber cables does not affect the communication over the CH1 or CH2 fiber ports.
GE Multilin F35 Multiple Feeder Protection System 3-27
3
NORMAL
ALTERNATE
COM1
10Base-FL
10Base-F
10Base-T
Tx1
Rx1
Tx2
Rx2
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B
input
CPU 9H
Co-axial cable
Co-axial cable
Shielded twisted-pairs
MM fiber
optic cable
Ground at
remote device
RS485
COM2
100Base-FL
COMMON
+
+ —
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B
input
CPU
RS485 COM2
9L
COM1NORMAL
Co-axial cable
Co-axial cable
SM fiber
optic cable
Ground at
remote device
NORMAL
ALTERNATE
COM1
100Base-FL
100Base-F
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B input
CPU 9M
Co-axial cable
Co-axial cable
Shielded twisted-pairs
SM fiber optic cable
Ground at
remote
device
RS485 COM2
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B
input
CPU 9E
RS485
COM2
COMMON
+
D1b D2b D3b
RS485
COM1
Ground at
remote device
Co-axial cable
Co-axial cable
Shielded twisted-pairs
NORMAL
COM1
10Base-FL
10Base-T
Tx1
Rx1
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B
input
CPU 9G
RS485
COM2
Shielded twisted-pairs
Co-axial cable
Co-axial cable
MM fiber
optic cable
Ground at
remote
device
842765A7b.CDR
CPU 9S
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B
input
Co-axial cable
Co-axial cable
Shielded twisted-pairs
Ground at
remote
device
RS485 COM2
Ground at
remote
device
NORMAL
10/100Base-T
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B input
CPU
Co-axial cable
Co-axial cable
Shielded twisted-pairs
RS485 COM2
COM1
9N
100Base-FL
Tx1
Rx1
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B
input
CPU
RS485
COM2
9J
COM1NORMAL
Co-axial cable
Co-axial cable
MM fiber
optic cable
Ground at
remote
device
10Base-T
NORMAL
ALTERNATE
COM1
100Base-FL
100Base-F
Tx1
Rx1
Tx2
Rx2
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
BNC
IRIG-B output
IRIG-B
input
CPU
9K
Co-axial cable
Co-axial cable
Shielded twisted-pairs
MM fiber optic cable
Ground at
remote
device
RS485
COM2
10Base-T
3.2 WIRING 3 HARDWARE
Figure 3–27: CPU MODULE COMMUNICATIONS WIRING
b) RS485 PORTS
RS485 data transmission and reception are accomplished over a single twisted pair with transmit and receive data alternat­ing over the same two wires. Through the use of these ports, continuous monitoring and control from a remote computer, SCADA system or PLC is possible.
To minimize errors from noise, the use of shielded twisted pair wire is recommended. Correct polarity must also be observed. For instance, the relays must be connected with all RS485 “+” terminals connected together, and all RS485 “–” terminals connected together. Though data is transmitted over a two-wire twisted pair, all RS485 devices require a shared
3-28 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
NOTICE
reference, or common voltage. This common voltage is implied to be a power supply common. Some systems allow the shield (drain wire) to be used as common wire and to connect directly to the F35 COM terminal (#3); others function cor­rectly only if the common wire is connected to the F35 COM terminal, but insulated from the shield.
To avoid loop currents, the shield should be grounded at only one point. If other system considerations require the shield to be grounded at more than one point, install resistors (typically 100 ohms) between the shield and ground at each grounding point. Each relay should also be daisy-chained to the next one in the link. A maximum of 32 relays can be connected in this manner without exceeding driver capability. For larger systems, additional serial channels must be added. It is also possible to use commercially available repeaters to have more than 32 relays on a single channel. Star or stub connections should be avoided entirely.
Lightning strikes and ground surge currents can cause large momentary voltage differences between remote ends of the communication link. For this reason, surge protection devices are internally provided at both communication ports. An iso­lated power supply with an optocoupled data interface also acts to reduce noise coupling. To ensure maximum reliability, all equipment should have similar transient protection devices installed.
Both ends of the RS485 circuit should also be terminated with an impedance as shown below.
3
Figure 3–28: RS485 SERIAL CONNECTION
c) 10BASE-FL AND 100BASE-FX FIBER OPTIC PORTS
Ensure that the dust covers are installed when the fiber is not in use. Dirty or scratched connectors can lead to high losses on a fiber link.
GE Multilin F35 Multiple Feeder Protection System 3-29
3.2 WIRING 3 HARDWARE
The fiber optic communication ports allow for fast and efficient communications between relays at 10 Mbps or 100 Mbps. Optical fiber may be connected to the relay supporting a wavelength of 820 nm in multi-mode or 1310 nm in multi-mode and single-mode. The 10 Mbps rate is available for CPU modules 9G and 9H; 100Mbps is available for modules 9H, 9J, 9K, 9L, 9M, and 9N. The 9H, 9K, and 9M modules have a second pair of identical optical fiber transmitter and receiver for redundancy.
The optical fiber sizes supported include 50/125 µm, 62.5/125 µm and 100/140 µm for 10 Mbps. The fiber optic port is designed such that the response times will not vary for any core that is 100 µm or less in diameter, 62.5 µm for 100 Mbps. For optical power budgeting, splices are required every 1 km for the transmitter/receiver pair. When splicing optical fibers, the diameter and numerical aperture of each fiber must be the same. In order to engage or disengage the ST type connec­tor, only a quarter turn of the coupling is required.
3
3-30 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.2 WIRING
RELAY
BNC (IN)
RECEIVER
RG58/59 COAXIAL CABLE
GPS SATELLITE SYSTEM
GPS CONNECTION OPTIONAL
IRIG-B(-)
4A
+
-
827756A5.CDR
IRIG-B
TIME CODE
GENERATOR
(DC SHIFT OR
AMPLITUDE MODULATED
SIGNAL CAN BE USED)
4B
IRIG-B(+)
BNC (OUT)
REPEATER
TO OTHER DEVICES
(DC-SHIFT ONLY)
NOTE

3.2.10 IRIG-B

IRIG-B is a standard time code format that allows stamping of events to be synchronized among connected devices within 1 millisecond. The IRIG time code formats are serial, width-modulated codes which can be either DC level shifted or ampli­tude modulated (AM). Third party equipment is available for generating the IRIG-B signal; this equipment may use a GPS satellite system to obtain the time reference so that devices at different geographic locations can also be synchronized.
3
Figure 3–29: IRIG-B CONNECTION
The IRIG-B repeater provides an amplified DC-shift IRIG-B signal to other equipment. By using one IRIG-B serial connec­tion, several UR-series relays can be synchronized. The IRIG-B repeater has a bypass function to maintain the time signal even when a relay in the series is powered down.
Figure 3–30: IRIG-B REPEATER
Using an amplitude modulated receiver will cause errors up to 1 ms in event time-stamping.
GE Multilin F35 Multiple Feeder Protection System 3-31
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
842006A1.CDR
Tx
Tx
Tx
Tx
UR #1
UR #2
UR #3
UR #4
Rx
Rx
Rx
Rx

3.3DIRECT INPUT/OUTPUT COMMUNICATIONS 3.3.1 DESCRIPTION

The F35 direct inputs and outputs feature makes use of the type 7 series of communications modules. These modules are also used by the L90 Line Differential Relay for inter-relay communications. The direct input and output feature uses the communications channels provided by these modules to exchange digital state information between relays. This feature is available on all UR-series relay models except for the L90 Line Differential relay.
The communications channels are normally connected in a ring configuration as shown below. The transmitter of one mod­ule is connected to the receiver of the next module. The transmitter of this second module is then connected to the receiver of the next module in the ring. This is continued to form a communications ring. The figure below illustrates a ring of four UR-series relays with the following connections: UR1-Tx to UR2-Rx, UR2-Tx to UR3-Rx, UR3-Tx to UR4-Rx, and UR4-Tx to UR1-Rx. A maximum of 16 URs can be connected in a single ring
3
Figure 3–31: DIRECT INPUT AND OUTPUT SINGLE CHANNEL CONNECTION
IRC modules with protocol C37.94 and G.703 are designed for back-to-back communication connections, so the ring con­figuration shown in the previous figure does not apply. To establish inter-relay communication in more than two URs, you need to have two channel IRC module and enable DIRECT I/O CHANNEL CROSSOVER function in all relays, as shown in the next figure. This configuration can be expanded to 16 URs, and this configuration does not provide redundancy ring since both channels are made into single ring by the channel crossover function. As per the figure Typical Pin Interconnec­tion between Two G.703 Interfaces later in this chapter, the clock is supplied typically by multiplexer (MUX) and all URs are in Loop Timing Mode. If there is no MUX, then UR1 and UR3 can be in Internal Timing Mode and UR2 and UR4 can be in Loop Timing Mode. That is, connected channels must have opposite timing modes.
Figure 3–32: RING CONFIGURATION FOR C37.94 MODULE (CONCEPT ALSO APPLIES TO G.703)
3-32 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
842007A1.CDR
Tx1
UR #1
UR #2
UR #3
UR #4
Tx1
Tx1
Tx1
Tx2
Tx2
Tx2
Tx2
Rx1
Rx1
Rx1
Rx1
Rx2
Rx2
Rx2
Rx2
842013A1.CDR
Tx
Tx
UR #1
Channel #1
Channel #2
UR #2
UR #3
Rx
Rx
Tx1
Tx2
Rx1
Rx2
NOTE
The interconnection for dual-channel Type 7 communications modules is shown below. Two channel modules allow for a redundant ring configuration. That is, two rings can be created to provide an additional independent data path. The required connections are: UR1-Tx1 to UR2-Rx1, UR2-Tx1 to UR3-Rx1, UR3-Tx1 to UR4-Rx1, and UR4-Tx1 to UR1-Rx1 for the first ring; and UR1-Tx2 to UR4-Rx2, UR4-Tx2 to UR3-Rx2, UR3-Tx2 to UR2-Rx2, and UR2-Tx2 to UR1-Rx2 for the second ring.
3
Figure 3–33: DIRECT INPUT AND OUTPUT DUAL CHANNEL CONNECTION
The following diagram shows the connection for three UR-series relays using two independent communication channels. UR1 and UR3 have single type 7 communication modules; UR2 has a dual-channel module. The two communication chan­nels can be of different types, depending on the Type 7 modules used. To allow the direct input and output data to cross- over from channel 1 to channel 2 on UR2, the
DIRECT I/O CHANNEL CROSSOVER setting should be “Enabled” on UR2. This
forces UR2 to forward messages received on Rx1 out Tx2, and messages received on Rx2 out Tx1.
The interconnection requirements are described in further detail in this section for each specific variation of type 7 commu­nications module. These modules are listed in the following table. All fiber modules use ST type connectors.
GE Multilin F35 Multiple Feeder Protection System 3-33
Figure 3–34: DIRECT INPUT AND OUTPUT SINGLE/DUAL CHANNEL COMBINATION CONNECTION
Not all the direct input and output communications modules may be applicable to the F35 relay. Only the modules specified in the order codes are available as direct input and output communications modules.
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
CAUTION
Table 3–6: CHANNEL COMMUNICATION OPTIONS
MODULE SPECIFICATION
2A C37.94SM, 1300 nm, single-mode, ELED, 1 channel single-mode
2B C37.94SM, 1300 nm, single-mode, ELED, 2 channel single-mode
2E Bi-phase, 1 channel
2F Bi-phase, 2 channel
2G IEEE C37.94, 820 nm, 128 kbps, multi-mode, LED, 1 channel
2H IEEE C37.94, 820 nm, 128 kbps, multi-mode, LED, 2 channels
2S Six-port managed Ethernet switch with high voltage power supply
2T Six-port managed Ethernet switch with low voltage power supply
72 1550 nm, single-mode, laser, 1 channel
3
73 1550 nm, single-mode, laser, 2 channels
74 Channel 1 - RS422; channel 2 - 1550 nm, single-mode, laser
75 Channel 1 - G.703; channel 2 - 1550 nm, single-mode, laser
76 IEEE C37.94, 820 nm, 64 kbps, multi-mode, LED, 1 channel
77 IEEE C37.94, 820 nm, 64 kbps, multi-mode, LED, 2 channels
7A 820 nm, multi-mode, LED, 1 channel
7B 1300 nm, multi-mode, LED, 1 channel
7C 1300 nm, single-mode, ELED, 1 channel
7D 1300 nm, single-mode, laser, 1 channel
7E Channel 1: G.703, Channel 2: 820 nm, multi-mode
7F Channel 1: G.703, Channel 2: 1300 nm, multi-mode
7G Channel 1: G.703, Channel 2: 1300 nm, single-mode ELED
7H 820 nm, multi-mode, LED, 2 channels
7I 1300 nm, multi-mode, LED, 2 channels
7J 1300 nm, single-mode, ELED, 2 channels
7K 1300 nm, single-mode, LASER, 2 channels
7L Channel 1: RS422, channel: 820 nm, multi-mode, LED
7M Channel 1: RS422, channel 2: 1300 nm, multi-mode, LED
7N Channel 1: RS422, channel 2: 1300 nm, single-mode, ELED
7P Channel 1: RS422, channel 2: 1300 nm, single-mode, laser
7Q Channel 1: G.703, channel 2: 1300 nm, single-mode, laser
7R G.703, 1 channel
7S G.703, 2 channels
7T RS422, 1 channel
7V RS422, 2 channels, 2 clock inputs
7W RS422, 2 channels
3-34 F35 Multiple Feeder Protection System GE Multilin
Observing any fiber transmitter output can cause eye injury.
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
Module: 7A / 7B / 7C 7H / 7I / 7J
Connection Location: Slot X Slot X
1 Channel 2 Channels
RX1 RX1
RX2
TX1 TX1
TX2
831719A2.CDR
Module:
Connection Location:
73/ 7K Slot X
72/ 7D Slot X
1 Channel 2 Channels
RX1 RX1
RX2
TX1 TX1
TX2
831720A3.CDR
CAUTION
NOTICE

3.3.2 FIBER: LED AND ELED TRANSMITTERS

The following figure shows the configuration for the 7A, 7B, 7C, 7H, 7I, and 7J fiber-only modules.
Figure 3–35: LED AND ELED FIBER MODULES

3.3.3 FIBER-LASER TRANSMITTERS

The following figure shows the configuration for the 72, 73, 7D, and 7K fiber-laser module.
3
GE Multilin F35 Multiple Feeder Protection System 3-35
Figure 3–36: LASER FIBER MODULES
When using a laser Interface, attenuators may be necessary to ensure that you do not exceed the maximum optical input power to the receiver.
When using a laser Interface, attenuators may be necessary to ensure that you do not exceed the maximum optical input power to the receiver.
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
NOTE
842773A2.CDR
X X X X X X X X X X X X
8a 8b
7S
Rx +
Tx +
Shield
Tx –
Shield
Rx –
Tx –
Rx +
Tx +
Rx –
Inter-relay communications
2b
6a
7a
1b
1a
3a
6b
7b
2a
3b
G.703
channel 2
G.703
channel 1
Surge
Surge
831727A3.CDR
X X X X X X X X X X X X
8a 8b
7S
Rx +
Tx +
Shld.
Tx -
Shld.
Rx -
Tx -
Rx +
Tx +
Rx -
COMM.
2b
6a
7a
1b
1a
3a
6b
7b
2a
3b
G.703
CHANNEL 2
G.703
CHANNEL 1
SURGE
SURGE
X X X X X X X X X X X X
8a 8b
7S
Rx +
Tx +
Shld.
Tx -
Shld.
Rx -
Tx -
Rx +
Tx +
Rx -
COMM.
2b
6a
7a
1b
1a
3a
6b
7b
2a
3b
G.703
CHANNEL 2
G.703
CHANNEL 1
SURGE
SURGE
NOTE

3.3.4 G.703 INTERFACE

a) DESCRIPTION
The following figure shows the 64K ITU G.703 co-directional interface configuration.
The G.703 module is fixed at 64 kbps. The
SETTINGS PRODUCT SETUP  DIRECT I/O  DIRECT I/O DATA RATE
setting is not applicable to this module.
AWG 24 twisted shielded pair is recommended for external connections, with the shield grounded only at one end. Con­necting the shield to pin X1a or X6a grounds the shield since these pins are internally connected to ground. Thus, if pin X1a or X6a is used, do not ground at the other end. This interface module is protected by surge suppression devices.
3
Figure 3–37: G.703 INTERFACE CONFIGURATION
The following figure shows the typical pin interconnection between two G.703 interfaces. For the actual physical arrange­ment of these pins, see the Rear terminal assignments section earlier in this chapter. All pin interconnections are to be maintained for a connection to a multiplexer.
Figure 3–38: TYPICAL PIN INTERCONNECTION BETWEEN TWO G.703 INTERFACES
Pin nomenclature may differ from one manufacturer to another. Therefore, it is not uncommon to see pinouts num­bered TxA, TxB, RxA and RxB. In such cases, it can be assumed that “A” is equivalent to “+” and “B” is equivalent to “–”.
b) G.703 SELECTION SWITCH PROCEDURES
1. Remove the G.703 module (7R or 7S). The ejector/inserter clips located at the top and at the bottom of each module, must be pulled simultaneously in order to release the module for removal. Before performing this action, control power must be removed from the relay. The original location of the module should be recorded to help ensure that the same or replacement module is inserted into the correct slot.
2. Remove the module cover screw.
3. Remove the top cover by sliding it towards the rear and then lift it upwards.
4. Set the timing selection switches (channel 1, channel 2) to the desired timing modes.
5. Replace the top cover and the cover screw.
3-36 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
6. Re-insert the G.703 module. Take care to ensure that the correct module type is inserted into the correct slot position.
The ejector/inserter clips located at the top and at the bottom of each module must be in the disengaged position as the module is smoothly inserted into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module will be fully inserted.
3
Figure 3–39: G.703 TIMING SELECTION SWITCH SETTING
Table 3–7: G.703 TIMING SELECTIONS
SWITCHES FUNCTION
S1 OFF octet timing disabled
S5 and S6 S5 = OFF and S6 = OFF loop timing mode
c) G.703 OCTET TIMING
If octet timing is enabled (on), this 8 kHz signal will be asserted during the violation of bit 8 (LSB) necessary for connecting to higher order systems. When F35s are connected back to back, octet timing should be disabled (off).
d) G.703 TIMING MODES
There are two timing modes for the G.703 module: internal timing mode and loop timing mode (default).
Internal Timing Mode: The system clock is generated internally. Therefore, the G.703 timing selection should be in
the internal timing mode for back-to-back (UR-to-UR) connections. For back-to-back connections, set for octet timing (S1 = OFF) and timing mode to internal timing (S5 = ON and S6 = OFF).
Loop Timing Mode: The system clock is derived from the received line signal. Therefore, the G.703 timing selection
should be in loop timing mode for connections to higher order systems. For connection to a higher order system (UR­to-multiplexer, factory defaults), set to octet timing (S1 = ON) and set timing mode to loop timing (S5 = OFF and S6 = OFF).
ON octet timing 8 kHz
S5 = ON and S6 = OFF internal timing mode S5 = OFF and S6 = ON → minimum remote loopback mode S5 = ON and S6 = ON dual loopback mode
GE Multilin F35 Multiple Feeder Protection System 3-37
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
842752A1.CDR
DMR
DMX
G7X
G7R
DMR = Differential Manchester Receiver DMX = Differential Manchester Transmitter G7X = G.703 Transmitter G7R = G.703 Receiver
842774A1.CDR
DMR
DMX
G7X
G7R
DMR = Differential Manchester Receiver DMX = Differential Manchester Transmitter G7X = G.703 Transmitter G7R = G.703 Receiver
842775A1.CDR
The switch settings for the internal and loop timing modes are shown below:
e) G.703 TEST MODES
In minimum remote loopback mode, the multiplexer is enabled to return the data from the external interface without any
3
processing to assist in diagnosing G.703 line-side problems irrespective of clock rate. Data enters from the G.703 inputs, passes through the data stabilization latch which also restores the proper signal polarity, passes through the multiplexer and then returns to the transmitter. The differential received data is processed and passed to the G.703 transmitter module after which point the data is discarded. The G.703 receiver module is fully functional and continues to process data and passes it to the differential Manchester transmitter module. Since timing is returned as it is received, the timing source is expected to be from the G.703 line side of the interface.
Figure 3–40: G.703 MINIMUM REMOTE LOOPBACK MODE
In dual loopback mode, the multiplexers are active and the functions of the circuit are divided into two with each receiver/ transmitter pair linked together to deconstruct and then reconstruct their respective signals. Differential Manchester data enters the Differential Manchester receiver module and then is returned to the differential Manchester transmitter module. Likewise, G.703 data enters the G.703 receiver module and is passed through to the G.703 transmitter module to be returned as G.703 data. Because of the complete split in the communications path and because, in each case, the clocks are extracted and reconstructed with the outgoing data, in this mode there must be two independent sources of timing. One source lies on the G.703 line side of the interface while the other lies on the differential Manchester side of the interface.
Figure 3–41: G.703 DUAL LOOPBACK MODE
3-38 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
~
~
~
~
~
~
~
~
~
~
~
~
~
~
Shield
Shield
COM
Tx +
Tx +
Tx –
Tx –
Rx –
Rx –
Rx +
Rx +
3b
5b
2a
4a
6a
7b
8b
Clock
RS422
channel 1
RS422
channel 2
Surge
3a
5a
4b
6b
7a
2b 8a
Inter-relay communications 7W
842776A3.CDR
Dual-channel RS422 module
~
~
~
~
~
Shield
Tx +
Tx –
Rx –
Rx +
3b
2a
6a
RS422
3a
4b
~
~
~
~
COM
8b
Clock
Surge
7a
2b 8a
Inter-relay comms. 7T
Single-channel RS422 module
~ indicates the slot position

3.3.5 RS422 INTERFACE

a) DESCRIPTION
There are two RS422 inter-relay communications modules available: single-channel RS422 (module 7T) and dual-channel RS422 (module 7W). The modules can be configured to run at 64 kbps or 128 kbps. AWG 24 twisted shielded pair cable is recommended for external connections. These modules are protected by optically-isolated surge suppression devices.
The shield pins (6a and 7b) are internally connected to the ground pin (8a). Proper shield termination is as follows:
Site 1: Terminate shield to pins 6a or 7b or both.
Site 2: Terminate shield to COM pin 2b.
The clock terminating impedance should match the impedance of the line.
3
The following figure shows the typical pin interconnection between two single-channel RS422 interfaces installed in slot W. All pin interconnections are to be maintained for a connection to a multiplexer.
b) TWO-CHANNEL APPLICATION VIA MULTIPLEXERS
The RS422 interface may be used for single channel or two channel applications over SONET/SDH or multiplexed sys­tems. When used in single-channel applications, the RS422 interface links to higher order systems in a typical fashion observing transmit (Tx), receive (Rx), and send timing (ST) connections. However, when used in two-channel applications, certain criteria must be followed since there is one clock input for the two RS422 channels. The system will function cor­rectly if the following connections are observed and your data module has a terminal timing feature. Terminal timing is a common feature to most synchronous data units that allows the module to accept timing from an external source. Using the terminal timing feature, two channel applications can be achieved if these connections are followed: The send timing out­puts from the multiplexer (data module 1), will connect to the clock inputs of the UR–RS422 interface in the usual fashion. In addition, the send timing outputs of data module 1 will also be paralleled to the terminal timing inputs of data module 2. By using this configuration, the timing for both data modules and both UR–RS422 channels will be derived from a single clock source. As a result, data sampling for both of the UR–RS422 channels will be synchronized via the send timing leads on data module 1 as shown below. If the terminal timing feature is not available or this type of connection is not desired, the G.703 interface is a viable option that does not impose timing restrictions.
GE Multilin F35 Multiple Feeder Protection System 3-39
Figure 3–42: RS422 INTERFACE CONNECTIONS
Figure 3–43: TYPICAL PIN INTERCONNECTION BETWEEN TWO RS422 INTERFACES
3
Data module 1
Data module 2
Signal name
Signal name
SD(A) - Send data
TT(A) - Terminal timing
TT(B) - Terminal timing
SD(B) - Send data
RD(A) - Received data
RD(A) - Received data
SD(A) - Send data
SD(B) - Send data
RD(B) - Received data
RD(B) - Received data
RS(A) - Request to send (RTS)
RS(A) - Request to send (RTS)
RT(A) - Receive timing
CS(A) - Clear To send
CS(A) - Clear To send
RT(B) - Receive timing
CS(B) - Clear To send
CS(B) - Clear To send
Local loopback
Local loopback
Remote loopback
Remote loopback
Signal ground
Signal ground
ST(A) - Send timing
ST(A) - Send timing
ST(B) - Send timing
ST(B) - Send timing
RS(B) - Request to send (RTS)
RS(B) - Request to send (RTS)
831022A3.CDR
W
7a
W
2b
W
8a
7W
Shld.
Shld.
Tx1(+)
Tx2(+)
Tx1(-)
Tx2(-)
Rx1(+)
Rx2(+)
+
com
Rx1(-)
Rx2(-)
INTER-RELAY COMMUNICATIONS
W
3a
W
5b
W
5a
W
3b
W
2a
W
6a
W
6b
W
7b
W
8b
W
4b
W
4a
RS422
CHANNEL 1
RS422
CHANNEL 2
CLOCK
SURGE
Tx Clock
Tx Data
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
Figure 3–44: TIMING CONFIGURATION FOR RS422 TWO-CHANNEL, 3-TERMINAL APPLICATION
Data module 1 provides timing to the F35 RS422 interface via the ST(A) and ST(B) outputs. Data module 1 also provides timing to data module 2 TT(A) and TT(B) inputs via the ST(A) and AT(B) outputs. The data module pin numbers have been omitted in the figure above since they may vary depending on the manufacturer.
c) TRANSMIT TIMING
The RS422 interface accepts one clock input for transmit timing. It is important that the rising edge of the 64 kHz transmit timing clock of the multiplexer interface is sampling the data in the center of the transmit data window. Therefore, it is impor­tant to confirm clock and data transitions to ensure proper system operation. For example, the following figure shows the positive edge of the Tx clock in the center of the Tx data bit.
d) RECEIVE TIMING
The RS422 interface utilizes NRZI-MARK modulation code and; therefore, does not rely on an Rx clock to recapture data. NRZI-MARK is an edge-type, invertible, self-clocking code.
3-40 F35 Multiple Feeder Protection System GE Multilin
Figure 3–45: CLOCK AND DATA TRANSITIONS
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
NOTICE
~
~
~
~
~
~
~
~
~
Shield
COM
Tx1 +
Tx1 –
Rx1 –
Rx1 +
1a
2b
3a
4b
Fiber
channel 2
Clock
(channel 1)
RS422
channel 1
Surge
1b
2a
3b
6a
8a
Tx2
Rx2
Inter-relay comms. 7L, 7M, 7N, 7P, 74
842777A1.CDR
NOTICE
~
~
~
~
~
~
Shield
Tx –
Tx +
Rx –
Rx +
1a
2a
3a
Fiber
channel 2
G.703
channel 1
Surge
1b
2b
3b
Tx2
Rx2
Inter-relay
communications
7E, 7F, 7G,
7Q,75
842778A1.CDR
To recover the Rx clock from the data-stream, an integrated DPLL (digital phase lock loop) circuit is utilized. The DPLL is driven by an internal clock, which is 16-times over-sampled, and uses this clock along with the data-stream to generate a data clock that can be used as the SCC (serial communication controller) receive clock.

3.3.6 RS422 AND FIBER INTERFACE

The following figure shows the combined RS422 plus Fiber interface configuration at 64K baud. The 7L, 7M, 7N, 7P, and 74 modules are used in two-terminal with a redundant channel or three-terminal configurations where channel 1 is employed via the RS422 interface (possibly with a multiplexer) and channel 2 via direct fiber.
AWG 24 twisted shielded pair is recommended for external RS422 connections and the shield should be grounded only at one end. For the direct fiber channel, power budget issues should be addressed properly.
When using a laser interface, attenuators can be necessary to ensure that you do not exceed maxi­mum optical input power to the receiver.
3
Figure 3–46: RS422 AND FIBER INTERFACE CONNECTION
Connections shown above are for multiplexers configured as DCE (data communications equipment) units.

3.3.7 G.703 AND FIBER INTERFACE

The figure below shows the combined G.703 plus fiber interface configuration at 64 kbps. The 7E, 7F, 7G, 7Q, and 75 mod­ules are used in configurations where channel 1 is employed via the G.703 interface (possibly with a multiplexer) and chan­nel 2 via direct fiber. AWG 24 twisted shielded pair is recommended for external G.703 connections connecting the shield to pin 1a at one end only. For the direct fiber channel, power budget issues should be addressed properly. See previous sec­tions for additional details on the G.703 and fiber interfaces.
When using a laser interface, attenuators can be necessary to ensure that you do not exceed the maximum optical input power to the receiver.
GE Multilin F35 Multiple Feeder Protection System 3-41
Figure 3–47: G.703 AND FIBER INTERFACE CONNECTION
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE

3.3.8 IEEE C37.94 INTERFACE

The UR-series IEEE C37.94 communication modules (modules types 2G, 2H, 76, and 77) are designed to interface with IEEE C37.94 compliant digital multiplexers or an IEEE C37.94 compliant interface converter for use with direct input and output applications for firmware revisions 3.30 and higher. The IEEE C37.94 standard defines a point-to-point optical link for synchronous data between a multiplexer and a teleprotection device. This data is typically 64 kbps, but the standard provides for speeds up to 64n kbps, where n = 1, 2,…, 12. The UR-series C37.94 communication modules are either 64 kbps (with n fixed at 1) or 128 kbps (with n fixed at 2). The frame is a valid International Telecommunications Union (ITU­T) recommended G.704 pattern from the standpoint of framing and data rate. The frame is 256 bits and is repeated at a frame rate of 8000 Hz, with a resultant bit rate of 2048 kbps.
The specifications for the module are as follows:.
IEEE standard: C37.94 for 1 × 128 kbps optical fiber interface (for 2G and 2H modules) or C37.94 for 2 × 64 kbps opti-
3
cal fiber interface (for 76 and 77 modules).
Fiber optic cable type: 50 mm or 62.5 mm core diameter optical fiber.
Fiber optic mode: multi-mode.
Fiber optic cable length: up to 2 km.
Fiber optic connector: type ST.
Wavelength: 830 ±40 nm.
Connection: as per all fiber optic connections, a Tx-to-Rx connection is required.
The UR-series C37.94 communication module can be connected directly to any compliant digital multiplexer that supports the IEEE C37.94 standard as shown below.
The UR-series C37.94 communication module can be connected to the electrical interface (G.703, RS422, or X.21) of a non-compliant digital multiplexer via an optical-to-electrical interface converter that supports the IEEE C37.94 standard, as shown below.
In 2008, GE Grid Solutions released revised modules 76 and 77 for C37.94 communication to enable multi-ended fault location functionality with firmware 5.60 release and higher. All modules 76 and 77 shipped since the change support this feature and are fully backward compatible with firmware releases below 5.60. For customers using firmware release 5.60 and higher, the module can be identified with "Rev D" printed on the module and is to be used on all ends of F35 communi­cation for two and three terminal applications. Failure to use it at all ends results in intermittent communication alarms. For customers using firmware revisions below 5.60, it is not required to match the revision of the modules installed.
3-42 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
842753A1.CDR
The UR-series C37.94 communication module has six switches that are used to set the clock configuration. The functions of these control switches is shown below.
For the internal timing mode, the system clock is generated internally. therefore, the timing switch selection should be inter­nal timing for relay 1 and loop timed for relay 2. There must be only one timing source configured.
For the looped timing mode, the system clock is derived from the received line signal. Therefore, the timing selection should be in loop timing mode for connections to higher order systems.
The IEEE C37.94 communications module cover removal procedure is as follows:
1. Remove the IEEE C37.94 module (type 2G, 2H, 76 or 77 module):
The ejector/inserter clips located at the top and at the bottom of each module, must be pulled simultaneously in order to release the module for removal. Before performing this action, control power must be removed from the relay. The original location of the module should be recorded to help ensure that the same or replacement module is inserted into the correct slot.
2. Remove the module cover screw.
3. Remove the top cover by sliding it towards the rear and then lift it upwards.
4. Set the timing selection switches (channel 1, channel 2) to the desired timing modes (see description above).
5. Replace the top cover and the cover screw.
6. Re-insert the IEEE C37.94 module. Take care to ensure that the correct module type is inserted into the correct slot
position. The ejector/inserter clips located at the top and at the bottom of each module must be in the disengaged posi­tion as the module is smoothly inserted into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module will be fully inserted.
3
GE Multilin F35 Multiple Feeder Protection System 3-43
3
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
Figure 3–48: IEEE C37.94 TIMING SELECTION SWITCH SETTING
3-44 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS

3.3.9 C37.94SM INTERFACE

The UR-series C37.94SM communication modules (2A and 2B) are designed to interface with modified IEEE C37.94 com­pliant digital multiplexers or IEEE C37.94 compliant interface converters that have been converted from 820 nm multi-mode fiber optics to 1300 nm ELED single-mode fiber optics. The IEEE C37.94 standard defines a point-to-point optical link for synchronous data between a multiplexer and a teleprotection device. This data is typically 64 kbps, but the standard pro­vides for speeds up to 64n kbps, where n = 1, 2,…, 12. The UR-series C37.94SM communication module is 64 kbps only with n fixed at 1. The frame is a valid International Telecommunications Union (ITU-T) recommended G.704 pattern from the standpoint of framing and data rate. The frame is 256 bits and is repeated at a frame rate of 8000 Hz, with a resultant bit rate of 2048 kbps.
The specifications for the module are as follows:
Emulated IEEE standard: emulates C37.94 for 1 × 64 kbps optical fiber interface (modules set to n = 1 or 64 kbps).
Fiber optic cable type: 9/125 μm core diameter optical fiber.
Fiber optic mode: single-mode, ELED compatible with HP HFBR-1315T transmitter and HP HFBR-2316T receiver.
Fiber optic cable length: up to 10 km.
Fiber optic connector: type ST.
Wavelength: 1300 ±40 nm.
Connection: as per all fiber optic connections, a Tx-to-Rx connection is required.
The UR-series C37.94SM communication module can be connected directly to any compliant digital multiplexer that sup­ports C37.94SM as shown below.
3
It can also can be connected directly to any other UR-series relay with a C37.94SM module as shown below.
In 2008, GE Grid Solutions released revised modules 2A and 2B for C37.94SM communication to enable multi-ended fault location functionality with firmware 5.60 release and higher. All modules 2A and 2B shipped since the change support this feature and are fully backward compatible with firmware releases below 5.60. For customers using firmware release 5.60 and higher, the module can be identified with "Rev D" printed on the module and is to be used on all ends of F35 communi­cation for two and three terminal applications. Failure to use it at all ends results in intermittent communication alarms. For customers using firmware revisions below 5.60, it is not required to match the revision of the modules installed.
GE Multilin F35 Multiple Feeder Protection System 3-45
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
842753A1.CDR
The UR-series C37.94SM communication module has six switches that are used to set the clock configuration. The func­tions of these control switches is shown below.
For the internal timing mode, the system clock is generated internally. Therefore, the timing switch selection should be internal timing for relay 1 and loop timed for relay 2. There must be only one timing source configured.
3
For the looped timing mode, the system clock is derived from the received line signal. Therefore, the timing selection should be in loop timing mode for connections to higher order systems.
The C37.94SM communications module cover removal procedure is as follows:
1. Remove the C37.94SM module (modules 2A or 2B):
The ejector/inserter clips located at the top and at the bottom of each module, must be pulled simultaneously in order to release the module for removal. Before performing this action, control power must be removed from the relay. The original location of the module should be recorded to help ensure that the same or replacement module is inserted into the correct slot.
2. Remove the module cover screw.
3. Remove the top cover by sliding it towards the rear and then lift it upwards.
4. Set the timing selection switches (channel 1, channel 2) to the desired timing modes (see description above).
5. Replace the top cover and the cover screw.
6. Re-insert the C37.94SM module. Take care to ensure that the correct module type is inserted into the correct slot position. The ejector/inserter clips located at the top and at the bottom of each module must be in the disengaged posi­tion as the module is smoothly inserted into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module will be fully inserted.
3-46 F35 Multiple Feeder Protection System GE Multilin
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
3
Figure 3–49: C37.94SM TIMING SELECTION SWITCH SETTING
GE Multilin F35 Multiple Feeder Protection System 3-47
3.4 MANAGED ETHERNET SWITCH MODULES 3 HARDWARE
NOTE
842867A2.CDR
Two 10/100Base-T ports
Four 100Base-FX multimode ports with ST connectors
Independent power supply. Options:
2S: high-voltage 2T: low-voltage
RS232
console port
REAR VIEW
FRONT VIEW

3.4MANAGED ETHERNET SWITCH MODULES 3.4.1 OVERVIEW

The type 2S and 2T embedded managed switch modules are supported by UR-series relays containing type 9S CPU mod­ules with revisions 5.5x and higher. The modules communicate to the F35 through an internal Ethernet port (referred to as the UR port or port 7) and provide an additional six external Ethernet ports: two 10/100Base-T ports and four multimode ST 100Base-FX ports.
The Ethernet switch module should be powered up before or at the same time as the F35. Otherwise, the switch module will not be detected on power up and the
EQUIPMENT MISMATCH: ORDERCODE XXX self-test warning will be
issued.

3.4.2 MANAGED ETHERNET SWITCH MODULE HARDWARE

The type 2S and 2T managed Ethernet switch modules provide two 10/100Base-T and four multimode ST 100Base-FX
3
external Ethernet ports accessible through the rear of the module. In addition, a serial console port is accessible from the front of the module (requires the front panel faceplate to be open).
The pin assignment for the console port signals is shown in the following table.
Table 3–8: CONSOLE PORT PIN ASSIGNMENT
PIN SIGNAL DESCRIPTION
1 CD Carrier detect (not used)
2 RXD Receive data (input)
3 TXD Transmit data (output)
4 N/A Not used
5 GND Signal ground
6 to 9 N/A Not used
Figure 3–50: MANAGED ETHERNET SWITCHES HARDWARE
3-48 F35 Multiple Feeder Protection System GE Multilin