Vertex F4 Installation And Operation Manual

1.Introduction
1.1.Highlight Features
Space saving, only 55mm panel depth required
Higher sampling rate (100mS) results in better control performance
Protect the load from thermal shock (unwanted rapid temperature rise) using the excellent ramp
rate feature
Protect the heating element from excess current during power-up using the soft start function
NEMA-4 IP65 front panel protection when used with panel gasket or IP63 without
1.2.Specification Input signal : User programmable. refer to table 1.
Thermocouple (T/C) : industry standard thermocouple types, J, K, T, E, B, R, S, N, C (ITS-90).
■ Pt100 : Excitation 180uA. 2 or 3 wire connection (ITS-90 α=0.00385).
Voltage : -60mVdc to 60mVdc or -10Vdc to 10Vdc.
Current : 0mA to 24mA
Measuring range : User programmable. Maximum range refer to table 1. Measuring accuracy : refer to Table 1. the accuracy is tested under the operating condition of
24°C±3°C.
*Factory Setting
Note 1 : Accuracy is not guaranteed between 0 and 400°C (0 and 752°F) for type B. Table 1 Input Signal
Sampling rate : 100mS Control Output :
Relay output : 5A/240Vac (Resistive load)
Pulsed Voltage output : DC 0/24V (Resistive load 1.2K ohms Min.)
Current output : 4~20mA (Resistive load 600 ohms Max.)
Voltage output : 0~10V ( Resistive load 600 ohms Min.)
Control Mode : PID with auto-tune, P with manual reset or On/Off with hysteresis available.
■ Proportional Band : 0.0~300.0% (0.0 % = On/Off mode)
Integral Time : 0.0~3000 sec.
Derivative Time : 0.0~1000 sec.
Cycle Time : 0~60 sec.
Hysteresis : 0~9999
Ramp Function :
■ Ramp rate : 0~9999 unit/minute or unit/second (0 = disable the ramp function)
Accuracy
±1°C
±1°C
±1°C
±1°C
±2°C
(Note1)
±2°C
±2°C
±2°C
±2°C
±0.2°C
±0.2°C
±4μA
±0.01mV
±2mV
Maximum Range
-50 to 1000°C (-58 to 1832°F)
-50 to 1370°C (-58 to 2498°F)
-270 to 400°C (-454 to 752°F)
-50 to 750°C (-58 to 1382°F)
0 to 1800°C (32 to 3272°F)
-50 to 1750°C (-58 to 3182°F)
-50 to 1750°C (-58 to 3182°F)
-50 to 1300°C (-58 to 2372°F)
-50 to 1800°C (-58 to 3272°F)
-200 to 850°C (-328 to 1562°F)
-200 to 600°C (-328 to 1112°F)
-24mA~24mA
-60mV~60mV
-10V~10V
Input signal
Thermocouple J
Thermocouple K*
Thermocouple T
Thermocouple E
Thermocouple B
Thermocouple R
Thermocouple S
Thermocouple N
Thermocouple C
Pt100 (DIN)
Pt100 (JIS)
mA
mV
Voltage
F4 Process Controller
Installation and Operation Guide
Alarm Output : 5A/240Vac (Resistive load) Alarm Function : Energized / De-energized with 0~30000 Sec. / Min. delay
No alarm
Process high alarm
Process low alarm
Deviation high alarm
Deviation low alarm
Inside deviation band alarm
Outside deviation band alarm
Alarm Mode :
Normal mode
Standby mode
Latch mode
Standby and Latch mode
Communication :
Interface : Half duplex based on EIA RS-485
Protocol : ModBus RTU mode
Data format :
Start bit : 1 Data bit : 8 Parity : None Stop bit : 2
Baud Rate : 2400, 4800, 9600, 19200 bps
Power supply : 100~240 Vac, 50/60 Hz / 24Vdc Power consumption : 4VA Max. Common mode rejection ratio : >80dB. Operating temperature : 0 to 50°C Humidity : 0 to 85% RH (Non-Condensing) Electromagnetic compatibility (EMC) : En 50081-2, En 50082-2 Dimension : 48x48x55 mm (WxHxD). Housing material : ABS plastic. UL 94V0 Weight : 100g
1.3.Ordering information
2.Installation
2.1.Panel mounting
1.Prepare the panel cutout with proper dimensions (45.5 X 45.5 mm)
2.Insert the controller into the panel cutout from the front of the panel.
3.Secure the controller by pushing the mounting bracket into the controller from the rear side.
4.Tighten the screws of the mounting bracket slightly if the controller is not firmly secured
Figure 1. Panel mounting
2.2.Connections and wiring
AC power supply
-0.0
+0.5
-0.0
+0.5
Input
T/C
PT100 (RTD)
0-60mV DC
0-10V DC
0-24mA DC
Code
T
D
L
V
M
Output 1 (Alarm2)
Relay
SSR
4~20mA
0-10V
Other
Alarm 2
Code
R
P
M
V
O
A
Alarm 1
(Output2)
Alarm 1
Relay
Code
A
R
Communication
None
RS-485
Code
N
C
Power Supply
100~240
Vac
24 Vdc
Code
A
D
Protection
IP 63
IP 65
Code
3
6
F4
Control output 1 (can be converted to 2nd Alarm) Relay output : 5A/240Vac (Resistive load) Pulsed Voltage output : DC 0/24V (Resistive load 1.2K ohms Min.) Current output : 4~20mA (Resistive load 600 ohms Max.) Voltage output : 0~10V ( Resistive load 600 ohms Min.)
Relay output : 5A/240Vac (Resistive load)
Power supply : 100~240 Vac, 50/60 Hz
Alarm 1 output (can be converted to 2nd output)
Figure 5. Menu flowchart
3.3.2.User Level
Process value offset correction The value to be added to the PV to correct the sensor offset error.
Control output percentage In Auto mode ( = ), it shows the percentage of power applied to the control output. In Manual mode ( = ), the upper display will show the process value (PV) and “ ” alternately and the “MA” indicator is lit. The value of percentage can be changed manually.
Control mode Select the control mode to be Off – Standby mode. Both control output and alarm are turned off. On – Auto mode (closed loop control). In this mode, the control output percentage is determined by PID algorithm or ON/OFF action. AT1 – Auto-tuning mode 1. In this mode, the controller will tune the PID parameters automatically at SV. The process will oscillate around the SV during AT1 process (Figure 6). Use AT2 mode if overshooting beyond the normal process is likely to cause damage. AT2 – Auto-tuning mode 2. In this mode, the controller will tune the PID parameters automatically at (SV-10%). The process will oscillate around (SV-10%) during AT2 process (Figure 6). Man – Manual mode (open loop control). In this mode, the control output can be set manually.
Figure 6. Auto-tuning Process
3.3.3.Alarm Level
Display Description
Alarm 1 set-point
Alarm 1 hysteresis
Alarm 1 function
Range
-1999~9999 ( =0000)
-199.9~999.9 ( =000.0)
-19.99~99.99 ( =00.00)
-1.999~9.999 ( =0.000) 0~9999 ( =0000) 0~999.9 ( =000.0) 0~99.99 ( =00.00) 0~9.999 ( =0.000)
Default 10
0
Unit unit
unit
DC power supply
Figure 2. Terminal connections
Wiring precaution: Inverter, mechanical contact relays, arc welders, and ignition transformers are all common sources of electrical noise in an industrial environment, so always keep signal wires away from those noise-generating devices.
3.Operation
3.1.Front panel description
Figure 3. Front panel description
PV ( Upper display ) : Display the process Value, parameter index code or error code
SV ( Lower display ) : Display the set point value or the set value of parameter
C1 : Control output 1 indicator
C2 : Control output 2 indicator
A1 : Alarm 1 indicator
A2 : Alarm 2 indicator
AT : Auto-tuning indicator (The right-most decimal point of upper display)
MA : Manual mode indicator (The right-most decimal point of lower display)
Keypad description
SET key : Use to menus navigation and set value registration
Shift key : Shift the digit of numeral
Down key : Decreases the parameter value or change the setting
Up key : Increases the parameter value or change the setting
SET + Shift key for 2 sec. : Enter set up mode
SET + up key : Return to PV/SV display
Shift + Down key on powering up : set all parameters to default setting
3.2.Powering up procedure
Figure 4. Powering up procedure
3.3.Configuration
3.3.1.Menu Flowchart After powering up procedure, the controller stays in PV/SV display. The upper display shows the process value (measuring value) and the lower display shows the set point value (target value). All the configurable parameters are located in different levels and can be accessed by keypad operation as shown in figure 5.
Display Description
Process value offset correction
Control output percentage Control mode
Range
-1000~1000 ( =0000)
-100.0~100.0 ( =000.0)
-10.00~10.00 ( =00.00)
-1.000~1.000 ( =0.000)
0.0~100.0% : Off : On : AT1 : AT2 : Man
Default 0
N/A On
Unit Unit
% N/A
Control output 1 (can be converted to 2nd Alarm) Relay output : 5A/240Vac (Resistive load) Pulsed Voltage output : DC 0/24V (Resistive load 1.2K ohms Min.) Current output : 4~20mA (Resistive load 600 ohms Max.) Voltage output : 0~10V ( Resistive load 600 ohms Min.)
Relay output : 5A/240Vac (Resistive load)
Alarm 1 output (can be converted to 2nd output)
DC24V
: A.oFF : A.Hi : A.Lo : A.diH : A.diL : A.bdH : A.bdL : b.oFF : b.Hi
A.diH N/A
*All the alarm 2 parameters are only shown when the control output is set as 2nd alarm action.
Alarm 1 set-point, Alarm 2 set-point The set point of alarm even Alarm 1 hysteresis, Alarm 2 hysteresis The hysteresis of alarm action Alarm 1 function, Alarm 2 function Select the alarm function A.oFF – Alarm action off. A.Hi – Process high alarm with Form A contact A.Lo – Process low alarm with Form A contact A.diH – Deviation high alarm with Form A contact A.diL – Deviation low alarm with Form A contact A.bdH – Deviation band high alarm with Form A contact A.bdL – Deviation band low alarm with Form A contact b.oFF – Alarm action off b.Hi – Process high alarm with Form B contact b.Lo – Process low alarm with Form B contact b.diH – Deviation high alarm with Form B contact b.diL – Deviation low alarm with Form B contact b.bdH – Deviation band high alarm with Form B contact b.bdL – Deviation band low alarm with Form B contact
Figure 7. Alarm function
Alarm 1 mode, Alarm 2 mode Select the alarm mode as None – Disable the alarm mode Stdy – Standby mode. When selected, prevents an alarm on power up. The alarm is active after alarm condition has been cleared and then alarm occurs again. LAtH – Latch mode. When selected, the alarm output and indicator latch as the alarm occurs. The alarm output and indicator will not change its state even if the alarm condition has been cleared unless the power is off. StLA – Both standby and Latch mode are applied. Figutr 8 shows the result of different alarm modes applied on Deviation Band High Alarm with alarm hysteresis set to 0. Alarm 1 delay time, Alarm 2 delay time Alarm delay time is set to postpone the alarm action by the setting time. Figure 8. Alarm Mode
3.3.4.Soft Level
: b.Lo : b.diH : b.diL : b.bdH : b.bdL : None : Stdy : LAtH : StLA oFF, 00.01~99.59 Same as Alarm1 set-point Same as Alarm1 set hysteresis Same as Alarm1 function Same as Alarm1 mode Same as Alarm1 delay time
Alarm 1 mode
Alarm 1 delay time Alarm 2 set-point* Alarm 2 set hysteresis* Alarm 2 function Alarm 2 mode* Alarm 2 delay time*
None
oFF 10 0 A.diL None oFF
N/A
HH.MM/MM.SS Unit Unit N/A N/A HH.MM/MM.SS
Description Ramp rate Soft start time
Range oFF, 1~9999 (0.1~999.9) oFF, 00.01~99.59
Default oFF oFF
Unit Unit / sec.(min) Minutes : Seconds
Display
Cut-off function
: None : Low : High : High/Low
None N/A
Description Input signal type
Range
: J type
: K type
: T type
: E type
: B type
: R type
Default K type
Unit N/A
Display
Description Proportional band Integral time Derivative time Manual reset Anti-reset windup Hysteresis for ON/Off control Cycle time Cooling proportional band Dead band Cooling cycle time
Range
0.0~300.0 oFF,1~3000 oFF,1~1000
0.0~51.0
0.0~100.0 0~1000 (0.0~100.0) 0~60
0.0~300.0
-1000~1000(-100.0~100.0) 1~60
Default
5.0 240 60
0.0
50.0 0 15 5 0 15
Unit % Sec. Sec. % % uint Sec. % °C, °F or Engineering Unit Sec.
Display
Ramp rate The controller can act as either a fixed set point controller or as a single ramp controller. If the ramp rate is set to a value other than “oFF”, the process will increase or decrease at the setting rate during initial power up or with set point change. The ramp rate is in degree per min. or sec. depends on the time scale set in PTME. Figure 9. Ramp Function Soft start time Soft start time can be programmed in situation where 100% output is not allowed at power up. The time duration for the output to rise from 0% to 100% is defined as soft start time.
Figure 10. Soft Start
3.3.5.PID Level
Proportional band Set the proportional band in percentage of SPAN (High limit - Low limit). It can be set automatically by auto-tuning process. Integral time Set the integral time constant in repetitions per second. It can be set automatically by auto-tuning process. Derivative time Set the derivative time constant in second. It can be set automatically by auto-tuning process. Manual reset For PID control, this value is set automatically after auto-tuning process. For P control, it is used to compensate the deviation between process value and set point. Anti-reset windup The anti-reset windup (ARW) inhibits the integral action until the process value is within the band thus reducing overshoot on start-up. The ARW can be set automatically by auto-tuning process and then can be changed manually if required Hysteresis for ON/OFF control In ON/OFF control (Proportional band set to 0.0%), the control output turns On/Off with respect to the set point. Therefore, the control output would change frequently in response to a slight change in process value. This might shorten the service life of the output device. To prevent Figure 11. ON/OFF Control Action this, a hysteresis is provided in the ON/OFF control. Cycle time Set the control output cycle time. It is recommended to set to 15 sec. for Relay output and set to 1 sec. for pulsed voltage output. Cooling proportional band Set the cooling proportional band in percentage of SPAN (High limit – Low limit). It can be set automatically by auto-tuning process. Set to 0.0 for ON/OFF control mode. Dead band This setting defines the area in which both heating and cooling outputs are inactive, known as dead band, or the area in which they are both active, known as overlap. A positive value results in a dead band, while a negative value results in an overlap. Cooling cycle time Set the cooling output cycle time. It is recommended to set to 15 sec. for Relay output.
3.3.6.Option Level
Low scale for linear input High scale for linear input
: S type
: N type : C type
: PT100 (DIN) : PT100 (JIS)
: mA
: mV : V
-1999~9999
-1999~9999
0 1000
Unit Unit
Error protection
0000 0001 0010 0011
A1 / C2
OFF OFF
ON ON
C1 / A2
OFF
ON
OFF
ON
Unit
Decimal point
Control action
Low limit High limit Digit filter Time scale
Error protection
Security lock
Setpoint offset
Communication ID Baud rate
: °C : °F : Engineer
0000
000.0
00.00 (for linear input signal only)
0.000 (for linear input signal only) : Dir : Rev
Refer to table 1. Refer to table 1.
0.0~99.9 : HH.MM : MM.SS
0000 0001 0010 0011 0000 0001 0010 0011 0100 0101 0110
-1999~9999 (
=0000)
-199.9~999.9 (
=000.0)
-19.99~99.99 (
=00.00)
-1.999~9.999 (
=0.000)
1~247
: 2.4K
: 4.8K
: 9.6K :19.2K
°C
0000
Rev
0 1000
0.0 HH.MM
0000
0110
0
247
19.2K
N/A
N/A
N/A
Unit Unit Sec. N/A
N/A
N/A
Unit
N/A bps
Thermocouple RTD 0~24 mA
-60~60 mV
-10~10 V
G1
Linked
Open
X X X
GA1 Linked Linked Linked Linked
Open
GB1 Open Open Open Open
Linked
GY Open Open
Linked
Open Open
Input signal type Select the input signal type. The available input signal types are : Thermocouple : J K T E B R S N C RTD : PT100 (JIS standard) or PT100 (DIN standard) Linear : 0~24mA, -60~60 mV or 0~10 V Please note that the internal gaps on the main board of F4 controller should be configured in accordance with input signal.
X : don’t care
Figure 12. Gaps Allocation
Low scale for linear input Select the low scale corresponding to low linear input signal. The default low linear input signal (INL) for mA, mV and V is 4.00mA, 0.00mV and 0.00V separately. This parameter is only showed when the input signal type is set to linear. (See also the cut-off function for further detail) High scale for linear input Select the high scale corresponding to high linear input signal. The default low linear input signal (INH) for mA, mV and V is 20.00mA, 50.00mV and 10.00V separately. This parameter is only showed when the input signal type is set to linear. (See also the cut-off function for further detail) Cut-off function The Cut-off function is used to limit the process value of linear input signal within the boundary whenever the input signal is out of the high/low limit range (set by Hilt and LoLt). The cut-off function can be set to “Low”, “High” or “High/Low”, set to “None” disables the cut-off function. The cut-off function has no effect for input signal other than linear input. Figure 13. Scale and Cut-off Function
Only the security lock is open to change, all other parameters are locked Only the security lock and set point value is changeable. all the other parameters are locked The user level is open to change. The user and alarm levels are open to change. The user, alarm, and soft levels are open to change. The user, alarm soft and PID levels are open to change. All parameters are open to change.
Security lock 0000 0001
0010 0011 0100 0101 0110
Range: 0 ~ 3 Unit: N/A PV scale calculation:
Where IN: the linear input signal. INH: the high calibration of linear input signal. It is set in calibration parameters (mAL, mVL and VL). INL: the low calibration of linear input signal. It is set in calibration parameters (mAH, mVH and VH). Example: For a 4~20mA input signal, the INL is set by mAL=4.00mA and the INH is set by mAH=20.00mA. Set SCAL=0.0 SCAH=100.0 (Of course, you may select other scale value and decimal point to alter the resolution) and LoLt=0.0 HiLt=100.0. For a 12mA input, the PV will be 50.0. For a 22mA input, the PV will be 112.5 with cut-off function set to “None” or 100.0 with cut-off function set to “High” or “High/Low”. For a 0mA input, the PV will be -25.0 with cut-off function set to “None” or 0.0 with cut-off function set to “Low” or “High/Low”. Unit Select the process value indication in °C or °F when the input signal type is set to thermocouple or PT100. Select engineer unit for linear input (mA, mV or V). Decimal point Select the decimal point position. The setting 00.00 and 0.000 is available for linear input only. Control action Dir – Direct action used for cooling process Rev – Reverse action used for heating process Low limit Set the low limit of measuring range. When the PV goes below the low limit, the PV display flashing indicates a low limit error. The control output and alarm will be set according to the Error Protection. High limit Set the high limit of measuring range. When the PV goes beyond the high limit, the PV display flashing indicates a high limit error. The control output and alarm will be set according to the Error Protection. Digit filter Set the time constant for digit filter (the first order filter). It is useful when the process value is too unstable to be read.
Figure 14. Digit Filter
Time scale Set the time scale used for alarm delay time and ramp rate. HH.MM – The alarm delay time is in hour and minute / The ramp rate is in per minute. MM.SS – The alarm delay time is in minute and second / The ramp rate is in per second. Error protection Set the control output and alarm status whenever an error occurred. (refer to 4 Error Message)
Security lock The security lock is useful to lock out the parameters from unauthorized changed
Set point offset Shift the set point value with an offset. The actual control target is shifted with this offset from set point value but not added to SV display. Communication ID Set the ID number in the communication network Baud rate Set the communication baud rate.
( )
SCALSCALSCAH
INLINH
INLIN
PV +
=
Display
Flashing
Error Description Sensor break or open
Input signal has out of A/D converter range
The content of EEPROM is corrupt
Fail to complete the auto-tuning process within 2 hours
The PV is out of range
Correction
1. Check the sensor is connected and input signal type is selected correctly.
2. Replace the sensor
1. Check the sensor is connected and input signal type is selected correctly.
2. Replace the sensor.
3. Return to the supplier for repairing
1. Return to default setting by pressing shift and down keys simultaneously while power on. And reconfigure the parameters
2. Return to the supplier for repairing
1. Retry the auto-tuning again.
2. Improve the control process to have fast response or use manual tuning instead of auto-tuning
1. Check the sensor is connected and input signal type is selected correctly
2. Check the polarity of sensor is connected correctly
3. Check the high/low limit is set properly.
4. Replace the sensor
4.Error Message
Loading...