KELCO F29 Programming Instructions Manual

KELCO F29 PROGRAMMABLE
FLOW SWITCH
PROGRAMMING INSTRUCTIONS
Version 010916
KELCO Engineering Pty Ltd
Sydney Australia www.kelco.com.au
VERY IMPORTANT
switched o󰀨.
On start up this controller will run the pump using its start-up timer. If it
nds normal operating conditions in the pipe system it will continue to run the pump. If pressure or ow conditions change the pump will continue to
run for a short period held on by the controller’s built in run-on timer. If acceptable conditions fail to return the pump will be shut down after the run-on time period. Pressing the red reset button on the controller’s lid or resetting the power will repeat this basic process.
To change the functions of this controller please rst read the programming
book supplied with this unit.
IMPORTANT
DO NOT EXPOSE THIS CONTROLLER TO VIBRATION. INSTALL ONLY IN PIPEWORK OR MANIFOLDS THAT DO NOT VIBRATE. Vibration will
damage the sensitive electronics within the controller and will void your product warranty.
Table Of Contents
Page
Introduction................................................................................................... 1
Programming the F29 Flow Switch & Basic Operation................................. 2
Alarm Relay.................................................................................................... 3
Start-Up & Run-On Timers............................................................................ 5
Advanced Functions, Reversing Relay1 Contacts........................................ 6
Pre-Start Delay Timer , Batch Control........................................................... 7
Batching with Additional Functions................................................................ 8
Delayed Restarting........................................................................................ 9
Cyclic Running............................................................................................... 10
Auto Restart................................................................................................... 11
Anti-Cycling................................................................................................... 12
Burst Pipe Detector........................................................................................ 13
Leak Detector................................................................................................ 15
Program Lock & Running Time Display......................................................... 16
The Hour Meter & LCD Screen Backlight....................................................... 17
Please Read Me First
The F29 ow switch is supplied unlocked and pre-loaded with a simple
program. It is set up with a 5 second start override time and a 5 second
run-on time. All other functions are turned o󰀨. With the default program loaded, the F29 will start a pump in spite of an initial lack of ow, run the pump for 5 seconds and expect to establish ow past its paddle within this start up time. Given ow is established it will then run the pump continuously while ow is present and it will shut the pump down if ow is interrupted for more than 5 seconds or if ow stops completely.
You can restore the F29 to this default state at any time by pressing and holding down the (P) button and pressing the (R) reset button at the same time. Release the (R) button and then release the (P) button. The timer
light will then ash rapidly red to indicate the process is complete. Doing
this removes any settings you may have entered and restores the F29 to its original default state. You can then enter new settings or just press reset (R) again and run the pump.
Introduction
The F29 programmable ow switch includes a set of functions that can be
set up to control a pump. The functions range from a simple override on
start timer that allows a pump to start in spite of an initial lack of ow, through to a range of sophisticated timing and ow based sequences. The
functions are independently accessible and adjustable through the F29’s simple programming interface. The pages that follow set out what each function does and how to set it up.
The actual selection of a suitable set of functions must be decided prior to programming and will depend on what level of control the pumping system
requires. In order to achieve the best performance from this ow switch
observe the following basic rules.
1) Use the least number of functions possible. Do not program in functions
you do not specically require, as to do so will make the system’s operation
unnecessarily complicated and may introduce unpredictable interactions that could cause the F29 to behave in a manner you had not anticipated.
2) The best way to switch o󰀨 a function that you have previously selected and subsequently decided not to use is to purge the entire program and
restore it to its default state rather than simply switch the particular function
o󰀨. Purging the program ensures the functions are properly disabled and their stored values are all set to zero or o󰀨. To purge the program press the
(P) button and the (R) reset button. Release the reset button while still holding the (P) button down, then release the (P) button. The LCD screen will display the message “Settings Cleared, Press (P) to Continue”. Press (P) and then step through the program making your new selections as you go.
3) Set realistic and sensible values into the various functions. For example,
do not set a pump to cycle on and o󰀨 rapidly. Always set the controller’s
running and stopping times to realistic values.
1
Programming The F29 Flow Switch
The F29 ow switch is fully programmable; it accepts input via 4 push
buttons. The buttons are marked (P) for programming, Up and Down for data entry and a reset button (R). Pressing the (P) button during normal
operation stops the pump and allows entry to the ow switch’s menu. Subsequent pressing of the (P) button steps you through the menu from
one option to the next. Each option can be adjusted using the up and down
buttons. Pressing the (P) button stores the settings you make into the ow switch’s memory and steps you to the next option. When you reach the end of the option list the ow switch asks you to accept the settings you have
made and to press the (P) button to resume normal running. You can automatically save any changes you have made and exit out of the menu at any stage during programming by simply pressing the (R) reset button.
The settings you make are non-volatile and are recorded in the ow switch’s memory. Your setting will not be lost if the ow switch is switched o󰀨 for extended periods. When the unit is switched back on the ow switch will
boot up and operate using the setting you recorded in its memory.
Basic Operation
Purging the F29 ow switch (pressing the (P) button and then pressing and
releasing the (R) reset button) automatically loads in a 5 second start-up time and a 5 second run-on time. This is the factory default setting for the
F29 ow switch. All other functions will be turned o󰀨 or set to zero. If you subsequently press the (P) button while the pump is running, the pump will
stop and the LCD screen will display the Kelco splash screen and the controller’s model number. Pressing the (P) button several more times
steps you to the rst selection in the menu, the remote input selection
screen.
Remote Input
The remote input operates in one of two ways, remote start only or remote
start and stop. You choose which of the two you require by pressing the up or down buttons and then conrming your selection by pressing the (P)
button. If you choose remote start only the F29 will start the pump each time the remote switch closes its contacts. If the remote switch was a pressure switch then its contacts would close on a falling pressure and that
2
could be used to start the pump. If you choose remote start and stop then the pump will only operate while the remote switch is closed. An example
of its use would be for tank lling where the remote input was connected to
a tank level switch such as a Kelco D30.
Alarm Relay
After selecting yes or no to the remote input question and pressing (P) you
are asked if you want to use the alarm relay. The F29 contains a dedicated
relay (relay 2) with 16 Amp 240VAC rated voltage free contacts. The contacts of the alarm relay can be used to control any required device
within its electrical rating including an external alarm or even a second pump. The alarm relay is very versatile and can be set to operate in one
of six di󰀨erent ways. If you choose yes to “use the alarm relay” you are confronted with the rst of seven screens asking you how you would like
the alarm relay’s contacts to behave. You can move through the choices using the up and down buttons. Details of the six choices follow.
1) Closed if any Fault Develops (Remains open if ow stops)
If you want the alarm relay to close its contacts only when a genuine fault develops simply press (P) to accept this choice. Alarm on a fault means
the alarm relay will only close its contacts if the pump runs dry, if ow is
interrupted while cyclically running or while a batch is running of if the anti cycling starts per hour rate is exceeded. To respond to dry running the F29 has to have an external pressure switch connected to its remote input and you must have selected “use remote input, yes” and then select “use
remote for starting only” for the F29 to be able to di󰀨erentiate between normal ow stopping and a genuine dry run.
If you have set run dry auto restart to on and have chosen repeated restarts from the run dry menu then in the event of the pump running dry the alarm relay will not close. This is because choosing repeated restarts means you accept the pump running dry as a normal event and not a true fault. If you
require an alarm using this run dry conguration then using “alarm on loss of ow would be the appropriate choice. If you choose single restart from
the run dry menu and the pump runs dry the alarm relay will not close its contacts unless the second attempt at restarting fails and the controller goes into permanent alarm mode.
3
2) Closed if Flow Stops (Remains open if a fault develops)
The second alarm choice means the alarm relay will close its contacts
every time ow stops, unless there is a fault. This means stopping under
normal circumstances. It means the alarm relay will not close its contacts if a fault occurs, as it would if you had made the previous choice. Such
faults that will not cause an alarm include running dry, ow interruptions to
batch or cyclic running and the anti cycling alarm.
3) Closed if Pump is O󰀨 (Regardless of ow or faults)
This choice e󰀨ectively provides a set of voltage free contacts that act in
reverse to the main pump relay’s contacts. That is, the alarm relay’s contacts will be closed when the pump relay’s contacts are open and they
will be open when the pump relay’s contacts are closed. This conguration
can be used for all manner of special applications where a set of independent
electrical contacts are required. It is even possible to control a second
pump via the relay’s contacts. This can be done either directly or via an interposing contactor. The standby pump would only run when the main
pump was o󰀨.
4) Closed if Pump is On (Regardless of ow or faults)
If this conguration is chosen the alarm relays contacts will mimic the main
pump relay’s contacts. They will be closed when the pump relay’s contacts are closed and open when the main pump relay’s contacts are open. Like
the previous choice, this conguration lends itself to all sorts of special
control applications.
5) Closed During Pre-Start Delay (Remains open at all other times)
If you decide to use this option the contacts of the alarm relay will only be closed while the pre-start timer is running. See details of what the pre-start timer is and what it does on page 6. Basically the alarm relay contacts can be used to control some external device for a period of time prior to the pump turning on. A typical application would be to have an aeration system or mixer run for a set period of time and then shut down and then have the pump turn on automatically. Such applications are often encountered in
inuent and e󰀪uent mixing and processing systems.
4
6) Closed on Faults Not in Cyc Run (No alarm in Cyclic Running)
This option is similar to option 1, “Closed if Any Fault Develops” the only
di󰀨erence being that the alarm relay will not close its contacts if an interruption to ow occurs during cyclic running. All other faults will cause
the alarm relay to close its contacts. This alarm option allows the pump to be used to cyclically pump a bore for a set period and then wait for the standing water level to recover before repeating the process. In this situation If the pump runs dry the cyclic running will simply revert to its set stopped time without locking out and instigating an alarm as it would if option 1 was used.
7) Closed on Flow, Opens on No Flow
If you select this option the alarm relay will behave like a separate basic
ow switch that will respond to ow independent of what the main pump
control relay, relay 1 may be doing. The contacts of the alarm relay (relay
2) will remain closed while ow is present and will remain open if no ow is
detected. There are no timer functions associated with this action. The
relay contacts will mimic the action of a simple on/o󰀨 ow switch and respond directly to ow.
Start-up and Run-on Timers
After the alarm relay selection comes the start-up timer screen. This is set to 5 seconds as the factory default. You can increase or decrease this by pressing the up or down buttons and then pressing the (P) button to step to the next function, the run-on timer. The run-on timer is also set to 5 seconds by default and again you can increase or decrease this by pressing
the up or down buttons. The start-up timer has a range of 0 to 240 seconds
and the run-on timer can be set from 0 to 900 seconds. Both the start-up and run-on timers are self terminating. This means they cancel out their
runs and revert to normal pump running as soon as ow is detected rather
than running for the full time that you have entered. In addition, the run-on
timer automatically resets its clock each time ow is detected. This feature means the F29 will ignore entrained gas in the pipe system. The ow has to remain continuously o󰀨 for whatever time you set on the run-on timer for
the pump to stop. The pump may be running dry for the period you set on the run-on timer so take care not to set a run-on time that is longer than absolutely necessary.
5
Once you have set the start-up and run-on timers and pressed (P) to
conrm the settings you are presented with a screen that asks if you want to use the advanced functions of the F29. If your application only requires
dry run protection for a pump and a start override to get the pump going in
spite of an initial lack of ow then you will not require the advanced functions.
In this situation just accept the default “NO” and press (P). You will then be
asked to conrm your choice and press the (R) reset button to run the
pump.
Advanced Functions
The F29 programmable ow switch includes a set of advanced functions that extend the capability of the ow switch well beyond basic loss of ow
protection. The advanced functions are directly accessible by moving beyond the more basic start-up and run-on timers previously described. There follows here a detailed description of each of the advanced functions. Advanced functions can be used singularly or in combination with other advanced functions as well as with the start-up and run-on timers and with
or without an external remote switch. Some advanced functions conict with others and the F29 ow switch will automatically step over conicting
functions in its menu based on your progressive selections.
Reversing the Contacts of Relay 1
On moving into the advanced functions section of the F29’s menu you are
rst presented with the option to reverse the contacts of relay 1. Relay 1 is normally used to control a pump and its contacts are open when o󰀨 and
closed when the pump is running. In some applications it is desirable to
have the contacts of relay 1 closed when the pump is o󰀨 and open when
the pump is running. An example of the use of reverse contacts would be on an engine pump set where the contacts of relay 1 are open while the engine is running and close to ground out the engines ignition circuit when the pump stops. To reverse the contacts of relay 1 simply select “YES” using the down arrow button. Pressing (P) locks your selection in and moves you to the next option.
6
Pre-Start Delay Timer
The F29 includes a pre-start delay time. The pre-start delay timer delays the starting of the pump for a selectable period. It can be set from zero to
64,800 seconds (18 hours) in 1 second increments. If you choose to use
this timer the actual starting of the pump will be delayed by whatever time you set this timer to. Each time the F29 is switched on it boots up but prevents the actual starting of the pump for the set period. As soon as the set time has elapsed the pump will start and run normally. The pre-start
timer can be used to allow peripheral equipment time to boot up or to run. For example, some VS drives require a few seconds to stabilise and the F29 pre-start delay timer can hold o󰀨 the starting of the pump until the
system has stabilised. The pre-start timer can also be used to stage or stagger the starting of multiple pumps. If you want to use the delayed starting function press the up or down buttons to display “YES” and then
press the (P) button. You will then be able to enter your required delay period using the up and down buttons. When you have entered your required time press (P) to move on to the next function.
Batch Control
The batch control function built into the F29 ow switch lets the user
program into the switch a set running time for the pump. The range of adjustment is 1 minute to 99 hours 59 minutes in increments of 1 minute.
If you select “YES” to batch control you are asked if you require single or
repeated batches. Single batch control is just that, a single batch that runs with no additional options. Selecting repeated batch enables delayed restarting, a function that follows batch control in the main menu. If the
batch run is interrupted by loss of ow it can be set to restart at the beginning
of its run after a delay period of 1 minute to 99 hours 59 minutes. If you select single batch from the menu, delayed restarting does not appear in the menu as an option.
The running of the set batch time can be initiated by powering up the F29 or by pressing the (R) reset button. The batch run can also be initiated by the closing of the contacts of a remote switch connected to the F29’s
remote input. To use the batch controller in this way, rst set the remote
7
input to on and to start only mode. Each time the remote switch closes its contacts a batch run will be initiated. If the remote switch contacts remain closed the F29 simply runs for the set period and then shuts down. To
initiate another run the remote switch contacts must rst open and then re-
close.
If ow is lost during a batch run, due to the pump running dry or a valve closing, the F29 will shut down the pump. If ow subsequently resumes
the batch controller will re-initiate its run from the beginning. It will not resume running from the point in its previous run that it shut down at. This
function can be used in tank lling applications to send a set volume of water to a tank but to terminate the batch run when the tank lls.
When using the batch control function with the remote input in start only
mode the F29 also uses the remote input as a means of detecting dry run. In this scenario the remote input would ordinarily be connected to an
external pressure switch. If ow is lost and the contacts of the remote switch are closed the F29 identies this as dry run , no pressure and no ow, shuts down the pump and displays the message “pump ran dry”. In this conguration the contacts of the alarm relay close. The contacts can
be used to actuate an external alarm or light. The alarm relay contacts also close at the completion of the batch run and again can be used to indicate the completion of the run via an external alarm or light.
Batching With Additional Functions
If you choose to use the F29 batch controller, you can also use some additional functions at the same time. Once you make the choice to use the batch controller the F29 automatically makes available to you functions that will work while the batch controller is in operation. Functions that will not work with the batch controller are automatically stepped over by the menu program. Functions that will not work include cyclic running, burst pipe detection and leak detection.
If you choose to use a function such as delayed restarting please be aware that when the delayed restart is invoked the batch controller resets its run time to your original entered value. At the end of the delay time the pump
8
will start and run your set batch from the beginning. This process will repeat each time the pump shuts down for any reason, the batch counter will reset and run your batch from the start.
If you choose to use the batch controller the F29’s cyclic running function will be disabled. If you choose not to use batch control then cyclic running will appear in the menu. Cyclic running can be used for batch control. To do this set the cyclic running time to some value and set the cyclic stopping
time to zero. In e󰀨ect, zero stopping time means innite stopping time as there is no dened set stop time. Set up this way the F29 will run for
whatever time you have entered into the cyclic running run time and will then stop. This batching process can be repeated by pressing the reset button or by closing the contacts of an external switch, if you have chosen to use the remote input.
Delayed Restarting
If you set this option to on, each time the pump stops, due to ow stopping
or pressure rising above your external pressure switch’s set point, the F29 will prevent the pump from restarting for the set period of time. The delay time can be set from zero to 99 hours 59 minutes in increments of 1 minute. Delayed restarting is a form of anti-cycling and cyclic running, wherein the
pump is limited in its ability to cycle on and o󰀨 by preventing it from restarting
for a set time period. Its uses include preventing rapid cycling if the system’s air cell becomes water logged or if a fault develops in a system’s external pressure switch. As an example of its use, consider a pressure system
lling a remote tank. If the tank has a oat valve that shuts when the tank
is full, then the system will pressurise and shut down each time the tank
lls and the valve closes. If the oat valve leaks or the level drops and the
valve opens the system will depressurise and the pump would ordinarily start. By utilising the F29’s delayed starting feature, the restarting of the pump can be delayed for a period of time. Perhaps until the water level in the tank has dropped by a substantial amount.
If you choose to use the delayed restarting function and press (P), you will be asked to enter the delay hours and minutes. You will then be asked if you want automatic starting at the end of the delay period. If you choose
yes to this question the ow switch will automatically start your pump at the end of the delay period. If you choose no, the ow switch will only start the
9
pump after the delay if an external switch connected to the F29’s remote input closes its contacts. In the example outlined above, consider a tank
that has intermittent or irregular draw o󰀨. You may choose to set the
delayed restart to perhaps 12 hours. At the end of the 12 hour period the pump will automatically start and if the tank level is low, the pump will run
continuously until the tank lls and the oat valve in the tank closes. If however, there has been no draw-o󰀨 from the tank during the 12 hour
period, the automatic restart at the end of the delay will start the pump and run it for whatever period you have set on the start timer (perhaps a few
seconds). The F29 will sense no ow because the oat valve will still be
closed. The F29 will then shut down the pump and again wait for 12 hours
before again attempting to start the pump. Using this technique prevents the pump from hunting on and o󰀨 when the tank is full because of slight leakage from the oat valve or pipework. It allows you to set the pump to
only operate after a chosen delay, and if there has been no usage of water, to test the system for demand by momentarily starting, and only run the pump if there is a genuine call for water.
The delayed starting function is distinctly di󰀨erent in the way it operates to
the cyclic running function that is also included in the F29. Delayed
restarting has no xed run time. Once started, the pump will run continuously provided ow is present until it is stopped by a valve closing or until it runs
dry. Cyclic running allows you to set how long the pump runs for as well as how long it stops for. If you choose to use the delayed restarting option the cyclic running function that follows it will not be available to you, as its
operation o󰀨ers an alternative to cyclic running that excludes the
combination of the two functions.
Cyclic Running
The F29 can be programmed to run and stop a pump for set periods of time. Both the running and stopping times can be set to any value you choose from 1 minute to 99 hours 59 minutes in increments of 1 minute.
The cyclic running option is highly exible. The run and stop timers are
totally independent of each other. If a set running and stopping time are
programmed in, the ow switch will run the pump for whatever time it is set
to and then stop for the time set on its stop timer.
10
If a run time is set to some value and the stop time is left set at zero, the
ow switch will behave as a one-shot batch controller. On pressing the
reset button or switching the pump on, the pump will run for the set period and then shut down. It will not then restart until you again press the reset
button or reset the power to the unit. In cyclic running mode the ow switch
monitors the elapsed time and displays the remaining time on its LCD screen in hours and minutes.
Cyclic running allows low yield bores to be pumped to their maximum capacity. A bore pump running under cyclic control can be set to pump the bore down to a low level, stop and wait for the standing water level to recover and then repeat the process endlessly. For transfer pumping applications cyclic running can be used to automatically top up remote
tanks without the need for oat valves or level control at the tank. It can also be used for one-shot tank lling. Press the reset button and pump a
set number of hours of water to a tank, and then stop until the reset is again pressed.
Auto Restart
If the F29 ow switch is used in conjunction with an external pressure
switch that is connected to its remote input it will be able to detect if the
pump has run dry as a combination of no ow and low or no line pressure.
If the pump does run dry the auto restart function can be set to automatically restart the pump after a settable time. Note that the auto restart function
only appears in the F29’s menu if you have rst selected to use the remote
input and have selected “start only” from its options.
If auto restart is chosen, the F29’s menu presents you with a choice, single restart or repeated restarts. Single restart will attempt to restart the pump after a set time and if the attempt fails the F29 then shuts down the pump and goes into permanent alarm mode. It displays a “pump ran dry”
message, ashes all its lights and closes the contacts of its alarm relay (if you have chosen to use the alarm relay). If however, it nds ow when it
restarts it resumes normal operation. If you choose repeated restart from
the menu the F29 will repeat the shut down and wait sequence and it will
not go into permanent alarm mode. Once you choose repeated restart or single restart the screens that follow ask you to enter a waiting period in hours and minutes. The range of adjustment is 1 minute to 99 hours 59
11
minutes (zero to just over 4 days) in one minute increments. If the pump
runs dry the F29 will shut it down and wait for the period you have set before attempting to restart.
The ability to restart the pump automatically if it runs dry can be a very useful function. Consider a jet pump or submersible pump installed in a low yield bore. The bore can be pumped until dry and the pump under the
control of the F29 can be set to shut down as soon as loss of ow is
detected and then wait until the standing water level in the bore recovers before attempting to restart and again pump the bore down.
Anti-Cycling
Electric motors are often limited in the number of times they can be safely started in an hour. This is particularly important in the operation of
submersible bore pumps. When a motor starts there is an initial inrush of
current that produces heat in the coils and iron rotor of the motor. If the
frequency of starts is excessive the accumulation of heat within the motor
can cause severe damage and eventual failure of the motor. Submersible bore pump motors are particularly prone to damage from excessive cycling (starting and stopping).
Maximum Starts Per Hour
The anti-cycling option built into the F29 allows the user to set the maximum number of times the pump can be safely started in any one hour period. If you select yes to this option the screen that follows will ask you to enter the maximum number of times the pump can be started in any one hour. The number of starts can be set from 1 start per hour to 1800 starts per hour.
Please contact your pump supplier to obtain the correct gure for your specic pump. In operation the anti-cycling system monitors both time and
the number of starts and compares the two. If the starts per hour rate is exceeded for a settable number of consecutive times in any one hour
period the pump will be automatically shut down and the ow switch will
display a message indicating the starts per hour rate was exceeded.
Number of Starts in Sequence
Once you have selected a suitable maximum number of starts per hour and pressed (P) the screen that follows asks you how many pump starts
12
you would like the F29 to tolerate in sequence. The default setting is 5.
You can change this using the up and down buttons. The range of
adjustment is 2 to 50 sequential starts.
As a simple example of the way the anti-cycling system works, if the starts per hour rate is set to 360 (one start every 10 seconds maximum) and the
pump started 4 times in a row at less than 10 seconds between each start
and then did not start again for 12 seconds, the anti-cycling shutdown will not be invoked. If however, the pump were to start 5 times in a row with less than 10 seconds between the starts the anti-cycling system would be invoked and the pump would be shut down.
In a conventional pressure system the anti-cycling function can be used to protect the pump from damage in the event of the system’s air cell losing its air charge. If air is lost from a system’s air cell due to a ruptured
diaphragm or leaking air valve, the pump will hunt on and o󰀨 rapidly.
Such rapid cycling will cause the pump to overheat very quickly. The F29’s
anti-cycling feature can be used to shut down the pump and prevent damage in such a situation. To use the anti-cycling function for this type of pump protection simply set the starts per hour to some value that is marginally higher than the system’s normal start rate. This will avoid
nuisance tripping but will shut the pump down if excessive sequential
cycling is encountered.
Burst Pipe Detector
The F29 includes a unique system for detecting burst pipes. It is most
commonly used in systems that are set up as a pressure system and are controlled by an external pressure switch connected to the remote input
terminal of the ow switch.
If a pressure system bursts its discharge pipe the system pressure will fall and the pump will start at its low pressure setting. The pump will then run continuously until the water source is depleted. If the discharge pipe splits
and the pump has su󰀩cient capacity the result may be continuous cycling
of the pump as it attempts to satisfy the leak. The F29 addresses these two scenarios with two separate functions, anti-cycling and burst pipe
13
detection. When both functions are activated the complete spectrum of
possibilities is covered. Anti-cycling will detect cyclic starting and stopping and can be set to shut the pump down after a predetermined number of cycles. This function detects split and leaking pipes.
The burst pipe detector addresses the issue of a completely burst pipe where the pump would ordinarily discharge at its full capacity until the source of water was depleted. It does this by using a timer that times out for a settable period each time the pump runs. The timer resets back to its original setting each time the pump stops. The range of adjustment is zero to 99 hours 59 minutes in increments of 1 minute.
In a typical application the burst pipe detector would be set to some time that was marginally longer than the longest time the pump would ordinarily run. For example, in a domestic pressure system day to day usage may
require the pump to run for no longer than 15 minutes (for showers etc.).
Perhaps once every few days the system is used for garden watering and
required to run for 30 minutes. In this scenario the burst pipe detector would be set to 35 or 40 minutes.
Each time the pump switches on the burst pipe detector begins to count
down. In normal circumstances the pump will shut o󰀨 in less than 30 minutes. This resets the burst pipe detector’s timer back to 40 minutes. If
however, the pump continues to run, due perhaps to a burst pipe, it will
eventually reach the set point of 40 minutes. The pump will then be instantly
shut down preserving whatever source water remains. The F29 will then display “burst pipe detected” on its LCD screen.
The setting of the burst pipe detector is a matter of balance between nuisance tripping and maximum preservation of the water source. If the burst pipe detection timer is set too close to the actual maximum usage time, the system may trip out occasionally due to slightly excessive water usage. If however, the timer is set too long the result will be wasted water in the event of a genuine burst pipe.
The burst pipe detection system can be used to protect water reserves in
tank lling and transfer pump applications. As an example, consider a tank lling application. The capacity of the pump and the tank are known so the
14
maximum run time of such a system will be the time required to ll the tank when it is completely empty. Draw o󰀨 from the tank may add to this time
but fundamentally the time will be known within reasonable bounds. If the
level switch in the tank fails or the oat valve fails and the tank continuously overows, eventually the pump under the control of the F29’s burst pipe
detector will reach the burst pipe detector’s set point and the pump will be shut down preserving what remains of the water source.
Leak Detector
The F29 includes a unique leak detection system that can be used to
analyse suspected leakage in a pressurised pumping system. The leak
detector can be switched on or o󰀨 in the main menu. It should be left switched o󰀨 when not required as its display screen excludes the display
of normal system messages when it is in use.
The leak detection system will only operate in systems where the F29 is connected to an external pressure switch as it relies on the opening and closing of the pressure switch to count pump starts and to evaluate pump running time. It will not operate in systems where the F29 is connected to tank level switches or other external devices. The leak detector will not
appear in the F29’s main menu unless all other functions are turned o󰀨 with
the exception of the remote input and the start and run-on timers.
When selected it operates in the following way. Open all valves feeding into
the pipe system to be checked. Close all valves at the extreme ends of the pipe system so the system can be pressurised. Press the reset button on the controller, this will zero the leak detector screen and run the pump until the system is fully pressurised. Leave the system unattended for a period of time perhaps an hour or even a day or two. On returning to the system,
the ow switch’s LCD screen will be displaying the number of times the
pump started and the total run time in hours minutes and seconds since the time the leak detector was zeroed.
If the leak detector screen displays no starts and no run time, then no leak has occurred from the system in the interim period. If the screen displays a number of starts and a total run time, a leak has occurred and the magnitude of the leak can be assessed by considering the total run time displayed and
the capacity of the specic pump. The leak detector can be used in any
15
pressurised pumping system, eg: from a small domestic pressure or transfer system to complex irrigation and stock watering systems comprised of many kilometres of pipe.
Program Lock
The F29 ow switch has a hidden security lock. When activated, the lock
disables the programming button P and prevents access to the F29’s
menu. To lock or unlock the ow switch, press the up and down buttons
together while the pump is in normal operation (not while it is being programmed). Pressing the up and down buttons together while in normal
running mode shuts down the pump and opens the ow switch’s lock screen. Once the lock screen is displayed the ow switch can be locked or
unlocked by pressing the up or down buttons. Pressing (P) then exits the
lock screen and the ow switch resumes normal operation. When locked, pressing the (P) button has no e󰀨ect on the ow switch and does not take
you into the menu in the usual way. Access to the menu can then only be
obtained by rst unlocking the program.
Running Time Display
The F29 keeps track of how long a pump under its control runs for. The total for any given run is displayed on the LCD screen each time the pump stops. This information is displayed along with any other relevant information about the state of the pump or the reason for the shutdown by alternating the information at 5 second intervals on the LCD screen while
the pump is o󰀨. The time display is in minutes and it accumulates while
ever the pump runs. The time resets to zero each time the pump starts or
the reset button is pressed or each time power is reset (switched o󰀨 and
back on). The time that a pump runs for can be useful information to have. For example if a pump under the control of the F29 runs dry then it is useful to know how long it ran for before it ran dry. Consider an irrigation system
where the F29 has detected a problem during a xed irrigation cycle and
shut the pump down. It is very useful to know how long the pump ran for before the shutdown occurred.
16
The Hour Meter
The F29 has a built in hour meter that keeps track of the total time a pump under its control runs for. The hour meter can be used for scheduling routine maintenance or for monitoring total water intermittently or continuously pumped over long periods. The hour meter displays the total hours run for 2 seconds each time the pump stops. It is viewable by watching the LCD screen carefully during this 2 second period as the F29 shuts the pump down. The hour meter can also be viewed and reset to zero from within the programming menu. Press the (P) button to access the main menu and press it again to display the controller’s model number
screen. With the display showing “F29 CONTROLLER”, press the UP
arrow button and the hour meter will display. The time displayed on the hour meter represents the actual hours the pump has run for in total. To reset the hour meter to zero, press the down arrow button. To exit out of the hour meter screen press (P). The hour meter accumulates running time and does not lose its memory of the total pumping hours even if the
power is switched o󰀨 for extended periods. The meter can accumulate up to 7.4 years of total running time ( in hours) before it automatically resets
to zero.
LCD Screen Back Light
The LCD screen on the F29 ow switch has a built-in backlight. The
backlight switches on automatically whenever you are programming the
ow switch and when the F29 is displaying certain fault conditions. In normal operation the backlight remains o󰀨.
The LCD screen backlight can be switched on manually at any time by pressing and holding down the down arrow button. The screen will remain illuminated while you are depressing the down button. The screen will
switch o󰀨 as soon as you release the button. The LCD backlight can’t be
permanently switched on, it only operates while the down button is pressed.
17
WARNING
If the F29 Flow switch is used in a manner not specied
by the manufacturer the pump protection provided by
the ow switch may be impaired or negated. In addition,
all warranties stated or implied will be rendered invalid.
Designed and Manufactured in Australia by
KELCO Engineering Pty Ltd
A.B.N. 20 002 834 844 Head O󰀩ce and Factory: 9/9 Powells Road Brookvale 2100 Australia Postal Address: PO Box 7485 Warringah Mall NSW 2100 Phone: +61 2 99056425 Fax: +61 2 99056420 Email: sales@kelco.com.au Web www.kelco.com.au
PLEASE NOTE: Kelco Engineering Pty Ltd reserves the right to change the specication of this
product without notice. Kelco Engineering Pty Ltd accepts no liability for personal injury or economic
loss as a consequence of the use of this product. All rights reserved copyright Kelco Engineering
Pty Ltd © 2016
DO NOT EXPOSE THIS CONTROLLER TO VIBRATION. INSTALL ONLY IN PIPEWORK OR MANIFOLDS
THAT DO NOT VIBRATE. Vibration will damage the sensitive electronics within the controller and will void
your product warranty.
To change the functions of this controller please rst read the programming book supplied with this unit.
This Kelco controller has been fully tested and calibrated. It is presently unlocked and has a simple
program loaded. It is set to operate in a basic way with most of its special functions and features
switched o󰀨.
On start up this controller will run the pump using its start-up timer. If it nds normal operating conditions in
the pipe system it will continue to run the pump. If pressure or ow conditions change the pump will continue
to run for a short period held on by the controller’s built in run-on timer. If acceptable conditions fail to return
the pump will be shut down after the run-on time period. Pressing the red reset button on the controller’s lid
or resetting the power will repeat this basic process.
VERY IMPORTANT
IMPORTANT
Loading...