Val-Matic Threaded Silent Check Valve User Manual

Threaded
Silent Check Valve
Operation, Maintenance and
Installation Manual
SCV-OM2-0
INTRODUCTION ........................................... 1
RECEIVING AND STORAGE ........................ 1
DESCRIPTION OF OPERATION .................. 1
INSTALLATION ............................................. 1
VALVE CONSTRUCTION ............................. 2
MAINTENANCE ............................................. 2
TROUBLESHOOTING ................................... 2
DISASSEMBLY .............................................. 3
REASSEMBLY ............................................... 3
PARTS AND SERVICE .................................. 3
WARRANTY .................................................. 4
VAL-MATIC
905 Riverside Dr. Elmhurst, IL 60126 Phone (630) 941-7600 Fax (630) 941-8042 www.valmatic.com
®
VALVE AND MANUFACTURING CORP.
THREADED STYLE SILENT CHECK VALVE
OPERATION, MAINTENANCE AND INSTALLATION
INTRODUCTION
This manual will provide you with the information to properly install and maintain the valve to ensure a long service life. The Threaded Silent Check Valve is ruggedly constructed of lead-free bronze to give years of trouble free operation. The valve should be installed in horizontal or vertical pipes carrying clean water.
The Threaded Silent Check Valve is designed to open fully to provide flow in the forward direction and close rapidly upon flow reversal. The valves are used to prevent reverse flow through pumps or in piping systems. The size and cold working pressure (250 CWP) are marked on the body for reference.
This valve is not intended for fluids containing suspended solids such as wastewater.
CAUTION This valve is not intended for fluids containing suspended solids or hazardous fluids.
RECEIVING AND STORAGE
Inspect valves upon receipt for damage in shipment. The valves should remain boxed, clean and dry until installed to prevent weather related damage. For long term storage, no special provisions are needed.
DESCRIPTION OF OPERATION
The Threaded Silent Check Valve is designed to prevent reverse flow automatically. On pump start­up, the flow of water enters the valve from the seat end (right side in Figure 1) and forces the disc open, allowing the passage of fluid through the valve.
On pump shut-down, the spring closes the disc rapidly before a flow reversal takes place. This type of closure, which prevents flow reversal, is the factor which provides “silent” operation and reduces water hammer associated with check valve slam.
The valve body is supplied with NPT tapered threads on each end for installation in pipelines.
FIGURE 1. THREADED SILENT CHECK VALVE
INSTALLATION
The installation of the valve is important for its
proper operation. The flow arrow on the valve body
must point in the direction of flow when the system is in operation. The valve can be installed in horizontal or vertical lines with the flow up or down.
Three diameters of straight pipe upstream of the valve are recommended to prevent turbulent flow streams through the valve, which can cause vibration and wear.
When installed in horizontal lines, the check valve does not have a specific upward orientation. Insert pipe nipples with thread sealant or thread tape and tighten while securing valve with a wrench on the body end nearest the pipe nipple.
CAUTION The use of excessive torque can damage the
valve.