The Viking Model F-1 Deluge Valve is a quick opening, differential diaphragm and flood
valve with one moving mechanism. The Deluge Valve is used to control water flow in
Deluge and Preaction sprinkler systems. The valve is held closed by system water pressure trapped in the priming chamber; keeping the outlet chamber and system piping
dry. In fire conditions, when the releasing system operates, pressure is released from
the priming chamber. The Deluge Valve clapper opens to allow water to flow into the
system piping.
Features:
Field replaceable Diaphragm and Seat Rubbers
1.
Designed for installation in the horizontal or vertical position
2.
Designed to be reset without opening the valve
3.
Compatible with Hydraulic, Pneumatic and/or Electric Release Systems
4.
NOTE: FOR PART NUMBERS OF ACCESSORIES, REFER TO VIKING LIST PRICE SCHEDULE.
2. LISTINGS AND APPROVALS:
U.L. Listed - Guide No. VLFT & VLJH
C-UL Listed
FM Approved - Deluge Sprinkler Systems, Preaction Sprinkler Systems, Refrigerated Area Sprinkler Systems
American Bureau of Shipping (ABS) - Certificate No. 05-HS502910C-PDA
NYC Department of Buildings - MEA 89-92-E Vol XXXI
CE - Pressure Equipment Directive 97/23/EC
STRAIGHT THROUGH STYLE
2-1/2” (DN65) - 8” (DN200)
3. TECHNICAL DATA
Specifications:
Maximum Working Water Pressure: 250 PSI (17.4 bar)
Style: Straight through
Connections: See Table 1.
Factory tested: to 500 psi (34.5 bar)
Valve differential: 2:1 (priming chamber to inlet chamber)
Priming chamber supply restriction (required): 0.0625” (1.6 mm)
Color of Valve: Red
Friction loss: Refer to Table 1.
Cv Factor: Refer to Table 1.
Material Standards:
Refer to Figure 2.
Ordering Information:
Part Numbers - Refer to Table 1
8” - Manufactured since 2002
4” & 6” - Manufactured since 2003
2-1/2” & 3” - Manufactured since 2004
ACCESSORIES:
Refer to Current VIKING PRICE LIST for Part Numbers.
A Conventional Trim Trim package for use with the Model F-1 Deluge Valve. The trim package includes the VALVE ACCESSORY
1.
PACKAGE and the fittings and nipples shown on the Viking Deluge Valve Conventional Trim Chart Trim Chart for the valve used.
Trim Charts are provided in trim packages and the Viking Engineering and Design Data book. For optional factory assembled
“modular” trim packages, refer to the Viking list price schedule or contact the manufacturer.
A Deluge VALVE ACCESSORY PACKAGE includes required trim components. This package is needed when Viking Trim
2.
Packages are not used.
Auxiliary Components are required for specific valve functions. For complete operating trim requirements, refer to system data
3.
for the system used. System data is provided in the Viking Engineering and Design Data book.
Additional accessories are available and may be required for system operation or supervision. Refer to the system description and
technical data for complete operating trim requirements for the system used.
Viking Technical Data may be found on
The Viking Corporation’s Web site at
http://www.vikinggroupinc.com.
The Web site may include a more recent
edition of this Technical Data Page.
Form No. F_110802
Replaces page 218a-j, dated April 15, 2011.
(Updated friction loss and weight values fo DN150 FF)
Deluge Valves 218b
May 7, 2014
DELUGE VALVE, MODEL F-1
TECHNICAL DATA
The Viking Corporation, 210 N Industrial Park Drive, Hastings MI 49058
DESCRIPTION Nominal Size Part Number Friction Loss*Cv FactorShipping Weight
Threaded
Flange/Flange
Flange/Groove
Flange Drilling / Pipe O.D.
Groove/Groove
*Expressed in equivalent length of Schedule 40 pipe based on Hazen & Williams C=120
4. INSTALLATION (Refer to Figure 1 identification of trim components.)
A. General Instruction
Viking Straight Through Deluge Valves may be installed in the horizontal or vertical position.
1.
The valve must be installed in an area not subject to freezing temperatures or physical damage.
2.
The valve must be trimmed according to current Viking Trim Charts and appropriate instructions for the system used. Trim Charts
3.
are printed in the Viking Engineering and Design Data book, and are provided with trim packages.
Remove all plastic protectors from the openings of the Deluge Valve.
a.
Apply a small amount of pipe joint compound or tape to the external threads of all pipe connections required. Take care not to
b.
allow any compound, tape, or other foreign matter inside any of the nipples or openings of the valve or trim components.
Viking Model F-1 Deluge Valve Conventional Trim Charts are provided with Trim Packages and in the Viking Engineering and
c.
Design Data book.
Verify that all system components are rated for the water working pressure of the system.
d.
Hydrostatic Test:
The Model F-1 Deluge Valve is manufactured and listed for use at a maximum Water Working Pressure of 250 PSI (17.2 bar). The
valve is factory tested at 500 PSI (34.5 bar). Model F-1 Deluge Valves may be hydrostatically tested at 300 PSI (20.7 bar) and/or 50
PSI (3.4 bar) above the normal Water Working Pressure, for limited periods of time (two hours), for the purpose of acceptance by the
Authority Having Jurisdiction. If air testing is required, do not exceed 60-PSI (4.1 bar) air pressure.
NOTE: NEVER CONDUCT THE HYDROSTATIC TEST AGAINST THE PRESSURE OPERATED RELIEF VALVE. (P.O.R.V.) TEMPORARILY REMOVE THE P.O.R.V. FROM THE TRIM AND PLUG TRIM OPENINGS WHILE CONDUCTING THE HYDROSTATIC TEST.
TRIM NOTE: DISCHARGE PIPING FROM THE AUXILIARY DRAIN VALVE, THE FLOW TEST VALVE, AND ALL SYSTEM DRAINS
SHOULD BE KEPT SEPARATE. DO NOT CONNECT THE OUTLET OF THE DRIP CHECK TO ANY OTHER DRAIN.
The priming line must be connected upstream of the system water supply main control valve or to a constant source of water at
4.
a pressure equal to the system water supply.
Pipe O.D.
NPT 65 mm2½"1240112 ft. (3.6 m)15567 lbs. (30 kg)
Flange Drilling
ANSI3"1201412 ft. (3.6 m)15582 lbs. (37 kg)
ANSI4"1195321 ft. (6.5 m)428146 lbs. (66 kg)
ANSI6"1195539 ft. (11.9 m)839271 lbs. (123 kg)
ANSI8"1199157 ft. (17.4 m)1577466 lbs. (212 kg)
ANSI/Japan6"1196439 ft. (11.9 m)839271 lbs. (123 kg)
PN10/16DN801202612 ft. (3.6 m)15582 lbs. (37 kg)
PN10/16DN1001196521 ft. (6.5 m)428127 lbs. (58 kg)
PN10/16DN1501195639 ft. (11.9 m)839271 lbs. (123 kg)
PN10DN2001199557 ft. (17.4 m)1577418 lbs. (190 kg)
PN16DN2001199957 ft. (17.4 m)1577466 lbs. (212 kg)
ANSI / 89 mm3"1201812 ft. (3.6 m)15575 lbs. (34 kg)
ANSI / 114 mm4"1195221 ft. (6.5 m)428136 lbs, (62 kg)
ANSI / 168 mm6"1195439 ft. (11.9 m)839261 lbs. (118 kg)
PN10/16 / 89 mmDN801203012 ft. (3.6 m)15575 lbs. (34 kg)
PN10/16 / 114 mmDN1001195821 ft. (6.5 m)428136 lbs. (62 kg)
PN10/16 / 165 mmDN1501264039 ft. (11.9 m)839261 lbs. (118 kg)
PN10/16 / 168 mmDN1501195439 ft. (11.9 m)839261 lbs. (118 kg)
Pipe O.D.
73 mm2½" / DN651240312 ft. (3.6 m)15567 lbs. (30 kg)
76 mmDN801272912 ft. (3.6 m)15567 lbs. (30 kg)
89 mm3" / DN801202212 ft. (3.6 m)15564 lbs. (29 kg)
114 mm4" / DN1001151321 ft. (6.5 m)428127 lbs. (58 kg)
165 mmDN1501191039 ft. (11.9 m)839245 lbs. (111 kg)
168 mm6" / DN1501152439 ft. (11.9 m)839245 lbs. (111 kg)
219 mm8" / DN2001101857 ft. (17.4 m)1577403 lbs. (183 kg)
STRAIGHT THROUGH STYLE
2-1/2” (DN65) - 8” (DN200)
∆P
Q= Cv
Q= Flow
Cv= Flow Factor (GPM/1 PSI ∆P)
∆P= Pressure Loss through Valve
S= Specific Gravity of Fluid
Table 1 - Valve
Part Numbers and
Specifications
√
S
May 7, 2014
Deluge Valves 218c
DELUGE VALVE, MODEL F-1
TECHNICAL DATA
The Viking Corporation, 210 N Industrial Park Drive, Hastings MI 49058
After the Deluge Valve is set, operation of the Deluge Valve requires the release of priming water from the priming chamber. This
5.
may be by automatic or manual operation of the release system. Viking Deluge Valves are compatible with hydraulic, pneumatic,
and electric release systems. For specific Trim arrangements refer to Trim Charts and System Data describing the system being
installed. Trim Charts are printed in the Viking Engineering and Design Data book, and are provided with trim packages. System
Data sheets are printed in the Viking Engineering and Design Data book.
Hydraulic Release Systems: See Figures 3-6 for the maximum allowable elevation of hydraulic release piping above the
a.
Deluge Valve. If the maximum height of hydraulic release piping exceeds the limit shown in Figures 3-6 for the valve used,
use a Pneumatic or Electric Release System.
Pneumatic Release Systems: A Viking Pneumatic Actuator is required between the release system connection provided on
b.
deluge valve trim and pneumatic release system piping.
Electric Release Systems: Solenoid Valves, System Control Panels, and Electrical Detectors must be compatible. Consult
c.
appropriate listing and/or approval guides.
NOTE: FOR OPERATION AT WATER PRESSURES IN EXCESS OF 175 PSI (12.1 BAR), A 250 PSI (17.2 BAR) RATED SOLENOID VALVE
MUST BE USED. REFER TO APPROPRIATE VIKING TECHNICAL DATA PAGE FOR TYPE OF SYSTEM USED.
CAUTION: OPERATION OF VIKING DELUGE VALVES BY PRESSURIZING THE PRIMING CHAMBER WITH AIR PRESSURE OR ANY
OTHER PRESSURIZED GAS IS NOT RECOMMENDED OR APPROVED.
STRAIGHT THROUGH STYLE
2-1/2” (DN65) - 8” (DN200)
B. Placing the Valve in Service
For Deluge Valves equipped with Conventional Deluge Valve Trim, follow steps 1 through 10 (and 11 & 12 if applicable) below.
Verify:
1.
The system Main Water Supply Control Valve (D.1) is closed and the Deluge Valve is trimmed according to current Viking Trim
a.
Charts and schematic drawings for the system used.
The system has been properly drained.
b.
Auxiliary Drain (B.13) is open.
c.
The Emergency Release (B.9) is closed.
d.
The system water supply piping is pressurized up to the closed Main Water Supply Control Valve (D.1) and the priming line
e.
is pressurized up to the closed Priming Valve (B.1).
For Systems equipped with:
2.
Hydraulic Release Systems:
a.
Verify that all releasing devices are set and that any Inspector’s Test Valve and/or auxiliary drain valves are closed.
i.
Open Priming Valve (B.1).Allow the hydraulic release system to fill. When priming pressure gauge (B.7) indicates that the
ii.
release piping and priming chamber pressure is equal to system supply pressure, proceed to step 3.
Proceed to step 3.
iii.
Pneumatic Release Systems:
b.
Set the release system.
i.
Open Priming Valve (B.1).
ii.
Proceed to step 3.
iii.
Electric Release Systems:
c.
Open Priming Valve (B.1).
i.
Set the electric release system.
ii.
Proceed to step 3.
iii.
Open Flow Test Valve (B.11).
3.
Partially open Main Water Supply Control Valve (D.1).
4.
When full flow develops from the Flow Test Valve (B.11), close the Flow Test Valve. Verify that there is no flow from the open
5.
Auxiliary Drain (B.13).
Close Auxiliary Drain (B.13).
6.
Fully open and secure the Main Water Supply Control Valve (D.1).
7.
Verify that the Alarm Shut-off Valve (B.6) is open and that all other valves are in their normal** operating position.
8.
Depress the plunger of Drip Check (B.14). No water should flow from the Drip Check when the plunger is pushed.
9.
Check for, and repair all leaks.
10.
On new installations, those systems that have been placed out of service, or where new equipment has been installed, trip test
11.
the system to verify that all equipment functions properly. Refer to INSPECTION, TESTS AND MAINTENANCE paragraph 6-II-C:
ANNUAL Trip Test instructions.
CAUTION! PERFORMING A TRIP TEST RESULTS IN OPERATION OF THE DELUGE VALVE. WATER WILL FLOW INTO THE SPRINKLER PIPING. TAKE NECESSARY PRECAUTIONS TO PREVENT DAMAGE.
After completing a trip test, perform SEMI-ANNUAL maintenance.
12.
Loading...