B+B SmartWorx SmartFlex SR300 User Manual

LAN Industrial Router
SmartFlex SR300
USER MANUAL
SmartFlex SR300
Advantech B+B SmartWorx – Americas
Advantech B+B SmartWorx
Phone +1 (815) 433-5100 Fax +1 (815) 433-5105
Website
www.advantech-bb.com
Advantech B+B SmartWorx – Europe
Advantech B+B SmartWorx s.r.o.
Sokolska 71 562 04, Usti nad Orlici, Czech Republic
Phone +420 465 524 421
Website
www.advantech-bb.com
c
2018 Advantech B+B SmartWorx s.r.o. No part of this publication may be reproduced or transmitted in any form or by any means, electronic or mechanical, including photography, recording, or any information storage and retrieval system without written consent. Information in this manual is subject to change without notice, and does not represent a commitment on the part of Advantech B+B SmartWorx.
Advantech B+B SmartWorx s.r.o. shall not be liable for incidental or consequential damages resulting from the furnishing, performance, or use of this manual.
All brand names used in this manual are the registered trademarks of their respective owners. The use of trademarks or other designations in this publication is for reference purposes only and does not constitute an endorsement by the trademark holder.
i
SmartFlex SR300
Used symbols
Danger – Information regarding user safety or potential damage to the router.
Attention – Problems that can arise in specific situations.
Information, notice – Useful tips or information of special interest.
GPL licence
Source codes under GPL licence are available free of charge by sending an email to:
techSupport@advantech-bb.com.
Please see http://ep.advantech-bb.cz/devzone for more information.
Advantech B+B SmartWorx s.r.o., Sokolska 71, 562 04 Usti nad Orlici, Czech Republic Document No. MAN-0005-EN, revision from June 27, 2018. Released in the Czech Republic.
ii
SmartFlex SR300
Contents
1 Safety Instructions 2
1.1 Hazardous Locations Installation Instructions . . . . . . . . . . . . . . . . . . . 2
1.2 Other Safety Instructions . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 3
2 WEEE directive 4
3 Router Description 5
4 Contents of Package 6
5 Router Design 7
5.1 Router versions . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 7
5.2 Delivery identification . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 8
5.3 Order codes . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 8
5.4 Basic dimensions of the router box . . . . . . . . . . . . . . . . . . . . . . . . . 10
5.5 Mounting recommendations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 10
5.6 Removal of the DIN rail . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 11
5.7 Description of the rear panel . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 12
5.8 Description of the front panel . . . . . . . . . . . . . . . . . . . . . . . . . . . . 12
5.8.1 Status indication . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 13
5.8.2 Power connector PWR . . . . . . . . . . . . . . . . . . . . . . . . . . . . 14
5.8.3 Antenna connector WiFi . . . . . . . . . . . . . . . . . . . . . . . . . . . 15
5.8.4 MicroSD card reader . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 16
5.8.5 Ethernet Ports (ETH0 and ETH1) . . . . . . . . . . . . . . . . . . . . . . 17
5.8.6 Power over Ethernet (PoE) . . . . . . . . . . . . . . . . . . . . . . . . . 18
5.8.7 USB Port . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 20
5.8.8 I/O Port . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 21
5.8.9 Reset . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 23
5.9 Interfaces Description . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 24
5.9.1 SWITCH interface . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 24
6 First Use 25
6.1 Connecting the router before first use . . . . . . . . . . . . . . . . . . . . . . . 25
6.2 Start . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 26
6.3 Configuration . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 26
6.3.1 Configuration over web browser . . . . . . . . . . . . . . . . . . . . . . . 26
7 Technical Parameters 28
iii
SmartFlex SR300
7.1 Basic parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 28
7.2 Standards and regulations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 29
7.3 Type tests and environmental conditions . . . . . . . . . . . . . . . . . . . . . . 30
7.4 Technical parameters of WiFi . . . . . . . . . . . . . . . . . . . . . . . . . . . . 31
7.5 Technical parameters of I/O port . . . . . . . . . . . . . . . . . . . . . . . . . . 31
7.6 Technical Parameters of Power over Ethernet (PoE) . . . . . . . . . . . . . . . 32
7.7 Other Technical Parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 32
8 Recommended Literature 33
9 Troubleshooting 34
9.1 FAQ . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 34
10 Customers Support 36
10.1 Customer Support for NAM . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 36
10.2 Customer Support for Europe . . . . . . . . . . . . . . . . . . . . . . . . . . . . 36
10.3 Customer Support for Asia . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 36
iv
SmartFlex SR300
List of Figures
1 Contents of package . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 6
2 Version SWITCH (plastic) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 7
3 Version SWITCH and WiFi (plastic) . . . . . . . . . . . . . . . . . . . . . . . . . 7
4 Version SWITCH (metal) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 7
5 Version SWITCH and WiFi (metal) . . . . . . . . . . . . . . . . . . . . . . . . . 7
6 Label examples . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 8
7 Basic dimensions of the router box . . . . . . . . . . . . . . . . . . . . . . . . . 10
8 Default position of DIN holder . . . . . . . . . . . . . . . . . . . . . . . . . . . . 11
9 Removal of the DIN rail . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 11
10 SPECTRE v3 ERT front panel . . . . . . . . . . . . . . . . . . . . . . . . . . . . 12
11 Power connector . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 14
12 Connection of power supply . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 14
13 Antenna connector . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 15
14 MicroSD card . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 16
15 Ethernet connector . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 17
16 Connection of Ethernet cable . . . . . . . . . . . . . . . . . . . . . . . . . . . . 17
17 PoE PD usage . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 18
18 PoE PSE usage . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 19
19 USB connector . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 20
20 I/O connector . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 21
21 Binary inputs connection . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 22
22 Binary output connection . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 22
23 Router reset . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 23
24 Version with SWITCH board . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 24
25 Router connection . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 25
26 Entering the IP address of the router . . . . . . . . . . . . . . . . . . . . . . . . 26
27 Entering login information . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 26
28 Router web interface . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 27
v
SmartFlex SR300
List of Tables
1 Router versions . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 7
2 Delivery identification . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 8
3 Order codes overview . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 8
4 Power over Ethernet . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 8
5 Type of router box . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 9
6 Type of power supply . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 9
7 Examples of order code . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 9
8 Front panel description . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 12
9 Status indication . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 13
10 Connection of power connector . . . . . . . . . . . . . . . . . . . . . . . . . . . 14
11 Technical specifications of microSD card . . . . . . . . . . . . . . . . . . . . . . 16
12 Connection of Ethernet connector . . . . . . . . . . . . . . . . . . . . . . . . . . 17
13 Insulation strength of Ethernet ports . . . . . . . . . . . . . . . . . . . . . . . . 17
14 Connection of USB connector . . . . . . . . . . . . . . . . . . . . . . . . . . . . 20
15 Connection of I/O port . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 21
16 Characteristics of inputs . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 21
17 Description of reset and restart router . . . . . . . . . . . . . . . . . . . . . . . 23
18 State indication of the SWITCH interface . . . . . . . . . . . . . . . . . . . . . . 24
19 SWITCH interface parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . 24
20 Basic parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 28
21 Standards and regulations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 29
22 Type tests and environmental conditions . . . . . . . . . . . . . . . . . . . . . . 30
23 Technical parameters of WiFi . . . . . . . . . . . . . . . . . . . . . . . . . . . . 31
24 Characteristics of inputs . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 31
25 PoE PD: parameters for opposite PSE . . . . . . . . . . . . . . . . . . . . . . . 32
26 PoE PSE parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 32
27 Other technical parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . 32
1
SmartFlex SR300
1. Safety Instructions
Please, observe the following instructions:
1.1 Hazardous Locations Installation Instructions
These devices are open-type devices that are to be installed in an enclosure suitable for the environment and can only be accessed with the use of a tool or key.
This equipment is suitable for use in Class I, Division 2, Groups A, B, C, AND D OR non­hazardous locations only.
WARNING – EXPLOSION HAZARD – DO NOT DISCONNECT EQUIPMENT UNLESS PO­WER HAS BEEN REMOVED OR THE AREA IS KNOWN TO BE NON-HAZARDOUS.
WARNING – EXPLOSION HAZARD – SUBSTITUTION OF ANY COMPONENTS MAY IM­PAIR SUITABILITY FOR CLASS I, DIVISION 2.
WARNING – EXPLOSION HAZARD – BATTERIES MUST ONLY BE CHANGED IN AN AREA FREE OF IGNITIBLE CONCENTRATION.
All antennas, antenna cables and wiring have not been evaluated as external wiring.
Cet équipement est convenable en Classe 1, Division 2, Groupes A, B, C, et D endroits dangereux OU endroits non dangereux seulement.
AVERTISSEMENT – RISQUE D’EXPLOSION – NE DÉCONNECTEZ PAS L’ÉQUIPEMENT, SAUF SI L’ALIMENTATION A ÉTÉ COUPÉE OU SI L’ENVIRONMEMENT EST CLASSÉ NON DANGEREUX.
AVERTISSEMENT – RISQUE D’EXPLOSION - SUBSTITUTION DE TOUTE COMPOSANTE RISQUERAIT LA QUALITÉ POUR CLASSE 1, DIVISION 2.
AVERTISSEMENT - RISQUE D’EXPLOSION - LES BATTERIES DOIVENT ÊTRE REMPLACÉ­ES DANS UN ENDROIT EXEMPT DE CONCENTRATIONS INFLAMMABLES.
This equipment shall be mounted in an ATEX Zone 2 certified enclosure with a minimum ingress protection rating of at least IP54 (as defined in EN 60529) and used in an environment of not more than Pollution Degree 2 (as defined in EN 60664-1) when applied in Zone 2 environments. The enclosure must be accessible only by the use of a tool.
Provision shall be made to prevent the rated voltage from being exceeded by transient distur­bances of more than 140 % of the rated voltage when applies in Zone 2 environments.
2
SmartFlex SR300
1.2 Other Safety Instructions
The router must be used in compliance with all applicable international and national laws and in compliance with any special restrictions regulating the utilization of the router in prescribed applications and environments.
To prevent possible injury and damage to appliances and to ensure compliance with all relevant provisions, use only the original accessories. Unauthorized modifications or the use of unapproved accessories may result in damage to the router and / or a breach of applicable regulations. Unauthorized modifications or use of unapproved accessories may void the warranty.
The router can not be opened.
Power supply must not exceed 60 V DC max.
Do not expose the router to extreme ambient conditions. Protect the router against dust,
moisture and high temperature.
Only routers with appropriate certification and labelling should be used in locations where flammable and explosive materials are present, including gas stations, chemical plants, or locations in which explosives are used. We remind the users of te duty to observe the restrictions concerning the utilization of radio devices at petrol stations, in chemical plants, or in the course of blasting works in which explosives are used.
Switch off the router when travelling by plane. Utilization of the router in a plane may endanger the operation of the plane or interfere with the mobile telephone network, and may be unlawful. Failure to observe these instructions may result in the suspension or cancellation of telephone services for the respective client, or, it may result in legal sanctions; it may also result in both eventualities.
When using the router in the close proximity of personal medical devices, such as cardiac pacemakers or hearing aids, you must proceed with heightened caution.
The router may cause interference when used in close proximity to TV sets, radio re­ceivers or personal computers.
It is recommended that you create an appropriate copy or backup of all important settings that are stored in the memory of the device.
3
SmartFlex SR300
2. Product Disposal Instructions
The WEEE (Waste Electrical and Electronic Equipment: 2012/19/EU) directive was in­troduced to ensure that electrical/electronic products are recycled using the best available recovery techniques in order to minimize impact on the environment. This product contains high quality materials and components which can be recycled. At the end of it’s life this pro­duct MUST NOT be mixed with other commercial waste for disposal. The device contains the battery. Remove the battery from the device before disposal. The battery in the device needs to be disposed apart accordingly. Check the terms and conditions of your supplier for disposal information.
4
SmartFlex SR300
3. Router Description
LAN Industrial router SmartFlex SR300 is an ideal device for the realization of a secure connection of two local area networks (LANs). Interconnection is carried out using two ETH­ERNET 10/100 interfaces and secure tunnel (IPSec, OpenVPN, L2TP).
The other equally important ways to use this router is to connect any device with RS232, RS485 or I/O interface to the local network (LAN). For this purpose, SmartFlex SR300 is equipped with two ETHERNET 10/100 ports and other interfaces based on the version of the router chosen by the user.
As a standard, this router is equipped with two ETHERNET 10/100 ports, one USB 2.0 Host port, two binary inputs and one output (I/O connector). An integral part of the router is also a memory card reader placed on the rear panel. This reader allows SmartFlex SR300 to operate with microSD cards and increase storage space of the router up to 64 GB (32 GB in case of SDHC cards). The router can be equipped with WiFi module on customer’s request, however it is not possible to order it and add to the router later. The router can be equipped with PoE PD (Power over Ethernet – powered device) to power the router via Ethernet, or PoE PSE (power source equipment) to power other devices by the router. Richer range of interfaces is available in versions containing three switched Ethernets. SmartFlex SR300 is supplied either in a plastic or metal casing, based on the requirements of the customer.
For configuration of the industrial router is available web interface protected by password. Web interface provides (after logging in) detailed statistics about the router activities, signal strength, detailed system log etc. This device supports the creation of VPN tunnels using tech­nologies IPSec, OpenVPN and L2TP for secure communications. There are also supported functions such as DHCP, NAT, NAT-T, DynDNS, NTP, VRRP, control by SMS, backup primary connection and many other functions.
Other diagnostic functions ensuring continuous communication include hardware watch­dog which monitors the status of the router. Using a special window (start up script window) you may insert Linux scripts for various actions. For some applications is crucial the possibility to create several different configurations for one router. These configurations can be switched as necessary (for example using SMS, binary input status, etc.). SmartFlex routers may auto­matically upgrade configuration and firmware from server. This allows mass reconfiguration of many routers in one time.
The router also supports additional software like R-SeeNet for permanent traffic monitoring of routers.
Examples of possible applications
mobile office
fleet management
security system
telematic
telemetric
remote monitoring
vending and dispatcher machines
5
SmartFlex SR300
4. Contents of Package
Basic delivered set of router includes:
router,
power supply,
crossover UTP cable,
2.4 GHz WiFi antenna (only for version with WiFi),
loose power and I/O connector (+8 pins∗),
clip for the DIN rail,
paper start guide.
Figure 1: Contents of package
Temperature range for power supply is reduced to 0◦C to +40◦C!
These pins are designed for cables with a diameter from 0.2 to 0.8 mm
2
6
SmartFlex SR300
5. Router Design
5.1 Router versions
SmartFlex SR300 router is supplied in the following versions (see table below). All versions are available in plastic or metal box according to customer requirements. All versions are available with PoE PD (Power over Ethernet – powered device) so you can power the router from both ETH0 and ETH1 interfaces, or with PoE PSE (power source equipment) so you can power other devices by the router.
Router versions
BIN
BOUT
USB
SD
ETH
WiFi
Version with SWITCH board 2 x 1 x 1 x 1 x 5 x Version with SWITCH board & WiFi 2 x 1 x 1 x 1 x 5 x 1 x
Table 1: Router versions
Figure 2: Version SWITCH (plastic)
Figure 3: Version SWITCH and WiFi (plastic)
Figure 4: Version SWITCH (metal)
Figure 5: Version SWITCH and WiFi (metal)
7
SmartFlex SR300
5.2 Delivery identification
Trade name Product name Description
SmartFlex SR300 SmartFlex Router in a plastic or metal box
Table 2: Delivery identification
Figure 6: Label examples
5.3 Order codes
Order codes overview is shown in the table below.
Product Name Order code Features – interfaces
SR300 BB-SR3000x1yz
5x ETH, 1x USB, 2x BI, 1x BO, 1x microSD reader,
SR300 BB-SR3001x1yz
5x ETH, 1x USB, 2x BI, 1x BO, 1x microSD reader, WiFi
Table 3: Order codes overview
Replace the letters "x", "y" and "z" with the values from the following tables:
Letter "x" – Power over Ethernet (PoE)
Power over Ethernet (PoE) Number "x" in code
Version without PoE 0 PoE PSE – Power Source Equipment – powers other devices 8 PoE PD – Powered Device – can be powered via Ethernet 9
Table 4: Power over Ethernet
8
SmartFlex SR300
Letter "y" – type of the router box
Type of box Number "y" in code
Plastic 1 Metal 2
Table 5: Type of router box
Letter "z" – type of the power supply connector
Type of power supply Number "z" in code
Europe 1 UK & Ireland 2 Australia 3 North America 4 Without accessories 0
Table 6: Type of power supply
Examples of complete order code:
Order code Features – interfaces Box Power
supply
BB-SR30008111 5x ETH, 1x USB, 2x BI, 1x BO, 1x microSD reader,
PoE PSE
plastic Europe
BB-SR30019121 5x ETH, 1x USB, 2x BI, 1x BO, 1x microSD reader,
WiFi, PoE PD
metal Europe
BB-SR30000113 5x ETH, 1x USB, 2x BI, 1x BO, 1x microSD reader plastic Australia BB-SR30010120 5x ETH, 1x USB, 2x BI, 1x BO, 1x microSD reader,
WiFi
metal None
Table 7: Examples of order code
You can use the order codes configurator on the www.bb-smartcellular.eu web pages.
9
SmartFlex SR300
5.4 Basic dimensions of the router box
Figure 7: Basic dimensions of the router box
5.5 Mounting recommendations
Possibility to be put on a work surface,
DIN rail EN 60715 with included plastic or metal clip.
For the most of applications with a built-in router in a switch board it is possible to recognize two kinds of environments:
no public and industry environment of low voltage with high interference,
public environment of low voltage without high interference.
For both of these environments it is possible to mount router to a switch board, the following there is no need to have examination immunity or issues in connection with EMC according to EN 60439-1 ed.2:00 + A1:04.
Attention: If the negative pole of the router is grounded, there is no protection against reversed polarity!
Compliance of EN 60439-1 ed.2:00 + A1:04 specification it is necessary to observe next assembly of the router to the switch – board:
For every cables we recommend to bind the bunch, we recommend for this use:
– Length of the bunch (combination of power supply and data cables) can be maxi-
mum 1.5 m. If the length of data cables exceeds 1.5 m or in the event of, the cable leads towards the switch – board. We recommend installing over – voltage protec­tors (surge suppressors).
– With data cables they mustn’t carry cables with reticular tension 230 V/50 Hz.
10
SmartFlex SR300
Sufficient space must be left before individual connectors for handling of cables,
For correct function of the router we recommend to use in the switch-board earth-bonding
distribution frame for grounding of power supply of router, data cables and antenna.
5.6 Removal of the DIN rail
The DIN holder is suitable for a DIN rail according to EN 60715 standard only. The default position of plastic or metal holder, which is used for mounting the router on a DIN rail, is shown in the following figure. Its position can be changed on some models (back or bottom). When changing the position of the DIN holder, tighten the screws with max. 0.4 Nm torque.
Figure 8: Default position of DIN holder
In order to remove the DIN rail it is necessary to lightly push the router upward so that the top part of the DIN holder hitched to the DIN rail comes out of this rail, then fold the top of the router away from the DIN rail.
Figure 9: Removal of the DIN rail
11
SmartFlex SR300
5.7 Description of the rear panel
The rear panel contains only one holder for SD card (SD) and RST button used to restore default configuration and reboot the router.
5.8 Description of the front panel
On the front panel is the following:
Caption Connector Description
PWR 2-pin Connector for the power supply ETH0 RJ45 Connector for connection into the computer network, PoE (only
for PoE PSE or PoE PD versions)
ETH1 RJ45 Connector for connection into the computer network, PoE (only
for PoE PSE or PoE PD versions)
WiFi R-SMA Connector for WiFi antenna (only for versions with WiFi
module!)
USB USB-A 2.0
Host
Connector for connection of USB devices to the router. Sup­ports devices with PL-2303 and FTDI USB/RS232 converters.
I/O 6-pin Connector for connection of the binary inputs and output
Table 8: Front panel description
Figure 10: SPECTRE v3 ERT front panel
12
SmartFlex SR300
5.8.1 Status indication
About router status inform nine LED indicators on the front panel. Each ETH port has two additional LEDs that provide information about port status.
Caption Color State Description
PWR Green Blinking
On Fast blinking
Router is ready Starting of the router
Updating firmware USR Yellow Function of this LED diode can be selected by user POE Yellow
Green
On Blinking On
Blinking Off
PSE: insufficient power supply via PWR connector
PSE: overload (device takes much power)/short circuit*
PoE PD versions: The voltage present in ETH port
PSE: correct power supply via PWR connector
PSE: The device is powered via one of the ETH ports
PD: The voltage not present in ETH port
PSE: disabled (not enabled on any of ETH ports) IN0 Green On Binary input no. 0 is active IN1 Green On Binary input no. 1 is active OUT Yellow On Binary output is active ETH0
ETH1
Green On
Off
Selected 100 Mbit/s
Selected 10 Mbit/s ETH0
ETH1
Yellow On
Blinking Off
The network cable is connected
Data transmission
The network cable is not connected
Table 9: Status indication
* Additionaly it can indicate a device without PoE support connected on the other side of the cable. In this case the indication is caused by low impedance (lesser than 500 ) of this device without PoE support. You can solve this by disabling the PoE PSE feature on the proper ETH port in the router’s Web interface, see Configuration manual for SmartFlex routers [2].
State indication of WAN LED is updated every 10 seconds.
13
SmartFlex SR300
5.8.2 Power connector PWR
Panel socket 2-pin.
Pin number Signal mark Description
1 GND(-) Negative pole of DC supply voltage 2 VCC(+) Positive pole of DC supply voltage (+10 to +60 V DC)
Table 10: Connection of power connector
Figure 11: Power connector
Unit has to be supplied by a power supply specified as a Limited Power Source (LPS) ac­cording to clause 2.5 of IEC/UL 60950-1 or CEC/NEC Class 2 source of supply as defined in the Canadian Electrical Code, CSA C22.1 and National Electrical Code, ANSI/NFPA 70. If the power supply/cable provided with device is not used, always use the cables with minimum wire size (nominal cross section) 0.5 square mm for power supply.
The power supply for the router must be between +10 V to +60 V DC supply. Protection against reversed polarity without signaling is built into the router. Note: The protection against reversed polarity is lost if the negative pole is grounded!
The router can be put into low power mode using a special command lpm. It can then be awakened, for example, by an activity on binary input or using an internal timer. Consumption in LPM mode may vary depending on the configuration of the router.
Circuit example:
Figure 12: Connection of power supply
Note for PoE: See Chapter 5.8.6 for information on how PoE versions of the router impact the power supply usage. The power supply for a PoE PSE router has to meet other specific requirements.
14
SmartFlex SR300
5.8.3 Antenna connector WiFi
If the router is equipped with WiFi module on the customer’s request, appropriate antenna is connected to the reverse SMA connector (WiFi).
The extarnal antenna is connected by screwing this antenna to the reverse SMA connector on the front panel of the router (see figure below).
Figure 13: Antenna connector
15
SmartFlex SR300
5.8.4 MicroSD card reader
The microSD card reader is placed on the rear panel of the router (there is only a single slot). This card reader allows the router to operate with memory cards microSD. Technical specifications are stated in the table below.
Technical specifications of microSD card
Supported technologies SDHC, SDXC Supported capacity SDHC
SDXC
up to 32 GB from 32 GB to 64 GB
Supported microSD card filesystems vfat, ext2, ext3, ext4*
Table 11: Technical specifications of microSD card
* Supported only with Ext4_tools User Module installed in the router.
Changing the microSD card:
Use the flat end of a spudger, or your fingernail, to press the microSD card slightly deeper into its slot until you hear a click.
After the click, release the card and it will pop out of its slot.
Remove the microSD card and push any other microSD card into the slot until it
clicks in place.
Figure 14: MicroSD card
Mounting microSD card to the system: To use the microSD card in the Linux system of the router, it is necessary to mount it. Use dmesg command to see the name of recently connected device (E. g. mmcblk0: p1) and then use mount command. Example:
mount /dev/mmcblk0p1 /mnt
16
SmartFlex SR300
5.8.5 Ethernet Ports (ETH0 and ETH1)
Panel socket RJ45.
Pin Signal mark Description Data flow direction
1 TXD+ Transmit Data – positive pole Input/Output 2 TXD- Transmit Data – negative pole Input/Output 3 RXD+ Receive Data – positive pole Input/Output 4 DC+ PoE power + (if it’s equipped by PoE) 5 DC+ PoE power + (if it’s equipped by PoE) 6 RXD- Receive Data – negative pole Input/Output 7 DC- PoE power - (if it’s equipped by PoE) 8 DC- PoE power - (if it’s equipped by PoE)
Table 12: Connection of Ethernet connector
Figure 15: Ethernet connector
The crossover UTP cable (Ethernet cable) plugs into the RJ45 connector labeled as ETH0
or ETH1 (see figure below).
Figure 16: Connection of Ethernet cable
The insulation strength of Ethernet ports from each other and from the rest of the router (grounding) is dependent on the router version:
Router Version Insul. Strength from Router Insul. Strength between Ports
Without PoE 1.5 kV 1.5 kV PoE PD 1.5 kV none PoE PSE none none
Table 13: Insulation strength of Ethernet ports
17
SmartFlex SR300
5.8.6 Power over Ethernet (PoE)
On the router models with PoE, the PoE+ standard IEEE 802.3at-2009 and PoE standard IEEE 802.3af-2003 are supported in both Ethernet ports (ETH0, ETH1). The PoE PD version allows the router to be powered over the Ethernet by another PoE PSE device. The PoE PSE version also allows the router to power other devices over the Ethernet.
PoE PD
Figure 17: PoE PD usage
The PoE PD parameters can be found in Chapter 7.6. The POE LED on the front panel of the router lights up green when voltage is present in an Ethernet port so the user knows the router can be PoE powered. You can still power the router with this connector even if the router is powered with PoE (in PoE PD version), but the input voltage must be higher than 15 V DC. If the input voltage is lower than 15 V DC and the PoE voltage is present (PoE LED green on), the router will still be powered from the Ethernet connector via PoE.
Note: You can not power the router via the ETH2 ports on the SWITCH router version. The PoE PD is available on the ETH0 and ETH1 ports only.
18
SmartFlex SR300
PoE PSE
Figure 18: PoE PSE usage
The power supply used with the PoE PSE router has to provide voltage from 44 to 57 V DC and the output power has to be at least 65 W for full PoE+ use (Class 4) in both Ethernet ports (ETH0 and ETH1).
The PoE PSE parameters can be found in Chapter 7.6. The PoE state is indicated by the POE LED on the front panel of the router, see Chap. 5.8.1. When sufficient voltage (44 to 57 V) and power is available is indicated by the green light. A yellow POE LED indicates insufficient power or voltage through the PWR connector. When a device is being powered from the router, the POE LED is will show blinking green. Yellow blinking is shown for an overload (the powered device is using too much power) or a short circuit (incorrect wiring of the cable or of the device without PoE support).
You can enable or disable the PoE PSE feature separately on the ETH0 and ETH1 ports via the Web interface of the router. This can be found in the LAN configuration pages (Primary for ETH0, Secondary for ETH1). When PoE PSE is enabled, you can find the current, voltage, power and power class information on the General page of the router’s Web interface. See the Configuration manual [2]. Via SSH or in scripts you can use the Shell command pse.
19
SmartFlex SR300
5.8.7 USB Port
Panel socket USB-A.
Pin Signal mark Description Data flow direction
1 +5 V Positive pole of 5 V DC supply voltage, 0.5 A 2 USB data - USB data signal – negative pole Input/Output 3 USB data + USB data signal – positive pole Input/Output 4 GND Negative pole of DC supply voltage
Table 14: Connection of USB connector
Figure 19: USB connector
The USB port is disabled on overload to prevent its damage (connected device is trying to get too high current). The port is enabled again af ter reboot of the router.
Mounting USB flash drive to the system: To use the USB flash drive in the Linux system of the router, it is necessary to mount it. Use dmesg command to see the name of recently connected device (E. g. sda: sda1) and then use mount command. Example:
mount /dev/sda1 /mnt
20
SmartFlex SR300
5.8.8 I/O Port
Panel socket 6-pin.
Pin Signal mark Description
1 IN0 Binary input 0 2 IN0 Binary input 0 3 IN1 Binary input 1 4 IN1 Binary input 1 5 OUT Binary output 6 OUT Binary output
Table 15: Connection of I/O port
Figure 20: I/O connector
The I/O user Interface is designed for the processing of binary input and control (setting) of binary output. Binary output is open in the default configuration. The isolation strength is
1.5 kV. The pins are isolated from each other with the same strength.
The input circuits are bipolar and allow connection as needed with common plus or minus (according to the connection of an external voltage).
Binary inputs
Characteristics of inputs:
logical 0 / 1
Voltage Current Web interface status
log. 1 max 3 V 0.4mA Off log. 0 min 5V 0.7mA On log. 0 type 12 V 2 mA On log. 0 max 60 V 7 mA On
Table 16: Characteristics of inputs
The binary input status in the Shell is returned via io get bin0 or io get bin1.
21
SmartFlex SR300
Binary inputs connection example:
Figure 21: Binary inputs connection
Binary output
Binary output parameters:
60 V AC/ 300 mA60 V DC /300 mA
The current of the binary output is limited by a resettable fuse (300 mA).
Binary output connection example:
Figure 22: Binary output connection
22
SmartFlex SR300
5.8.9 Reset
When PWR LED starts flashing on the front panel, it is possible to restore the default con­figuration of the router by pressing the RST button on the rear panel. After pressing this button the default configuration is restored and then router reboots (green LED will be on).
For pressing the RST button could be used a narrow screwdriver.
Figure 23: Router reset
We recommend backing up configuration of the router (see Configuration manual ) be­cause reset of the router sets the configuration to the default state.
It is important to distinguish between reset and reboot the router.
Action Router behavior Invoking events
Reboot Turn off and then turn on router Disconnect and connect the power,
Press the Reboot button in the web configuration
Reset Restore default configuration and reboot
the router
Press RST button
Table 17: Description of reset and restart router
23
SmartFlex SR300
5.9 Interfaces Description
There are available versions with one of the following inter faces:
SWITCH interface
5.9.1 SWITCH interface
Three LAN ports of SWITCH interface for SmartFlex routers (RJ45 connectors for connect­ing Ethernet devices) act as a typical switch device. This means that the router reads Ethernet frames (data packets on an Ethernet link) from any port on SWITCH interface and transmits them on other ports of the SWITCH interface. Each port can transmit frames independently on the other ports. State indication is provided on every connector. Router in this version com­plies with the standards and temperature ranges declared in Chap. 7.1 except for the lower maximum operating temperature which is +70◦C.
Figure 24: Version with SWITCH board
State indication of the interface:
Description of indication
Green LED On
Off
Selected 100 Mbps Selected 10 Mbps
Yellow LED On
Blinking Off
The network cable is connected Data transmission The network cable is not connected
Table 18: State indication of the SWITCH interface
Technical specification of Ethernet IEEE 802.3:
Ethernet interface, IEEE 802.3 standard
Maximum data rate 100 Mbps Max. total cable length (300 Bd, 200 nF/km) 100 m
Table 19: SWITCH interface parameters
24
SmartFlex SR300
6. First Use
6.1 Connecting the router before first use
Before putting the router into operation it is necessary to connect all components which are required to run your applications.
The router can not operate without connected power supply.
Figure 25: Router connection
25
SmartFlex SR300
6.2 Start
The router is put into operation when the power supply is connected to this router. By default, the router will automatically start to log on to the default APN. DHCP server will start to assign addresses for devices on the Ethernet port ETH0. Router behavior can be changed via the web interface. This is described in detail in the Configuration manual for SmartFlex routers.
6.3 Configuration
6.3.1 Configuration over web browser
For status monitoring, configuration and administration of the router is available a web interface which can be accessed by entering the IP address of the router into the web browser. The default IP address of the router is 192.168.1.1. Attention, it is necessary to use HTTPS
protocol for secure communication over a network!
Figure 26: Entering the IP address of the router
Configuration may be performed only by the user "root" with default password "root".
Figure 27: Entering login information
26
SmartFlex SR300
After successfully entering login information user gains access to the router via his internet browser.
Figure 28: Router web interface
A detailed description of the router settings via the Web interface can be found in the document Configuration manual for SmartFlex routers.
27
SmartFlex SR300
7. Technical Parameters
7.1 Basic parameters
SmartFlex SR300
Temperature range Operating
Storage
-40◦C to +80◦C
-40◦C to +85◦C Cold start -40◦C Humidity Operating
Storage
0 to 95 % relative humidity non condensing
0 to 95 % relative humidity non condensing Altitude Operating 2000 m / 70 kPa Degree of protection IP30 Supply voltage 10 to 60 V DC Battery for RTC CR1225 Consumption Idle
Average Peak Sleep mode
2 W
3.3 W
4.5 W
10 mW Dimensions 55 x 97 x 125 mm (DIN 35 mm, EN 60715) Weight Plastic box
Metal box
approximately 211 g (depends on interface)
approximately 327 g (depends on interface) Antenna connectors Reverse SMA – 50 (only for versions with
WiFi module) User interface 2x ETH
USB I/O Micro SD
Ethernet (10/100 Mbps)
USB 2.0
6-pin panel soc ket
SDHC, SDXC
Table 20: Basic parameters
28
SmartFlex SR300
7.2 Standards and regulations
The router complies with the following standards and regulations:
Standards and regulations
Radio ETSI EN 300 328 V2.1.1, ETSI EN 301 893 V2.1.1 EMC ETSI EN 301 489-1 V1.9.2, ETSI EN 301 489-1 V2.1.1,
ETSI EN 301 489-17 V3.1.1
Safety EN 60950-1:2006 + A11:2009 + A1:2010 + A12:2011
+ A2:2013 + AC:2011, EN 62311:2008 UL C1D2 and ATEX: UL 60950-1, 2nd ed. + am1 + am2 * CAN/CSA C22.2 No. 60950-1-07, 2nd ed. + am1 + am2 * UL E486108 * ATEX II 3 G Ex nA IIC T4 Gc, DEMKO 16 ATEX 1801X *
Table 21: Standards and regulations
* Excluding versions with PoE PSE.
29
SmartFlex SR300
7.3 Type tests and environmental conditions
Phenomena Test Description Test levels
ESD EN 61000-4-2 Enclosure contact
Enclosure air
± 6 kV (crit. A) ± 8 kV (crit. A)
RF field AM modulated
EN 61000-4-3 Enclosure 20 V/m (crit. A)
(80 – 2700 MHz) 3 V/m (crit. A) (2700 – 6000 MHz)
Fast transient EN 61000-4-4 Signal ports
Power ports Ethernet ports
± 2 kV (crit. A) ± 2 kV (crit. A) ± 2 kV (crit. A)
Surge EN 61000-4-5 Ethernet ports
Power ports I/O ports
± 2 kV (crit. B), shielded cab. ± 0,5 kV (crit. B) ± 1 kV, L to L (crit. A) ± 2 kV, L to GND (crit. A)
RF conducted EN 61000-4-6 All ports 10 V/m (crit. A)
(0,15 – 80 MHz) Radiated emission EN 55022 Enclosure Class B Conducted
emission
EN 55022 DC power ports
Ethernet ports
Class B
Class B Power frequency
magnetic field
EN 61000-4-8 Enclosure 160 A/m (crit. A)
Dry heat EN 60068-2-2 +75◦C *, 40 % rel. humidity Cold EN 60068-2-1 -40◦C *
Table 22: Type tests and environmental conditions
* The temperatures given are for the basic version of the router. These can vary for other versions.
30
SmartFlex SR300
7.4 Technical parameters of WiFi
WiFi
Antenna connector R-SMA – 50 Supported WiFi band 2.4 GHz, 5 Ghz Standards 802.11a, 802.11b, 802.11g, 802.11n
2.4 GHz supported channels 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13 5 GHz supported channels
36, 38, 40, 42, 44, 46, 48, 52, 56, 60, 64, 100, 104, 108, 112, 116, 120, 124, 128, 132, 136, 140, 149, 153, 157,
161, 165 Type of device Access point, station Max. clients in AP mode 10 WiFi TX Output Power 17,3 dBm WiFi RX Sensitivity -96,3 dBm
Table 23: Technical parameters of WiFi
7.5 Technical parameters of I/O port
Characteristics of inputs:
logical 0 / 1
Voltage Current Web interface status
log. 1 max 3 V 0.4mA Off log. 0 min 5 V 0.7 mA On log. 0 type 12 V 2 mA On log. 0 max 60 V 7 mA On
Table 24: Characteristics of inputs
The binary input status in the Shell is returned via io get bin0 or io get bin1.
Binary output parameters:
60 V AC/ 300 mA60 V DC /300 mA
The number of supported channels depends on selected Country Code.
31
SmartFlex SR300
7.6 Technical Parameters of Power over Ethernet (PoE)
Standards IEEE 802.3at-2009 (PoE+) and IEEE 802.3af-2003 (PoE) are supported. Ca-
bling needed is Category 5, up to 12.5 . It is possible to use a passive PoE injector.
PoE PD: parameters for opposite PSE
Input voltage range 42.5 – 57 V Power available 25.50 W Maximum current 600 mA
Table 25: PoE PD: parameters for opposite PSE
PoE PSE parameters
Power supply needed 44 – 57 V, 65 W Power available 2x 25.50 W (ETH0, ETH1)
Table 26: PoE PSE parameters
7.7 Other Technical Parameters
Other technical parameters
CPU power 2 DMIPS per MHz Flash memory 256 MB RAM 512 MB M-RAM 128 kB
Table 27: Other technical parameters
32
SmartFlex SR300
8. Recommended Literature
[1] Advantech B+B SmartWorx: Start Guide, [2] Advantech B+B SmartWorx: Configuration Manual for SmartFlex Routers.
33
SmartFlex SR300
9. Troubleshooting
If you cannot connect to the router from your PC, your network card may be configured in such a way that it is not possible to connect to the router. Take one or more of the following steps in order to solve the problem:
Make sure your PC’s network card is configured to obtain the IP address form the DHCP server (by default the DHCP server is running in the router).
Set the communication rate to 10 MB/s in the properties of your network card.
Connect the router to the PC via Switch.
Connect the router to the PC, start the router first and then start the PC after the
router’s initialization.
9.1 FAQ
- The router reboots itself and the Ethernet connection fails.
The router will not work well without an antenna. Keep the antenna as far as possi-
ble from the power supply.
- Ethernet connection fails or is not establishing.
It is possible to turn auto negotiation off and set a rate and duplex manually on the
Ethernet interface of the router. Available on "LAN Configuration" page in the router.
- I cannot connect from the Internet to the device behind the router. I have NAT
enabled.
The device’s gateway has to be configured so it points to the router.
- I can’t access my Web server placed behind the router over NAT.
The remote HTTP access to the router has to be disabled on "NAT Configuration"
page in the router. Also enable "Send all remaining incoming packets to default server" feature and fill in the IP address of your Web server. On the Web server, the default gateway has to be the IP address of the router.
- DynDNS doesn’t work.
If the same IP address is recorded in your canonic name as a dynamically assigned
address, it means that the provider is using NAT or a firewall.
You can verify NAT using ping to your ser ver with static address and then compare
with router’s IP address.
34
SmartFlex SR300
You can verify a Firewall by accessing remotely to the router’s Web interface.
The operator may not provide the address of DNS server and without DNS server’s
address it is impossible to connect to the dyndns.org server. The following mes­sages will be shown in the System Log:
DynDNS daemon startedError resolving hostname: no such file or directoryConnect to DynDNS server failed
- L2TP or IPSec isn’t establishing.
Chec k the "System Log" page for error messages.
- IPSec tunnel establishes but the communication does not run.
Probably there are bad routing rules defined in the connected devices, or the default
gateway.
- Serial communication is not working.
Verify that the router model supports serial communications. Also verify the serial
communication settings. To do so, open the router’s configuration menu via the web browser, select the appropriate "Expansion Port" from "Configuration" part of the menu and verify the settings.
- Is the router Cisco compatible? Can I use the Cisco configuration?
No, the Firmware in the router (Conel OS) is based on Linux with BusyBox. Thus
the Cisco configuration cannot be used. But network connections are defined by standards so connecting the router to the Cisco or other networking devices is pos­sible and will be compatible.
- FTP or SFTP does not work
FTP will work on v2 routers only. You can use SFTP on all routers to transfer files
to/from the router. If having troubles with FTP on v2 routers, make sure you have FTP enabled: "Configuration" section, "Services", "FTP". Then you can connect with any client on port 21 with name and password same as for the Web interface. If having troubles with SFTP, make sure you have SSH enabled: "Configuration" section, "Services", "SSH". Then you can connect with any client on port 22 with name and password same as for the Web interface.
- How can I connect to the router’s command line? (SSH, Telnet)
You can use SSH on all routers or Telnet on v2 routers only. SSH is enabled by
default, but you can verify in Web interface in "Configuration" section, "Services", "SSH". Then connect with any SSH client on port 22 of the router. User and pass­word is the same as for the Web inter face. Telnet on v2 routers can be enabled here: "Configuration" section, "Services", "Telnet".
35
SmartFlex SR300
10. Customers Support
10.1 Customer Support for NAM
Phone: +1-800-346-3119 (Monday – Friday, 7 a.m. to 5:30 p.m. CST) Fax: +1-815-433-5109 E-mail: support@advantech-bb.com Web: www.advantech-bb.com
10.2 Customer Support for Europe
Phone: +353 91 792444 Fax: +353 91 792445 E-mail: techSupport@advantech-bb.com Web: www.advantech-bb.com
10.3 Customer Support for Asia
Phone: +886-2-2792-7818 #1299 (Monday – Friday, 9 a.m. to 5:30 p.m. UTC+8) Fax: +886-2-2794-7327 E-mail: icg.support@advantech.com.tw Web: www.advantech.com
Upkeep – Advices:
During cleaning of the router do not use aggressive chemicals, solvents and abrasive cleaners!
Hereby, Advantech B+B SmartWorx s.r.o. company declares that the radio equipment narrated in this user’s guide is in compliance with EU Directive 2014/53/EU.
The full text of the EU Declaration of Conformity is available at the following internet address:
www.advantech-bb.cz/eudoc