B+B Sensors N321 Operation Manual

OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
DescriptionDescription
Content
1. Product Description 05
1.1. Scope of delivery 04
1.2. Variations 04
1.3. Identication 04
1.4. Description of the buttons on the front of the Controller 05
1.5. Terminals 05
2. Operations 05
2.1. Level 1 - Setpoint Adjustment 06
2.2. Level 2 - Conguration - Parameters conguration Level 06
2.3. Level 3 - Calibration level 07
3. Working with the controller 07
3.1. Conguration Protection 07
3.2. Conguration Protection Usage 08
3.3. The Master-Password 08
4. Error messages 08
5. Electrical wiring 08
6. Technical data 09 Questions 09
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
1 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
Foreword
Dear customer,
We thank you for having purchased the controller N321 and we are very glad that you decided to buy a product of B+B Thermo-Technik GmbH. We hope this product will fully satisfy you and will assist you effectively in your work. This Device has been developed to be technically highly up-to-date and has been designed in accordance with the regnant European and German national directives and rules. For a proper and effective usage of the product the customer shall observe the following Operating Instructions. In the case that against one’s expectations any trouble occurs which you can not resolve yourself, please contact our service centers or our authorized dealer. We will provide you rapid and competent help to minimize the risk of long time outfalls.
The following operating Instruction is an indispensable part of this Product. It contains important advices for the starting up and further use of the device.
General information
This Operation Manual is intended to serve as an aid in the proper setup, installation and operating of the B+B product.
All essential details of the equipment and all actions required on the part are clearly presented and explained. We thus ask that you read this manual carefully before proceeding to work with the equipment. Keep this manual available for ready reference in a convenient and conspicuous location near the equipment.
Symbols employed
Sign Meaning Notice
Advice
It is necessary to read the following advices before using the product. The used symbols in the manual
acts rst of all as eye catcher for security risks. The symbols do not replace the security advices. The text
must be read completely.
Necessarily to observe
This symbol designates important advices and tips which are necessary for the success of a procedure. They have to be followed in order to get good results.
Warning signs
Sign Meaning
This symbol advises the user of danger for persons, material or environment. The text gives information that must be necessarily followed to avoid any risks
Caution against hot surfaces (BGV A8, GUV-V A8/W26) and hot liquids or substances
Caution against liquids and hot substances
Caution against dangerous explosive substances (BGV A8, GUV-V A8/W02)
Caution against moving maschines (W29) Caution against moving parts
Caution against electromagnetic elds (BGV A8, GUV-V A8/W12)
Caution against severe cold (BGV A8, GUV-V A8/W17ice
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
2 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
Caution against dangerous high electrical voltage (BGV A8, GUV-V A8/W08)
Caution against dangerous explosive atmosphere (BGV A8, GUV-V A8/W21)
Electronic waste
Safety instructions
For damages caused by failure to observe these safety and operating instructions, takes over the B + B Thermo-Technik GmbH is not liable.
This device has been designed and tested in accordance to the safety regulations for electronic devices. However, its trouble-free operation and reliability cannot be guaranteed unless the standard safety measures and special safety advises given in this manual will be adhered to when using it.
Trouble-free operation and reliability of the device can only be guaranteed if it is not subjected to any other climatic conditions than those
stated under “Specication”.
If the device is transported from a cold to a warm environment condensation may result in a failure of the function. In such a case make sure the device temperature has adjusted to the ambient temperature before trying a new start-up.
If device is to be connected to other devices the circuitry has to be designed most carefully. Internal connection in third party devices (e.g. connection GND and earth) may result in not-permissible voltages impairing or destroying the device or another device connected.
Warning:
Only devices with mains input: If device is operated with a defective mains power supply (e.g. short circuit from mains voltage to output volt­age) this may result in hazardous voltages at the device (e.g. at sensor socket) . If there is a risk whatsoever involved in running it, the device has to be switched off immediately and to be marked accordingly to avoid re­starting. Operator safety may be at risk if:
● there is visible damage to the device
the device is not working as specied
● the device has been stored under unsuitable conditions for a longer time
In case of doubt, please return device to manufacturer for repair or maintenance.
Caution:
Do not use these product as safety or emergency stop devices, or in any other application where failure of the product could result in per­sonal injury or material damage. Failure to comply with these instructions could result in death or serious injury and material damage.
Intended Use
The use of the unit in elds other than those indicated under “SAFETY INSTRUCTIONS” is not allowed for safety reasons.
This instruction manual does not at all substitute any additional instruction manual of connected accessoriy!
Disposal
This unit has been marked in accordance with the European Device 2002/96/EC on waste electrical and electronic equipment (WEEE) At the end of its operating life-time, dispose of the unit as electrical scrap. Please ask either B+B Thermo-Technik GmbH or your specialist dealer for information on your local collection point.
Within the scope of application of this Directive, B+B Thermo-Technik GmbH is responsible for proper disposal of this unit.
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
3 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
1. Product description
The Controller N321 is a temperature controller to measure, display and control of temperature. It can be used various types of sensors: Pt1000, Pt100, NTC and thermocouples type K, J and T. The controller can be easily programmed for the application by the user. (cooling or heating). The internal 10 A relay can be used to control of refrigeration compressors or heaters with on / off function. An offset correction of the sensor is provided. The output can be used as control or alarm. The characteristics of the model (sensor-type, sensor-range, power, etc.) can be found on the label located on the controller housing.
2. Scope of delivery
Articlename Articleno. Description
Controller N321 0556 0108 xxx 1 x Controller N321, 1x User Manual
1.2. Variations
Articlename Articleno.
Controller N321 for Pt1000 0556 0108
Controller N321 for NTC 10K incl. Probe (-50 to +120°C)* 0556 0108-01
Controller N321 for Pt100 0556 0108-02
Controller N321 for Thermoelement J, K und T 0556 0108-03
Controller N321 2 x NTC 10K incl. Probe (-50 to +120°C)* 0556 0108-04
1.3. Identication
The rating plate is located on the housing of the data logger. Verify that the properties described the same as your job. The following controls can be found on the front page of the data logger.
Programming keys
Display
Messages
*0556 0108-01 and 0556 0108-04 incl. NTC 10K Probe
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
4 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
1.4. Description of the buttons on the front of the Controller
1.5. Terminals
The gure below shows the controller connections to sensor, main and outputs.
Pt100 with 3 conductors: Terminals 11, 12 and 13 must have the same wire resistance for proper cable length compensation. For 2 wire Pt100, short circuit terminals 12 and 13.
2. Operations
The controller requires the internal parameters to be congured according to the intended use for the instrument.
The parameters are organized in 4 groups or levels:
Level Function
0 Temperature measurement
1 Setpoint adjustment
2 Conguration
3 Calibration
Upon power-up, the N321 display shows for 1 second its rmware version. This information is useful when consulting the
factory. Then, the temperature measured by the sensor is shown on the display. This is the parameter level 0 (temperature measurement level).
To access level 1, press
for 1 second until the “SP1” message shows up. Pressing again to go back to level 0.
To access level 2 of paramenters, press
for 2 seconds until the “uNT” message is shown. Release the key to
remain in this level. Each new pressing on the
key will advance to the next parameter in the level. At the end of the level,
the controller returns to the rst level (0). Use the
and keys to alter a parameter value.
Notes:
1. A parameter conguration is saved when the
key is pressed to advance to the next parameter in the cycle.
The conguration is stored in a non-volatile memory, retaining its value when the controller is de-energized.
2. If no programm key is detected for over 20 seconds, the controller saves the current parameter value and returns to the measurement level.
Programm-key (P)
Back-key (R)
Up-key
Down-key
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
5 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
2.1. Level 1 - Setpoint Adjustment
In this level only the Setpoint (SP) parameter is available, alternating the name with its respective value. Adjust the desired temperature for setpoint by clicking on the
and keys.
Level Function
SP (Set Point) Temperature adjustment for control OUTPUT 1. SP value is limited to the values programmed in SPL and SPk in the
programming level (Parameter conguration, level 2).
2.2. Level 2 - Conguration - Parameters conguration Level
Contains the conguration parameters to be dened by the user, according to the system’s requirements.
Use
and keys to set the value. The display alternates the parameter name and respective value.
Level Function
Unt
Temperature Unit: Selects display indication for degrees Celsius or Fahrenheit.
0 - Temperature in degrees Celsius 1 - Temperature in degrees Fahrenheit
typ
Input Type: Selects the input sensor type to be connected to the controller. Available only for thermocouple models, al­lowing selection of types J, K and T.
0 - Thermocouple type J 1 - Thermocouple type K 2 - Thermocouple type T
ofs
Sensor Offset: Offset value to be added to the measured temperature to compensate sensor error.
spl SP Low Limit: Lower range for SP. spl must be programmed with a lower value than SPH.
SPH SP High Limit: Upper range for SP. SPH must be greater than SPL.
Hy1
OUTPUT 1 Hysteresis: Denes the differential range between the temperature value at which the
OUTPUT 1 is turned on and the value at which it is turned off. (In degrees).
Ac1
Control action for OUTPUT 1:
0 - Reverse: For heating applications. Outputs turn on when temperature is lower than SP. 1 - Direct: For cooling applications. Output turns on when temperature is above SP.
of1 (Off time)
Off time: Denes the minimum off time for control OUTPUT 1. Once OUTPUT 1 is turned off, it remains so for at least the
time programmed in oft. For thermocouple inputs this parameter is not available. This parameter is intended for refrigera­tion systems where longer compressor life is desired. For heating systems, program of1 to zero. Value in seconds, 0 to 999 s.
on1 (On time)
On time: Denes the minimum on time for control OUTPUT 1. Once turned on, OUTPUT 1 remains so for at least
the time programmed in on1. For thermocouple inputs this parameter is not available. This parameter is intended for refrigeration systems where increased compressor life is desired. For heating systems, program on1 to zero. Value in seconds, 0 to 999 s.
dl1 (Delay 1)
Delay time to start control: Upon power-on, control OUTPUT 1 is kept off until the time programmed in dl1 is elapsed. Its usage is intended to prevent multiple compressors to start simultaneouly after the turn-on of a system with several controllers. Value in seconds, 0 to 250 s.
Add (Adress)
Adress: Controllers with the optional RS485 Modbus RTU communication interface have the Add parameter at the Conguration level. Set a unique Modbus address for each equipment connected to the network. Address range is from 1
to 247.
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
6 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
2.3. Level 3 - Calibration Level
The controller is factory calibrated. The following parameters should be accessed only by experienced personnel. To enter this cycle, the
key must be kept pressed for 4 seconds.
Don’t press the
and keys if you are not sure of the calibration procedures. Just press the key a few times until the
temperature measurement level is reached again.
Level Function
PAS
Password: Enter the correct password to unlock write operations for the parameters in the following levels.
CAL
Calibration low: Offset value of the input. It adjusts the lower measurement range of the sensor.
CAH
Calibration High: Gain calibration. It adjusts the upper measurement range of the sensor.
CJL
Cold Junction Offset calibration: This parameter is available only for thermocouple.
FAC
Factory Calibration: Restores factory calibration parameters. Change from 0 to 1 to restore the calibration param­eters with factory values.
Prt
Protection: Denes the levels of parameters that will be password protected. See „Conguration
Protection“ for details.
PAC
Password Change: Allows changing the current password to a new one. Values from 1 to 999 are allowed.
Sn2
Serial number: First part of the controller electronic serial number.
Sn1
Serial number: Second part of the controller electronic serial number.
Sn0
Serial number: Third part of the controller electronic serial number.
3. Working with the Controller
The Controller N321 energizes the output relay such as to maintain the process temperature on the setpoint value
dened by the user. The output status led P1 signals when the control output is on.
3.1. Conguration Protection
A protection system to avoid unwanted changes to the controller parameters is implemented. The level of protection can be selected from partial to full. The following parameters are part of the protection system:
Pas: When this parameter is presented, the correct password should be entered to allow changes of parameters in the following levels.
Prt: Denes the level of parameters that will be password protected:
1. Only calibration level is protected (factory conguration);
2. Calibration and Conguration levels are protected;
3. All levels are protected: Calibration, conguration and setpoints. PAC: Parameter to dene a new password. The password is located in the calibration level, and can only be changed by a user that knows the current password. Valid passwords are in the range 1 to 999.
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
7 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
3.2. Conguration Protection Usage
PAS -parameter: PAS -parameter is displayed before entering a protected level. If the correct password is entered, parameters in all following
levels can be changed. If a wrong or no password is entered, parameters in the following levels will be read only.
Important notes:
1. After ve consecutive attempts to enter a wrong password, new tentative will be blocked for the next 10 minutes. If the current valid password is unknown, the master password can be used only to dene a new password for the controller.
2. The password for a brand new device is 111.
3.3. Master-Password
The master password allows user to dene a new password for the controller, even if the current password is unknown. The
master password is based on the serial number of the controller, and calculated as following:
[ 1 ] + [ higher digit of SN2 ] + [ higher digit of SN1 ] + [ higher digit of SN0 ] for example the master password for the device with serial number 987123465 is: 1 9 3 6 as follows: 1 + sn2 = 987; sn1 = 123; sn0 = 465 = 1 + 9 + 3 + 6
How to use the master password:
1. Enter the master password value at „PaS“ prompt.
2. Go to PA( parameter and enter the new password, which must not be zero (0).
3. Now you can use this new password to access all controller parameters with modify rights.
4. Error Messages
Sensor measurement errors force the controller outputs to be turned off. The cause for these errors may have origin in a bad connection, sensor defect (cable or element) or system temperature outside the sensor working range. The display signs related to measurement errors are shown below:
5. Electrical Wiring
It is important to follow the recommendations below:
Signal wires should be installed in grounded conduits and away from power or contactor wires.
The instrument should have its own power supply wires that should not be shared with electrical motors,
coils, contactors, etc.
Installing RC lters (47 R and 100 nF, series combination) is strongly recommended at contactor coils or any
other inductors.
System failure should always be taken into account when designing a control panel to avoid irreversible damage
to equipment or people.
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
8 / 9
OPERATION MANUAL
Technical changes reserved
0141 0315-150 29.06.2016
Controller N321
6. Technical Data
Properties Values
Input Sensor Thermocouples J, K, T, Pt100, Pt1000 and NTC
Note: In the controller with NTC input, a 3 m sensor-cable is bundled with the controller. The cable can be extended up to 200 m
Measuring range J 0 to 600°C (32 to 1400°F)
K -50 to 1000°C (-58 to 1832°F) T -50 to 400°C (-58 to 752°F) Pt100 -50 to 300°C (-58 to 572°F) Pt1000 -200 to 530°C (-328 to 986°F)
Accuracy Thermocouples J, K and T: ±3°C (±5.4°F)
Pt100: ±0,7°C (±1,3°F) Pt1000: ±0,7°C (±1,3°F)
Resolution from -19.9 to 199.9°C display units with NTC, Pt100 and Pt1000 = 0.1
from -19.9 to 199.9°C display units with Thermocouples = 1
Output 1 Relay SPDT, 1 HP 250 V AC / 1/3 HP 125 V AC (16 A Resistive)
Power supply 100 - 240 V AC (± 10%) or 24 V AC/DC
Mains frequency: 50-60 Hz, Power consumption: 5 VA
Caution: Check the power supply specication before energizing the controller
Environment Operating temperature: 0 to 40°C (32 to 122°F)
Storage temperature: -20 to 60°C (-4 to 140°F)
Relative humidity: 20 to 85%, non condensing
Case Polycarbonate UL94, V-2, Suitable wiring: up to 4,0 mm
2
Ingress Protection Front panel: IP65, Box IP42
Dimensions 74 x 32 x 75 mm
Warm-Up 15 minutes
CE-Conformance EN 61326-1 according to 2014/30/EU
RS485 digital communication; RTU MODBUS protocol (optional)
Serial interface not isolated from input circuitry. Serial interface isolated from input circuitry, except in 24 V powered model
Questions
If you still have questions concerning this product of B+B Thermo-Technik GmbH, please do not hesitate to contact us at:
B+B Thermo-Technik GmbH Tel.: +49 771 83160 Heinrich-Hertz-Straße 4 Fax: +49 771 831650 D-78166 Donaueschingen E-Mail: info@bv-sensors.com Germany www.bb-sensors.com
We wish you a successful measuring!
Your Temperature-Partner
B+B Thermo-Technik GmbH
All technical information in this document are proved by us with high accuracy and shall inform you about all application possibilities. This information are not
conrmed by us and need to be proved by every user in regard to his intended use of the equipment. All foreign trade mark rights need to be considered.
B+B Thermo-Technik GmbH | Heinrich-Hertz-Str. 4 | D-78166 Donaueschingen Fon +49 771 83160 | Fax +49 771 831650 | info@bb-sensors.com | bb-sensors.com
9 / 9