Before you begin, be sure you have the following:
Fast and easy on the web:
www.advantech-bb.com
+ Wzzard Intelligent Edge Node + Wire Harness + (2) Lithium Thionyl Chloride AA Batteries + External Antenna + Anti-skid Disk
QUICK START GUIDE
As nodes join the network, they will be added to the device tree under the gateway MAC address.
When all nodes’ MAC addresses show in the tree, click the checkbox next to each node.
Click the “Claim Nodes” button to prevent the nodes from joining another open network.
Congure the Node
Mount the Node
5
6
Refer to the IWzzard Mesh Wireless Sensor user manual for
detailed conguration instructions.
Flange Mounting - Wzzard nodes may be mounted via their mounting ears. (M5, #10)
Magnetic Mounting* - Wzzard nodes contain a powerful, internal mounting magnet in the base of the node – pull force 2.13 kg (4.7 lb) – convenient for temporary position-
ing and conguration of nodes.
Apply the anti-skid disk to the bottom of unit for extra grip.
* Note: UL Class1/Division2 rating does not apply (voided) when using magnetic mounting.
Putting the Node in Deep Sleep
7
When not using the node for some time, the node should be put into deep sleep.
Press the Status/Sleep/Reset conguration button for 5
seconds until the Status LED turns off. The node will retain all settings, including the associated
network if the node has been claimed. It will not reset the device back to factory settings.
Restoring Node to Factory Default
8
To reset the node to factory defaults, press and hold the Status/Sleep/Reset conguration button for 10 seconds until
the Status LED ashes quickly. This will:
1) Clear the sensor type information.
2) Clear the associated network information if the node has been claimed.
3) Allow the node to search for a new network.
Models BB-WSD2C31010, BB-WSD2M31010, BB-WSD2C21150, BB-WSD2C06010, BB-WSD2M06010
for Industrial Applications
Intelligent Edge Node with SmartMesh IP
Wzzard Mesh Wireless Sensor
Review Network & Claim Nodes
4
Follow the SmartSwarm quck start guide to claim and congure the gateway. With the gateway connected to the internet, click on the “Wzzard Mesh” button.
(continued)
IP67
Enclosure
Product Overview
Connect Your Sensor
Wake Up The Node
1
2
Check LEDs
3
After you wake the node, the Status LED will begin to blink. This indicates that the node is attempting to establish a network connection. The Status LED will come on solid when a connection is made.
Note: The Status LED goes off after 10 seconds to conserve battery life. To
check status, use a short press of the Status/Sleep/Reset conguration button.
Status LED
Data
Slow Blink (1 per sec.)
Attempting to establish connection with SmartMesh IP network.
Fast Blink (10 per sec.)
Firmware update in progress.
ON (solid) Unit is connected to wireless network.
MODEL
1
Brown2Red3 Pink4Yellow 5 Green6 Blue7 White8Gray
WSD2C31010 10-30VDC AIN1 AIN2 AIN3 DIN1 GND GND GND
WSD2C21150 10-30VDC AIN1 AIN2 DO1 DIN1 GND GND GND
WSD2C06010 10-30VDC DIN1 DIN2 DIN3 DIN4 DIN5 DIN6 GND
MODEL
1
White2 Brown3Green4Yellow 5Gray6 Pink7Blue8 Red
WSD2M31010 10-30VDC AIN1 AIN2 AIN3 DIN1 GND GND GND
WSD2M06010 10-30VDC DIN1 DIN2 DIN3 DIN4 DIN5 DIN6 GND
Wiring for Conduit Connector Nodes
– with Attached Wiring Harness
Wiring for M12 Connector Nodes*
– with M12 Accessory Cable (from B+B SmartWorx)
Wiring Chart Abbreviations:
10-30V = 10 -30V DC Power Input AINx = Analog Input #x DINx = Digital Input #x GND = Ground Input
Wiring Chart Abbreviations:
10-30V = 10 -30V DC Power Input AINx = Analog Input #x DINx = Digital Input #x DOx = Digit al Output #x GND = Ground Input
* Note: UL Class1/Division2 rating is voided when using M12 model outdoors.
Status
LED
Antenna
Conduit or M12
Conguration
Button
Mounting Flanges
Case
Screws
Internal Magnet
(in the base)
Press and hold Status/Sleep/Reset conguration button
for 5 seconds until the Status LED comes on and begins blinking.
Remove the four (4) black screws that hold the top of the node in place. Connect your sensor.
Tip: It is a best practice that wiring is done prior to installing batteries or powering up the device.
Note: UL C1/D2 rating is voided when using non UL-specied batteries.
Thread the included wire harness through the conduit and into the node. Plug it into the circuit board inside the node.
Conduit Models: Analog & Digital
M12 Models*: Analog & Digital
– with Accessory Cable
You can use your own M12 cable or order B+B SmartWorx accessory cable #BB-WSCAM12-6.
1 White 2 Brown 3 Green 4 Yellow 5 Gray 6 Pink 7 Blue 8 Red
Terminal Block Connections
– Thermocouple & Thermistor
Thread the thermocouple and thermistor wires through the conduit and attach them to the terminal block.
1 Brown 2 Red 3 Pink 4 Yellow 5 Green 6 Blue 7 White 8 Gray
Connect your sensor to the wires running from the node’s conduit. Consult the following chart for wiring instructions.
Consult the following chart for wiring instructions.
M12 Accessory Cable Detail
#BB-WSCAM12-6 (from B+B SmartWorx)
UL Class 1, Division 2 Notications and Warnings
Conduit Models Only
Model Numbers BB-WSD2C31010, BB-WSD2C21150, BB-WSD2C06010:
10
Radio Equipment Directive
(RED) Statement
9
Hereby, B+B SmartWorx, Inc. declares that the radio equipment type “Wzzard Wireless Mesh” is in compliance with Directive 2014/53/EU.
The complete CE Declaration of Conformity is available at:
https://support.advantech-bb.com/
Keywords, enter [model number]
Material Type, select Reference Click Search
SUITABLE FOR USE IN CLASS I, DIVISION 2, GROUPS A, B, C AND D HAZARDOUS LOCATIONS, OR NONHAZARDOUS LOCATIONS ONLY.
CONVENANT À L’EMPLOI DANS LES SITES DANGEREUX DE CLASSE I, DIVISION 2, GROUPES A, B, C ET D, OU DANS LES SITES NON HASARDEUX SEULEMENT
WARNING - EXPLOSION HAZARD - DO NOT DISCONNECT EQUIPMENT WHILE THE CIRCUIT IS LIVE OR UNLESS THE AREA IS KNOW TO BE FREE OF IGNITABLE CONCENTRATIONS.
ATTENTION - RISQUE D’EXPLOSION - NE PAS DÉCONNECTER L’ÉQUIPEMENT PENDANT QUE LE CIRCUIT EST VIVANT OU À MOINS QUE LA ZONE NE SAIT ÊTRE EXEMPTE DE CONCENTRATIONS IGNIFIABLES.
For M12 Model Numbers
BB-WSD2M31010, BB-WSD2M06010:
THIS EQUIPMENT IS TO BE INSTALLED IN AN ENCLOSURE SUITABLE FOR THE ENVIRONMENT THAT IS ONLY ACCESSIBLE WITH THE USE OF A TOOL.
CET ÉQUIPEMENT DOIT ÊTRE INSTALLÉ DANS UNE ENCEINTE ADAPTÉE À L’ENVIRONNEMENT QUI N’EST ACCESSIBLE QUE POUR L’UTILISATION D’UN OUTIL.
The unit is to be connected to a Class 2 power source via the terminal block.
L’unité doit être connectée à une source d’alimentation de classe 2 via le bornier.
These products must use only the following batteries: either Model XL-060F manufactured by XENO Energy co LTD. Or Model ER14505 manufactured by EVE. Please be advised of the following warning statement regarding battery replacement.
Ces produits utilisent les batteries suivantes: soit le modèle XL-060F fabriqué par XENO Energy co LTD. Ou Modèle ER14505 fabriqué par EVE. Veuillez prendre connaissance de l’avertissement suivant concernant le remplacement de la batterie.
WARNING: Risk of Fire and Burns. Do Not Recharge,
Open, Crush, Heat Above 100˚C, Or Incinerate the
batteries. Batteries are not user replaceable, only
a qualied technician should replace the batteries.
Do not mix battery types, Do not mix old and new batteries” or similar shall be included on the device or accompanying documentation.
ATTENTION: Risque d’incendie et de brûlures. Ne pas recharger, ouvrir, écraser, chauffer au-dessus de 100 °C, ou incinérer les batteries. Les piles ne sont pas remplaçables par l’utilisateur, seul un technicien
qualié doit remplacer les piles. Ne pas mélanger
les types de piles. Ne pas mélanger les anciennes et les nouvelles piles “ou similaires sur l’appareil ou la documentation qui l’accompagne.
Torque value of 5 to 8 lb-in for screws used to secure the cover to main housing must be included in accompanying documentation.
Une valeur de couple de 5 à 8 lb-in pour les vis utilisées
pour xer le couvercle au boîtier principal doit être
incluse dans la documentation d’accompagnement.
WSD2C devices are suitable for use in a Type 3 (outdoor) environment. WSD2M devices (with M12 connector) are suitable or use in a Type 1 environment and must be used in a suitable enclosure.
Les appareils WSD2C peuvent être utilisés dans un environnement de type 3 (extérieur). Les appareils WSD2M (avec connecteur M12) conviennent ou sont utilisés dans un environnement de type 1 et doivent être
utilisés dans un boîtier approprié.
Operating temperature code for these products is T5.
Le code de température de fonctionnement pour ces produits est T5.
See User Manual for information that is provided separately.
Voir le manuel de l’utilisateur pour des informations fournies séparément.
UL Class1/Division2 Applications
B+B SmartWorx Product Exceptions Summary
UL C1/D2 rating is voided when using M12 model outdoors.
UL C1/D2 rating is voided if magnetic mounting is used for permanent installation.
UL C1/D2 rating is voided when using non UL-specied
batteries. Do not mix old and new batteries.