GE F35 Instruction Manual

832761A2.CDR

Title Page

IISO 9001
G
N
E
I
L
M
I
U
T
L
T
E
S
I
R
G
E
E
D
R
LISTED
52TL
IND.CONT. EQ.
E83849
GE
Grid Solutions
F35 Multiple Feeder Protection
System
UR Series Instruction Manual
F35 Revision: 5.8x
Manual P/N: 1601-0106-V2 (GEK-113550A)
Copyright © 2017 GE Multilin Inc.
650 Markland Street
Markham, Ontario
Canada L6C 0M1
Tel: +1 905 927 7070 Fax: +1 905 927 5098
Internet: http://www.GEGridSolutions.com
*1601-0106-V2*
GE Multilin's Quality Management
System is registered to
ISO9001:2008
QMI # 005094
UL # A3775

Addendum

ADDENDUM
This addendum contains information that relates to the F35 Multiple Feeder Protection System, version 5.8x. This addendum lists a number of information items that appear in the instruction manual GEK-113550A (revision V2) but are not included in the current F35 operations.
The following functions and items are not yet available with the current version of the F35 relay:
•N/A.
Version 4.0x and higher releases of the F35 relay includes new hardware (CPU and CT/VT modules).
• The new CPU modules are specified with the following order codes: 9E, 9G, 9H, 9J, 9K, 9L, 9M, 9N, 9P, 9R, and 9S.
• The new CT/VT modules are specified with the following order codes: 8F, 8G, 8H, 8J 8L, 8M, 8N, 8R.
The following table maps the relationship between the old CPU and CT/VT modules to the newer versions:
MODULE OLD NEW DESCRIPTION
CPU 9A 9E RS485 and RS485 (Modbus RTU, DNP)
9C 9G RS485 and 10Base-F (Ethernet, Modbus TCP/IP, DNP)
9D 9H RS485 and redundant 10Base-F (Ethernet, Modbus TCP/IP, DNP)
--- 9J RS485 and multi-mode ST 100Base-FX
--- 9K RS485 and multi-mode ST redundant 100Base-FX
--- 9L RS485 and single mode SC 100Base-FX
--- 9M RS485 and single mode SC redundant 100Base-FX
--- 9N RS485 and 10/100Base-T
--- 9P RS485 and single mode ST 100Base-FX
--- 9R RS485 and single mode ST redundant 100Base-FX
--- 9S RS485 and six-port managed Ethernet switch
CT/VT 8A 8F Standard 4CT/4VT
8B 8G Sensitive ground 4CT/4VT
8C 8H Standard 8CT
8D 8J Sensitive ground 8CT
-- 8L Standard 4CT/4VT with enhanced diagnostics
-- 8M Sensitive ground 4CT/4VT with enhanced diagnostics
-- 8N Standard 8CT with enhanced diagnostics
-- 8R Sensitive ground 8CT with enhanced diagnostics
The new CT/VT modules can only be used with the new CPUs (9E, 9G, 9H, 9J, 9K, 9L, 9M, 9N, 9P, 9R, and 9S), and the old CT/VT modules can only be used with the old CPU modules (9A, 9C, 9D). To prevent any hardware mis­matches, the new CPU and CT/VT modules have blue labels and a warning sticker stating “Attn.: Ensure CPU and DSP module label colors are the same!”. In the event that there is a mismatch between the CPU and CT/VT module, the relay will not function and a
DSP ERROR or HARDWARE MISMATCH error will be displayed.
All other input/output modules are compatible with the new hardware.
With respect to the firmware, firmware versions 4.0x and higher are only compatible with the new CPU and CT/VT mod­ules. Previous versions of the firmware (3.4x and earlier) are only compatible with the older CPU and CT/VT modules.

Table of Contents

TABLE OF CONTENTS
1. GETTING STARTED 1.1 IMPORTANT PROCEDURES
1.1.1 CAUTIONS AND WARNINGS ........................................................................... 1-1
1.1.2 INSPECTION CHECKLIST ................................................................................ 1-2
1.2 UR OVERVIEW
1.2.1 INTRODUCTION TO THE UR ........................................................................... 1-3
1.2.2 HARDWARE ARCHITECTURE......................................................................... 1-4
1.2.3 SOFTWARE ARCHITECTURE.......................................................................... 1-5
1.2.4 IMPORTANT CONCEPTS ................................................................................. 1-5
1.3 ENERVISTA UR SETUP SOFTWARE
1.3.1 PC REQUIREMENTS ........................................................................................ 1-6
1.3.2 INSTALLATION.................................................................................................. 1-6
1.3.3 CONFIGURING THE F35 FOR SOFTWARE ACCESS .................................... 1-7
1.3.4 USING THE QUICK CONNECT FEATURE..................................................... 1-10
1.3.5 CONNECTING TO THE F35 RELAY............................................................... 1-16
1.4 UR HARDWARE
1.4.1 MOUNTING AND WIRING............................................................................... 1-17
1.4.2 COMMUNICATIONS........................................................................................ 1-17
1.4.3 FACEPLATE DISPLAY.................................................................................... 1-17
1.5 USING THE RELAY
1.5.1 FACEPLATE KEYPAD..................................................................................... 1-18
1.5.2 MENU NAVIGATION ....................................................................................... 1-18
1.5.3 MENU HIERARCHY ........................................................................................ 1-18
1.5.4 RELAY ACTIVATION....................................................................................... 1-18
1.5.5 RELAY PASSWORDS..................................................................................... 1-19
1.5.6 FLEXLOGIC™ CUSTOMIZATION................................................................... 1-19
1.5.7 COMMISSIONING ........................................................................................... 1-20
2. PRODUCT DESCRIPTION 2.1 INTRODUCTION
2.1.1 OVERVIEW........................................................................................................ 2-1
2.1.2 ORDERING........................................................................................................ 2-2
2.1.3 REPLACEMENT MODULES ............................................................................. 2-6
2.2 SPECIFICATIONS
2.2.1 PROTECTION ELEMENTS ............................................................................... 2-9
2.2.2 USER-PROGRAMMABLE ELEMENTS........................................................... 2-10
2.2.3 MONITORING.................................................................................................. 2-11
2.2.4 METERING ...................................................................................................... 2-12
2.2.5 INPUTS ............................................................................................................2-13
2.2.6 POWER SUPPLY ............................................................................................ 2-14
2.2.7 OUTPUTS ........................................................................................................2-14
2.2.8 COMMUNICATIONS........................................................................................ 2-16
2.2.9 INTER-RELAY COMMUNICATIONS............................................................... 2-17
2.2.10 ENVIRONMENTAL .......................................................................................... 2-18
2.2.11 TYPE TESTS ................................................................................................... 2-19
2.2.12 PRODUCTION TESTS .................................................................................... 2-19
2.2.13 APPROVALS ................................................................................................... 2-20
2.2.14 MAINTENANCE ............................................................................................... 2-20
3. HARDWARE 3.1 DESCRIPTION
3.1.1 PANEL CUTOUT ............................................................................................... 3-1
3.1.2 MODULE WITHDRAWAL AND INSERTION ..................................................... 3-6
3.1.3 REAR TERMINAL LAYOUT............................................................................... 3-8
3.2 WIRING
3.2.1 TYPICAL WIRING............................................................................................ 3-10
3.2.2 DIELECTRIC STRENGTH ............................................................................... 3-11
3.2.3 CONTROL POWER ......................................................................................... 3-11
3.2.4 CT/VT MODULES ............................................................................................ 3-12
3.2.5 PROCESS BUS MODULES ............................................................................ 3-14
3.2.6 CONTACT INPUTS AND OUTPUTS............................................................... 3-14
GE Multilin F35 Multiple Feeder Protection System v
TABLE OF CONTENTS
3.2.7 TRANSDUCER INPUTS/OUTPUTS.................................................................3-26
3.2.8 RS232 FACEPLATE PORT..............................................................................3-27
3.2.9 CPU COMMUNICATION PORTS.....................................................................3-27
3.2.10 IRIG-B ...............................................................................................................3-31
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
3.3.1 DESCRIPTION .................................................................................................3-32
3.3.2 FIBER: LED AND ELED TRANSMITTERS ......................................................3-35
3.3.3 FIBER-LASER TRANSMITTERS .....................................................................3-35
3.3.4 G.703 INTERFACE...........................................................................................3-36
3.3.5 RS422 INTERFACE .........................................................................................3-39
3.3.6 RS422 AND FIBER INTERFACE .....................................................................3-41
3.3.7 G.703 AND FIBER INTERFACE ......................................................................3-41
3.3.8 IEEE C37.94 INTERFACE................................................................................3-42
3.3.9 C37.94SM INTERFACE ...................................................................................3-45
3.4 MANAGED ETHERNET SWITCH MODULES
3.4.1 OVERVIEW ......................................................................................................3-48
3.4.2 MANAGED ETHERNET SWITCH MODULE HARDWARE..............................3-48
3.4.3 MANAGED SWITCH LED INDICATORS .........................................................3-49
3.4.4 CONFIGURING THE MANAGED ETHERNET SWITCH MODULE.................3-49
3.4.5 UPLOADING F35 SWITCH MODULE FIRMWARE .........................................3-52
3.4.6 ETHERNET SWITCH SELF-TEST ERRORS...................................................3-54
4. HUMAN INTERFACES 4.1 ENERVISTA UR SETUP SOFTWARE INTERFACE
4.1.1 INTRODUCTION ................................................................................................4-1
4.1.2 CREATING A SITE LIST ....................................................................................4-1
4.1.3 ENERVISTA UR SETUP OVERVIEW................................................................4-1
4.1.4 ENERVISTA UR SETUP MAIN WINDOW..........................................................4-3
4.2 EXTENDED ENERVISTA UR SETUP FEATURES
4.2.1 SETTINGS TEMPLATES ...................................................................................4-4
4.2.2 SECURING AND LOCKING FLEXLOGIC™ EQUATIONS ................................4-8
4.2.3 SETTINGS FILE TRACEABILITY.....................................................................4-10
4.3 FACEPLATE INTERFACE
4.3.1 FACEPLATE.....................................................................................................4-13
4.3.2 LED INDICATORS............................................................................................4-14
4.3.3 CUSTOM LABELING OF LEDS .......................................................................4-17
4.3.4 DISPLAY...........................................................................................................4-23
4.3.5 KEYPAD ...........................................................................................................4-23
4.3.6 BREAKER CONTROL ......................................................................................4-23
4.3.7 MENUS.............................................................................................................4-24
4.3.8 CHANGING SETTINGS ...................................................................................4-26
5. SETTINGS 5.1 OVERVIEW
5.1.1 SETTINGS MAIN MENU ....................................................................................5-1
5.1.2 INTRODUCTION TO ELEMENTS......................................................................5-4
5.1.3 INTRODUCTION TO AC SOURCES..................................................................5-5
5.2 PRODUCT SETUP
5.2.1 SECURITY..........................................................................................................5-8
5.2.2 DISPLAY PROPERTIES ..................................................................................5-12
5.2.3 CLEAR RELAY RECORDS ..............................................................................5-14
5.2.4 COMMUNICATIONS ........................................................................................5-15
5.2.5 MODBUS USER MAP ......................................................................................5-37
5.2.6 REAL TIME CLOCK .........................................................................................5-38
5.2.7 FAULT REPORTS ............................................................................................5-39
5.2.8 OSCILLOGRAPHY ...........................................................................................5-41
5.2.9 DATA LOGGER................................................................................................5-43
5.2.10 DEMAND ..........................................................................................................5-45
5.2.11 USER-PROGRAMMABLE LEDS .....................................................................5-46
5.2.12 USER-PROGRAMMABLE SELF TESTS .........................................................5-49
5.2.13 CONTROL PUSHBUTTONS ............................................................................5-50
vi F35 Multiple Feeder Protection System GE Multilin
TABLE OF CONTENTS
5.2.14 USER-PROGRAMMABLE PUSHBUTTONS ...................................................5-51
5.2.15 FLEX STATE PARAMETERS..........................................................................5-56
5.2.16 USER-DEFINABLE DISPLAYS .......................................................................5-57
5.2.17 DIRECT INPUTS/OUTPUTS ........................................................................... 5-59
5.2.18 TELEPROTECTION......................................................................................... 5-67
5.2.19 INSTALLATION................................................................................................ 5-67
5.3 REMOTE RESOURCES
5.3.1 REMOTE RESOURCES CONFIGURATION ................................................... 5-69
5.4 SYSTEM SETUP
5.4.1 AC INPUTS ......................................................................................................5-70
5.4.2 POWER SYSTEM............................................................................................ 5-71
5.4.3 SIGNAL SOURCES ......................................................................................... 5-72
5.4.4 BREAKERS......................................................................................................5-75
5.4.5 DISCONNECT SWITCHES .............................................................................5-79
5.4.6 FLEXCURVES™..............................................................................................5-82
5.5 FLEXLOGIC™
5.5.1 INTRODUCTION TO FLEXLOGIC™............................................................... 5-89
5.5.2 FLEXLOGIC™ RULES .................................................................................... 5-98
5.5.3 FLEXLOGIC™ EVALUATION.......................................................................... 5-98
5.5.4 FLEXLOGIC™ EXAMPLE ............................................................................... 5-99
5.5.5 FLEXLOGIC™ EQUATION EDITOR ............................................................. 5-103
5.5.6 FLEXLOGIC™ TIMERS................................................................................. 5-103
5.5.7 FLEXELEMENTS™ ....................................................................................... 5-105
5.5.8 NON-VOLATILE LATCHES ........................................................................... 5-109
5.6 GROUPED ELEMENTS
5.6.1 OVERVIEW.................................................................................................... 5-110
5.6.2 SETTING GROUP .........................................................................................5-110
5.6.3 PHASE CURRENT ........................................................................................ 5-110
5.6.4 NEUTRAL CURRENT.................................................................................... 5-119
5.6.5 GROUND CURRENT..................................................................................... 5-121
5.6.6 NEGATIVE SEQUENCE CURRENT ............................................................. 5-123
5.6.7 VOLTAGE ELEMENTS.................................................................................. 5-126
5.7 CONTROL ELEMENTS
5.7.1 OVERVIEW.................................................................................................... 5-132
5.7.2 TRIP BUS.......................................................................................................5-132
5.7.3 SETTING GROUPS ....................................................................................... 5-134
5.7.4 SELECTOR SWITCH..................................................................................... 5-135
5.7.5 UNDERFREQUENCY.................................................................................... 5-141
5.7.6 AUTORECLOSE ............................................................................................ 5-142
5.7.7 DIGITAL ELEMENTS..................................................................................... 5-148
5.7.8 DIGITAL COUNTERS .................................................................................... 5-151
5.7.9 8-BIT SWITCHES .......................................................................................... 5-153
5.7.10 MONITORING ELEMENTS ........................................................................... 5-155
5.7.11 PID REGULATOR.......................................................................................... 5-161
5.8 INPUTS AND OUTPUTS
5.8.1 CONTACT INPUTS........................................................................................ 5-164
5.8.2 VIRTUAL INPUTS.......................................................................................... 5-166
5.8.3 CONTACT OUTPUTS.................................................................................... 5-167
5.8.4 VIRTUAL OUTPUTS...................................................................................... 5-169
5.8.5 REMOTE DEVICES....................................................................................... 5-170
5.8.6 REMOTE INPUTS.......................................................................................... 5-171
5.8.7 REMOTE DOUBLE-POINT STATUS INPUTS .............................................. 5-172
5.8.8 REMOTE OUTPUTS...................................................................................... 5-172
5.8.9 RESETTING...................................................................................................5-173
5.8.10 DIRECT INPUTS AND OUTPUTS ................................................................. 5-174
5.8.11 TELEPROTECTION INPUTS AND OUTPUTS.............................................. 5-177
5.8.12 IEC 61850 GOOSE ANALOGS...................................................................... 5-179
5.8.13 IEC 61850 GOOSE INTEGERS.....................................................................5-180
5.9 TRANSDUCER INPUTS AND OUTPUTS
5.9.1 DCMA INPUTS .............................................................................................. 5-181
5.9.2 RTD INPUTS.................................................................................................. 5-182
5.9.3 DCMA OUTPUTS .......................................................................................... 5-184
GE Multilin F35 Multiple Feeder Protection System vii
TABLE OF CONTENTS
5.10 TESTING
5.10.1 TEST MODE ...................................................................................................5-187
5.10.2 FORCE CONTACT INPUTS...........................................................................5-188
5.10.3 FORCE CONTACT OUTPUTS.......................................................................5-189
6. ACTUAL VALUES 6.1 OVERVIEW
6.1.1 ACTUAL VALUES MAIN MENU.........................................................................6-1
6.2 STATUS
6.2.1 CONTACT INPUTS ............................................................................................6-3
6.2.2 VIRTUAL INPUTS ..............................................................................................6-3
6.2.3 REMOTE INPUTS ..............................................................................................6-3
6.2.4 REMOTE DOUBLE-POINT STATUS INPUTS...................................................6-4
6.2.5 TELEPROTECTION INPUTS .............................................................................6-4
6.2.6 CONTACT OUTPUTS ........................................................................................6-4
6.2.7 VIRTUAL OUTPUTS ..........................................................................................6-5
6.2.8 AUTORECLOSE.................................................................................................6-5
6.2.9 REMOTE DEVICES............................................................................................6-5
6.2.10 DIGITAL COUNTERS.........................................................................................6-6
6.2.11 SELECTOR SWITCHES ....................................................................................6-6
6.2.12 FLEX STATES....................................................................................................6-6
6.2.13 ETHERNET ........................................................................................................6-7
6.2.14 DIRECT INPUTS ................................................................................................6-7
6.2.15 DIRECT DEVICES STATUS ..............................................................................6-8
6.2.16 IEC 61850 GOOSE INTEGERS .........................................................................6-8
6.2.17 EGD PROTOCOL STATUS................................................................................6-8
6.2.18 TELEPROTECTION CHANNEL TESTS.............................................................6-9
6.2.19 INCIPIENT FAULT DETECTOR.........................................................................6-9
6.2.20 ETHERNET SWITCH .......................................................................................6-10
6.3 METERING
6.3.1 METERING CONVENTIONS ...........................................................................6-11
6.3.2 SOURCES ........................................................................................................6-14
6.3.3 TRACKING FREQUENCY................................................................................6-19
6.3.4 FLEXELEMENTS™..........................................................................................6-20
6.3.5 IEC 61580 GOOSE ANALOG VALUES ...........................................................6-20
6.3.6 TRANSDUCER INPUTS/OUTPUTS.................................................................6-21
6.4 RECORDS
6.4.1 FAULT REPORTS ............................................................................................6-22
6.4.2 EVENT RECORDS...........................................................................................6-22
6.4.3 OSCILLOGRAPHY ...........................................................................................6-23
6.4.4 DATA LOGGER................................................................................................6-23
6.4.5 BREAKER MAINTENANCE .............................................................................6-24
6.5 PRODUCT INFORMATION
6.5.1 MODEL INFORMATION...................................................................................6-25
6.5.2 FIRMWARE REVISIONS..................................................................................6-25
7. COMMANDS AND TARGETS
7.1 COMMANDS
7.1.1 COMMANDS MENU...........................................................................................7-1
7.1.2 VIRTUAL INPUTS ..............................................................................................7-1
7.1.3 CLEAR RECORDS.............................................................................................7-2
7.1.4 SET DATE AND TIME ........................................................................................7-2
7.1.5 RELAY MAINTENANCE.....................................................................................7-3
7.2 TARGETS
7.2.1 TARGETS MENU ...............................................................................................7-4
7.2.2 TARGET MESSAGES ........................................................................................7-4
7.2.3 RELAY SELF-TESTS .........................................................................................7-4
viii F35 Multiple Feeder Protection System GE Multilin
TABLE OF CONTENTS
8. SECURITY 8.1 PASSWORD SECURITY
8.1.1 OVERVIEW........................................................................................................ 8-1
8.1.2 PASSWORD SECURITY MENU ....................................................................... 8-2
8.1.3 LOCAL PASSWORDS....................................................................................... 8-2
8.1.4 REMOTE PASSWORDS ................................................................................... 8-3
8.1.5 ACCESS SUPERVISION................................................................................... 8-3
8.1.6 DUAL PERMISSION SECURITY ACCESS....................................................... 8-4
8.2 SETTINGS SECURITY
8.2.1 SETTINGS TEMPLATES................................................................................... 8-6
8.2.2 SECURING AND LOCKING FLEXLOGIC™ EQUATIONS ............................. 8-10
8.2.3 SETTINGS FILE TRACEABILITY.................................................................... 8-12
8.3 ENERVISTA SECURITY MANAGEMENT SYSTEM
8.3.1 OVERVIEW...................................................................................................... 8-15
8.3.2 ENABLING THE SECURITY MANAGEMENT SYSTEM................................. 8-15
8.3.3 ADDING A NEW USER ................................................................................... 8-15
8.3.4 MODIFYING USER PRIVILEGES ................................................................... 8-16
9. THEORY OF OPERATION 9.1 FAULT LOCATOR
9.1.1 FAULT TYPE DETERMINATION....................................................................... 9-1
10. COMMISSIONING 10.1 TESTING
10.1.1 TESTING UNDERFREQUENCY ELEMENTS ................................................. 10-1
A. FLEXANALOG AND
FLEXINTEGER PARAMETERS
B. MODBUS
COMMUNICATIONS
A.1 PARAMETER LISTS
A.1.1 FLEXANALOG ITEMS .......................................................................................A-1
A.1.2 FLEXINTEGER ITEMS ....................................................................................A-16
B.1 MODBUS RTU PROTOCOL
B.1.1 INTRODUCTION................................................................................................B-1
B.1.2 PHYSICAL LAYER.............................................................................................B-1
B.1.3 DATA LINK LAYER............................................................................................B-1
B.1.4 CRC-16 ALGORITHM........................................................................................B-2
B.2 MODBUS FUNCTION CODES
B.2.1 SUPPORTED FUNCTION CODES ...................................................................B-3
B.2.2 READ ACTUAL VALUES OR SETTINGS (FUNCTION CODE 03/04H) ...........B-3
B.2.3 EXECUTE OPERATION (FUNCTION CODE 05H) ...........................................B-4
B.2.4 STORE SINGLE SETTING (FUNCTION CODE 06H).......................................B-4
B.2.5 STORE MULTIPLE SETTINGS (FUNCTION CODE 10H) ................................B-5
B.2.6 EXCEPTION RESPONSES...............................................................................B-5
B.3 FILE TRANSFERS
B.3.1 OBTAINING RELAY FILES VIA MODBUS........................................................B-6
B.3.2 MODBUS PASSWORD OPERATION ...............................................................B-7
B.4 MEMORY MAPPING
B.4.1 MODBUS MEMORY MAP .................................................................................B-8
B.4.2 DATA FORMATS .............................................................................................B-65
C. IEC 61850
COMMUNICATIONS
C.1 OVERVIEW
C.1.1 INTRODUCTION................................................................................................C-1
C.1.2 COMMUNICATION PROFILES .........................................................................C-1
GE Multilin F35 Multiple Feeder Protection System ix
TABLE OF CONTENTS
C.2 SERVER DATA ORGANIZATION
C.2.1 OVERVIEW .......................................................................................................C-2
C.2.2 GGIO1: DIGITAL STATUS VALUES.................................................................C-2
C.2.3 GGIO2: DIGITAL CONTROL VALUES..............................................................C-2
C.2.4 GGIO3: DIGITAL STATUS AND ANALOG VALUES FROM RECEIVED GOOSE
DATAC-2
C.2.5 GGIO4: GENERIC ANALOG MEASURED VALUES.........................................C-2
C.2.6 MMXU: ANALOG MEASURED VALUES ..........................................................C-3
C.2.7 PROTECTION AND OTHER LOGICAL NODES............................................... C-3
C.3 SERVER FEATURES AND CONFIGURATION
C.3.1 BUFFERED/UNBUFFERED REPORTING........................................................C-5
C.3.2 FILE TRANSFER...............................................................................................C-5
C.3.3 TIMESTAMPS AND SCANNING....................................................................... C-5
C.3.4 LOGICAL DEVICE NAME .................................................................................C-5
C.3.5 LOCATION ........................................................................................................C-5
C.3.6 LOGICAL NODE NAME PREFIXES..................................................................C-6
C.3.7 CONNECTION TIMING.....................................................................................C-6
C.3.8 NON-IEC 61850 DATA...................................................................................... C-6
C.3.9 COMMUNICATION SOFTWARE UTILITIES.....................................................C-6
C.4 GENERIC SUBSTATION EVENT SERVICES: GSSE AND GOOSE
C.4.1 OVERVIEW .......................................................................................................C-7
C.4.2 GSSE CONFIGURATION..................................................................................C-7
C.4.3 FIXED GOOSE.................................................................................................. C-7
C.4.4 CONFIGURABLE GOOSE ................................................................................ C-7
C.4.5 ETHERNET MAC ADDRESS FOR GSSE/GOOSE ..........................................C-9
C.4.6 GSSE ID AND GOOSE ID SETTINGS............................................................C-10
C.5 IEC 61850 IMPLEMENTATION VIA ENERVISTA UR SETUP
C.5.1 OVERVIEW .....................................................................................................C-11
C.5.2 CONFIGURING IEC 61850 SETTINGS .......................................................... C-12
C.5.3 ABOUT ICD FILES ..........................................................................................C-13
C.5.4 CREATING AN ICD FILE WITH ENERVISTA UR SETUP.............................. C-17
C.5.5 ABOUT SCD FILES.........................................................................................C-17
C.5.6 IMPORTING AN SCD FILE WITH ENERVISTA UR SETUP........................... C-20
C.6 ACSI CONFORMANCE
C.6.1 ACSI BASIC CONFORMANCE STATEMENT ................................................ C-22
C.6.2 ACSI MODELS CONFORMANCE STATEMENT............................................C-22
C.6.3 ACSI SERVICES CONFORMANCE STATEMENT .........................................C-23
C.7 LOGICAL NODES
C.7.1 LOGICAL NODES TABLE ............................................................................... C-26
D. IEC 60870-5-104 COMMS. D.1 IEC 60870-5-104 PROTOCOL
D.1.1 INTEROPERABILITY DOCUMENT...................................................................D-1
D.1.2 POINTS LIST.....................................................................................................D-9
E. DNP COMMUNICATIONS E.1 DEVICE PROFILE DOCUMENT
E.1.1 DNP V3.00 DEVICE PROFILE .......................................................................... E-1
E.1.2 IMPLEMENTATION TABLE .............................................................................. E-4
E.2 DNP POINT LISTS
E.2.1 BINARY INPUT POINTS ................................................................................... E-8
E.2.2 BINARY AND CONTROL RELAY OUTPUT...................................................... E-9
E.2.3 COUNTERS..................................................................................................... E-10
E.2.4 ANALOG INPUTS............................................................................................ E-11
F. MISCELLANEOUS F.1 CHANGE NOTES
F.1.1 REVISION HISTORY......................................................................................... F-1
F.1.2 CHANGES TO THE MANUAL ........................................................................... F-2
x F35 Multiple Feeder Protection System GE Multilin
TABLE OF CONTENTS
F.2 ABBREVIATIONS
F.2.1 STANDARD ABBREVIATIONS ......................................................................... F-8
F.3 WARRANTY
F.3.1 GE MULTILIN WARRANTY ............................................................................. F-10
INDEX
GE Multilin F35 Multiple Feeder Protection System xi
TABLE OF CONTENTS
xii F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.1 IMPORTANT PROCEDURES
DANGER
WARNING
CAUTION
NOTICE
DANGER
1 GETTING STARTED 1.1IMPORTANT PROCEDURES
Please read this chapter to help guide you through the initial setup of your new relay.

1.1.1 CAUTIONS AND WARNINGS

Before attempting to install or use the device, review all safety indicators in this document to help prevent injury, equipment damage, or downtime.
The following safety and equipment symbols are used in this document.
Indicates a hazardous situation which, if not avoided, will result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in minor or moderate injury.
Indicates practices not related to personal injury.
a) GENERAL CAUTIONS AND WARNINGS
The following general safety precautions and warnings apply.
Ensure that all connections to the product are correct so as to avoid accidental risk of shock and/or fire, for example such as can arise from high voltage connected to low voltage termi­nals.
Follow the requirements of this manual, including adequate wiring size and type, terminal torque settings, voltage, current magnitudes applied, and adequate isolation/clearance in external wiring from high to low voltage circuits.
Use the device only for its intended purpose and application.
Ensure that all ground paths are uncompromised for safety purposes during device operation and service.
Ensure that the control power applied to the device, the AC current, and voltage input match the ratings specified on the relay nameplate. Do not apply current or voltage in excess of the specified limits.
Only qualified personnel are to operate the device. Such personnel must be thoroughly familiar with all safety cau­tions and warnings in this manual and with applicable country, regional, utility, and plant safety regulations.
Hazardous voltages can exist in the power supply and at the device connection to current transformers, voltage transformers, control, and test circuit terminals. Make sure all sources of such voltages are isolated prior to attempting work on the device.
Hazardous voltages can exist when opening the secondary circuits of live current transformers. Make sure that current transformer secondary circuits are shorted out before making or removing any connection to the current transformer (CT) input terminals of the device.
For tests with secondary test equipment, ensure that no other sources of voltages or currents are connected to such equipment and that trip and close commands to the circuit breakers or other switching apparatus are iso­lated, unless this is required by the test procedure and is specified by appropriate utility/plant procedure.
When the device is used to control primary equipment, such as circuit breakers, isolators, and other switching apparatus, all control circuits from the device to the primary equipment must be isolated while personnel are working on or around this primary equipment to prevent any inadvertent command from this device.
Use an external disconnect to isolate the mains voltage supply.
Personal safety can be affected if the product is physically modified by the end user. Modifications to the product outside of recommended wiring configuration, hardware, or programming boundaries is not recommended end­use practice. Product disassembly and repairs are not permitted. All service needs to be conducted by the factory.
This product is rated to Class A emissions levels and is to be used in Utility, Substation Industrial environments. Not to be used near electronic devices rated for Class B levels.
1
GE Multilin F35 Multiple Feeder Protection System 1-1
1.1 IMPORTANT PROCEDURES 1 GETTING STARTED
CAUTION
®
®
Technical Support: Tel: (905) 294-6222 Fax: (905) 201-2098
http://www.GEmultilin.com
Model: Mods: Wiring Diagram: Inst. Manual: Serial Number: Firmware: Mfg. Date:
F35E00HCHF8AH6AM6BP8BX7A 000 832767A3 GEK-113271 MAZB98000029 D 2005/01/05
Control Power: Contact Inputs: Contact Outputs:
88-300V DC @ 35W / 77-265V AC @ 35VA 300V DC Max 10mA Standard Pilot Duty / 250V AC 7.5A 360V A Resistive / 125V DC Break 4A @ L/R = 40mS / 300W
RATINGS:
F35
GE Multilin
Made in Canada
- M A A B 9 7 0 0 0 0 9 9 -
Multiple Feeder Management Relay
®
832772A1.CDR
NOTE
LED transmitters are classified as IEC 60825-1 Accessible Emission Limit (AEL) Class 1M. Class 1M devices are considered safe to the unaided eye. Do not view directly with optical
1
instruments.

1.1.2 INSPECTION CHECKLIST

1. Open the relay packaging and inspect the unit for physical damage.
2. View the rear nameplate and verify that the correct model has been ordered.
Figure 1–1: REAR NAMEPLATE (EXAMPLE)
3. Ensure that the following items are included:
• Instruction manual.
• GE EnerVista CD (includes the EnerVista UR Setup software and manuals in PDF format).
• Mounting screws.
For product information, instruction manual updates, and the latest software updates, please visit the GE Grid Solutions website.
If there is any noticeable physical damage, or any of the contents listed are missing, contact GE Multilin immedi­ately.
GE MULTILIN CONTACT INFORMATION AND CALL CENTER FOR PRODUCT SUPPORT:
TELEPHONE: Worldwide +1 905 927 7070
Europe/Middle East/Africa +34 94 485 88 54 North America toll-free 1 800 547 8629
FAX: +1 905 927 5098 E-MAIL: Worldwide multilin.tech@ge.com
Europe multilin.tech.euro@ge.com
HOME PAGE: http://www.gegridsolutions.com/multilin
1-2 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.2 UR OVERVIEW

1.2UR OVERVIEW 1.2.1 INTRODUCTION TO THE UR

Historically, substation protection, control, and metering functions were performed with electromechanical equipment. This first generation of equipment was gradually replaced by analog electronic equipment, most of which emulated the single­function approach of their electromechanical precursors. Both of these technologies required expensive cabling and auxil­iary equipment to produce functioning systems.
Recently, digital electronic equipment has begun to provide protection, control, and metering functions. Initially, this equip­ment was either single function or had very limited multi-function capability, and did not significantly reduce the cabling and auxiliary equipment required. However, recent digital relays have become quite multi-functional, reducing cabling and aux­iliaries significantly. These devices also transfer data to central control facilities and Human Machine Interfaces using elec­tronic communications. The functions performed by these products have become so broad that many users now prefer the term IED (Intelligent Electronic Device).
It is obvious to station designers that the amount of cabling and auxiliary equipment installed in stations can be even further reduced, to 20% to 70% of the levels common in 1990, to achieve large cost reductions. This requires placing even more functions within the IEDs.
Users of power equipment are also interested in reducing cost by improving power quality and personnel productivity, and as always, in increasing system reliability and efficiency. These objectives are realized through software which is used to perform functions at both the station and supervisory levels. The use of these systems is growing rapidly.
High speed communications are required to meet the data transfer rates required by modern automatic control and moni­toring systems. In the near future, very high speed communications will be required to perform protection signaling with a performance target response time for a command signal between two IEDs, from transmission to reception, of less than 3 milliseconds. This has been established by the IEC 61850 standard.
IEDs with the capabilities outlined above will also provide significantly more power system data than is presently available, enhance operations and maintenance, and permit the use of adaptive system configuration for protection and control sys­tems. This new generation of equipment must also be easily incorporated into automation systems, at both the station and enterprise levels. The GE Multilin Universal Relay (UR) has been developed to meet these goals.
1
GE Multilin F35 Multiple Feeder Protection System 1-3
1.2 UR OVERVIEW 1 GETTING STARTED
827822A2.CDR
Input Elements
LAN
Programming
Device
Operator Interface
Contact Inputs Contact Outputs
Virtual Inputs
Virtual Outputs
Analog Inputs
Analog Outputs
CT Inputs
VT Inputs
Input
Status
Table
Output
Status
Table
Pickup Dropout Operate
Protective Elements
Logic Gates
Remote Outputs
-DNA
-USER
CPU Module Output Elements
Remote Inputs
Direct Inputs
Direct Outputs

1.2.2 HARDWARE ARCHITECTURE

1
a) UR BASIC DESIGN
The UR is a digital-based device containing a central processing unit (CPU) that handles multiple types of input and output signals. The UR can communicate over a local area network (LAN) with an operator interface, a programming device, or another UR device.
Figure 1–2: UR CONCEPT BLOCK DIAGRAM
The CPU module contains firmware that provides protection elements in the form of logic algorithms, as well as program­mable logic gates, timers, and latches for control features.
Input elements accept a variety of analog or digital signals from the field. The UR isolates and converts these signals into logic signals used by the relay.
Output elements convert and isolate the logic signals generated by the relay into digital or analog signals that can be used to control field devices.
b) UR SIGNAL TYPES
The contact inputs and outputs are digital signals associated with connections to hard-wired contacts. Both ‘wet’ and ‘dry’ contacts are supported.
The virtual inputs and outputs are digital signals associated with UR-series internal logic signals. Virtual inputs include signals generated by the local user interface. The virtual outputs are outputs of FlexLogic™ equations used to customize the device. Virtual outputs can also serve as virtual inputs to FlexLogic™ equations.
The analog inputs and outputs are signals that are associated with transducers, such as Resistance Temperature Detec- tors (RTDs).
The CT and VT inputs refer to analog current transformer and voltage transformer signals used to monitor AC power lines. The UR-series relays support 1 A and 5 A CTs.
The remote inputs and outputs provide a means of sharing digital point state information between remote UR-series devices. The remote outputs interface to the remote inputs of other UR-series devices. Remote outputs are FlexLogic™ operands inserted into IEC 61850 GSSE and GOOSE messages.
The direct inputs and outputs provide a means of sharing digital point states between a number of UR-series IEDs over a dedicated fiber (single or multimode), RS422, or G.703 interface. No switching equipment is required as the IEDs are con­nected directly in a ring or redundant (dual) ring configuration. This feature is optimized for speed and intended for pilot­aided schemes, distributed logic applications, or the extension of the input/output capabilities of a single relay chassis.
1-4 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.2 UR OVERVIEW
827823A1.CDR
PKP DPO OP
Protective Elements
Protection elements
serviced by sub-scan
Read Inputs
Solve Logic
Set Outputs
c) UR SCAN OPERATION
The UR-series devices operate in a cyclic scan fashion. The device reads the inputs into an input status table, solves the logic program (FlexLogic™ equation), and then sets each output to the appropriate state in an output status table. Any resulting task execution is priority interrupt-driven.
Figure 1–3: UR-SERIES SCAN OPERATION
1

1.2.3 SOFTWARE ARCHITECTURE

The firmware (software embedded in the relay) is designed in functional modules which can be installed in any relay as required. This is achieved with object-oriented design and programming (OOD/OOP) techniques.
Object-oriented techniques involve the use of objects and classes. An object is defined as “a logical entity that contains both data and code that manipulates that data”. A class is the generalized form of similar objects. By using this concept, one can create a protection class with the protection elements as objects of the class, such as time overcurrent, instanta­neous overcurrent, current differential, undervoltage, overvoltage, underfrequency, and distance. These objects represent completely self-contained software modules. The same object-class concept can be used for metering, input/output control, hmi, communications, or any functional entity in the system.
Employing OOD/OOP in the software architecture of the F35 achieves the same features as the hardware architecture: modularity, scalability, and flexibility. The application software for any UR-series device (for example, feeder protection, transformer protection, distance protection) is constructed by combining objects from the various functionality classes. This results in a common look and feel across the entire family of UR-series platform-based applications.

1.2.4 IMPORTANT CONCEPTS

As described above, the architecture of the UR-series relays differ from previous devices. To achieve a general understand­ing of this device, some sections of Chapter 5 are quite helpful. The most important functions of the relay are contained in “elements”. A description of the UR-series elements can be found in the Introduction to elements section in chapter 5. Examples of simple elements, and some of the organization of this manual, can be found in the Control elements section of chapter 5. An explanation of the use of inputs from CTs and VTs is in the Introduction to AC sources section in chapter 5. A description of how digital signals are used and routed within the relay is contained in the Introduction to FlexLogic™ section in chapter 5.
GE Multilin F35 Multiple Feeder Protection System 1-5
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED

1.3ENERVISTA UR SETUP SOFTWARE 1.3.1 PC REQUIREMENTS

1
The faceplate keypad and display or the EnerVista UR Setup software interface can be used to communicate with the relay. The EnerVista UR Setup software interface is the preferred method to edit settings and view actual values because the PC monitor can display more information in a simple comprehensible format.
The following minimum requirements must be met for the EnerVista UR Setup software to properly operate on a PC.
Pentium class or higher processor (Pentium II 300 MHz or higher recommended)
Windows 95, 98, 98SE, ME, NT 4.0 (Service Pack 4 or higher), 2000, XP
Internet Explorer 4.0 or higher
128 MB of RAM (256 MB recommended)
200 MB of available space on system drive and 200 MB of available space on installation drive
Video capable of displaying 800 x 600 or higher in high-color mode (16-bit color)
RS232 and/or Ethernet port for communications to the relay
The following qualified modems have been tested to be compliant with the F35 and the EnerVista UR Setup software.
US Robotics external 56K FaxModem 5686
US Robotics external Sportster 56K X2
PCTEL 2304WT V.92 MDC internal modem

1.3.2 INSTALLATION

After ensuring the minimum requirements for using EnerVista UR Setup are met (see previous section), use the following procedure to install the EnerVista UR Setup from the enclosed GE EnerVista CD.
1. Insert the GE EnerVista CD into your CD-ROM drive.
2. Click the Install Now button and follow the installation instructions to install the no-charge EnerVista software.
3. When installation is complete, start the EnerVista Launchpad application.
4. Click the IED Setup section of the Launch Pad window.
5. In the EnerVista Launch Pad window, click the Add Product button and select the “F35 Multiple Feeder Protection System” from the Install Software window as shown below. Select the “Web” option to ensure the most recent software
1-6 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
release, or select “CD” if you do not have a web connection, then click the Add Now button to list software items for the F35.
6. EnerVista Launchpad will obtain the software from the Web or CD and automatically start the installation program.
7. Select the complete path, including the new directory name, where the EnerVista UR Setup will be installed.
8. Click on Next to begin the installation. The files will be installed in the directory indicated and the installation program
will automatically create icons and add EnerVista UR Setup to the Windows start menu.
9. Click Finish to end the installation. The UR-series device will be added to the list of installed IEDs in the EnerVista
Launchpad window, as shown below.
1

1.3.3 CONFIGURING THE F35 FOR SOFTWARE ACCESS

a) OVERVIEW
The user can connect remotely to the F35 through the rear RS485 port or the rear Ethernet port with a PC running the EnerVista UR Setup software. The F35 can also be accessed locally with a laptop computer through the front panel RS232 port or the rear Ethernet port using the Quick Connect feature.
GE Multilin F35 Multiple Feeder Protection System 1-7
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
To configure the F35 for remote access via the rear RS485 port(s), refer to the Configuring Serial Communications
1
section.
To configure the F35 for remote access via the rear Ethernet port, refer to the Configuring Ethernet Communications section. An Ethernet module must be specified at the time of ordering.
To configure the F35 for local access with a laptop through either the front RS232 port or rear Ethernet port, refer to the Using the Quick Connect Feature section. An Ethernet module must be specified at the time of ordering for Ethernet communications.
b) CONFIGURING SERIAL COMMUNICATIONS
Before starting, verify that the serial cable is properly connected to the RS485 terminals on the back of the device. The faceplate RS232 port is intended for local use and is not described in this section; see the Using the Quick Connect Feature section for details on configuring the RS232 port.
A GE Multilin F485 converter (or compatible RS232-to-RS485 converter) is will be required. Refer to the F485 instruction manual for additional details.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE EnerVista CD or online from http://www.gegridsolutions.com/multilin
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
3. Click the Device Setup button to open the Device Setup window and click the Add Site button to define a new site.
4. Enter the desired site name in the “Site Name” field. If desired, a short description of site can also be entered along with the display order of devices defined for the site. In this example, we will use “Location 1” as the site name. Click the OK button when complete.
5. The new site will appear in the upper-left list in the EnerVista UR Setup window. Click the Device Setup button then select the new site to re-open the Device Setup window.
6. Click the Add Device button to define the new device.
7. Enter the desired name in the “Device Name” field and a description (optional) of the site.
8. Select “Serial” from the Interface drop-down list. This will display a number of interface parameters that must be entered for proper serial communications.
). See the Software Installation section for installation details.
Figure 1–4: CONFIGURING SERIAL COMMUNICATIONS
1-8 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
9. Enter the relay slave address, COM port, baud rate, and parity settings from the SETTINGS PRODUCT SETUP  COM-
MUNICATIONS  SERIAL PORTS menu in their respective fields.
10. Click the Read Order Code button to connect to the F35 device and upload the order code. If an communications error
occurs, ensure that the EnerVista UR Setup serial communications values entered in the previous step correspond to the relay setting values.
11. Click “OK” when the relay order code has been received. The new device will be added to the Site List window (or
Online window) located in the top left corner of the main EnerVista UR Setup window.
The Site Device has now been configured for RS232 communications. Proceed to the Connecting to the F35 section to begin communications.
c) CONFIGURING ETHERNET COMMUNICATIONS
Before starting, verify that the Ethernet network cable is properly connected to the Ethernet port on the back of the relay. To setup the relay for Ethernet communications, it will be necessary to define a Site, then add the relay as a Device at that site.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE EnerVista CD or
online from http://www.gegridsolutions.com/multilin
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
3. Click the Device Setup button to open the Device Setup window, then click the Add Site button to define a new site.
4. Enter the desired site name in the “Site Name” field. If desired, a short description of site can also be entered along
with the display order of devices defined for the site. In this example, we will use “Location 2” as the site name. Click the OK button when complete.
5. The new site will appear in the upper-left list in the EnerVista UR Setup window. Click the Device Setup button then
select the new site to re-open the Device Setup window.
6. Click the Add Device button to define the new device.
7. Enter the desired name in the “Device Name” field and a description (optional) of the site.
8. Select “Ethernet” from the Interface drop-down list. This will display a number of interface parameters that must be
entered for proper Ethernet functionality.
). See the Software Installation section for installation details.
1
Figure 1–5: CONFIGURING ETHERNET COMMUNICATIONS
GE Multilin F35 Multiple Feeder Protection System 1-9
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
9. Enter the relay IP address specified in the SETTINGS PRODUCT SETUP  COMMUNICATIONS  NETWORK IP
1
ADDRESS) in the “IP Address” field.
10. Enter the relay slave address and Modbus port address values from the respective settings in the SETTINGS PROD-
UCT SETUP  COMMUNICATIONS  MODBUS PROTOCOL menu.
11. Click the Read Order Code button to connect to the F35 device and upload the order code. If an communications error occurs, ensure that the three EnerVista UR Setup values entered in the previous steps correspond to the relay setting values.
12. Click OK when the relay order code has been received. The new device will be added to the Site List window (or Online window) located in the top left corner of the main EnerVista UR Setup window.
The Site Device has now been configured for Ethernet communications. Proceed to the Connecting to the F35 section to begin communications.

1.3.4 USING THE QUICK CONNECT FEATURE

a) USING QUICK CONNECT VIA THE FRONT PANEL RS232 PORT
Before starting, verify that the serial cable is properly connected from the laptop computer to the front panel RS232 port with a straight-through 9-pin to 9-pin RS232 cable.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE EnerVista CD or online from http://www.gegridsolutions.com/multilin
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
3. Click the Quick Connect button to open the Quick Connect dialog box.
). See the Software Installation section for installation details.
4. Select the Serial interface and the correct COM Port, then click Connect.
5. The EnerVista UR Setup software will create a site named “Quick Connect” with a corresponding device also named “Quick Connect” and display them on the upper-left corner of the screen. Expand the sections to view data directly from the F35 device.
Each time the EnerVista UR Setup software is initialized, click the Quick Connect button to establish direct communica­tions to the F35. This ensures that configuration of the EnerVista UR Setup software matches the F35 model number.
b) USING QUICK CONNECT VIA THE REAR ETHERNET PORTS
To use the Quick Connect feature to access the F35 from a laptop through Ethernet, first assign an IP address to the relay from the front panel keyboard.
1. Press the MENU key until the SETTINGS menu is displayed.
2. Navigate to the
3. Enter an IP address of “1.1.1.1” and select the ENTER key to save the value.
4. In the same menu, select the
5. Enter a subnet IP address of “255.0.0.0” and press the ENTER key to save the value.
SETTINGS PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting.
SUBNET IP MASK setting.
1-10 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
842799A1.CDR
END 1 END 2 Pin Wire color Diagram Pin Wire color Diagram
1 White/orange 1 White/green 2 Orange 2 Green
3 White/green 3 White/orange 4 Blue 4 Blue 5 White/blue 5 White/blue 6 Green 6 Orange 7 White/brown 7 White/brown 8 Brown 8 Brown
1
2
3
4
5
6
7
8
Next, use an Ethernet cross-over cable to connect the laptop to the rear Ethernet port. The pinout for an Ethernet cross­over cable is shown below.
Figure 1–6: ETHERNET CROSS-OVER CABLE PIN LAYOUT
Now, assign the laptop computer an IP address compatible with the relay’s IP address.
1. From the Windows desktop, right-click the My Network Places icon and select Properties to open the network con-
nections window.
1
2. Right-click the Local Area Connection icon and select Properties.
GE Multilin F35 Multiple Feeder Protection System 1-11
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
3. Select the Internet Protocol (TCP/IP) item from the list provided and click the Properties button.
1
4. Click on the “Use the following IP address” box.
5. Enter an IP address with the first three numbers the same as the IP address of the F35 relay and the last number dif­ferent (in this example, 1.1.1.2).
6. Enter a subnet mask equal to the one set in the F35 (in this example, 255.0.0.0).
7. Click OK to save the values.
Before continuing, it will be necessary to test the Ethernet connection.
1. Open a Windows console window by selecting Start > Run from the Windows Start menu and typing “cmd”.
2. Type the following command:
C:\WINNT>ping 1.1.1.1
3. If the connection is successful, the system will return four replies as follows:
Pinging 1.1.1.1 with 32 bytes of data:
Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 4, Lost = 0 (0% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
4. Note that the values for time and TTL will vary depending on local network configuration.
If the following sequence of messages appears when entering the
C:\WINNT>ping 1.1.1.1 command:
1-12 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
Pinging 1.1.1.1 with 32 bytes of data:
Request timed out. Request timed out. Request timed out. Request timed out.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
Verify the physical connection between the F35 and the laptop computer, and double-check the programmed IP address in
PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting, then repeat step 2 in the above procedure.
the
If the following sequence of messages appears when entering the
Pinging 1.1.1.1 with 32 bytes of data:
Hardware error. Hardware error. Hardware error. Hardware error.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
C:\WINNT>ping 1.1.1.1 command:
Verify the physical connection between the F35 and the laptop computer, and double-check the programmed IP address in
PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting, then repeat step 2 in the above procedure.
the
If the following sequence of messages appears when entering the
Pinging 1.1.1.1 with 32 bytes of data:
Destination host unreachable. Destination host unreachable. Destination host unreachable. Destination host unreachable.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milli-seconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
C:\WINNT>ping 1.1.1.1 command:
Verify the IP address is programmed in the local PC by entering the ipconfig command in the command window.
C:\WINNT>ipconfig
Windows 2000 IP Configuration
Ethernet adapter <F4FE223E-5EB6-4BFB-9E34-1BD7BE7F59FF>:
Connection-specific DNS suffix. . :
IP Address. . . . . . . . . . . . : 0.0.0.0
Subnet Mask . . . . . . . . . . . : 0.0.0.0
Default Gateway . . . . . . . . . :
Ethernet adapter Local Area Connection:
Connection-specific DNS suffix . :
IP Address. . . . . . . . . . . . : 1.1.1.2
Subnet Mask . . . . . . . . . . . : 255.0.0.0
Default Gateway . . . . . . . . . :
C:\WINNT>
It may be necessary to restart the laptop for the change in IP address to take effect (Windows 98 or NT).
1
GE Multilin F35 Multiple Feeder Protection System 1-13
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
Before using the Quick Connect feature through the Ethernet port, it is necessary to disable any configured proxy settings in Internet Explorer.
1
1. Start the Internet Explorer software.
2. Select the Tools > Internet Options menu item and click on Connections tab.
3. Click on the LAN Settings button to open the following window.
4. Ensure that the “Use a proxy server for your LAN” box is not checked.
If this computer is used to connect to the Internet, re-enable any proxy server settings after the laptop has been discon­nected from the F35 relay.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE enerVista CD or online from http://www.gegridsolutions.com/multilin). See the Software Installation section for installation details.
2. Start the Internet Explorer software.
3. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
4. Click the Quick Connect button to open the Quick Connect dialog box.
5. Select the Ethernet interface and enter the IP address assigned to the F35, then click Connect.
6. The EnerVista UR Setup software will create a site named “Quick Connect” with a corresponding device also named “Quick Connect” and display them on the upper-left corner of the screen. Expand the sections to view data directly from the F35 device.
Each time the EnerVista UR Setup software is initialized, click the Quick Connect button to establish direct communica­tions to the F35. This ensures that configuration of the EnerVista UR Setup software matches the F35 model number.
When direct communications with the F35 via Ethernet is complete, make the following changes:
1. From the Windows desktop, right-click the My Network Places icon and select Properties to open the network con­nections window.
2. Right-click the Local Area Connection icon and select the Properties item.
3. Select the Internet Protocol (TCP/IP) item from the list provided and click the Properties button.
1-14 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
4. Set the computer to “Obtain a relay address automatically” as shown below.
If this computer is used to connect to the Internet, re-enable any proxy server settings after the laptop has been discon­nected from the F35 relay.
AUTOMATIC DISCOVERY OF ETHERNET DEVICES
The EnerVista UR Setup software can automatically discover and communicate to all UR-series IEDs located on an Ether­net network.
Using the Quick Connect feature, a single click of the mouse will trigger the software to automatically detect any UR-series relays located on the network. The EnerVista UR Setup software will then proceed to configure all settings and order code options in the Device Setup menu, for the purpose of communicating to multiple relays. This feature allows the user to identify and interrogate, in seconds, all UR-series devices in a particular location.
1
GE Multilin F35 Multiple Feeder Protection System 1-15
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
842743A3.CDR
Communications status indicators:
Green = OK Red = No communications UR icon = report is open
Quick action hot links
Expand the site list by double-clicking or selecting the +/– box.
NOTE
1
1. Open the Display Properties window through the Site List tree as shown below:

1.3.5 CONNECTING TO THE F35 RELAY

2. The Display Properties window will open with a status indicator on the lower left of the EnerVista UR Setup window.
3. If the status indicator is red, verify that the Ethernet network cable is properly connected to the Ethernet port on the back of the relay and that the relay has been properly setup for communications (steps A and B earlier).
If a relay icon appears in place of the status indicator, than a report (such as an oscillography or event record) is open. Close the report to re-display the green status indicator.
4. The Display Properties settings can now be edited, printed, or changed according to user specifications.
See chapter 4 in this manual and the EnerVista UR Setup Help File for more information about the using the EnerV­ista UR Setup software interface.
QUICK ACTION HOT LINKS
The EnerVista UR Setup software has several new quick action buttons that provide users with instant access to several functions that are often performed when using F35 relays. From the online window, users can select which relay to interro­gate from a pull-down window, then click on the button for the action they wish to perform. The following quick action func­tions are available:
View the F35 event record.
View the last recorded oscillography record.
View the status of all F35 inputs and outputs.
View all of the F35 metering values.
View the F35 protection summary.
1-16 F35 Multiple Feeder Protection System GE Multilin
1 GETTING STARTED 1.4 UR HARDWARE

1.4UR HARDWARE 1.4.1 MOUNTING AND WIRING

Please refer to Chapter 3: Hardware for detailed mounting and wiring instructions. Review all WARNINGS and CAUTIONS carefully.

1.4.2 COMMUNICATIONS

The EnerVista UR Setup software communicates to the relay via the faceplate RS232 port or the rear panel RS485 / Ether­net ports. To communicate via the faceplate RS232 port, a standard straight-through serial cable is used. The DB-9 male end is connected to the relay and the DB-9 or DB-25 female end is connected to the PC COM1 or COM2 port as described in the CPU communications ports section of chapter 3.
1
Figure 1–7: RELAY COMMUNICATIONS OPTIONS
To communicate through the F35 rear RS485 port from a PC RS232 port, the GE Multilin RS232/RS485 converter box is required. This device (catalog number F485) connects to the computer using a “straight-through” serial cable. A shielded twisted-pair (20, 22, or 24 AWG) connects the F485 converter to the F35 rear communications port. The converter termi­nals (+, –, GND) are connected to the F35 communication module (+, –, COM) terminals. Refer to the CPU communica- tions ports section in chapter 3 for option details. The line should be terminated with an R-C network (that is, 120 Ω, 1 nF) as described in the chapter 3.

1.4.3 FACEPLATE DISPLAY

All messages are displayed on a 2 × 20 backlit liquid crystal display (LCD) to make them visible under poor lighting condi­tions. Messages are descriptive and should not require the aid of an instruction manual for deciphering. While the keypad and display are not actively being used, the display will default to user-defined messages. Any high priority event driven message will automatically override the default message and appear on the display.
GE Multilin F35 Multiple Feeder Protection System 1-17
1.5 USING THE RELAY 1 GETTING STARTED

1.5USING THE RELAY 1.5.1 FACEPLATE KEYPAD

1
Display messages are organized into pages under the following headings: actual values, settings, commands, and targets. The MENU key navigates through these pages. Each heading page is broken down further into logical subgroups.
The MESSAGE keys navigate through the subgroups. The VALUE keys scroll increment or decrement numerical setting values when in programming mode. These keys also scroll through alphanumeric values in the text edit mode. Alterna­tively, values may also be entered with the numeric keypad.
The decimal key initiates and advance to the next character in text edit mode or enters a decimal point. The HELP key may be pressed at any time for context sensitive help messages. The ENTER key stores altered setting values.

1.5.2 MENU NAVIGATION

Press the MENU key to select the desired header display page (top-level menu). The header title appears momentarily fol­lowed by a header display page menu item. Each press of the MENU key advances through the following main heading pages:
Actual values.
Settings.
Commands.
Targets.
User displays (when enabled).

1.5.3 MENU HIERARCHY

The setting and actual value messages are arranged hierarchically. The header display pages are indicated by double scroll bar characters (), while sub-header pages are indicated by single scroll bar characters (). The header display pages represent the highest level of the hierarchy and the sub-header display pages fall below this level. The MESSAGE UP and DOWN keys move within a group of headers, sub-headers, setting values, or actual values. Continually pressing the MESSAGE RIGHT key from a header display displays specific information for the header category. Conversely, contin­ually pressing the MESSAGE LEFT key from a setting value or actual value display returns to the header display.
HIGHEST LEVEL LOWEST LEVEL (SETTING VALUE)
 SETTINGS  PRODUCT SETUP
 SETTINGS  SYSTEM SETUP
The relay is defaulted to the “Not Programmed” state when it leaves the factory. This safeguards against the installation of a relay whose settings have not been entered. When powered up successfully, the Trouble LED will be on and the In Ser­vice LED off. The relay in the “Not Programmed” state will block signaling of any output relay. These conditions will remain until the relay is explicitly put in the “Programmed” state.
Select the menu message
RELAY SETTINGS: Not Programmed
SETTINGS PRODUCT SETUP  INSTALLATION RELAY SETTINGS
PASSWORD SECURITY
ACCESS LEVEL: Restricted

1.5.4 RELAY ACTIVATION

1-18 F35 Multiple Feeder Protection System GE Multilin
Loading...