GE Grid Solutions F60 Instruction Manual

Page 1
832762A2.CDR
GE
LISTED
52TL
IND.CONT. EQ.
E83849
Grid Solutions
F60 Feeder Protection System
UR Series Instruction Manual
F60 Revision: 7.2x
Manual P/N: 1601-0093-AA5 (GEK-119559D)
GE Grid Solutions 650 Markland Street Markham, Ontario Canada L6C 0M1 Tel: +1 905 927 7070 Fax: +1 905 927 5098 Internet: http://www.GEGridSolutions.com
*1601-0093-AA5*
GE Multilin's Quality Management
System is registered to ISO
9001:2008
QMI # 005094
UL # A3775
Page 2
Copyright © 2017 GE Multilin Inc. All rights reserved. F60 Feeder Protection System UR Series Instruction Manual revision 7.2x. FlexLogic, FlexElement, FlexCurve, FlexAnalog, FlexInteger, FlexState, EnerVista,
CyberSentry, HardFiber, Multilin, and GE Multilin are trademarks or registered trademarks of GE Multilin Inc.
The contents of this manual are the property of GE Multilin Inc. This documentation is furnished on license and may not be reproduced in whole or in part without the permission of GE Multilin. The content of this manual is for informational use only and is subject to change without notice. Part number: 1601-0093-AA5 (August 2017)
Page 3
TABLE OF CONTENTS
1. GETTING STARTED 1.1 IMPORTANT PROCEDURES
1.1.1 CAUTIONS AND WARNINGS ........................................................................... 1-1
1.1.2 INSPECTION PROCEDURE .............................................................................1-2
1.2 UR OVERVIEW
1.2.1 INTRODUCTION TO THE UR ........................................................................... 1-3
1.2.2 HARDWARE ARCHITECTURE......................................................................... 1-3
1.2.3 SOFTWARE ARCHITECTURE.......................................................................... 1-4
1.3 ENERVISTA UR SETUP SOFTWARE
1.3.1 SYSTEM REQUIREMENTS ..............................................................................1-5
1.3.2 INSTALLATION..................................................................................................1-5
1.3.3 CONFIGURING THE F60 FOR SOFTWARE ACCESS .................................... 1-6
1.3.4 USING THE QUICK CONNECT FEATURE.......................................................1-9
1.3.5 CONNECTING TO THE F60 RELAY...............................................................1-14
1.3.6 SETTING UP CYBERSENTRY AND CHANGING DEFAULT PASSWORD ... 1-15
1.4 UR HARDWARE
1.4.1 MOUNTING AND WIRING............................................................................... 1-16
1.4.2 COMMUNICATIONS........................................................................................ 1-16
1.4.3 FACEPLATE DISPLAY.................................................................................... 1-16
1.5 USING THE RELAY
1.5.1 FACEPLATE KEYPAD..................................................................................... 1-17
1.5.2 MENU NAVIGATION ....................................................................................... 1-17
1.5.3 MENU HIERARCHY ........................................................................................ 1-17
1.5.4 RELAY ACTIVATION....................................................................................... 1-18
1.5.5 RELAY PASSWORDS..................................................................................... 1-18
1.5.6 FLEXLOGIC CUSTOMIZATION ...................................................................... 1-18
1.5.7 COMMISSIONING ...........................................................................................1-19
2. PRODUCT DESCRIPTION 2.1 INTRODUCTION
2.1.1 OVERVIEW........................................................................................................ 2-1
2.1.2 SECURITY ......................................................................................................... 2-2
2.1.3 IEC 870-5-103 PROTOCOL............................................................................... 2-7
2.2 ORDER CODES
2.2.1 OVERVIEW........................................................................................................ 2-8
2.2.2 ORDER CODES WITH ENHANCED CT/VT MODULES................................... 2-8
2.2.3 ORDER CODES WITH PROCESS BUS MODULES ...................................... 2-11
2.2.4 REPLACEMENT MODULES ...........................................................................2-14
2.3 SIGNAL PROCESSING
2.3.1 UR SIGNAL PROCESSING............................................................................. 2-17
2.4 SPECIFICATIONS
2.4.1 PROTECTION ELEMENTS ............................................................................. 2-19
2.4.2 USER-PROGRAMMABLE ELEMENTS...........................................................2-22
2.4.3 MONITORING.................................................................................................. 2-23
2.4.4 METERING ...................................................................................................... 2-24
2.4.5 INPUTS............................................................................................................2-25
2.4.6 POWER SUPPLY ............................................................................................ 2-26
2.4.7 OUTPUTS........................................................................................................2-26
2.4.8 COMMUNICATION PROTOCOLS .................................................................. 2-28
2.4.9 INTER-RELAY COMMUNICATIONS............................................................... 2-28
2.4.10 ENVIRONMENTAL .......................................................................................... 2-30
2.4.11 TYPE TESTS ...................................................................................................2-31
2.4.12 PRODUCTION TESTS ....................................................................................2-31
2.4.13 APPROVALS ................................................................................................... 2-32
2.4.14 MAINTENANCE ............................................................................................... 2-32
3. HARDWARE 3.1 DESCRIPTION
3.1.1 PANEL CUTOUT ............................................................................................... 3-1
3.1.2 REAR TERMINAL LAYOUT............................................................................... 3-7
GE Multilin F60 Feeder Protection System iii
Page 4
TABLE OF CONTENTS
3.2 WIRING
3.2.1 TYPICAL WIRING ..............................................................................................3-9
3.2.2 DIELECTRIC STRENGTH................................................................................3-11
3.2.3 CONTROL POWER..........................................................................................3-11
3.2.4 CT AND VT MODULES ....................................................................................3-12
3.2.5 PROCESS BUS MODULES .............................................................................3-14
3.2.6 CONTACT INPUTS AND OUTPUTS................................................................3-15
3.2.7 TRANSDUCER INPUTS/OUTPUTS.................................................................3-26
3.2.8 RS232 FACEPLATE PORT..............................................................................3-28
3.2.9 CPU COMMUNICATION PORTS.....................................................................3-29
3.2.10 IRIG-B...............................................................................................................3-31
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
3.3.1 DESCRIPTION .................................................................................................3-32
3.3.2 FIBER: LED AND ELED TRANSMITTERS ......................................................3-34
3.3.3 FIBER-LASER TRANSMITTERS .....................................................................3-34
3.3.4 G.703 INTERFACE...........................................................................................3-36
3.3.5 RS422 INTERFACE .........................................................................................3-39
3.3.6 RS422 AND FIBER INTERFACE .....................................................................3-41
3.3.7 G.703 AND FIBER INTERFACE ......................................................................3-41
3.3.8 IEEE C37.94 INTERFACE................................................................................3-42
3.3.9 C37.94SM INTERFACE ...................................................................................3-45
4. HUMAN INTERFACES 4.1 ENERVISTA UR SETUP SOFTWARE INTERFACE
4.1.1 INTRODUCTION ................................................................................................4-1
4.1.2 CREATING A SITE LIST ....................................................................................4-1
4.1.3 ENERVISTA UR SETUP OVERVIEW................................................................4-1
4.1.4 ENERVISTA UR SETUP MAIN WINDOW..........................................................4-3
4.1.5 SETTINGS TEMPLATES ...................................................................................4-4
4.1.6 SECURING AND LOCKING FLEXLOGIC EQUATIONS....................................4-8
4.1.7 SETTINGS FILE TRACEABILITY.....................................................................4-10
4.2 FACEPLATE INTERFACE
4.2.1 FACEPLATE.....................................................................................................4-13
4.2.2 LED INDICATORS............................................................................................4-14
4.2.3 CUSTOM LABELING OF LEDS .......................................................................4-17
4.2.4 DISPLAY...........................................................................................................4-22
4.2.5 BREAKER CONTROL ......................................................................................4-22
4.2.6 KEYPAD ...........................................................................................................4-23
4.2.7 MENUS.............................................................................................................4-23
4.2.8 CHANGING SETTINGS ...................................................................................4-25
5. SETTINGS 5.1 OVERVIEW
5.1.1 SETTINGS MENU ..............................................................................................5-1
5.1.2 INTRODUCTION TO ELEMENTS......................................................................5-4
5.1.3 INTRODUCTION TO AC SOURCES..................................................................5-5
5.2 PRODUCT SETUP
5.2.1 SECURITY..........................................................................................................5-8
5.2.2 DISPLAY PROPERTIES ..................................................................................5-24
5.2.3 CLEAR RELAY RECORDS..............................................................................5-25
5.2.4 COMMUNICATIONS ........................................................................................5-27
5.2.5 MODBUS USER MAP ......................................................................................5-65
5.2.6 REAL TIME CLOCK .........................................................................................5-65
5.2.7 FAULT REPORTS............................................................................................5-70
5.2.8 OSCILLOGRAPHY...........................................................................................5-72
5.2.9 DATA LOGGER................................................................................................5-74
5.2.10 DEMAND ..........................................................................................................5-76
5.2.11 USER-PROGRAMMABLE LEDS .....................................................................5-77
5.2.12 USER-PROGRAMMABLE SELF-TESTS.........................................................5-80
5.2.13 CONTROL PUSHBUTTONS ............................................................................5-81
5.2.14 USER-PROGRAMMABLE PUSHBUTTONS....................................................5-83
5.2.15 FLEX STATE PARAMETERS ..........................................................................5-87
iv F60 Feeder Protection System GE Multilin
Page 5
TABLE OF CONTENTS
5.2.16 USER-DEFINABLE DISPLAYS ....................................................................... 5-88
5.2.17 DIRECT INPUTS/OUTPUTS ........................................................................... 5-90
5.2.18 TELEPROTECTION......................................................................................... 5-98
5.2.19 INSTALLATION................................................................................................5-99
5.3 REMOTE RESOURCES
5.3.1 REMOTE RESOURCES CONFIGURATION.................................................5-100
5.4 SYSTEM SETUP
5.4.1 AC INPUTS....................................................................................................5-101
5.4.2 POWER SYSTEM.......................................................................................... 5-102
5.4.3 SIGNAL SOURCES ....................................................................................... 5-103
5.4.4 BREAKERS....................................................................................................5-107
5.4.5 DISCONNECT SWITCHES ...........................................................................5-111
5.4.6 FLEXCURVES ............................................................................................... 5-114
5.4.7 PHASOR MEASUREMENT UNIT.................................................................. 5-121
5.5 FLEXLOGIC
5.5.1 INTRODUCTION TO FLEXLOGIC ................................................................ 5-145
5.5.2 FLEXLOGIC RULES...................................................................................... 5-155
5.5.3 FLEXLOGIC EVALUATION ........................................................................... 5-156
5.5.4 FLEXLOGIC EXAMPLE ................................................................................. 5-156
5.5.5 FLEXLOGIC EQUATION EDITOR................................................................. 5-161
5.5.6 FLEXLOGIC TIMERS .................................................................................... 5-161
5.5.7 FLEXELEMENTS........................................................................................... 5-162
5.5.8 NON-VOLATILE LATCHES ........................................................................... 5-167
5.6 GROUPED ELEMENTS
5.6.1 OVERVIEW.................................................................................................... 5-168
5.6.2 SETTING GROUP .........................................................................................5-168
5.6.3 LOAD ENCROACHMENT.............................................................................. 5-169
5.6.4 PHASE CURRENT ........................................................................................5-171
5.6.5 NEUTRAL CURRENT.................................................................................... 5-181
5.6.6 WATTMETRIC GROUND FAULT.................................................................. 5-190
5.6.7 GROUND CURRENT..................................................................................... 5-194
5.6.8 NEGATIVE-SEQUENCE CURRENT ............................................................. 5-201
5.6.9 BREAKER FAILURE (ANSI 50BF/50NBF) ....................................................5-208
5.6.10 VOLTAGE ELEMENTS.................................................................................. 5-217
5.6.11 SENSITIVE DIRECTIONAL POWER (ANSI 32)............................................ 5-225
5.7 CONTROL ELEMENTS
5.7.1 OVERVIEW.................................................................................................... 5-228
5.7.2 TRIP BUS.......................................................................................................5-228
5.7.3 SETTING GROUPS ....................................................................................... 5-230
5.7.4 SELECTOR SWITCH..................................................................................... 5-232
5.7.5 UNDERFREQUENCY (ANSI 81U) ................................................................ 5-238
5.7.6 OVERFREQUENCY (ANSI 81O)................................................................... 5-239
5.7.7 FREQUENCY RATE OF CHANGE (ANSI 81R) ............................................ 5-240
5.7.8 SYNCHROCHECK (ANSI 25)........................................................................ 5-242
5.7.9 AUTORECLOSE (ANSI 79) ...........................................................................5-246
5.7.10 DIGITAL ELEMENTS..................................................................................... 5-252
5.7.11 DIGITAL COUNTERS .................................................................................... 5-255
5.7.12 MONITORING ELEMENTS ...........................................................................5-257
5.7.13 COLD LOAD PICKUP.................................................................................... 5-284
5.8 INPUTS/OUTPUTS
5.8.1 CONTACT INPUTS........................................................................................ 5-286
5.8.2 VIRTUAL INPUTS.......................................................................................... 5-288
5.8.3 CONTACT OUTPUTS.................................................................................... 5-289
5.8.4 VIRTUAL OUTPUTS...................................................................................... 5-292
5.8.5 REMOTE DEVICES....................................................................................... 5-292
5.8.6 REMOTE INPUTS.......................................................................................... 5-294
5.8.7 REMOTE DOUBLE-POINT STATUS INPUTS .............................................. 5-295
5.8.8 REMOTE OUTPUTS...................................................................................... 5-295
5.8.9 RESETTING...................................................................................................5-296
5.8.10 DIRECT INPUTS AND OUTPUTS................................................................. 5-297
5.8.11 TELEPROTECTION INPUTS AND OUTPUTS..............................................5-300
5.8.12 IEC 61850 GOOSE ANALOGS...................................................................... 5-302
5.8.13 IEC 61850 GOOSE INTEGERS..................................................................... 5-303
GE Multilin F60 Feeder Protection System v
Page 6
TABLE OF CONTENTS
5.9 TRANSDUCER INPUTS AND OUTPUTS
5.9.1 DCMA INPUTS ...............................................................................................5-305
5.9.2 RTD INPUTS ..................................................................................................5-306
5.9.3 DCMA OUTPUTS ...........................................................................................5-308
5.10 TESTING
5.10.1 TEST MODE...................................................................................................5-311
5.10.2 FORCE CONTACT INPUTS...........................................................................5-312
5.10.3 FORCE CONTACT OUTPUTS.......................................................................5-313
5.10.4 PHASOR MEASUREMENT UNIT TEST VALUES.........................................5-314
6. ACTUAL VALUES 6.1 OVERVIEW
6.1.1 ACTUAL VALUES MENU...................................................................................6-1
6.2 STATUS
6.2.1 CONTACT INPUTS ............................................................................................6-4
6.2.2 VIRTUAL INPUTS ..............................................................................................6-4
6.2.3 REMOTE INPUTS ..............................................................................................6-4
6.2.4 REMOTE DOUBLE-POINT STATUS INPUTS...................................................6-5
6.2.5 TELEPROTECTION INPUTS.............................................................................6-5
6.2.6 CONTACT OUTPUTS ........................................................................................6-5
6.2.7 VIRTUAL OUTPUTS ..........................................................................................6-6
6.2.8 AUTORECLOSE.................................................................................................6-6
6.2.9 REMOTE DEVICES............................................................................................6-6
6.2.10 DIGITAL COUNTERS.........................................................................................6-7
6.2.11 SELECTOR SWITCHES ....................................................................................6-7
6.2.12 FLEX STATES....................................................................................................6-8
6.2.13 ETHERNET ........................................................................................................6-8
6.2.14 REAL TIME CLOCK SYNCHRONIZING ............................................................6-8
6.2.15 HI-Z STATUS......................................................................................................6-9
6.2.16 DIRECT INPUTS ................................................................................................6-9
6.2.17 DIRECT DEVICES STATUS ............................................................................6-10
6.2.18 IEC 61850 GOOSE INTEGERS .......................................................................6-10
6.2.19 EGD PROTOCOL STATUS..............................................................................6-10
6.2.20 TELEPROTECTION CHANNEL TESTS...........................................................6-11
6.2.21 INCIPIENT FAULT DETECTOR.......................................................................6-12
6.2.22 REMAINING CONNECTION STATUS.............................................................6-12
6.2.23 PARALLEL REDUNDANCY PROTOCOL (PRP) .............................................6-12
6.3 METERING
6.3.1 METERING CONVENTIONS ...........................................................................6-14
6.3.2 SOURCES ........................................................................................................6-17
6.3.3 SENSITIVE DIRECTIONAL POWER ...............................................................6-23
6.3.4 SYNCHROCHECK ...........................................................................................6-23
6.3.5 TRACKING FREQUENCY................................................................................6-24
6.3.6 FREQUENCY RATE OF CHANGE ..................................................................6-24
6.3.7 FLEXELEMENTS .............................................................................................6-24
6.3.8 IEC 61580 GOOSE ANALOG VALUES ...........................................................6-25
6.3.9 WATTMETRIC GROUND FAULT.....................................................................6-25
6.3.10 PHASOR MEASUREMENT UNIT ....................................................................6-25
6.3.11 PMU AGGREGATOR .......................................................................................6-26
6.3.12 RESTRICTED GROUND FAULT......................................................................6-26
6.3.13 TRANSDUCER INPUTS AND OUTPUTS........................................................6-27
6.4 RECORDS
6.4.1 FAULT REPORTS............................................................................................6-28
6.4.2 EVENT RECORDS...........................................................................................6-28
6.4.3 OSCILLOGRAPHY...........................................................................................6-29
6.4.4 DATA LOGGER................................................................................................6-29
6.4.5 PHASOR MEASUREMENT UNIT RECORDS .................................................6-30
6.4.6 BREAKER MAINTENANCE .............................................................................6-30
6.4.7 HI-Z RECORDS................................................................................................6-31
6.5 PRODUCT INFORMATION
6.5.1 MODEL INFORMATION...................................................................................6-32
6.5.2 FIRMWARE REVISIONS..................................................................................6-32
vi F60 Feeder Protection System GE Multilin
Page 7
TABLE OF CONTENTS
7. COMMANDS AND TARGETS
7.1 COMMANDS
7.1.1 COMMANDS MENU .......................................................................................... 7-1
7.1.2 VIRTUAL INPUTS.............................................................................................. 7-1
7.1.3 CLEAR RECORDS ............................................................................................ 7-2
7.1.4 SET DATE AND TIME ....................................................................................... 7-2
7.1.5 RELAY MAINTENANCE .................................................................................... 7-3
7.1.6 PHASOR MEASUREMENT UNIT ONE-SHOT.................................................. 7-4
7.1.7 SECURITY ......................................................................................................... 7-5
7.1.8 TARGETS MENU............................................................................................... 7-6
7.1.9 TARGET MESSAGES ....................................................................................... 7-6
7.1.10 RELAY SELF-TESTS.........................................................................................7-6
8. THEORY OF OPERATION 8.1 HIGH-IMPEDANCE (HI-Z) FAULT DETECTION
8.1.1 DESCRIPTION...................................................................................................8-1
8.1.2 ENERGY ALGORITHM...................................................................................... 8-1
8.1.3 RANDOMNESS ALGORITHM........................................................................... 8-2
8.1.4 EXPERT ARC DETECTOR ALGORITHM.........................................................8-2
8.1.5 SPECTRAL ANALYSIS ALGORITHM ...............................................................8-2
8.1.6 LOAD EVENT DETECTOR ALGORITHM ......................................................... 8-2
8.1.7 LOAD ANALYSIS ALGORITHM ........................................................................ 8-3
8.1.8 LOAD EXTRACTION ALGORITHM...................................................................8-3
8.1.9 ARC BURST PATTERN ANALYSIS ALGORITHM............................................8-3
8.1.10 ARCING SUSPECTED ALGORITHM................................................................8-3
8.1.11 OVERCURRENT DISTURBANCE MONITORING ............................................ 8-3
8.1.12 HI-Z EVEN HARMONIC RESTRAINT ALGORITHM ......................................... 8-3
8.1.13 HI-Z VOLTAGE SUPERVISION ALGORITHM .................................................. 8-4
8.2 FAULT LOCATOR
8.2.1 FAULT TYPE DETERMINATION....................................................................... 8-5
9. COMMISSIONING 9.1 TESTING
9.1.1 TESTING UNDERFREQUENCY AND OVERFREQUENCY ELEMENTS......... 9-1
10. MAINTENANCE 10.1 MODULES
10.1.1 REPLACE A MODULE..................................................................................... 10-1
10.2 BATTERIES
10.2.1 REPLACE BATTERY....................................................................................... 10-3
10.2.2 DISPOSE OF BATTERY.................................................................................. 10-5
10.3 UNINSTALL AND CLEAR FILES AND DATA
10.3.1 UNINSTALL AND CLEAR FILES AND DATA.................................................. 10-8
10.4 REPAIRS
10.4.1 REPAIRS ......................................................................................................... 10-9
10.5 STORAGE
10.5.1 STORAGE......................................................................................................10-10
10.6 DISPOSAL
10.6.1 DISPOSAL ..................................................................................................... 10-11
A. FLEXANALOG AND
FLEXINTEGER PARAMETERS
A.1 PARAMETER LISTS
A.1.1 FLEXANALOG ITEMS .......................................................................................A-1
A.1.2 FLEXINTEGER ITEMS ....................................................................................A-22
GE Multilin F60 Feeder Protection System vii
Page 8
TABLE OF CONTENTS
B. MODBUS
COMMUNICATIONS
C. IEC 61850
COMMUNICATIONS
B.1 MODBUS RTU PROTOCOL
B.1.1 INTRODUCTION ............................................................................................... B-1
B.1.2 PHYSICAL LAYER ............................................................................................ B-1
B.1.3 DATA LINK LAYER ........................................................................................... B-1
B.1.4 MODBUS RTU CRC-16 ALGORITHM ..............................................................B-2
B.2 MODBUS FUNCTION CODES
B.2.1 SUPPORTED FUNCTION CODES ...................................................................B-4
B.2.2 READ ACTUAL VALUES OR SETTINGS (FUNCTION CODE 03/04H) ...........B-4
B.2.3 EXECUTE OPERATION (FUNCTION CODE 05H)........................................... B-5
B.2.4 STORE SINGLE SETTING (FUNCTION CODE 06H).......................................B-5
B.2.5 STORE MULTIPLE SETTINGS (FUNCTION CODE 10H)................................ B-6
B.2.6 EXCEPTION RESPONSES...............................................................................B-6
B.3 FILE TRANSFERS
B.3.1 OBTAINING RELAY FILES VIA MODBUS........................................................ B-7
B.4 MEMORY MAPPING
B.4.1 MODBUS MEMORY MAP ................................................................................. B-9
B.4.2 DATA FORMATS............................................................................................. B-79
C.1 OVERVIEW
C.1.1 INTRODUCTION ...............................................................................................C-1
C.1.2 COMMUNICATION PROFILES.........................................................................C-1
C.1.3 FILE TRANSFER BY IEC 61850.......................................................................C-2
C.2 SERVER DATA ORGANIZATION
C.2.1 OVERVIEW .......................................................................................................C-3
C.2.2 GGIO1: DIGITAL STATUS VALUES.................................................................C-3
C.2.3 GGIO2: DIGITAL CONTROL VALUES..............................................................C-3
C.2.4 GGIO3: DIGITAL STATUS AND ANALOG VALUES FROM GOOSE DATA ....C-3
C.2.5 GGIO4: GENERIC ANALOG MEASURED VALUES.........................................C-3
C.2.6 MMXU: ANALOG MEASURED VALUES ..........................................................C-4
C.2.7 PROTECTION AND OTHER LOGICAL NODES............................................... C-4
C.3 SERVER FEATURES AND CONFIGURATION
C.3.1 BUFFERED/UNBUFFERED REPORTING........................................................C-6
C.3.2 FILE TRANSFER...............................................................................................C-6
C.3.3 TIMESTAMPS AND SCANNING....................................................................... C-6
C.3.4 LOGICAL DEVICE NAME .................................................................................C-6
C.3.5 LOCATION ........................................................................................................C-6
C.3.6 LOGICAL NODE NAME PREFIXES..................................................................C-7
C.3.7 CONNECTION TIMING.....................................................................................C-7
C.3.8 NON-IEC 61850 DATA...................................................................................... C-7
C.3.9 COMMUNICATION SOFTWARE UTILITIES.....................................................C-7
C.4 GENERIC SUBSTATION EVENT SERVICES: GSSE AND GOOSE
C.4.1 OVERVIEW .......................................................................................................C-8
C.4.2 GSSE CONFIGURATION..................................................................................C-8
C.4.3 FIXED GOOSE..................................................................................................C-8
C.4.4 CONFIGURABLE GOOSE ................................................................................ C-8
C.4.5 ETHERNET MAC ADDRESS FOR GSSE/GOOSE ........................................C-11
C.4.6 GSSE ID AND GOOSE ID SETTINGS............................................................C-11
C.5 IEC 61850 IMPLEMENTATION VIA ENERVISTA UR SETUP
C.5.1 OVERVIEW .....................................................................................................C-12
C.5.2 CONFIGURING IEC 61850 SETTINGS ..........................................................C-13
C.5.3 ABOUT ICD FILES ..........................................................................................C-14
C.5.4 CREATING AN ICD FILE WITH ENERVISTA UR SETUP.............................. C-18
C.5.5 ABOUT SCD FILES.........................................................................................C-18
C.5.6 IMPORTING AN SCD FILE WITH ENERVISTA UR SETUP...........................C-21
C.6 ACSI CONFORMANCE
C.6.1 ACSI BASIC CONFORMANCE STATEMENT ................................................ C-23
C.6.2 ACSI MODELS CONFORMANCE STATEMENT............................................C-23
C.6.3 ACSI SERVICES CONFORMANCE STATEMENT .........................................C-24
viii F60 Feeder Protection System GE Multilin
Page 9
TABLE OF CONTENTS
C.7 LOGICAL NODES
C.7.1 LOGICAL NODES TABLE ...............................................................................C-27
D. IEC 60870-5-103
COMMUNICATIONS
E. IEC 60870-5-104
COMMUNICATIONS
D.1 IEC 60870-5-103
D.1.1 OVERVIEW........................................................................................................D-1
D.1.2 FACTOR AND OFFSET CALCULATION TO TRANSMIT MEASURAND.........D-1
D.1.3 INTEROPERABILITY DOCUMENT ...................................................................D-2
E.1 IEC 60870-5-104
E.1.1 INTEROPERABILITY DOCUMENT...................................................................E-1
E.1.2 IEC 60870-5-104 POINT LIST ...........................................................................E-9
F. DNP COMMUNICATIONS F.1 DEVICE PROFILE DOCUMENT
F.1.1 DNP V3.00 DEVICE PROFILE ..........................................................................F-1
F.1.2 IMPLEMENTATION TABLE ............................................................................... F-4
F.2 DNP POINT LISTS
F.2.1 BINARY INPUT POINTS.................................................................................... F-8
F.2.2 BINARY AND CONTROL RELAY OUTPUT ......................................................F-9
F.2.3 COUNTERS .....................................................................................................F-10
F.2.4 ANALOG INPUTS ............................................................................................F-11
G. RADIUS SERVER G.1 RADIUS SERVER CONFIGURATION
G.1.1 RADIUS SERVER CONFIGURATION.............................................................. G-1
H. MISCELLANEOUS H.1 CHANGE NOTES
H.1.1 REVISION HISTORY .........................................................................................H-1
H.1.2 CHANGES TO THE F60 MANUAL ....................................................................H-2
H.2 ABBREVIATIONS
H.2.1 STANDARD ABBREVIATIONS .........................................................................H-6
H.3 WARRANTY
H.3.1 GE MULTILIN WARRANTY ...............................................................................H-9
INDEX
GE Multilin F60 Feeder Protection System ix
Page 10
TABLE OF CONTENTS
x F60 Feeder Protection System GE Multilin
Page 11
1 GETTING STARTED 1.1 IMPORTANT PROCEDURES
DANGER
WARNING
CAUTION
NOTICE
DANGER
CAUTION
1 GETTING STARTED 1.1IMPORTANT PROCEDURES
Use this chapter for initial setup of your new F60 Feeder Protection System.

1.1.1 CAUTIONS AND WARNINGS

Before attempting to install or use the device, review all safety indicators in this document to help prevent injury, equipment damage, or downtime.
The following safety and equipment symbols are used in this document.
Indicates a hazardous situation which, if not avoided, will result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in death or serious injury.
Indicates a hazardous situation which, if not avoided, could result in minor or moderate injury.
Indicates practices not related to personal injury.
a) GENERAL CAUTIONS AND WARNINGS
The following general safety precautions and warnings apply.
Ensure that all connections to the product are correct so as to avoid accidental risk of shock and/or fire, for example such as can arise from high voltage connected to low voltage termi­nals.
Follow the requirements of this manual, including adequate wiring size and type, terminal torque settings, voltage, current magnitudes applied, and adequate isolation/clearance in external wiring from high to low voltage circuits.
Use the device only for its intended purpose and application.
Ensure that all ground paths are uncompromised for safety purposes during device operation and service.
Ensure that the control power applied to the device, the AC current, and voltage input match the ratings specified on the relay nameplate. Do not apply current or voltage in excess of the specified limits.
Only qualified personnel are to operate the device. Such personnel must be thoroughly familiar with all safety cau­tions and warnings in this manual and with applicable country, regional, utility, and plant safety regulations.
Hazardous voltages can exist in the power supply and at the device connection to current transformers, voltage transformers, control, and test circuit terminals. Make sure all sources of such voltages are isolated prior to attempting work on the device.
Hazardous voltages can exist when opening the secondary circuits of live current transformers. Make sure that current transformer secondary circuits are shorted out before making or removing any connection to the current transformer (CT) input terminals of the device.
For tests with secondary test equipment, ensure that no other sources of voltages or currents are connected to such equipment and that trip and close commands to the circuit breakers or other switching apparatus are iso­lated, unless this is required by the test procedure and is specified by appropriate utility/plant procedure.
When the device is used to control primary equipment, such as circuit breakers, isolators, and other switching apparatus, all control circuits from the device to the primary equipment must be isolated while personnel are working on or around this primary equipment to prevent any inadvertent command from this device.
Use an external disconnect to isolate the mains voltage supply.
Personal safety can be affected if the product is physically modified by the end user. Modifications to the product outside of recommended wiring configuration, hardware, or programming boundaries is not recommended end­use practice. Product disassembly and repairs are not permitted. All service needs to be conducted by the factory.
LED transmitters are classified as IEC 60825-1 Accessible Emission Limit (AEL) Class 1M. Class 1M devices are considered safe to the unaided eye. Do not view directly with optical instruments.
1
GE Multilin F60 Feeder Protection System 1-1
Page 12
1.1 IMPORTANT PROCEDURES 1 GETTING STARTED
832773A3.CDR
Model: Mods: Wiring Diagram: Inst. Manual: Serial Number: Firmware: Mfg. Date: PO Num: Item Num:
F60H00HCHF8FH6AM6BP8BX7A 000 See manual 1601-0093 MAZB98000029 D NOV 26, 2012
600001234.56
Control Power: Contact Inputs: Contact Outputs:
88-300V DC @ 35W / 77-265V AC @ 35VA 300V DC Max 10mA Refer to Instruction Manual
RATINGS:
F60
GE Multilin
- M A A B 9 7 0 0 0 0 9 9 -
®
Feeder Management Relay
- M A A B 9 7 0 0 0 0 9 9 -
LISTED
52TL
IND.CONT. EQ.
E83849
This product is rated to Class A emissions levels and is to be used in Utility, Substation Industrial environments. Not to be used near electronic devices rated for Class B levels.
1

1.1.2 INSPECTION PROCEDURE

1. Open the relay packaging and inspect the unit for physical damage.
2. View the rear nameplate and verify that the correct model has been ordered and delivered. The model number is at the top right.
Figure 1–1: REAR NAMEPLATE (EXAMPLE)
3. Ensure that the following items are included:
• Instruction manual (if ordered)
• GE EnerVista™ DVD (includes the EnerVista UR Setup software and manuals in PDF format)
• Mounting screws
4. If there is any noticeable physical damage, or any of the contents listed are missing, contact GE Grid Solutions as fol­lows.
GE GRID SOLUTIONS CONTACT INFORMATION AND CALL CENTER FOR PRODUCT SUPPORT:
GE Grid Solutions 650 Markland Street Markham, Ontario Canada L6C 0M1
TELEPHONE: Worldwide +1 905 927 7070
Europe/Middle East/Africa +34 94 485 88 54 North America toll-free 1 800 547 8629
FAX: +1 905 927 5098 E-MAIL: Worldwide multilin.tech@ge.com
Europe multilin.tech.euro@ge.com
HOME PAGE: http://www.gegridsolutions.com/multilin
For updates to the instruction manual, firmware, and software, visit the GE Grid Solutions website.
1-2 F60 Feeder Protection System GE Multilin
Page 13
1 GETTING STARTED 1.2 UR OVERVIEW
827822A3.CDR
Input elements
LAN
Programming
device
Operator interface
Contact inputs Contact outputs
Virtual inputs
Virtual outputs
Analog inputs
Analog outputs
CT inputs
VT inputs
Input
status
table
Output
status
table
Pickup Dropout Operate
Protective elements
Logic Gates
Remote outputs
- IEC 61850
CPU module
Output elements
Remote inputs
Direct inputs Direct outputs

1.2UR OVERVIEW 1.2.1 INTRODUCTION TO THE UR

The GE Universal Relay (UR) series is a new generation of digital, modular, and multifunction equipment that is easily incorporated into automation systems, at both the station and enterprise levels.

1.2.2 HARDWARE ARCHITECTURE

a) UR BASIC DESIGN
The UR is a digital-based device containing a central processing unit (CPU) that handles multiple types of input and output signals. The UR device can communicate over a local area network (LAN) with an operator interface, a programming device, or another UR device.
1
Figure 1–2: UR BLOCK DIAGRAM
The CPU module contains firmware that provides protection elements in the form of logic algorithms, as well as program­mable logic gates, timers, and latches for control features.
Input elements accept a variety of analog or digital signals from the field. The UR isolates and converts these signals into logic signals used by the relay.
Output elements convert and isolate the logic signals generated by the relay into digital or analog signals that are used to control field devices.
The unit and software are backwards-compatible with UR devices.
b) UR SIGNAL TYPES
The contact inputs and outputs are digital signals associated with connections to hard-wired contacts. Both ‘wet’ and ‘dry’ contacts are supported.
The virtual inputs and outputs are digital signals associated with UR-series internal logic signals. Virtual inputs include signals generated by the local user interface. The virtual outputs are outputs of FlexLogic™ equations used to customize the device. Virtual outputs can also serve as virtual inputs to FlexLogic equations.
The analog inputs and outputs are signals that are associated with transducers, such as Resistance Temperature Detec- tors (RTDs).
The CT and VT inputs are analog current transformer and voltage transformer signals used to monitor AC power lines. The UR-series relays support 1 A and 5 A CTs.
The remote inputs and outputs provide a means of sharing digital point state information between remote UR-series devices. The remote outputs interface to the remote inputs of other UR-series devices. Remote outputs are FlexLogic oper­ands inserted into IEC 61850 GSSE and GOOSE messages.
GE Multilin F60 Feeder Protection System 1-3
Page 14
1.2 UR OVERVIEW 1 GETTING STARTED
The direct inputs and outputs provide a means of sharing digital point states between a number of UR-series intelligent electronic devices (IEDs) over dedicated fiber, RS422, or G.703 interface. No switching equipment is required as the IEDs
1
are connected directly in a ring or redundant (dual) ring configuration. This feature is optimized for speed and intended for pilot-aided schemes, distributed logic applications, or the extension of the input/output capabilities of a single relay chassis.

1.2.3 SOFTWARE ARCHITECTURE

Firmware is the software embedded in the relay in functional modules that can be installed in any relay as required. This is achieved with object-oriented design and programming (OOD/OOP) techniques.
Object-oriented techniques involve the use of objects and classes. An object is defined as “a logical entity that contains both data and code that manipulates data.” A class is the generalized form of similar objects. By using this approach, one can create a protection class with the protection elements as objects of the class, such as time overcurrent, instantaneous overcurrent, current differential, undervoltage, overvoltage, underfrequency, and distance. These objects represent com­pletely self-contained software modules. The same object-class concept can be used for metering, input/output control, software interface, communications, or any functional entity in the system.
Employing OOD/OOP in the software architecture of the F60 achieves the same features as the hardware architecture: modularity, scalability, and flexibility. The application software for any UR-series device (for example, feeder protection, transformer protection, distance protection) is constructed by combining objects from the various functional classes. This results in a common interface across the UR series.
1-4 F60 Feeder Protection System GE Multilin
Page 15
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE

1.3ENERVISTA UR SETUP SOFTWARE 1.3.1 SYSTEM REQUIREMENTS

The relay front panel or the EnerVista UR Setup software can be used to communicate with the relay. The software inter­face is the preferred method to edit settings and view actual values because the computer monitor can display more infor­mation.
The minimum system requirements for the EnerVista UR Setup software are as follows:
Pentium 4 (Core Duo recommended)
Windows XP with Service Pack 2 (Service Pack 3 recommended), Windows 7, or Windows Server 2008 Release 2
64-bit
1 GB of RAM (2 GB recommended)
500 MB free hard drive space (1 GB recommended)
1024 x 768 display (1280 x 800 recommended)
•Serial port
Ethernet port of the same type as one of the UR CPU ports or a LAN connection to the UR
Internet access or a DVD drive The following qualified modems have been tested to be compatible with the F60 and the EnerVista UR Setup software:
US Robotics external 56K FaxModem 5686
US Robotics external Sportster 56K X2
PCTEL 2304WT V.92 MDC internal modem

1.3.2 INSTALLATION

1
After ensuring that the requirements for using EnerVista UR Setup software are met, install the software from the GE EnerVista DVD. Or download the UR EnerVista software from http://www.gegridsolutions.com/multilin
To install the UR EnerVista software from the DVD:
1. Insert the GE EnerVista DVD into the DVD drive of your computer.
2. Click the Install Now button and follow the instructions.
3. When installation is complete, start the EnerVista Launchpad application.
4. Click the IED Setup section of the Launch Pad window.
Figure 1–3: ADDING A UR DEVICE IN LAUNCHPAD WINDOW
5. In the EnerVista Launch Pad window, click the Add Product button and select the appropriate product as follows.
Select the Web option to ensure the most recent software release, or select CD if you do not have an Internet connec-
and install it.
GE Multilin F60 Feeder Protection System 1-5
Page 16
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
tion, then click the Add Now button to list software items for the product. EnerVista Launchpad obtains the software from the Internet or DVD and automatically starts the installation program.
1
Figure 1–4: IDENTIFYING THE UR DEVICE TYPE
6. Select the complete path, including the new directory name, where the EnerVista UR Setup software is to be installed.
7. Click the Next button to begin the installation. The files are installed in the directory indicated, and the installation pro­gram automatically creates icons and adds an entry to the Windows start menu.
8. Click Finish to complete the installation. The UR device is added to the list of installed intelligent electronic devices (IEDs) in the EnerVista Launchpad window, as shown.
Figure 1–5: UR DEVICE ADDED TO LAUNCHPAD WINDOW

1.3.3 CONFIGURING THE F60 FOR SOFTWARE ACCESS

a) OVERVIEW
You connect remotely to the F60 through the rear RS485 or Ethernet port with a computer running the EnerVista UR Setup software. The F60 can also be accessed locally with a computer through the front panel RS232 port or the rear Ethernet port using the Quick Connect feature.
To configure the F60 for remote access via the rear RS485 port, see the Configuring Serial Communications section.
To configure the F60 for remote access via the rear Ethernet port, see the Configuring Ethernet Communications sec­tion.
To configure the F60 for local access with a computer through either the front RS232 port or rear Ethernet port, see the Using the Quick Connect Feature section.
1-6 F60 Feeder Protection System GE Multilin
Page 17
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
b) CONFIGURING SERIAL COMMUNICATIONS
A computer with an RS232 port and a serial cable is required. To use the RS485 port at the back of the relay, a GE Multilin F485 converter (or compatible RS232-to-RS485 converter) is required. See the F485 instruction manual for details.
1. Connect the computer to the F485 and the F485 to the RS485 terminal on the back of the UR device, or connect the
computer to the RS232 port on the front of the relay.
2. In the EnerVista Launchpad software on the computer, select the UR device to start the software.
3. Click the Device Setup button to open the Device Setup window, and click the Add Site button to define a new site.
4. Enter a site name in the Site Name field. Optionally add a short description of the site along with the display order of
devices defined for the site. This example uses “Location 1” as the site name. When done, click the OK button. The new site appears in the upper-left list in the EnerVista UR Setup window.
5. Click the Device Setup button, then select the new site to re-open the Device Setup window.
6. Click the Add Device button to define the new device.
7. Enter a name in the "Device Name” field and a description (optional) of the site.
8. Select “Serial” from the Interface drop-down list. This displays a number of interface parameters that must be entered
for serial communications.
1
Figure 1–6: CONFIGURING SERIAL COMMUNICATIONS
9. Enter the COM port used by the computer, the baud rate, and parity settings from the front panel
SETUP  COMMUNICATIONS SERIAL PORTS menu, and the relay slave address setting from the front panel SETTINGS
PRODUCT SETUP  COMMUNICATIONS  MODBUS PROTOCOL MODBUS SLAVE ADDRESS menu in their respective
fields.
10. Click the Read Order Code button to connect to the F60 device and upload the order code. If a communications error
occurs, ensure that the EnerVista UR Setup serial communications values entered in the previous step correspond to the relay setting values.
11. Click the OK button when the relay order code has been received. The new device is added to the Site List window (or
Online window) located in the top left corner of the main EnerVista UR Setup window.
The device has now been configured for RS232 communications. Proceed to the Connecting to the F60 section to begin communication.
GE Multilin F60 Feeder Protection System 1-7
SETTINGS PRODUCT
Page 18
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
c) CONFIGURING ETHERNET COMMUNICATIONS
Before starting, verify that the Ethernet network cable is properly connected to the Ethernet port on the back of the relay. To
1
setup the relay for Ethernet communications, you define a Site, then add the relay as a Device at that site.The computer and UR device must be on the same subnet.
12. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
13. Click the Device Setup button to open the Device Setup window, then click the Add Site button to define a new site.
14. Enter the desired site name in the “Site Name” field. If desired, a short description of site can also be entered along with the display order of devices defined for the site. In this example, we use “Location 2” as the site name. Click the OK button when complete.
15. The new site appears in the upper-left list in the EnerVista UR Setup window. Click the Device Setup button then select the new site to re-open the Device Setup window.
16. Click the Add Device button to define the new device.
17. Enter the desired name in the “Device Name” field and a description (optional) of the site.
18. Select “Ethernet” from the Interface drop-down list. This displays a number of interface parameters that must be entered for proper Ethernet functionality.
Figure 1–7: CONFIGURING ETHERNET COMMUNICATIONS
19. Enter the relay IP address specified in the front panel
WORK
IP ADDRESS in the “IP Address” field.
20. Enter the relay slave address and Modbus port address values from the respective settings in the front panel
PRODUCT SETUP  COMMUNICATIONS  MODBUS PROTOCOL menu.
21. Click the Read Order Code button to connect to the F60 device and upload the order code. If an communications error occurs, ensure that the three EnerVista UR Setup values entered in the previous steps correspond to the relay setting values.
22. Click OK when the relay order code has been received. The new device is added to the Site List window (or Online window) located in the top left corner of the main EnerVista UR Setup window.
The Site Device has now been configured for Ethernet communications. Proceed to the Connecting to the F60 section to begin communications.
1-8 F60 Feeder Protection System GE Multilin
SETTINGS PRODUCT SETUP  COMMUNICATIONS  NET-
SETTINGS
Page 19
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
842799A1.CDR
END 1 END 2 Pin Wire color Diagram Pin Wire color Diagram
1 White/orange 1 White/green 2 Orange 2 Green
3 White/green 3 White/orange 4 Blue 4 Blue 5 White/blue 5 White/blue 6 Green 6 Orange 7 White/brown 7 White/brown 8 Brown 8 Brown
1
2
3
4
5
6
7
8

1.3.4 USING THE QUICK CONNECT FEATURE

a) USING QUICK CONNECT VIA THE FRONT PANEL RS232 PORT
Before starting, verify that the serial cable is properly connected from the computer to the front panel RS232 port with a straight-through 9-pin to 9-pin RS232 cable.
1. Verify that the latest version of the EnerVista UR Setup software is installed (available from the GE EnerVista CD or
online from http://www.gegridsolutions.com/multilin
). See the Software Installation section if not already installed.
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
3. Click the Quick Connect button to open the Quick Connect dialog box.
4. Select the Serial interface and the correct COM Port, then click Connect.
5. The EnerVista UR Setup software creates a site named “Quick Connect” with a corresponding device also named
“Quick Connect” and displays them at the upper-left of the screen. Expand the sections to view data directly from the F60 device.
Each time that the EnerVista UR Setup software is initialized, click the Quick Connect button to establish direct communi­cations to the F60 device. This ensures that configuration of the EnerVista UR Setup software matches the F60 model number.
1
b) USING QUICK CONNECT VIA THE REAR ETHERNET PORTS
To use the Quick Connect feature to access the F60 from a computer through Ethernet, first assign an IP address to the relay from the front panel keyboard.
1. Press the MENU key until the SETTINGS menu displays.
2. Navigate to the
SETTINGS PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting.
3. Enter an IP address, for example “1.1.1.1,” and select the ENTER key to save the value.
4. In the same menu, select the
SUBNET IP MASK setting.
5. Enter a subnet IP address, for example “255.0.0.0,” and press the ENTER key to save the value. Next, use an Ethernet cross-over cable to connect the computer to the rear Ethernet port. In case you need it, the figure
shows the pinout for an Ethernet cross-over cable.
Figure 1–8: ETHERNET CROSS-OVER CABLE PIN LAYOUT
Now, assign the computer an IP address compatible with the relay’s IP address.
GE Multilin F60 Feeder Protection System 1-9
Page 20
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
1. From the Windows desktop, right-click the My Network Places icon and select Properties to open the network con­nections window.
1
2. Right-click the Local Area Connection icon and select Properties.
3. Select the Internet Protocol (TCP/IP) item from the list, and click the Properties button.
4. Click the “Use the following IP address” box.
1-10 F60 Feeder Protection System GE Multilin
Page 21
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
5. Enter an IP address with the first three numbers the same as the IP address of the F60 relay and the last number dif-
ferent (in this example, 1.1.1.2).
6. Enter a subnet mask equal to the one set in the F60 (in this example, 255.0.0.0).
7. Click the OK button to save the values. Before continuing, test the Ethernet connection.
1. Open a Windows console window by selecting Start > Run from the Windows Start menu and typing “cmd”.
2. Type the following command, substituting the IP address of 1.1.1.1 with yours:
C:\WINNT>ping 1.1.1.1
3. If the connection is successful, the system returns four replies similar to the following:
Pinging 1.1.1.1 with 32 bytes of data:
Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255 Reply from 1.1.1.1: bytes=32 time<10ms TTL=255
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 4, Lost = 0 (0% loss),
Approximate round trip time in milliseconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
4. Note that the values for time and TTL vary depending on local network configuration.
5. If the following sequence of messages appears when entering the C:\WINNT>ping 1.1.1.1 command:
Pinging 1.1.1.1 with 32 bytes of data:
Request timed out. Request timed out. Request timed out. Request timed out.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milliseconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
verify the physical connection between the F60 and the computer, and double-check the programmed IP address in the PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting, then repeat step 2.
6. If the following sequence of messages appears when entering the C:\WINNT>ping 1.1.1.1 command:
Pinging 1.1.1.1 with 32 bytes of data:
Hardware error. Hardware error. Hardware error. Hardware error.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milliseconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
verify the physical connection between the F60 and the computer, and double-check the programmed IP address in
PRODUCT SETUP  COMMUNICATIONS  NETWORK IP ADDRESS setting, then repeat step 2.
the
7. If the following sequence of messages appears when entering the
C:\WINNT>ping 1.1.1.1 command:
1
GE Multilin F60 Feeder Protection System 1-11
Page 22
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
Pinging 1.1.1.1 with 32 bytes of data:
1
Destination host unreachable. Destination host unreachable. Destination host unreachable. Destination host unreachable.
Ping statistics for 1.1.1.1:
Packets: Sent = 4, Received = 0, Lost = 4 (100% loss),
Approximate round trip time in milliseconds:
Minimum = 0ms, Maximum = 0ms, Average = 0 ms
Pinging 1.1.1.1 with 32 bytes of data:
verify the IP address is programmed in the local computer by entering the ipconfig command in the command window.
C:\WINNT>ipconfig
Windows IP Configuration
Ethernet adapter <F4FE223E-5EB6-4BFB-9E34-1BD7BE7F59FF>:
Connection-specific DNS suffix. . :
IP Address. . . . . . . . . . . . : 0.0.0.0
Subnet Mask . . . . . . . . . . . : 0.0.0.0
Default Gateway . . . . . . . . . :
Ethernet adapter Local Area Connection:
Connection-specific DNS suffix . :
IP Address. . . . . . . . . . . . : 1.1.1.2
Subnet Mask . . . . . . . . . . . : 255.0.0.0
Default Gateway . . . . . . . . . :
C:\WINNT>
Before using the Quick Connect feature through the Ethernet port, disable any configured proxy settings in Internet Explorer.
1. Start the Internet Explorer software.
2. Select the Tools > Internet Options menu item and click the Connections tab.
3. Click on the LAN Settings button to open the following window.
4. Ensure that the “Use a proxy server for your LAN” box is not checked.
If this computer is used to connect to the Internet, re-enable any proxy server settings after the computer has been discon­nected from the F60 relay.
1. Start the Internet Explorer software.
2. Select the “UR” device from the EnerVista Launchpad to start EnerVista UR Setup.
1-12 F60 Feeder Protection System GE Multilin
Page 23
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE
3. Click the Quick Connect button to open the Quick Connect dialog box.
4. Select the Ethernet interface and enter the IP address assigned to the F60, then click the Connect button. The EnerV-
ista UR Setup software creates a site named “Quick Connect” with a corresponding device also named “Quick Con­nect” and displays them at the upper-left of the screen.
5. Expand the sections to view data directly from the F60 device. Each time the EnerVista UR Setup software is initialized, click the Quick Connect button to establish direct communica-
tions to the F60. This ensures that configuration of the EnerVista UR Setup software matches the F60 model number. When direct communications with the F60 via Ethernet is complete, make the following changes:
1. From the Windows desktop, right-click the My Network Places icon and select Properties to open the network con-
nections window.
2. Right-click the Local Area Connection icon and select the Properties item.
3. Select the Internet Protocol (TCP/IP) item from the list provided and click the Properties button.
4. Set the computer to “Obtain a relay address automatically” as shown.
1
If this computer is used to connect to the Internet, re-enable any proxy server settings after the computer has been discon­nected from the F60 relay.
AUTOMATIC DISCOVERY OF ETHERNET DEVICES
The EnerVista UR Setup software can automatically discover and communicate to all UR-series IEDs located on an Ether­net network.
Using the Quick Connect feature, a single click of the mouse triggers the software to automatically detect any UR-series relays located on the network. The EnerVista UR Setup software then proceeds to configure all settings and order code options in the Device Setup menu. This feature allows the user to identify and interrogate all UR-series devices at a loca­tion.
GE Multilin F60 Feeder Protection System 1-13
Page 24
1.3 ENERVISTA UR SETUP SOFTWARE 1 GETTING STARTED
842743A3.CDR
Communications status indicators:
Green = OK Red = No communications UR icon = report is open
Quick action hot links
Expand the site list by double-clicking or selecting the +/– box.
NOTE

1.3.5 CONNECTING TO THE F60 RELAY

1
When unable to connect because of an "ACCESS VIOLATION," access Device Setup and refresh the order code for the device.
1. Open the Display Properties window through the Site List tree as shown. The Display Properties window opens with a status indicator on the lower left of the EnerVista UR Setup window.
2. If the status indicator is red, verify that the Ethernet network cable is properly connected to the Ethernet port on the back of the relay and that the relay has been properly setup for communications (steps A and B earlier).
If a relay icon appears in place of the status indicator, than a report (such as an oscillography or event record) is open. Close the report to re-display the green status indicator.
3. The Display Properties settings can now be edited, printed, or changed.
See chapter 4 in this manual or the EnerVista UR Setup Help File for information about the using the EnerVista UR Setup software interface.
QUICK ACTION HOT LINKS
The EnerVista UR Setup software has several quick action buttons to provide instant access to several functions that are often performed when using F60 relays. From the online window, users can select the relay to interrogate from a pull-down window, then click the button for the action they want to perform. The following quick action functions are available:
View the F60 event record
View the last recorded oscillography record
View the status of all F60 inputs and outputs
View all of the F60 metering values
View the F60 protection summary
Generate a service report
1-14 F60 Feeder Protection System GE Multilin
Page 25
1 GETTING STARTED 1.3 ENERVISTA UR SETUP SOFTWARE

1.3.6 SETTING UP CYBERSENTRY AND CHANGING DEFAULT PASSWORD

If and when first using CyberSentry security, use the following procedure for set up.
1. Log in to the relay as Administrator by using the Value keys on the front panel or through EnerVista connected serially
(so that no IP address is required). If logging in through EnerVista choose Device authentication. Enter the default password "ChangeMe1#". Note that the "Lock relay" setting needs to be disabled in the Security > Supervisory menu. When this setting is disabled, configuration and firmware upgrade are possible. By default, this setting is dis­abled.
2. Enable the Supervisor role if you have a need for it.
3. Make any required changes in configuration, such as setting a valid IP address for communication over Ethernet.
4. Log out of the Administrator account by choosing None. Next, device or server authentication can be chosen on the login screen, but the choice is available only in EnerVista. Use
device authentication to log in using the five pre-configured roles (Administrator, Supervisor, Engineer, Operator, Observer, or Administrator and Supervisor when device authentication is disabled). When using a serial connection, only device authentication is supported. When server authentication is required, characteristics for communication with a RADIUS server must be configured on the UR. This is possible only through the EnerVista software. The RADIUS server itself also must be configured. The appendix called RADIUS Server gives an example of how to setup a simple RADIUS server. Once both the RADIUS server and the parameters for connecting UR to the server have been configured, you can choose server authentication on the login screen of EnerVista.
Figure 1–9: LOGIN SCREEN FOR CYBERSENTRY
1
During the commissioning phase, you have the option to bypass the use of passwords. Do so by enabling the
ACCESS
commissioning the device. You can change the password for any role either from the front panel or through EnerVista. If using EnerVista, navigate to Settings > Product Setup > Security. Change the Local Administrator Password, for
example. It is strongly recommended that the password for the Administrator be changed from the default. Changing the passwords for the other three roles is optional.
GE Multilin F60 Feeder Protection System 1-15
setting under SETTINGS > PRODUCT SETUP > SECURITY > SUPERVISORY. Be sure to disable this bypass setting after
BYPASS
Page 26
1.4 UR HARDWARE 1 GETTING STARTED
EnerVista
Ethernet 10/100 Mbps
Regional
control
center
Modem
Remote
communications link Local control
Engineer
GE Multilin F485 communications converter
UR-series IED
Troubleshooting Commissioning Setting changes
Reports
RS485 115 kbps
RS232
EnerVista
EnerVista
842759A2.CDR

1.4UR HARDWARE 1.4.1 MOUNTING AND WIRING

1
See Chapter 3: Hardware for mounting and wiring instructions.

1.4.2 COMMUNICATIONS

The EnerVista UR Setup software communicates to the relay via the faceplate RS232 port or the rear panel RS485 / Ether­net ports. To communicate via the faceplate RS232 port, a standard straight-through serial cable is used. The DB-9 male end is connected to the relay and the DB-9 or DB-25 female end is connected to the computer COM2 port as described in the CPU Communication Ports section of chapter 3.
Figure 1–10: RELAY COMMUNICATION OPTIONS
To communicate through the F60 rear RS485 port from a computer RS232 port, the GE Multilin RS232/RS485 converter box is required. This device (catalog number F485) connects to the computer using a straight-through serial cable. A shielded twisted-pair (20, 22, or 24 AWG) connects the F485 converter to the F60 rear communications port. The converter terminals (+, –, GND) are connected to the F60 communication module (+, –, COM) terminals. See the CPU Communica- tion Ports section in chapter 3 for details. The line is terminated with an R-C network (that is, 120 Ω, 1 nF) as described in the chapter 3.
All messages are displayed on a backlit liquid crystal display (LCD) to make them visible under poor lighting conditions. While the keypad and display are not actively being used, the display defaults to user-defined messages. Any high-priority event-driven message automatically overrides the default message and appears on the display.
Settings files conversion from previous firmware versions is supported.
1-16 F60 Feeder Protection System GE Multilin

1.4.3 FACEPLATE DISPLAY

Page 27
1 GETTING STARTED 1.5 USING THE RELAY

1.5USING THE RELAY 1.5.1 FACEPLATE KEYPAD

Display messages are organized into pages under the following headings: actual values, settings, commands, and targets. The MENU key navigates through these pages. Each heading page is divided further into logical subgroups.
The MESSAGE keys navigate through the subgroups. The VALUE keys increment or decrement numerical setting values when in programming mode. These keys also scroll through alphanumeric values in the text edit mode. Alternatively, val­ues can be entered with the numeric keypad.
The decimal key initiates and advances to the next character in text edit mode or enters a decimal point. The HELP key can be pressed at any time for context-sensitive help messages. The ENTER key stores altered setting values. When entering an IP address on the front panel, key in the first sequence of the number, then press the • key for the deci-
mal place. For example, for 127.0.0.1, press 127, then •, then 0, then •, then 0, then •, then 1. To save the address, press the ENTER key.

1.5.2 MENU NAVIGATION

Press the MENU key to select a header display page (top-level menu). The header title appears momentarily followed by a header display page menu item. Each press of the MENU key advances through the following main heading pages:
Actual values
Settings
Commands
Targets
User displays (when enabled)
1

1.5.3 MENU HIERARCHY

The setting and actual value messages are arranged hierarchically. The header display pages are indicated by double scroll bar characters (), while sub-header pages are indicated by single scroll bar characters (). The header display pages represent the highest level of the hierarchy and the sub-header display pages fall below this level. The MESSAGE UP and DOWN keys move within a group of headers, sub-headers, setting values, or actual values. Continually pressing the MESSAGE RIGHT key from a header display displays specific information for the header category. Conversely, contin­ually pressing the MESSAGE LEFT key from a setting value or actual value display returns to the header display.
HIGHEST LEVEL LOWEST LEVEL (SETTING
 SETTINGS  PRODUCT SETUP
 SETTINGS  SYSTEM SETUP
SECURITY
VALUE )
ACCESS LEVEL: Restricted
GE Multilin F60 Feeder Protection System 1-17
Page 28
1.5 USING THE RELAY 1 GETTING STARTED
NOTE

1.5.4 RELAY ACTIVATION

1
The relay is in the default “Not Programmed” state when it leaves the factory. When powered up successfully, the Trouble LED is on and the In Service LED off. The relay in the “Not Programmed” state blocks signaling of any output relay. These conditions remain until the relay is explicitly put in the “Programmed” state.
Select the menu message
RELAY SETTINGS: Not Programmed
1. To put the relay in the “Programmed” state, press either of the VALUE keys once and then press ENTER. The face­plate Trouble LED turns off and the In Service LED turns on.
The settings for the relay can be programmed manually (see Chapter 5) via the faceplate keypad or remotely via the EnerVista UR Setup software (see the EnerVista UR Setup help file).
a) PASSWORD SECURITY
It is recommended that passwords be set for each security level and assigned to specific personnel. There are two user security access levels, COMMAND and SETTING.
1. COMMAND
The COMMAND access level restricts the user from making any settings changes, but allows the user to perform the fol­lowing operations:
Operate breakers via faceplate keypad
Change state of virtual inputs
Clear event records
Clear oscillography records
Operate user-programmable pushbuttons
2. SETTING
The SETTING access level allows the user to make any changes to any of the setting values.
See the Changing Settings section in Chapter 4 for complete instructions on setting security-level passwords.
SETTINGS PRODUCT SETUP  INSTALLATION RELAY SETTINGS

1.5.5 RELAY PASSWORDS

b) CYBERSENTRY
When the CyberSentry option is purchased, advanced security services are available, using either device authentication or server authentication using RADIUS. When this option is purchased, the basic password security is disabled automatically. For more information, see the CyberSentry content in the Security section of the next chapter.

1.5.6 FLEXLOGIC CUSTOMIZATION

FlexLogic equation editing is required for setting user-defined logic for customizing the relay operations. See the FlexLogic section in Chapter 5.
1-18 F60 Feeder Protection System GE Multilin
Page 29
1 GETTING STARTED 1.5 USING THE RELAY

1.5.7 COMMISSIONING

The F60 requires minimal maintenance after it is commissioned into service. Since the F60 is a microprocessor-based relay, its characteristics do not change over time. As such, no further functional tests are required. Expected service life is 20 years for UR devices manufactured June 2014 or later when applied in a controlled indoors environment and electrical conditions within specification.
The F60 performs a number of continual self-tests and takes the necessary action in case of any major errors (see the Relay Self-tests section in chapter 7). However, it is recommended that F60 maintenance be scheduled with other system maintenance. This maintenance can involve in-service, out-of-service, or unscheduled maintenance.
In-service maintenance:
1. Visual verification of the analog values integrity, such as voltage and current (in comparison to other devices on the
corresponding system).
2. Visual verification of active alarms, relay display messages, and LED indications.
3. LED test.
4. Visual inspection for any damage, corrosion, dust, or loose wires.
5. Event recorder file download with further events analysis. Out-of-service maintenance:
1. Check wiring connections for firmness.
2. Analog values (currents, voltages, RTDs, analog inputs) injection test and metering accuracy verification. Calibrated
test equipment is required.
3. Protection elements setting verification (analog values injection or visual verification of setting file entries against relay
settings schedule).
4. Contact inputs and outputs verification. This test can be conducted by direct change of state forcing or as part of the
system functional testing.
5. Visual inspection for any damage, corrosion, or dust.
6. Event recorder file download with further events analysis.
7. LED Test and pushbutton continuity check. Unscheduled maintenance, such as a disturbance causing system interruption:
1. View the event recorder and oscillography or fault report for correct operation of inputs, outputs, and elements. If it is concluded that the relay or one of its modules is of concern, contact GE Multilin for service.
1
GE Multilin F60 Feeder Protection System 1-19
Page 30
1
1.5 USING THE RELAY 1 GETTING STARTED
1-20 F60 Feeder Protection System GE Multilin
Page 31
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION

2 PRODUCT DESCRIPTION 2.1INTRODUCTION 2.1.1 OVERVIEW

The F60 Feeder Protection System is a microprocessor based relay designed for feeder protection. Overvoltage and undervoltage protection, overfrequency and underfrequency protection, breaker failure protection, direc-
tional current supervision, fault diagnostics, RTU, and programmable logic functions are provided. This relay also provides phase, neutral, ground and negative sequence, instantaneous and time overcurrent protection. The time overcurrent func­tion provides multiple curve shapes or FlexCurves™ for optimum co-ordination. Automatic reclosing, synchrocheck, and line fault locator features are also provided. When equipped with a type 8Z CT/VT module, an element for detecting high impedance faults is provided.
Voltage, current, and power metering is built into the relay as a standard feature. Current parameters are available as total waveform RMS magnitude, or as fundamental frequency only RMS magnitude and angle (phasor).
Diagnostic features include a sequence of records capable of storing 1024 time-tagged events. The internal clock used for time-tagging can be synchronized with an IRIG-B signal, using the Simple Network Time Protocol (SNTP) over the Ethernet port, or using the Precision Time Protocol (PTP). This precise time stamping allows the sequence of events to be deter­mined throughout the system. Events can also be programmed (via FlexLogic™ equations) to trigger oscillography data capture which may be set to record the measured parameters before and after the event for viewing on a personal com­puter (PC). These tools significantly reduce troubleshooting time and simplify report generation in the event of a system fault.
Several options are available for communication. A faceplate RS232 port can be used to connect to a computer for the pro­gramming of settings and the monitoring of actual values. The RS232 port has a fixed baud rate of 19.2 kbps. The rear RS485 port allows independent access by operating and engineering staff. It can be connected to system computers with baud rates up to 115.2 kbps. All serial ports use the Modbus RTU protocol. The IEC 60870-5-103 protocol is supported on the RS485 interface. IEC 60870-5-103, DNP, and Modbus cannot be enabled simultaneously on this interface. Also only one of the DNP, IEC 60870-5-103, and IEC 60870-5-104 protocols can be enabled at any time on the relay. When the IEC 60870-5-103 protocol is chosen, the RS485 port has a fixed even parity and the baud rate can be either 9.6 kbps or 19.2 kbps. The 100Base-FX or 100Base-T Ethernet interface provides fast, reliable communications in noisy environments. The Ethernet port supports IEC 61850, IEC 61850-90-5, Modbus/TCP, and TFTP protocols, PTP (according to IEEE Std. 1588­2008 or IEC 61588), and allows access to the relay via any standard web browser (F60 web pages). The IEC 60870-5-104 protocol is supported on the Ethernet port. The Ethernet port also supports the Parallel Redundancy Protocol (PRP) of IEC 62439-3 (clause 4, 2012) when purchased as an option.
Settings and actual values can be accessed from the front panel or EnerVista software. The F60 IEDs use flash memory technology which allows field upgrading as new features are added. The following single
line diagram illustrates the relay functionality using ANSI (American National Standards Institute) device numbers.
2
Table 2–1: ANSI DEVICE NUMBERS AND FUNCTIONS
DEVICE NUMBER
25 Synchrocheck 51_2 Negative-sequence time overcurrent 27P Phase undervoltage 52 AC circuit breaker 27X Auxiliary undervoltage 59N Neutral overvoltage 32 Sensitive directional power 59P Phase overvoltage 32N Wattmetric zero-sequence directional 59X Auxiliary overvoltage 49 Thermal overload protection 59_2 Negative-sequence overvoltage 50BF/50NBF Breaker failure 67N Neutral directional overcurrent 50DD Disturbance detector 67P Phase directional overcurrent 50G Ground instantaneous overcurrent 67_2 Negative-sequence directional overcurrent 50N Neutral instantaneous overcurrent 79 Automatic recloser 50P Phase instantaneous overcurrent 81O Overfrequency 50_2 Negative-sequence instantaneous overcurrent 81R Rate of change frequency 51G Ground time overcurrent 81U Underfrequency 51N Neutral time overcurrent 87RGF Restricted ground fault 51P Phase time overcurrent
FUNCTION DEVICE
NUMBER
FUNCTION
GE Multilin F60 Feeder Protection System 2-1
Page 32
2
832726A2.CDR
52
50P
50G
50_2
51G
51_2
79
CLOSE TRIP
50BF
51P/V
67P
67_2
32
50N
51N
67N/G
50NBF
81U
81O
27P
59P
59N
59X
59_2
27X
25
Monitoring
F60 Feeder Protection System
TM
FlexElement
Transducer
Inputs
Metering + PMU
32N
49
87RGF
2.1 INTRODUCTION 2 PRODUCT DESCRIPTION
Figure 2–1: SINGLE LINE DIAGRAM
Table 2–2: OTHER DEVICE FUNCTIONS
FUNCTION FUNCTION FUNCTION
Breaker arcing current (I Breaker control Event recorder Setting groups (6) Breaker flashover Fault detector and fault report Synchrophasor (PMU) Breaker restrike Fault locator Thermal overload protection Broken conductor detection FlexElements™ (8) Time synchronization over IRIG-B or IEEE
Cold load pickup FlexLogic equations Time synchronization over SNTP Contact inputs (up to 96) High impedance fault detection (Hi-Z) Transducer inputs and outputs Contact outputs (up to 64) IEC 60870-5-103 communications
Control pushbuttons IEC 61850 communications (optional) User-programmable LEDs CyberSentry™ security Incipient cable fault detection User-programmable pushbuttons Data logger Load encroachment User-programmable self-tests Demand Metering: current, voltage, power, PF,
Digital counters (8) Modbus user map Virtual outputs (96) Digital elements (48) Non-volatile latches VT fuse failure Direct inputs and outputs (32) Non-volatile selector switch
The following security features are available:
Password security — Basic security present in the default offering of the product
EnerVista security — Role-based access to various EnerVista software screens and configuration elements. The fea­ture is available in the default offering of the product and only in the EnerVista software.
CyberSentry security — Advanced security options available as a software option. When purchased, the options are automatically enabled, and the default Password security and EnerVista security are disabled.
2-2 F60 Feeder Protection System GE Multilin
2
t) Disconnect switches Oscillography
1588
User-definable displays
Virtual inputs (64)
(optional)
energy, frequency, harmonics, THD

2.1.2 SECURITY

Page 33
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION
Changing the password, or any other setting, does not take the relay out of service. The relay is taken out of service when a settings file is written to it.
a) ENERVISTA SECURITY
The EnerVista security management system is a role-based access control (RBAC) system that allows an administrator to manage the privileges of multiple users. This allows for access control of UR devices by multiple personnel within a substa­tion and conforms to the principles of RBAC as defined in ANSI INCITS 359-2004. The EnerVista security management system is disabled by default to allow the administrator direct access to the EnerVista software after installation. It is recom­mended that security be enabled before placing the device in service.
Basic password or enhanced CyberSentry security applies, depending on purchase.
b) PASSWORD SECURITY
Password security is a basic security feature present in the default offering of the product. Two levels of password security are provided: command and setting. The following operations are under command password supervision:
Operating the breakers via faceplate keypad
Changing the state of virtual inputs
Clearing the event records
Clearing the oscillography records
Clearing fault reports
Changing the date and time
Clearing the breaker arcing current
Clearing energy records
Clearing the data logger
Clearing the user-programmable pushbutton states The following operations are under setting password supervision:
Changing any setting
Test mode operation The F60 supports password entry from a local or remote connection. Local access is defined as any access to settings or
commands via the faceplate interface. This includes both keypad entry and the through the faceplate RS232 port. Remote access is defined as any access to settings or commands via any rear communications port. This includes both Ethernet and RS485 connections. Any changes to the local or remote passwords enables this functionality.
When entering a settings or command password via EnerVista or any serial interface, the user must enter the correspond­ing connection password. If the connection is to the back of the F60, the remote password must be used. If the connection is to the RS232 port of the faceplate, the local password applies.
Password access events are logged in the Event Recorder.
2
c) CYBERSENTRY SECURITY
CyberSentry Embedded Security is a software option that provides advanced security services. When this option is pur­chased, the basic password security is disabled automatically.
CyberSentry provides security through the following features:
An Authentication, Authorization, Accounting (AAA) Remote Authentication Dial-In User Service (RADIUS) client that
is centrally managed, enables user attribution, provides accounting of all user activities, and uses secure standards­based strong cryptography for authentication and credential protection.
A Role-Based Access Control (RBAC) system that provides a permission model that allows access to UR device oper-
ations and configurations based on specific roles and individual user accounts configured on the AAA server (that is, Administrator, Supervisor, Engineer, Operator, Observer).
GE Multilin F60 Feeder Protection System 2-3
Page 34
2.1 INTRODUCTION 2 PRODUCT DESCRIPTION
842838A2.CDR
Administrator
Engineer
Supervisor
Operator
Observer
Security event reporting through the Syslog protocol for supporting Security Information Event Management (SIEM) systems for centralized cybersecurity monitoring.
Strong encryption of all access and configuration network messages between the EnerVista software and UR devices using the Secure Shell (SSH) protocol, the Advanced Encryption Standard (AES), and 128-bit keys in Galois Counter Mode (GCM) as specified in the U.S. National Security Agency Suite B extension for SSH and approved by the National Institute of Standards and Technology (NIST) FIPS-140-2 standards for cryptographic systems.
CYBERSENTRY USER ROLES
2
CyberSentry user roles (Administrator, Engineer, Operator, Supervisor, Observer) limit the levels of access to various UR device functions. This means that the EnerVista software allows for access to functionality based on the user’s logged in role.
Example: Administrative functions can be segmented away from common operator functions, or engineering type access, all of which are defined by separate roles, as shown in the following figure, so that access of UR devices by multiple per­sonnel within a substation is allowed.
Figure 2–2: CYBERSENTRY USER ROLES
The table lists the roles that are supported and their corresponding capabilities.
Table 2–3: PERMISSIONS BY USER ROLE FOR CYBERSENTRY
Roles Administrator Engineer Operator Supervisor Observer
Device Definition RRRRR
Settings
|------------ Product Setup
Complete access Complete access
|--------------- Security (CyberSentry) RW R R R R |--------------- Supervisory see table notes R R see table notes R |--------------- Display Properties RW RW R R R
|--------------­|--------------- Communications RW RW R R R |--------------- Modbus user map RW RW R R R |--------------- Real Time Clock RW RW R R R |--------------- Oscillography RW RW R R R |--------------- Data Logger RW RW R R R |--------------- Demand RW RW R R R
|---------------
|--------------­|--------------- Control Pushbuttons RW RW R R R
Clear relay records (settings) RW RW R R R
User Programmable LEDs RW RW R R R
User Programmable self test RW RW R R R
except for CyberSentry Security
Command menu
Authorizes writing
Default role
2-4 F60 Feeder Protection System GE Multilin
Page 35
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION
Roles Administrator Engineer Operator Supervisor Observer
|--------------­|--------------- Flex states RW RW R R R
|--------------­|--------------- Direct I/O RW RW R R R |--------------- Tele-protection RW RW R R R
|--------------- Installation RW RW R R R |------------ System Setup RW RW R R R |------------ FlexLogic RW RW R R R |------------ Grouped Elements RW RW R R R |------------ Control Elements RW RW R R R |------------ Inputs / Outputs RW RW R R R
|--------------- Contact Input RW RW R R R
|---------------
|--------------- Virtual Inputs RW RW R R R
|--------------- Contact Output RW RW R R R
|--------------- Virtual Output RW RW R R R
|--------------- Remote Devices RW RW R R R
|--------------- Remote Inputs RW RW R R R
|--------------- Remote DPS input RW RW R R R
|---------------
|---------------
|--------------- Resetting RW RW R R R
|--------------- Direct Inputs RW RW R R R
|--------------- Direct Outputs RW RW R R R
|--------------- Teleprotection RW RW R R R
|--------------- Direct Analogs RW RW R R R
|--------------- Direct Integers RW RW R R R
|---------------
|--------------­|------------ Transducer I/O RW RW R R R |------------ Testing RW RW R R R |------------ Front Panel Labels Designer NA NA NA NA NA
|------------ Protection Summary NA NA NA NA NA Commands RW RW RW R R |------------ Virtual Inputs RW RW RW R R |------------ Clear Records RW RW RW R R
|------------ Set date and time RW RW RW R R
User Displays RRRRR
Targets RRRRR Actual Values RRRRR
|------------ Front Panel Labels Designer R R R R R |------------ Status R R R R R
User programmable Pushbuttons RW RW R R R
User definable dis­plays RW RW R R R
2
Contact Input thresh­old RW RW R R R
Remote Output DNA Bit Pair RW RW R R R
Remote Output user Bit Pair RW RW R R R
IEC61850 GOOSE Analogs RW RW R R R
IEC61850 GOOSE Integers RW RW R R R
GE Multilin F60 Feeder Protection System 2-5
Page 36
2.1 INTRODUCTION 2 PRODUCT DESCRIPTION
Roles Administrator Engineer Operator Supervisor Observer
|------------ Metereing R R R R R |------------ Transducer I/O R R R R R |------------ Records R R R R R
|------------ Product Info R R R R R
Maintenance RW RW R R R
2
|------------ Modbus Analyzer NA NA NA NA NA |------------ Change Front Panel RW RW RW R R |------------ Update Firmware Yes No No No No
|------------ Retrieve File Yes No No No No
Table Notes:
1. RW = read and write access
2. R = read access
3. Supervisor = RW (default), Administrator = R (default), Administrator = RW (only if Supervisor role is disabled)
4. NA = the permission is not enforced by CyberSentry Security
CYBERSENTRY USER AUTHENTICATION
There are two types of authentication supported by CyberSentry that can be used to access the UR device:
Device Authentication (local UR device authenticates)
Server Authentication (RADIUS server authenticates) The EnerVista software allows access to functionality that is determined by the user role, which comes either from the local
UR device or RADIUS server. The EnerVista software has a device authentication option on the login screen for accessing the UR device. When the
"Device" button is selected, the UR uses its local authentication database and not the RADIUS server to authenticate the user. In this case, it uses its built-in roles (Administrator, Engineer, Supervisor, Observer, Operator, or Administrator and Supervisor when Device Authentication is disabled) as login names and the associated passwords are stored on the UR device. As such, when using the local accounts, access is not user-attributable.
In cases where user attributable access is required especially to facilitate auditable processes for compliance reasons, use RADIUS authentication only.
When the "Server" Authentication Type option is selected, the UR uses the RADIUS server and not its local authentication database to authenticate the user.
No password or security information are displayed in plain text by the EnerVista software or UR device, nor are they ever transmitted without cryptographic protection.
CyberSentry Server Authentication
The UR has been designed to automatically direct authentication requests based on user names. In this respect, local account names on the UR are considered as reserved, and not used on a RADIUS server.
The UR automatically detects whether an authentication request is to be handled remotely or locally. As there are only five local accounts possible on the UR, if the user ID credential does not match one of the five local accounts, the UR automat­ically forwards the request to a RADIUS server when one is provided.
If a RADIUS server is provided, but is unreachable over the network, server authentication requests are denied. In this situ­ation, use local UR accounts to gain access to the UR system.
2-6 F60 Feeder Protection System GE Multilin
Page 37
2 PRODUCT DESCRIPTION 2.1 INTRODUCTION

2.1.3 IEC 870-5-103 PROTOCOL

IEC 870-5-103 is a companion standard to IEC 870-5 suit of standards for transmission protocols. It defines messages and procedures for interoperability between protection equipment and devices of a control system in a substation for communi­cating on a serial line.
The IEC 60870-5-103 is an unbalanced (master-slave) protocol for coded-bit serial communication, exchanging information with a control system. In the context of this protocol, the protection equipment is the slave and the control system is the master. The communication is based on a point to point principle. The master must be able to interpret the IEC 60870-5­103 communication messages.
The UR implementation of IEC 60870-5-103 consists of the following functions:
Report binary inputs
Report analog values (measurands)
Commands
Time synchronization The RS485 port supports IEC 60870-5-103.
2
GE Multilin F60 Feeder Protection System 2-7
Page 38
2.2 ORDER CODES 2 PRODUCT DESCRIPTION
NOTE

2.2ORDER CODES 2.2.1 OVERVIEW

The F60 is available as a 19-inch rack horizontal mount or reduced-size (¾) vertical unit and consists of the following mod­ules: power supply, CPU, CT/VT, contact input and output, transducer input and output, and inter-relay communications. Each of these modules can be supplied in a number of configurations specified at the time of ordering. The information required to completely specify the relay is provided in the following tables (see chapter 3 for full details of relay modules).
Order codes are subject to change without notice. See the ordering page at
2
http://www.gegridsolutions.com/multilin/order.htm
for the latest options.
The order code structure is dependent on the mounting option (horizontal or vertical) and the type of CT/VT modules (enhanced diagnostic CT/VT modules or HardFiber
TM
process bus modules). The order code options are described in the
following sub-sections.

2.2.2 ORDER CODES WITH ENHANCED CT/VT MODULES

The order codes for the horizontal mount units are shown below.
Table 2–4: F60 ORDER CODES (HORIZONTAL UNITS)
BASE UNIT F60 | | | | | | | | | | | Base Unit CPU T | | | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/ X ** Full Size Horizontal Mount
U | | | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP w ith LC), One 10/100Base-T (SFP with RJ45) V | | | | | | | | | | RS485 and Three 10/100Base-T (SFP with RJ45)
01 | | | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | | | IEC 61850 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | | | IEEE 1588 B1 | | | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | | | PRP and IEC 61850 C4 | | | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | | | PRP and PMU C7 | | | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (P MU) E0 | | | | | | | | | IEEE 1588 and PRP E1 | | | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada E3 | | | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | | | IEC 60870-5-103 J1 | | | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 K1 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU
2-8 F60 Feeder Protection System GE Multilin
Page 39
2 PRODUCT DESCRIPTION 2.2 ORDER CODES
Table 2–4: F60 ORDER CODES (HORIZONTAL UNITS)
MOUNT/COATING H | | | | | | | | Horizontal (19” rack) - Standard
FACEPLATE/ DISPLAY C | | | | | | | English display
POWER SUPPLY (redundant supply must be same type as main supply)
ENHANCED DIAGNOSTICS CT/VT DSP (8L, 8M, 8N, 8R require DSP to be enhanced diagnostic)
DIGITAL INPUTS/OUTPUTS XX XX XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
A | | | | | | | | Horizontal (19” rack) - With harsh environmental coating
D | | | | | | | French display R | | | | | | | Russian display A | | | | | | | Chinese display P | | | | | | | English display with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons
K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons
W | | | | | | | Enhanced front panel with Turkish display
Y | | | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons
I | | | | | | | Enhanced front panel with German display
J | | | | | | | Enhanced front panel with German display and user-programmable pushbuttons
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
| | XX | XX | No DSP module (slots M and U only) 8L | 8L | | | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | | | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | | | Standard 8CT with enhanced diagnostics 8R | 8R | | | Sensitive Ground 8CT with enhanced diagnostics
| | 8Z * | | | Hi-Z 4CT (required for high-impedance fault detection element)
4A 4A 4A 4A 4A 4 Solid-State (no monitoring) MOSFET outputs 4B 4B 4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 4D 4D 16 digital inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs 6B 6B 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs 6C 6C 6C 6C 6C 8 Form-C outputs 6D 6D 6D 6D 6D 16 digital inputs 6E 6E 6E 6E 6E 4 Form-C outputs, 8 digital inputs 6F 6F 6F 6F 6F 8 Fast Form-C outputs 6G 6G 6G 6G 6G 4 For m-A (voltage with optional current) outputs, 8 digital inputs 6H 6H 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 6K 6K 6K 6K 4 Form-C and 4 Fast Form-C outputs 6L 6L 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 6M 6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 6N 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6P 6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 digital inputs 6R 6R 6R 6R 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs 6S 6S 6S 6S 6S 2 Form-A (no monitoring) and 4 Form-C o utputs, 4 digital inputs 6T 6T 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 digital inputs 6U 6U 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 6V 6V 6V 6V 2 Form-A outputs, 1 Form-C output, 1 Form-A latching output, 8 digital inputs 5A 5A 5A 5A 5A 4 DCmA inputs, 4 DCmA outputs 5C 5C 5C 5C 5C 8 RTD inputs 5D 5D 5D 5D 5D 4 RTD inputs, 4 DCmA outputs 5E 5E 5E 5E 5E 4 RTD inputs, 4 DCmA inputs 5F 5F 5F 5F 5F 8 DCmA inputs
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEE E C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels
2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser 2J Channel 1 - IE EE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels
7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED
7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED
7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel
7W RS422, 2 Channels
2
GE Multilin F60 Feeder Protection System 2-9
Page 40
2.2 ORDER CODES 2 PRODUCT DESCRIPTION
The order codes for the reduced size vertical mount units are shown below.
Table 2–5: F60 ORDER CODES (REDUCED SIZE VERTICAL UNITS)
BASE UNIT F60 | | | | | | | | | Base Unit CPU T | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | No Software Options
2
MOUNT/COATING V | | | | | | Vertical (3/4 rack) - Standard
FACEPLATE/ DISPLAY F | | | | | English display
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-T (SFP with RJ45) V | | | | | | | | RS485 and Three 10/100Base-T (SFP with RJ45)
01 | | | | | | | Ethernet Global Da ta (EGD) 03 | | | | | | | IEC 61850 04 | | | | | | | Ethernet Glob al Data (EGD) and IEC 61850 06 | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | CyberSentry Lvl 1 and E thernet Global Data (EGD) A3 | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | IEE E 1588 B1 | | | | | | | IEEE 15 88 and Ethernet Global Data (EGD) B3 | | | | | | | IEEE 15 88 and IEC 61850 B4 | | | | | | | IEEE 1588 and I EC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | IEEE 1588 and p hasor measurement unit (PMU) B7 | | | | | | | IEEE 1588 and I EC 61850 and phasor measurement unit (PMU) C0 | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | PRP and IEC 61850 C4 | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | PRP and PMU C7 | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | IEEE 1588 and CyberSentr y Lvl 1 D1 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | IEEE 1588 and CyberSentr y Lvl 1 and IEC 61850 D4 | | | | | | | IEEE 1588 and CyberSentr y Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 a nd phasor measurement unit (PMU) D7 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 a nd IEC 61850 and phasor measurement unit (PMU) E0 | | | | | | | IEEE 15 88 and PRP E1 | | | | | | | IEEE 15 88, PRP, and Ethernet Global Dada E3 | | | | | | | IEEE 15 88, PRP, and IEC 61850 E4 | | | | | | | IEEE 15 88, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | IEEE 15 88, PRP, and PMU E7 | | | | | | | IEEE 15 88, PRP, IEC 61850, and PMU F0 | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | PR P, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | IEC 60870-5-103 J1 | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 K1 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU
B | | | | | | Vertical (3/4 rack) - With harsh environmental coating
K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display L | | | | | Enhanced front panel with English display and user-programmable pushbut tons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user- programmable pushbuttons V | | | | | Enhanced front panel with Chinese display and user-programmable pushbut tons W | | | | | Enhanced front panel with Turkish display Y | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons
I | | | | | Enhanced front panel with German displ ay
J | | | | | Enhanced front panel with German display and user-programmable pushbuttons
2-10 F60 Feeder Protection System GE Multilin
Page 41
2 PRODUCT DESCRIPTION 2.2 ORDER CODES
Table 2–5: F60 ORDER CODES (REDUCED SIZE VERTICAL UNITS)
POWER SUPPLY H | | | | 125 / 250 V AC/DC power supply
ENHANCED DIAGNOSTICS CT/VT DSP (8L, 8M, 8N, 8R require DSP to be enhanced diagnostic)
DIGITAL INPUTS/OUTPUTS XX XX XX No Module
TRANSDUCER INPUTS/OUTPUTS (select a maximum of 3 per unit)
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital and transducer input/output modules; slot R is used for inter-relay communications modules.
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
L | | | | 24 to 48 V (DC only) power supply
XX | XX | No DSP module (slots F and M only) 8L | 8L | Standard 4CT/4VT with enhanced diagnostics 8M | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics 8N | 8N | Standard 8CT with enhanced diagnostics 8R | 8R | Sensitive Ground 8CT with enhanced diagnostics
| | 8Z * | Hi-Z 4CT (required for high-impedance fault detection element)
4A 4A 4A 4 Sol id-State (no monitoring) MOSFET outputs 4B 4B 4B 4 Sol id-State (voltage with optional current) MOSFET outputs 4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D 4D 16 digital inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L 4L 14 Form-A (no monitoring) Latching outputs 67 67 67 8 Form-A (no monitoring) outputs 6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs 6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs 6C 6C 6C 8 Form-C outputs 6D 6D 6D 16 digital inputs 6E 6E 6E 4 Form-C outputs, 8 digital inputs 6F 6F 6F 8 Fast Form-C outputs 6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 digital inputs 6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 6K 6K 4 Form- C and 4 Fast Form-C outputs 6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 digital inputs 6R 6R 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs 6S 6S 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs 6T 6T 6T 4 Form-A (no monitoring) outputs, 8 digital inputs 6U 6U 6U 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 6V 6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs 5A 5A 5A 4 DCmA i nputs, 4 DCmA outputs (only one 5A module is allowed) 5C 5C 5C 8 RTD inputs 5D 5D 5D 4 RTD inputs, 4 DCmA outputs (only one 5D module is allowed) 5E 5E 5E 4 RTD inputs, 4 DCmA inputs 5F 5F 5F 8 DCmA inputs
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEE E C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels
2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser 2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 n m, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED , 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED , 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels
7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELE D, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
2

2.2.3 ORDER CODES WITH PROCESS BUS MODULES

The order codes for the horizontal mount units with the process bus module are shown below.
Table 2–6: F60 ORDER CODES (HORIZONTAL UNITS WITH PROCESS BUS)
BASE UNIT F60 | | | | | | | | | | | Base Unit CPU T | | | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | | | No Software Options
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
U | | | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP w ith LC), One 10/100Base-T (SFP with RJ45) V | | | | | | | | | | RS485 and Three 10/100Base-T (SFP with RJ45)
01 | | | | | | | | | Ethernet Global Data (EGD) 03 | | | | | | | | | IEC 61850 04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850 06 | | | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD) A3 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) B0 | | | | | | | | | IEEE 1588 B1 | | | | | | | | | IEEE 1588 and Ethernet Global Data (EGD) B3 | | | | | | | | | IEEE 1588 and IEC 61850 B4 | | | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | | | IEEE 1588 and phasor measurement unit (PMU) B7 | | | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU) C0 | | | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | | | PRP and IEC 61850 C4 | | | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | | | PRP and PMU C7 | | | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 D1 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 D4 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU) D7 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU) E0 | | | | | | | | | IEEE 1588 and PRP E1 | | | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada
GE Multilin F60 Feeder Protection System 2-11
Page 42
2.2 ORDER CODES 2 PRODUCT DESCRIPTION
Table 2–6: F60 ORDER CODES (HORIZONTAL UNITS WITH PROCESS BUS)
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
2
MOUNT/COATING H | | | | | | | | Horizontal (19” rack) - Standard
FACEPLATE/ DISPLAY C | | | | | | | English display
POWER SUPPLY (redundant supply must be same type as main supply)
PROCESS BUS MODULE | 81 | | | | Eight-port digital process bus module DIGITAL INPUTS/OUTPUTS XX XX XX XX XX No Module
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit)
E3 | | | | | | | | | IEEE 1588, PRP, and IEC 61850 E4 | | | | | | | | | IEEE 1588, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | | | IEEE 1588, PRP, and PMU E7 | | | | | | | | | IEEE 1588, PRP, IEC 61850, and PMU F0 | | | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | | | PRP, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | | | IEC 60870-5-103 J1 | | | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 K1 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | | | IEC 60870-5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU
A | | | | | | | | Horizontal (19” rack) - With harsh environmental coating
D | | | | | | | French display R | | | | | | | Russian display A | | | | | | | Chinese display P | | | | | | | English display with 4 small and 12 large programmable pushbuttons G | | | | | | | French display with 4 small and 12 large programmable pushbuttons S | | | | | | | Russian display with 4 small and 12 large programmable pushbuttons B | | | | | | | Chinese display with 4 small and 12 large programmable pushbuttons K | | | | | | | Enhanced front panel with English display M | | | | | | | Enhanced front panel with French display Q | | | | | | | Enhanced front panel with Russian display U | | | | | | | Enhanced front panel with Chinese display L | | | | | | | Enhanced front panel with English display and user-programmable pushbuttons N | | | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | | | Enhanced front panel with Chinese display and user-programmable pushbuttons W | | | | | | | Enhanced front panel with Turkish display Y | | | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons
I | | | | | | | Enhanced front panel with German display J | | | | | | | Enhanced front panel with German display and user-programmable pushbuttons
H | | | | | | 125 / 250 V AC/DC power supply H | | | | | SH 125 / 250 V AC/DC with redundant 125 / 250 V AC/DC power supply L | | | | | | 24 to 48 V (DC only) power supply L | | | | | SL 24 to 48 V (DC only) with redundant 24 to 48 V DC power supply
4A 4A | 4 Solid-State (no monitoring) MOSFET outputs 4B 4B | 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4C | 4 Solid-State (current with optional voltage) MOSFET outputs 4D 4D | 16 digital inputs with Auto-Burnishing (maximum of three modules within a case) 4L 4L | 14 Form-A (no monitoring) Latching outputs 67 67 | 8 Form-A (no monitoring) outputs 6A 6A | 2 Form-A (voltage with optional curr ent) and 2 Form-C outputs, 8 digital inputs 6B 6B | 2 Form-A (voltage with optional curr ent) and 4 Form-C outputs, 4 digital inputs 6C 6C | 8 Form-C outputs 6D 6D | 16 digital inputs 6E 6E | 4 Form-C outputs, 8 digital inputs
6F 6F | 8 Fast Form-C outputs 6G 6G | 4 Form-A (voltage with optional current) outputs, 8 digital inputs 6H 6H | 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 6K | 4 Form-C and 4 Fast Form -C outputs 6L 6L | 2 Form-A (current w ith optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 6M | 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 6N | 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6P | 6 Form-A (current with optional voltage) outputs, 4 digital inputs 6R 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs 6S 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs 6T 6T | 4 Form-A (no monitoring) outputs, 8 digital inputs 6U 6U | 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 6V | 2 Form-A outputs, 1 Form-C output , 2 Form-A (no monitoring) latching outputs, 8 digital inputs
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEE E C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels
2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channe l 2 - 1300 nm, single-mode, Laser 2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels
7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELED, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels
The order codes for the reduced size vertical mount units with the process bus module are shown below.
2-12 F60 Feeder Protection System GE Multilin
Page 43
2 PRODUCT DESCRIPTION 2.2 ORDER CODES
Table 2–7: F60 ORDER CODES (REDUCED SIZE VERTICAL UNITS WITH PROCESS BUS)
BASE UNIT F60 | | | | | | | | | Base Unit CPU T | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
SOFTWARE 00 | | | | | | | No Software Options
MOUNT/COATING V | | | | | | Vertical (3/4 rack) - Standard
FACEPLATE/ DISPLAY F | | | | | English display
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
U | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-T (SFP with RJ45) V | | | | | | | | RS485 and Three 10/100Base-T (SFP with RJ45)
01 | | | | | | | Ethernet Global Da ta (EGD) 03 | | | | | | | IEC 61850 04 | | | | | | | Ethernet Glob al Data (EGD) and IEC 61850 06 | | | | | | | Phasor measurement unit (PMU) 07 | | | | | | | Phasor measurement unit (PMU) and IEC 61850 A0 | | | | | | | CyberSentry Lvl 1 A1 | | | | | | | CyberSentry Lvl 1 and E thernet Global Data (EGD) A3 | | | | | | | CyberSentry Lvl 1 and IEC 61850 A4 | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) A6 | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU) A7 | | | | | | | CyberSentry Lvl 1 and IE C 61850 and phasor measurement unit (PMU) B0 | | | | | | | IEE E 1588 B1 | | | | | | | IEEE 15 88 and Ethernet Global Data (EGD) B3 | | | | | | | IEEE 15 88 and IEC 61850 B4 | | | | | | | IEEE 1588 and I EC 61850 and Ethernet Global Data (EGD) B6 | | | | | | | IEEE 1588 and p hasor measurement unit (PMU) B7 | | | | | | | IEEE 1588 and I EC 61850 and phasor measurement unit (PMU) C0 | | | | | | | Parallel Redundancy Protocol (PRP) C1 | | | | | | | PRP and Ethernet Global Data C3 | | | | | | | PRP and IEC 61850 C4 | | | | | | | PRP, Ethernet Global Data, and IEC 61850 C6 | | | | | | | PRP and PMU C7 | | | | | | | PRP, IEC 61850, and PMU D0 | | | | | | | IEEE 1588 and CyberSentr y Lvl 1 D1 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD) D3 | | | | | | | IEEE 1588 and CyberSentr y Lvl 1 and IEC 61850 D4 | | | | | | | IEEE 1588 and CyberSentr y Lvl 1 and IEC 61850 and Ethernet Global Data (EGD) D6 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 a nd phasor measurement unit (PMU) D7 | | | | | | | IEEE 1588 and CyberSentry Lvl 1 a nd IEC 61850 and phasor measurement unit (PMU) E0 | | | | | | | IEEE 15 88 and PRP E1 | | | | | | | IEEE 15 88, PRP, and Ethernet Global Dada E3 | | | | | | | IEEE 15 88, PRP, and IEC 61850 E4 | | | | | | | IEEE 15 88, PRP, Ethernet Global Data, and IEC 61850 E6 | | | | | | | IEEE 15 88, PRP, and PMU E7 | | | | | | | IEEE 15 88, PRP, IEC 61850, and PMU F0 | | | | | | | PRP and CyberSentry Lvl1 F1 | | | | | | | PR P, CyberSentry Lvl1, and Ethernet Global Data F3 | | | | | | | PRP, CyberSentry Lvl 1, and IEC 61850 F4 | | | | | | | PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 F6 | | | | | | | PRP, CyberSentry Lvl 1, and PMU F7 | | | | | | | PRP, CyberSentry Lvl 1, IEC 61850, and PMU G0 | | | | | | | IEEE 1588, PRP, and CyberSentry Lvl 1 G1 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data G3 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and IEC 61850 G4 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, Ethernet Global Data, and IEC 61850 G6 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, and PMU G7 | | | | | | | IEEE 1588, PRP, CyberSentry Lvl 1, IEC 61850, and PMU J0 | | | | | | | IEC 60870-5-103 J1 | | | | | | | IEC 60870-5-103 + EGD J3 | | | | | | | IEC 60870-5-103 + IEC 61850 J4 | | | | | | | IEC 60870-5-103 + EGD + IEC 61850 J6 | | | | | | | IEC 60870-5-103 + PMU J7 | | | | | | | IEC 60870-5-103 + IEC 61850 + PMU K0 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 K1 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD K3 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 K4 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + EGD + IEC 61850 K6 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + PMU K7 | | | | | | | IEEE1588 + PRP + IEC 60870-5-103 + IEC 61850 + PMU L0 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 L1 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD L3 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 L4 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + EGD + IEC 61850 L6 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + PMU L7 | | | | | | | IEC 60870- 5-103 + IEEE1588 + PRP + CyberSentry Lvl 1 + IEC 61850 + PMU
B | | | | | | Vertical (3/4 rack) - With harsh environmental coating
D | | | | | French display R | | | | | Russian display A | | | | | Chinese display K | | | | | Enhanced front panel with English display M | | | | | Enhanced front panel with French display Q | | | | | Enhanced front panel with Russian display U | | | | | Enhanced front panel with Chinese display L | | | | | Enhanced front panel with English display and user-programmable pushbut tons N | | | | | Enhanced front panel with French display and user-programmable pushbuttons T | | | | | Enhanced front panel with Russian display and user-programmable pushbuttons V | | | | | Enhanced front panel with Chinese display and user-programmable pushbut tons
W | | | | | Enhanced front panel with Turkish display
Y | | | | | Enhanced front panel with Turkish display and user-programmable pushbuttons
I | | | | | Enhanced front panel with German displ ay J | | | | | Enhanced front panel with German display and user-programmable pushbuttons
2
GE Multilin F60 Feeder Protection System 2-13
Page 44
2.2 ORDER CODES 2 PRODUCT DESCRIPTION
NOTE
NOTE
Table 2–7: F60 ORDER CODES (REDUCED SIZE VERTICAL UNITS WITH PROCESS BUS)
POWER SUPPLY H | | | | 125 / 250 V AC/DC power supply
PROCESS BUS MODULE | 81 | | Eight-port digital process bus module DIGITAL INPUTS/OUTPUTS XX XX XX No Module
2
INTER-RELAY COMMUNICATIONS (select a maximum of 1 per unit) For the last module, slot P is used for digital input/output modules; slot R is used for inter-relay communications modules.
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)
L | | | | 24 to 48 V (DC only) power supply
4A 4 Solid-State (no monitoring) MOSFET outputs
4B 4 Solid-State (voltage with optional current) MOSFET outputs 4C 4 Solid-State (current with optional voltage) MOSFET outputs 4D 16 digital inputs with Auto-Burnishing (maximum of three modules within a case) 4L 14 Form-A (no monitoring) Lat ching outputs 67 8 Form-A (no monitoring) outputs 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs 6C 8 Form-C outputs 6D 16 digital inputs 6E 4 Form-C outputs, 8 digital inputs 6F 8 Fast Form-C outputs 6G 4 For m-A (voltage with optional current) outputs, 8 digital inputs 6H 6 Form-A (voltage with optional current) outputs, 4 digital inputs 6K 4 Form-C and 4 Fast Form-C outputs 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs 6M 2 Form-A (current wi th optional voltage) and 4 Form-C outputs, 4 digital inputs 6N 4 Form-A (current with optional voltage) outputs, 8 digital inputs 6P 6 Form-A (current with optional voltage) outputs, 4 digital inputs 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs 6T 4 Form-A (no monitoring) outputs, 8 digital inputs 6U 6 Form-A (no monitoring) outputs, 4 digital inputs 6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs 2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode 2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode 2E Bi-phase, single channel 2F Bi-phase, dual channel 2G IEE E C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel 2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels
2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser 2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser 72 1550 nm, single-mode, Laser, 1 Channel 73 1550 nm, single-mode, Laser, 2 Channel 74 Channel 1 - RS422; Channel 2 - 1550 n m, single-mode, Laser 75 Channel 1 - G.703; Channel 2 - 1550 nm, Single-mode Laser 76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED , 1 Channel 77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED , 2 Channels 7A 820 nm, multimode, LED, 1 Channel 7B 1300 nm, multimode, LED, 1 Channel 7C 1300 nm, single-mode, ELED, 1 Channel 7D 1300 nm, single-mode, Laser, 1 Channel 7E Channel 1 - G.703; Channel 2 - 820 nm, multimode 7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode 7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED 7H 820 nm, multimode, LED, 2 Channels
7I 1300 nm, multimode, LED, 2 Channels 7J 1300 nm, single-mode, ELE D, 2 Channels 7K 1300 nm, single-mode, Laser, 2 Channels 7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED 7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED 7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED 7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser 7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser 7R G.703, 1 Channel 7S G.703, 2 Channels 7T RS422, 1 Channel 7W RS422, 2 Channels

2.2.4 REPLACEMENT MODULES

Replacement modules can be ordered separately. When ordering a replacement CPU module or faceplate, provide the serial number of your existing unit.
Not all replacement modules may be applicable to the F60 relay. Only the modules specified in the order codes are available as replacement modules.
Replacement module codes are subject to change without notice. See the ordering page at
http://www.gegridsolutions.com/multilin/order.htm
for the latest options.
The replacement module order codes for the horizontal mount units are shown below.
Table 2–8: ORDER CODES FOR REPLACEMENT MODULES, HORIZONTAL UNITS
POWER SUPPLY redundant supply only available in horizontal units and must be same type as main supply, for example must swap both power supplies when switching from RH to SH CPU | T | RS485 with 3 100Base-FX Ethernet, multimode, SFP with LC
FACEPLATE/DISPLAY | 3C | Horizontal faceplate with keypad and English display
UR - ** - *
| SH A | 125 / 300 V AC/DC
| SL H | 24 to 48 V (DC only)
| U | RS 485 with 1 100Base-T Ethernet, SFP RJ-45 + 2 100Base-FX Ethernet, multimode, SFP with LC | V | RS485 with 3 100Base-T Ethernet, SFP with RJ-45
| 3D | Hor izontal faceplate with keypad and French display | 3R | Hor izontal faceplate with keypad and Russian display | 3A | Horizontal faceplate wit h keypad and Chinese display | 3P | Horizontal faceplate wit h keypad, user-programmable pushbuttons, and English display | 3G | Horizontal faceplate with keypad, user-programmable pushbuttons, and French display | 3S | Horizontal faceplate with keypad, user-programmable pushbuttons, and Russian display | 3B | Horizontal faceplate wit h keypad, user-programmable pushbuttons, and Chinese display | 3K | Enhanced fro nt panel with English display | 3M | Enhanced front panel with French display | 3Q | Enhanced front panel with Russian display | 3U | Enhanced front panel with Chinese display | 3L | Enhanced front panel with Eng lish display and user-programmable pushbuttons | 3N | Enhanced front panel with French display and user-programmable pushbuttons | 3T | Enhanced front panel with Russian display and user-programmable pushbuttons | 3V | Enhanced fro nt panel with Chinese display and user-programmable pushbuttons | 3I | Enhanced front panel with German display | 3J | Enhanced front panel with German display and user -programmable pushbuttons
2-14 F60 Feeder Protection System GE Multilin
Page 45
2 PRODUCT DESCRIPTION 2.2 ORDER CODES
Table 2–8: ORDER CODES FOR REPLACEMENT MODULES, HORIZONTAL UNITS
CONTACT INPUTS AND OUTPUTS | 4A | 4 Solid-State (no monitoring) MOSFET o utputs
CT/VT MODULES (NOT AVAILABLE FOR THE C30)
INTER-RELAY COMMUNICATIONS | 2A | C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode
TRANSDUCER INPUTS/OUTPUTS
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
UR - ** - *
| 4B | 4 Solid-State (voltage with optional current) MOSFET outputs | 4C | 4 Solid-State (current with optional voltage) MOSFET out puts | 4D | 16 contact inputs with Auto -Burnishing | 4L | 14 Form-A (no monitoring) Latching outputs | 67 | 8 Form-A (no monitoring) outputs | 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs | 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs | 6C | 8 Form-C outputs | 6D | 16 contact inputs | 6E | 4 Form-C outputs, 8 contact inputs | 6F | 8 Fast Form-C outputs | 6G | 4 Form -A (voltage with optional current) outputs, 8 contact inputs | 6H | 6 Form-A (voltage wit h optional current) outputs, 4 contact inputs | 6K | 4 Form-C and 4 Fast Form-C outputs | 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs | 6M | 2 Form-A (current with optiona l voltage) and 4 Form-C outputs, 4 contact inputs | 6N | 4 Form-A (current with optional voltage) outputs, 8 contact inputs | 6P | 6 Form-A (current with optional voltage) outputs, 4 contact inputs | 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs | 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs | 6T | 4 Form-A (no monitoring ) outputs, 8 contact inputs | 6U | 6 Form-A (no monitoring) outputs, 4 contact inputs | 6V | 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 contact inputs | 8L | Standard 4CT/4VT with enhanced diagnostics | 8N | Standard 8CT with enhanced diagnostics | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics | 8R | Sensit ive Ground 8CT with enhanced diagnostics | 8Z * | HI-Z 4CT
| 2B | C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode | 2E | Bi-phase, single channel | 2F | Bi-phase, dual channel | 2G | IEEE C 37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel | 2H | IEEE C37.94 , 820 nm, 128 kbps, multimode, LED, 2 Channels | 2I | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser | 2J | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser | 72 | 1550 nm, single-mode, Laser, 1 Channel | 73 | 1550 nm, single-mode, Laser, 2 Channel | 74 | Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser | 75 | Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser | 76 | IEEE C37.94, 820 nm, multimode, LED, 1 Channel | 77 | IEEE C37.94, 820 nm, multimode, LED, 2 Channels | 7A | 820 nm, multimode, LED, 1 Channel | 7B | 1300 nm, multimode, LED, 1 Channel | 7C | 1300 nm, single-mode, EL ED, 1 Channel | 7D | 1300 nm, single-mode, Laser, 1 Channel | 7E | Channel 1 - G.703; Channel 2 - 820 nm, multimode | 7F | Channel 1 - G.703; Channel 2 - 1300 nm, multimode | 7G | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED | 7H | 820 nm, multimode, LED, 2 Channels | 7I | 1300 nm, multimode, LED, 2 Channels | 7J | 1300 nm, single-mode, ELED, 2 Channels | 7K | 1300 nm, single-mode, Laser, 2 Channels | 7L | Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED | 7M | Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED | 7N | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED | 7P | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser | 7Q | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser | 7R | G.703, 1 Channel | 7S | G.703, 2 Channels | 7T | RS422, 1 Channel | 7W | RS422, 2 Chan nels | 5A | 4 DCmA inputs, 4 DCmA ou tputs (only one 5A module is allowed) | 5C | 8 RTD inputs | 5D | 4 RTD inputs, 4 DC mA outputs (only one 5D module is allowed) | 5E | 4 DCmA inputs, 4 RTD inputs | 5F | 8 DCmA inputs
The replacement module order codes for the reduced-size vertical mount units are shown below.
2
Table 2–9: ORDER CODES FOR REPLACEMENT MODULES, VERTICAL UNITS
POWER SUPPLY | SH B | 125 / 300 V AC/DC
CPU | T | RS485 with 3 100Base-FX Ethernet, multimode, SFP with LC
FACEPLATE/DISPLAY | 3F | Vertical faceplate with keypad and English display
CONTACT INPUTS/OUTPUTS | 4A | 4 Solid-State (no monitoring) MOSFET outputs
CT/VT MODULES (NOT AVAILABLE FOR THE C30)
INTER-RELAY COMMUNICATIONS | 2A | C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode
UR - ** - *
| SL V | 24 to 48 V (DC only)
| U | RS 485 with 1 100Base-T Ethernet, SFP RJ-45 + 2 100Base-FX Ethernet, multimode, SFP with LC | V | RS485 with 3 100Base-T Ethernet, SFP with RJ-45
| 3D | Vertical faceplate with keypad and French display | 3R | Vertical faceplate with keypad and Russian display | 3A | Vertical faceplate with keypad and Chinese display | 3K | Enhanced fro nt panel with English display | 3M | Enhanced front panel with French display | 3Q | Enhanced front panel with Russian display | 3U | Enhanced front panel with Chinese display | 3L | Enhanced front panel with En glish display and user-programmable pushbuttons | 3N | Enhanced front panel with French display and user-programmable pushbuttons | 3T | Enhanced front panel with Russian display and user-programmable pushbuttons | 3V | Enhanced fro nt panel with Chinese display and user-programmable pushbuttons | 3I | Enhanced front panel with German display | 3J | Enhanced front panel with German display and user -programmable pushbuttons
| 4B | 4 Solid-State (voltage with optional current) MOSFET outputs | 4C | 4 Solid-State (current with optional voltage) MOSFET out puts | 4D | 16 contact inputs with Auto -Burnishing | 4L | 14 Form-A (no monitoring) Latching outputs | 67 | 8 Form-A (no monitoring) outputs | 6A | 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 contact inputs | 6B | 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 contact inputs | 6C | 8 Form-C outputs | 6D | 16 contact inputs | 6E | 4 Form-C outputs, 8 contact inputs | 6F | 8 Fast Form-C outputs | 6G | 4 Form -A (voltage with optional current) outputs, 8 contact inputs | 6H | 6 Form-A (voltage wit h optional current) outputs, 4 contact inputs | 6K | 4 Form-C and 4 Fast Form-C outputs | 6L | 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 contact inputs | 6M | 2 Form-A (current with optiona l voltage) and 4 Form-C outputs, 4 contact inputs | 6N | 4 Form-A (current with optional voltage) outputs, 8 contact inputs | 6P | 6 Form-A (current with optional voltage) outputs, 4 contact inputs | 6R | 2 Form-A (no monitoring) and 2 Form-C outputs, 8 contact inputs | 6S | 2 Form-A (no monitoring) and 4 Form-C outputs, 4 contact inputs | 6T | 4 Form-A (no monitoring ) outputs, 8 contact inputs | 6U | 6 Form-A (no monitoring) outputs, 4 contact inputs | 6V | 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 contact inputs | 8L | Standard 4CT/4VT with enhanced diagnostics | 8N | Standard 8CT with enhanced diagnostics | 8R | Sensit ive Ground 8CT with enhanced diagnostics | 8Z * | HI-Z 4CT
| 2B | C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode
GE Multilin F60 Feeder Protection System 2-15
Page 46
2.2 ORDER CODES 2 PRODUCT DESCRIPTION
Table 2–9: ORDER CODES FOR REPLACEMENT MODULES, VERTICAL UNITS
UR - ** - *
| 2E | Bi-phase, single channel | 2F | Bi-phase, dual channel | 2G | IEEE C 37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel | 2H | IEEE C37.94 , 820 nm, 128 kbps, multimode, LED, 2 Channels | 2I | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser | 2J | Channel 1 - IEEE C37.94, multimode, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser | 72 | 1550 nm, single-mode, Laser, 1 Channel | 73 | 1550 nm, single-mode, Laser, 2 Channel | 74 | Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser | 75 | Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser | 76 | IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel | 77 | IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels | 7A | 820 nm, multimode, LED, 1 Channel | 7B | 1300 nm, multimode, LED, 1 Channel
2
TRANSDUCER INPUTS/OUTPUTS
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
| 7C | 1300 nm, single-mode, EL ED, 1 Channel | 7D | 1300 nm, single-mode, Laser, 1 Channel | 7E | Channel 1 - G.703; Channel 2 - 820 nm, multimode | 7F | Channel 1 - G.703; Channel 2 - 1300 nm, multimode | 7G | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED | 7H | 820 nm, multimode, LED, 2 Channels | 7I | 1300 nm, multimode, LED, 2 Channels | 7J | 1300 nm, single-mode, ELED, 2 Channels | 7K | 1300 nm, single-mode, Laser, 2 Channels | 7L | Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED | 7M | Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED | 7N | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED | 7P | Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser | 7Q | Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser | 7R | G.703, 1 Channel | 7S | G.703, 2 Channels | 7T | RS422, 1 Channel | 7W | RS422, 2 Chan nels | 5A | 4 DCmA inputs, 4 DCmA ou tputs (only one 5A module is allowed) | 5C | 8 RTD inputs | 5D | 4 RTD inputs, 4 DC mA outputs (only one 5D module is allowed) | 5E | 4 DCmA inputs, 4 RTD inputs | 5F | 8 DCmA inputs
2-16 F60 Feeder Protection System GE Multilin
Page 47
2 PRODUCT DESCRIPTION 2.3 SIGNAL PROCESSING
From
CT/VT
U
I
Analog Inputs
Analog low-
pass filter
Analog-to-
Digital
Converter
A
Digital band-
pass filter
DSP module
Phasor
estimation
½ cycle
Fourier
1 cycle
Fourier
RMS
values
Fundamen
tal freq.
Phasors,
Seq. com-
ponents
D
Sampling
frequency
CPU module
I> Z< U<
Protection algorithms
IRIG-B IEEE
1588
SNTP
Tracking
frequency
selection,
estimation
Accurate
Real-Time
clock
Synchrophasors
calculations
Serial ports
Ethernet ports
Communi-
cation
protocols
Control
elements,
monitoring
elements, FlexLogic,
Aggregation, post-filtering
Contact Inputs
module
HMI
Ddebounce
filtering
Optoisolated
Analog Inputs
module
DCmA, RTD
A
D
Inter-relay
comms
module
Channel
monitoring
CRC check
G.703, RS-422,
C37.94, direct fiber
Contact Outputs
module
Et
h
e
r
n
e
t
Serial
PMU (IEEE C37.118,
IEC 61850-90-5)
IEC 61850 (GOOSE,
MMS Server)
DNP, Modbus,
IEC60870
Comtrade, data
logger
Events
Inter-relay
comms module
Frequency
T
Analog Outputs
module
Time stamping
Synchro­phasors filtering
859740A1.vsd
2± 260 V()

2.3SIGNAL PROCESSING 2.3.1 UR SIGNAL PROCESSING

The UR series relays are microprocessor-based protective relays that are designed to measure power system conditions directly via CT and PT inputs and via other sources of information, such as analog inputs, communications inputs and con­tact inputs. The following figure shows the overall signal processing in URs.
An analog low pass anti-aliasing filter with a 3 dB corner frequency is set at 2.4 kHz and is used for current and voltage analog filtering as well as signal conditioning. The same filtering is applied for phase, ground currents, phase-to-phase (when applicable), and auxiliary voltages. The 2.4 kHz cut-off frequency applies to both 50 Hz and 60 Hz applications and fixed in the hardware, and thus is not dependent on the system nominal frequency setting.
2
The UR samples its AC signals at 64 samples per cycle, that is, at 3840 Hz in 60 Hz systems, and 3200 Hz in 50 Hz sys­tems. The sampling rate is dynamically adjusted to the actual system frequency by an accurate and fast frequency tracking system.
The A/D converter has the following ranges of AC signals: Voltages:
Figure 2–3: UR SIGNAL PROCESSING
Currents:
GE Multilin F60 Feeder Protection System 2-17
(EQ 2.1)
Page 48
2.3 SIGNAL PROCESSING 2 PRODUCT DESCRIPTION
2± 46rated A()
I
RMS t()
1
T
---
i
2
t() td
tT–()
t
=
Current harmonics are estimated based on raw samples with the use of the full-cycle Fourier filter. Harmonics 2nd through 25th are estimated.
True RMS value for the current is calculated on a per-phase basis. The true RMS can be used for demand recording or as an input signal to Time Overcurrent function, if the latter is intended for thermal protection. The true RMS is calculated as per the widely accepted definition:
2
RMS values include harmonics, inter-harmonics, DC components, and so on, along with fundamental frequency values. The true RMS value reflects thermal effects of the current and is used for the thermal related monitoring and protection functions.
Protection and control functions respond to phasors of the fundamental and/or harmonic frequency components (magni­tudes and angles), with an exception for some functions that have an option for RMS or fundamental measurements, or some function responding to RMS only. This type of response is explained typically in each element's section in the instruc­tion manual.
Currents are pre-filtered using a Finite Impulse Response (FIR) digital filter. The filter is designed to reject DC components and low-frequency distortions, without amplifying high-frequency noise. This filter is referred to as a modified MIMIC filter, which provides excellent filtering and overall balance between speed and accuracy of filtering. The filter is cascaded with the full-cycle Fourier filter for the current phasor estimation.
Voltages are pre-filtered using a patented Finite Impulse Response (FIR) digital filter. The filter has been optimized to reject voltage transformers specific distortions, such as Capacitive Voltage Transformer (CVT) noise and high-frequency oscilla­tory components. The filter is cascaded with the half-cycle Fourier filter for the voltage phasor estimation.
The URs measure power system frequency using the Clarke transformation by estimating the period of the waveform from two consecutive zero-crossings in the same direction (negative-to-positive). Voltage or current samples are pre-filtered using a Finite Impulse Response (FIR) digital filter to remove high frequency noise contained in the signal. The period is used after several security conditions are met, such as true RMS signal must be above 6% nominal for a certain time and others. If these security conditions are not met, the last valid measurement is used for a specific time after which the UR reverts to nominal system frequency.
Synchrophasors are calculated using a patented convolution integral algorithm. This algorithm allows use of the same time stamped samples, which are used for protection and taken at the same sampling frequency. This allows URs to use one sampling clock for both protection algorithms and synchrophasors.
Synchrophasors on firmware versions 7.23 and up have been tested and certified to meet IEEE C.37.118-2011 and C.37.118.1a-2014 standards for both metering and protection classes with outputs available up to 60 synchrophasors per second for the metering class and 120 synchrophasors per second for the protection class. Synchrophasors measurement are also available via IEC 61850-90-5 protocol.
Contact inputs threshold is settable in the firmware with 17, 33, 84, 166 VDC settings available. Inputs are scanned every
0.5 ms and can be conditioned for the critical applications, using debounce time timer, settable from 0.0 ms to 16.0 ms. Contact inputs with auto-burnishing are available as well, when external contacts are exposed to the contamination in a harsh industrial environment.
All measured values are available in the UR metering section on the front panel and via communications protocols. Mea­sured analog values and binary signals can be captured in COMTRADE format with sampling rates from 8 to 64 samples per power cycle. Analog values can be captured with Data Logger, allowing much slower rates extended over long period of time.
Other advanced UR order code options are available to support IEC 61850 Ed2.0 (including fast GOOSE, MMS server, 61850 services, ICD/CID/IID files, and so on), IEEE 1588 (IEEE C37.238 power profile) based time synchronization, Cyber­Sentry (advanced cyber security), the Parallel Redundancy Protocol (PRP), IEC 60870-5-103, and so on.
(EQ 2.2)
(EQ 2.3)
2-18 F60 Feeder Protection System GE Multilin
Page 49
2 PRODUCT DESCRIPTION 2.4 SPECIFICATIONS
NOTE
2.4SPECIFICATIONSSPECIFICATIONS ARE SUBJECT TO CHANGE WITHOUT NOTICE

2.4.1 PROTECTION ELEMENTS

The operating times include the activation time of a trip rated form-A output contact unless otherwise indicated. FlexLogic operands of a given element are 4 ms faster. Take this into account when using FlexLogic to interconnect with other protection or control elements of the relay, building FlexLogic equations, or interfacing with other IEDs or power system devices via communications or different output contacts. If not specified, the operate times given here are for a 60 Hz system at nominal system frequency. Operate times for a 50 Hz system are 1.2 times longer.
RESTRICTED GROUND FAULT
Pickup: 0.005 to 30.000 pu in steps of 0.001 Dropout: 97 to 98% of pickup Level accuracy:
0.1 to 2.0 x CT rating: ±0.5% of reading or ±1% of rated (which­ever is greater)
>2.0 x CT rating ±1.5% of reading Slope: 0 to 100% in steps of 1% Pickup delay: 0 to 600.00 s in steps of 0.01 Dropout delay: 0 to 600.00 s in steps of 0.01 Operate time: <1 power system cycle
PHASE/NEUTRAL/GROUND TOC
Current: Phasor or RMS Pickup level: 0.000 to 30.000 pu in steps of 0.001 Dropout level: 97% to 98% of pickup Level accuracy:
0.1 to 2.0 × CT: ±0.5% of reading or ±0.4% of rated (whichever is greater)
> 2.0 × CT: ±1.5% of reading > 2.0 × CT rating
Curve shapes: IEEE Moderately/Very/Extremely
Inverse; IEC (and BS) A/B/C and Short Inverse; GE IAC Inverse, Short/Very/ Extremely Inverse; I (programmable); Definite Time (0.01 s base curve)
Curve multiplier: Time Dial = 0.00 to 600.00 in steps of
0.01
Reset type: Instantaneous/Timed (per IEEE) Curve timing accuracy at 1.03 to 20 x pickup: ±3.5% of operate time or ±½ cycle
(whichever is greater) from pickup to operate
Voltage restraint: modifies pickup current for voltage in the
range of 0.1<V<0.9 VT Nominal in a fixed linear relationship
2
t; FlexCurves™
PHASE/NEUTRAL/GROUND IOC
Pickup level: 0.000 to 30.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy:
0.1 to 2.0 × CT rating: ±0.5% of reading or ±0.4% of rated (whichever is greater)
> 2.0 × CT rating ±1.5% of reading Overreach: <2% Pickup delay: 0.00 to 600.00 s in steps of 0.01 Reset delay: 0.00 to 600.00 s in steps of 0.01 Operate time: <16 ms at 3 × pickup at 60 Hz
Timer accuracy: ±3% of operate time or ±1/4 cycle
(Phase/Ground IOC) <20 ms at 3 × pickup at 60 Hz (Neutral IOC)
(whichever is greater)
NEGATIVE SEQUENCE TOC
Pickup level: 0.000 to 30.000 pu in steps of 0.001 Dropout level: 97% to 98% of pickup Level accuracy: ±0.5% of reading or ±0.4% of rated
(whichever is greater) from 0.1 to 2.0 x CT rating ±1.5% of reading > 2.0 x CT rating
Curve shapes: IEEE Moderately/Very/Extremely
Inverse; IEC (and BS) A/B/C and Short Inverse; GE IAC Inverse, Short/Very/ Extremely Inverse; I (programmable); Definite Time (0.01 s
base curve) Curve multiplier (Time dial): 0.00 to 600.00 in steps of 0.01 Reset type: Instantaneous/Timed (per IEEE) and Lin-
ear Curve timing accuracy at 1.03 to 20 x pickup: ±3.5% of operate time or ±½ cycle
(whichever is greater) from pickup to
operate
2
t; FlexCurves™
NEGATIVE SEQUENCE IOC
Pickup level: 0.000 to 30.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: 0.1 to 2.0 × CT rating: ±0.5% of reading
Overreach: <2% Pickup delay: 0.00 to 600.00 s in steps of 0.01 Reset delay: 0.00 to 600.00 s in steps of 0.01 Operate time: <20 ms at 3 × pickup at 60 Hz Timer accuracy: ±3% of operate time or ±1/4 cycle
or ±0.4% of rated (whichever is greater);
> 2.0 × CT rating: ±1.5% of reading
(whichever is greater)
2
GE Multilin F60 Feeder Protection System 2-19
Page 50
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
PHASE DIRECTIONAL OVERCURRENT
Relay connection: 90° (quadrature) Quadrature voltage: ABC phase seq.: phase A (V
B (V
), phase C (VAB); ACB phase
CA
seq.: phase A (V
phase C (V Polarizing voltage threshold: 0.000 to 3.000 pu in steps of 0.001 Current sensitivity threshold: 0.05 pu
2
Characteristic angle: 0 to 359 Angle accuracy: ±2° Operation time (FlexLogic operands):
° in steps of 1
Tripping (reverse load, forward fault):<
12 ms, typically
Blocking (forward load, reverse fault):<
8 ms, typically
BA
CB
)
), phase B (VAC),
NEUTRAL DIRECTIONAL OVERCURRENT
Directionality: Co-existing forward and reverse Polarizing: Voltage, Current, Dual, Dual-V, Dual-I Polarizing voltage: V_0 or VX Polarizing current: IG Operating current: I_0 Level sensing: 3 × (|I_0| – K × |I_1|), IG Restraint, K: 0.000 to 0.500 in steps of 0.001 Characteristic angle: –90 to 90° in steps of 1 Limit angle: 40 to 90° in steps of 1, independent for
forward and reverse Angle accuracy: ±2° Offset impedance: 0.00 to 250.00 Ω in steps of 0.01 Pickup level: 0.002 to 30.000 pu in steps of 0.01 Dropout level: 97 to 98% Operation time: <16 ms at 3 × pickup at 60 Hz
NEGATIVE SEQUENCE DIRECTIONAL OC
Directionality: Co-existing forward and reverse Polarizing: Voltage Polarizing voltage: V_2 Operating current: I_2 Level sensing:
Zero-sequence:|I_0| – K × |I_1|
Negative-sequence:|I_2| – K × |I_1| Restraint, K: 0.000 to 0.500 in steps of 0.001 Characteristic angle: 0 to 90° in steps of 1 Limit angle: 40 to 90° in steps of 1, independent for
Angle accuracy: ±2° Offset impedance: 0.00 to 250.00 Ω in steps of 0.01 Pickup level: 0.015 to 30.000 pu in steps of 0.01 Dropout level: 97 to 98% Operation time: <16 ms at 3 × pickup at 60 Hz
forward and reverse
), phase
BC
WATTMETRIC ZERO-SEQUENCE DIRECTIONAL
Measured power: zero-sequence Number of elements: 2 Characteristic angle: 0 to 360° in steps of 1 Minimum power: 0.001 to 1.200 pu in steps of 0.001 Pickup level accuracy: ±1% or ±0.0025 pu, whichever is greater Hysteresis: 3% or 0.001 pu, whichever is greater Pickup delay: definite time (0 to 600.00 s in steps of
0.01), inverse time, or FlexCurve Inverse time multiplier: 0.01 to 2.00 s in steps of 0.01 Curve timing accuracy: ±3.5% of operate time or ±1 cycle
(whichever is greater) from pickup to operate
Operate time: <30 ms at 60 Hz
SENSITIVE DIRECTIONAL POWER
Measured power: 3-phase, true RMS Number of stages: 2 Characteristic angle: 0 to 359° in steps of 1 Calibration angle: 0.00 to 0.95° in steps of 0.05 Minimum power: –1.200 to 1.200 pu in steps of 0.001 Pickup level accuracy: ±1% or ±0.001 pu, whichever is greater Hysteresis: 2% or 0.001 pu, whichever is greater Pickup delay: 0 to 600.00 s in steps of 0.01 Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time: <50 ms
PHASE UNDERVOLTAGE
Voltage: Phasor only Pickup level: 0.000 to 3.000 pu in steps of 0.001 Dropout level: 102 to 103% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Curve shapes: GE IAV Inverse;
Definite Time (0.1s base curve)
Curve multiplier: Time dial = 0.00 to 600.00 in steps of
0.01 Curve timing accuracy at <0.90 x pickup: ±3.5% of operate time or ±1/2 cycle
(whichever is greater) from pickup to operate
Operate time: <30 ms at 0.9 pickup at 60 Hz for Defi-
nite Time mode
AUXILIARY UNDERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001 Dropout level: 102 to 103% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Curve shapes: GE IAV Inverse, Definite Time Curve multiplier: Time Dial = 0 to 600.00 in steps of 0.01 Curve timing accuracy at <0.90 x pickup: ±3.5% of operate time or ±1/2 cycle
(whichever is greater) from pickup to operate
Operate time: <30 ms at 0.9 pickup at 60 Hz for Defi-
nite Time mode
2-20 F60 Feeder Protection System GE Multilin
Page 51
2 PRODUCT DESCRIPTION 2.4 SPECIFICATIONS
PHASE OVERVOLTAGE
Voltage: Phasor only Pickup level: 0.000 to 3.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0.00 to 600.00 in steps of 0.01 s Operate time: <30 ms at 1.10 × pickup at 60 Hz Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater)
NEUTRAL OVERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0.00 to 600.00 s in steps of 0.01 (definite
time) or user-defined curve Reset delay: 0.00 to 600.00 s in steps of 0.01 Curve timing accuracy at >1.1 x pickup: ±3.5% of operate time or ±1 cycle
(whichever is greater) from pickup to
operate Operate time: <30 ms at 1.10 × pickup at 60 Hz
AUXILIARY OVERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0 to 600.00 s in steps of 0.01 Reset delay: 0 to 600.00 s in steps of 0.01 Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater) Operate time: <30 ms at 1.10 × pickup at 60 Hz
NEGATIVE SEQUENCE OVERVOLTAGE
Pickup level: 0.000 to 1.250 pu in steps of 0.001 Dropout level: 97 to 98% of pickup Level accuracy: ±0.5% of reading from 10 to 208 V Pickup delay: 0 to 600.00 s in steps of 0.01 Reset delay: 0 to 600.00 s in steps of 0.01 Timer accuracy: ±3% of operate time or ±20 ms, which-
ever is greater Operate time: <30 ms at 1.10 × pickup at 60 Hz
UNDERFREQUENCY
Minimum signal: 0.10 to 1.25 pu in steps of 0.01 Pickup level: 20.00 to 65.00 Hz in steps of 0.01 Dropout level: pickup + 0.03 Hz Level accuracy: ±0.001 Hz Time delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater) Operate time: typically 4 cycles at 0.1 Hz/s change
typically 3.5 cycles at 0.3 Hz/s change
typically 3 cycles at 0.5 Hz/s change Typical times are average operate times including variables such
as frequency change instance, test method, etc., and may vary by ±0.5 cycles.
OVERFREQUENCY
Pickup level: 20.00 to 65.00 Hz in steps of 0.01 Dropout level: pickup – 0.03 Hz Level accuracy: ±0.001 Hz Time delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time: typically 4 cycles at 0.1 Hz/s change
Typical times are average operate times including variables such as frequency change instance, test method, etc., and may vary by ±0.5 cycles.
typically 3.5 cycles at 0.3 Hz/s change typically 3 cycles at 0.5 Hz/s change
RATE OF CHANGE OF FREQUENCY
df/dt trend: increasing, decreasing, bi-directional df/dt pickup level: 0.10 to 15.00 Hz/s in steps of 0.01 df/dt dropout level: 96% of pickup df/dt level accuracy: 80 mHz/s or 3.5%, whichever is greater Overvoltage supv.: 0.100 to 3.000 pu in steps of 0.001 Overcurrent supv.: 0.000 to 30.000 pu in steps of 0.001 Pickup delay: 0 to 65.535 s in steps of 0.001 Reset delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater) 95% settling time for df/dt: <24 cycles Operate time: typically 9.5 cycles at 2 × pickup
Typical times are average operate times including variables such as frequency change instance, test method, etc., and may vary by ±0.5 cycles.
typically 8.5 cycles at 3 × pickup
typically 6.5 cycles at 5 × pickup
BREAKER FAILURE
Mode: 1-pole, 3-pole Current supervision: phase, neutral current Current supv. pickup: 0.001 to 30.000 pu in steps of 0.001 Current supv. dropout: 97 to 98% of pickup Current supv. accuracy:
0.1 to 2.0 × CT rating: ±0.75% of reading or ±2% of rated
above 2 × CT rating: ±2.5% of reading
(whichever is greater)
BREAKER ARCING CURRENT
Principle: accumulates breaker duty (I2t) and mea-
Initiation: programmable per phase from any Flex-
Compensation for auxiliary relays: 0 to 65.535 s in steps of 0.001 Alarm threshold: 0 to 50000 kA Fault duration accuracy: 0.25 of a power cycle Availability: 1 per CT bank with a minimum of 2
sures fault duration
Logic operand
2
-cycle in steps of 1
2
GE Multilin F60 Feeder Protection System 2-21
Page 52
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
BREAKER FLASHOVER
Operating quantity: phase current, voltage and voltage differ-
ence Pickup level voltage: 0 to 1.500 pu in steps of 0.001 Dropout level voltage: 97 to 98% of pickup Pickup level current: 0 to 1.500 pu in steps of 0.001 Dropout level current: 97 to 98% of pickup Level accuracy: ±0.5% or ±0.1% of rated, whichever is
2
Pickup delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±42 ms, which-
Operate time: <42 ms at 1.10 × pickup at 60 Hz
greater
ever is greater
BREAKER RESTRIKE
Principle: detection of high-frequency overcurrent
condition ¼ cycle after breaker opens Availability: one per CT/VT module (not including 8Z
modules) Pickup level: 0.1 to 2.00 pu in steps of 0.01 Reset delay: 0.000 to 65.535 s in steps of 0.001
INCIPIENT CABLE FAULT DETECTION
Principle: detection of ½ cycle or less overcurrent
condition during normal load Availability: two per CT/VT module (not including 8Z
modules) Pickup level: 0.1 to 10.00 pu in steps of 0.01 Reset delay: 0.000 to 65.535 s in steps of 0.001 Operating mode: number of counts, counts per time win-
dow
SYNCHROCHECK
Max voltage difference: 0 to 400000 V in steps of 1 Max angle difference: 0 to 100 Max freq. difference: 0.00 to 2.00 Hz in steps of 0.01 Hysteresis for max. freq. diff.: 0.00 to 0.10 Hz in steps of 0.01 Dead source function: None, LV1 & DV2, DV1 & LV2, DV1 or
° in steps of 1
DV2, DV1 xor DV2, DV1 & DV2
(L = Live, D = Dead)
AUTORECLOSURE
Single breaker applications, 3-pole tripping schemes Up to 4 reclose attempts before lockout Independent dead time setting before each shot Possibility of changing protection settings after each shot with
FlexLogic
LOAD ENCROACHMENT
Responds to: Positive-sequence quantities Minimum voltage: 0.000 to 3.000 pu in steps of 0.001 Reach (sec. Ω): 0.02 to 250.00 Ω in steps of 0.01 Impedance accuracy: ±5% Angle: 5 to 50° in steps of 1 Angle accuracy: ±2° Pickup delay: 0 to 65.535 s in steps of 0.001 Reset delay: 0 to 65.535 s in steps of 0.001 Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time: <30 ms at 60 Hz
THERMAL OVERLOAD PROTECTION
Thermal overload curves: IEC 255-8 curve Base current: 0.20 to 3.00 pu in steps of 0.01 Overload (k) factor: 1.00 to 1.20 pu in steps of 0.05 Trip time constant: 0 to 1000 min. in steps of 1 Reset time constant: 0 to 1000 min. in steps of 1 Minimum reset time: 0 to 1000 min. in steps of 1 Timer accuracy (cold curve): ±100 ms or 2%, whichever is greater Timer accuracy (hot curve): ±500 ms or 2%, whichever is greater
< 0.9 × k × Ib and I / (k × Ib) > 1.1
for I
p
TRIP BUS (TRIP WITHOUT FLEXLOGIC)
Number of elements: 6 Number of inputs: 16 Operate time: <2 ms at 60 Hz Timer accuracy: ±3% or 10 ms, whichever is greater

2.4.2 USER-PROGRAMMABLE ELEMENTS

FLEXLOGIC
Programming language: Reverse Polish Notation with graphical
visualization (keypad programmable) Lines of code: 512 Internal variables: 64 Supported operations: NOT, XOR, OR (2 to 16 inputs), AND (2
to 16 inputs), NOR (2 to 16 inputs),
NAND (2 to 16 inputs), latch (reset-domi-
nant), edge detectors, timers Inputs: any logical variable, contact, or virtual
input Number of timers: 32 Pickup delay: 0 to 60000 (ms, sec., min.) in steps of 1 Dropout delay: 0 to 60000 (ms, sec., min.) in steps of 1
FLEXCURVES™
Number: 4 (A through D) Reset points: 40 (0 through 1 of pickup) Operate points: 80 (1 through 20 of pickup) Time delay: 0 to 65535 ms in steps of 1
FLEX STATES
Number: up to 256 logical variables grouped
under 16 Modbus addresses
Programmability: any logical variable, contact, or virtual
input
2-22 F60 Feeder Protection System GE Multilin
Page 53
2 PRODUCT DESCRIPTION 2.4 SPECIFICATIONS
FLEXELEMENTS™
Number of elements: 8 Operating signal: any analog actual value, or two values in
differential mode Operating signal mode: signed or absolute value Operating mode: level, delta Comparator direction: over, under Pickup Level: –90.000 to 90.000 pu in steps of 0.001 Hysteresis: 0.1 to 50.0% in steps of 0.1 Delta dt: 20 ms to 60 days Pickup & dropout delay: 0.000 to 65.535 s in steps of 0.001
NON-VOLATILE LATCHES
Type: set-dominant or reset-dominant Number: 16 (individually programmed) Output: stored in non-volatile memory Execution sequence: as input prior to protection, control, and
FlexLogic
USER-PROGRAMMABLE LEDs
Number: 48 plus trip and alarm Programmability: from any logical variable, contact, or vir-
tual input Reset mode: self-reset or latched
LED TEST
Initiation: from any contact input or user-program-
mable condition Number of tests: 3, interruptible at any time Duration of full test: approximately 3 minutes Test sequence 1: all LEDs on Test sequence 2: all LEDs off, one LED at a time on for 1 s Test sequence 3: all LEDs on, one LED at a time off for 1 s
USER-DEFINABLE DISPLAYS
Number of displays: 16 Lines of display: 2 × 20 alphanumeric characters Parameters: up to 5, any Modbus register addresses Invoking and scrolling: keypad, or any user-programmable con-
dition, including pushbuttons
CONTROL PUSHBUTTONS
Number of pushbuttons: 7 Operation: drive FlexLogic operands
USER-PROGRAMMABLE PUSHBUTTONS (OPTIONAL)
Number of pushbuttons: 12 on standard front panel
16 on enhanced horizontal front panel
6 on enhanced vertical front panel Mode: self-reset, latched Display message: 2 lines of 20 characters each Drop-out timer: 0.00 to 60.00 s in steps of 0.05 Autoreset timer: 0.2 to 600.0 s in steps of 0.1 Hold timer: 0.0 to 10.0 s in steps of 0.1
SELECTOR SWITCH
Number of elements: 2 Upper position limit: 1 to 7 in steps of 1 Selecting mode: time-out or acknowledge Time-out timer: 3.0 to 60.0 s in steps of 0.1 Control inputs: step-up and 3-bit Power-up mode: restore from non-volatile memory or syn-
chronize to a 3-bit control input or synch/
restore mode
DIGITAL ELEMENTS
Number of elements: 48 Operating signal: any FlexLogic operand Pickup delay: 0.000 to 999999.999 s in steps of 0.001 Dropout delay: 0.000 to 999999.999 s in steps of 0.001 Timing accuracy: ±3% or ±4 ms, whichever is greater
2

2.4.3 MONITORING

OSCILLOGRAPHY
Maximum records: 64 Sampling rate: 64 samples per power cycle Triggers: any element pickup, dropout, or operate;
contact input change of state; contact output change of state; FlexLogic equa­tion
Data: AC input channels; element state; con-
tact input state; contact output state
Data storage: in non-volatile memory
EVENT RECORDER
Capacity: 1024 events Time-tag: to 1 microsecond Triggers: any element pickup, dropout, or operate;
contact input change of state; contact output change of state; self-test events
Data storage: in non-volatile memory
DATA LOGGER
Number of channels: 1 to 16 Parameters: any available analog actual value Sampling rate: 15 to 3600000 ms in steps of 1 Trigger: any FlexLogic operand Mode: continuous or triggered Storage capacity: (NN is dependent on memory)
1-second rate:
01 channel for NN days
16 channels for NN days
60-minute rate:
01 channel for NN days 16 channels for NN days
GE Multilin F60 Feeder Protection System 2-23
Page 54
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
FAULT LOCATOR
Method: single-ended Voltage source: wye-connected VTs, delta-connected
VTs and neutral voltage, delta-connected VTs and zero-sequence current (approxi­mation)
Maximum accuracy if: fault resistance is zero or fault currents
from all line terminals are in phase
2
Relay accuracy: ±1.5% (V > 10 V, I > 0.1 pu) Worst-case accuracy:
+ user data
VT
%error
+ user data
CT
%error
Z
Line%error
METHOD RELAY ACCURACY
+ user data
+ see chapter 8
%error
+ (1.5%)
%error
HI-Z
Detections: Arc Suspected, Arc Detected, Downed
Conductor, Phase Identification
RMS CURRENT: PHASE, NEUTRAL, AND GROUND
Accuracy at
0.1 to 2.0 × CT rating: ±0.25% of reading or ±0.1% of rated
> 2.0 × CT rating: ±1.0% of reading
(whichever is greater)
RMS VOLTAGE
Accuracy: ±0.5% of reading from 10 to 208 V
REAL POWER (WATTS)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to
1.2 x VT rating: ±1.0% of reading at –1.0 PF< –0.8 and
0.8 < PF 10
REACTIVE POWER (VARS)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to
1.2 x VT rating: ±1.0% of reading at –0.2 PF 0.2
APPARENT POWER (VA)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to
1.2 x VT rating: ±1.0% of reading
WATT-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading Range: ±0 to 1 × 10 Parameters: three-phase only Update rate: 50 ms
6
MWh
PHASOR MEASUREMENT UNIT
Output format: per IEEE C37.118 or IEC 61850-90-5
standard
Number of channels: 14 synchrophasors, 8 analogs, 16 digi-
TVE (total vector error) <1% Triggering: frequency, voltage, current, power, rate
Reporting rate: 1, 2, 5, 10, 12, 15, 20, 25, 30, 50, or 60
Number of clients: One over TCP/IP port and one over
AC ranges: As indicated in appropriate specifications
Network reporting format: 16-bit integer (for IEEE C37.118) or 32-
Network reporting style: rectangular (real and imaginary for IEEE
Post-filtering: none, 3-point, 5-point, 7-point Calibration: ±5° (angle) and ±5% (magnitude)
tals
of change of frequency, user-defined
times per second for P and M class, and 100 or 120 times per second for P class only
UDP/IP per aggregator
sections
bit IEEE floating point numbers
C37.188) or polar (magnitude and angle) coordinates

2.4.4 METERING

VAR-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading Range: ±0 to 1 × 10 Parameters: three-phase only Update rate: 50 ms
6
Mvarh
CURRENT HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, dis-
Accuracy:
HARMONICS: 1. f
THD: 1. f1 > 0.4pu: (0.25% + 0.035% / harmonic) of
played as a % of f quency phasor) THD: per phase, displayed as a % of f
> 0.4pu: (0.20% + 0.035% / harmonic) of
1
reading or 0.15% of 100%, whichever is greater
2. f
< 0.4pu: as above plus %error of f
1
reading or 0.20% of 100%, whichever is greater
2. f
< 0.4pu: as above plus %error of f
1
(fundamental fre-
1
1
1
1
VOLTAGE HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, dis-
played as a % of f quency phasor) THD: per phase, displayed as a % of f
Accuracy:
HARMONICS: 1. f
THD: 1. f1 > 0.4pu: (0.25% + 0.035% / harmonic) of
> 0.4pu: (0.20% + 0.035% / harmonic) of
1
reading or 0.15% of 100%, whichever is greater
2. f
< 0.4pu: as above plus %error of f
1
reading or 0.20% of 100%, whichever is greater
2. f
< 0.4pu: as above plus %error of f
1
(fundamental fre-
1
1
1
1
2-24 F60 Feeder Protection System GE Multilin
Page 55
2 PRODUCT DESCRIPTION 2.4 SPECIFICATIONS
FREQUENCY
Accuracy at
V = 0.8 to 1.2 pu: ±0.001 Hz (when voltage signal is used
for frequency measurement) I = 0.1 to 0.25 pu: ±0.005 Hz I > 0.25 pu: ±0.02 Hz (when current signal is used for
frequency measurement)
AC CURRENT
CT rated primary: 1 to 50000 A CT rated secondary: 1 A or 5 A by connection Relay burden: < 0.2 VA at rated secondary Conversion range:
Standard CT: 0.02 to 46 × CT rating RMS symmetrical Sensitive Ground CT module:
0.002 to 4.6 × CT rating RMS symmetrical
HI-Z CT module: 0.002 to 4.6 × CT rating RMS symmetri-
cal
Current withstand: 20 ms at 250 times rated
1 sec at 100 times rated
continuous 4xInom
Short circuit rating:150000 RMS sym-
metrical amperes, 250 V maximum (pri-
mary current to external CT)
AC VOLTAGE
VT rated secondary: 50.0 to 240.0 V VT ratio: 1.00 to 24000.00 Relay burden: < 0.25 VA at 120 V Conversion range: 1 to 275 V Voltage withstand: continuous at 260 V to neutral
1 min/hr at 420 V to neutral
FREQUENCY
Nominal frequency setting:25 to 60 Hz Sampling frequency: 64 samples per power cycle Tracking frequency range:20 to 70 Hz
CONTACT INPUTS
Dry contacts: 1000 Ω maximum Wet contacts: 300 V DC maximum Selectable thresholds: 17 V, 33 V, 84 V, 166 V Tolerance: ±10% Contacts per common return: 4 Recognition time: < 1 ms Debounce time: 0.0 to 16.0 ms in steps of 0.5 Continuous current draw:4 mA (when energized)
DEMAND
Measurements: Phases A, B, and C present and maxi-
mum measured currents 3-Phase Power (P, Q, and S) present and maximum measured currents
Accuracy: ±2.0%

2.4.5 INPUTS

CONTACT INPUTS WITH AUTO-BURNISHING
Dry contacts: 1000 Ω maximum Wet contacts: 300 V DC maximum Selectable thresholds: 17 V, 33 V, 84 V, 166 V Tolerance: ±10% Contacts per common return: 2 Recognition time: < 1 ms Debounce time: 0.0 to 16.0 ms in steps of 0.5 Continuous current draw:4 mA (when energized) Auto-burnish impulse current: 50 to 70 mA Duration of auto-burnish impulse: 25 to 50 ms
DCMA INPUTS
Current input (mA DC): 0 to –1, 0 to +1, –1 to +1, 0 to 5, 0 to 10,
0 to 20, 4 to 20 (programmable) Input impedance: 379 Ω ±10% Conversion range: –1 to + 20 mA DC Accuracy: ±0.2% of full scale Type: Passive
RTD INPUTS
Types (3-wire): 100 Ω Platinum, 100 & 120 Ω Nickel, 10
Ω Copper
Sensing current: 5 mA Range: –50 to +250°C Accuracy: ±2°C Isolation: 36 V pk-pk
IRIG-B INPUT
IRIG formats accepted: B000…B007, B120…B127 IRIG control bits: IEEE Std C37.118.1-2011 Amplitude modulation: 1 to 10 V pk-pk DC shift: TTL–Compatible Input impedance: 50 kΩ Isolation: 2 kV
REMOTE INPUTS (IEC 61850 GSSE/GOOSE)
Input points: 32, configured from 64 incoming bit pairs Remote devices: 16 Default states on loss of comms.: On, Off, Latest/Off, Latest/On Remote DPS inputs: 5
2
GE Multilin F60 Feeder Protection System 2-25
Page 56
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
DIRECT INPUTS
Input points: 32 Remote devices: 16 Default states on loss of comms.: On, Off, Latest/Off, Latest/On Ring configuration: Yes, No Data rate: 64 or 128 kbps CRC: 32-bit CRC alarm:
2
Responding to: Rate of messages failing the CRC Monitoring message count: 10 to 10000 in steps of 1 Alarm threshold: 1 to 1000 in steps of 1
Unreturned message alarm:
Responding to: Rate of unreturned messages in the ring
configuration Monitoring message count: 10 to 10000 in steps of 1 Alarm threshold: 1 to 1000 in steps of 1
LOW RANGE
Nominal DC voltage: 24 to 48 V Minimum DC voltage: 20 V Maximum DC voltage: 60 V for RL power supply module (obso-
lete), 75 V for SL power supply module
Voltage loss hold-up: 200 ms duration at maximum load NOTE: Low range is DC only.
HIGH RANGE
Nominal DC voltage: 125 to 250 V Minimum DC voltage: 88 V Maximum DC voltage: 300 V Nominal AC voltage: 100 to 240 V at 50/60 Hz Minimum AC voltage: 88 V at 25 to 100 Hz Maximum AC voltage: 265 V at 25 to 100 Hz Voltage loss hold-up: 200 ms duration at maximum load
TELEPROTECTION
Input points: 16 Remote devices: 3 Default states on loss of comms.: On, Off, Latest/Off, Latest/On Ring configuration: No Data rate: 64 or 128 kbps CRC: 32-bit

2.4.6 POWER SUPPLY

ALL RANGES
Volt withstand: 2 × Highest Nominal Voltage for 10 ms Power consumption: typical = 15 to 20 W/VA
maximum = 45 W/VA contact factory for exact order code con­sumption
INTERNAL FUSE
RATINGS
Low range power supply: 8 A / 250 V High range power supply: 4 A / 250 V
INTERRUPTING CAPACITY
AC: 100 000 A RMS symmetrical DC: 10 000 A

2.4.7 OUTPUTS

FORM-A RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90 Carry continuous: 6 A Break (DC inductive, L/R = 40 ms):
VOLTAGE CURRENT
24 V 1 A
48 V 0.5 A 125 V 0.3 A 250 V 0.2 A
Operate time: < 4 ms Contact material: silver alloy
LATCHING RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90 Carry continuous: 6 A as per IEEE C37.90 Break (DC resistive as per IEC61810-1):
VOLTAGE CURRENT
24 V 6 A
48 V 1.6 A 125 V 0.4 A 250 V 0.2 A
Operate time: < 4 ms Contact material: silver alloy Control: separate operate and reset inputs Control mode: operate-dominant or reset-dominant
FORM-A VOLTAGE MONITOR
Applicable voltage: approx. 15 to 250 V DC Trickle current: approx. 1 to 2.5 mA
FORM-A CURRENT MONITOR
Threshold current: approx. 80 to 100 mA
2-26 F60 Feeder Protection System GE Multilin
Page 57
2 PRODUCT DESCRIPTION 2.4 SPECIFICATIONS
FORM-C AND CRITICAL FAILURE RELAY
Make and carry for 0.2 s: 30 A as per ANSI C37.90 Carry continuous: 8 A Break (DC inductive, L/R = 40 ms):
VOLTAGE CURRENT
24 V 1 A
48 V 0.5 A 125 V 0.3 A 250 V 0.2 A
Operate time: < 8 ms Contact material: silver alloy
FAST FORM-C RELAY
Make and carry: 0.1 A max. (resistive load) Minimum load impedance:
INPUT
VOLTAGE
250 V DC 20 KΩ 50 KΩ 120 V DC 5 KΩ 2 KΩ
48 V DC 2 KΩ 2 KΩ 24 V DC 2 KΩ 2 KΩ
Note: values for 24 V and 48 V are the same due to a required 95% voltage drop across the load impedance.
2 W RESISTOR 1 W RESISTOR
Operate time: < 0.6 ms Internal Limiting Resistor: 100 Ω, 2 W
IMPEDANCE
SOLID-STATE OUTPUT RELAY
Operate and release time: <100 µs Maximum voltage: 265 V DC Maximum leakage current in off state (excluding voltage monitor circuit current): 100 µA Maximum continuous current: 5 A at 45°C; 4 A at 65°C Make and carry:
for 0.2 s: 30 A as per ANSI C37.90 for 0.03 s 300 A
Breaking capacity:
Operations/ interval
Break capability (0 to 250 V DC)
UL508 Utility
5000 ops /
1 s-On, 9 s-Off
1000 ops /
0.5 s-On, 0.5 s-Off
3.2 A
L/R = 10 ms
1.6 A
L/R = 20 ms
0.8 A
L/R = 40 ms
application
(autoreclose
scheme)
5ops/
0.2 s-On,
0.2 s-Off within 1
minute
10 A
L/R = 40 ms
Industrial
application
10000 ops /
0.2 s-On, 30 s-Off
10 A
L/R = 40 ms
CONTROL POWER EXTERNAL OUTPUT (FOR DRY CONTACT INPUT)
Capacity: 100 mA DC at 48 V DC Isolation: ±300 Vpk
REMOTE OUTPUTS (IEC 61850 GSSE/GOOSE)
Standard output points: 32 User output points: 32
DIRECT OUTPUTS
Output points: 32
DCMA OUTPUTS
Range: –1 to 1 mA, 0 to 1 mA, 4 to 20 mA Max. load resistance: 12 kΩ for –1 to 1 mA range
12 kΩ for 0 to 1 mA range 600 Ω for 4 to 20 mA range
Accuracy: ±0.75% of full-scale for 0 to 1 mA range
99% Settling time to a step change: 100 ms Isolation: 1.5 kV Driving signal: any FlexAnalog quantity Upper and lower limit for the driving signal: –90 to 90 pu in steps of
±0.5% of full-scale for –1 to 1 mA range ±0.75% of full-scale for 0 to 20 mA range
0.001
2
GE Multilin F60 Feeder Protection System 2-27
Page 58
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
NOTE

2.4.8 COMMUNICATION PROTOCOLS

RS232
Front port: 19.2 kbps, Modbus RTU
RS485
1 rear port: Up to 115 kbps, Modbus RTU, DNP 3,
Typical distance: 1200 m
2
Isolation: 2 kV, isolated together at 36 Vpk
IEC 60870-5-103
FIBER ETHERNET PORT
PARAMETER FIBER TYPE
100 MB MULTI-
MODE
Wavelength 1310 nm Connector LC Transmit power –20 dBm Receiver sensitivity –30 dBm Power budget 10 dB Maximum input
power Typical distance 2 km Full duplex yes Redundancy yes
–14 dBm
ETHERNET (10/100 MB TWISTED PAIR)
Modes: 10 MB, 10/100 MB (auto-detect) Connector: RJ45
SIMPLE NETWORK TIME PROTOCOL (SNTP)
clock synchronization error: <10 ms (typical)
PRECISION TIME PROTOCOL (PTP)
PTP IEEE Std 1588 2008 (version 2) Power Profile (PP) per IEEE Standard PC37.238TM2011 Slave-only ordinary clock Peer delay measurement mechanism
PARALLEL REDUNDANCY PROTOCOL (PRP) (IEC 62439-3 CLAUSE 4, 2012)
Ethernet ports used: 2 and 3 Networks supported: 10/100 MB Ethernet
OTHER
TFTP, HTTP, IEC 60870-5-104, Ethernet Global Data (EGD)
SHIELDED TWISTED-PAIR INTERFACE OPTIONS
INTERFACE TYPE TYPICAL DISTANCE
RS422 1200 m G.703 100 m
RS422 distance is based on transmitter power and does not take into consideration the clock source provided by the user.
LINK POWER BUDGET AND MAXIMUM OPTICAL INPUT POWER

2.4.9 INTER-RELAY COMMUNICATIONS

2-28 F60 Feeder Protection System GE Multilin
Page 59
2 PRODUCT DESCRIPTION 2.4 SPECIFICATIONS
NOTE
NOTE
The following specifications apply to filter interface modules implemented from January 2012.
EMITTER, FIBER TYPE
820 nm, Multimode 62.5/125 μm -16 dBm -32 dBm 16 dBm -8 dBm
1300 nm, Multimode
1300 nm, Single mode
1300 nm Laser, Single mode
1550 nm Laser, Single mode
CABLE TYPE
50/125 μm -20 dBm 12 dBm
62.5/125 μm -16 dBm -32 dBm 16 dBm -8 dBm
50/125 μm -20 dBm 12 dBm
9/125 μm -15 dBm -32 dBm 17 dBm -8 dBm
9/125 μm 0 dBm -34 dBm 34 dBm -8 dBm
9/125 μm 5 dBm -34 dBm 39 dBm -10 dBm
TRANSMIT POWER
RECEIVED SENSITIVITY
POWER BUDGET
MAXIMUM OPTICAL INPUT POWER
The following specifications apply to filter interface modules implemented before January 2012.
EMITTER, FIBER TYPE
820 nm LED, Multimode
1300 nm LED, Multimode
1300 nm ELED, Single mode
1300 nm Laser, Single mode
1550 nm Laser, Single mode
TRANSMIT POWER
–20 dBm –30 dBm 10 dB –7.6 dBm
–21 dBm –30 dBm 9 dB –11 dBm
–23 dBm –32 dBm 9 dB –14 dBm
–1 dBm –30 dBm 29 dB –14 dBm
+5 dBm –30 dBm 35 dB –14 dBm
RECEIVED SENSITIVITY
POWER BUDGET
MAX. OPTICAL INPUT POWER
2
These power budgets are calculated from the manu­facturer’s worst-case transmitter power and worst case receiver sensitivity.
The power budgets for the 1300 nm ELED are calcu­lated from the manufacturer's transmitter power and receiver sensitivity at ambient temperature. At
EMITTER TYPE CABLE
820 nm LED, multimode
1300 nm LED, multimode
1300 nm ELED, single mode
1300 nm Laser, single mode
1550 nm Laser, single mode
TYPE
62.5/125 μmST 1.65 km2 km 50/125 μmST1.65 km2 km
62.5/125 μm ST 4 km 5 km 50/125 μm ST 4 km 5 km 9/125 μm ST 11.4 km 20 km
9/125 μm ST 64 km 65 km
9/125 μm ST 105 km 125 km
CONNECTOR
TYPE
extreme temperatures these values deviate based on com­ponent tolerance. On average, the output power decreases as the temperature is increased by a factor 1dB / 5°C.
TYPICAL LINK DISTANCE
TYPICAL DISTANCE
BEFORE
JANUARY
2012
FROM
JANUARY
2012
GE Multilin F60 Feeder Protection System 2-29
Page 60
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
NOTE
Typical distances listed are based on the follow­ing assumptions for system loss. As actual losses vary from one installation to another, the distance covered by your system may vary.
CONNECTOR LOSSES (TOTAL OF BOTH ENDS)
ST connector 0.7 dB (each)
2
FIBER LOSSES
820 nm multimode 3 dB/km 1300 nm multimode 1 dB/km 1300 nm single mode 0.35 dB/km 1550 nm single mode 0.25 dB/km Splice losses: One splice every 2 km,
at 0.05 dB loss per splice.
SYSTEM MARGIN
3 dB additional loss added to calculations to compensate for all other losses.
AMBIENT TEMPERATURES
Storage temperature: –40 to 85°C Operating temperature: –40 to 60°C; the LCD contrast can be
impaired at temperatures less than – 20°C
HUMIDITY
Humidity: operating up to 95% (non-condensing) at
55°C (as per IEC60068-2-30 variant 1, 6 days).
Compensated difference in transmitting and receiving (channel asymmetry) channel delays using GPS satellite clock: 10 ms

2.4.10 ENVIRONMENTAL

OTHER
Altitude: 2000 m (maximum) Pollution degree: II Overvoltage category: II Ingress protection: IP20 front, IP10 back Noise: 0 dB
2-30 F60 Feeder Protection System GE Multilin
Page 61
2 PRODUCT DESCRIPTION 2.4 SPECIFICATIONS

2.4.11 TYPE TESTS

F60 TYPE TESTS
TEST REFERENCE STANDARD TEST LEVEL
Dielectric voltage withstand EN 60255-5 2.2 kV Impulse voltage withstand EN 60255-5 5 kV Damped oscillatory IEC 61000-4-18 / IEC 60255-22-1 2.5 kV CM, 1 kV DM Electrostatic discharge EN 61000-4-2 / IEC 60255-22-2 Level 3 RF immunity EN 61000-4-3 / IEC 60255-22-3 Level 3 Fast transient disturbance EN 61000-4-4 / IEC 60255-22-4 Class A and B Surge immunity EN 61000-4-5 / IEC 60255-22-5 Level 3 and 4 Conducted RF immunity EN 61000-4-6 / IEC 60255-22-6 Level 3 Power frequency immunity EN 61000-4-7 / IEC 60255-22-7 Class A and B Voltage interruption and ripple DC IEC 60255-11 12% ripple, 200 ms interrupts Radiated and conducted emissions CISPR11 / CISPR22 / IEC 60255-25 Class A Sinusoidal vibration IEC 60255-21-1 Class 1 Shock and bump IEC 60255-21-2 Class 1 Seismic IEC 60255-21-3 Class 1 Power magnetic immunity IEC 61000-4-8 Level 5 Pulse magnetic immunity IEC 61000-4-9 Level 4 Damped magnetic immunity IEC 61000-4-10 Level 4 Voltage dip and interruption IEC 61000-4-11 0, 40, 70, 80% dips; 250 / 300 cycle interrupts Damped oscillatory IEC 61000-4-12 2.5 kV CM, 1 kV DM Conducted RF immunity, 0 to 150 kHz IEC 61000-4-16 Level 4 Voltage ripple IEC 61000-4-17 15% ripple Ingress protection IEC 60529 IP20 front, IP10 back Cold IEC 60068-2-1 –40°C for 16 hours Hot IEC 60068-2-2 85°C for 16 hours Humidity IEC 60068-2-30 6 days, variant 1 Damped oscillatory IEEE/ANSI C37.90.1 2.5 kV, 1 MHz RF immunity IEEE/ANSI C37.90.2 20 V/m, 80 MHz to 1 GHz Safety UL 508 e83849 NKCR Safety UL C22.2-14 e83849 NKCR7 Safety UL 1053 e83849 NKCR Safety IEC 60255-27 Insulation: class 1, Pollution degree: 2, Over
voltage cat II
2

2.4.12 PRODUCTION TESTS

THERMAL
Products go through an environmental test based upon an
Accepted Quality Level (AQL) sampling process.
GE Multilin F60 Feeder Protection System 2-31
Page 62
2
NOTICE
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION

2.4.13 APPROVALS

APPROVALS
COMPLIANCE APPLICABLE COUNCIL
CE Low voltage directive EN 60255-5
C-UL-US --- UL 508
DIRECTIVE
EMC directive EN 60255-26 / EN 50263
ACCORDING TO
EN 61000-6-5
UL 1053 C22.2 No. 14

2.4.14 MAINTENANCE

MOUNTING
Attach mounting brackets using 20 inch-pounds (±2 inch-pounds) of torque.
CLEANING
Normally, cleaning is not required; but for situations where dust has accumulated on the faceplate display, a dry cloth can be used.
To avoid deterioration of electrolytic capacitors, power up units that are stored in a de-energized state once per year, for one hour continuously.
2-32 F60 Feeder Protection System GE Multilin
Page 63
3 HARDWARE 3.1 DESCRIPTION
17.56”
[446,02 mm]
9.687”
[246,05 mm]
11.016”
[279,81 mm]
7.460
[189,48 mm
6.960” [176,78 mm]
19.040”
[483,62 mm]
6.995”
[177,67 mm]
842807A1.CDR

3 HARDWARE 3.1DESCRIPTION 3.1.1 PANEL CUTOUT

a) HORIZONTAL UNITS
The F60 Feeder Protection System is available as a 19-inch rack horizontal mount unit with a removable faceplate. The faceplate can be specified as either standard or enhanced at the time of ordering. The enhanced faceplate contains addi­tional user-programmable pushbuttons and LED indicators.
The modular design allows the relay to be easily upgraded or repaired by a qualified service person. The faceplate is hinged to allow easy access to the removable modules, and is itself removable to allow mounting on doors with limited rear depth.
The case dimensions are shown below, along with panel cutout details for panel mounting. When planning the location of your panel cutout, ensure that provision is made for the faceplate to swing open without interference to or from adjacent equipment.
The relay must be mounted such that the faceplate sits semi-flush with the panel or switchgear door, allowing the operator access to the keypad and the RS232 communications port. The relay is secured to the panel with the use of four screws supplied with the relay.
3
Figure 3–1: F60 HORIZONTAL DIMENSIONS (ENHANCED PANEL)
GE Multilin F60 Feeder Protection System 3-1
Page 64
3.1 DESCRIPTION 3 HARDWARE
18.370”
[466,60 mm]
842808A1.CDR
0.280” [7,11 mm] Typ. x 4
4.000”
[101,60 mm]
17.750”
[450,85 mm]
CUT-OUT
19.00”
(482.6 mm)
7.00” (177.8 mm)
Horizontal front view
Horizontal top view (19”, 4 RU)
17.52”
(445.0 mm)
Brackets repositioned for switchgear mounting
10.90” (276.8 mm)
9.80”
(248.9 mm)
8.97”
(227.8 mm)
17.75”
(450.8 mm)
7.13”
(181.1 mm)
Cutout
18.37”
(466.6 mm)
4.00” (101.6 mm)
1.57” (39.8 mm)
4 × 0.28” (7.1 mm) diameter
17.72”
(450.1 mm)
14.52”
(368.8 mm)
9.52”
(241.8 mm)
8 × 0.156 Ø
5.00”
(127.0 mm)
0.375”
(9.5 mm)
0.375” (9.5 mm)
Remote mounting, view from the rear of the panel
Bezel
outline
0.375” (9.5)
1.875”
(47.6)
0.375” (9.5)
4.875” (121.5 mm)
6.96” (176.8 mm)
827704B4.CDR
3
Figure 3–2: F60 HORIZONTAL MOUNTING (ENHANCED PANEL)
Figure 3–3: F60 HORIZONTAL MOUNTING AND DIMENSIONS (STANDARD PANEL)
b) VERTICAL UNITS
The F60 Feeder Protection System is available as a reduced size (¾) vertical mount unit, with a removable faceplate. The faceplate can be specified as either standard or enhanced at the time of ordering. The enhanced faceplate contains addi­tional user-programmable pushbuttons and LED indicators.
The modular design allows the relay to be easily upgraded or repaired by a qualified service person. The faceplate is hinged to allow easy access to the removable modules, and is itself removable to allow mounting on doors with limited rear depth.
The case dimensions are shown below, along with panel cutout details for panel mounting. When planning the location of your panel cutout, ensure that provision is made for the faceplate to swing open without interference to or from adjacent equipment.
The relay must be mounted such that the faceplate sits semi-flush with the panel or switchgear door, allowing the operator access to the keypad and the RS232 communications port. The relay is secured to the panel with the use of four screws supplied with the relay.
3-2 F60 Feeder Protection System GE Multilin
Page 65
3 HARDWARE 3.1 DESCRIPTION
7.48”
(190.0 mm)
15.00” (381.0 mm)
13.56” (344.4 mm)
1.38” (35.2 mm)
9.58”
(243.4 mm)
7.00”
(177.7 mm)
4.00”
(101.6 mm)
7.10”
(180.2 mm)
13.66” (347.0 mm)
14.03” (356.2 mm)
0.20” (5.1 mm)
1.55” (39.3 mm)
4 Places
0.213” (5.41 mm)
Front of Panel
Mounting Bracket
Vertical Enhanced Front View
Vertical Enhanced Top View
Vertical Enhanced Mounting Panel
CUTOUT
Front of Panel Reference only
Terminal Blocks
Front Bezel
Front of Panel
Mounting Bracket
Vertical Enhanced Side View
843809A2.cdr
3
Figure 3–4: F60 VERTICAL DIMENSIONS (ENHANCED PANEL)
GE Multilin F60 Feeder Protection System 3-3
Page 66
3
13.72"
(348.5 mm)
7.00"
(177.8 mm)
13.50"
(342.9 mm)
Front of
panel
Front bezel
Panel
Mounting bracket
1.57”
(39.9 mm)
4.00
(101.6)
7.13”
(181.1 mm)
0.46” (11.7 mm)
13.65” (346.7 mm)
14.40” (365.8 mm)
0.213" (5.4 mm), 4 places
Vertical front view
Vertical side view
843755A4.CDR
Vertical panel mounting
1.85"
(47.0 mm)
9.00"
(228.6 mm)
7.00"
(177.8 mm)
Terminal blocks
Mounting bracket
Panel shown for reference only
Vertical bottom view
3.1 DESCRIPTION 3 HARDWARE
Figure 3–5: F60 VERTICAL MOUNTING AND DIMENSIONS (STANDARD PANEL)
For side mounting F60 devices with the enhanced front panel, see the following documents available on the UR DVD and the GE Grid Solutions website:
GEK-113180: UR-Series UR-V Side-Mounting Front Panel Assembly Instructions
GEK-113181: Connecting a Remote UR-V Enhanced Front Panel to a Vertical UR Device Instruction Sheet
GEK-113182: Connecting a Remote UR-V Enhanced Front Panel to a Vertically-Mounted Horizontal UR Device Instruction Sheet
For side mounting F60 devices with the standard front panel, use the following figures.
3-4 F60 Feeder Protection System GE Multilin
Page 67
PANEL
UR 19"
MOUNTING
BRACKET
UR-V FRONT BEZEL
ASSEMBLY
#6x1/2" PAN PHILIPS
HEAD
BLACK OXIDE
PLASTITE SCREW
#10-3/8" PAN PHILIPS HEAD
ZINC
P/N: 1410-0006
4 PLACES TO MOUNT THE
BRACKETS
STEP 3
MOUNT FRONT BEZEL TO
PANEL
STEP 2
MOUNT BRACKETS TO
PANEL
#10-32 NYLOCK
NUT
P/N: 1422-1032
4 PLACES
#8-3/8" PAN PHILIPS HEAD
BLACK OXIDE SCREW
P/N: 1408-0306
8 PLACES TO MOUNT THE UNIT
#8 LOCKWASHER
EXTERNAL TOOTH
P/N: 1435-0002
8 PLACES TO MOUNT
STEP 4
ASSEMBLE UR-V UNIT
TO MOUNTING BRACKETS
UR-V UNIT
STEP 1 - CREATE THE HOLES AND CUT-OUT INTO THE PANEL
AS PER DRAWING 843753.
PLUG THE DISPLAY CABLE INTO
THE FRONT BEZEL
BEFORE MOUNTING THE
UNIT ON THE PANEL
DISPLAY CABLE
GROUND CABLE
ATTACH CABLE TO
FRONT BEZEL
BEFORE MOUNTING
FRONT BEZEL ON
THE
PANEL
SIDE MOUNT COVER
P/N: 1004-0018
#8-3/8"
PAN PHILIPS HEAD
BLACK OXIDE
SCREW
843757A2.cdr
3 HARDWARE 3.1 DESCRIPTION
3
Figure 3–6: F60 VERTICAL SIDE MOUNTING INSTALLATION (STANDARD PANEL)
GE Multilin F60 Feeder Protection System 3-5
Page 68
3
CUT-OUT
1.33" (33.9)
2.83" (71.9)
6.66"
(169.2)
12.20"
(309.9)
0.159" DIA. (6 PLACES) (4.0)
0.213" DIA. (5.4) (4 PLACES) SEE HOLES MARKED 'X'
INCHES
(MILLIMETERS)
5.33"
(135.4)
PANEL SHOWN FOR REFERENCE ONLY (VIEWED FROM FRONT)
'X' 'X'
'X' 'X'
1.00" (25.4)
1.00" (25.4)
10.05 (255.3)
"
0.04 (1.0)
"
0.68" (17.3)
5.27
(133.8)
"
843753A3.cdr
3.1 DESCRIPTION 3 HARDWARE
Figure 3–7: F60 VERTICAL SIDE MOUNTING REAR DIMENSIONS (STANDARD PANEL)
3-6 F60 Feeder Protection System GE Multilin
Page 69
3 HARDWARE 3.1 DESCRIPTION
XWVU TS PNM LKJ H DGF BR
8
4
7
3
6
2
5
1
b
8
4
7
3
6
2
5
1
a
abc abc
Optional
direct
input/output
module
CPU module
(T module shown)
Optional
HI-Z CT or
contact
input/output
module
CT/VT
module
Power supply
module
Tx1
Tx2
Rx1
Rx2
Tx1
Tx2
832782A3.CDR
abc
Optional
contact
input/output
module
4
3
2
1
4
3
2
1
b
a
IN
ACT3
LK3
ACT2
LK2
ACT1
LK1
Model: Mods: Wiring Diagram: Inst. Manual: Serial Number: Firmware: Mfg. Date: PO Num: Item Num:
F60H00HCHF8FH6AM6BP8BX7A 000 See manual 1601-0093 MAZB98000029 D NOV 26, 2012
600001234.56
Control Power: Contact Inputs: Contact Outputs:
88-300V DC @ 35W / 77-265V AC @ 35VA 300V DC Max 10mA Refer to Instruction Manual
RATINGS:
F60
GE Multilin
- M A A B 9 7 0 0 0 0 9 9 -
®
Feeder Management Relay
- M A A B 9 7 0 0 0 0 9 9 -
LISTED
52TL
IND.CONT. EQ.
E83849
WARNING
NOTICE

3.1.2 REAR TERMINAL LAYOUT

3
The relay follows a convention with respect to terminal number assignments which are three characters long assigned in order by module slot position, row number, and column letter. Two-slot wide modules take their slot designation from the first slot position (nearest to CPU module) which is indicated by an arrow marker on the terminal block. See the following figure for an example of rear terminal assignments.
Figure 3–8: REAR TERMINAL VIEW
Do not touch any rear terminals while the relay is energized.
The small form-factor pluggable ports (SFPs) are pluggable transceivers. Do not use non-validated transceivers or install validated transceivers in the wrong Ethernet slot, else damage can occur.
Figure 3–9: EXAMPLE OF MODULES IN F AND H SLOTS
GE Multilin F60 Feeder Protection System 3-7
Page 70
3.1 DESCRIPTION 3 HARDWARE
The torque used to connect the terminal blocks to the back of the relay chassis (screws a, b, c shown) is 9 inch-pounds. For the connections to the terminal blocks (rows 1 to 8), use a minimum of 17 inch-pounds. During manufacturing, the power supply and CPU modules are installed in slots B and D of the chassis with 13 inch-pounds of torque on the screws at the top and bottom of the modules.
3
3-8 F60 Feeder Protection System GE Multilin
Page 71

3.2WIRING 3.2.1 TYPICAL WIRING

8F / 8G
F8c
F8a
F5a
F5c
F7c
F6a
F7a
F6c
VX
VA
VB
VC
VOLTAGE INPUTS
VX
VA
VB
VC
F1c
F4a
F3c
CURRENT INPUTS
F2c
F4c
F1a
F4b
F1b
F2a
F3a
F2b
F3b
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
F5a
F5c
F7c
F6a
F7a
F6c
VA
VB
VC
VOLTAGE INPUTS
VA
VB
VC
CONNECTION AS REQUIRED
(Rear view)
1
Power
Supply
9
CPU
8
CT/VT
6
Inputs/ outputs
6
Inputs/
outputs
*
6 Inputs/ outputs
*
6
Inputs/
outputs
*
6 Inputs/ outputs
*
MODULE ARRANGEMENT
JU
MXLWKVBHTD
N
GSP FR
OPEN DELTA VT CONNECTION (ABC)
A
B
C
POSITIVE WATTS
(5 Amp CT)
TYPICAL CONFIGURATION
THE AC SIGNAL PATH IS CONFIGURABLE
52
CONTACTS SHOWN
WITH NO
CONTROL POWER
I
V
I
V
CONTACT INPUT H7a CONTACT INPUT H7c CONTACT INPUT H8a CONTACT INPUT H8c
COMMON H7b
DIGITAL INPUTS/OUTPUTS
6B
H1b
H2b
H3b
H4b
H5b
H6b
H1a
H2a
H3a
H4a
H5a
H6a
H1c
H2c
H3c
H4c
H5c
H6c
H1
H5
H2
H6
H3
H4
H8a
H7b
H7a
H8c
H7c
SURGE
H8b
CRITICAL
FAILURE
48 VDC OUTPUT
CONTROL
POWER
HI
LO
POWER SUPPLY
1
FILTER
SURGE
B3a
B1b
B8a
B6b
B8b
B6a
B3b
B1a B2b
B5b
RS-232
DB-9
(front)
UR COMPUTER
1
TXD RXD RXD TXD
SGND SGND
1
8 3 2
20
7 6 4 5
22
25 PIN CONNECTOR
9 PIN
CONNECTOR
22 33 44 55 66 77 88 99
F60
FEEDER MANAGEMENT RELAY
AC or DC
DC
( DC ONLY )
M7a
M1a
M2b
M7c
M1c
M7b
M1b
M8c
M8b
M2c
M8a
M2a
M4a
M5b
M4c
M6b
M3b
M3a
M6a
M4b
M5c
M5a
M3c
M6c
6K
DIGITAL INPUTS/OUTPUTS
M1
M5
M2
M6
M3
M7
M4
M8
* Optional
6C
DIGITAL INPUTS/OUTPUTS
P1
P5
P2
P6
P3
P7
P4
P8
P7a
P1a
P2b
P7c
P1c
P7b
P1b
P8c
P8b
P2c
P8a
P2a
P4a
P5b
P4c
P6b
P3b
P3a
P6a
P4b
P5c
P5a
P3c
P6c
U6a
U8a
U5b
U7b
U5a
U7a
U6c
U8c
U5c
U7c
CONTACT INPUT U1a
CONTACT INPUT U4c
COMMON U5b
COMMON U7b
COMMON U1b
COMMON U3b
CONTACT INPUT U2a
CONTACT INPUT U5a
CONTACT INPUT U3c
CONTACT INPUT U6a
CONTACT INPUT U8a
CONTACT INPUT U1c
CONTACT INPUT U3a
CONTACT INPUT U5c
CONTACT INPUT U7c
CONTACT INPUT U7a
CONTACT INPUT U2c
SURGE
CONTACT INPUT U4a
CONTACT INPUT U6c
CONTACT INPUT U8c
U1a
U8b
U4c
U2c
U3a U3c
U1c
U3b
U1b
U4a
U2a
6D
DIGITAL INPUTS/OUTPUTS
CONTACT INPUT W5a
CONTACT INPUT W7a
CONTACT INPUT W5c
CONTACT INPUT W7c
CONTACT INPUT W6a
CONTACT INPUT W8a
CONTACT INPUT W6c
CONTACT INPUT W8c
COMMON W5b
COMMON W7b
SURGE
W6a
W8a
W5b
W7b
W8b
W5a
W7a
W6c
W8c
W5c
W7c
6A
W1
W2
W3
W4
W1a
W2b
W1c
W1b
W2c
W2a
W4a
W4c
W3b
W3a
W4b
W3c
DIGITAL INPUTS/OUTPUTS
I
V
I
V
GROUND BUS
No. 10AWG
Minimum
MODULES MUST BE
GROUNDED IF TERMINAL IS
PROVIDED
TC
1
VOLTAGE AND
CURRENT SUPERVISION
TC
2
VOLTAGE SUPERVISION
832779A2.CDR
This diagram is based on the following order code:
F60-T00-HCH-F8F-H6B-M6K-P6C-U6D-W6A
This diagram provides an example of how the device is wired, not specifically how to wire the device. Please refer to the Instruction Manual for additional details on wiring based on various configurations.
com
100BaseFX
D1a D2a
D4b
D3a
D4a
IRIG-B
Input
RS485 COM 2
PORT 1
CPU
Tx2
Rx2
Tx1
Rx1
BNC
Fibre Optic
*
Ground at
Remote Device
Shielded
twisted pairs
Co-axial
T
100BaseFX
100BaseFX
Tx3
Rx3
PORT 2
PORT 3
3 HARDWARE 3.2 WIRING
3
GE Multilin F60 Feeder Protection System 3-9
Figure 3–10: TYPICAL WIRING DIAGRAM (T MODULE SHOWN FOR CPU)
Page 72
3.2 WIRING 3 HARDWARE
832780A2.CDR
(Rear view)
1
Power Supply
9
CPU
8
CT/VT
6 Digital inputs/
outputs
8
CT
8
Digital inputs/ outputs
6 Digital inputs/
outputs
6
Digital inputs/ outputs
MODULE ARRANGEMENT
JU
MXLWKVBHTD
N
GS
PFR
CONTACTS SHOWN
WITH NO
CONTROL POWER
TYPICAL CONFIGURATION
THE AC SIGNAL PATH IS CONFIGURABLE
F60
FEEDER MANAGEMENT RELAY
AC or DC
DC
( DC ONLY )
F60 COMPUTER
1
TXD RXD RXD TXD
SGND SGND
1
8 3 2
20
7 6 4 5
22
25 PIN CONNECTOR
9 PIN
CONNECTOR
22 33 44 55 66 77 88 99
RS-232
(front)
DB-9
CRITICAL FAILURE
48 VDC
OUTPUT
CONTROL
POWER
HI LO
POWER SUPPLY
1
FILTER
SURGE
B3a
B1b
B8a
B6b
B8b
B6a
B3b
B1a
B2b
B5b
GROUND BUS
No. 10AWG
minimum
MODULES MUST BE
GROUNDED IF TERMINAL IS
PROVIDED
I
V
I
V
CONTACT INPUT H7a CONTACT INPUT H7c CONTACT INPUT H8a CONTACT INPUT H8c
COMMON H7b
DIGITAL INPUTS/OUTPUTS
6B
H1b
H2b
H3b
H4b
H5b
H6b
H1a
H2a
H3a
H4a
H5a
H6a
H1c
H2c
H3c
H4c
H5c
H6c
H1
H5
H2
H6
H3
H4
H8a
H7b
H7a
H8c
H7c
SURGE
H8b
6C
DIGITAL INPUTS/OUTPUTS
P1
P5
P2
P6
P3
P7
P4
P8
P7a
P1a
P2b
P7c
P1c
P7b
P1b
P8c
P8b
P2c
P8a
P2a
P4a
P5b
P4c
P6b
P3b
P3a
P6a
P4b
P5c
P5a
P3c
P6c
M7c
M8c
M8b
M8a
M5c
M5b
M5a
M7b
M7a
M3c
M4b
M4a
M4c
M1c
M2b
M2a
M6b
M6a
M6c
M2c
M1b
M1a
M3b
M3a
CURRENT INPUTS NOT USED
8Z
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
CONNECTION
AS REQUIRED
OPEN DELTA
VT CONNECTION (ABC)
A
B
C
POSITIVE WATTS
(5 Amp CT)
52
8F / 8L / 8G / 8M
F8c
F8a
F7c
F5a
F5c
F6a
F7a
F6c
VX
VA
VB
VC
VOLTAGE INPUTS
VX
VA
VB
VC
F1c
F3c
F3b
CURRENT INPUTS
F2c
F4c
F1a
F4b
F4a
F1b
F2a
F3a
F2b
IA
IB
IC
IG
IA5
IA1
IB5
IC5
IG5
IB1
IC1
IG1
F5a
F5c
F6a
F7a
F7c
F6c
VA
VB
VC
VOLTAGE INPUTS
VA
VB
VC
* Optional
D1a D2a
D4b
D3a
D4a
IRIG-B Input
COM
2
RS485 COM 2
ALTERNATE
NORMAL
com
CPU T
100BaseFX
Tx2
Rx2
Tx1
Rx1
BNC
Fibre Optic
*
Ground at
Remote
Device
Shielded
twisted pairs
Co-axial
Co-axial *
Co-axial * - For IRIG-B Input only use one terminal as input
This diagram is based on the following order code:
F60-T00-HCH-F8F-H6B-M8Z-P6C-UXX-WXX
This diagram provides an example of how the device is wired, not specifically how to wire the device. Please refer to the Instruction Manual for additional details on wiring based on various configurations.
100BaseFX
100BaseFX
Tx3
Rx3
3
Figure 3–11: TYPICAL WIRING DIAGRAM WITH HIGH-IMPEDANCE DETECTION (T MODULE SHOWN FOR CPU)
3-10 F60 Feeder Protection System GE Multilin
Page 73
3 HARDWARE 3.2 WIRING
NOTICE
NOTICE

3.2.2 DIELECTRIC STRENGTH

The dielectric strength of the UR-series module hardware is shown in the following table:
Table 3–1: DIELECTRIC STRENGTH OF UR-SERIES MODULE HARDWARE
MODULE
TYPE
1 Power supply High (+); Low (+); (–) Chassis 2000 V AC for 1 minute 1 Power supply 48 V DC (+) and (–) Chassis 2000 V AC for 1 minute 1 Power supply Relay terminals Chassis 2000 V AC for 1 minute 2 Reserved N/A N/A N/A 3 Reserved N/A N/A N/A 4 Digital contact inputs/
5 Analog inputs/outputs All except 8b Chassis < 50 V DC 6 Digital contact inputs/
7
8 CT/VT All Chassis 2000 V AC for 1 minute 9 CPU All Chassis 2000 V AC for 1 minute
MODULE FUNCTION TERMINALS DIELECTRIC STRENGTH
FROM TO
outputs
outputs
G.703 All except 2b, 3a, 7b, 8a Chassis 2000 V AC for 1 minute
RS422 All except 6a, 7b, 8a Chassis < 50 V DC
Filter networks and transient protection clamps are used in the hardware to prevent damage caused by high peak voltage transients, radio frequency interference (RFI), and electromagnetic interference (EMI). These protective components can be damaged by application of the ANSI/IEEE C37.90 spec­ified test voltage for a period longer than the specified one minute.
All Chassis 2000 V AC for 1 minute
All Chassis 2000 V AC for 1 minute
(AC)
3

3.2.3 CONTROL POWER

Control power supplied to the relay must be connected to the matching power supply range of the relay. If voltage is applied to the wrong terminals, damage can occur.
The F60 relay, like almost all electronic relays, contains electrolytic capacitors. These capacitors are well-known to deteriorate over time if voltage is not applied periodically. Deterioration can be avoided by powering up the relay at least once a year.
The power supply module can be ordered for two possible voltage ranges, and the UR can be ordered with or without a redundant power supply module option. Each range has a dedicated input connection for proper operation. The ranges are as shown below (see the Specifications section of chapter 2 for details):
Low (LO) range: 24 to 48 V (DC only) nominal.
High (HI) range: 125 to 250 V nominal. The power supply module provides power to the relay and supplies power for dry contact input connections. The power supply module provides 48 V DC power for dry contact input connections and a critical failure relay (see the
Typical wiring diagram earlier). The critical failure relay is a form-C device that is energized once control power is applied and the relay has successfully booted up with no critical self-test failures. If on-going self-test diagnostic checks detect a critical failure (see the Self-test Errors section in chapter 7) or control power is lost, the relay is de-energize.
For high reliability systems, the F60 has a redundant option in which two F60 power supplies are placed in parallel on the bus. If one of the power supplies become faulted, the second power supply assumes the full load of the relay without any interruptions. Each power supply has a green LED on the front of the module to indicate it is functional. The critical fail relay of the module also indicates a faulted power supply.
GE Multilin F60 Feeder Protection System 3-11
Page 74
3.2 WIRING 3 HARDWARE
AC or DC
NOTE: 14 gauge stranded wire with suitable disconnect devices is recommended.
Heavy copper conductor
or braided wire
Switchgear
ground bus
UR-series
protection system
FILTER
SURGE
+
LOW
+
HIGH
B8b B8a B6a B6b B5b
CONTROL
POWER
827247A1.CDR
NOTICE
An LED on the front of the control power module shows the status of the power supply:
LED INDICATION POWER SUPPLY
CONTINUOUS ON OK ON / OFF CYCLING Failure OFF Failure
3
Figure 3–12: CONTROL POWER CONNECTION

3.2.4 CT AND VT MODULES

A CT/VT module can have voltage or current inputs on channels 1 through 4 inclusive, or channels 5 through 8 inclusive. Channels 1 and 5 are intended for connection to phase A, and are labeled as such in the relay. Likewise, channels 2 and 6 are intended for connection to phase B, and channels 3 and 7 are intended for connection to phase C.
Channels 4 and 8 are intended for connection to a single-phase source. For voltage inputs, these channel are labelled as auxiliary voltage (VX). For current inputs, these channels are intended for connection to a CT between system neutral and ground, and are labelled as ground current (IG).
Verify that the connection made to the relay terminals for nominal current of 1 A or 5 A matches the secondary rating of the connected CTs. Unmatched CTs can result in equipment damage or inade-
quate protection. To connect the module, size 12 American Wire Gauge (AWG) is commonly used; the maximum size is 10 AWG. CT/VT modules can be ordered with a standard ground current input that is the same as the phase current input. Each AC
current input has an isolating transformer and an automatic shorting mechanism that shorts the input when the module is withdrawn from the chassis. There are no internal ground connections on the current inputs. Current transformers with 1 to 50000 A primaries and 1 A or 5 A secondaries can be used.
CT/VT modules with a sensitive ground input are also available. The ground CT input of the sensitive ground modules is 10 times more sensitive than the ground CT input of standard CT/VT modules. However, the phase CT inputs and phase VT inputs are the same as those of regular CT/VT modules.
The above modules have enhanced diagnostics that can automatically detect CT/VT hardware failure and take the relay out of service.
CT connections for both ABC and ACB phase rotations are identical as shown in the Typical wiring diagram. The exact placement of a zero-sequence core balance CT to detect ground fault current is shown as follows. Twisted-pair
cabling on the zero-sequence CT is recommended.
3-12 F60 Feeder Protection System GE Multilin
Page 75
3 HARDWARE 3.2 WIRING
Ground connection to neutral must be on the source side
UNSHIELDED CABLE
LOAD
ABCN G
Ground outside CT
Source
LOAD
SHIELDED CABLE
996630A6.CDR
ABC
Source
To ground; must be on load side
Stress cone
shields
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
1a
1b
1c
2a
2b
2c
3a
4a
5a
6a
7a
8a
3b
4b
5c
6c
7c
8c
3c
4c
Current inputs
8F and 8G modules (4 CTs and 4 V Ts)
Voltage inputs
VA
VB
VC
VX
VA
VB
VC
VX
IA
IC
IB
IG
IA5
IC5
IB5
IG5
IA1
IC1
IB1
IG1
Current inputs Not used
8Z module (used for high-impedance fault detection)
~
~
~
~
~
~
~
~
~
~
~
~
1a
1b
1c
2a
2b
2c
3a
4a
3b
4b
3c
4c
IA
IC
IB
IG
IA5
IC5
IB5
IG5
IA1
IC1
IB1
IG1
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
1a
5a
1b
5b
1c
5c
2a
6a
2b
6b
2c
6c
3a
7a
4a
8a
3b
7b
4b
8b
3c
7c
4c
8c
Current inputs
8H and 8J modules (8 CTs)
IA
IA
IC
IC
IB
IB
IG
IG
IA5
IA5
IC5
IC5
IB5
IB5
IG5
IG5
IA1
IA1
IC1
IC1
IB1
IB1
IG1
IG1
842769A1.CDR
Figure 3–13: ZERO-SEQUENCE CORE BALANCE CT INSTALLATION
The phase voltage channels are used for most metering and protection purposes. The auxiliary voltage channel is used as input for the synchrocheck and volts-per-hertz features.
Substitute the tilde “~” symbol with the slot position of the module in the following figure.
3
Figure 3–14: CT/VT MODULE WIRING
GE Multilin F60 Feeder Protection System 3-13
Page 76
3.2 WIRING 3 HARDWARE
A
B
C
Positive watts
(5 amp CT)
52
F1a
F1b
F1c
F2a
F2b
F2c
F3a
F4a
F5a
F6a
F7a
F8a
F3b
F4b
F5c
F6c
F7c
F8c
F3c
F4c
Current inputs
8F, 8G, 8L, and 8M modules (4 CTs and 4 VTs)
Voltage inputs
VA
VB
VC
VX
VA
VB
VC
VX
IA
IC
IB
IG
IA5
IC5
IB5
IG5
IA1
IC1
IB1
IG1
M1a
M1b
M1c
M2a
M2b
M2c
M3a
M4a
M3b
M4b
M3c
M4c
Current inputs
IA
IC
IB
IG
IA5
IC5
IB5
IG5
IA1
IC1
IB1
IG1
8Z module (used for high-impedance fault detection)
832752A4.CDR
A relay configured for high impedance fault detection element includes two CT/VT modules: one type 8F, 8G, 8H, or 8J module and one type 8Z module. For correct operation of the high impedance fault detection element, the ground current terminals of the two CT modules must be connected to a ground current source, either a zero-sequence CT (see the Ty pi- cal wiring diagram with high impedance fault detection earlier in this chapter) or, if a zero-sequence CT is not available, to the neutral conductor of the phase CTs (see diagram below).
3
Figure 3–15: TYPICAL 8Z MODULE WIRING WITH PHASE CTS

3.2.5 PROCESS BUS MODULES

The F60 can be ordered with a process bus interface module. This module is designed to interface with the GE Multilin HardFiber system, allowing bidirectional IEC 61850 fiber optic communications with up to eight HardFiber merging units, known as Bricks. The HardFiber system has been designed to integrate seamlessly with the existing UR-series applica­tions, including protection functions, FlexLogic, metering, and communications.
The IEC 61850 process bus system offers the following benefits:
Reduces labor associated with design, installation, and testing of protection and control applications using the F60 by
reducing the number of individual copper terminations
Integrates seamlessly with existing F60 applications, since the IEC 61850 process bus interface module replaces the
traditional CT/VT modules
Communicates using open standard IEC 61850 messaging For additional details on the HardFiber system, see GE publication GEK-113658: HardFiber Process Bus System Instruc-
tion Manual.
3-14 F60 Feeder Protection System GE Multilin
Page 77
3 HARDWARE 3.2 WIRING
Load
I
~#a
~#b
~#c
V
827862A4.CDR
+
+
+
+
+
a) Voltage with optional current monitoring
Voltage monitoring only
Load
I
V
Both voltage and current monitoring
Load
I
V
b) Current with optional voltage monitoring
Current monitoring only Both voltage and current monitoring
(external jumper a-b is required)
Load
V
Load
c) No monitoring
~#a
~#b
~#c
~#a
~#b
~#c
~#a
~#b
~#c
~#a
~#b
~#c
I

3.2.6 CONTACT INPUTS AND OUTPUTS

Every contact input/output module has 24 terminal connections. They are arranged as three terminals per row, with eight rows in total. A given row of three terminals can be used for the outputs of one relay. For example, for form-C relay outputs, the terminals connect to the normally open (NO), normally closed (NC), and common contacts of the relay. For a form-A output, there are options of using current or voltage detection for feature supervision, depending on the module ordered. The terminal configuration for contact inputs is different for the two applications.
The contact inputs are grouped with a common return. The input/output modules have two versions of grouping: four inputs per common return and two inputs per common return. When a contact input/output module is ordered, four inputs per com­mon is used. If the inputs must be isolated per row, then two inputs per common return should be selected (4D module).
The tables and diagrams on the following pages illustrate the module types (6A, etc.) and contact arrangements that can be ordered for the relay. Since an entire row is used for a single contact output, the name is assigned using the module slot position and row number. However, since there are two contact inputs per row, these names are assigned by module slot position, row number, and column position.
Some form-A / solid-state relay outputs include circuits to monitor the DC voltage across the output contact when it is open, and the DC current through the output contact when it is closed. Each of the monitors contains a level detector whose out­put is set to logic “On” when the current in the circuit is above the threshold setting. The voltage monitor is set to “On” when there is a voltage across open contact (the detector allows a current of about 1 to 2.5 mA), and the current monitor is set to “On” when the current flowing through the closed contact exceeds about 80 to 100 mA. The voltage monitor is intended to check the health of the overall trip circuit, and the current monitor can be used to seal-in the output contact until an external contact has interrupted current flow. If enabled, the current monitoring can be used as a seal-in signal to ensure that the form-A contact does not attempt to break the energized inductive coil circuit and weld the output contacts.
Block diagrams are shown as follows for form-A and solid-state relay outputs with optional voltage monitor, optional current monitor, and with no monitoring. The actual values shown for contact output 1 are the same for all contact outputs. Form-A contact output with or without a current or voltage monitoring option is not polarity sensitive. The polarity shown in the figure is required for solid-state contact output connection.
3
Figure 3–16: FORM-A AND SOLID-STATE CONTACT OUTPUTS WITH VOLTAGE AND CURRENT MONITORING
GE Multilin F60 Feeder Protection System 3-15
Page 78
3.2 WIRING 3 HARDWARE
WARNING
NOTE
NOTE
NOTICE
The operation of voltage and current monitors is reflected with the corresponding FlexLogic operands (CONT OP # VON,
CONT OP # VOFF, and CONT OP # ION) which can be used in protection, control, and alarm logic. The typical application of
the voltage monitor is breaker trip circuit integrity monitoring; a typical application of the current monitor is seal-in of the control command.
See the Digital Elements section of chapter 5 for an example of how form-A and solid-state relay contacts can be applied for breaker trip circuit integrity monitoring.
Consider relay contacts unsafe to touch when the unit is energized.
USE OF FORM-A AND SOLID-STATE RELAY OUTPUTS IN HIGH IMPEDANCE CIRCUITS
For form-A and solid-state relay output contacts internally equipped with a voltage measuring circuit across the con­tact, the circuit has an impedance that can cause a problem when used in conjunction with external high input
3
impedance monitoring equipment such as modern relay test set trigger circuits. These monitoring circuits may con­tinue to read the form-A contact as being closed after it has closed and subsequently opened, when measured as an impedance.
The solution is to use the voltage measuring trigger input of the relay test set, and connect the form-A contact through a voltage-dropping resistor to a DC voltage source. If the 48 V DC output of the power supply is used as a source, a 500 Ω, 10 W resistor is appropriate. In this configuration, the voltage across either the form-A contact or the resistor can be used to monitor the state of the output.
Wherever a tilde “~” symbol appears, substitute with the slot position of the module; wherever a number sign “#” appears, substitute the contact number
When current monitoring is used to seal-in the form-A and solid-state relay contact outputs, the Flex-
Logic operand driving the contact output should be given a reset delay of 10 ms to prevent damage
of the output contact (in situations when the element initiating the contact output is bouncing, at val-
ues in the region of the pickup value).
Table 3–2: CONTACT INPUT AND OUTPUT MODULE ASSIGNMENTS
~6A MODULE ~6B MODULE ~6C MODULE ~6D MODULE
TERMINAL
ASSIGNMENT
~1 Form-A ~1 Form-A ~1 Form-C ~1a, ~1c 2 Inputs ~2 Form-A ~2 Form-A ~2 Form-C ~2a, ~2c 2 Inputs ~3 Form-C ~3 Form-C ~3 Form-C ~3a, ~3c 2 Inputs
~4 Form-C ~4 Form-C ~4 Form-C ~4a, ~4c 2 Inputs ~5a, ~5c 2 Inputs ~5 Form-C ~5 Form-C ~5a, ~5c 2 Inputs ~6a, ~6c 2 Inputs ~6 Form-C ~6 Form-C ~6a, ~6c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7 Form-C ~7a, ~7c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8 Form-C ~8a, ~8c 2 Inputs
TERMINAL
ASSIGNMENT
~1Form-C ~1 Fast Form-C ~1Form-A ~1Form-A
~2Form-C ~2 Fast Form-C ~2Form-A ~2Form-A
~3Form-C ~3 Fast Form-C ~3Form-A ~3Form-A
~4Form-C ~4 Fast Form-C ~4Form-A ~4Form-A ~5a, ~5c 2 Inputs ~5 Fast Form-C ~5a, ~6a, ~6c 2 Inputs ~6 Fast Form-C ~6a, ~6c 2 Inputs ~6 Form-A ~7a, ~7c 2 Inputs ~7 Fast Form-C ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~8a, ~8c 2 Inputs ~8 Fast Form-C ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
OUTPUT OR
INPUT
~6E MODULE ~6F MODULE ~6G MODULE ~6H MODULE
OUTPUT OR
INPUT
TER MINA L
ASSIGNMENT
TER MINA L
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT TERMINAL
TERMINAL
ASSIGNMENT
ASSIGNMENT
OUTPUT TERMINAL
OUTPUT OR
INPUT
~5c 2 Inputs ~5 Form-A
ASSIGNMENT
TER MINA L
ASSIGNMENT
OUTPUT
OUTPUT OR
INPUT
3-16 F60 Feeder Protection System GE Multilin
Page 79
3 HARDWARE 3.2 WIRING
~6K MODULE ~6L MODULE ~6M MODULE ~6N MODULE
TERMINAL
ASSIGNMENT
~1 Form-C ~1Form-A ~1Form-A ~1Form-A ~2 Form-C ~2Form-A ~2Form-A ~2Form-A ~3 Form-C ~3Form-C ~3Form-C ~3Form-A ~4 Form-C ~4Form-C ~4Form-C ~4Form-A ~5 Fast Form-C ~5a, ~5c 2 Inputs ~5Form-C ~5a, ~5c 2 Inputs ~6 Fast Form-C ~6a, ~6c 2 Inputs ~6Form-C ~6a, ~6c 2 Inputs ~7 Fast Form-C ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~8 Fast Form-C ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
~6P MODULE ~6R MODULE ~6S MODULE ~6T MODULE
TERMINAL
ASSIGNMENT
~1 Form-A ~1Form-A ~1Form-A ~1Form-A ~2 Form-A ~2Form-A ~2Form-A ~2Form-A ~3 Form-A ~3Form-C ~3Form-C ~3Form-A ~4 Form-A ~4Form-C ~4Form-C ~4Form-A ~5 Form-A ~5a, ~5c 2 Inputs ~5Form-C ~5a, ~5c 2 Inputs ~6 Form-A ~6a, ~6c 2 Inputs ~6Form-C ~6a, ~6c 2 Inputs
~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs
OUTPUT TERMINAL
OUTPUT OR
INPUT
ASSIGNMENT
TER MINA L
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT OR
INPUT
TERMINAL
ASSIGNMENT
TERMINAL
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT OR
INPUT
TER MINA L
ASSIGNMENT
TER MINA L
ASSIGNMENT
OUTPUT OR
INPUT
OUTPUT OR
INPUT
3
~6U MODULE ~6V MODULE ~67 MODULE ~4A MODULE
TERMINAL
ASSIGNMENT
~1 Form-A ~1 Form-A ~1Form-A ~1Not Used ~2 Form-A ~2 Form-A ~2Form-A ~2 Solid-State ~3 Form-A ~3 Form-C ~3Form-A ~3Not Used ~4 Form-A ~4 2 Outputs ~4Form-A ~4 Solid-State ~5 Form-A ~5a, ~5c 2 Inputs ~5Form-A ~5Not Used ~6 Form-A ~6a, ~6c 2 Inputs ~6Form-A ~6 Solid-State
~7a, ~7c 2 Inputs ~7a, ~7c 2 Inputs ~7Form-A ~7Not Used ~8a, ~8c 2 Inputs ~8a, ~8c 2 Inputs ~8Form-A ~8 Solid-State
TERMINAL
ASSIGNMENT
~1Not Used ~1 Not Used ~1a, ~1c 2 Inputs ~1 2 Outputs ~2 Solid-State ~2 Solid-State ~2a, ~2c 2 Inputs ~2 2 Outputs ~3Not Used ~3 Not Used ~3a, ~3c 2 Inputs ~3 2 Outputs ~4 Solid-State ~4 Solid-State ~4a, ~4c 2 Inputs ~4 2 Outputs ~5Not Used ~5 Not Used ~5a, ~5c 2 Inputs ~5 2 Outputs ~6 Solid-State ~6 Solid-State ~6a, ~6c 2 Inputs ~6 2 Outputs ~7Not Used ~ ~8 Solid-State ~8 Solid-State ~8a, ~8c 2 Inputs ~8Not Used
OUTPUT OR
INPUT
~4B MODULE ~4C MODULE ~4D MODULE ~4L MODULE
OUTPUT TERMINAL
TER MINA L
ASSIGNMENT
ASSIGNMENT
7 Not Used ~7a, ~7c 2 Inputs ~72 Outputs
OUTPUT OR
INPUT
OUTPUT TERMINAL
TERMINAL
ASSIGNMENT
ASSIGNMENT
OUTPUT TERMINAL
OUTPUT TERMINAL
ASSIGNMENT
ASSIGNMENT
OUTPUT
OUTPUT
GE Multilin F60 Feeder Protection System 3-17
Page 80
3
842762A3.CDR
3.2 WIRING 3 HARDWARE
Figure 3–17: CONTACT INPUT AND OUTPUT MODULE WIRING (1 of 2)
3-18 F60 Feeder Protection System GE Multilin
Page 81
3 HARDWARE 3.2 WIRING
DIGITAL I/O
6K
1b
2b
3b
4b
5b
7b
6b
8b
1a
2a
3a
4a
5a
7a
6a
8a
1c
2c
3c
4c
5c
7c
6c
8c
1
5
7
2
6
8
3
4
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
I
V
I
V
I
V
I
V
DIGITAL I/O
6P
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
DIGITAL I/O
6U
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
DIGITAL I/O
6M
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
DIGITAL I/O
6S
1b
2b
3b
4b
5b
6b
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
6c
1
5
2
6
3
4
8a
7b
7a
CONTACT IN 7a CONTACT IN 7c CONTACT IN 8a CONTACT IN 8c
COMMON 7b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
I
V
I
V
DIGITAL I/O
6N
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
DIGITAL I/O
6T
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
I
V
I
V
DIGITAL I/O
6L
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
DIGITAL I/O
6R
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
842763A2.CDR
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
~
DIGITAL I/O
6V
1b
2b
3b
4b
6c
1a
2a
3a
4a
5a
6a
1c
2c
3c
4c
5c
5b
1
2
3
4a
8a
7b
7a
CONTACT IN 7a
CONTACT IN 5a
CONTACT IN 7c
CONTACT IN 5c
CONTACT IN 8a
CONTACT IN 6a
CONTACT IN 8c
CONTACT IN 6c
COMMON 7b
COMMON 5b
SURGE
8c
7c
8b
~
4c
I
V
I
V
NOTICE
3
GE Multilin F60 Feeder Protection System 3-19
Figure 3–18: CONTACT INPUT AND OUTPUT MODULE WIRING (2 of 2)
For proper functionality, observe the polarity shown in the figures for all contact input and output con­nections.
Page 82
3.2 WIRING 3 HARDWARE
827741A5.CDR
24 to 250 V
(Wet) (Dry)
Contact input 1 Contact input 2 Contact input 3
Surge
Contact input 4
~7a
Common
~7b
~7c ~8a
~8b
~8c
Contact input 1 Contact input 2 Contact input 3
Surge
Contact input 4
~7a
Common
~7b
~7c ~8a
~8b
~8c
Control power
Surge
B5b
Filter
B8b
B6b B6a B8a
Critical failure
B1b
48 V DC output
B3b
B1a B2b B3a
HI+ LO+
Power supply module
Terminals from type 6B contact input/output module
Terminals from type 6B contact input/output module
NOTE
CONTACT INPUTS
A dry contact has one side connected to terminal B3b. This is the positive 48 V DC voltage rail supplied by the power sup­ply module. The other side of the dry contact is connected to the required contact input terminal. Each contact input group has its own common (negative) terminal which must be connected to the DC negative terminal (B3a) of the power supply module. When a dry contact closes, a current of 1 to 3 mA flows through the associated circuit.
A wet contact has one side connected to the positive terminal of an external DC power supply. The other side of this contact is connected to the required contact input terminal. If a wet contact is used, then the negative side of the external source must be connected to the relay common (negative) terminal of each contact group. The maximum external source voltage for this arrangement is 300 V DC.
The voltage threshold at which each group of four contact inputs detects a closed contact input is programmable as 17 V DC for 24 V sources, 33 V DC for 48 V sources, 84 V DC for 110 to 125 V sources, and 166 V DC for 250 V sources.
3
Figure 3–19: DRY AND WET CONTACT INPUT CONNECTIONS
Wherever a tilde “~” symbol appears, substitute with the slot position of the module.
There is no provision in the relay to detect a DC ground fault on 48 V DC control power external output. We recommend using an external DC supply.
GENERAL APPLICATION CONSIDERATIONS
Contacts outputs of protective relays, auxiliary contacts from breakers, disconnectors and other devices, are generally con­nected to contacts inputs of protective relays. In some situations, the contact outputs of some protective relays can have high impedance connected across it. When such a contact output is connected across a F60 contact input, it can spuriously operate the F60 input even when the output is open, if there is a substantial distributed capacitance (represented by C1) present in the wiring between the output and the F60 input and the debounce time setting in the F60 relay is low enough. This false assertion of the contact input, when there is inadvertent ground present at the DC positive terminal, can be pre­vented by inserting a resistor across the F60 input.
The following figure shows a typical DC circuit, with battery ground detection, of contact input. The contact output has par­allel impedance across it (represented by R1).
3-20 F60 Feeder Protection System GE Multilin
Page 83
3 HARDWARE 3.2 WIRING
Figure 3–20: TYPICAL CONTACT INPUT DC CIRCUIT
The presence of the impedance path (R1) across the contact output allows the stray (distributed) capacitance C1 to charge as shown, thus developing a voltage across the contact input enough to momentarily operate the input while the capaci­tance discharges in the presence of DC ground on the positive terminal of the battery.
The duration of the discharge depends on the value of the distributed capacitance, the initial voltage of the distributed capacitance, and the input impedance of the contact input. If the duration is greater than the debounce time setting, then the contact input operates.
The application example that follows describes how to mitigate this problem by connecting a resistor across the contact input, as shown in the next figure, or by adjusting the debounce time setting to a value greater than the discharge time to prevent spurious operation of the contact input only if the voltage (with output open) across the contact input due to trickle current is less than the threshold voltage. This operation of contact inputs also can be prevented by using the Auto-Burnish contact inputs or contact inputs with active impedance.
3
Figure 3–21: CONTACT INPUT CONNECTED TO A CONTACT OUTPUT WITH RESISTOR (R2) ACROSS THE INPUT
GE Multilin F60 Feeder Protection System 3-21
Page 84
3.2 WIRING 3 HARDWARE
APPLICATION EXAMPLE
This example is for illustrative purposes only and the calculations present the worst-case scenario. In practice, the value of debounce time can be lower.
Contact input ON state impedance used in the calculation of the discharge period is based on the following table.
Table 3–3: DISCHARGE PERIOD
BATTERY VOLTAGE (V) INPUT IMPEDANCE (KΩ)
130 50 250 97
Debounce time setting = 2 ms Assume a stray capacitance of 0.1 μF. Assume an initial voltage across the stray capacitance "Vinitial" = 19 V (Vthreshold - 65 V), where Vthreshold = 84 V. The
3
initial voltage Vinitial depends on values of impedance of R1 and contact inputs when the contact input is OFF (non-acti­vated state).
Therefore, discharge time constant (τ) =50 k *0.1 μF = 5 ms. Discharge period t is calculated from the following equation:
Vthreshold = (Vbatt - VInitial) *e^ (-t/τ)
84 = -149 *e^ (t/0.005) (EQ 3.1)
T = -0.005 * ln (84/149) = 0.0029 s
Therefore, in this example the contact inputs operate. To prevent this operation, the debounce time must be increased to 4 ms (set debounce time as per the following table) or
insert a resistor less than or equal to "R" as calculated later.
Table 3–4: TYPICAL DEBOUNCE TIME SETTING
STRAY CAPACITANCE (μF) BATTERY VOLTAGE (V) DEBOUNCE TIME (MS)
0.05 130 2
0.1 130 4
0.2 130 6
0.05 250 3
0.1 250 6
0.2 250 11
The value of this resistor "R" is calculated as follows:
1. Determine the minimum voltage (V threshold) required to turn on the input. This is determined by direct measurement or referenced in the input specifications.
2. Calculate the resistance necessary to limit the voltage to 1/3 V threshold (when the contact is OFF, the non-activated state) as follows:
R = (Vthreshold / 3) / (2 mA) (EQ 3.2)
The 2 mA current is used in case the contact input is connected across the GE Form A contact output with voltage monitoring. Otherwise use the amperage of the active circuit connected to the contact input when its contact output is open and the voltage across the contact input is third trigger threshold to calculate the resistor value.
3. When the contact is ON (operate state), the battery voltage appears across the resistor. The wattage rating of the resistor is then:
PR = 1.3 * (Vbatt) ^2 / R Watts (EQ 3.3)
4. Applying the following equation to our example:
R = 84 V / 3*(1 / 2 mA) = 14 k
PR = 1.57 Watts (EQ 3.4)
5. Calculating the voltage across the contact input with the Burden Resistor, Voltage across the contact Input:
3-22 F60 Feeder Protection System GE Multilin
Page 85
3 HARDWARE 3.2 WIRING
Vresistor = 2 mA * 14 Kohm = 28 V
Vresistor < contact input threshold (84 V) (EQ 3.5)
In conclusion, in this example, the contact input does NOT operate falsely with the Burden Resistor across its input AND when a battery ground is present.
3
GE Multilin F60 Feeder Protection System 3-23
Page 86
3.2 WIRING 3 HARDWARE
842749A1.CDR
50 to 70 mA
3 mA
25 to 50 ms
current
time
CONTACT INPUT 1 AUTO-BURNISH = OFF
= OFFCONTACT INPUT 2 AUTO-BURNISH
CONTACT INPUT 1 AUTO-BURNISH CONTACT INPUT 2 AUTO-BURNISH
= ON = OFF
CONTACT INPUT 1 AUTO-BURNISH CONTACT INPUT 2 AUTO-BURNISH
= OFF = ON
CONTACT INPUT 1 AUTO-BURNISH CONTACT INPUT 2 AUTO-BURNISH
= ON = ON
842751A1.CDR
USE OF CONTACT INPUTS WITH AUTO-BURNISHING
The contact inputs sense a change of the state of the external device contact based on the measured current. When exter­nal devices are located in a harsh industrial environment (either outdoor or indoor), their contacts can be exposed to vari­ous types of contamination. Normally, there is a thin film of insulating sulfidation, oxidation, or contaminates on the surface of the contacts, sometimes making it difficult or impossible to detect a change of the state. This film must be removed to establish circuit continuity – an impulse of higher than normal current can accomplish this.
The contact inputs with auto-burnish create a high current impulse when the threshold is reached to burn off this oxidation layer as a maintenance to the contacts. Afterwards the contact input current is reduced to a steady-state current. The impulse has a 5 second delay after a contact input changes state.
3
Figure 3–22: CURRENT THROUGH CONTACT INPUTS WITH AUTO-BURNISHING
Regular contact inputs limit current to less than 3 mA to reduce station battery burden. In contrast, contact inputs with auto­burnishing allow currents up to 50 to 70 mA at the first instance when the change of state was sensed. Then, within 25 to 50 ms, this current is slowly reduced to 3 mA as indicated above. The 50 to 70 mA peak current burns any film on the con­tacts, allowing for proper sensing of state changes. If the external device contact is bouncing, the auto-burnishing starts when external device contact bouncing is over.
Another important difference between the auto-burnishing input module and the regular input modules is that only two con­tact inputs have common ground, as opposed to four contact inputs sharing one common ground (refer to the Contact Input and Output Module Wiring diagrams). This is beneficial when connecting contact inputs to separate voltage sources. Con­sequently, the threshold voltage setting is also defined per group of two contact inputs.
The auto-burnish feature can be disabled or enabled using the DIP switches found on each daughter card. There is a DIP switch for each contact, for a total of 16 inputs.
Figure 3–23: AUTO-BURNISH DIP SWITCHES
3-24 F60 Feeder Protection System GE Multilin
Page 87
3 HARDWARE 3.2 WIRING
NOTE
The auto-burnish circuitry has an internal fuse for safety purposes. During regular maintenance, check the auto­burnish functionality using an oscilloscope.
USE OF CONTACT INPUTS WITH ACTIVE IMPEDANCE
Contact inputs susceptible to parasitic capacitance caused by long cable runs affected by switching surges from external circuits can result in inadvertent activation of contact inputs with the external contact open. In this case, GE recommends using the digital I/O module with active impedance circuit.
Active impedance contact input can tolerate external cable capacitance of up to 0.2 µF, without entering the ON state for more than 2 ms. The contact input debounce time can still be set above 2 ms for added security to prevent contact input activations cause by external transient ON states.
An active impedance contact input is normally in Low impedance mode during OFF contact state (non-activated condition). During Low impedance state contact input impedance is maintained at 10 K Ohms impedance to allow fast discharge of the stray capacitance of the long cables.
When the contact input voltage exceeds the set threshold, active impedance maintains 10 K Ohms impedance value. If voltage starts rapidly decreasing, this indicates that stray capacitance is being discharged through the contact input. If, however, voltage stabilizes above the set threshold, the input impedance is switched to High impedance mode of 100 K Ohms. This value reduces the input current to <3 mA, and contact input switched to the ON state (operated state).
The figure shows the active impedance contact input V-I characteristic. Different thresholds with their corresponding char­acteristics are shown by color. The contact input is in the ON (operated) state if the input voltage is to the right of the col­ored threshold band (+/-10% tolerance), and the contact input is in the OFF (non-activated) state when input voltage is to the left of the band. A contact input is in LOW state during non-operated system condition, and actively switches to HIGH state upon detection of input voltage above the settable threshold.
3
GE Multilin F60 Feeder Protection System 3-25
Page 88
3
3.2 WIRING 3 HARDWARE
Figure 3–24: ACTIVE IMPEDANCE CONTACT INPUT V-I CHARACTERISTIC

3.2.7 TRANSDUCER INPUTS/OUTPUTS

Transducer input modules can receive input signals from external DCmA output transducers (DCmA In) or resistance tem­perature detectors (RTDs). Hardware and software are provided to receive signals from these external transducers and convert these signals into a digital format for use as required.
Transducer output modules provide DC current outputs in several standard DCmA ranges. Software is provided to config­ure virtually any analog quantity used in the relay to drive the analog outputs.
Every transducer input/output module has a total of 24 terminal connections. These connections are arranged as three ter­minals per row with a total of eight rows. A given row can be used for either inputs or outputs, with terminals in column "a" having positive polarity and terminals in column "c" having negative polarity. Since an entire row is used for a single input/ output channel, the name of the channel is assigned using the module slot position and row number.
Each module also requires that a connection from an external ground bus be made to terminal 8b. The current outputs require a twisted-pair shielded cable, where the shield is grounded at one end only. The following figure illustrates the trans­ducer module types (5A, 5C, 5D, 5E, and 5F) and channel arrangements that can be ordered for the relay.
Wherever a tilde “~” symbol appears, substitute with the slot position of the module.
3-26 F60 Feeder Protection System GE Multilin
Page 89
3 HARDWARE 3.2 WIRING
842764A1.CDR
3
Figure 3–25: TRANSDUCER INPUT/OUTPUT MODULE WIRING
The following figure show how to connect RTDs.
GE Multilin F60 Feeder Protection System 3-27
Page 90
3
Three-wire shielded cable
RTD terminals
Maximum total lead resistance: 25 ohms for Platinum RTDs
Route cable in separate conduit from current carrying conductors
RTD
859736A1.CDR
RTD terminals
RTD
RTD
For RTD
RTD
SURGE
~1
~1 &
~2
~2
~8b
~1a
~1b
~2a
Hot
Hot
Return
Comp
Comp
~2c
~1c
NOTE
3.2 WIRING 3 HARDWARE
Figure 3–26: RTD CONNECTION

3.2.8 RS232 FACEPLATE PORT

A 9-pin RS232C serial port is located on the F60 faceplate for programming with a computer. All that is required to use this interface is a computer running the EnerVista UR Setup software provided with the relay. Cabling for the RS232 port is shown in the following figure for both 9-pin and 25-pin connectors.
The baud rate for this port is fixed at 19200 bps.
Figure 3–27: RS232 FACEPLATE PORT CONNECTION
3-28 F60 Feeder Protection System GE Multilin
Page 91
3 HARDWARE 3.2 WIRING
NOTE
842722A3.CDR
100Base-T
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
IRIG-B
input
CPU V
Co-axial cable
Shielded twisted-pairs
Ground at
remote
device
RS485 COM2
100Base-T
100Base-T
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
IRIG-B
input
CPU U
Co-axial cable
Shielded twisted-pairs
Ground at
remote
device
RS485 COM2
100Base-T
100Base-FX
Port 1
Port 2
100Base-FX
Tx1
Rx1
COMMON
+
+
D1a D2a D3a D4b D4a
BNC
IRIG-B
input
CPU T
Co-axial cable
Shielded twisted-pairs
MM fiber-
optic cable
Ground at
remote
device
RS485 COM2
100Base-FX
100Base-FX
Tx2
Rx2
Tx3
Rx3
Tx1
Rx1
Port 3
Port 1
Port 2
Port 3
Port 1
Port 2
Port 3
100Base-FX
Tx1
Rx1

3.2.9 CPU COMMUNICATION PORTS

a) OVERVIEW
In addition to the faceplate RS232 port, the F60 provides a rear RS485 communication port.
The CPU modules do not require a surge ground connection.
3
b) RS485 PORTS
RS485 data transmission and reception are accomplished over a single twisted pair with transmit and receive data alternat­ing over the same two wires. Through the use of the port, continuous monitoring and control from a remote computer, SCADA system, or PLC is possible.
Figure 3–28: CPU MODULE COMMUNICATIONS WIRING
To minimize errors from noise, the use of shielded twisted pair wire is recommended. Correct polarity must also be observed. For instance, the relays must be connected with all RS485 “+” terminals connected together, and all RS485 “–” terminals connected together. Though data is transmitted over a two-wire twisted pair, all RS485 devices require a shared reference, or common voltage. This common voltage is implied to be a power supply common. Some systems allow the shield (drain wire) to be used as common wire and to connect directly to the F60 COM terminal (#3); others function cor­rectly only if the common wire is connected to the F60 COM terminal, but insulated from the shield.
GE Multilin F60 Feeder Protection System 3-29
Page 92
3.2 WIRING 3 HARDWARE
SCADA / PLC / computer
Optocoupler
Data
UR-series device
Shield
827757AA.CDR
Last device
Z (*)
T
Z (*) Terminating impedance at
T
each end (typically 120 Ω and 1 nF)
Twisted pair
RS485 +
RS485 –
COMP 485COM
Relay
Relay
Ground shield at SCADA / PLC /
computer only or at
UR-series device only
Data
Optocoupler
Up to 32 devices,
maximum 4000 feet
(1200 m)
Z (*)
T
RS485 +
RS485 –
COMP 485COM
RS485 + RS485 –
COMP 485COM
COM
To avoid loop currents, ground the shield at only one point. If other system considerations require the shield to be grounded at more than one point, install resistors (typically 100 ohms) between the shield and ground at each grounding point. Each relay needs to be daisy-chained to the next one in the link. A maximum of 32 relays can be connected in this manner with­out exceeding driver capability. For larger systems, additional serial channels must be added. It is also possible to use com­mercially available repeaters to have more than 32 relays on a single channel. Avoid star or stub connections entirely.
Lightning strikes and ground surge currents can cause large momentary voltage differences between remote ends of the communication link. For this reason, surge protection devices are internally provided at both communication ports. An iso­lated power supply with an optocoupled data interface also acts to reduce noise coupling. To ensure maximum reliability, all equipment should have similar transient protection devices installed.
Terminate both ends of the RS485 circuit with an impedance as shown below.
3
c) 100BASE-FX FIBER OPTIC PORTS
Ensure that the dust covers are installed when the fiber is not in use. Dirty or scratched connectors can lead to high losses on a fiber link.
The fiber optic communication ports allow for fast and efficient communications between relays at 100 Mbps. Optical fiber can be connected to the relay supporting a wavelength of 1310 nm in multi-mode.
3-30 F60 Feeder Protection System GE Multilin
Figure 3–29: RS485 SERIAL CONNECTION
Page 93
3 HARDWARE 3.2 WIRING
UR-series device
BNC (in)
Receiver
RG58/59 coaxial cable
GPS satellite system
GPS connection
IRIG-B (–)
4A
+
827756A8.CDR
IRIG-B time code generator
(DC-shift or amplitude modulated signal can be used)
4B
IRIG-B (+)
UR-series device
BNC (in)
Receiver
Twisted-pair cable
GPS satellite system
GPS connection
IRIG-B (–)
4A
+
IRIG-B time code generator
(DC-shift or amplitude modulated signal can be used)
4B
IRIG-B (+)
NOTE

3.2.10 IRIG-B

IRIG-B is a standard time code format that allows stamping of events to be synchronized among connected devices. The IRIG-B code allows time accuracies of up to 100 ns. Using the IRIG-B input, the F60 operates an internal oscillator with 1 µs resolution and accuracy. The IRIG time code formats are serial, pulse width-modulated codes that can be either DC level shifted or amplitude modulated (AM). The GE MultiSync 100 1588 GPS Clock as well as third-party equipment are available for generating the IRIG-B signal; this equipment can use a global positioning system (GPS) satellite system to obtain the time reference so that devices at different geographic locations can be synchronized.
3
Figure 3–30: OPTIONS FOR THE IRIG-B CONNECTION
Using an amplitude modulated receiver causes errors up to 1 ms in event time-stamping. The F60 is intended for use with external clocks that set the IRIG-B control bits according to IEEE Std C37.118.1-
2011. When used with a source that sets the IRIG-B control bits according to IEEE Std 1344-1995, the source must have the sign of its local time offset setting reversed, and if daylight savings time (DST) is used, the source's DST start and DST stop date settings must be interchanged.
GE Multilin F60 Feeder Protection System 3-31
Page 94
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
842006A2.CDR
Tx
Tx
Tx
Tx
UR 1
UR 2
UR 3
UR 4
Rx
Rx
Rx
Rx
MUX
842236A1.CDR
Tx2
UR 1
Rx2
Tx2
UR 2
Rx2
UR 3
MUX
Tx1
Rx1
Tx1
Rx1
UR 4
MUX
MUX
Tx1
Rx1
Tx2
Rx2
MUX
Tx2
MUX
Rx2
MUX
MUX
Tx1
Rx1

3.3DIRECT INPUT/OUTPUT COMMUNICATIONS 3.3.1 DESCRIPTION

The direct inputs and outputs feature makes use of the type 7 series of communications modules, which allow direct mes­saging between UR devices. These communications modules are outlined in the table later in this section.
The communications channels are normally connected in a ring configuration as shown in the following figure. The trans­mitter of one module is connected to the receiver of the next module. The transmitter of this second module is then con­nected to the receiver of the next module in the ring. This is continued to form a communications ring. The figure illustrates a ring of four UR-series relays with the following connections: UR1-Tx to UR2-Rx, UR2-Tx to UR3-Rx, UR3-Tx to UR4-Rx, and UR4-Tx to UR1-Rx. A maximum of 16 URs can be connected in a single ring
3
Figure 3–31: DIRECT INPUT AND OUTPUT SINGLE CHANNEL CONNECTION
IRC modules with protocol C37.94 and G.703 are designed for back-to-back communication connections, so the ring con­figuration shown in the previous figure does not apply. To establish inter-relay communication in more than two URs, you need to have two channel IRC module and enable DIRECT I/O CHANNEL CROSSOVER function in all relays, as shown in the next figure. This configuration can be expanded to 16 URs, and this configuration does not provide redundancy ring since both channels are made into single ring by the channel crossover function. As per the figure Typical Pin Interconnec­tion between Two G.703 Interfaces later in this chapter, the clock is supplied typically by multiplexer (MUX) and all URs are in Loop Timing Mode. If there is no MUX, then UR1 and UR3 can be in Internal Timing Mode and UR2 and UR4 can be in Loop Timing Mode. That is, connected channels must have opposite timing modes.
Figure 3–32: RING CONFIGURATION FOR C37.94 MODULE (CONCEPT ALSO APPLIES TO G.703)
3-32 F60 Feeder Protection System GE Multilin
Page 95
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
842007A3.CDR
Tx1
UR 1
Tx2
Rx1
Rx2
Tx1
UR 2
Tx2
Rx1
Rx2
Tx1
UR 3
Tx2
Rx1
Rx2
Tx1
UR 4
Tx2
Rx1
Rx2
842013A2.CDR
Channel 1
Channel 2
Tx1
UR 2
Tx2
Rx1
Rx2
Tx
UR 1
Rx
Tx
UR 3
Rx
The interconnection for dual-channel type 7 communications modules is shown as follows. Two channel modules allow for a redundant ring configuration. That is, two rings can be created to provide an additional independent data path. The required connections are: UR1-Tx1 to UR2-Rx1, UR2-Tx1 to UR3-Rx1, UR3-Tx1 to UR4-Rx1, and UR4-Tx1 to UR1-Rx1 for the first ring; and UR1-Tx2 to UR4-Rx2, UR4-Tx2 to UR3-Rx2, UR3-Tx2 to UR2-Rx2, and UR2-Tx2 to UR1-Rx2 for the second ring.
3
Figure 3–33: DIRECT INPUT AND OUTPUT DUAL CHANNEL CONNECTION
The following diagram shows the connection for three UR-series relays using two independent communication channels. UR1 and UR3 have single type 7 communication modules; UR2 has a dual-channel module. The two communication chan­nels can be of different types, depending on the Type 7 modules used. To allow the direct input and output data to cross- over from channel 1 to channel 2 on UR2, the
DIRECT I/O CHANNEL CROSSOVER setting should be “Enabled” on UR2. This
forces UR2 to forward messages received on Rx1 out Tx2, and messages received on Rx2 out Tx1.
Figure 3–34: DIRECT INPUT AND OUTPUT SINGLE/DUAL CHANNEL COMBINATION CONNECTION
The inter-relay communications modules are available with several interfaces and some are outlined here in more detail. Those that apply depend on options purchased. The options are outlined in the Inter-Relay Communications section of the Order Code tables in Chapter 2. All of the fiber modules use ST type connectors.
GE Multilin F60 Feeder Protection System 3-33
Page 96
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
7A, 7B, and
7C modules
7H, 7I, and
7J modules
1 channel 2 channels
Rx1
Rx1
Rx2
Tx1 Tx1
Tx2
831719A3.CDR
1 channel 2 channels
Rx1 Rx1
Rx2
Tx1 Tx1
Tx2
831720A5.CDR
72 and 7D
modules
73 and 7K
modules

3.3.2 FIBER: LED AND ELED TRANSMITTERS

The following figure shows the configuration for the 7A, 7B, 7C, 7H, 7I, and 7J fiber-only modules.
3
Figure 3–35: LED AND ELED FIBER MODULES

3.3.3 FIBER-LASER TRANSMITTERS

The following figure shows the configuration for the 72, 73, 7D, and 7K fiber-laser modules.
Figure 3–36: 7X LASER FIBER MODULES
3-34 F60 Feeder Protection System GE Multilin
Page 97
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
2 channels
Tx1
Tx2
Rx1
Rx2
831827A1.CDR
2I and 2J
modules
CAUTION
NOTICE
The following figure shows configuration for the 2I and 2J fiber-laser module.
Figure 3–37: 2I AND 2J LASER FIBER MODULE
Observing any fiber transmitter output can injure the eye.
When using a laser Interface, attenuators can be necessary to ensure that you do not exceed the maximum optical input power to the receiver.
3
GE Multilin F60 Feeder Protection System 3-35
Page 98
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
842773A3.CDR
~8a ~8b
7S
Rx +
Tx +
Shield Tx –
Shield
Rx –
Tx –
Rx +
Tx +
Rx –
G.703 communications
~2b
~6a
~7a
~1b
~1a
~3a
~6b
~7b
~2a
~3b
G.703 channel 2
G.703 channel 1
Surge
Surge
X8a X8b
7S
Rx +
Tx +
Shield Tx –
Shield
Rx –
Tx –
Rx +
Tx +
Rx –
G.703 communications
X2b
X6a
X7a
X1b
X1a
X3a
X6b
X7b
X2a
X3b
G.703 channel 2
G.703 channel 1
Surge
Surge
831727A5.CDR
X8a X8b
7S
Rx +
Tx +
Shield Tx –
Shield
Rx –
Tx –
Rx +
Tx +
Rx –
G.703 communications
X2b
X6a
X7a
X1b
X1a
X3a
X6b
X7b
X2a
X3b
G.703 channel 2
G.703 channel 1
Surge
Surge
NOTE

3.3.4 G.703 INTERFACE

a) DESCRIPTION
The following figure shows the 64K ITU G.703 co-directional interface configuration.
The G.703 module is fixed at 64 kbps. The SETTINGS > PRODUCT SETUP > DIRECT I/O > DIRECT I/O DATA RATE setting is not applicable to this module.
AWG 24
twisted shielded pair is recommended for external connections, with the shield grounded only at one end. Con-
necting the shield to pin X1a or X6a grounds the shield since these pins are internally connected to ground. Thus, if pin X1a or X6a is used to ground the shield at one end, do not ground the shield at the other end. This interface module is protected by surge suppression devices.
3
Figure 3–38: G.703 INTERFACE CONFIGURATION
The following figure shows the typical pin interconnection between two G.703 interfaces. For the actual physical arrange­ment of these pins, see the Rear Terminal Layout section earlier in this chapter. All pin interconnections are to be main­tained for a connection to a multiplexer.
b) G.703 SELECTION SWITCH PROCEDURES
1. With the power to the relay off, remove the G.703 module (7R or 7S) as follows. Record the original location of the
2. Simultaneously pull the ejector/inserter clips located at the top and at the bottom of each module in order to release the
3. Remove the module cover screw.
4. Remove the top cover by sliding it towards the rear and then lift it upwards.
5. Set the timing selection switches (channel 1, channel 2) to the desired timing modes.
3-36 F60 Feeder Protection System GE Multilin
Figure 3–39: TYPICAL PIN INTERCONNECTION BETWEEN TWO G.703 INTERFACES
Pin nomenclature can differ from one manufacturer to another. Therefore, it is not uncommon to see pinouts num­bered TxA, TxB, RxA and RxB. In such cases, it can be assumed that “A” is equivalent to “+” and “B” is equivalent to “–”.
module to help ensure that the same or replacement module is inserted into the correct slot.
module for removal.
Page 99
3 HARDWARE 3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS
Cover screw
Top cover
Bottom cover
Ejector/inserter clip
Ejector/inserter clip
Timing selection
switches
Channel 1
Channel 2
FRONT
REAR
831774A3.CDR
6. Replace the top cover and the cover screw.
7. Re-insert the G.703 module. Take care to ensure that the correct module type is inserted into the correct slot position.
The ejector/inserter clips located at the top and at the bottom of each module must be in the disengaged position as the module is smoothly inserted into the slot. Once the clips have cleared the raised edge of the chassis, engage the clips simultaneously. When the clips have locked into position, the module is fully inserted.
3
Figure 3–40: G.703 TIMING SELECTION SWITCH SETTING
Table 3–5: G.703 TIMING SELECTIONS
SWITCHES FUNCTION
S1 OFF octet timing disabled
S5 and S6 S5 = OFF and S6 = OFF loop timing mode
c) G.703 OCTET TIMING
ON octet timing 8 kHz
S5 = ON and S6 = OFF internal timing mode S5 = OFF and S6 = ON → minimum remote loopback mode S5 = ON and S6 = ON dual loopback mode
If octet timing is enabled (ON), this 8 kHz signal is asserted during the violation of bit 8 (LSB) necessary for connecting to higher order systems. When F60s are connected back-to-back, octet timing is disabled (OFF).
d) G.703 TIMING MODES
There are two timing modes for the G.703 module: internal timing mode and loop timing mode (default).
Internal Timing Mode: The system clock is generated internally. Therefore, the G.703 timing selection should be in
the internal timing mode for back-to-back (UR-to-UR) connections. For back-to-back connections, set for octet timing (S1 = OFF) and timing mode to internal timing (S5 = ON and S6 = OFF).
Loop Timing Mode: The system clock is derived from the received line signal. Therefore, the G.703 timing selection
should be in loop timing mode for connections to higher order systems. For connection to a higher order system (UR-
GE Multilin F60 Feeder Protection System 3-37
Page 100
3.3 DIRECT INPUT/OUTPUT COMMUNICATIONS 3 HARDWARE
842752A2.CDR
Internal timing mode
Loop timing mode
(factory default)
DMR
DMX
G7X
G7R
DMR = Differential Manchester Receiver DMX = Differential Manchester Transmitter G7X = G.703 Transmitter G7R = G.703 Receiver
842774A1.CDR
DMR
DMX
G7X
G7R
DMR = Differential Manchester Receiver DMX = Differential Manchester Transmitter G7X = G.703 Transmitter G7R = G.703 Receiver
842775A1.CDR
to-multiplexer, factory defaults), set to octet timing (S1 = ON) and set timing mode to loop timing (S5 = OFF and S6 = OFF).
The switch settings for the internal and loop timing modes are shown below:
3
e) G.703 TEST MODES
In minimum remote loopback mode, the multiplexer is enabled to return the data from the external interface without any processing to assist in diagnosing G.703 line-side problems irrespective of clock rate. Data enters from the G.703 inputs, passes through the data stabilization latch which also restores the proper signal polarity, passes through the multiplexer and then returns to the transmitter. The differential received data is processed and passed to the G.703 transmitter module after which point the data is discarded. The G.703 receiver module is fully functional and continues to process data and passes it to the differential Manchester transmitter module. Since timing is returned as it is received, the timing source is expected to be from the G.703 line side of the interface.
In dual loopback mode, the multiplexers are active and the functions of the circuit are divided into two with each receiver/ transmitter pair linked together to deconstruct and then reconstruct their respective signals. Differential Manchester data enters the Differential Manchester receiver module and then is returned to the differential Manchester transmitter module. Likewise, G.703 data enters the G.703 receiver module and is passed through to the G.703 transmitter module to be returned as G.703 data. Because of the complete split in the communications path and because, in each case, the clocks are extracted and reconstructed with the outgoing data, in this mode there must be two independent sources of timing. One source lies on the G.703 line side of the interface while the other lies on the differential Manchester side of the interface.
3-38 F60 Feeder Protection System GE Multilin
Figure 3–41: G.703 MINIMUM REMOTE LOOPBACK MODE
Figure 3–42: G.703 DUAL LOOPBACK MODE
Loading...