F116 Series 2 Self-Contained
Ductable Commercial Air Cleaner
The F116 Series 2 Self-Contained Ductab l e Commercial Air Cleaner is a media air cleaner that uses a three-speed direct drive forward curve blower/motor with a variety of filter combinations to remove airborne contaminants. The air cleaner is designed to provide its own air circulation. In addition it can accomodate ducting which can be attached to the intake and/or the outlet of the cabinet as the application requires.
PRODUCT DATA
FEATURES
• Variety of filter combinations available; High Efficiency Particulate Air (HEPA) filter is 99.97% efficient and the hospital grade particle filter is 95% D.O.P. efficient at
0.3 micron particles. There is also a 95% ASHRAE filter.
• Circulates up to 2600 cfm.
• Designed to overcome the increase in air flow resistance normally caused by filter loading.
• Negative and positive pressure rooms can be created with air cleaner.
• CPZ™ module removes up to 95% of the space odors for up to 24 months.
• 3-Speed remote wall switch.
• 120 Vac, 60 Hz and 230 Vac, 50Hz models available.
• READ AND SAVE THESE INSTRUCTIONS
The air cleaner is suitable for the collection of smoke, bacteria and viruses, gases, odors and volatile organic compounts (VOCs), fine saw dust, paper dust, brazing, normal atmospheric dusts such as pollens, allergens, dust mites and soot, and virutally any other respirable airborne contaminant. When equipped with CPZ™ modules, gases and odors are adsorbed from the air passing through the unit.
The Honeywell Trademark is used under license from Honeywell International Inc. by Air-Pure Systems. Honeywell International Inc. makes no representations or warranties with respect to this product.
Contents
Application.........................................................................1
Features ............................................................................1
Specifications....................................................................2
Ordering Information .........................................................2
Planning the Installation ....................................................6
Installation.........................................................................10
Operation...........................................................................12
Service ..............................................................................13
Troubleshooting.................................................................14
Parts List.............................. ... ....................................... ... .14
Limited Two-Year Warranty ................................... ............16
68-0200-5
Page 2
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
SPECIFICATIONS
IMPORTANT
The specifications given in this publication do not include normal manufacturing tolerances. Therefore, this unit may not exactly match the listed specifica­tions. Also, this product is tested and calibrated under closely controlled conditions, and some minor differences in performance can be expected if those conditions are changed.
Blower/Motor: Three speed direct drive forward curve. Models / Electrical Ratings / Air Volume: Refer to Table 1.
The F116 Series 2 air cleaner is available in two cabinet sizes.
The shorter cabinet uses a prefilter with one primary filter while the longer cabinet (3 bay) uses a prefilter with two primary filters. Refer to Table 1 for models.
Table 1. F116 Series 2 Filter Configuration and Air Volu me.
Filters ( 2 stage and 3 stage)
Model* Electrical Ratings
F116A1021-3S 120 Vac, 60 Hz, 8.7A 99.97% HEPA N/A 1975 (3355) 1825 (3100) 1500 (2550) F116A1047-3S** 120 Vac, 60 Hz, 11.2A 95% at 0.3 micron N/A 2450 (4160) 2 150 (3650) 1575 (2675) F116A1047-3S** 120 Vac, 60 Hz, 12.0A 95% ASHRAE N/A 2600 (4425) 2125 (3600) 1575 (2675) F116A1047-3S** 120 Vac, 60 Hz, 12.5A CPZ™ modules N/A 2575 (4375) 2075 (3525) 1475 (2500) F116A1120-3S** 120 Vac, 60 Hz, 7.0A 99.97% HEPA CPZ™ modules 1475 (2500) 1 425 (2425) 1275 (21 50) F116A1120-3S** 120 Vac, 60 Hz, 7.5A 95% at 0.3 micron CPZ™ modules 1775 (3000) 1 700 (2875) 1500 (2550) F116A1120-3S** 120 Vac, 60 Hz, 7.8A 95% ASHRAE CPZ™ modules 1825 (3100) 1700 (2875) 1475 (2500) F116A1120-3S** 120 Vac, 60 Hz, 7.5A CPZ™ modules CPZ™ modules 1675 (2850) 1600 (2700) 1400 (2375) F116A2021-3S 230 Vac, 50 Hz, 3.2A 99.97% HEPA N/A 1475 (2500) 1 375 (2325) 117 5 (2000) F116A2048-3S** 230 Vac, 50 Hz, 3.7A 95% at 0.3 micron N/A 2050 (3475) 1825 (3100) 1375 (2325) F116A2048-3S** 230 Vac, 50 Hz, 4.0A 95% ASHRAE N/A 2225 (2775) 1925 (3275) 1375 (2325) F116A2048-3S** 230 Vac, 50 Hz, 3.5A CPZ™ modules N/A 1775 (3000) 1650 (2800) 1325 (2250) F116A2121-3S** 230 Vac, 50 Hz, 3.0A 99.97% HEPA CPZ™ modules 1175 (2000) 1100 (1875) 1000 (1700) F116A2121-3S** 230 Vac, 50 Hz, 3.2A 95% at 0.3 micron CPZ™ modules 1450 (2475) 1375 (2325) 1200 (2025) F116A2121-3S** 230 Vac, 50 Hz, 3.2A 95% ASHRAE CPZ™ modules 1525 (2600) 1425 (2425) 1225 (2075) F116A2121-3S** 230 Vac, 50 Hz, 3.0A CPZ™ modules CPZ™ modules 1375 (2325) 1300 (2200) 1150 (1950)
*
All Models come with 30% ASHRAE Prefilter in Bay 1.
**
Filters purchased separately
Accessories:
Remote 3-Speed Wall Switch
Approvals:
Underwriters Laboratories Inc.: cULus pending.
Starting Internal Static Pressure: See Table 2 . Initial Internal Static Pressure / Installation Weight:
Approximately 108 lb to 229 lb (kg) depending on the filter
configuration. Refer to Table 2.
High
cfm(m
3
/hr)
Medium
cfm (m3/hr)
Low
cfm (m3/hr)Bay 2 Bay 3
ORDERING INFORMATION
If you have additional questions, need further information, or would like to comment on our products or services, please write or phone:
1. Your local Honeywell Commercial Air Products Distributor.
2. Air-Pure Systems
16873 Fish Point Rd. SE Prior Lake, MN 55372 www.cleanairfacility.com Phone: (800) 998-1919 Fax: (800) 221-3248
68-0200-5 Release 05/2011 2
Page 3
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
Table 2. F116 Series 2 Filter Configuration, Internal Static Pressure, and Hanging Weight with Filters.
Filters ( 2 stage and 3 stage)
Starting Internal Static Pressure
( inches of Water Gauge)
Hanging
Weight with
Filters in
Model**
lbs (kg)Bay 2 Bay 3 High Medium Low
F116A1021-3S 99.97% HEPA N/A 1.5” 1.4” 1.1” 149 (68) F116A1047-3S* 95% at 0.3 micron N/A 1.2” 1.0” 0.6” 130 (59) F116A1047-3S* 95% ASHRAE N/A 1.1” 0.8” 0.5” 108 (49) F116A1047-3S* CPZ™ modules N/A 1.6” 1.3” 0.9” 143 (65) F116A1120-3S* 99.97% HEPA CPZ™ modules 1.7” 1.6” 1.4” 205 (93) F116A1120-3S* 95% at 0.3 micron CPZ™ modules 1.6” 1.5” 1.3” 193 (88) F116A1120-3S* 95% ASHRAE CPZ™ modules 1.6” 1.5” 1.2” 189 (86) F116A1120-3S* CPZ™ modules CPZ™ modules 1.7” 1.6” 1.3” 229 (104) F116A2021-3S 99.97% HEPA N/A 1.1” 1.0” 0.8” 149 (68) F116A2048-3S* 95% at 0.3 micron N/A 1.0” 0.8” 0.5” 130 (59) F116A2048-3S* 95% ASHRAE N/A 0.9” 0.7” 0.4” 108 (49) F116A2048-3S* CPZ™ modules N/A 1.1” 1.0” 0.6” 143 (65) F116A2121-3S* 99 .9 7% HEPA CPZ™ modules 1.2” 1.1” 0.9” 205 (93) F116A2121-3S* 95% at 0.3 micron CPZ™ modules 1.1” 1.0” 0.8” 193 (88) F116A2121-3S* 95% ASHRAE CPZ™ modules 1.1” 1.0” 0.8” 189 (86) F116A2121-3S* CPZ™ modules CPZ™ modules 1.2” 1.1” 0.9” 229 (104)
Filtration Efficiency:
See Table 3.
Dimensions:
Refer to Figures 1 and 2 for dimensions
Table 3. F116 Series 2 Filter Description.
Dimensions in
Filter
inches (mm) Efficiency Description
Prefilter 24 x 24 x 4
(610 x 610 x 102)
HEPA 24 x 24 x 12
(610 x 610 x 305)
D.O.P. 24 x 24 x 12
(610 x 610 x 305)
ASHRAE 24 x 24 x 12
(610 x 610 x 305)
Sorbent Module Options:
Charcoal only
Permanganate only
Zeolite only or
12 x 12 x 22
(305 x 305 x 559)
CPZ material (combination of the above ingredients)
Replacement Parts See Parts List, Table 5.
30% to 40% Disposable pleated synthetic
fiber in beverage board frame.
99.97% at 0.3 micron at 2000 cfm (57 m3/min)
95% at 0.3 micron at
In metal frame with aluminum pleat separators in the media.
In metal frame.
2000 cfm (57 m3/min)
95% ASHRAE dust spot at
In metal frame.
2000 cfm (57 m3/min)
85% first pass at 1600 cfm
for most gases / odors.
Diposable filter with at least twenty pounds of CPZ. Must use two modules per bay.
3 68-0200-5
Page 4
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
10
(254)
TOP
7
(178)
FRONT VIEW
12-1/8 (308)
7/8 (22) FLANGE
13-1/2
(343)
5 TYP (127)
3/8 THREADED INSERT HOLE FOR HANGING INSTALLATION
16 TYP (406)
24-1/4 (616)
48 (1219)
22-1/4
(565)
26
(660)
SORBENT MODULES
HEPA, D.O.P. OR ASHRAE FILTER
26
(660)
ALL MODELS, EXCEPT F116A1021 AND F116A2021, ARE EQUIPPED WITH A DISPOSABLE ALUMINUM SPACER. THE SPACER IS SUPPLIED TO ACCOMMODATE THE CPZ MODULES. IF YOU DO NOT USE THE CPZ MODULES, REMOVE THE SPACER. IF YOU USE TWO SETS OF CPZ MODULES (4 MODULES) IN A THREE STAGE CABINET, YOU WILL REQUIRE AN ADDITIONAL SPACER. SAVE A FEW SPACERS THAT ARE NOT NEEDED TO ACCOMMODATE FUTURE NEEDS.
M7829D
PREFILTER
M10810B
Fig. 1. Approximate dimensions of F116 2-stage filtering model in inches (mm).
68-0200-5 Revised 05/2011 4
Page 5
FRONT VIEW
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
10
254)
TOP
7
(178)
7/8 (22) FLANGE
13-1/2 (343)
5 TYP (127)
12-1/8 (308)
3/8 THREADED INSERT HOLE FOR A HANGING INSTALLATION
16 TYP
(406)
24-1/4
(616)
17
(432)
64
(1626)
21-1/4
(540)
26
(660)
SORBENT MODULES
CAN BE POSITIONED IN EITHER SPACE OR IN BOTH SPACES FOR DOUBLE PASS
D.O.P. OR ASHRAE FILTER
CAN BE POSITIONED IN EITHER SPACE OR IN BOTH SPACES FOR DOUBLE PASS
26
(660)
ALL MODELS, EXCEPT F116A1021 AND F116A2021, ARE EQUIPPED WITH A DISPOSABLE ALUMINUM SPACER. THE SPACER IS SUPPLIED TO ACCOMMODATE THE CPZ MODULES. IF YOU DO NOT USE THE CPZ MODULES, REMOVE THE SPACER. IF YOU USE TWO SETS OF CPZ MODULES (4 MODULES) IN A THREE STAGE CABINET, YOU WILL REQUIRE AN ADDITIONAL SPACER. SAVE A FEW SPACERS THAT ARE NOT NEEDED TO ACCOMMODATE FUTURE NEEDS.
M7829D
PREFILTER
M10811B
Fig. 2. Approximate dimensions of F116 3-stage filtering model in inches (mm).
5 68-0200-5
Page 6
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
PLANNING THE INSTALLATION
WARNING
TO REDUCE THE RISK OF FIRE,ELECTRICAL SHOCK, OR INJURY TO PERSONS,OBSERVE THE FOLLOWING:
1. Installation Work And Electrical Wiring Must Be Done
By Qualified Person(s) In Accordance With All Applica­ble Codes And Standard, Including Fire Rated Con­structions.
2. When Cutting Or Drilling Into The Wall Or Ceiling, Do Not Damage Electrical Wiring And Other Hidden Utili­ties.
3. Never Place A Switch Where It Can Be Reached From A Tub Or Shower.
4. Use This Unit Only In The Manner Intended By The Manufacturer. If You have Questions, Contact The Man­ufacturer.
5. Before Servicing Or Cleaning Unit, Switch Power Off At Service Panel And Lock Service Panel To Prevent Power From Being Switched on Accidentally.
6. If This Unit Is To Be Installed Over A Tub Or Shower, It Must Be Marked As appropriate For The Application and be connected to a GFCI (Ground Fault Circuit Inter­rupter) - protected branch circuit.
Consult with a mechanical engineer or contractor experienced in duct design and pressure calculations for assistance in ducting your F116 Series 2 air cleaner.
Choose Location
Choosing a location that is readiliy accessible for regular inspection and cleaning. Allow enough room for removing the prefilter and primary filters. Be sure there is room for servicing without removing pipes, ducts, or other heating system components. See Fig. 3 through 11 for suggested locations.
AIR CLEANER
Static Pressure / Ducting
Smooth round duct offers the least resistance (static pressure) to airflow. Round ducting with a total inside area of 200 square inches (approximately 16” diameter) and a maximum straight run length of 100 feet, with approximately 2300 CFM passing through it, develops approximately 0.2” W.G. of static pressure.
A square or rectangular duct with 100 feet of straight length, 240 square inches of opening ( approximately 15” x 16”) with approximately 2300 CFM passing through it, develops 0.2” W.G. of static pressure.
Add 0.35” W.G. presssure for each 90 and 0.05” W.G. for each change in duct diameter, slight bend, and grill / diffuser used. Use a duct system whose face area is equal to those mentioned. Increase the duct face area to reduce pressure, decrease the duct face to increase pressure.
Use of flexible ducting, corrugated ducting and duct board will add approximately 15% to 30% additional static pressure compared with smooth surface metal ducts (galvanized or painted sheet metal) of equal size.
To compute round duct face area in square inches, multiply the square of the diameter in inches by 0.7854. Multiply the width in inches by the height in inches of a rectangular or square duct to find its face area in square inches.
If there is too much ducting pressure, the net air volume will reduce from the system, thus stressing the motor and potentially causing motor damage.
0
elbow in the system,
M10795
Fig. 3. Positioning air cleaner for vapor control in
printing, brazing, soldering, or glue shop s.
AIR  CLEANER
AIR CLEANER
TOP VIEW
SIDEVIEW
CURTAIN
OUTPUT
CONVEYOR
CURTAIN
DRYER
DRYER HOOD
INPUT
INPUT
M10797
Fig. 4. Positioning air cleaner to remove po llut ant s from a
conveyor feed process such as screen printing.
68-0200-5 Revised 05/2011 6
Page 7
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
Smoking
Section
Non-
Smoking
M7783
Fig. 5. Positioning air cleaners at the far end of the restaurant smoking section to draw the smoke away from the
nonsmoking section.
M7782
Fig. 6. Positioning air cleaners to create a negative pressure in polluted spaces and creating a positive pressure in
nonpolluted areas. Use this positioning in in-plant offices and hospitals.
7 68-0200-5
Page 8
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
AIR CLEANER
AIR CLEANER
FLEXIBLESTATIONARY
Fig. 7. Positioning air cleaner for suspended side draft applications.
M10799
AIR CLEANER
DO NOT INSTALL WHERE THERE IS  HEAVY OIL SMOKE, COOKING,  HEAVY WELDING OR HEAVY CUTTING.
M10800
Fig. 8. Connecting air cleaner direct ly to a canopy hood
with a minimum air entrance velocity of 120 fpm.
DO NOT INSTALL WHERE THERE IS  HEAVY OIL SMOKE, COOKING,  HEAVY WELDING OR HEAVY CUTTING.
AIR CLEANER
M10801
Fig. 9. Positioning air cleaner to recirculate existing
exhaust system air which contains light to medium
quantities of pollutants.
68-0200-5 Revised 05/2011 8
Page 9
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
POSITIVE PRESSURE ROOMS SUCH AS IN PLANT SATELLITE OFFICES
AIR CLEANER
AIR CLEANER
AIR CLEANER
AIR CLEANER
CURTAIN
M10796
30 FT (9M)
WORK AREA
30 FT
(9M)
30 FT
(9M)
AIRFLOW
Fig. 10. Positioning air cleaner to create a negative
pressure booth that cont ain s a co ntamination generating
process.
M10798
Fig. 11. Positioning air cleaner to create positive pressure
for plant satellite office.
9 68-0200-5
Page 10
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
INSTALLATION
WARNING
Explosion Hazard Possible. Can cause personal injury or equipment damage.
Do not install or use the F116 Series 2 air cleaner where there is any danger of gas, vapor or dust explosion.
IMPORTANT
This air cleaner has not been investigated for use in the ceilings of fire-resistant assemblies.
CAUTION
Electrical Hazard. Can cause personal injury or equipment damage.
Turn off power before installing or servicing the air cleaner.
IMPORTANT
Stand on a stable platform when working with the air cleaner.
When Installing this Product…
1. Read these instructions carefully. Failure to follow them
could damage the product or cause a hazardous condi­tion.
2. Check the ratings given in the instructions and on the product to make sure the product is suitable for your application.
3. Installer must be a trained, experienced service techni­cian.
4. After installation is complete, check out product opera­tion as provided in these instructions.
Threaded rod, eyebolts with chains, or any standard practice and hardware for hanging method can be used in the suspension of the air cleaner. See Fig. 12.
NOTE: State and local codes and accepted installation prac-
tices must be followed.
FASTEN SECURELY TO STRUCTURAL SUPPORT SYSTEM I.E. BAR JOIST, CONCRETE SLAB, TIMBER FRAMING, ETC.
ALL EXTERNAL HARDWARE FURNISHED BY OWNER.
THREADED  ROD
JAM NUT
TOP OF  AIR CLEANER CABINET
3/8 x 16T NUTS INSTALLED IN CABINET CORNERS
CHAIN
HEX BOLT
LOCK  WASHER
EYEBOLT
JAM NUT 3/8 x 16T
M10802
Fig. 12. Fastening air cleaner t o a str uctural support
system (bar joist, concrete slab, or timber framing).
Installation with Ducting
Use a transition or box plenum to attach the ducting to the air cleaner inlet and outlet. On the inlet, a transition plenum is preferred, see Fig. 13.
WARNING
Remove packing materials / Parts from inside the Motor / Blower compartment prior to installation or initial power on.
Mount Air Cleaner Cabinet
The F116 Series 2 air cleaner must be attached to a structure capable of supporting the weight of the unit with filters, ducting and plenums when used. Roof trusses, bar joists and floor joists are examples of suitable structures.
MPORTANT
All suspension points (either six or eight depending on the model) must be used for proper and safe installation. See Fig. 1 and 2 for dimensions between the suspension points.
68-0200-5 Revised 05/2011 10
AIR CLEANER
M7793A
Fig. 13. Transition plenum connected to the air cleaner
inlet.
If a box plenum is used on the inlet, a diffusion screen must be installed in the box, see Fig. 14. A box plenum can accomodate more than one inlet
Page 11
DIFFUSION SCREEN
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
IMPORTANT
• Be sure the air cleaner is grounded for correct operation and safety.
AIR CLEANER
• Canadian installation: NEVER install in ceilings with thermal insulation value greater than R-40.
FACTORY WIRING
BLACK
BLACK
M10803
Fig. 14. Box plenum with diffusion screen and three inlets
connected to the air cleaner inlet.
On the outlet, use a square-to-round or square-to-square connection when attaching the air cleaner outlet to the blower discharge flange, see Fig. 15. The outlet connection can be used with a Y-branch, distribution box or manifold as required.
AIR CLEANER
Y-BRANCH
SQUARE-TO-ROUND CONNECTION
M7792A
Fig. 15. Square-to-round connection attached to the air
cleaner outlet.
Electrical Hookup
All wiring must comply with applicable codes and ordinances. The power source must agree with the model type: 120V, 60 Hz or 230V, 50 Hz. Refer to figure 16 for electrical connection setup.
1. Remove screws on motor compartment cover and remove.
2. Refer to figure 16 for typical electrical diagram
WARNING
Risk of Fire or Electric Shock. Can cause personal injury or equipment damage.
Use only Honeywell 190097C Remote Speed Switch (3-speed models only) to regulate air cleaner speed. Using a different speed switch may void the warranty.
A100002
RED
BLUE
VIOLET
SWITCH
REMOTE 3-SPEED
EXTERNAL WIRING BY INSTALLER
CAPACITOR
BROWN
WHITE GREEN
MOTOR
Fig. 16. Typical F116 Series 2 only 120V, 60 Hz or
230V, 50 Hz wiring diagram.
Remote 3 Speed Wall Switch (F116 Series 2)
The 190097C Remote Wall Switch Assembly allows control of the F111 model air cleaners from a a location separate from the air cleaner. The assembly includes a remote switch with an outlet box cover, outlet box, extension ring, and a wire harness. Wiring to connect the remote switch and air cleaner must be furnished separately.
CAUTION
• This installation to be performed only by a qualified installer.
• All wiring to comply with local electrical codes.
• Disconnect power to air cleaner at fuse or breaker before beginning work. Failure to do so can result in shock hazard endangering equipment and personal safety of installer.
• Only one air cleaner can be connected to a remote switch
1. Disconnect power to air cleaner.
2. Mount 4” x 4” outlet box at desired remote location.
3. Attach 3/4” extension ring to outlet box.
4. Run five conductor, color-coded, 14-gauge wires from
the remote switch location to the air cleaner.
5. Use three wire nuts to connect three color-coded, lead wires on the remote switch to three color-coded wires from the air cleaner. (Red, Blue, Violet)
6. Use one wire nut to connect white color-coded, lead wire from the air cleaner to single color-coded wire from the power supply. (White)
11 68-0200-5
Page 12
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
OPERATION
Because the F116 Series 2 air cleaner provides its own circulation, it can be mounted independently or in a duct system. When used in a duct, the air cleaner volume must be
BLACK
A100001
Fig. 17. Wiring 3-Speed Remote Switch
7. Connect the ground wire from the power supply to a
ground stud of the outlet box.(Green)
8. Connect the ground wire from the air cleaner to the ground stud of the outlet box.(Green)
9. Use one wire nut to connect the black color-coded, lead wire on the remote switch to the black color-coded wire from the power supply.
10. Fold wires into box and mount remote switch on outlet box. Leave switch in OFF position.
11. On the air cleaner remove two screws on wiring com­partment cover and open
12. Run five conductor, color coded, 14 gauge wires from the remote switch through the air cleaner access open­ing into the wiring compartment. Strip ends of remote switch lead wires
13. Connect three wires on air cleaner to remote switch lead wires with wire nuts following color code used at remote switch. (Red, Blue, Violet)
14. Connect one wire on air cleaner to power supply wire with a wire nut following color code used at remote switch. (White)
15. Connect the ground wire from the remote switch to a ground stud of the wiring compartment cover.(Green)
16. Fold wires into wiring compartment. Replace wiring compartment cover.
17. Turn on power to air cleaner at fuse or breaker.
18. Check operation by turning air cleaner at HIGH,
MEDIUM, and LOW. Note
that only the remote switch
will operate the air cleaner.
19. Turn off the power and install the filters in the cabinet.
NOTE: Select models have a disposable aluminum spacer.
the spacer is necessary only when using the CPZ modules. All other filters need to remove and save the spacer for future needs. Refer to figures 1 and 2.
20. Replace the motor compartment cover.
the same as the duct and plenum. When the air cleaner is powered, the blower/motor draws the
contaminated air into the air cleaner. Particles that are too small to be caught in the prefilter are trapped by the primary filter. The clean air is then discharged (two stage) or goes through a second primary filter (three stage) and is then discharged.
The F116 Series 2 air cleaner has been engineered to improve indoor air quality for commercial and industrial applications. The filters are the most practical and effective filtering system for removing atmospheric dust, pollens, bacteria, viruses, mold spores, smoke, fumes, mists and aerosols. Refer to Fig. 8.
The air cleaner is either operating or off. There are no other operational options available. Even when the area is unoccupied, the air cleaner can be operated continuously to prevent buildup of airborne contaminants. Operate the air cleaner only when the area is occupied when specific activities produce contaminants.
The CPZ™ sorbent module has the ability to collect and hold gas-phase compounds and vapors typically found in commercial and light industrial facilities. These gases and vapors frequently appear as odors that, at times, can be annoying and irritating. The modules become saturated after collecting 25% to 50% of their weight in gaseous odors. The quantity of CPZ™ material provides adequate dwell time to ensure up to 95% collection efficiency in the first pass. This also provides a long maintenance-free service life.
The minimum recommended air exchange rate is 2.5 times per hour. In a heavily contaminated area, up to 15 air exchanges per hour can be necessary. The factors that determine what the rate of air exchange should be are:
• generation rates of the various pollutants;
• concentration level of the pollutants;
• desired contamination reduction level. Airborne contaminants will always be present in the air where
contaminant generations take place. Air cleaning systems and ventilators do not eliminate airborne contaminants, they reduce the excessive accumulation of the contaminants. To eliminate the contamination, the source of contamination must be removed.
Local, Federal and professional ventilation engineering standards and codes prescribe minimum ventilation rates to dilute air contamination in specific applications. The ventilation rates usually assume the injection of outdoor air measured as air exchange rate. The use of the F116 air cleaner to comply with ventilation requirements is an acceptable alternative to ventilation with outdoor air. However, at least 20% of a specified ventilation rate or code must be derived from outdoor air. The F116 air clean er filtered and recirculated air can be the remaining 80%.
68-0200-5 Revised 05/2011 12
Page 13
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
SERVICE
CAUTION
Electrical Hazard. Can cause personal injury or equipment damage.
Turn off power before installing or servicing the air cleaner.
IMPORTANT
Be sure to change filters as recommended to prevent reduced airflow in the air cleaner. Stand on a stable platform when working with the air cleaner.
IMPORTANT
Air cleaner and components are susceptible to damage. T ake care when working with them to avoid equipment damage.
The air cleaner removes a variety of particulate contaminants from the air. In the process of cleaning the air, the air cleaner filters become dirty and the cleaning efficiency is lowered.
To maintain a high standard of reliability and efficiency, it is necessary to periodically service the air cleaner. The maintenance is determined by the quantity and type of contaminants present and the frequency of air cleaner use. The frequency of servicing can be established after a period of use.
NOTE: Some full-service distributors provide regular
servicing to commercial establishments.
The particle filter life ranges from 6 to 24 months with 12 to 18 months as an average.The useful life of the CPZ™ sorbent modules may vary from 4 to 24 months, depending on the application. In most applications, the sorbent media life ranges from 4 to12 months. The filters and modules need to be changed more frequently in facilities that operate 24 hours a day.
CPZ™ Adsorbent Module
The CPZ™ adsorbent module is used to collect gases, vapors, odors and volatile organic compounds (V.O.C.) from the air that passes through the air cleaner. Adsorbents collect and hold 25% to 50% of their weight in odorous gases and vapors. The impurities are collected until the adsorbents reach saturation. At saturation, the adsorbents emit a continuous strong pungent odor. If the air cleaner is turned off for 8 to 10 hours, there will a temporary odor when it is turned back on. If the odor persists for 30 minutes, it is time to replace the filters.
Prefilter, Media Filters and CPZ Modules
The disposable prefilter collects large dust particulates and lint- type airborne fibers. Check the filter every 3 months to determine the replacement frequency:
IMPORTANT
Do not touch the pleated filter media. Handle only the filter frame to prevent damage to the filter media.
1. Verify power shut off
2. Remove the air cleaner cover and set aside.
3. Remove the prefilter and primary filters.
4. Check the prefilter and replace if it is fully coated with
dust and lint. (approximately every 3 months)
5. Replace the primary media filter(s) when there is a noticeable loss of air volume from the air cleaner (approximately every 12 - 18 months)
6. Replace the CPZ sorbent modules when a continuous noticeable odor is emitted from the air cleaner. (approximately every 4 to 12 months).
7. Reassemble the air cleaner and turn the power on.
On initial startup, a small amount of dust can blow from the air cleaner. This is normal and stops a few minutes after startup. After running the unit for 5 minutes, turn off the unit, the unit is ready for operation.
Determining Media Filter Change
Media type particulate filters cause an increase in pressure as they collect and retain airborne particulates. The best way to determine when to replace these filters involves monitoring the pressure across the filters with a differential pressure gauge.
If a differential pressure gauge is not used, the apparent air volume that one feels is a good indicator of the filter loading. When the air volume is noticeably less, the cleanliness of the air in the space will decline. When that occurs, change the primary media filter(s). Then schedule the next primary media filter(s) change to occur 60 days earlier that the first filter change. Typically, change the prefilter at least every 3 months and the primary media filter(s) 12 to 18 months.
13 68-0200-5
TROUBLESHOOTING
CAUTION
Electrical Hazard. Can cause personal injury or equipment damage.
The following procedures expose hazardous live parts. Disconnect power before installing or servicing the air cleaner.
Page 14
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
Table 4. Troobleshooting the F116 Series 2 Air Cleaner
Model* Electrical Ratings
• Check wiring for loose connections - Tighten if neccessary.
• Check capacitor - Replace if necessary.
Motor will not start
Vibration - High Frequency • Check that blower wheel is balanced - remove and balance or
Vibration - Low Frequency • Check if system is operating above 2.0” W.G. pressure - reduce
Scraping noise • Check if the blower wheel is touching the blower housing - adjust
Squeal or whistle noise • Check for air leaks in the cabinet doors or ducting - plug air leaks.
• Check for hot motor - Thermal protection relay is tripped, reset it.
•Replace motor.
replace wheel.
total pressure by replacing filters.
blower and position wheel in the center of the inlet ring.
PARTS LIST
Refer to Fig. 18 and Ta ble 5 for replacement part information
T able 5. Replacement Parts.
Fig.
Reference No. Description Pack Qty Order Number Reference No.
1 Prefilter 1 box of 6 32000200 860039
99.97% HEPA media filter 1 32000198 860023 95% D.O.P hospital grade filter 1 32000195 860024
2
OPTIONAL Parts not shown in Fig. 9.
95% ASHRAE particle filter 1 32000196 860025 CPZ™ sorbent module (requires 2) 1 32004078-001 N/A Charcoal sorbent module (requires 2) 1 32004078-002 N/A Zeolite sorbent module (requires 2) 1 32004078-003 N/A Permanganate sorbent module (requires 2) 1 32004078-004 N/A
Remote Wall 3-Speed Switch, Series 3 1 190097C Capacitor, Series 2 1 32000551-001 Motor / Blower; 120 V, 60 Hz, Series 2 1 32000552-003 Motor / Blower; 230V, 50 Hz, Series 2 1 32000552-004 Motor; Three Speed 120 VAC, 60Hz, Series 2 1 32000553-003 Motor; Three Speed 230 VAC, 50Hz, Series 2 1 32000553-004
68-0200-5 Revised 05/2011 14
Page 15
F116 SERIES 2 SELF-CONTAINED DUCTABLE COMMERCIAL AIR CLEANER
1
2 (SORBENT MODULES)
(HEPA, D.O.P.
2
OR ASHRAE FILTERS)
1
TWO STAGE MODELS WILL HAVE ONLY ONE PRIMARY FILTER AREA.
Fig. 18. Exploded view of F116 Series Air Cleaner components.
1 (PREFILTER)
M10812B
15 68-0200-5
Page 16
LIMITED TWO-YEAR WARRANTY
Air-Pure Systems warrants its air cleaner products to be free from defects in workmanship or materials under normal use and service, for a period of two (2) years from the date of purchase by the original end-user. If at anytime during the warranty period the product is defective or malfunc­tions, Air-Pure Systems, through the distributor or dealer, from which the product was purchased, or through an authorized warranty repair station, shall at Air-Pure Systems option, replace or repair the defective product or component.
This warranty does not cover removal or installation costs. This warranty shall not apply if it is shown that the defect or malfunction was caused by damage which occurred during handling or shipment, improper electrical connections, improper use of the product or abuse.
Air-Pure Systems sole responsibility shall be to repair or replace the product within the terms stated above. AIR-PURE SYSTEMS SHALL NOT
BE LIABLE FOR ANY LOSS OR DAMAGE OF ANY KIND, INCLUDING ANY INCIDENTAL OR CONSEQUENTIAL DAMAGES RESULTING, DIRECTLY OR INDIRECTLY, FROM ANY BREACH OF WARRANTY, EXPRESS OR IMPLIED, OR ANY OTHER FAILURE OF THIS PROD­UCT. (Some states do not allow the exclusion or limitation of incidental or consequential damages, so this limitation may not apply to you.) THE WARRANTIES SET FORTH HEREIN ARE EXCLUSIVE AND AIR-PURE SYSTEMS’ EXPRESSLY DISCLAIMS ALL OTHER WARRANTIES, WHETHER WRITTEN OR ORAL, IMPLIED OR STATUTORY, INCLUDING BUT NOT LIMITED TO ANY WARRANTIES OF MERCHANTABIL­ITY, WORKMANSHIP, OR FITNESS FOR A PARTICULAR USE.
This warranty gives you specific legal rights and you may have other rights which vary from state to state.
How to make a warranty claim or have questions answered:
Should you have a warranty claim or questions about the warranty policy, contact the distributor or dealer from which you purchased the product or the authorized warranty repair stations nearest your location.
NOTE: Do not return any products or parts to the factory without a factory issued “Returned Warranty Goods Label” issued by Air Pure Sys-
In the event you or other persons, have any questions concerning the use and care of this product or this warranty please call or write the factory.
Air-Pure Systems
16873 Fish Point Rd. SE Prior Lake, MN 55372-1714 Phone: (800) 998-1919 Fax: (800) 221-3248
tems.
Air-Pure Systems
16873 Fish Point Rd. SE Prior Lake, MN 55372-1714 Phone (800) 998-1919 Fax: (800) 221-3248
68-0200-5 Revised 05/2011 www.cleanairfacility.com
Loading...